UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 57
Default Boiler wiring - Flex or T+E

Hi all,

As some of you may know I'm installing gas central heating with the
boiler in the loft. Things are progressing well, I've done all the
pipework bar the last metre or so of the gas, and now I just have to
finish off the wiring.

It's a standard Y-plan with the wiring centre in the airing cupboard.
Thermostat in hall and programmer in the kitchen. The boiler is a
Vaillant Ecotec plus 624 system boiler.

From the airing cupboard up to the loft I have run 2 * 1.5mm T+E, the
first of which is the main feed to the boiler which is switched
directly from a 3A switched spur, and the second feeds the programmer
and all other associated switchgear, with the brown wire providing the
live feed and the blue, the call for heat. This is as recommended by
Vaillant - the idea being that if the boiler is switched off at the
applicance, ALL other associated controls are no longer live.

So my question is how to I present these feeds to the boiler, in their
existing T+E, or do I install a couple of accessories adjacent to the
boiler and make the final run in flex? I am leaning towards flex, as
the terminations at the boiler end are clearly designed to take flex,
but essentially, I'm providing fixed wiring to a fixed appliance.

Assuming flex (and feel free to correct me) what accessories would I
install? 1* unswitched socket for the boiler feed, and 1 * unfused
flex outlet plate do you think? Or 2 * flex outlet plates? Any other
suggestions?

I have put a photo here which shows the current wiring arrangements.

http://tinyurl.com/LukesWiring

The FCU to the left of the wiring centre feeds the boiler.

Thanks in advance.

Luke
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,188
Default Boiler wiring - Flex or T+E

On 27 Sep, 09:10, Luke wrote:
Hi all,

As some of you may know I'm installing gas central heating with the
boiler in the loft. Things are progressing well, I've done all the
pipework bar the last metre or so of the gas, and now I just have to
finish off the wiring.

It's a standard Y-plan with the wiring centre in the airing cupboard.
Thermostat in hall and programmer in the kitchen. The boiler is a
Vaillant Ecotec plus 624 system boiler.

From the airing cupboard up to the loft I have run 2 * 1.5mm T+E, the
first of which is the main feed to the boiler which is switched
directly from a 3A switched spur, and the second feeds the programmer
and all other associated switchgear, with the brown wire providing the
live feed and the blue, the call for heat. This is as recommended by
Vaillant - the idea being that if the boiler is switched off at the
applicance, ALL other associated controls are no longer live.

So my question is how to I present these feeds to the boiler, in their
existing T+E, or do I install a couple of accessories adjacent to the
boiler and make the final run in flex? I am leaning towards flex, as
the terminations at the boiler end are clearly designed to take flex,
but essentially, I'm providing fixed wiring to a fixed appliance.

Assuming flex (and feel free to correct me) what accessories would I
install? 1* unswitched socket for the boiler feed, and 1 * unfused
flex outlet plate do you think? Or 2 * flex outlet plates? Any other
suggestions?

I have put a photo here which shows the current wiring arrangements.

http://tinyurl.com/LukesWiring

The FCU to the left of the wiring centre feeds the boiler.

Thanks in advance.

Luke


You can buy heat resisting flex which you sould use. 2, 3 or four
core.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Boiler wiring - Flex or T+E

Luke wrote:
Hi all,

As some of you may know I'm installing gas central heating with the
boiler in the loft. Things are progressing well, I've done all the
pipework bar the last metre or so of the gas, and now I just have to
finish off the wiring.

It's a standard Y-plan with the wiring centre in the airing cupboard.
Thermostat in hall and programmer in the kitchen. The boiler is a
Vaillant Ecotec plus 624 system boiler.

From the airing cupboard up to the loft I have run 2 * 1.5mm T+E, the
first of which is the main feed to the boiler which is switched
directly from a 3A switched spur, and the second feeds the programmer
and all other associated switchgear, with the brown wire providing the
live feed and the blue, the call for heat. This is as recommended by
Vaillant - the idea being that if the boiler is switched off at the
applicance, ALL other associated controls are no longer live.

