Default Flickering supply causes breaker tripping

Title says it really.
Yesterday we had some lightning which obviously led to some supply
issues resulting in flickering supply.

I thnk I reset the breaker 10x yesterday
I've tested the RCD and it trips at exactly 30mA.
[Tested by connecting 1 through 6 47K resistors from live to earth -
each adds 2mA of leakage.]

I had a visit from EDF a few months ago. The first guy found something
that I believe is key. [Not certain of the exact numbers here as I'm
working from memory.] He said my earth imedance was 0.37 ohm to
substation, and the spec limit is 0.38 ohms..

Then [just to get out I feel] he said he would arrange for a voltage
recorder for a week or so. Of course everything was perfect during
that period, so no action.
I called up EDF again today and got through to someone who insisted it
is my problem and that their supply could not possibly cause my
breaker to trip. Further the earth impedance is in spec - even if
1/100 ohm from spec. I really didn't like his atitude.

Any suggestions ?
I'm at the end of my tether and tired of re-setting the clocks!
My ideas (pssibly off the wall) include:
1. 100mA breaker instead of 30mA - but I don't like the loss of safety
protection so it's a last resort.
2. I believe it may be related to capacitance of the wiring as it's a
large extended 70s house. I'm thinking about adding a 240VAC rated
capacitor(s) at the entry point to try and swamp my wiring
capacitance.
3. Add my own earth spike to reduce earth impedance.

Thanks,
Fred
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,532
Default Flickering supply causes breaker tripping

On Aug 27, 2:11*pm, Fred wrote:
Title says it really.
Yesterday we had some lightning which obviously led to some supply
issues resulting in flickering supply.

I thnk I reset the breaker 10x yesterday
I've tested the RCD and it trips at exactly 30mA.
[Tested by connecting 1 through 6 *47K resistors from live to earth -
each adds 2mA of leakage.]

I had a visit from EDF a few months ago. The first guy found something
that I believe is key. *[Not certain of the exact numbers here as I'm
working from memory.] He said my earth imedance was 0.37 ohm to
substation, and the spec limit is 0.38 ohms..

Then [just to get out I feel] he said he would arrange for a voltage
recorder for a week or so. Of course everything was perfect during
that period, so no action.
I called up EDF again today and got through to someone who insisted it
is my problem and that their supply could not possibly cause my
breaker to trip.


right

Further the earth impedance is in spec - even if
1/100 ohm from spec. I really didn't like his atitude.

Any suggestions ?


A good start would be to stop trying to blame someone else for what's
happening on your system. It wont achieve anything useful.


I'm at the end of my tether and tired of re-setting the clocks!
My ideas (pssibly off the wall) include:
1. 100mA breaker instead of 30mA - but I don't like the loss of safety
protection so it's a last resort.
2. I believe it may be related to capacitance of the wiring as it's a
large extended 70s house. I'm thinking about adding a 240VAC rated
capacitor(s) at the entry point to try and swamp my wiring
capacitance.
3. Add my own earth spike to reduce earth impedance.

Thanks,
Fred


2&3 wont help any. You need to begin by determining where the problem
is. Since the RCD works ok, the next thing I'd do is leakage test all
your appliances. A megger is the right tool, but if really necessary
you can often spot the faulty one with a multimeter.
http://wiki.diyfaq.org.uk/index.php?title=Megger
http://wiki.diyfaq.org.uk/index.php?title=Multimeter


NT
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,036
Default Flickering supply causes breaker tripping



--
Graham.

%Profound_observation%
"Fred" wrote in message ...
Title says it really.
Yesterday we had some lightning which obviously led to some supply
issues resulting in flickering supply.

I thnk I reset the breaker 10x yesterday
I've tested the RCD and it trips at exactly 30mA.
[Tested by connecting 1 through 6 47K resistors from live to earth -
each adds 2mA of leakage.]

I had a visit from EDF a few months ago. The first guy found something
that I believe is key. [Not certain of the exact numbers here as I'm
working from memory.] He said my earth imedance was 0.37 ohm to
substation, and the spec limit is 0.38 ohms..

Then [just to get out I feel] he said he would arrange for a voltage
recorder for a week or so. Of course everything was perfect during
that period, so no action.
I called up EDF again today and got through to someone who insisted it
is my problem and that their supply could not possibly cause my
breaker to trip. Further the earth impedance is in spec - even if
1/100 ohm from spec. I really didn't like his atitude.

