UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 298
Default Cable in the floor?

Hi,

Sorry this is long! - A mate of mine has just bought a new house, with solid
floors downstairs.

In the Kitchen, there is one just one 15A radial installed, with the cable
dropping down to just one double socket near the internal door.

He would like a few more sockets, including a couple in the cupboards for
the washing machine and dishwasher.

Is it allowed to extend this radial and then run it back to the CU to create
a ring, but have part of the cable in the solid floor?

It will be protected by a 32A/30mA RCBO.

With a wall, you have to have a visible accessory and then run cables up,
down or sideways from that - what happens in a floor? - we would rather not
sink a box in the floor!

Assuming this is allowed, I assume the cable needs to be in conduit?

Would it also have to be 50mm deep too, or does the 30mA RCBO negate that?

The only other practical option would be to run the cable from the last
socket, up the wall to the ceiling, then along to the left in the safe zone
until we reach the corner, take it round the corner to the next wall, then
immediately down the wall, in the safe zone, then through the wall to the
under-stairs cupboard, which seems a little convoluted to me.
Running it under the 1st floor is not practical, as there is a bathroom
above with a tiled floor, so we would need to rip that up, or take the
ceiling down in the kitchen.

On another note, he would also like to bury a 22mm gas pipe in the floor
too, as it currently runs along the wall, at just above door level, and
looks absolutely hideous as the boiler is in the opposite corner of the room
where the gas enters - what are the rules for this, other than running it in
copper, wrapped in denso tape with soldered connections, is there a minimum
depth?

It, like the power cable, will need to run from the under stairs cupboard
(next "room" from the kitchen), in a straight line (parallel to the wall) to
appear under the kitchen cupboards, approximately 50-100mm from the wall
(external wall, and will pass across a doorway to the back garden) total
under floor run is about 1.5-2m, once it has got to the cupboards, it would
be run under the cupboards until it is under the boiler (Old Potterton
Profile 40, but likely to be upgraded at some point, hence the 22mm) then
run up to the boiler. The gas hob is where the gas pipe would pop up from
under the floor.

It is not practical to run the gas pipe outside, along the wall, then back
into the Kitchen, as there is a door in the way, with something in the way
above and below the door.

Thanks!

Toby...

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,683
Default Cable in the floor?

On Aug 8, 12:21*am, "Toby" wrote:
In the Kitchen, there is one just one 15A radial installed, with the cable
dropping down to just one double socket near the internal door.


Check what the CU is - is it recent, circuit breakers rather than
fuses still available, large enough?
Check what the cable is - is it PVC of 2.5mm size or old TRS or lead?
Check what the meter tails are - 25mm PVC grey outer double insulated
(6181Y)?
Check the DNO cutout type - modern plastic fuse-holder rather than
metalclad?

He may be in for a "migration".
New CU fitted via Henley Blocks (splitters) off the meter tails, with
2-3 RCD or all RCBO (bought as needed). Migrate circuits to the new CU
as each cable is replaced during room redecoration.

You can do anything under Part P SI2006. However you can not change a
CU nor add a new final circuit without notifying BC who will charge a
fee to come and inspect it. So it comes down to what is needed re how
to manage it.


Is it allowed to extend this radial


Yes if the cable is in good condition and PVC rather than say TRS
rubber or lead.


and then run it back to the CU to create a ring,
but have part of the cable in the solid floor?


Solid floor means a) cable 50mm from the surface b) protected by 3mm
steel which would really need to be galvanised or c) BS8436 cable
which complies with 526.6 (has a foil sheath). You can not use SWA
because the glands have to be accessible for inspection & testing at
each end.

Why can you not run the cable around the walls or thro the ceiling
void?
You have corner vertical zones of 150mm and ceiling zones of 150mm.
You run up or across to one of them and around.

If you have a sloping ceiling (leanto) you can use a 1G or 2G box with
blank plate for routing (not particularly common but an acceptable
technique re BS7671 Wiring Zones).


It will be protected by a 32A/30mA RCBO.


If the CU will take them, fine.


With a wall, you have to have a visible accessory and then run cables up,
down or sideways from that - what happens in a floor? - we would rather not
sink a box in the floor!


If you can avoid sinking into a floor, do so, particularly a kitchen
as people do put screws in it (end panels for kitchen units).

You need to pick up the 17th On Site Guide (OSG) from Amazon/anywhere
and a good Electrician's Guide (do an Amazon search if only as a
"catalog").


Assuming this is allowed, I assume the cable needs to be in conduit?


As above (yes you can use steel conduit, but unless this is a straight
run things get difficult).


The only other practical option would be to run the cable from the last
socket, up the wall to the ceiling, then along to the left in the safe zone
until we reach the corner, take it round the corner to the next wall, then
immediately down the wall, in the safe zone, then through the wall to the
under-stairs cupboard, which seems a little convoluted to me.


