Lighting circuit earth at 120V
Hi all,
The other day I bought a new screwdriver set from B&Q and decided to try it out on the nearest available screw. It turned out to be one of the screws in the light switch in our kitchen. I noticed a strange tingling sensation when I touched the side of the screwdriver... very mysterious... On further investigation it seems that the earth conductors in all of my light switches are at 120V (with respect to neutral or live - tested with multimeter set to AC mode). However at the consumer unit, all appears to be fine. I have a functioning RCD and it's not tripped. All the lights work. No (obvious) dodgy wiring in any of the switches. Before I spend weeks lifting floorboards and crawling around in the loft, can anyone suggest a reason why this might be going on? And is there any way to systematically track down the source of the problem? And why is it at exactly half mains voltage? And, as an aside, could this have anything to do with the fact that my energy-saving lightbulbs seem to flicker every few seconds when switched off? Any advice would be appreciated... my electrical experience is still fairly limited... Thanks Martin |
#2
|
|||
|
|||
Lighting circuit earth at 120V
In article , Martin Brook
writes Hi all, The other day I bought a new screwdriver set from B&Q and decided to try it out on the nearest available screw. It turned out to be one of the screws in the light switch in our kitchen. I noticed a strange tingling sensation when I touched the side of the screwdriver... very mysterious... On further investigation it seems that the earth conductors in all of my light switches are at 120V (with respect to neutral or live - tested with multimeter set to AC mode). However at the consumer unit, all appears to be fine. I have a functioning RCD and it's not tripped. All the lights work. No (obvious) dodgy wiring in any of the switches. Before I spend weeks lifting floorboards and crawling around in the loft, can anyone suggest a reason why this might be going on? And is there any way to systematically track down the source of the problem? And why is it at exactly half mains voltage? And, as an aside, could this have anything to do with the fact that my energy-saving lightbulbs seem to flicker every few seconds when switched off? Any advice would be appreciated... my electrical experience is still fairly limited... Sounds like the earth wire on your lighting circuit is not connected to earth, which is a cause for concern. You often get 120V on a disconnected earth when some type of surge arrestor is connected to the circuit. (It's very very high impedance, so you don't feel a shock when you touch it, just a tingle. If you measured it with an analogue meter rather than a digital one, the voltage would be much lower or would disappear). I am not sure how a surge arrestor would get onto a lighting circuit however, unless there is a wider earthing problem in your house and the surge arrestor equipment is on a ring main; the ring main earth is connected to the lighting earth, but neither is connected to real earth. -- Tim Mitchell |
#3
|
|||
|
|||
Lighting circuit earth at 120V
Martin Brook wrote:
Before I spend weeks lifting floorboards and crawling around in the loft, can anyone suggest a reason why this might be going on? And is there any way to systematically track down the source of the problem? And why is it at exactly half mains voltage? Have you checked to see if all the earths on the other circuits are doing the same thing (even money they are as all earths should be commoned, natch)? If so, then I'd guess you've got a faulty earthed appliance on one of the ring mains. Go round unplugging things while someone keeps an eye on the multimeter. My first stop would be any television sets as although not usually earthed directly, they often have floating chassis (there was a discussion a while back on this) which might be electrifying the aerial cable and, from there, the earth circuit of the house. And, as an aside, could this have anything to do with the fact that my energy-saving lightbulbs seem to flicker every few seconds when switched off? Can't see how as earth is really a non-used connection in lighting ccts. Again, I think this has been discussed before and could be down to the neutral side of the light being switched or a particularly high floating neutral. -- Scott Where are we going and why am I in this handbasket? |
#4
|
|||
|
|||
Lighting circuit earth at 120V
|
#5
|
|||
|
|||
Lighting circuit earth at 120V
Thanks for the reply,
