How are single socket spurs adequately protected on a 32A ring?
In a bout of man flu, I lay in bed wondering: If the MCB is supposed
to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. ? Cheers, David. |
#2
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On 15/12/10 19:54, David Robinson wrote:
In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. ? Cheers, David. Fuse in the plug at max of 13A. Odd as it may seem, overload protection *can* exist downstream as well as upstream. In the case or a short circuit in the back of the socket, the 32A breaker will still protect the cable (ie interrupt the current before the cable overheats). -- Tim Watts |
#3
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
David Robinson wrote:
In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. The short version - You have to consider the difference between overcurrent protection and fault protection. If an MCB is used for overcurrent protection then the circuit has to be capable of running at the full current allowed by the MCB. For a B type MCB this is 1.45 times the rating of the MCB. If the MCB is to be used only for fault current protection (ie a short circuit) then the cable only needs to be able to pass the short circuit current long enough to allow the MCB to trip within the required times when there is a fault. A ring from 2.5 T&E is capable of meeting the 32 x 1.45 current overload protection that a B type MCB provides. Now a spur from a ring is "self" overcurrent protecting as is is only allowed to feed 1 single socket or 1 double socket. The maximum normal current that you get down this spur is 26A (assuming a double socket loaded to the maximum) which is less than the 27A capacity of 2.5 T&E when clipped direct (or buried in plaster) so there is no overcurrent problem and the MCB is now only needed for short circuit protection to protect the spur. However if there is a short on the spur (nail, angle grinder etc) then the resistance reading at the end of the spur must be low enough to trip the MCB in the times required for a short circuit. The resistance reading is made up from the supply impedance plus the cable impedance, so the longer the length of the spur the greater the chance that the spur is not compliant and may not clear a short in the required time. -- Cheers Adam |
#4
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On Dec 15, 7:57*pm, Tim Watts wrote:
On 15/12/10 19:54, David Robinson wrote: In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. ? Cheers, David. Fuse in the plug at *max of 13A. Odd as it may seem, overload protection *can* exist downstream as well as upstream. In the case or a short circuit in the back of the socket, the 32A breaker will still protect the cable (ie interrupt the current before the cable overheats). Thanks Tim. So on a 20A radial, the 20A is to protect against overloads (lots of "up to 13A" loads, potentially causing damage over time without ever tripping a 32A) whereas a short circuit would generate enough current to trip a 32A before the cable suffered harm? Where can I find that calculation? I saw those MCB and fuse trip-time vs current graphs the posted the other week, but can't remember reading a shot circuit disconnect time requirement. Do I need to change my 40A to a 32A, or leave it as it is? Cheers, David. |
#5
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On Dec 15, 8:25*pm, "ARWadsworth"
wrote: David Robinson wrote: In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. The short version - You have to consider the difference between overcurrent protection and fault protection. If an MCB is used for overcurrent protection then the circuit has to be capable of running at the full current allowed by the MCB. For a B type MCB this is 1.45 times the rating of the MCB. If the MCB is to be used only for fault current protection (ie a short circuit) then the cable only needs to be able to pass the short circuit current long enough to allow the MCB to trip within the required times when there is a fault. A ring from 2.5 T&E is capable of meeting the 32 x 1.45 current overload protection that a B type MCB provides. Now a spur from a ring is "self" overcurrent protecting as is is only allowed to feed 1 single socket or 1 double socket. The maximum normal current that you get down this spur is 26A (assuming a double socket loaded to the maximum) which is less than the 27A capacity of *2.5 T&E when clipped direct (or buried in plaster) so there is no overcurrent problem and the MCB is now only needed for short circuit protection to protect the spur. However if there is a short on the spur (nail, angle grinder etc) then the resistance reading at the end of the spur must be low enough to trip the MCB in the times required for a short circuit. The resistance reading is made up from the supply impedance plus the cable impedance, so the longer the length of the spur the greater the chance that the spur is not compliant and may not clear a short in the required time. brilliantly clear - thanks Adam. Cheers, David. |
#6
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
David Robinson wrote:
On Dec 15, 7:57 pm, Tim Watts wrote: On 15/12/10 19:54, David Robinson wrote: In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. ? Cheers, David. Fuse in the plug at max of 13A. Odd as it may seem, overload protection *can* exist downstream as well as upstream. In the case or a short circuit in the back of the socket, the 32A breaker will still protect the cable (ie interrupt the current before the cable overheats). Thanks Tim. So on a 20A radial, the 20A is to protect against overloads (lots of "up to 13A" loads, potentially causing damage over time without ever tripping a 32A) whereas a short circuit would generate enough current to trip a 32A before the cable suffered harm? NO. A 20 radial is a circuit with a 20A MCB. A spur from a 32A ring is a different thing. ( my other post did not make that one clear) Where can I find that calculation? I saw those MCB and fuse trip-time vs current graphs the posted the other week, but can't remember reading a shot circuit disconnect time requirement. http://wiki.diyfaq.org.uk/index.php?title=Fuse for the graphs. Do I need to change my 40A to a 32A, or leave it as it is? I would change it. Far easier than doing calculations. However I would not use the 2.5 T&E for use with an electric cooker without making some very accurate calculations. -- Adam |
#7
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"ARWadsworth" wrote in message ... Do I need to change my 40A to a 32A, or leave it as it is? I would change it. Far easier than doing calculations. However I would not use the 2.5 T&E for use with an electric cooker without making some very accurate calculations. Its self protecting exactly as a spur on a 32A ring is (it only has a single 13 socket). I would change it too, most electricians would reject it as they don't know how to do the calculations and its just easier to use the regs than to explain why its OK. |
#8
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
"ARWadsworth" wrote in message ... Do I need to change my 40A to a 32A, or leave it as it is? I would change it. Far easier than doing calculations. However I would not use the 2.5 T&E for use with an electric cooker without making some very accurate calculations. Its self protecting exactly as a spur on a 32A ring is (it only has a single 13 socket). Yes it is at the moment, but it will not be if the OP installs an electric cooker, and he has hinted that he may do so. I would change it too, most electricians would reject it as they don't know how to do the calculations and its just easier to use the regs than to explain why its OK. (the regs tell you what is OK and they give you the calculations, the regs and what is OK are inclusive not exclusive) I have to take the bigger view. I might be able to show that a certain cooker is safe when installed with the 2.5 T&E, however the customer may change the cooker for a higher powered one or sell the house and a new owner may fit a higher powered cooker. I would rather see a cooker circuit correctly fused to the actual cable rating and not to some diversity calculations that mean nothing when a cooker is swapped. -- Adam |
#9
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"ARWadsworth" wrote in message ... dennis@home wrote: "ARWadsworth" wrote in message ... Do I need to change my 40A to a 32A, or leave it as it is? I would change it. Far easier than doing calculations. However I would not use the 2.5 T&E for use with an electric cooker without making some very accurate calculations. Its self protecting exactly as a spur on a 32A ring is (it only has a single 13 socket). Yes it is at the moment, but it will not be if the OP installs an electric cooker, and he has hinted that he may do so. I would change it too, most electricians would reject it as they don't know how to do the calculations and its just easier to use the regs than to explain why its OK. (the regs tell you what is OK and they give you the calculations, the regs and what is OK are inclusive not exclusive) You can do anything you like if you are competent to do the calcs, I believe that's in the regs somewhere. The majority of electricians mean the onsite guide when they refer to the regs. I have to take the bigger view. I might be able to show that a certain cooker is safe when installed with the 2.5 T&E, however the customer may change the cooker for a higher powered one or sell the house and a new owner may fit a higher powered cooker. I would rather see a cooker circuit correctly fused to the actual cable rating and not to some diversity calculations that mean nothing when a cooker is swapped. That I agree with.. diversity is a PITA. It doesn't even work when someone swaps a few single plugs for doubles in a ring and then plugs in a few fan heaters at one end. That sort of things makes rings run out of spec. I suppose its regarded as unlikely that some will use 9kW of heating in a room, even one they are trying to dry out after the recent floods. ;-) |
#10
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
