UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10
Default new better clearer photos posted see link below

http://picasaweb.google.co.uk/simon....terTankPhotos#

this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,120
Default new better clearer photos posted see link below

On 08/10/2010 10:55, Simon wrote:
http://picasaweb.google.co.uk/simon....terTankPhotos#

this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!



OK, that tells us a bit more.

One thing which may be significant is the gate valve which can be seen
in photos 23 and 29 (among others). The pipe in which that valve is
fitted appears to be some sort of by-pass across the cylinder's heating
coil - maybe so as to provide a flow path when the TRV-like valve
closes. How open or closed is that gate valve? (Count the number of
turns required to close it from the current position, and then the turns
required to open it fully from closed, to give a measure of its current
state). If fully open, it provides a dead short for the coil - with the
result that nearly all the primary water will go down the by-pass and
very little through the coil - which could well explain your problem.

If it's open a long way (or fully open even) try running with it only
open a little - maybe half a turn from closed) and see what happens.
If you *need* a by-pass at all - and you may or may not depending on the
requirements of the boiler and on how the system 'controls' are
configured - you'd be far better off with a spring-loaded auto by-pass
valve which only opens when it needs to, rather than a manual gate valve.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,419
Default new better clearer photos posted see link below

In message , Roger Mills
writes
On 08/10/2010 10:55, Simon wrote:
http://picasaweb.google.co.uk/simon....terTankPhotos#

this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!



OK, that tells us a bit more.

One thing which may be significant is the gate valve which can be seen
in photos 23 and 29 (among others). The pipe in which that valve is
fitted appears to be some sort of by-pass across the cylinder's heating
coil - maybe so as to provide a flow path when the TRV-like valve
closes. How open or closed is that gate valve? (Count the number of
turns required to close it from the current position, and then the
turns required to open it fully from closed, to give a measure of its
current state). If fully open, it provides a dead short for the coil -
with the result that nearly all the primary water will go down the
by-pass and very little through the coil - which could well explain
your problem.


I'm not sure if we ever heard if the tank was actually getting hot or
not (or was there some other problem after the tank with the HW) - a
quick hand test on the metal of the tank will confirm. (near the top of
the HW tank obviously)

If it isn't then the capillary valve would seem like a prime candidate
for failure of some sort (either valve or capillary tube/sensor).
Presumably they are like a TRV inside. If you remove the top (ours has a
knurled ring at the base of the body you unscrew) then presumably it
just leaves the valve open. That would be my first try.

I'm not sure about how they actually work, but assuming they have a pin
operated by the capillary senor, this could be stuck like the ones in
TRV's do.
--
Chris French

  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 854
Default new better clearer photos posted see link below


Simon wrote:

http://picasaweb.google.co.uk/simon....terTankPhotos#

this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!


The photos strongly suggest you have the same sort of heating system
that we've just left behind.

This is a boiler that heats primary water (usually fed by a jockey
tank somewhere above the hot water tank) that circulates through a
heating coil in the HWT to provide domestic hot water, and via a gate
valve to the radiator system.

Helpfully, the photos show that this valve is marked 'heating system'
on the wall just above it. It's a racing cert that all your radiators
have thermostatic valves on them.

Normally, primary water from the boiler will circulate through the
heating coil in the HWT until the capillary valve (the one with the
thin pipe going to the sensor strapped to the tank) shuts down at the
temperature set by control knob.

Also, if the heating gate valve is opened, primary water will
circulate through the radiators until their TRVs shut.

With both the capillary valve and central heating shut off due to
reaching the set temperatures, the pump will still be running as it is
controlled by a timer. In this case the pump must not run in the
'stalled' condition, it needs to pump water continuously. This is
obtained through a bypass controlled by another gate valve, almost
certainly the one on the vertical pipe running towards the top of the
HWT.

As others have pointed out, if the bypass valve is too 'open' water
will preferentially pass through it rather than the heating coil in
the HWT, leading to a lack of domestic hot water.

Another problem is a fault with the capillary valve; either it is
stuck shut and not allowing primary to flow through the heating coil,
or the capillary or sensor is faulty leading to the valve not opening.

Try this sequence of fault-finding:

Unscrew the knurled ring holding the capillary valve head to the body,
and gently place to one side. If there is a plunger pin on the valve
body, gently try pulling it upwards with pair of pliers to see if it
is free. Use a folded rag to avoid marking the pin. Wick some WD40
down the shaft of the pin.

If there is no pin in sight, leave the valve head off.

Now shut the 'heating system' valve, ensure the boiler thermostat is
nat about two-thirds of maximum.

Turn on the system at the timer/control clock.

If the pipe both sides of the capillary valve gets hot, then water
will be flowing through it and the heating coil, and hopefully heating
the DHW. If there is no or little flow of hot water past the capillary
valve after say ten minutes (feel the pipes as far away from it as
possible), shut the gate valve on the vertical pipe, and then open
half-a turn. See if this makes any difference to the water hopefully
flowing past the capillary valve.

With the system running, the bypass valve almost shut, yet no hot
water flowing past the capillary valve, a fault in the body of the
latter is almost certain, suggesting replacement is necessary.

If hot water is passing the capillary valve, screw the valve head back
on and set it at maximum. Wait some minutes to see if hot water is
still passing through it; after ten or fifteen minutes the water in
the HWT should be heating up. If so, turn the setting to minimum. If
not, there may be a fault in the valve head, again suggesting
replacement is necessary.

Now. listening to the heating pump, shut the bypass gate valve. The
speed of the motor may increase as it is now doing nothing; crack open
the valve slowly until the speed of the motor drops to almost 'normal'
(when it is pumping hard). Although water will be bypassing the
heating coil, it should nevertheless be a limited amount. This water
is not 'lost', it is merely going back the boiler, but you only need
enough of it to keep the pump happy when it has noting else to do.

Hopefully this will have either shown up faults in the capillary
valve, and set the bypass valve to a reasonable setting.
Unfortunately, gate valves can get sludged up and although apparently
shut, may in reality still be partially open, confusing the picture.

Nevertheless, give this a try and see what happens - it might get the
system working properly, or at least give some pointers to where the
fault might lie.

If all is well, you can try fine-tuning the system by e.g. increasing
the boiler thermostat setting (quicker heating by the CH circuit) and
the setting on the capillary valve to give the temperature you want.

Good luck!

TF
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,679
Default new better clearer photos posted see link below

On 11 Oct, 17:59, Terry Fields wrote:
Simon wrote:
http://picasaweb.google.co.uk/simon....terTankPhotos#


this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!


The photos strongly suggest you have the same sort of heating system
that we've just left behind.

This is a boiler that heats primary water (usually fed by a jockey
tank somewhere above the hot water tank) that circulates through a
heating coil in the HWT to provide domestic hot water, and via a gate
valve to the radiator system.

Helpfully, the photos show that this valve is marked 'heating system'
on the wall just above it. It's a racing cert that all your radiators
have thermostatic valves on them.

Normally, primary water from the boiler will circulate through the
heating coil in the HWT until the capillary valve (the one with the
thin pipe going to the sensor strapped to the tank) shuts down at the
temperature set by control knob.

Also, if the heating gate valve is opened, primary water will
circulate through the radiators until their TRVs shut.

With both the capillary valve and central heating shut off due to
reaching the set temperatures, the pump will still be running as it is
controlled by a timer. In this case the pump must not run in the
'stalled' condition, it needs to pump water continuously. This is
obtained through a bypass controlled by another gate valve, almost
certainly the one on the vertical pipe running towards the top of the
HWT.