On Thu, 5 Aug 2004 14:46:36 +0100, Tim Mitchell wrote: Sounds like the earth wire on your lighting circuit is not connected to earth, which is a cause for concern. You often get 120V on a disconnected earth when some type of surge arrestor is connected to the circuit. (It's very very high impedance, so you don't feel a shock when you touch it, just a tingle. If you measured it with an analogue meter rather than a digital one, the voltage would be much lower or would disappear). I am not sure how a surge arrestor would get onto a lighting circuit however, unless there is a wider earthing problem in your house and the surge arrestor equipment is on a ring main; the ring main earth is connected to the lighting earth, but neither is connected to real earth. I'm not aware of there being any kind of surge arrestor anywhere... Also, most of the wiring in the house seems to be fine, earth-wise. I've already rewired two ring mains and added a new one, and everything is fine on those. The lighting circuit is the only one I haven't touched, but there is no voltage on the earth at the CU. So it seems to me that the problem must be somewhere in the rest of the circuit. Which, of course, disappears through a hole in the cellar roof. -- Using Opera's revolutionary e-mail client: http://www.opera.com/m2/ |
#6
|
|||
|
|||
Lighting circuit earth at 120V
In article , Martin Brook
writes Thanks for the reply, On Thu, 5 Aug 2004 14:46:36 +0100, Tim Mitchell wrote: Sounds like the earth wire on your lighting circuit is not connected to earth, which is a cause for concern. You often get 120V on a disconnected earth when some type of surge arrestor is connected to the circuit. (It's very very high impedance, so you don't feel a shock when you touch it, just a tingle. If you measured it with an analogue meter rather than a digital one, the voltage would be much lower or would disappear). I am not sure how a surge arrestor would get onto a lighting circuit however, unless there is a wider earthing problem in your house and the surge arrestor equipment is on a ring main; the ring main earth is connected to the lighting earth, but neither is connected to real earth. I'm not aware of there being any kind of surge arrestor anywhere... Also, most of the wiring in the house seems to be fine, earth-wise. I've already rewired two ring mains and added a new one, and everything is fine on those. The lighting circuit is the only one I haven't touched, but there is no voltage on the earth at the CU. So it seems to me that the problem must be somewhere in the rest of the circuit. Which, of course, disappears through a hole in the cellar roof. It might be just floating then, but you don't normally get enough induced voltage to feel a tingle. -- Tim Mitchell |
#7
|
|||
|
|||
Lighting circuit earth at 120V
In article ,
tony sayer wrote: The lighting earth isn't used that much except if you have any metal light fittings like candelabra's or such like. It must be earth just in case some "real" leakage develops!.... I'd be more worried about metal plate switches. -- *Born free - taxed to death * Dave Plowman London SW To e-mail, change noise into sound. |
#8
|
|||
|
|||
Lighting circuit earth at 120V
In article ,
Martin Brook wrote: So it seems to me that the problem must be somewhere in the rest of the circuit. Which, of course, disappears through a hole in the cellar roof. Are all your fittings standard ceiling roses? If so it's easy enough to do a visual check as a first step. If, however, some have been changed because of the fittings, I'd guess the earth hasn't been looped through at these. -- *Laugh alone and the world thinks you're an idiot. Dave Plowman London SW To e-mail, change noise into sound. |
#9
|
|||
|
|||
Lighting circuit earth at 120V
"Tim Mitchell" wrote in message ... Sounds like the earth wire on your lighting circuit is not connected to earth, which is a cause for concern. You often get 120V on a disconnected earth when some type of surge arrestor is connected to the circuit. (It's very very high impedance, so you don't feel a shock when you touch it, just a tingle. If you measured it with an analogue meter rather than a digital one, the voltage would be much lower or would disappear). I am not sure how a surge arrestor would get onto a lighting circuit however, unless there is a wider earthing problem in your house and the surge arrestor equipment is on a ring main; the ring main earth is connected to the lighting earth, but neither is connected to real earth. I'm not aware of there being any kind of surge arrestor anywhere... Also, most