should i go for 2 or 3 core swa down to my garage? its about 40 meters away and i am going for 16mm3 cheers steve |
#2
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
John Rumm wrote:
On 18/05/2011 11:26, John Rumm wrote: On 18/05/2011 09:09, Mr Sandman wrote: hi all, should i go for 2 or 3 core swa down to my garage? its about 40 meters away and i am going for 16mm3 Two, unless you are exporting a PME earth as well (and hence the main bonding conductor). Pardon me talking to myself, but its just been pointed out to me that you were talking about 16mm^2 SWA. The armour on that has enough copper equivalent CSA to be used as a main bonding conductor as well - so you will only need two core regardless. http://wiki.diyfaq.org.uk/index.php?...ricity_outside Sorry John, I was working when I pointed that out to you and I needed to check before posting to the newsgroup. I would say a 16mm two core is fine for a 40m run using a 40A MCB. This should cover voltage drop for a lighting circuit in the garage and allow any mains bonding in the garage to meet the regs. -- Adam |
#4
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
Bruce Burnett wrote:
In article , says... John Rumm wrote: On 18/05/2011 11:26, John Rumm wrote: On 18/05/2011 09:09, Mr Sandman wrote: hi all, should i go for 2 or 3 core swa down to my garage? its about 40 meters away and i am going for 16mm3 Two, unless you are exporting a PME earth as well (and hence the main bonding conductor). Pardon me talking to myself, but its just been pointed out to me that you were talking about 16mm^2 SWA. The armour on that has enough copper equivalent CSA to be used as a main bonding conductor as well - so you will only need two core regardless. http://wiki.diyfaq.org.uk/index.php?...ricity_outside Sorry John, I was working when I pointed that out to you and I needed to check before posting to the newsgroup. I would say a 16mm two core is fine for a 40m run using a 40A MCB. This should cover voltage drop for a lighting circuit in the garage and allow any mains bonding in the garage to meet the regs. 16mm2 armour is fine in copper equivalence terms to act as a cpc for fault protection, but NOT to act as a main protective bonding conductor. See note at bottom of 544.1.1. For bonding it is the equivalent conductance that matters. Regards The CSA of the armour of a 2 core 16mm SWA cable is 42mm^2. That gives it the copper equivalent of 18.6mm^2. For most domestic installations that will be fine. -- Adam |
#5
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
In article ,
says... Bruce Burnett wrote: In article , says... John Rumm wrote: On 18/05/2011 11:26, John Rumm wrote: On 18/05/2011 09:09, Mr Sandman wrote: hi all, should i go for 2 or 3 core swa down to my garage? its about 40 meters away and i am going for 16mm3 Two, unless you are exporting a PME earth as well (and hence the main bonding conductor). Pardon me talking to myself, but its just been pointed out to me that you were talking about 16mm^2 SWA. The armour on that has enough copper equivalent CSA to be used as a main bonding conductor as well - so you will only need two core regardless. http://wiki.diyfaq.org.uk/index.php?...ricity_outside Sorry John, I was working when I pointed that out to you and I needed to check before posting to the newsgroup. I would say a 16mm two core is fine for a 40m run using a 40A MCB. This should cover voltage drop for a lighting circuit in the garage and allow any mains bonding in the garage to meet the regs. 16mm2 armour is fine in copper equivalence terms to act as a cpc for fault protection, but NOT to act as a main protective bonding conductor. See note at bottom of 544.1.1. For bonding it is the equivalent conductance that matters. Regards The CSA of the armour of a 2 core 16mm SWA cable is 42mm^2. That gives it the copper equivalent of 18.6mm^2. For most domestic installations that will be fine. I agree it gives a copper equivalence in K terms which includes specific heat. That is relevant for temperature rise in the adiabatic equation in relation to sizing a cpc. But that is the wrong equivalence for a bonding conducter which has to be done in pure conductance terms. I said above it was at the bottom of 544.1.1, it is actually at the bottom of Table 54.8 immediately below that regulation. You need to be around 70mm2 cable before the armour reaches an equivalence of 10mm2 copper in conductance terms. Regards Bruce |
#6
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
BruceB wrote:
In article , says... Bruce Burnett wrote: In article , says... John Rumm wrote: On 18/05/2011 11:26, John Rumm wrote: On 18/05/2011 09:09, Mr Sandman wrote: hi all, should i go for 2 or 3 core swa down to my garage? its about 40 meters away and i am going for 16mm3 Two, unless you are exporting a PME earth as well (and hence the main bonding conductor). Pardon me talking to myself, but its just been pointed out to me that you were talking about 16mm^2 SWA. The armour on that has enough copper equivalent CSA to be used as a main bonding conductor as well - so you will only need two core regardless. http://wiki.diyfaq.org.uk/index.php?...ricity_outside Sorry John, I was working when I pointed that out to you and I needed to check before posting to the newsgroup. I would say a 16mm two core is fine for a 40m run using a 40A MCB. This should cover voltage drop for a lighting circuit in the garage and allow any mains