Any suggestions ?
I'm at the end of my tether and tired of re-setting the clocks!
My ideas (pssibly off the wall) include:
1. 100mA breaker instead of 30mA - but I don't like the loss of safety
protection so it's a last resort.
2. I believe it may be related to capacitance of the wiring as it's a
large extended 70s house. I'm thinking about adding a 240VAC rated
capacitor(s) at the entry point to try and swamp my wiring
capacitance.
3. Add my own earth spike to reduce earth impedance.

Thanks,
Fred


Sounds like a classic case of supply transients causing earth referenced EMC
capacitors to briefly conduct heavily enough to trip the RCD.
Not the capacitance of the wiring, you understand;
the capacitance of a capacitor in one or more of your appliances.
I would suspect the washing machine in the first instance.

When the RCD was tripping regularly, did you take the opportunity
to switch off circuits in turn to eliminate the appliances on them?

I am no expert in these matters, but I don't think the earth impendence has
much baring on what you describe, and in any case I cant help wondering
about the digit resolution and calibration tolerance of the instrument.


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Flickering supply causes breaker tripping

Fred wrote:
Title says it really.
Yesterday we had some lightning which obviously led to some supply
issues resulting in flickering supply.

I thnk I reset the breaker 10x yesterday
I've tested the RCD and it trips at exactly 30mA.



For some reason I can hear Baldrick saying "I have a cunning plan"

--
Adam


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,683
Default Flickering supply causes breaker tripping

On Aug 27, 4:04*pm, "ARWadsworth"
wrote:
For some reason I can hear Baldrick saying "I have a cunning plan"


He went to work on the breakup of the electricity network in the
UK :-)

OP:
If your supply is TN-C-S (PME) the limit is 0.35ohms however the
measurement tools have quite a substantial error when you get down
that far, never mind the test lead contact resistance. It would only
become an issue if the figure rose sufficiently high at the furthest
point on your install to mean a circuit breaker will not disconnect on
a L-E fault within a reasonable time (which is about 0.4sec). Thus
that is not a concern.

There is a Wiki / uk.d-i-y FAQ on RCD tripping. Basically unplug
everything (not just turn off), then see if the RCD trips.

If you have a split-load RCD system you may want to create a dual RCD
setup (RCD1 RCD2) or convert to split load, or convert to a couple of
RCBO thereby (say) keeping lights (up & hall) and one power circuit on
(cooker) if the main RCD trips out.

RCDs will trip on N-E faults - damp socket, screw touching a cable,
trapped cable in a floorboard, water penetration into an external
circuit, or on L-E faults such as failing immersion element, kettle
element, heater element, washing machine or dryer or cooker element,
clothes iron, even microwaves are not unknown.

If you do buy an IR tester from say Ebay to test each cable
individually, you need to ensure any burglar alarm & smoke alarm is
disconnected, along with all other appliances. Neon's will give fake
low IR (eg, 0.67megohm) so they need to be out of circuit (fuse out or
turned off).


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 754
Default Flickering supply causes breaker tripping

On 27 Aug, 14:11, Fred wrote:
Title says it really.
Yesterday we had some lightning which obviously led to some supply
issues resulting in flickering supply.

I thnk I reset the breaker 10x yesterday
I've tested the RCD and it trips at exactly 30mA.
[Tested by connecting 1 through 6 *47K resistors from live to earth -
each adds 2mA of leakage.]


Are you using precision resistors then? 20% is the tolerance of common
resistors. This also assumes a stable voltage which you already state
is varying (flickering).


I had a visit from EDF a few months ago. The first guy found something
that I believe is key. *[Not certain of the exact numbers here as I'm
working from memory.] He said my earth imedance was 0.37 ohm to
substation, and the spec limit is 0.38 ohms..


You need to understand just how a 30mA RCD works. It compares the L &
N currents and trips if there is a difference in the order of 30mA -
(more comonly around 25 to 30) A minor variation in external earth
loop impedance is immaterial to its operation.


Then [just to get out I feel] he said he would arrange for a voltage
recorder for a week or so. Of course everything was perfect during
that period, so no action.
I called up EDF again today and got through to someone who insisted it
is my problem and that their supply could not possibly cause my
breaker to trip. Further the earth impedance is in spec - even if
1/100 ohm from spec. I really didn't like his atitude.


You were getting factual advice - attitudes regardless


Any suggestions ?
I'm at the end of my tether and tired of re-setting the clocks!
My ideas (pssibly off the wall) include:
1. 100mA breaker instead of 30mA - but I don't like the loss of safety
protection so it's a last resort.
2. I believe it may be related to capacitance of the wiring as it's a
large extended 70s house. I'm thinking about adding a 240VAC rated
capacitor(s) at the entry point to try and swamp my wiring
capacitance.
3. Add my own earth spike to reduce earth impedance.