I would change it too, most electricians would reject it as they don't know how to do the calculations and its just easier to use the regs than to explain why its OK. (the regs tell you what is OK and they give you the calculations, the regs and what is OK are inclusive not exclusive) You can do anything you like if you are competent to do the calcs, I believe that's in the regs somewhere. The majority of electricians mean the onsite guide when they refer to the regs. The same rules and regs apply to both the full BS7671 and the OSG. I have to take the bigger view. I might be able to show that a certain cooker is safe when installed with the 2.5 T&E, however the customer may change the cooker for a higher powered one or sell the house and a new owner may fit a higher powered cooker. I would rather see a cooker circuit correctly fused to the actual cable rating and not to some diversity calculations that mean nothing when a cooker is swapped. That I agree with.. diversity is a PITA. It doesn't even work when someone swaps a few single plugs for doubles in a ring and then plugs in a few fan heaters at one end. That makes no difference in most cases. Most people do not have a massive store of fan heaters ready to be used. That sort of things makes rings run out of spec. For a short time that will not matter. I suppose its regarded as unlikely that some will use 9kW of heating in a room, even one they are trying to dry out after the recent floods. ;-) But you know damn well the correct tool is a dehumidifer not a heater for this job. -- Adam |
#11
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"ARWadsworth" wrote in message ... I suppose its regarded as unlikely that some will use 9kW of heating in a room, even one they are trying to dry out after the recent floods. ;-) But you know damn well the correct tool is a dehumidifer not a heater for this job. OK, 9 kW of heating + 1kW of dehumidifier. |
#12
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
"ARWadsworth" wrote in message ... I suppose its regarded as unlikely that some will use 9kW of heating in a room, even one they are trying to dry out after the recent floods. ;-) But you know damn well the correct tool is a dehumidifer not a heater for this job. OK, 9 kW of heating + 1kW of dehumidifier. But that never happens. I doubt that three 3kW fan heaters will stay on for long if they are in the same room. They have thermostats. -- Adam |
#13
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"ARWadsworth" wrote in message ... dennis@home wrote: "ARWadsworth" wrote in message ... I suppose its regarded as unlikely that some will use 9kW of heating in a room, even one they are trying to dry out after the recent floods. ;-) But you know damn well the correct tool is a dehumidifer not a heater for this job. OK, 9 kW of heating + 1kW of dehumidifier. But that never happens. I doubt that three 3kW fan heaters will stay on for long if they are in the same room. They have thermostats. The problem being that there is no way to know, it might be a big room with the doors and windows open with a gale blowing through, they would stay on then. The reason why I brought it up is because I have seen it happen BTW. Not everyone would think about running an extension lead from somewhere else to make sure there wasn't a problem. They would leave it running until the room was dry or it all failed. |
#14
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
"ARWadsworth" wrote in message ... dennis@home wrote: "ARWadsworth" wrote in message ... I suppose its regarded as unlikely that some will use 9kW of heating in a room, even one they are trying to dry out after the recent floods. ;-) But you know damn well the correct tool is a dehumidifer not a heater for this job. OK, 9 kW of heating + 1kW of dehumidifier. But that never happens. I doubt that three 3kW fan heaters will stay on for long if they are in the same room. They have thermostats. The problem being that there is no way to know, it might be a big room with the doors and windows open with a gale blowing through, they would stay on then. The reason why I brought it up is because I have seen it happen BTW. Not everyone would think about running an extension lead from somewhere else to make sure there wasn't a problem. They would leave it running until the room was dry or it all failed. You are missing one important point. Ring mains are designed for normal domestic use not for clearing floods. -- Adam |
#15
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"ARWadsworth" wrote in message ... You are missing one important point. Ring mains are designed for normal domestic use not for clearing floods. Shame that very few know that it can be dangerous, something that could be designed out. |
#16
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
"ARWadsworth" wrote in message ... You are missing one important point. Ring mains are designed for normal domestic use not for clearing floods. Shame that very few know that it can be dangerous, something that could be designed out. The IET must be stupid. Why did they not let you design the new regs for them? -- Adam |
#17
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"ARWadsworth" wrote in message ... dennis@home wrote: "ARWadsworth" wrote in message ... You are missing one important point. Ring mains are designed for normal domestic use not for clearing floods. Shame that very few know that it can be dangerous, something that could be designed out. The IET must be stupid. Why did they not let you design the new regs for them? So you don't think they got the compromise between cost and safety on ring mains wrong then? That would be why they added radials with breakers that actually match the cables because they didn't need to. Who knows, sometime in the future when all the old electricians have retired rings will finally die. |
#18
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On 16/12/10 08:58, dennis@home wrote:
"ARWadsworth" wrote in message ... dennis@home wrote: "ARWadsworth" wrote in message ... You are missing one important point. Ring mains are designed for normal domestic use not for clearing floods. Shame that very few know that it can be dangerous, something that could be designed out. The IET must be stupid. Why did they not let you design the new regs for them? So you don't think they got the compromise between cost and safety on ring mains wrong then? That would be why they added radials with breakers that actually match the cables because they didn't need to. Who knows, sometime in the future when all the old electricians have retired rings will finally die. Rings have notable safety benefits over radials, namely that the CPC is doubled up over two paths. Also, show me a practical 32A radial with multiple socket drops noting the BS standard restrictions on terminal capacities of socket and FCU accessories. -- Tim Watts |
#19
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"Tim Watts" wrote in message ... Rings have notable safety benefits over radials, namely that the CPC is doubled up over two paths. They also have several safety problems. They can have latent faults that the householder will only find out about when its too late. Things like broken earths (which negates your above argument) can just be there undetected for years unless you have regular inspections and real continuity tests. This isn't a solution though as the act of doing the test will make the faults more likely to occur. Also, show me a practical 32A radial with multiple socket drops noting the BS standard restrictions on terminal capacities of socket and FCU accessories. Why do you need a 32A radial? I don't think you will find them in the OSG. 4mm will do the job with many accessories and you could always crimp in a joint if the accessory is to small. I wouldn't bother with a 32A radial to replace a ring. |
#20
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On 16/12/10 09:38, dennis@home wrote:
"Tim Watts" wrote in message ... Rings have notable safety benefits over radials, namely that the CPC is doubled up over two paths. They also have several safety problems. They can have latent faults that the householder will only find out about when its too late. Things like broken earths (which negates your above argument) can just be there undetected for years unless you have regular inspections and real continuity tests. This isn't a solution though as the act of doing the test will make the faults more likely to occur. Also, show me a practical 32A radial with multiple socket drops noting the BS standard restrictions on terminal capacities of socket and FCU accessories. Why do you need a 32A radial? Because 20A is **** all use to me. I do not want to be thinking - are these sockets on the same 20A circuit - damn I cannot plug this 3kW appliance in because there are already two high load appliances on that circuit. I already also have enough RCBOs in my CU - I don't have space for even more, let alone the expense. I don't think you will find them in the OSG. Bugger the OSG, it is a guide only. I think you WILL find them in Appendix 15 of the 17th. 4mm will do the job with many accessories 4mm doesn't cut it for Reference Method B (a common installation method in my house). and you could always crimp in a joint if the accessory is to small. I wouldn't bother with a 32A radial to replace a ring. -- Tim Watts |
#21
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On 16/12/10 09:38, dennis@home wrote:
This isn't a solution though as the act of doing the test will make the faults more likely to occur. ********. Have you ever done any testing and inspection work? Inspections will disturb the accessory, so you do that first[1]. The testing requires disturbing the connections at the CU only and the first test you do is an end-end test on all 3conductors which will pick up this problem. In fact that is the one test you could validly do with any old cheap multimeter or even a bulb and battery. The next test is the 500V inter-conductor insulation test. Once those have passed, you now know that the ring is continuous and has no single wiring error (though it may have multiple erros that cancel. The 3rd set of figure-8 tests prove the absence of any wiring error or open circuit fault and demonstrate the soundness of the circuit both under load and fault conditions for all bar the most obscure and unlikely problem scenarios. As long as you can reinsert the wires into the CU correctly you are good. I add an extra test of my own which is to do a few live loop impedance tests afterwards which would pick up any issues there. [1] As we are talking about socket circuits. Lighting circuits are more of a PITA as you need to bridge out any electronic devices which unfortunately means fiddling with the accessories after the tests are done. -- Tim Watts |
#22
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
"Tim Watts" wrote in message ... Rings have notable safety benefits over radials, namely that the CPC is doubled up over two paths. They also have several safety problems. They can have latent faults that the householder will only find out about when its too late. Things like broken earths (which negates your above argument) can just be there undetected for years unless you have regular inspections and real continuity tests. This isn't a solution though as the act of doing the test will make the faults more likely to occur. Also, show me a practical 32A radial with multiple socket drops noting the BS standard restrictions on terminal capacities of socket and FCU accessories. Why do you need a 32A radial? I don't think you will find them in the OSG. Pages 49 and 158 to name two references to 32A radials in the OSG. -- Adam |