That would be considered normal :-)

Running it under the 1st floor is not practical, as there is a bathroom
above with a tiled floor, so we would need to rip that up, or take the
ceiling down in the kitchen.


Cables should not be run through the bathroom unless they are destined
for it, however the underfloor void is a grey area. In practice you
would take down the ceiling if necessary below. There are also Cable
Access Rods with chains, magnets, flexible & rigid fibreglass rods,
lights on the end etc.


On another note, he would also like to bury a 22mm gas pipe in the floor
too, as it currently runs along the wall, at just above door level, and
looks absolutely hideous as the boiler is in the opposite corner of the room
where the gas enters - what are the rules for this, other than running it in
copper, wrapped in denso tape with soldered connections, is there a minimum
depth?


No longer denso tape.

You would use factory PVC coated yellow-ochre coiled flexible copper
pipe, run in plastic conduit.
www.bes.co.uk (think that is the URL) list it. Alternatively you could
use Tracpipe but beware due to its plastic coated convoluted stainless
steel nature it is large diameter - eg, 22mm measures out to 28mm
externally. Thus you need a big trench in a floor which then begs the
question how deep your screed is.


It is not practical to run the gas pipe outside, along the wall, then back
into the Kitchen, as there is a door in the way, with something in the way
above and below the door.


Check outside again, sometimes it can work, but yes it is ugly.

You need to find out a) what you have and b) understand how to do it
re good electrician's guide. That is even if you get someone else in
to do it so you can understand why / how things are done so you get
what you want.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Cable in the floor?

Toby wrote:
Hi,

Sorry this is long! - A mate of mine has just bought a new house,
with solid floors downstairs.

In the Kitchen, there is one just one 15A radial installed, with the
cable dropping down to just one double socket near the internal door.

He would like a few more sockets, including a couple in the cupboards
for the washing machine and dishwasher.

Is it allowed to extend this radial and then run it back to the CU to
create a ring, but have part of the cable in the solid floor?

It will be protected by a 32A/30mA RCBO.

With a wall, you have to have a visible accessory and then run cables
up, down or sideways from that - what happens in a floor? - we would
rather not sink a box in the floor!

Assuming this is allowed, I assume the cable needs to be in conduit?

Would it also have to be 50mm deep too, or does the 30mA RCBO negate
that?


No the RCD would not negate that. But if it is close to a corner (15cm)
between the wall and floor then no problem.

I recently used two 4mm 32A radials for a kitchen. One on each side to save
the ceiling getting pulled down. Would that work in your case?


--
Adam


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,532
Default Cable in the floor?

On Aug 8, 12:21*am, "Toby" wrote:
Hi,

Sorry this is long! - A mate of mine has just bought a new house, with solid
floors downstairs.

In the Kitchen, there is one just one 15A radial installed, with the cable
dropping down to just one double socket near the internal door.

He would like a few more sockets, including a couple in the cupboards for
the washing machine and dishwasher.

Is it allowed to extend this radial and then run it back to the CU to create
a ring, but have part of the cable in the solid floor?

It will be protected by a 32A/30mA RCBO.


That would work fine, but you need to find out what size the old cable
is and ensure your mcb is within the cable's ratings. Sounds to me
like extending the existing circuit.


With a wall, you have to have a visible accessory and then run cables up,
down or sideways from that - what happens in a floor? - we would rather not
sink a box in the floor!

Assuming this is allowed, I assume the cable needs to be in conduit?

Would it also have to be 50mm deep too, or does the 30mA RCBO negate that?

The only other practical option would be to run the cable from the last
socket, up the wall to the ceiling, then along to the left in the safe zone
until we reach the corner, take it round the corner to the next wall, then
immediately down the wall, in the safe zone, then through the wall to the
under-stairs cupboard, which seems a little convoluted to me.
Running it under the 1st floor is not practical, as there is a bathroom
above with a tiled floor, so we would need to rip that up, or take the
ceiling down in the kitchen.


Or you can cut 3 portals in the ceiling, one each end and one half
way. Sounds like youre making a mountain out of a molehill though.


NT
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 298
Default Cable in the floor?


"ARWadsworth" wrote in message
news:QBz7o.131242$tB1.25144@hurricane...
Toby wrote:
Hi,

Sorry this is long! - A mate of mine has just bought a new house,
with solid floors downstairs.

In the Kitchen, there is one just one 15A radial installed, with the
cable dropping down to just one double socket near the internal door.

He would like a few more sockets, including a couple in the cupboards
for the washing machine and dishwasher.

Is it allowed to extend this radial and then run it back to the CU to
create a ring, but have part of the cable in the solid floor?

It will be protected by a 32A/30mA RCBO.

With a wall, you have to have a visible accessory and then run cables
up, down or sideways from that - what happens in a floor? - we would
rather not sink a box in the floor!