As others have pointed out, if the bypass valve is too 'open' water
will preferentially pass through it rather than the heating coil in
the HWT, leading to a lack of domestic hot water.

Another problem is a fault with the capillary valve; either it is
stuck shut and not allowing primary to flow through the heating coil,
or the capillary or sensor is faulty leading to the valve not opening.

Try this sequence of fault-finding:

Unscrew the knurled ring holding the capillary valve head to the body,
and gently place to one side. If there is a plunger pin on the valve
body, gently try pulling it upwards with pair of pliers to see if it
is free. Use a folded rag to avoid marking the pin. Wick some WD40
down the shaft of the pin.

If there is no pin in sight, leave the valve head off.

Now shut the 'heating system' valve, ensure the boiler thermostat is
nat about two-thirds of maximum.

Turn on the system at the timer/control clock.

If the pipe both sides of the capillary valve gets hot, then water
will be flowing through it and the heating coil, and hopefully heating
the DHW. If there is no or little flow of hot water past the capillary
valve after say ten minutes (feel the pipes as far away from it as
possible), shut the gate valve on the vertical pipe, and then open
half-a turn. See if this makes any difference to the water hopefully
flowing past the capillary valve.

With the system running, the bypass valve almost shut, yet no hot
water flowing past the capillary valve, a fault in the body of the
latter is almost certain, suggesting replacement is necessary.

If hot water is passing the capillary valve, screw the valve head back
on and set it at maximum. Wait some minutes to see if hot water is
still passing through it; after ten or fifteen minutes the water in
the HWT should be heating up. If so, turn the setting to minimum. If
not, there may be a fault in the valve head, again suggesting
replacement is necessary.

Now. listening to the heating pump, shut the bypass gate valve. The
speed of the motor may increase as it is now doing nothing; crack open
the valve slowly until the speed of the motor drops to almost 'normal'
(when it is pumping hard). Although water will be bypassing the
heating coil, it should nevertheless be a limited amount. This water
is not 'lost', it is merely going back the boiler, but you only need
enough of it to keep the pump happy when it has noting else to do.

Hopefully this will have either shown up faults in the capillary
valve, and set the bypass valve to a reasonable setting.
Unfortunately, gate valves can get sludged up and although apparently
shut, may in reality still be partially open, confusing the picture.

Nevertheless, give this a try and see what happens - it might get the
system working properly, or at least give some pointers to where the
fault might lie.

If all is well, you can try fine-tuning the system by e.g. increasing
the boiler thermostat setting (quicker heating by the CH circuit) and
the setting on the capillary valve to give the temperature you want.

Good luck!

TF


good post!
Jim K


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,835
Default new better clearer photos posted see link below

"Jim K" wrote in message
...
On 11 Oct, 17:59, Terry Fields wrote:
Simon wrote:
http://picasaweb.google.co.uk/simon....terTankPhotos#


this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!


The photos strongly suggest you have the same sort of heating system
that we've just left behind.

This is a boiler that heats primary water (usually fed by a jockey
tank somewhere above the hot water tank) that circulates through a
heating coil in the HWT to provide domestic hot water, and via a gate
valve to the radiator system.

Helpfully, the photos show that this valve is marked 'heating system'
on the wall just above it. It's a racing cert that all your radiators
have thermostatic valves on them.

Normally, primary water from the boiler will circulate through the
heating coil in the HWT until the capillary valve (the one with the
thin pipe going to the sensor strapped to the tank) shuts down at the
temperature set by control knob.

Also, if the heating gate valve is opened, primary water will
circulate through the radiators until their TRVs shut.

With both the capillary valve and central heating shut off due to
reaching the set temperatures, the pump will still be running as it is
controlled by a timer. In this case the pump must not run in the
'stalled' condition, it needs to pump water continuously. This is
obtained through a bypass controlled by another gate valve, almost
certainly the one on the vertical pipe running towards the top of the
HWT.

As others have pointed out, if the bypass valve is too 'open' water
will preferentially pass through it rather than the heating coil in
the HWT, leading to a lack of domestic hot water.

Another problem is a fault with the capillary valve; either it is
stuck shut and not allowing primary to flow through the heating coil,
or the capillary or sensor is faulty leading to the valve not opening.

Try this sequence of fault-finding:

Unscrew the knurled ring holding the capillary valve head to the body,
and gently place to one side. If there is a plunger pin on the valve
body, gently try pulling it upwards with pair of pliers to see if it
is free. Use a folded rag to avoid marking the pin. Wick some WD40
down the shaft of the pin.

If there is no pin in sight, leave the valve head off.

Now shut the 'heating system' valve, ensure the boiler thermostat is
nat about two-thirds of maximum.

Turn on the system at the timer/control clock.

If the pipe both sides of the capillary valve gets hot, then water
will be flowing through it and the heating coil, and hopefully heating
the DHW. If there is no or little flow of hot water past the capillary
valve after say ten minutes (feel the pipes as far away from it as
possible), shut the gate valve on the vertical pipe, and then open
half-a turn. See if this makes any difference to the water hopefully
flowing past the capillary valve.

With the system running, the bypass valve almost shut, yet no hot
water flowing past the capillary valve, a fault in the body of the
latter is almost certain, suggesting replacement is necessary.

If hot water is passing the capillary valve, screw the valve head back
on and set it at maximum. Wait some minutes to see if hot water is
still passing through it; after ten or fifteen minutes the water in
the HWT should be heating up. If so, turn the setting to minimum. If
not, there may be a fault in the valve head, again suggesting
replacement is necessary.

Now. listening to the heating pump, shut the bypass gate valve. The
speed of the motor may increase as it is now doing nothing; crack open
the valve slowly until the speed of the motor drops to almost 'normal'
(when it is pumping hard). Although water will be bypassing the
heating coil, it should nevertheless be a limited amount. This water
is not 'lost', it is merely going back the boiler, but you only need
enough of it to keep the pump happy when it has noting else to do.

Hopefully this will have either shown up faults in the capillary
valve, and set the bypass valve to a reasonable setting.
Unfortunately, gate valves can get sludged up and although apparently
shut, may in reality still be partially open, confusing the picture.

Nevertheless, give this a try and see what happens - it might get the
system working properly, or at least give some pointers to where the
fault might lie.

If all is well, you can try fine-tuning the system by e.g. increasing
the boiler thermostat setting (quicker heating by the CH circuit) and
the setting on the capillary valve to give the temperature you want.

Good luck!

TF


good post!
Jim K




As I recall it was a cheap alternative to a motorised valve. The capillary
tube is strapped to the tank and this will close of the gravity feed to the
cylinder when it reaches the right temp - leaving the boiler output to be
solely for the central heating. I nearly fitted on about 35 years ago to my
back boiler system.


  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,835
Default new better clearer photos posted see link below

"John" wrote in message
news
"Jim K" wrote in message
...
On 11 Oct, 17:59, Terry Fields wrote:
Simon wrote:
http://picasaweb.google.co.uk/simon....terTankPhotos#

this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!

The photos strongly suggest you have the same sort of heating system
that we've just left behind.

This is a boiler that heats primary water (usually fed by a jockey
tank somewhere above the hot water tank) that circulates through a
heating coil in the HWT to provide domestic hot water, and via a gate
valve to the radiator system.

Helpfully, the photos show that this valve is marked 'heating system'
on the wall just above it. It's a racing cert that all your radiators
have thermostatic valves on them.

Normally, primary water from the boiler will circulate through the
heating coil in the HWT until the capillary valve (the one with the
thin pipe going to the sensor strapped to the tank) shuts down at the
temperature set by control knob.