of the wiring in the house seems to be fine, earth-wise. I've already rewired two ring mains and added a new one, and everything is fine on those. The lighting circuit is the only one I haven't touched, but there is no voltage on the earth at the CU. So it seems to me that the problem must be somewhere in the rest of the circuit. Which, of course, disappears through a hole in the cellar roof. It might be just floating then, but you don't normally get enough induced voltage to feel a tingle. But you occasionally do through certain poor quality electronic transformers for 12v lights. Does the OP have any of these ? These rely on the high frequency transformer being earthed properly and if it isn't a voltage is induced in the earth lead, albeit at a high impedance. |
#10
|
|||
|
|||
Lighting circuit earth at 120V
"Martin Brook" wrote in
news On further investigation it seems that the earth conductors in all of my light switches are at 120V (with respect to neutral or live - tested with multimeter set to AC mode). However at the consumer unit, all appears to be fine. I have a functioning RCD and it's not tripped. All the lights work. No (obvious) dodgy wiring in any of the switches. What does your earth measure with respect to a "real" earth (e.g. conductive thing in the ground, bonded water pipe, earth at the consumer unit) ? Boris |
#11
|
|||
|
|||
Lighting circuit earth at 120V
Dave Plowman (News) wrote: The lighting earth isn't used that much except if you have any metal light fittings like candelabra's or such like. It must be earth just in I'd be more worried about metal plate switches. I'd be inclined to measure every earth on your lighting circuit, seeing which switches/fittings have the 120v on them and which don't. Then you will probably be able to deduce where it is not connected. If lucky in this process you will find the loose or missing earth. If not you will have to do some continuity checking and disconecting of things to deduce which cable is broken and then replace it. |
#12
|
|||
|
|||
Lighting circuit earth at 120V
On Thu, 5 Aug 2004 23:18:12 +0100, G&M wrote:
"Tim Mitchell" wrote in message ... Sounds like the earth wire on your lighting circuit is not connected to earth, which is a cause for concern. You often get 120V on a disconnected earth when some type of surge arrestor is connected to the circuit. (It's very very high impedance, so you don't feel a shock when you touch it, just a tingle. If you measured it with an analogue meter rather than a digital one, the voltage would be much lower or would disappear). I am not sure how a surge arrestor would get onto a lighting circuit however, unless there is a wider earthing problem in your house and the surge arrestor equipment is on a ring main; the ring main earth is connected to the lighting earth, but neither is connected to real earth. I'm not aware of there being any kind of surge arrestor anywhere... Also, most of the wiring in the house seems to be fine, earth-wise. I've already rewired two ring mains and added a new one, and everything is fine on those. The lighting circuit is the only one I haven't touched, but there is no voltage on the earth at the CU. So it seems to me that the problem must be somewhere in the rest of the circuit. Which, of course, disappears through a hole in the cellar roof. It might be just floating then, but you don't normally get enough induced voltage to feel a tingle. But you occasionally do through certain poor quality electronic transformers for 12v lights. Does the OP have any of these ? I don't have any that I'm aware of... These rely on the high frequency transformer being earthed properly and if it isn't a voltage is induced in the earth lead, albeit at a high impedance. -- Using Opera's revolutionary e-mail client: http://www.opera.com/m2/ |
#13
|
|||
|
|||
Lighting circuit earth at 120V
On Thu, 05 Aug 2004 17:54:56 +0100, Dave Plowman (News)
wrote: In article , Martin Brook wrote: So it seems to me that the problem must be somewhere in the rest of the circuit. Which, of course, disappears through a hole in the cellar roof. Are all your fittings standard ceiling roses? If so it's easy enough to do a visual check as a first step. If, however, some have been changed because of the fittings, I'd guess the earth hasn't been looped through at these. Yes, they all are... forgive my ignorance, but I'm picturing a setup where there is a junction box above each light fitting, which is why I was expecting to be having to spend a lot of time lifting floorboards... am I getting this completely wrong? -- Using Opera's revolutionary e-mail client: http://www.opera.com/m2/ |