So my question is how to I present these feeds to the boiler, in their
existing T+E, or do I install a couple of accessories adjacent to the
boiler and make the final run in flex? I am leaning towards flex, as
the terminations at the boiler end are clearly designed to take flex,
but essentially, I'm providing fixed wiring to a fixed appliance.

Assuming flex (and feel free to correct me) what accessories would I
install? 1* unswitched socket for the boiler feed, and 1 * unfused
flex outlet plate do you think? Or 2 * flex outlet plates? Any other
suggestions?

I have put a photo here which shows the current wiring arrangements.

http://tinyurl.com/LukesWiring

The FCU to the left of the wiring centre feeds the boiler.

Thanks in advance.

Luke


I would terminate the T&Es with a fan isolator switch (relabelled BOILER)
and use 4 core heat resistant flex to the boiler. This will allow local
isolation of the boiler in the loft (ie you can then isolate perm live,
switched live and the neutral)

Cheers

--
Adam


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 57
Default Boiler wiring - Flex or T+E

On Sep 27, 9:24*am, "ARWadsworth"
wrote:
Luke wrote:
Hi all,


As some of you may know I'm installing gas central heating with the
boiler in the loft. Things are progressing well, I've done all the
pipework bar the last metre or so of the gas, and now I just have to
finish off the wiring.


It's a standard Y-plan with the wiring centre in the airing cupboard.
Thermostat in hall and programmer in the kitchen. The boiler is a
Vaillant Ecotec plus 624 system boiler.


From the airing cupboard up to the loft I have run 2 * 1.5mm T+E, the
first of which is the main feed to the boiler which is switched
directly from a 3A switched spur, and the second feeds the programmer
and all other associated switchgear, with the brown wire providing the
live feed and the blue, the call for heat. This is as recommended by
Vaillant - the idea being that if the boiler is switched off at the
applicance, ALL other associated controls are no longer live.


So my question is how to I present these feeds to the boiler, in their
existing T+E, or do I install a couple of accessories adjacent to the
boiler and make the final run in flex? I am leaning towards flex, as
the terminations at the boiler end are clearly designed to take flex,
but essentially, I'm providing fixed wiring to a fixed appliance.


Assuming flex (and feel free to correct me) what accessories would I
install? 1* unswitched socket for the boiler feed, and 1 * unfused
flex outlet plate do you think? Or 2 * flex outlet plates? Any other
suggestions?


I have put a photo here which shows the current wiring arrangements.


http://tinyurl.com/LukesWiring


The FCU to the left of the wiring centre feeds the boiler.


Thanks in advance.


Luke


I would terminate the T&Es with a fan isolator switch (relabelled BOILER)
and use 4 core heat resistant flex to the boiler. This will allow local
isolation of the boiler in the loft (ie you can then isolate perm live,
switched live and the neutral)

Cheers

--
Adam- Hide quoted text -


Thanks Adam, but I would need a 4-way isolating switch, and 5 core
flex, as from my two T+Es, none of them are common, so could not merge
them into a 3-way fan isolator. This is because the boiler presents a
separate live feed to the programmer, and in turn a call for heat, in
addition to its live and neutral supply, hence the 2 * T+Es. From a
quick google I am not sure a 4-way isolator is available.

Luke

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Boiler wiring - Flex or T+E

Luke wrote:
On Sep 27, 9:24 am, "ARWadsworth"
wrote:
Luke wrote:
Hi all,


As some of you may know I'm installing gas central heating with the
boiler in the loft. Things are progressing well, I've done all the
pipework bar the last metre or so of the gas, and now I just have to
finish off the wiring.


It's a standard Y-plan with the wiring centre in the airing
cupboard. Thermostat in hall and programmer in the kitchen. The
boiler is a Vaillant Ecotec plus 624 system boiler.


From the airing cupboard up to the loft I have run 2 * 1.5mm T+E,
the first of which is the main feed to the boiler which is switched
directly from a 3A switched spur, and the second feeds the
programmer and all other associated switchgear, with the brown wire
providing the live feed and the blue, the call for heat. This is as
recommended by Vaillant - the idea being that if the boiler is
switched off at the applicance, ALL other associated controls are
no longer live.