Thanks,
Fred


Stop poking around without the requisite knowledge, you might do well
to get hold of a copy of the "On Site Guide to BS7671", or engage
someone competent. Obtain proper test equipment and carry out a ramp
test on the RCD with its load terminals disconnected, carry out
insulation resistance tests L & N to earth on your installation but
take precautions not to apply 500v dc to electronic equipment as it
will in all probability die if you do.
A lot of electronic equipment is supplied with noise spike filtering
circuitry and many appliances have suppressor circuits. This can and
does create an earth leakage path - enough of these and you are into
nuisance tripping country.
I have yet to find a domestic installation with sufficient fixed
wiring inter-conductor capacitance to cause enough leakage to cause
tripping. I think you can forget the theory that capacitive leakage is
your problem. If capacitive leakage is the problem its in an appliance
or several of them combined.
Domestic electrical systems are relatively simple but do need someone
with competence not the "a little knowledge is a dangerous thing" as
per the old adage.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,896
Default Flickering supply causes breaker tripping

If your supply is TN-C-S (PME) the limit is 0.35ohms however the
measurement tools have quite a substantial error when you get down
that far, never mind the test lead contact resistance. It would only
become an issue if the figure rose sufficiently high at the furthest
point on your install to mean a circuit breaker will not disconnect on
a L-E fault within a reasonable time (which is about 0.4sec). Thus
that is not a concern.

There is a Wiki / uk.d-i-y FAQ on RCD tripping. Basically unplug
everything (not just turn off), then see if the RCD trips.

If you have a split-load RCD system you may want to create a dual RCD
setup (RCD1 RCD2) or convert to split load, or convert to a couple of
RCBO thereby (say) keeping lights (up & hall) and one power circuit on
(cooker) if the main RCD trips out.

RCDs will trip on N-E faults - damp socket, screw touching a cable,
trapped cable in a floorboard, water penetration into an external
circuit, or on L-E faults such as failing immersion element, kettle
element, heater element, washing machine or dryer or cooker element,
clothes iron, even microwaves are not unknown.

If you do buy an IR tester from say Ebay to test each cable
individually, you need to ensure any burglar alarm & smoke alarm is
disconnected, along with all other appliances. Neon's will give fake
low IR (eg, 0.67megohm) so they need to be out of circuit (fuse out or
turned off).



JOOI with a PME system where the leccy co supplies the "Earth" thats
just a connection to the neutral of the incoming cable is it not?.

Well it is here..

So if thats providing the "Earth" as such is it that critical if the
resistance to actual "Earth" (being the ground in this instance) is high
at all?.

After all if a cable hits anything thats "earthed" then the fault
current is flowing from Live to wherever that Earth is. Course if thats
connected to the mains incomer earth then thats a full short across the
incoming cable and that should take the fuses to Kingdom come very
quickly.

However if that live should short to some other metal in the gaff then
the resistance of that to "Earth" can either be via a PME system or
wherever that bit of metal is or is not connected to?..

And the fault current can then be lots or rather little?..

So seem to me best protection is via RCD in most all cases..


--
Tony Sayer



  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default Flickering supply causes breaker tripping

cynic wrote:
On 27 Aug, 14:11, Fred wrote:
Title says it really.
Yesterday we had some lightning which obviously led to some supply
issues resulting in flickering supply.

I thnk I reset the breaker 10x yesterday
I've tested the RCD and it trips at exactly 30mA.
[Tested by connecting 1 through 6 47K resistors from live to earth -
each adds 2mA of leakage.]


Are you using precision resistors then? 20% is the tolerance of common
resistors. This also assumes a stable voltage which you already state
is varying (flickering).

I had a visit from EDF a few months ago. The first guy found something
that I believe is key. [Not certain of the exact numbers here as I'm
working from memory.] He said my earth imedance was 0.37 ohm to
substation, and the spec limit is 0.38 ohms..


You need to understand just how a 30mA RCD works. It compares the L &
N currents and trips if there is a difference in the order of 30mA -
(more comonly around 25 to 30) A minor variation in external earth
loop impedance is immaterial to its operation.

Then [just to get out I feel] he said he would arrange for a voltage
recorder for a week or so. Of course everything was perfect during
that period, so no action.
I called up EDF again today and got through to someone who insisted it
is my problem and that their supply could not possibly cause my
breaker to trip. Further the earth impedance is in spec - even if
1/100 ohm from spec. I really didn't like his atitude.