#14
|
|||
|
|||
Lighting circuit earth at 120V
On Fri, 06 Aug 2004 06:42:08 GMT, Boris wrote:
"Martin Brook" wrote in news On further investigation it seems that the earth conductors in all of my light switches are at 120V (with respect to neutral or live - tested with multimeter set to AC mode). However at the consumer unit, all appears to be fine. I have a functioning RCD and it's not tripped. All the lights work. No (obvious) dodgy wiring in any of the switches. What does your earth measure with respect to a "real" earth (e.g. conductive thing in the ground, bonded water pipe, earth at the consumer unit) ? Boris As things stand, I have no easy way to measure that... _but_ at the consumer unit, the live conductor of the lighting circuit (which presumably is wired correctly, or the lights wouldn't be working) measures 240V with respect to real earth. So from that i'm assuming the earth in the lighting circuit is at 120v with respect to earth. Martin -- Using Opera's revolutionary e-mail client: http://www.opera.com/m2/ |
#15
|
|||
|
|||
Lighting circuit earth at 120V
On Fri, 06 Aug 2004 12:24:12 +0100, Mike wrote:
I'd be inclined to measure every earth on your lighting circuit, seeing which switches/fittings have the 120v on them and which don't. Then you will probably be able to deduce where it is not connected. Haven't checked every fitting but it is at 120v at every switch. (Haven't checked the pull-cord switch in the bathroom), but in terms of layout I would expect that to be near the end of the circuit. I think this suggests the fault is between the CU and the first ground floor light. If lucky in this process you will find the loose or missing earth. If not you will have to do some continuity checking and disconecting of things to deduce which cable is broken and then replace it. Thought so... I guess I'll be doing that then! -- Using Opera's revolutionary e-mail client: http://www.opera.com/m2/ |
#16
|
|||
|
|||
Lighting circuit earth at 120V
"Boris" wrote in message
.37... "Martin Brook" wrote in news On further investigation it seems that the earth conductors in all of my light switches are at 120V (with respect to neutral or live - tested with multimeter set to AC mode). However at the consumer unit, all appears to be fine. I have a functioning RCD and it's not tripped. All the lights work. No (obvious) dodgy wiring in any of the switches. What does your earth measure with respect to a "real" earth (e.g. conductive thing in the ground, bonded water pipe, earth at the consumer unit) ? That can be very misleading real earth "the conductive thing in the ground"- may not be connected to your mains earth at all eg a PME installation. It seems there are two issues here. Why is the the lighting earth not earthed and why is it it at 120V. First one in easy- probably a simple break or unmade connection. Check the continuity (power off) from the lighting earth to the earth bus in the consumer unit and the meter board. To help with the second bit, do the ring mains and other spurs (eg cooker and shower) at the same time. Second one is more complicated- I suspect a filter in something on the circuit is the culprit. These filters have capacitors from L and N to earth. If the earth is not connnected it will be at the mid-point of a 1:1 potential divider, in this case 120V. Earth the earth and all is well. The filter isn't broken- just effectively incorrectly wired. You may be able to isolate the fault by unpluging appliances. -- Brian Reay www.g8osn.org.uk www.amateurradiotraining.org.uk FP#898 |
#17
|
|||
|
|||
Lighting circuit earth at 120V
In article ,
Martin Brook wrote: Are all your fittings standard ceiling roses? If so it's easy enough to do a visual check as a first step. If, however, some have been changed because of the fittings, I'd guess the earth hasn't been looped through at these. Yes, they all are... forgive my ignorance, but I'm picturing a setup where there is a junction box above each light fitting, which is why I was expecting to be having to spend a lot of time lifting floorboards... am I getting this completely wrong? If you unscrew the cover from a 'standard' ceiling rose, you'll expose the connections. The earth wires are pretty obvious - if they exist. For some reason, I've often seen them cut off. -- *Growing old is inevitable, growing up is optional * Dave Plowman London SW To e-mail, change noise into sound. |
#18
|
|||
|
|||
Lighting circuit earth at 120V
"Martin Brook" wrote in message ...