So my question is how to I present these feeds to the boiler, in
their existing T+E, or do I install a couple of accessories
adjacent to the boiler and make the final run in flex? I am leaning
towards flex, as the terminations at the boiler end are clearly
designed to take flex, but essentially, I'm providing fixed wiring
to a fixed appliance.


Assuming flex (and feel free to correct me) what accessories would I
install? 1* unswitched socket for the boiler feed, and 1 * unfused
flex outlet plate do you think? Or 2 * flex outlet plates? Any other
suggestions?


I have put a photo here which shows the current wiring arrangements.


http://tinyurl.com/LukesWiring


The FCU to the left of the wiring centre feeds the boiler.


Thanks in advance.


Luke


I would terminate the T&Es with a fan isolator switch (relabelled
BOILER) and use 4 core heat resistant flex to the boiler. This will
allow local isolation of the boiler in the loft (ie you can then
isolate perm live, switched live and the neutral)

Cheers

--
Adam- Hide quoted text -


Thanks Adam, but I would need a 4-way isolating switch, and 5 core
flex, as from my two T+Es, none of them are common, so could not merge
them into a 3-way fan isolator. This is because the boiler presents a
separate live feed to the programmer, and in turn a call for heat, in
addition to its live and neutral supply, hence the 2 * T+Es. From a
quick google I am not sure a 4-way isolator is available.

Luke


I'll bet that some of them are common!

You will have to explain a little bit more about your wiring set up.
I am guessing that you are using terminal 4 on the boiler to supply power to
the programmer etc. Where is the programmer getting the neutral from?

Terminal 4 is in effect a permanent live when the boiler is switched on and
you could use a double pole switch as your isolator (just isolate the cable
running from the fused spur in the airing cubpoard) and use heat resistant
flex from the double pole switch to the boiler.

Cheers
--
Adam




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Boiler wiring - Flex or T+E

Luke wrote:
On Sep 27, 9:24 am, "ARWadsworth"
wrote:
Luke wrote:
Hi all,


As some of you may know I'm installing gas central heating with the
boiler in the loft. Things are progressing well, I've done all the
pipework bar the last metre or so of the gas, and now I just have to
finish off the wiring.


It's a standard Y-plan with the wiring centre in the airing
cupboard. Thermostat in hall and programmer in the kitchen. The
boiler is a Vaillant Ecotec plus 624 system boiler.


From the airing cupboard up to the loft I have run 2 * 1.5mm T+E,
the first of which is the main feed to the boiler which is switched
directly from a 3A switched spur, and the second feeds the
programmer and all other associated switchgear, with the brown wire
providing the live feed and the blue, the call for heat. This is as
recommended by Vaillant - the idea being that if the boiler is
switched off at the applicance, ALL other associated controls are
no longer live.


So my question is how to I present these feeds to the boiler, in
their existing T+E, or do I install a couple of accessories
adjacent to the boiler and make the final run in flex? I am leaning
towards flex, as the terminations at the boiler end are clearly
designed to take flex, but essentially, I'm providing fixed wiring
to a fixed appliance.


Assuming flex (and feel free to correct me) what accessories would I
install? 1* unswitched socket for the boiler feed, and 1 * unfused
flex outlet plate do you think? Or 2 * flex outlet plates? Any other
suggestions?


I have put a photo here which shows the current wiring arrangements.


http://tinyurl.com/LukesWiring


The FCU to the left of the wiring centre feeds the boiler.


Thanks in advance.


Luke


I would terminate the T&Es with a fan isolator switch (relabelled
BOILER) and use 4 core heat resistant flex to the boiler. This will
allow local isolation of the boiler in the loft (ie you can then
isolate perm live, switched live and the neutral)

Cheers

--
Adam- Hide quoted text -


Thanks Adam, but I would need a 4-way isolating switch, and 5 core
flex, as from my two T+Es, none of them are common, so could not merge
them into a 3-way fan isolator. This is because the boiler presents a
separate live feed to the programmer, and in turn a call for heat, in
addition to its live and neutral supply, hence the 2 * T+Es. From a
quick google I am not sure a 4-way isolator is available.