#23
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
"ARWadsworth" wrote in message ... dennis@home wrote: "ARWadsworth" wrote in message ... You are missing one important point. Ring mains are designed for normal domestic use not for clearing floods. Shame that very few know that it can be dangerous, something that could be designed out. The IET must be stupid. Why did they not let you design the new regs for them? So you don't think they got the compromise between cost and safety on ring mains wrong then? No, I believe that the compromise is very good and we have a good safe system. That would be why they added radials with breakers that actually match the cables because they didn't need to. I am not sure what you mean. All circuits have breakers designed to match the cable. Who knows, sometime in the future when all the old electricians have retired rings will finally die. Maybe, it is suggested everytime there is an update to the regs. -- Adam |
#24
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On Dec 16, 12:44*am, John Rumm wrote:
On 15/12/2010 19:54, David Robinson wrote: In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? This is one of those occasions where the responsibility for overload protection and fault protection can be split. The fault protection (i.e. very high short circuit currents) must always be at the origin of the circuit, however the overload protection can be at the load end in some cases. (others would include a 3A drop wire to a pendent fixing on a 6A protected lighting circuit for example - the largest bulb you can get won't come close to 3A so no chance of overload)) An unfused spur can power a total of one double or single socket. The diverse load of a double socket is taken as being 20A. (That is lower than the current carrying capacity of 2.5mm^2 T&E in all but the most adverse installation methods). Even the theoretically possible 26A is just under the maximum rating when clipped direct or buried in masonry. * So the conditions at the load end (i.e. only one double socket) enforce the overload protection. The next question concerns the fault protection. i.e. what happens when you nail through the cable or some other drastic fault occurs. Here you will get a fault current that limited only by the the resistance of the wires themselves and that of the supply and earth connections. This is one of the reasons for their being a maximum cable length specified for most circuits - to ensure the so called "Earth Loop Impedance" (i.e. round trip resistance from supply through circuit wires, and to earth) can't get too high. A 32A breaker will typically need as much as 160A to open "instantly" i.e. on the magnetic part of its trip response. Instant in this case means 0.1 secs or less. See charts he http://wiki.diyfaq.org.uk/index.php?...ypes_B.2CC.2CD Lets say you work out that your prospective fault current is going to be 200A, you now need to assess[1] what happens when you try and stick that down the skimpy 1.5mm^2 earth wire. Needless to say that will get hot, and quickly. Its also going to be heating so fast that the natural heat losses to its surroundings are going to be negligible during the time scale we are interested in. So we have what can be though of as adiabatic heating. What you need to check is that it won't melt before its done its job and tripped the MCB. For this you use what is called the adiabatic equation: s = sqrt( I^2 x t ) / k, where s = the minimum cross sectional area of copper required in the conductor, and k is a factor specific to the the type of cable (115 in the case of PVC T&E). So 200A, a check of the MCB charts says this is plenty to open the breaker in 0.1 secs. So our sum becomes s = ( 200 x 200 x 0.1 ) / 115 = 0.56mm^2, which is significantly less than the 1.5mm^2 we actually have an hence is ok. [1] In reality you can skip this stage since these are "standard" circuit designs where as long as you obay the length limits, you know the design "works". You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). Current carrying capacities are listed he http://wiki.diyfaq.org.uk/index.php?title=Cables#T.26E I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. Well the overload protection is achieved by the 13A maximum load on the socket. The only other question is will it be adequately fault protected. Assuming the rest of the circuit is a more substantial cable, the the loop impedance ought to be fairly low to that point. Hence it seems reasonable to assume you will get *fault current in excess of 200A. That will open the 40A circuit breaker in 0.1 secs, and we know from the sum above that the wire will handle it. Yes, the rest of the circuit is 6mm T+E, from CU to cooker switch (inc socket) to cooker outlet. It's only the last jump from cooker outlet to adjacent single socket that's 2.5mm. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. Indeed. In fact due to the nature of the load presented by cookers, even a very powerful cooker with a theoretical peak load over 60A will usually be fine on a 32A circuit. (cooker diversity is calculated as 10A plus 30% of the remainder). So a 60A cooker would need a circuit provisioned for 10A + 0.3 x 50 = 25A, or 30A if there is also a socket on the cooker point. IIRC the cooker claims to be 13A but instructs use of heat resistant 2.5mm cable into a cooker outlet, not a 13A plug. So I've followed those instructions. Cheers, David. |