You were getting factual advice - attitudes regardless

Any suggestions ?
I'm at the end of my tether and tired of re-setting the clocks!
My ideas (pssibly off the wall) include:
1. 100mA breaker instead of 30mA - but I don't like the loss of safety
protection so it's a last resort.
2. I believe it may be related to capacitance of the wiring as it's a
large extended 70s house. I'm thinking about adding a 240VAC rated
capacitor(s) at the entry point to try and swamp my wiring
capacitance.
3. Add my own earth spike to reduce earth impedance.

Thanks,
Fred


Stop poking around without the requisite knowledge, you might do well
to get hold of a copy of the "On Site Guide to BS7671", or engage
someone competent. Obtain proper test equipment and carry out a ramp
test on the RCD with its load terminals disconnected, carry out
insulation resistance tests L & N to earth on your installation but
take precautions not to apply 500v dc to electronic equipment as it
will in all probability die if you do.
A lot of electronic equipment is supplied with noise spike filtering
circuitry and many appliances have suppressor circuits. This can and
does create an earth leakage path - enough of these and you are into
nuisance tripping country.
I have yet to find a domestic installation with sufficient fixed
wiring inter-conductor capacitance to cause enough leakage to cause
tripping. I think you can forget the theory that capacitive leakage is
your problem. If capacitive leakage is the problem its in an appliance
or several of them combined.
Domestic electrical systems are relatively simple but do need someone
with competence not the "a little knowledge is a dangerous thing" as
per the old adage.


I had a very sensitive main trip: Too many compueters and filters.
Replace the main trip with 100mA..if you are running on the edge thats
only 70mA..and that's enough for any common faults. Then fit RCBO's to
the rings that REALLY need 30mA protection. Yes it costs, but it
works.. On the way check any rings or spurs for neutral earth shorts.

Frankly I dont think a main single 30mA fast trip is suitable for modern
installations with a lot of electronics connected.


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,188
Default Flickering supply causes breaker tripping

On 27 Aug, 14:11, Fred wrote:
Title says it really.
Yesterday we had some lightning which obviously led to some supply
issues resulting in flickering supply.

I thnk I reset the breaker 10x yesterday
I've tested the RCD and it trips at exactly 30mA.
[Tested by connecting 1 through 6 *47K resistors from live to earth -
each adds 2mA of leakage.]

I had a visit from EDF a few months ago. The first guy found something
that I believe is key. *[Not certain of the exact numbers here as I'm
working from memory.] He said my earth imedance was 0.37 ohm to
substation, and the spec limit is 0.38 ohms..

Then [just to get out I feel] he said he would arrange for a voltage
recorder for a week or so. Of course everything was perfect during
that period, so no action.
I called up EDF again today and got through to someone who insisted it
is my problem and that their supply could not possibly cause my
breaker to trip. Further the earth impedance is in spec - even if
1/100 ohm from spec. I really didn't like his atitude.

Any suggestions ?
I'm at the end of my tether and tired of re-setting the clocks!
My ideas (pssibly off the wall) include:
1. 100mA breaker instead of 30mA - but I don't like the loss of safety
protection so it's a last resort.
2. I believe it may be related to capacitance of the wiring as it's a
large extended 70s house. I'm thinking about adding a 240VAC rated
capacitor(s) at the entry point to try and swamp my wiring
capacitance.
3. Add my own earth spike to reduce earth impedance.

Thanks,
Fred


In days of yore, RCDs were very prone to tripping due to transients in
the system. New ones are much better. It's possible you won't find
any insulation problem at all or even the source of any transients.
If this is the case, if you RCD is old, a new one may well cure the
problem.
The source of any transients may not be in your property at all.

It's not possible to completely test out RCD devices at home, often
substitution is the answer & see what happens.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker tripping Higgs Boson[_2_] Home Repair 7 August 24th 10 10:55 PM
A/C Unit Keeps Tripping Circuit Breaker - How to test breaker before calling repair man? C5Ya Home Repair 10 August 26th 05 07:34 PM
Tripping Breaker jozep7075 Home Ownership 5 January 14th 05 11:50 PM
a/c tripping circuit breaker PipoG Electronics Repair 3 July 29th 03 04:30 PM
breaker tripping barry martin Home Repair 0 June 23rd 03 08:58 PM


All times are GMT +1. The time now is 09:19 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"