bonding in the garage to meet the regs. 16mm2 armour is fine in copper equivalence terms to act as a cpc for fault protection, but NOT to act as a main protective bonding conductor. See note at bottom of 544.1.1. For bonding it is the equivalent conductance that matters. Regards The CSA of the armour of a 2 core 16mm SWA cable is 42mm^2. That gives it the copper equivalent of 18.6mm^2. For most domestic installations that will be fine. I agree it gives a copper equivalence in K terms which includes specific heat. That is relevant for temperature rise in the adiabatic equation in relation to sizing a cpc. But that is the wrong equivalence for a bonding conducter which has to be done in pure conductance terms. I said above it was at the bottom of 544.1.1, it is actually at the bottom of Table 54.8 immediately below that regulation. You need to be around 70mm2 cable before the armour reaches an equivalence of 10mm2 copper in conductance terms. I get you. With an 8 times greater resistivity for the steel than the copper then yes it will need to be 70mm^2 2 core SWA (as that is where the armourings reaches 80mm CSA) -- Adam |
#7
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
On 20/05/2011 13:25, ARWadsworth wrote:
I get you. With an 8 times greater resistivity for the steel than the copper then yes it will need to be 70mm^2 2 core SWA (as that is where the armourings reaches 80mm CSA) Quite right - as debated previously at length both here and in the IET forum. I do wonder whether it's what the committee intended to say though, or whether it's just badly worded. After all there's no upper limit allowed on the resistance of a copper main bonding conductor, so why limit the conductance of a steel one? Logically it should be either the adiabatic (I^2*t) capacity of the conductor or its continuous current carrying capacity that should matter for main bonding. -- Andy |
#8
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
|
#9
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
On 21/05/2011 09:35, BruceB wrote:
[...] The bonding is there to hold the touch voltage down during a fault and hence the conductance/resistance of the bonding conductor compared to say the cable introducing a fault is relevant. Agreed, so why don't they stipulate a maximum resistance for copper main bonding? There is a resistance limit for supplementary bonding of course, fist introduced in the 16th ed., IIRC. I can only imagine that it's a non-issue in practice, with the length in practice unlikely to be enough to lead to an excessive resistance. Large buildings will have larger capacity supplies, mandating larger main bonding conductors. Supplementary bonding, OTOH, can be as small as 1 mm^2 if incorporated in a cable or otherwise mechanically protected, so the possibility of excessive resistance is more likely. -- Andy |
#10
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
John Rumm wrote:
I am no fan of exporting PME earths and equipotential zones anyway in most cases. So you would be better off making the far end TT and sticking with two core SWA and isolating the earth at the far end IMHO. It's a tricky issue. That solution is clean if you are doing a single submain to a remote shed. But what would be the best solution for running a lighting circuit round the garden (gatepost lamps, couple of lamps in the garden sort of thing? The same circuit might supply a small lamp in a bike shed and other odds and sods. This would be a single supply circuit with local switching. I suppose you could make everything class II and worry less (we'll assume an RCD at the house end of the circuit source). Or you could TT it - but if it goes to a variety of distant loads would you have to stake it in several places? What if it was desirable to use this circuit in the vicinity of another circuit, eg in the workshop[1] so that if a power tool tripped the socket circuit, the lights stayed on - you'd have to have the same earthing system and cross bond them. I'm still undecided on mine. My original plan was: 20A radial to a few waterproof sockets on the house wall (one on each corner) - In theory a class I appliance *could* be plugged in outside from this. 32A supply to workshop for sockets only (re point about tripping and lights not going out as a result) 10A general lighting supply going all over the place including the workshop (which would have a pair of DP isolators locally on point of entry) This seemed like a good idea when I believed I had a TN-S earth, but got a bit unravelled when the bloke proved EDF's records were wrong by opening up the cutout housing (I actually have TN-C-S). Thoughts appreciated -- Tim Watt |
#11
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
|
#12
Posted to uk.d-i-y
|
|||
|
|||
SWA 2 or 3 core to garage?
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Alarm Cable: 8 core vs 6 core | UK diy | |||
guide sleeves, polit bit, core bit, core lifter, core barrel, TUDEX, ODEX, DTH hammer, drilling | Woodturning | |||
Underground, quarrying, mining, air-leg, jack-leg, hand-held rock drills, button bit, drag bits,drill rod, drill tube, drill bit, core bit, core barrel, diamonde core bit, DTH hammer, taper rod, integral drill rod, taper bit, rock drilling tools | Woodturning | |||
thread bit, tapered bit, diamond core bit, core barrel, shank adaptors | Woodturning | |||
Drag bit, button bit, cross bit, diamond core bit, core barrel | Woodturning |