Also, if the heating gate valve is opened, primary water will
circulate through the radiators until their TRVs shut.

With both the capillary valve and central heating shut off due to
reaching the set temperatures, the pump will still be running as it is
controlled by a timer. In this case the pump must not run in the
'stalled' condition, it needs to pump water continuously. This is
obtained through a bypass controlled by another gate valve, almost
certainly the one on the vertical pipe running towards the top of the
HWT.

As others have pointed out, if the bypass valve is too 'open' water
will preferentially pass through it rather than the heating coil in
the HWT, leading to a lack of domestic hot water.

Another problem is a fault with the capillary valve; either it is
stuck shut and not allowing primary to flow through the heating coil,
or the capillary or sensor is faulty leading to the valve not opening.

Try this sequence of fault-finding:

Unscrew the knurled ring holding the capillary valve head to the body,
and gently place to one side. If there is a plunger pin on the valve
body, gently try pulling it upwards with pair of pliers to see if it
is free. Use a folded rag to avoid marking the pin. Wick some WD40
down the shaft of the pin.

If there is no pin in sight, leave the valve head off.

Now shut the 'heating system' valve, ensure the boiler thermostat is
nat about two-thirds of maximum.

Turn on the system at the timer/control clock.

If the pipe both sides of the capillary valve gets hot, then water
will be flowing through it and the heating coil, and hopefully heating
the DHW. If there is no or little flow of hot water past the capillary
valve after say ten minutes (feel the pipes as far away from it as
possible), shut the gate valve on the vertical pipe, and then open
half-a turn. See if this makes any difference to the water hopefully
flowing past the capillary valve.

With the system running, the bypass valve almost shut, yet no hot
water flowing past the capillary valve, a fault in the body of the
latter is almost certain, suggesting replacement is necessary.

If hot water is passing the capillary valve, screw the valve head back
on and set it at maximum. Wait some minutes to see if hot water is
still passing through it; after ten or fifteen minutes the water in
the HWT should be heating up. If so, turn the setting to minimum. If
not, there may be a fault in the valve head, again suggesting
replacement is necessary.

Now. listening to the heating pump, shut the bypass gate valve. The
speed of the motor may increase as it is now doing nothing; crack open
the valve slowly until the speed of the motor drops to almost 'normal'
(when it is pumping hard). Although water will be bypassing the
heating coil, it should nevertheless be a limited amount. This water
is not 'lost', it is merely going back the boiler, but you only need
enough of it to keep the pump happy when it has noting else to do.

Hopefully this will have either shown up faults in the capillary
valve, and set the bypass valve to a reasonable setting.
Unfortunately, gate valves can get sludged up and although apparently
shut, may in reality still be partially open, confusing the picture.

Nevertheless, give this a try and see what happens - it might get the
system working properly, or at least give some pointers to where the
fault might lie.

If all is well, you can try fine-tuning the system by e.g. increasing
the boiler thermostat setting (quicker heating by the CH circuit) and
the setting on the capillary valve to give the temperature you want.

Good luck!

TF


good post!
Jim K




As I recall it was a cheap alternative to a motorised valve. The capillary
tube is strapped to the tank and this will close of the gravity feed to
the cylinder when it reaches the right temp - leaving the boiler output to
be solely for the central heating. I nearly fitted on about 35 years ago
to my back boiler system.




What you have is a Drayton D20-8 Tapstat Cylinder Control

http://www.draytoncontrols.co.uk/sea...lectric&page=1


  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10
Default new better clearer photos posted see link below

On 8 Oct, 22:05, Roger Mills wrote:
On 08/10/2010 10:55, Simon wrote:

http://picasaweb.google.co.uk/simon....terTankPhotos#


this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!


OK, that tells us a bit more.

One thing which may be significant is the gate valve which can be seen
in photos 23 and 29 (among others). The pipe in which that valve is
fitted appears to be some sort of by-pass across the cylinder's heating
coil - maybe so as to provide a flow path when the TRV-like valve
closes. How open or closed is that gate valve? (Count the number of
turns required to close it from the current position, and then the turns
required to open it fully from closed, to give a measure of its current
state). If fully open, it provides a dead short for the coil - with the
result that nearly all the primary water will go down the by-pass and
very little through the coil - which could well explain your problem.

If it's open a long way (or fully open even) try running with it only
open a little - maybe half a turn from closed) and see what happens.
If you *need* a by-pass at all - and you may or may not depending on the
requirements of the boiler and on how the system 'controls' are
configured - you'd be far better off with a spring-loaded auto by-pass
valve which only opens when it needs to, rather than a manual gate valve.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.


hi,

many thanks for your reply. the gate valve directly above the TRV-like
valve in photo 23 was fully open. It took seven full turns to make it
fully closed so I have turned it six turns and put on the gas boiler
to see what happens. I will post and let you know.

btw - to clarify: the gas boiler has not been heating the water above
tepid. I had the gas boiler on max for one hour and the hot water was
barely warmed at all. Because of this I have been using the electric
heater to heat the water, which it does but it takes about 90 mins to
make a hot bath, which costs a fortune. When the electric heater has
been left on accidentally, the water boils merrily, filling the attic
room with condensation. For this reason, I am fairly sure that there
is no temperature sensor cut-off system in place for hot water tank.

many thanks for your help. i'll post in about an hour to let you know
how having the manual gate valve nearly closed affected the HW temp.

Simon
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10
Default new better clearer photos posted see link below

On 11 Oct, 17:59, Terry Fields wrote:
Simon wrote:
http://picasaweb.google.co.uk/simon....terTankPhotos#


this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!


The photos strongly suggest you have the same sort of heating system
that we've just left behind.

This is a boiler that heats primary water (usually fed by a jockey
tank somewhere above the hot water tank) that circulates through a
heating coil in the HWT to provide domestic hot water, and via a gate
valve to the radiator system.

Helpfully, the photos show that this valve is marked 'heating system'
on the wall just above it. It's a racing cert that all your radiators
have thermostatic valves on them.

Normally, primary water from the boiler will circulate through the
heating coil in the HWT until the capillary valve (the one with the
thin pipe going to the sensor strapped to the tank) shuts down at the
temperature set by control knob.

Also, if the heating gate valve is opened, primary water will
circulate through the radiators until their TRVs shut.

With both the capillary valve and central heating shut off due to
reaching the set temperatures, the pump will still be running as it is
controlled by a timer. In this case the pump must not run in the
'stalled' condition, it needs to pump water continuously. This is
obtained through a bypass controlled by *another gate valve, almost
certainly the one on the vertical pipe running towards the top of the
HWT.

As others have pointed out, if the bypass valve is too 'open' water
will preferentially pass through it rather than the heating coil in
the HWT, leading to a lack of domestic hot water.

Another problem is a fault with the capillary valve; either it is
stuck shut and not allowing primary to flow through the heating coil,
or the capillary or sensor is faulty leading to the valve not opening.

Try this sequence of fault-finding:

Unscrew the knurled ring holding the capillary valve head to the body,
and gently place to one side. If there is a plunger pin on the valve
body, gently try pulling it upwards with pair of pliers to see if it
is free. Use a folded rag to avoid marking the pin. Wick some WD40
down the shaft of the pin.

If there is no pin in sight, leave the valve head off.

Now shut the 'heating system' valve, ensure the boiler thermostat is
nat about two-thirds of maximum.

Turn on the system at the timer/control clock.