#25
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On Dec 15, 9:48*pm, "ARWadsworth"
wrote: dennis@home wrote: "ARWadsworth" wrote in message ... Do I need to change my 40A to a 32A, or leave it as it is? I would change it. Far easier than doing calculations. However I would not use the 2.5 T&E for use with an electric cooker without making some very accurate calculations. Its self protecting exactly as a spur on a 32A ring is (it only has a single 13 socket). Yes it is at the moment, but it will not be if the OP installs an electric cooker, and he has hinted that he may do so. No, see my reply to John: the rest of the circuit is 6mm T+E, and the cooker will be run from a cooker outlet, not the socket. Cheers, David. |
#26
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On 16/12/10 10:31, David Robinson wrote:
IIRC the cooker claims to be 13A but instructs use of heat resistant 2.5mm cable into a cooker outlet, not a 13A plug. So I've followed those instructions. 13A plugtops do have quite low specified limits on operating temperature. Whilst it won't be a problem for a gas cooker that only draws power for a light, spark and maybe a low powered warming cupboard, it might be anticipated to be an issue for a cooker that actually draws 3kW (eg dual fuel with a lumpy electric oven). -- Tim Watts |
#27
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"Tim Watts" wrote in message ... On 16/12/10 09:38, dennis@home wrote: "Tim Watts" wrote in message ... Rings have notable safety benefits over radials, namely that the CPC is doubled up over two paths. They also have several safety problems. They can have latent faults that the householder will only find out about when its too late. Things like broken earths (which negates your above argument) can just be there undetected for years unless you have regular inspections and real continuity tests. This isn't a solution though as the act of doing the test will make the faults more likely to occur. Also, show me a practical 32A radial with multiple socket drops noting the BS standard restrictions on terminal capacities of socket and FCU accessories. Why do you need a 32A radial? Because 20A is **** all use to me. I do not want to be thinking - are these sockets on the same 20A circuit - damn I cannot plug this 3kW appliance in because there are already two high load appliances on that circuit. But you need to do that if you want to plug them into one end of a 2.5 mm ring, even more so with three appliances. It causes imbalance currents in the ring that can take them out of spec. Its why fixed heating shouldn't go on a ring, they don't like high load stuff at one end. |
#28
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"Tim Watts" wrote in message ... On 16/12/10 09:38, dennis@home wrote: This isn't a solution though as the act of doing the test will make the faults more likely to occur. ********. Have you ever done any testing and inspection work? Inspections will disturb the accessory, so you do that first[1]. The testing requires disturbing the connections at the CU only and the first test you do is an end-end test on all 3conductors which will pick up this problem. In fact that is the one test you could validly do with any old cheap multimeter or even a bulb and battery. The next test is the 500V inter-conductor insulation test. Once those have passed, you now know that the ring is continuous and has no single wiring error (though it may have multiple erros that cancel. The 3rd set of figure-8 tests prove the absence of any wiring error or open circuit fault and demonstrate the soundness of the circuit both under load and fault conditions for all bar the most obscure and unlikely problem scenarios. As long as you can reinsert the wires into the CU correctly you are good. I add an extra test of my own which is to do a few live loop impedance tests afterwards which would pick up any issues there. [1] As we are talking about socket circuits. Lighting circuits are more of a PITA as you need to bridge out any electronic devices which unfortunately means fiddling with the accessories after the tests are done. every time you disconnect the wire and reconnect it you work harden the copper and make it more likely to fail due to passing traffic, etc. If the consumer unit was correctly designed it would have test links so you could do the tests without disconnecting the wires. But why do things right when you can do them cheap? |
#29
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"ARWadsworth" wrote in message ... Who knows, sometime in the future when all the old electricians have retired rings will finally die. Maybe, it is suggested everytime there is an update to the regs. That would be because a lot of engineers don't think rings are safe. |
#30
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On Dec 15, 8:25*pm, "ARWadsworth"
