  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 51
Default Wiring Immersion Heater

The plumber doing some work on the cylinder commented on wing the immersion
heater through a double pole switch rather than the single pole spur switch.
He mentioned the heating from the high load of the heater but I don't see
why a double pole switch will handle the heat effect better. Doesn't a
double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the consumer
unit then via a single pole switch in the kitchen and a second single pole
switch in the airing cupboard. The immersion heater is only ever used when
the boiler is out of commission for any reason.

Kevin

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,434
Default Wiring Immersion Heater

On 24/06/14 13:42, Kevin wrote:
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole spur switch.
He mentioned the heating from the high load of the heater but I don't
see why a double pole switch will handle the heat effect better. Doesn't
a double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer unit then via a single pole switch in the kitchen and a second
single pole switch in the airing cupboard. The immersion heater is only
ever used when the boiler is out of commission for any reason.

Kevin


Normal switched fused spur is fine.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,631
Default Wiring Immersion Heater

Of course it is, for many y years the cheap timer on ours worked and it was
just a single contact on the live side. I think the newer clock has a double
pole relay in it though, for whatever reason.
Brian

--
From the Sofa of Brian Gaff Reply address is active
"Tim Watts" wrote in message
...
On 24/06/14 13:42, Kevin wrote:
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole spur switch.
He mentioned the heating from the high load of the heater but I don't
see why a double pole switch will handle the heat effect better. Doesn't
a double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer unit then via a single pole switch in the kitchen and a second
single pole switch in the airing cupboard. The immersion heater is only
ever used when the boiler is out of commission for any reason.

Kevin


Normal switched fused spur is fine.



  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default Wiring Immersion Heater

On Tuesday, June 24, 2014 1:42:43 PM UTC+1, K wrote:
The plumber doing some work on the cylinder commented on wing the immersion
heater through a double pole switch rather than the single pole spur switch.
He mentioned the heating from the high load of the heater but I don't see
why a double pole switch will handle the heat effect better. Doesn't a
double pole just switch the neutral as well?


Fused connection unit (spur switch) should also have a double pole switch anyway. However they're rated at 13 amp max and contain a cartridge fuse. The fuse contacts especially can be vulnerable to poor contact and heating from a sustained 3 kW load.

A 20 amp switch would be more robust.

Owain

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Wiring Immersion Heater

On 24/06/2014 13:42, Kevin wrote:
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole spur switch.
He mentioned the heating from the high load of the heater but I don't
see why a double pole switch will handle the heat effect better. Doesn't
a double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer unit then via a single pole switch in the kitchen and a second
single pole switch in the airing cupboard. The immersion heater is only
ever used when the boiler is out of commission for any reason.


Either are fine in most cases (yes the DP does just switch the N in
addition).

There is a small advantage to DP switching if the immersion is on a
circuit that shares a RCD with other circuits, since a fault heater
could cause nuisance trips via N to E leakage, so being able to fully
isolate it is handy.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,396
Default Wiring Immersion Heater

I have had to replace melted fused spur units.

I guess it is vital to go for best quality.


  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Wiring Immersion Heater

In article 2,
DerbyBorn writes:
I have had to replace melted fused spur units.

I guess it is vital to go for best quality.


Absolutely, and good tight connections.

If it's on a circuit which is protected by 16A MCB, don't use a
fused spur, just use a 20A switch. In this case, the 13A fuse is
doing nothing except getting hot and possibly contributing to
earlier failure...

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 14,085
Default Wiring Immersion Heater

On Tue, 24 Jun 2014 15:51:33 +0000 (UTC), Andrew Gabriel wrote:

I have had to replace melted fused spur units.

I guess it is vital to go for best quality.


If it's on a circuit which is protected by 16A MCB, don't use a
fused spur, just use a 20A switch. In this case, the 13A fuse is
doing nothing except getting hot and possibly contributing to
earlier failure...


+1 Hager are a decent make I believe. Didn't stop one of their
switched fused connection units going into meltdown when feeding one
of the storage heaters. All the storage heaters had SFCU's, note past
tense they all have 20A DP switches now.

--
Cheers
Dave.



  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,339
Default Wiring Immersion Heater


"Kevin" wrote in message
...
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single pole
spur switch.
He mentioned the heating from the high load of the heater but I don't see
why a double pole switch will handle the heat effect better. Doesn't a
double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the consumer
unit then via a single pole switch in the kitchen and a second single pole
switch in the airing cupboard. The immersion heater is only ever used when
the boiler is out of commission for any reason.