If the pipe both sides of the capillary valve gets hot, then water
will be flowing through it and the heating coil, and hopefully heating
the DHW. If there is no or little flow of hot water past the capillary
valve after say ten minutes (feel the pipes as far away from it as
possible), shut the gate valve on the vertical pipe, and then open
half-a turn. See if this makes any difference to the water hopefully
flowing past the capillary valve.

With the system running, the bypass valve almost shut, yet no hot
water flowing past the capillary valve, a fault in the body of the
latter is almost certain, suggesting replacement is necessary.

If hot water is passing the capillary valve, screw the valve head back
on and set it at maximum. Wait some minutes to see if hot water is
still passing through it; after ten or fifteen minutes the water in
the HWT should be heating up. If so, turn the setting to minimum. If
not, there may be a fault in the valve head, again suggesting
replacement is necessary.

Now. listening to the heating pump, shut the bypass gate valve. The
speed of the motor may increase as it is now doing nothing; crack open
the valve slowly until the speed of the motor drops to almost 'normal'
(when it is pumping hard). Although water will be bypassing the
heating coil, it should nevertheless be a limited amount. This water
is not 'lost', it is merely going back the boiler, but you only need
enough of it to keep the pump happy when it has noting else to do.

Hopefully this will have either shown up faults in the capillary
valve, and set the bypass valve to a reasonable setting.
Unfortunately, gate valves can get sludged up and although apparently
shut, may in reality still be partially open, confusing the picture.

Nevertheless, give this a try and see what happens - it might get the
system working properly, or at least give some pointers to where the
fault might lie.

If all is well, you can try fine-tuning the system by e.g. increasing
the boiler thermostat setting (quicker heating by the CH circuit) and
the setting on the capillary valve to give the temperature you want.

Good luck!

TF


hi TF,

Many thanks for your detailed answer. I really appreciate your help.

I apologise that I have to ask this, but I really don't have your
technical expertise or understanding. In your note you outline various
different valves and what they do and how their settings might be
affecting the working of the system, but from reading your answer I am
not sure which valve is which. Could you indicate which photo/s the
valve/s are in?

i think the "bypass valve" you speak of is the same as the "manual
gate valve" that Roger mentions in his reply. It was fully open and so
I have almost closed it and put the boiler on to see if that helps the
gas boiler to heat the DHW.

I presume that the "capillary valve" you refer to is the TRV
lookalike? What is the optimum setting for this valve?

i'll post in about an hour to let you know if closing the manual gate
valve/bypass valve made any difference.

many thanks for your help.


Simon
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 854
Default new better clearer photos posted see link below


Simon wrote:

Many thanks for your detailed answer. I really appreciate your help.


You're welcome.

I apologise that I have to ask this, but I really don't have your
technical expertise or understanding. In your note you outline various
different valves and what they do and how their settings might be
affecting the working of the system, but from reading your answer I am
not sure which valve is which. Could you indicate which photo/s the
valve/s are in?


i think the "bypass valve" you speak of is the same as the "manual
gate valve" that Roger mentions in his reply. It was fully open and so
I have almost closed it and put the boiler on to see if that helps the
gas boiler to heat the DHW.


You have two gates valves.

One is a bypass for the heating coil in the hot water tank. It's
function is to give the pump soemthing to do when all the other
valves in the system have shut. It is the one shown in photos 2 and 8
and is on the vertical pipe that leads towards the top of the hot
water tank.

It needs to be cracked open just a little, probably half-a-turn might
be too much, but you have to start somewhere.

The other gate valve is the one that lets hot water circulate to the
radiators. It is shown in photos 3, 4, 5, 6 and has the words 'heating
valve' on the wall above it. This needs to be fully open if you want
the radiators on, or fully shut if you don't. For this experiment,
keep it closed.

I presume that the "capillary valve" you refer to is the TRV
lookalike?


Yes.

What is the optimum setting for this valve?


You set this to give the temperaure you want of the water from the hot
water taps. At the moment the valve isn't doing anything as the bypass
gate-valve is fully open and so there is very little flow of primary
water from the boiler through the heating coil. As a start, set this
TRV look-alike at mid-value. If the bypass gate-valve trick works and
the water in the tank gets hotter, then you can experiment to get a
temperature to suit you.

i'll post in about an hour to let you know if closing the manual gate
valve/bypass valve made any difference.


OK.

You appear to have a fault with the immersion heater thermostat, but
let's deal with one issue at a time. If the problems with the valve
settings can be overcome, you might not need the immdersion heater
'til spring.

many thanks for your help.


You're welcome. I hope it all works for you.

TF


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,835
Default new better clearer photos posted see link below

"Terry Fields" wrote in message
...

Simon wrote:

Many thanks for your detailed answer. I really appreciate your help.


You're welcome.

I apologise that I have to ask this, but I really don't have your
technical expertise or understanding. In your note you outline various
different valves and what they do and how their settings might be
affecting the working of the system, but from reading your answer I am
not sure which valve is which. Could you indicate which photo/s the
valve/s are in?


i think the "bypass valve" you speak of is the same as the "manual
gate valve" that Roger mentions in his reply. It was fully open and so
I have almost closed it and put the boiler on to see if that helps the
gas boiler to heat the DHW.


You have two gates valves.

One is a bypass for the heating coil in the hot water tank. It's
function is to give the pump soemthing to do when all the other
valves in the system have shut. It is the one shown in photos 2 and 8
and is on the vertical pipe that leads towards the top of the hot
water tank.

It needs to be cracked open just a little, probably half-a-turn might
be too much, but you have to start somewhere.

The other gate valve is the one that lets hot water circulate to the
radiators. It is shown in photos 3, 4, 5, 6 and has the words 'heating
valve' on the wall above it. This needs to be fully open if you want
the radiators on, or fully shut if you don't. For this experiment,
keep it closed.

I presume that the "capillary valve" you refer to is the TRV
lookalike?


Yes.

What is the optimum setting for this valve?


You set this to give the temperaure you want of the water from the hot
water taps. At the moment the valve isn't doing anything as the bypass
gate-valve is fully open and so there is very little flow of primary
water from the boiler through the heating coil. As a start, set this
TRV look-alike at mid-value. If the bypass gate-valve trick works and
the water in the tank gets hotter, then you can experiment to get a
temperature to suit you.

i'll post in about an hour to let you know if closing the manual gate
valve/bypass valve made any difference.


OK.

You appear to have a fault with the immersion heater thermostat, but
let's deal with one issue at a time. If the problems with the valve
settings can be overcome, you might not need the immdersion heater
'til spring.

many thanks for your help.


You're welcome. I hope it all works for you.

TF




Bear in mind that a thermostat for an immersion heater only costs about £8.

New ones trip out if the thermostat contacts weld together and the water
gets dangerously hot.


  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10
Default new better clearer photos posted see link below

On 14 Oct, 22:56, "John" wrote:
"Terry Fields" wrote in message

...







Simon wrote:


Many thanks for your detailed answer. I really appreciate your help.


You're welcome.


I apologise that I have to ask this, but I really don't have your
technical expertise or understanding. In your note you outline various
different valves and what they do and how their settings might be
affecting the working of the system, but from reading your answer I am
not sure which valve is which. Could you indicate which photo/s the
valve/s are in?


i think the "bypass valve" you speak of is the same as the "manual
gate valve" that Roger mentions in his reply. It was fully open and so
I have almost closed it and put the boiler on to see if that helps the
gas boiler to heat the DHW.


You have two gates valves.


One is a bypass for the heating coil in the hot water tank. It's
function is to give the pump soemthing to do when all the other
valves in the system have shut. It is the one shown in photos 2 and 8
and is on the vertical pipe that leads towards the top of the hot
water tank.


