A couple of q's on boiler wiring:

The boiler manual says to run the pump live, earth & neutral from three
terminals on the boiler.
I must also run live, neutral and earth to the wiring box for the
controls. This needs to be fed from the same switch as the boiler so it
is not possible to switch part of the system of and have the rest live.

I also need a switched live from the wiring box to the boiler.

I plan to put the wiring box and pump in the airing cupboard. The boiler
will be in the kitchen.

First q - the boiler wiring must be 90deg heat resistant, I can only
find flex that is high temp rated and I understand that flex mustn't be
buried in walls. Why is this? For a fixed installation, can I run the
flex in conduit that is buried? I would rather do this than surface mount.

Second q - ignoring the permanent L/N/E from the switch to the wiring
box, according to the instructions I need four conductors going from the
boiler to the airing cupboard - pump live, pump neutral, pump earth and
switched live. All the heat resistant flex I've seen is three core. Can
I get away with using the earth cable in the flex as the switched live
and take the pump earth from the wiring box if I tag (or sleeve) the
cable appropriately? To me this is similar to using the black connector
for switched live in a lighting circuit.

Answers, comments and suggestions appreciated as always.

Pete
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Boiler wiring

In article ,
pm writes:
A couple of q's on boiler wiring:

The boiler manual says to run the pump live, earth & neutral from three
terminals on the boiler.
I must also run live, neutral and earth to the wiring box for the
controls. This needs to be fed from the same switch as the boiler so it
is not possible to switch part of the system of and have the rest live.

I also need a switched live from the wiring box to the boiler.

I plan to put the wiring box and pump in the airing cupboard. The boiler
will be in the kitchen.

First q - the boiler wiring must be 90deg heat resistant, I can only
find flex that is high temp rated and I understand that flex mustn't be
buried in walls. Why is this? For a fixed installation, can I run the
flex in conduit that is buried? I would rather do this than surface mount.


Flex isn't normally buried in walls, but there's nothing in the
wiring regulations which forbids it. 90deg T&E is available; it
has a white sheath with the new wiring colours (white sheath with
old wiring colours doesn't mean 90deg). You would probably have
to go to an electrical wholesaler or other specialist supplier
though.

Second q - ignoring the permanent L/N/E from the switch to the wiring
box, according to the instructions I need four conductors going from the
boiler to the airing cupboard - pump live, pump neutral, pump earth and
switched live. All the heat resistant flex I've seen is three core. Can
I get away with using the earth cable in the flex as the switched live
and take the pump earth from the wiring box if I tag (or sleeve) the
cable appropriately? To me this is similar to using the black connector
for switched live in a lighting circuit.


No, the cable needs an earth conductor in it even if it isn't
used at the other end.

I suggest you go along to a wholesaler and see if you can get a
small reel of 90deg triple and earth. You will probably have
difficuly buying it by the metre.

--
Andrew Gabriel
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3
Default Boiler wiring

pm wrote:

First q - the boiler wiring must be 90deg heat resistant, I can only
find flex that is high temp rated and I understand that flex mustn't be
buried in walls. Why is this? For a fixed installation, can I run the
flex in conduit that is buried? I would rather do this than surface mount.


Electricians do not normally bury flex in walls - T&E cable is cheaper
and we always have loads of it.

The "official" reason is that the thermal and mechanical properties of
the flex can differ widely from those of a flat cable.

Most electricians will wire the boiler to a flex outlet plate

http://www.screwfix.com/app/sfd/cat/pro.jsp?id=46753

with heat-resistant flex, and then to wire the rest of the
installation in T&E cable.

Second q - ignoring the permanent L/N/E from the switch to the wiring
box, according to the instructions I need four conductors going from the
boiler to the airing cupboard - pump live, pump neutral, pump earth and
switched live. All the heat resistant flex I've seen is three core. Can
I get away with using the earth cable in the flex as the switched live
and take the pump earth from the wiring box if I tag (or sleeve) the
cable appropriately?


No. Don't do this as anybody cutting into the cable in the middle
would expect the bare conductor to be earth. Use 1.0mm or 1.5mm
three-core and earth cable instead.

To me this is similar to using the black connector
for switched live in a lighting circuit.


No that's using an insulated conductor not the earth. You should also
add sleeving to indicate that the conductor is live and not neutral.

If you are in England or Wales then "Part P" will apply to this work.

John
--
John White,
Electrical Contractor
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Boiler wiring

pm wrote:

First q - the boiler wiring must be 90deg heat resistant, I can only
find flex that is high temp rated and I understand that flex mustn't be
buried in walls. Why is this? For a fixed installation, can I run the
flex in conduit that is buried? I would rather do this than surface mount.


The normal approach if you want it burried, would be to run it most of
the way in T&E and terminate it at a flex connection unit. Then do the
last bit in heat resistant flex.

Second q - ignoring the permanent L/N/E from the switch to the wiring
box, according to the instructions I need four conductors going from the
boiler to the airing cupboard - pump live, pump neutral, pump earth and
switched live. All the heat resistant flex I've seen is three core. Can
I get away with using the earth cable in the flex as the switched live
and take the pump earth from the wiring box if I tag (or sleeve) the
cable appropriately? To me this is similar to using the black connector
for switched live in a lighting circuit.


I have seen people re-designate the earth in this way, and to be honest
it is poor practice.

A better way would be to wire the bulk in three core and earth, and then
use flex for the last bit. If you need more than the normal number of
cores in a flex you can either use more than one of them, or get some
"control flex" which is usually available in upto seven core. For example:

http://cpc.farnell.com/jsp/endecaSea...sp?SKU=CB08736

(note that is only a 70 degree one)

High temp:

http://cpc.farnell.com/jsp/endecaSea...p?SKU=CBBR0097

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #5   Report Post  
Posted to uk.d-i-y
PM PM is offline
external usenet poster
 
Posts: 31
Default Boiler wiring

Thanks Andrew and the Johns, I have sourced some 4-way heat resistant flex,
available by the metre, and bought two flex outlets.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring a room thermostat to a combi boiler [email protected] UK diy 7 March 18th 06 04:18 PM
Sime boiler, year old, never worked properly Tricky UK diy 3 December 1st 05 08:56 PM
11degC across Boiler, why? Tom UK diy 54 September 24th 04 08:32 AM
Heat banks (again!) Dave UK diy 148 September 6th 04 09:45 PM
Boiler TP valve problems? Linc Vannah Home Repair 9 May 8th 04 03:20 AM


All times are GMT +1. The time now is 11:23 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"