Kevin


All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric shower,
all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.

In days of yore, single pole switches were normal on sockets and "spur
switches"
Now you can get ones with double pole switches

This is why some fans need a three pole switch. L+N+control wire.


  #10   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Wiring Immersion Heater

"harryagain" wrote in message
...

"Kevin" wrote in message
...
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single pole
spur switch.
He mentioned the heating from the high load of the heater but I don't see
why a double pole switch will handle the heat effect better. Doesn't a
double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the consumer
unit then via a single pole switch in the kitchen and a second single
pole switch in the airing cupboard. The immersion heater is only ever
used when the boiler is out of commission for any reason.

Kevin


All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric shower,
all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.



I am not sure that it has ever been a requirement to switch the neutral on a
TN system and that that "requirement" is a load of ******** made up by
people talking themselves into believing it after misreading the regs.




--
Adam



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default Wiring Immersion Heater

On 24/06/14 20:31, ARW wrote:
"harryagain" wrote in message
...

"Kevin" wrote in message
...
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole spur switch.
He mentioned the heating from the high load of the heater but I don't
see why a double pole switch will handle the heat effect better.
Doesn't a double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer unit then via a single pole switch in the kitchen and a
second single pole switch in the airing cupboard. The immersion
heater is only ever used when the boiler is out of commission for any
reason.

Kevin


All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric
shower, all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.



I am not sure that it has ever been a requirement to switch the neutral
on a TN system and that that "requirement" is a load of ******** made up
by people talking themselves into believing it after misreading the regs.


Its fairly common practice and in SOME of the regs that SOME kit must be
totally isolatable.

That includes all bathroom kit and usually cookers and immersion heaters.

Not sure the latter is a regulation tho.





--
Ineptocracy

(in-ep-toc-ra-cy) €“ a system of government where the least capable to
lead are elected by the least capable of producing, and where the
members of society least likely to sustain themselves or succeed, are
rewarded with goods and services paid for by the confiscated wealth of a
diminishing number of producers.

  #12   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Wiring Immersion Heater

"The Natural Philosopher" wrote in message
...
On 24/06/14 20:31, ARW wrote:
"harryagain" wrote in message
...

"Kevin" wrote in message
...
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole spur switch.
He mentioned the heating from the high load of the heater but I don't
see why a double pole switch will handle the heat effect better.
Doesn't a double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer unit then via a single pole switch in the kitchen and a
second single pole switch in the airing cupboard. The immersion
heater is only ever used when the boiler is out of commission for any
reason.

Kevin

All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric
shower, all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.



I am not sure that it has ever been a requirement to switch the neutral
on a TN system and that that "requirement" is a load of ******** made up
by people talking themselves into believing it after misreading the regs.


Its fairly common practice and in SOME of the regs that SOME kit must be
totally isolatable.

That includes all bathroom kit and usually cookers and immersion heaters.

Not sure the latter is a regulation tho.



The manufacturers of the equipment often say you need "Omnipolar
switching" - but you would not switch the earth would you?

The main switch of the CU is an isolator suitable for all isolation
purposes. This is local isolation that the OP is talking about. If you are
allowed to work on a circuit with a single pole MCB as the isolation why can
you not work on an appliance that is locally isolated via a single pole
device?

If a cooker switch need changing where is the isolation for the cooker
switch? On a TN system you would use the MCB for the cooker circuit - and
nothing else.

Anyway - I have proof that I am correct.

harry said "All electrical equipment must be capable of isolation and that
must be adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral So a plug and socket
would be fine. Or a double pole switch. But not a single pole switch.".

I rest my case;-)


--
Adam

  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Wiring Immersion Heater

On 24/06/2014 21:44, ARW wrote:
"The Natural Philosopher" wrote in message
...
On 24/06/14 20:31, ARW wrote:
"harryagain" wrote in message
...

"Kevin" wrote in message
...
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole spur switch.
He mentioned the heating from the high load of the heater but I don't
see why a double pole switch will handle the heat effect better.
Doesn't a double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer unit then via a single pole switch in the kitchen and a
second single pole switch in the airing cupboard. The immersion
heater is only ever used when the boiler is out of commission for any
reason.

Kevin

All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric
shower, all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.


I am not sure that it has ever been a requirement to switch the neutral
on a TN system and that that "requirement" is a load of ******** made up
by people talking themselves into believing it after misreading the
regs.


Its fairly common practice and in SOME of the regs that SOME kit must
be totally isolatable.