It needs to be cracked open just a little, probably half-a-turn might
be too much, but you have to start somewhere.


The other gate valve is the one that lets hot water circulate to the
radiators. It is shown in photos 3, 4, 5, 6 and has the words 'heating
valve' on the wall above it. This needs to be fully open if you want
the radiators on, or fully shut if you don't. For this experiment,
keep it closed.


I presume that the "capillary valve" you refer to is the TRV
lookalike?


Yes.


What is the optimum setting for this valve?


You set this to give the temperaure you want of the water from the hot
water taps. At the moment the valve isn't doing anything as the bypass
gate-valve is fully open and so there is very little flow of primary
water from the boiler through the heating coil. As a start, set this
TRV look-alike at mid-value. If the bypass gate-valve trick works and
the water in the tank gets hotter, then you can experiment to get a
temperature to suit you.


i'll post in about an hour to let you know if closing the manual gate
valve/bypass valve made any difference.


OK.


You appear to have a fault with the immersion heater thermostat, but
let's deal with one issue at a time. If the problems with the valve
settings can be overcome, you might not need the immdersion heater
'til spring.


many thanks for your help.


You're welcome. I hope it all works for you.


TF


Bear in mind that a thermostat for an immersion heater only costs about £8.

New ones trip out if the thermostat contacts weld together and the water
gets dangerously hot.


Hi Terry,

Many thanks for your messages. I actually think I am beginning to
understand the system!!!

Sorry I didn't post up the results as I said I would. I went to test
the bypass valve only for my son to put the electric water heater on
halfway through the test, so the water got hotter but i didn't know
why. I will try tomorrow when the water is cold and there are no
teenagers walking around the house randomly turning stuff on ;-)

btw - you mention that the Heating Valve needs to be either fully on
(if the radiators are on) or fully off (if the radiators are off). Do
I understand you correctly if i take it to mean that the Heating Valve
cannot be partially open at all? The Heating Valve has to be either
fully closed or fully open, nothing inbetween?

If it was left, say, half open, what would be the ramifications?

If the Heating Valve is kept closed and the radiators kept off would
this actually help the gas boiler to heat the water quicker/ hotter? I
ask this as we rarely use/need the radiators at all (we live in Devon,
so it's v.mild here), but having the gas boiler actually heat the tap/
bath water would be a real boon!

But are their any downsides/ramifications/considerations to leaving
the radiators off all the time and the HV closed?

Many thanks again.


Simon
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,419
Default new better clearer photos posted see link below

In message
,
Simon writes
On 8 Oct, 22:05, Roger Mills wrote:
On 08/10/2010 10:55, Simon wrote:

http://picasaweb.google.co.uk/simon....terTankPhotos#


this is the third time i've tried to post this link. third time
lucky!!!!!!!!!!!


OK, that tells us a bit more.

One thing which may be significant is the gate valve which can be seen
in photos 23 and 29 (among others). The pipe in which that valve is
fitted appears to be some sort of by-pass across the cylinder's heating
coil - maybe so as to provide a flow path when the TRV-like valve
closes. How open or closed is that gate valve? (Count the number of
turns required to close it from the current position, and then the turns
required to open it fully from closed, to give a measure of its current
state). If fully open, it provides a dead short for the coil - with the
result that nearly all the primary water will go down the by-pass and
very little through the coil - which could well explain your problem.

If it's open a long way (or fully open even) try running with it only
open a little - maybe half a turn from closed) and see what happens.
If you *need* a by-pass at all - and you may or may not depending on the
requirements of the boiler and on how the system 'controls' are
configured - you'd be far better off with a spring-loaded auto by-pass
valve which only opens when it needs to, rather than a manual gate valve.
--



many thanks for your reply. the gate valve directly above the TRV-like
valve in photo 23 was fully open. It took seven full turns to make it
fully closed so I have turned it six turns and put on the gas boiler
to see what happens. I will post and let you know.

btw - to clarify: the gas boiler has not been heating the water above
tepid. I had the gas boiler on max for one hour and the hot water was
barely warmed at all. Because of this I have been using the electric
heater to heat the water, which it does but it takes about 90 mins to
make a hot bath, which costs a fortune. When the electric heater has
been left on accidentally, the water boils merrily, filling the attic
room with condensation. For this reason, I am fairly sure that there
is no temperature sensor cut-off system in place for hot water tank.


The latter issue of the water in the tank boiling when using the
immersion heater is almost certainly due to a failed thermostat
controlling the immersion heater (this is all separate from the temp
control relating to heating it via the boiler). The thermostat is cheap
(about a tenner) and easily replaced.

This page show what is involved:

http://www.diydata.com/problem/immersion/immersion_heaters.php

Re the problem of heating via the boiler, I suspect the culprit might
be the TRV-a-lke/Tapstat . It sounds to me as if it either has got stuck
in a mostly closed position. Radiator TRV's do this qiute often.

I guess they are basically the same inside. If you remove the head of
the valve - at the base of the white body of the top of the valve should
be a metal ring. This can be unscrewed (might be tight and need
pliers/wrench to start) and then the body removed. Inside you should see
a pin sticking up. This pin can stick - typically with the valve closed
so stopping it operating. You should be able to push it up and down. f
you can't you can use pliers to wiggle it or gently tap it to free it
up. If it will move freely than leave the top off this should leave it
open, and then hopefully then water in the tank will heat up
--
Chris French

  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 854
Default new better clearer photos posted see link below


Simon wrote:

Sorry I didn't post up the results as I said I would. I went to test
the bypass valve only for my son to put the electric water heater on
halfway through the test, so the water got hotter but i didn't know
why. I will try tomorrow when the water is cold and there are no
teenagers walking around the house randomly turning stuff on ;-)


Teenagers are rather like that :-(

For the next test either tell them not to turn the immersion heater
on, or tell them anyway and also put some sticky tape or a post-it
note over the switch.

Bear in mind you might have more than one fault in the system.

To try and find one fault at a time, try this scheme:

[1] Shut the 'Heating Valve' gate-valve. This shuts off the supply to
the radiators, so the heated water from the boiler has nowhere else to
go but to the heating coil/bypass gate-valve. It takes the whole issue
of the central heating out of the fault-finding loop.

Now, we don't know if the boiler is producing enough water at the
right temperature - it too could have a failed thermostat. However, we
have to start somewhere.

[2] set this boiler stat at two-thirds of its Max setting.

[3] shut the bypass gate valve, then open it half a turn.

[4] open the TRV-like capillary valve fully. This valve may be faulty,
but this is an easy place to start.

[5] Put your hand on the hot water tank near the top and see how warm
it is.

[6] Turn the boiler on.

[6] After about 15 minutes, feel the pipe below the bypass gate-valve,
it should be warm to hot. Then feel the pipe above the bypass
gate-valve, hopefully it won't be so warm but if it isn't, don't worry
at this stage. Feel the hot water tank in the same place as last time.
Is there any difference yet? If the hot water tank is getting warmer,
well and good. In any case, let the system run for a total of 30
minutes or so.

[7] After 30 minutes, you should be in one of two positions: a) the
hot water tank is heating up significantly or b) there is no real
change.

If the former is the case, then you're on the right track, and skip
the paragraph below.

If the latter, then gently and carefully unscrew the head of the
TRV-like capillary valve. Does the body of the valve have a central
pin protruding it, underneath the head that you've just removed? If it
hasn't, ignore the next step. If it has, then with a pair of pliers
and protected by a rag or several folds of paper, genty pull the pin
up.