wrote: David Robinson wrote: In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. The short version - You have to consider the difference between overcurrent protection and fault protection. Queue :::Jerry::: MBQ |
#31
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
Man at B&Q wrote:
On Dec 15, 8:25 pm, "ARWadsworth" wrote: David Robinson wrote: In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. The short version - You have to consider the difference between overcurrent protection and fault protection. Queue :::Jerry::: And Dennis. -- Adam |
#32
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On 16/12/10 11:53, dennis@home wrote:
every time you disconnect the wire and reconnect it you work harden the copper and make it more likely to fail due to passing traffic, etc. If the consumer unit was correctly designed it would have test links so you could do the tests without disconnecting the wires. But why do things right when you can do them cheap? Whilst I don't disagree with the sentiment, a decently laid out CU isn't too bad - and your idea would require at least 3 terminals per current terminal (L,N and PE) all with per terminal links and test points - so that's 9 links and test points per device. I wish that all dimmers came with a small shorting plug though, that could be inserted from the back of the device - that would save some faffing. -- Tim Watts |
#33
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
"ARWadsworth" wrote in message ... Who knows, sometime in the future when all the old electricians have retired rings will finally die. Maybe, it is suggested everytime there is an update to the regs. That would be because a lot of engineers don't think rings are safe. But 60 years of history prove them wrong. Are you going to clarify what you meant by "That would be why they added radials with breakers that actually match the cables because they didn't need to." -- Adam |
#34
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"David Robinson" wrote in message ... On Dec 15, 9:48 pm, "ARWadsworth" wrote: dennis@home wrote: "ARWadsworth" wrote in message ... Do I need to change my 40A to a 32A, or leave it as it is? I would change it. Far easier than doing calculations. However I would not use the 2.5 T&E for use with an electric cooker without making some very accurate calculations. Its self protecting exactly as a spur on a 32A ring is (it only has a single 13 socket). Yes it is at the moment, but it will not be if the OP installs an electric cooker, and he has hinted that he may do so. No, see my reply to John: the rest of the circuit is 6mm T+E, and the cooker will be run from a cooker outlet, not the socket. It doesn't actually significantly change the level of protection if you fit a full power cooker. It does change the possibility of tripping the circuit as it allows more current to be drawn. However it is still safe (well as safe as a spur on a ring) as there is no way to overload it that won't trip the circuit. You will trip the plug fuse if you overload the socket whatever cooker you have and trip the MCB if you overload the total circuit. The same is true for if you fit a double socket but I wouldn't put a double on a 2.5 mm spur in a kitchen, someone is bound to plug in a big tea urn and a combo microwave and overload it for a couple of hours. That's what Murphy told me. There is quite a lot of difference between it being safe and it being user friendly, you don't want circuits to trip frequently to maintain safety. |
#35
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
On Dec 16, 12:07*pm, "ARWadsworth"
wrote: Man at B&Q wrote: On Dec 15, 8:25 pm, "ARWadsworth" wrote: David Robinson wrote: In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. The short version - You have to consider the difference between overcurrent protection and fault protection. Queue :::Jerry::: And Dennis. You don't think... MBQ |
#36
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
Man at B&Q wrote:
On Dec 16, 12:07 pm, "ARWadsworth" wrote: Man at B&Q wrote: On Dec 15, 8:25 pm, "ARWadsworth" wrote: David Robinson wrote: In a bout of man flu, I lay in bed wondering: If the MCB is supposed to protect the cable to the fitting, and the fuse in the plug is supposed to protect the cable to the appliance, how is the single bit of 2.5mm T+E run to a single socket spur adequately protected by anything? You've basically got 2 bits of 2.5mm in parallel (usually unequal lengths), feeding a single bit of 2.5mm. 32A MCB. Whereas if it was a standard radial circuit, you'd have just the single bit of 2.5mm, and you'd only be allowed a 20A MCB on it. (IIRC they even dropped the 2.5mm rating down to 18A, which is "correct" in accordance with the calculations, but then increased it back to 20A because that's what everyone does anyway). I'm not worried. I just don't see the logic. I have 10cm of 2.5mm T+E protected by a 40A MCB on the cooker circuit (feeding a socket that can only supply the gas hob ignition) and that seems very wrong too - but wiring a socket in 6mm is just too painful. However, the cooker circuit may yet drop back to 32A (because I suspect that's all it needs) which makes it no worse than the socket spur discussed above. The short version - You have to consider the difference between overcurrent protection and fault protection. Queue :::Jerry::: And Dennis. You don't think... Well they certainly don't...... -- Adam |
#37