Assuming this is allowed, I assume the cable needs to be in conduit?

Would it also have to be 50mm deep too, or does the 30mA RCBO negate
that?


No the RCD would not negate that. But if it is close to a corner (15cm)
between the wall and floor then no problem.

I recently used two 4mm 32A radials for a kitchen. One on each side to
save the ceiling getting pulled down. Would that work in your case?


--
Adam


Don't think so, as getting access to the existing 2.5 will be a pain, as it
runs under the bathroom.

Having looked at it again, there is a water pipe that runs up to the right
of the door that goes out to the garden, and ends up on the landing, just
outside the bathroom, so we should be able to route a cable to the 1st floor
under-floor void here (he wants to bury that pipe in the wall too), just
means installing an accessory in line, which we can actually power the
cooker hood from anyway, presuming it is OK to put this above the hood?

Toby...



  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Cable in the floor?

js.b1 wrote:

Solid floor means a) cable 50mm from the surface b) protected by 3mm
steel which would really need to be galvanised or c) BS8436 cable
which complies with 526.6 (has a foil sheath).


There's no 50 mm rule for cables buried in solid floors. You're
thinking of 552.6.6 which only applies to walls or partitions and
552.6.5 which only applies to cables passing /through joists/ in floor
and/or ceiling constructions.

522.6.4 is the relevant reg. here and all it says is:

"A wiring system buried in a floor shall be sufficiently protected to
prevent damage caused by the intended use of the floor".

For a domestic screeded floor in places where drilling is pretty
unlikely it's OK, IMHO, to run T&E cable in PVC conduit buried in the
floor at depths of 50 mm without further reinforcement. To facilitate
rewiring, should anything untoward happen, keep the conduit runs simple
with minimal use of bends (don't use elbows). Use 20 mm conduit only
for one 2.5 T&E cable, 25 mm for two such. Ribbed flexible conduit is
another possibility.

--
Andy
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Cable in the floor?

Toby wrote:
"ARWadsworth" wrote in message
news:QBz7o.131242$tB1.25144@hurricane...
Toby wrote:
Hi,

Sorry this is long! - A mate of mine has just bought a new house,
with solid floors downstairs.

In the Kitchen, there is one just one 15A radial installed, with the
cable dropping down to just one double socket near the internal
door. He would like a few more sockets, including a couple in the
cupboards for the washing machine and dishwasher.

Is it allowed to extend this radial and then run it back to the CU
to create a ring, but have part of the cable in the solid floor?

It will be protected by a 32A/30mA RCBO.

With a wall, you have to have a visible accessory and then run
cables up, down or sideways from that - what happens in a floor? -
we would rather not sink a box in the floor!

Assuming this is allowed, I assume the cable needs to be in conduit?

Would it also have to be 50mm deep too, or does the 30mA RCBO
negate that?


No the RCD would not negate that. But if it is close to a corner
(15cm) between the wall and floor then no problem.

I recently used two 4mm 32A radials for a kitchen. One on each side
to save the ceiling getting pulled down. Would that work in your
case? --
Adam


Don't think so, as getting access to the existing 2.5 will be a pain,
as it runs under the bathroom.

Having looked at it again, there is a water pipe that runs up to the
right of the door that goes out to the garden, and ends up on the
landing, just outside the bathroom, so we should be able to route a
cable to the 1st floor under-floor void here (he wants to bury that
pipe in the wall too), just means installing an accessory in line,
which we can actually power the cooker hood from anyway, presuming it
is OK to put this above the hood?


It is best not to hide the power supply for an extractor behind a hood (if
it is one of those tall hoods). But above a hood without a chimney is fine.

--
Adam


  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,683
Default Cable in the floor?

On Aug 10, 12:39*am, Andy Wade wrote:
522.6.4 is the relevant reg. here and all it says is:
"A wiring system buried in a floor shall be sufficiently protected to
prevent damage caused by the intended use of the floor".


It might be our kitchen fitters were a bit nasty. Whilst the kitchen
units sit on adjustable feet, the end panels & corner panels got L-
brackets into the floor particularly by the washing machine re
wandering capability.

On a U shaped kitchen with 4 end panels (appliance cavities) there are
12 such L-brackets into the floor and a load into the worktop above.

Then again, considering the size of a floor, with a bit of ingenuity
it should be possible to miss conduit buried in it.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Floor power sockets and cable runs mcready UK diy 4 April 11th 06 08:06 AM
Ring Main Cable under Bathroom Floor [email protected] UK diy 6 July 3rd 05 10:49 AM
Laying cable in screed floor Ken UK diy 3 October 26th 04 03:19 PM
cable between floor joists jim_in_sussex UK diy 11 October 13th 04 01:38 AM
Floor nailer - Bostich or Porter Cable Dave Falls Woodworking 5 May 7th 04 12:28 AM


All times are GMT +1. The time now is 12:18 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"