Leave the system running for another 30 minutes, for a total of one
hour. This is enough time to heat a tank of hot water, so after this
span of time, you should have the following results:

1) TRV-like caplliary valve in place: water either heats up or it
doesn't. Please report this result.

2) TRV-like capillary valve head removed (and pin pulled up if there
is one): water either heats up or it doesn't. Please report this
result.

At his point domestice needs suggest you replace the TRV-like
capillary valve and temporarily go back to whatever system you were
using to obtain hot water. Depending on the results of these tests,
there may be more to do - but do these first.

btw - you mention that the Heating Valve needs to be either fully on
(if the radiators are on) or fully off (if the radiators are off). Do
I understand you correctly if i take it to mean that the Heating Valve
cannot be partially open at all? The Heating Valve has to be either
fully closed or fully open, nothing inbetween?


There is no benefit to having the Heating Valve gate-valve partially
open. The system should be (but clearly isn't) balanced to share the
water-heating and radiator heating with this valve fully open.
Fiddling with this at this time will only confuse the issues - we need
to make progress in getting hot water. I suspect the central heating
part will be OK, but that's for later.

If it was left, say, half open, what would be the ramifications?


A bodged system with potential faults all confusing the picture.
Normally, you'd have this fully open or fully shut.

If the Heating Valve is kept closed and the radiators kept off would
this actually help the gas boiler to heat the water quicker/ hotter?


Very likely.

I ask this as we rarely use/need the radiators at all (we live in Devon,
so it's v.mild here), but having the gas boiler actually heat the tap/
bath water would be a real boon!


That's the point we're trying to get you to. Playing with the central
heating at this point will only confuse the issues.

But are their any downsides/ramifications/considerations to leaving
the radiators off all the time and the HV closed?


The rooms won't be so warm! Also, the TRVs can stick shut - but if
you've got the hot water working by this time and you need central
heating, it's just a case of taking the head off and freeing up the
pin - although this isn't the only failure mechanism. My advice:
ignore the central heating for now. Get the hot water working.

Lets us know the results of the tests.

TF
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 854
Default new better clearer photos posted see link below


Terry Fields wrote:

If the latter, then


oops...

That should read "..gently and carefully unscrew the knurled collar
under the head of theTRV-like capillary valve, and gently remove the
valve head - it will have the delicate capillary pipe attached".



TF


  #16   Report Post  
Posted to uk.d-i-y
No Name
 
Posts: n/a
Default new better clearer photos posted see link below

On 15 Oct,
Terry Fields wrote:

There is no benefit to having the Heating Valve gate-valve partially
open. The system should be (but clearly isn't) balanced to share the
water-heating and radiator heating with this valve fully open.
Fiddling with this at this time will only confuse the issues - we need
to make progress in getting hot water. I suspect the central heating
part will be OK, but that's for later.


Gate valves are notoriously unreliable. A possible complication is that it
doesn't shut off. feel a foot or so of each side when it is off to see if it
is sealing. (it shouldn't need to be off for hot water anyway, so shouldn't
matter).

Are you in a hard or soft water area?

--
B Thumbs
Change lycos to yahoo to reply
  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 854
Default new better clearer photos posted see link below


wrote:

On 15 Oct,
Terry Fields wrote:

There is no benefit to having the Heating Valve gate-valve partially
open. The system should be (but clearly isn't) balanced to share the
water-heating and radiator heating with this valve fully open.
Fiddling with this at this time will only confuse the issues - we need
to make progress in getting hot water. I suspect the central heating
part will be OK, but that's for later.


Gate valves are notoriously unreliable. A possible complication is that it
doesn't shut off. feel a foot or so of each side when it is off to see if it
is sealing. (it shouldn't need to be off for hot water anyway, so shouldn't
matter).


I did mention this problem in a previous post, but the OP has to start
somewhere in sorting out his hot-water problems, so put it towards the
back burner for now.

Are you in a hard or soft water area?


The OP is in Devon, so I guess it's a soft-water area.

TF
  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 82
Default new better clearer photos posted see link below

On Oct 15, 2:51*am, Simon wrote:

btw - you mention that the Heating Valve needs to be either fully on
(if the radiators are on) or fully off (if the radiators are off). Do
I understand you correctly if i take it to mean that the Heating Valve
cannot be partially open at all? The Heating Valve has to be either
fully closed or fully open, nothing inbetween?

If it was left, say, half open, what would be the ramifications?

At this time of year, when heating requirements are relatively low and
the radiator TRVs will be nearly closed, there shouldn't be much
effect. If/when the weather gets colder, there will come a point where
the valve is restricting the flow too much and the system will fail to
keep the rooms at the desired temperature.

Mike
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10
Default new better clearer photos posted see link below

On 15 Oct, 09:57, Terry Fields wrote:
Simon wrote:
Sorry I didn't post up the results as I said I would. I went to test
the bypass valve only for my son to put the electric water heater on
halfway through the test, so the water got hotter but i didn't know
why. I will try tomorrow when the water is cold and there are no
teenagers walking around the house randomly turning stuff on ;-)


Teenagers are rather like that :-(

For the next test either tell them not to turn the immersion heater
on, or tell them anyway and also put some sticky tape or a post-it
note over the switch.

Bear in mind you might have more than one fault in the system.

To try and find one fault at a time, try this scheme:

[1] Shut the 'Heating Valve' gate-valve. This shuts off the supply to
the radiators, so the heated water from the boiler has nowhere else to
go but to the heating coil/bypass gate-valve. It takes the whole issue
of the central heating out of the fault-finding loop.

Now, we don't know if the boiler is producing enough water at the
right temperature - it too could have a failed thermostat. However, we
have to start somewhere.

[2] set this boiler stat at *two-thirds of its Max setting.

[3] shut the bypass gate valve, then open it half a turn.

[4] open the TRV-like capillary valve fully. This valve may be faulty,
but this is an easy place to start.

[5] Put your hand on the hot water tank near the top and see how warm
it is.

[6] Turn the boiler on.

[6] After about 15 minutes, feel the pipe below the bypass gate-valve,
it should be warm to hot. Then feel the pipe above the bypass
gate-valve, hopefully it won't be so warm but if it isn't, don't worry
at this stage. Feel the hot water tank in the same place as last time.
Is there any difference yet? If the hot water tank is getting warmer,
well and good. In any case, let the system run for a total of 30
minutes or so.

[7] After 30 minutes, you should be in one of two positions: a) the
hot water tank is heating up significantly or b) there is no real
change.

If the former is the case, then you're on the right track, and skip
the paragraph below.

If the latter, then gently and carefully unscrew the head of the
TRV-like capillary valve. Does the body of the valve have a central
pin protruding it, underneath the head that you've just removed? If it
hasn't, ignore the next step. If it has, then with a pair of pliers
and protected by a rag or several folds of paper, genty pull the pin
up.

Leave the system running for another 30 minutes, for a total of one
hour. This is enough time to heat a tank of hot water, so after this
span of time, you should have the following results:

*1) TRV-like caplliary valve in place: water either *heats up or it
doesn't. Please report this result.

*2) TRV-like capillary valve head removed (and pin pulled up if there
is one): water either heats up or it doesn't. Please report this
result.

At his point domestice needs suggest you replace the TRV-like
capillary valve and temporarily go back to whatever system you were
using to obtain hot water. Depending on the results of these tests,
there may be more to do - but do these first.

btw - you mention that the Heating Valve needs to be either fully on
(if the radiators are on) or fully off (if the radiators are off). Do
I understand you correctly if i take it to mean that the Heating Valve
cannot be partially open at all? The Heating Valve has to be either
fully closed or fully open, nothing inbetween?