Luke


I think I have worked out how you have wired it up (the clue was in the
photo with the gripfill just before the plaster was stuck on)

All you need is 5 core flex, a double pole switch with a deep patress and
strip connector (or crimps).

Use the double pole switch to isolate the live neutral feed to the boiler
(local electrical isolation is required for boilers) and the two other cores
in the flex need strip connecting to the other T&E behind the switch. You do
not need a 3 or 4 pole isolator as when the double pole switch is off then
there is no power down to your wiring centre in the airing cupboard

Cheers

--
Adam


  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 57
Default Boiler wiring - Flex or T+E

On Sep 27, 11:11*am, "ARWadsworth"
wrote:
Luke wrote:
On Sep 27, 9:24 am, "ARWadsworth"
wrote:
Luke wrote:
Hi all,


As some of you may know I'm installing gas central heating with the
boiler in the loft. Things are progressing well, I've done all the
pipework bar the last metre or so of the gas, and now I just have to
finish off the wiring.


It's a standard Y-plan with the wiring centre in the airing
cupboard. Thermostat in hall and programmer in the kitchen. The
boiler is a Vaillant Ecotec plus 624 system boiler.


From the airing cupboard up to the loft I have run 2 * 1.5mm T+E,
the first of which is the main feed to the boiler which is switched
directly from a 3A switched spur, and the second feeds the
programmer and all other associated switchgear, with the brown wire
providing the live feed and the blue, the call for heat. This is as
recommended by Vaillant - the idea being that if the boiler is
switched off at the applicance, ALL other associated controls are
no longer live.


So my question is how to I present these feeds to the boiler, in
their existing T+E, or do I install a couple of accessories
adjacent to the boiler and make the final run in flex? I am leaning
towards flex, as the terminations at the boiler end are clearly
designed to take flex, but essentially, I'm providing fixed wiring
to a fixed appliance.


Assuming flex (and feel free to correct me) what accessories would I
install? 1* unswitched socket for the boiler feed, and 1 * unfused
flex outlet plate do you think? Or 2 * flex outlet plates? Any other
suggestions?


I have put a photo here which shows the current wiring arrangements.


http://tinyurl.com/LukesWiring


The FCU to the left of the wiring centre feeds the boiler.


Thanks in advance.


Luke


I would terminate the T&Es with a fan isolator switch (relabelled
BOILER) and use 4 core heat resistant flex to the boiler. This will
allow local isolation of the boiler in the loft (ie you can then
isolate perm live, switched live and the neutral)


Cheers


--
Adam- Hide quoted text -


Thanks Adam, but I would need a 4-way isolating switch, and 5 core
flex, as from my two T+Es, none of them are common, so could not merge
them into a 3-way fan isolator. This is because the boiler presents a
separate live feed to the programmer, and in turn a call for heat, in
addition to its live and neutral supply, hence the 2 * T+Es. From a
quick google I am not sure a 4-way isolator is available.


Luke


I think I have worked out how you have wired it up (the clue was in the
photo with the gripfill just before the plaster was stuck on)

All you need is 5 core flex, a double pole switch with a deep patress and
strip connector (or crimps).

Use the double pole switch to isolate the live neutral feed to the boiler
(local electrical isolation is required for boilers) and the two other cores
in the flex need strip connecting to the other T&E behind the switch. You do
not need a 3 or 4 pole isolator as when the double pole switch is off then
there is no power down to your wiring centre in the airing cupboard

Cheers

--
Adam- Hide quoted text -

- Show quoted text -


Yes! That's exactly right - excellent deduction work! That makes good
sense, I will take your advice and wire it as you suggest.

Thanks

Luke
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wire Flex or Aluminum Flex for Heater Duct Tube Audio Home Repair 0 May 28th 08 05:19 PM
What's the best way of wiring a screw-terminal plug with flex? [email protected] UK diy 10 July 25th 07 10:27 PM
boiler wiring Andrew L. UK diy 6 January 7th 07 10:12 PM
Boiler wiring pm UK diy 4 September 13th 06 01:13 PM
short runs of flex hose vs hvac aluminum flex vs pvc pipe for DC ductwork [email protected] Woodworking 4 December 15th 04 03:43 AM


All times are GMT +1. The time now is 03:37 AM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"