On Thu, 5 Aug 2004 14:46:36 +0100, Tim Mitchell wrote: Sounds like the earth wire on your lighting circuit is not connected to earth, which is a cause for concern. Also, most of the wiring in the house seems to be fine, earth-wise. I've already rewired two ring mains and added a new one, and everything is fine on those. The lighting circuit is the only one I haven't touched, but there is no voltage on the earth at the CU. So it seems to me that the problem must be somewhere in the rest of the circuit. Which, of course, disappears through a hole in the cellar roof. This does beg the q what did you connect the other meter lead to in each case? But assuming for a mo that you used the same point at all times, and that piont was really earthed, you likely have lost an earth connection somewhere in lighting cct. It matters if you have fittings needing earth - of course that does include plastic switches which have metal screws. Regards, NT |
#19
|
|||
|
|||
Lighting circuit earth at 120V
"Brian Reay" wrote in
: That can be very misleading real earth "the conductive thing in the ground"- may not be connected to your mains earth at all eg a PME installation. Agreed, but surely you wouldn't get 120 volts? Unless your electricity suppliers neutral had a fault... It seems there are two issues here. Why is the the lighting earth not earthed and why is it it at 120V. First one in easy- probably a simple break or unmade connection. Check the continuity (power off) from the lighting earth to the earth bus in the consumer unit and the meter board. To help with the second bit, do the ring mains and other spurs (eg cooker and shower) at the same time. Second one is more complicated- I suspect a filter in something on the circuit is the culprit. These filters have capacitors from L and N to earth. If the earth is not connnected it will be at the mid-point of a 1:1 potential divider, in this case 120V. Earth the earth and all is well. The filter isn't broken- just effectively incorrectly wired. You may be able to isolate the fault by unpluging appliances. That sounds entirely reasonable. The tingling noted by the OP would be as a result of current through filter caps. Boris |
#20
|
|||
|
|||
Lighting circuit earth at 120V
"Brian Reay" wrote in message ...
"Boris" wrote in message .37... "Martin Brook" wrote in news That can be very misleading real earth "the conductive thing in the ground"- may not be connected to your mains earth at all eg a PME installation. Incoming "conductive things" like water pipes should of course be firmly bonded to the PME terminal (main bonding). Network faults apart - and these would usually clear in a matter of seconds - the PME earth shouldn't be more than a volt or three adrift of the local 'true' ground. It seems there are two issues here. Why is the the lighting earth not earthed and why is it it at 120V. It is at ~120 V _because_ the connection to the main earth terminal is either absent or broken. (There's a lot to be said for Occam's razor, you know.) Second one is more complicated- I suspect a filter in something on the circuit is the culprit. These filters have capacitors from L and N to earth. If the earth is not connnected it will be at the mid- point of a 1:1 potential divider, in this case 120V. Earth the earth and all is well. The filter isn't broken- just effectively incorrectly wired. No need to postulate a filter: the capacitance in the wiring is quite enough to produce the effect described. T&E cable will have roughly equal capacitance between L and E and N and E. If the earth wire (CPC, strictly) is left floating then a high-impedance meter will measure 120 V AC on it, due to the capacitive divider principle that you describe. The few microamps of leakage through your body (and its own capacitance to earth) that you'd get when touching the CPC in these circumstances is quite enough to produce a tingle. On a lighting circuit like this I'd expect to see almost exactly half-mains voltage when all the lights are switched off, with the voltage rising as lights are switched on (because in the switch-drops sections both L and SL conductors are 'live' when the light is on and all the capacitance in such section is now between L and E, IYSWIM). Could this whole thing be a simple case of incompetent extension(s) to an old unearthed lighting circuit - somebody adding new wiring and accessories and having nothing to connect the CPC to? -- Andy |
#21
|
|||
|
|||
Lighting circuit earth at 120V
In article ,