There is no benefit to having the Heating Valve gate-valve partially
open. The system should be (but clearly isn't) balanced to share the
water-heating and radiator heating with this valve fully open.
Fiddling with this at this time will only confuse the issues - we need
to make progress in getting hot water. I suspect the central heating
part will be OK, but that's for later.

If it was left, say, half open, what would be the ramifications?


A bodged system with potential faults all confusing the picture.
Normally, you'd have this fully open or fully shut.

If the Heating Valve is kept closed and the radiators kept off would
this actually help the gas boiler to heat the water quicker/ hotter?


Very likely.

I ask this as we rarely use/need the radiators at all (we live in Devon,
so it's v.mild here), but having the gas boiler actually heat the tap/
bath water would be a real boon!


That's the point we're trying to get you to. Playing with the central
heating at this point will only confuse the issues.

But are their any downsides/ramifications/considerations to leaving
the radiators off all the time and the HV closed?


The rooms won't be so warm! Also, the TRVs can stick shut - but if
you've got the hot water working by this time and you need central
heating, it's just a case of taking the head off and freeing up the
pin - although this isn't the only failure mechanism. My advice:
ignore the central heating for now. Get the hot water working.

Lets us know the results of the tests.

TF


Hi,

I did the test with the settings as suggested by Terry: ie, bypass
valve a quarter-turn open, heating valve completely closed, gas boiler
thermostat set on 4 (max is 5), TRV-like capillary valve fully open).
After half an hour the tank was slightly warmer (you could feel it was
a bit warmer but not much and certainly not near "hot"). The pipe
going from the tank to the TRV capillary valve was somewhere between
"no difference" to maybe "slightly warm"), but the pipe going from the
TRV capillary valve off to the top tank and the rest of the system was
very hot (too hot to touch). Is this the way it should be?

After 30 mins I ran the bathwater and the water was warm but not
enough for a bath. After 90 mins I ran the bath and it was running too
hot to touch and there was enough for a bath.

So... yippee!!! Many many thanks Terry! This is the first time we have
ever been able to have a hot bath without having the electric heater
on for more than an hour (usually 90mins min). Just this on its own
will save me a fortune and make life so much easier. All i need to do
now is try the gas boiler thermostat on diff settings for diff lengths
of time to find the optimum setting for water temperature, time to
heat, and units used etc.

But... from the above, is this HW system now working well or should it
be better?

btw - When I say "gas boiler thermostat" set on 4" I presumed you
meant the actual dial-setting on the boiler itself, and not something
on the water tank or associated pipework. Is this right? I couldn't
see anything else on the tank that could be adjusted and so I presumed
that the dial setting on the boiler was what you meant.

Because of the success of the above test I didn't remove the top of
the TRV-like capillary valve and see if the pin was stuck in a
partially closed position, from the above do you think this is
necessary or a still a good idea?

Because the water can reach boiling in the tank I guess it means there
is a failed thermostat that needs replacing as you say, and this is
something I should look at (even though i presume limiting the heat is
purely a safety measure, and is not something that is done for the
efficiency or otherwise of the system).

@B Trends - I live in a hard water area (I can tell from the build-up
in the kettle, the taps etc, and how hard it is to get up decent suds
for washing). I had thought about this possibly being part of the
problem and could see how limescale could serious affect the
efficiency of a CH/ DHW system. One solution I looked at was
Scalewatcher (http://www.selfbuilder.net/products/scalewatcher.html)
which looked good but expensive (£150ish). What do you think about the
cost/benefits of these kind of limescale removal systems? Are they
worth it? Is it applicable to my situation?

When we move into winter and we want to have the radiators on for at
least part of the day, will it be okay to switch between having the
heating valve fully open to take the heat of the gas boiler to the
radiators, and then close it fully to heat the water for a bath, and
then after the bath to open the heating valve again to heat the
radiators, or could this cause problems? Is it okay to simply switch
between fully open and fully closed in this fashion?

Once again, many thanks for all your help. Any further advice that
could help is gratefully received.


Simon

ps - i have ordered R.D.Treloar's "Plumbing: Heating & Gas
Installations" to get a better overall understanding of how these
systems should be set-up and should work. Supposedly it's the best one
for the layman. It's on its way and I'm really looking forward to it!
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 854
Default new better clearer photos posted see link below


Simon wrote:

I did the test with the settings as suggested by Terry: ie, bypass
valve a quarter-turn open, heating valve completely closed, gas boiler
thermostat set on 4 (max is 5), TRV-like capillary valve fully open).
After half an hour the tank was slightly warmer (you could feel it was
a bit warmer but not much and certainly not near "hot"). The pipe
going from the tank to the TRV capillary valve was somewhere between
"no difference" to maybe "slightly warm"), but the pipe going from the
TRV capillary valve off to the top tank and the rest of the system was
very hot (too hot to touch). Is this the way it should be?

After 30 mins I ran the bathwater and the water was warm but not
enough for a bath. After 90 mins I ran the bath and it was running too
hot to touch and there was enough for a bath.


I'm extremely pleased you have got this far, and hopefully (someone)
enjoyed a bath!

I'm not sure from the above description exactly what's heppening, but
that's my fault.

You may have the bypass gate valve too far shut - try opening it to
half a turn. It lets water through the bypass, but you need some to
keep the pump happy.

So... yippee!!! Many many thanks Terry! This is the first time we have
ever been able to have a hot bath without having the electric heater
on for more than an hour (usually 90mins min). Just this on its own
will save me a fortune and make life so much easier. All i need to do
now is try the gas boiler thermostat on diff settings for diff lengths
of time to find the optimum setting for water temperature, time to
heat, and units used etc.


No, no, no...

Leave the boiler thermostat setting where it is for now. The boiler is
designed to run to its own settings - that's why you have control
valves such as the TRV-like capillary valve and the TRVs on the
radiator. Trying to run the whole system from the boiler is simply not
the way to go - let each part it do its own job.

You control the temperature of the water delivered to the hot water
taps (domestic hot water or DHW) via the TRV-like capillary valve
only.

I suggested setting it on 'max' as an initial setting. Clearly it's
too hot - possibly dangerously so. On the one in the system I used to
have, the difference between setting no. 4 and setting no. 5 (out of
8) was the difference between hot water and very hot water.

I suggest you now try a setting about half-way as a start, and then
experiment over the next few days to give you the DHW at the
temperature you want. This will be a major milestone in getting your
system running properly.

But... from the above, is this HW system now working well or should it
be better?


Difficult to say, but you do need to get the DHW temperature down to
something more reasonable (hot but not very hot....you'll need to
decide for yourself).

btw - When I say "gas boiler thermostat" set on 4" I presumed you
meant the actual dial-setting on the boiler itself, and not something
on the water tank or associated pipework. Is this right?


Yes, it was the setting on the boiler thermostat.

I couldn't
see anything else on the tank that could be adjusted and so I presumed
that the dial setting on the boiler was what you meant.


Yes, that's right.

Because of the success of the above test I didn't remove the top of
the TRV-like capillary valve and see if the pin was stuck in a
partially closed position, from the above do you think this is
necessary or a still a good idea?


It's not necessary. What I suggested was an experiment in case the DHW
wasn't heating up at all. Clearly this isn't the case and your
TRV-like capillary valve appears to be working fine - except that it
just could be stuck open. However, if you can control the temperature
of the DHW by adjusting it as mentioned above, that rules out another
problem.