That includes all bathroom kit and usually cookers and immersion heaters.

Not sure the latter is a regulation tho.



The manufacturers of the equipment often say you need "Omnipolar
switching" - but you would not switch the earth would you?

The main switch of the CU is an isolator suitable for all isolation
purposes. This is local isolation that the OP is talking about. If you
are allowed to work on a circuit with a single pole MCB as the isolation
why can you not work on an appliance that is locally isolated via a
single pole device?

If a cooker switch need changing where is the isolation for the cooker
switch? On a TN system you would use the MCB for the cooker circuit -
and nothing else.


16th edition wording[1]:

"Except as required by Regulation 476-01-03, in TN-S or TN-C-S systems
the neutral conductor need not be isolated or switched, where the
neutral conductor can reliably be regarded as being at earth potential.
For supplies which arc provided in accordance with the Electricity
Safety, Quality and Continuity Regulations 2002, the supply neutral
conductor (PEN or N) is considered to be connected with earth by a
suitably low resistance."

There are additional requirements for isolation for items requiring
mechanical maintenance.

[1] cos I have that to hand in a PDF and can't be arsed to get the book
down from the shelf and scan it!


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default Wiring Immersion Heater

On 24/06/14 21:44, ARW wrote:
"The Natural Philosopher" wrote in message
...
On 24/06/14 20:31, ARW wrote:
"harryagain" wrote in message
...

"Kevin" wrote in message
...
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole spur switch.
He mentioned the heating from the high load of the heater but I don't
see why a double pole switch will handle the heat effect better.
Doesn't a double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer unit then via a single pole switch in the kitchen and a
second single pole switch in the airing cupboard. The immersion
heater is only ever used when the boiler is out of commission for any
reason.

Kevin

All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric
shower, all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.


I am not sure that it has ever been a requirement to switch the neutral
on a TN system and that that "requirement" is a load of ******** made up
by people talking themselves into believing it after misreading the
regs.


Its fairly common practice and in SOME of the regs that SOME kit must
be totally isolatable.

That includes all bathroom kit and usually cookers and immersion heaters.

Not sure the latter is a regulation tho.



The manufacturers of the equipment often say you need "Omnipolar
switching" - but you would not switch the earth would you?

safer to have it left in place

The main switch of the CU is an isolator suitable for all isolation
purposes. This is local isolation that the OP is talking about. If you
are allowed to work on a circuit with a single pole MCB as the isolation
why can you not work on an appliance that is locally isolated via a
single pole device?

At the CU you can GUARANTEE - because its attached to the bus - that its
the live you are disconnecting..

Do you trust the sparky to have not swapped live and neutral down on a spur?


If a cooker switch need changing where is the isolation for the cooker
switch? On a TN system you would use the MCB for the cooker circuit -
and nothing else.

Anyway - I have proof that I am correct.

harry said "All electrical equipment must be capable of isolation and
that must be adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral So a plug and
socket would be fine. Or a double pole switch. But not a single pole
switch.".

I rest my case;-)


Never said Harry was right, just that you weren't 100% right either.



--
Ineptocracy

(in-ep-toc-ra-cy) €“ a system of government where the least capable to
lead are elected by the least capable of producing, and where the
members of society least likely to sustain themselves or succeed, are
rewarded with goods and services paid for by the confiscated wealth of a
diminishing number of producers.

  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,339
Default Wiring Immersion Heater


"ARW" wrote in message
...
"The Natural Philosopher" wrote in message
...
On 24/06/14 20:31, ARW wrote:
"harryagain" wrote in message
...

"Kevin" wrote in message
...
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole spur switch.
He mentioned the heating from the high load of the heater but I don't
see why a double pole switch will handle the heat effect better.
Doesn't a double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer unit then via a single pole switch in the kitchen and a
second single pole switch in the airing cupboard. The immersion
heater is only ever used when the boiler is out of commission for any
reason.

Kevin

All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric
shower, all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.


I am not sure that it has ever been a requirement to switch the neutral
on a TN system and that that "requirement" is a load of ******** made up
by people talking themselves into believing it after misreading the
regs.


Its fairly common practice and in SOME of the regs that SOME kit must be
totally isolatable.

That includes all bathroom kit and usually cookers and immersion heaters.

Not sure the latter is a regulation tho.



The manufacturers of the equipment often say you need "Omnipolar
switching" - but you would not switch the earth would you?