Andy Wade wrote: Could this whole thing be a simple case of incompetent extension(s) to an old unearthed lighting circuit - somebody adding new wiring and accessories and having nothing to connect the CPC to? I never cease to be surprised how many DIY bodges leave out the earth. Perhaps because things 'work' without it? A physics teacher friend ran a lighting circuit from the CU into a new garage at an old house. The house lighting wiring was pretty old, with no earth, but the consumer unit had been changed when rings were installed and was properly earthed etc. I was mildly surprised to find it wasn't earthed - with the ec cut off. He reckoned if it wasn't needed in the rest of the house, why bother with it now... -- *Re-elect nobody Dave Plowman London SW To e-mail, change noise into sound. |
#22
|
|||
|
|||
Lighting circuit earth at 120V
|
#23
|
|||
|
|||
Lighting circuit earth at 120V
In article ,
Huge wrote: I was mildly surprised to find it wasn't earthed - with the ec cut off. He reckoned if it wasn't needed in the rest of the house, why bother with it now... Errr, I thought one shouldn't run the house earth into an outbuilding? Perhaps that's just for {mumble} (I'd call it PME, but WTF) installations, like what we've got. It wasn't an outbuilding, but a lean to. IIRC, it's the distance from the main earth point that matters (and the size of the cable) -- *A fine is a tax for doing wrong. A tax is a fine for doing well. Dave Plowman London SW To e-mail, change noise into sound. |
#24
|
|||
|
|||
Lighting circuit earth at 120V
"Dave Plowman (News)" wrote in message
... It wasn't an outbuilding, but a lean to. IIRC, it's the distance from the main earth point that matters (and the size of the cable) No, distance doesn't have much to do with it: it's whether it's practicable to apply the equipotential zone concept in the remote installation (see http://www.google.com/groups?selm=01c1a135%244dc3c9e0%24LocalHost%40dog4 0 for an example from a previous discussion). The existence of any sort of 'damp floor' conditions suggests that an 'exported' PME earth is inadvisable. Where an exported earth is used, local bonding of any incoming services in the outbuilding is essential. When it comes to "the size of the cable" you must ensure (as always) that disconnection time and earth fault loop impedance requirements are met, bearing in mind the type of fusing, etc. -- Andy |
#25
|
|||
|
|||
Lighting circuit earth at 120V
"Andy Wade" wrote in message ... "Dave Plowman (News)" wrote in message ... It wasn't an outbuilding, but a lean to. IIRC, it's the distance from the main earth point that matters (and the size of the cable) No, distance doesn't have much to do with it: it's whether it's practicable to apply the equipotential zone concept in the remote installation (see http://www.google.com/groups?selm=01c1a135%244dc3c9e0%24LocalHost%40dog4 0 for an example from a previous discussion). The existence of any sort of 'damp floor' conditions suggests that an 'exported' PME earth is inadvisable. Which does raise the question, why do old rural houses with inherently slightly damp stone floors usually have PME in them ? Ours had a quite noticable tingly 40volts from 'earth' to 'ground'. |
#26
|
|||
|
|||
Lighting circuit earth at 120V
In message , "Dave Plowman (News)"
writes A physics teacher friend ran a lighting circuit from the CU into a new garage at an old house. The house lighting wiring was pretty old, with no earth, but the consumer unit had been changed when rings were installed and was properly earthed etc. I was mildly surprised to find it wasn't earthed - with the ec cut off. He reckoned if it wasn't needed in the rest of the house, why bother with it now... Physics teachers!!!! PPHHHAAAAAAAA When I was at school 30+ years ago my physics teacher had a small cruiser, boat, that he wired spot lights on using bell wire. Well it was only 12V wasn't it. The whole lot went up in smoke when he turned them on. -- Bill |
#27
Posted to uk.d-i-y
|
|||
|
|||
Lighting circuit earth at 120V
replying to Andy Wade, Iain wrote:
I had same problem. Different voltage readings. But nonetheless the solution was the same. Reconnect the broken earth connection in one of the ceiling roses. Thanks for the ideas here. Sorted in half hour after reading your post. Spent hours writing down values before. -- for full context, visit https://www.homeownershub.com/uk-diy...20v-94971-.htm |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Repairing Lightning Damaged Tv's | Electronics Repair | |||
Typical domestic electrical circuits | UK diy | |||
Lighting circuit - loop through in switch | UK diy | |||
Lighting circuit problems | UK diy | |||
Ceiling fan earth | UK diy |