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"Tim Watts" wrote in message ... On 16/12/10 11:53, dennis@home wrote: every time you disconnect the wire and reconnect it you work harden the copper and make it more likely to fail due to passing traffic, etc. If the consumer unit was correctly designed it would have test links so you could do the tests without disconnecting the wires. But why do things right when you can do them cheap? Whilst I don't disagree with the sentiment, a decently laid out CU isn't too bad - and your idea would require at least 3 terminals per current terminal (L,N and PE) all with per terminal links and test points - so that's 9 links and test points per device. Less if its not a ring though. I wish that all dimmers came with a small shorting plug though, that could be inserted from the back of the device - that would save some faffing. You should invent one.. a crimp on termination pin for each wire with a suitable socket should do it. -- Tim Watts |
#38
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
"ARWadsworth" wrote in message ... dennis@home wrote: "ARWadsworth" wrote in message ... Who knows, sometime in the future when all the old electricians have retired rings will finally die. Maybe, it is suggested everytime there is an update to the regs. That would be because a lot of engineers don't think rings are safe. But 60 years of history prove them wrong. How does it? Nobody knows how many faulty rings there are as the householder doesn't know and very few are ever checked. There could be 10 there could be 100,000, until people get hurt no one cares. Are you going to clarify what you meant by "That would be why they added radials with breakers that actually match the cables because they didn't need to." It is illogical to rely on downstream breakers to protect up stream cables. It makes modification to the circuit potentially dangerous. People do modify the circuits by putting the wrong fuse in plugs (including nails) rendering them useless for protecting the upstream circuit against overload. There was even a large batch of "genuine" fuses for plugs that didn't protect the circuit a few decades back. These led to certification being required to show batch testing had been done. God knows how many of these faulty fuses are still out there. Do you check the plug fuse for certification when you come across one? |
#39
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
dennis@home wrote:
"ARWadsworth" wrote in message ... dennis@home wrote: "ARWadsworth" wrote in message ... Who knows, sometime in the future when all the old electricians have retired rings will finally die. Maybe, it is suggested everytime there is an update to the regs. That would be because a lot of engineers don't think rings are safe. But 60 years of history prove them wrong. How does it? Nobody knows how many faulty rings there are as the householder doesn't know and very few are ever checked. There could be 10 there could be 100,000, until people get hurt no one cares. Ditto for faulty radials. Are you going to clarify what you meant by "That would be why they added radials with breakers that actually match the cables because they didn't need to." It is illogical to rely on downstream breakers to protect up stream cables. It makes modification to the circuit potentially dangerous. Only if you do not know what you are doing. People do modify the circuits by putting the wrong fuse in plugs (including nails) rendering them useless for protecting the upstream circuit against overload. Non of which alters the load on the spur or makes any difference at all to a fault current on the spur. There was even a large batch of "genuine" fuses for plugs that didn't protect the circuit a few decades back. These led to certification being required to show batch testing had been done. God knows how many of these faulty fuses are still out there. Do you check the plug fuse for certification when you come across one? And the relevance to spurs and radials is? -- Adam |
#40
Posted to uk.d-i-y
|
|||
|
|||
How are single socket spurs adequately protected on a 32A ring?
Tim Watts wrote:
On 16/12/10 09:38, dennis@home wrote: "Tim Watts" wrote in message ... Rings have notable safety benefits over radials, namely that the CPC is doubled up over two paths. They also have several safety problems. They can have latent faults that the householder will only find out about when its too late. Things like broken earths (which negates your above argument) can just be there undetected for years unless you have regular inspections and real continuity tests. This isn't a solution though as the act of doing the test will make the faults more likely to occur. Also, show me a practical 32A radial with multiple socket drops noting the BS standard restrictions on terminal capacities of socket and FCU accessories. Why do you need a 32A radial? Because 20A is **** all use to me. 20A radials often use more cable when installing than a ring, offer very little in the way of diversity and require just as much (if not more) work to install than a ring. There are times when they are useful but not very often. -- Adam |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
uses of 4mm TWE / single kitchen ring | UK diy | |||
Spurs from a ring | UK diy | |||
Spurs off a ring main | UK diy | |||
socket from the ring main | UK diy | |||
Is my main socket ring too big? | UK diy |