The main switch of the CU is an isolator suitable for all isolation
purposes. This is local isolation that the OP is talking about. If you are
allowed to work on a circuit with a single pole MCB as the isolation why
can you not work on an appliance that is locally isolated via a single
pole device?

If a cooker switch need changing where is the isolation for the cooker
switch? On a TN system you would use the MCB for the cooker circuit - and
nothing else.


The cooker switch next to the cooker is double pole.
So the cooker can be tested and repaired.

Anyway - I have proof that I am correct.

harry said "All electrical equipment must be capable of isolation and that
must be adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral So a plug and socket
would be fine. Or a double pole switch. But not a single pole switch.".

I rest my case;-)


The reason for isoation is simple.
It is for repairs and maintenance.
How can you perform an insulation test if the neutral is still connected (to
earth)?
Also in certain (unsual) fault cases the neutral might become live.




  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 395
Default Wiring Immersion Heater

harryagain posted

"Kevin" wrote in message
...
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single pole
spur switch.
He mentioned the heating from the high load of the heater but I don't see
why a double pole switch will handle the heat effect better. Doesn't a
double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the consumer
unit then via a single pole switch in the kitchen and a second single pole
switch in the airing cupboard. The immersion heater is only ever used when
the boiler is out of commission for any reason.

Kevin


All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric shower,
all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.


But why not just an ordinary plug that you can pull out from an ordinary
socket?

--
Les
  #17   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Wiring Immersion Heater

"Big Les Wade" wrote in message
...
harryagain posted

"Kevin" wrote in message
.. .
The plumber doing some work on the cylinder commented on wing the
immersion heater through a double pole switch rather than the single
pole
spur switch.
He mentioned the heating from the high load of the heater but I don't
see
why a double pole switch will handle the heat effect better. Doesn't a
double pole just switch the neutral as well?
The immersion heater circuit is a spur off of its own mcb on the
consumer
unit then via a single pole switch in the kitchen and a second single
pole
switch in the airing cupboard. The immersion heater is only ever used
when
the boiler is out of commission for any reason.

Kevin


All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric shower,
all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.


But why not just an ordinary plug that you can pull out from an ordinary
socket?



Allowable by the regs (especially with an unswitched socket). It's just not
best practice due to the 3kW loading.

--
Adam

  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,434
Default Wiring Immersion Heater

On 03/07/14 20:30, ARW wrote:
"Big Les Wade" wrote in message
...


All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric
shower,
all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.


But why not just an ordinary plug that you can pull out from an
ordinary socket?



Allowable by the regs (especially with an unswitched socket). It's just
not best practice due to the 3kW loading.


Could always use a 16A Commando
  #19   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Wiring Immersion Heater

"Tim Watts" wrote in message
...
On 03/07/14 20:30, ARW wrote:
"Big Les Wade" wrote in message
...


All electrical equipment must be capable of isolation and that must be
adjacent to it for repairs and maintenance.
Isolation means cutting off Live/phase(s) and Neutral
So a plug and socket would be fine. Or a double pole switch.
But not a single pole switch.
So your electric cooker, immersion heater, instantaneous electric
shower,
all fixed equipment, has a double pole switch. (Or should)
It has been so for fifty years to my knowledge.

But why not just an ordinary plug that you can pull out from an
ordinary socket?



Allowable by the regs (especially with an unswitched socket). It's just
not best practice due to the 3kW loading.


Could always use a 16A Commando


That would be allowed.



--
Adam

  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,591
Default Wiring Immersion Heater

On 2014-07-03, Tim Watts wrote:

On 03/07/14 20:30, ARW wrote:
"Big Les Wade" wrote in message
...


But why not just an ordinary plug that you can pull out from an
ordinary socket?



Allowable by the regs (especially with an unswitched socket). It's just
not best practice due to the 3kW loading.


That's what I was told years ago by an electrician I respected --- if
you run a plug right at 3 kW for long periods (whereas a kettle runs
for a few minutes then has a break) you're pushing it.


Could always use a 16A Commando


Please wear underwear while wiring.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Immersion heater wiring David Hearn UK diy 21 May 2nd 10 03:56 PM
Immersion Heater Timer wiring. Uno Hoo! UK diy 9 September 16th 05 09:39 PM
Wiring Immersion Heater Timer Ken Knott UK diy 15 September 13th 04 01:42 PM
Immersion Heater Wiring Andrew Gabriel UK diy 5 July 14th 04 11:47 PM
Wiring an Immersion Heater Timer Nathan UK diy 4 December 5th 03 10:23 AM


All times are GMT +1. The time now is 08:45 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"