Because the water can reach boiling in the tank I guess it means there
is a failed thermostat that needs replacing as you say, and this is
something I should look at (even though i presume limiting the heat is
purely a safety measure, and is not something that is done for the
efficiency or otherwise of the system).


I take it you mean when the immersion is on. Hopefully you won't need
it now 'til Spring.

Replacing an immersion heater thermostat is a straightforward job if
one knows what one is doing. You could ask the question in a separate
thread to get more knowledgeable people than myself to offer more
informed comment.

@B Trends - I live in a hard water area (I can tell from the build-up
in the kettle, the taps etc, and how hard it is to get up decent suds
for washing). I had thought about this possibly being part of the
problem and could see how limescale could serious affect the
efficiency of a CH/ DHW system. One solution I looked at was
Scalewatcher (http://www.selfbuilder.net/products/scalewatcher.html)
which looked good but expensive (£150ish). What do you think about the
cost/benefits of these kind of limescale removal systems? Are they
worth it? Is it applicable to my situation?


I'm sorry, I couldn't advise on that. You might like to ask a seperate
question to get informed comment from people who have installed and
used these. I would suggest not rushing out to spend big money yet as
although the DHW is on its way to working properly things have yet to
be fine-tuned.

When we move into winter and we want to have the radiators on for at
least part of the day, will it be okay to switch between having the
heating valve fully open to take the heat of the gas boiler to the
radiators, and then close it fully to heat the water for a bath, and
then after the bath to open the heating valve again to heat the
radiators, or could this cause problems? Is it okay to simply switch
between fully open and fully closed in this fashion?


When winter strikes, or you just feel cold, put the system on and open
the Heating Valve gate-valve fully. The flow of hot primary water from
the boiler will be shared by both the DHW and CH circuits, so it will
take longer to get a tankful of hot water and longer for the radiators
to heat up fully. However, if you have set the TRV-like capillary
valve to give you the DHW temperature you want, and the TRVs on the
radiators to give the room temperatures you want, then these various
valves will after a time start shutting down and thus passing hot
primary water to the other circuit. When they've all shut down, the
only flow left - necessary to keep the pump happy - is through the
bypass system.

It may take noticeably longer to get a tankful of DHW under these
circumstances, and you may need to anticipate family demands for DHW
and room heating! Starting with last night's DHW still in the tank
goes a fair way to getting everything up to temperature sooner -
starting with a tankful of cold water straight from the mains means
much longer for everything to heat up.

On the sytem I had, heating up a tank of mains-cold water took about
an hour. Starting with last night's DHW in the tank, it took an hour
to heat the water and get the rooms warm. Conserving hot water in this
way can help a lot, as can anticipating family demands. After all the
upheaval of the last few days, take time to ensure the lagging jacket
on the HWT is properly fitted.

Once again, many thanks for all your help. Any further advice that
could help is gratefully received.


I'm glad I was able to help - but you do need to get the DHW
temperature right for you by adjusting the TRV-like caplillary-valve
settings.

ps - i have ordered R.D.Treloar's "Plumbing: Heating & Gas
Installations" to get a better overall understanding of how these
systems should be set-up and should work. Supposedly it's the best one
for the layman. It's on its way and I'm really looking forward to it!


Well, I've just taken over a house with a complex thermal-store system
and more than twice the number of radiators I had - some of the
radiators have TRVs and some don't, and there's a room thermostat as
well. Although the system in seven years old, all the lockshield
valves (LSVs) on the radiators are fully open, meaning the system has
never been balanced. Using the groups' FAQ, I have now set about this
task, you can find it he

http://www.diyfaq.org.uk/

However, I would caution you not to make too many changes to your
system at one time, otherwise you could easily get lost in maze of
changes that don't give you the results you anticipated. You've come a
long way to get the DHW system started, and you need to fine-tune
that. With the DHW system running satisfactorily, there'll be the
whole new world of Central Heating to explore....take it one step at a
time. Good Luck!

TF


  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,120
Default new better clearer photos posted see link below

On 16/10/2010 15:17, Simon wrote:

Hi,

I did the test with the settings as suggested by Terry: ie, bypass
valve a quarter-turn open, heating valve completely closed, gas boiler
thermostat set on 4 (max is 5), TRV-like capillary valve fully open).
After half an hour the tank was slightly warmer (you could feel it was
a bit warmer but not much and certainly not near "hot"). The pipe
going from the tank to the TRV capillary valve was somewhere between
"no difference" to maybe "slightly warm"), but the pipe going from the
TRV capillary valve off to the top tank and the rest of the system was
very hot (too hot to touch). Is this the way it should be?


After how long? The return from the coil won't be very hot until the
water in the cylinder has heated up quite a lot - whereas the by-pass
*will* be hot if there's water flowing through it.

After 30 mins I ran the bathwater and the water was warm but not
enough for a bath. After 90 mins I ran the bath and it was running too
hot to touch and there was enough for a bath.


It shouldn't take 90 minutes to heat a tankful of water. It may take
more than 30, but even then, the water at the top should be hot.

So... yippee!!! Many many thanks Terry! This is the first time we have
ever been able to have a hot bath without having the electric heater
on for more than an hour (usually 90mins min). Just this on its own
will save me a fortune and make life so much easier. All i need to do
now is try the gas boiler thermostat on diff settings for diff lengths
of time to find the optimum setting for water temperature, time to
heat, and units used etc.

But... from the above, is this HW system now working well or should it
be better?


It should be better!

btw - When I say "gas boiler thermostat" set on 4" I presumed you
meant the actual dial-setting on the boiler itself, and not something
on the water tank or associated pipework. Is this right? I couldn't
see anything else on the tank that could be adjusted and so I presumed
that the dial setting on the boiler was what you meant.


Yes, I'm sure he meant the boiler stat.


Because of the success of the above test I didn't remove the top of
the TRV-like capillary valve and see if the pin was stuck in a
partially closed position, from the above do you think this is
necessary or a still a good idea?


Yes. I suspect that water still isn't flowing through the coil as fast
as it should. Try running with the thermostatic head removed, having
made sure that the pin is fully up.

Because the water can reach boiling in the tank I guess it means there
is a failed thermostat that needs replacing as you say, and this is
something I should look at (even though i presume limiting the heat is
purely a safety measure, and is not something that is done for the
efficiency or otherwise of the system).


It is an extremely important safety measure - particularly when you have
a plastic header tank in the attic (which you don't appear to have).


When we move into winter and we want to have the radiators on for at
least part of the day, will it be okay to switch between having the
heating valve fully open to take the heat of the gas boiler to the
radiators, and then close it fully to heat the water for a bath, and
then after the bath to open the heating valve again to heat the
radiators, or could this cause problems? Is it okay to simply switch
between fully open and fully closed in this fashion?


I think you should seriously consider upgrading the controls of your
system by replacing the manual heating valve with a motorised zone
valve, and replacing the TRV-like cylinder valve with a zone valve plus
cylinder stat, with independent timers for each circuit - in other
words, convert it to a proper S-Plan system.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Posted some photos steamer Metalworking 3 October 1st 10 02:43 AM
Shelf units and stools photos posted Nonny Woodworking 0 December 20th 09 06:06 AM
Picassa Link Test (same photos as other post) Tom Watson Woodworking 7 November 29th 09 03:38 AM
a.b.p.w photos posted Making a Backstaff - Intro Saville Woodworking 0 January 7th 06 02:46 PM
Posted photos of router table... Terry Sumner Woodworking 0 December 5th 05 02:15 AM