My old mother has just had a new consumer unit fitted (old one was rewireable fuses).

The old cables were not long enough, so some had to be lengthened via a block.

Does the sparky have to issue a full test cert for all circuits, as the cables were lengthened.

Was he right originally in saying that he could not install a new circuit, without a new consumer box being fitted.


--------------= Posted using GrabIt =----------------
------= Binary Usenet downloading made easy =---------
-= Get GrabIt for free from http://www.shemes.com/ =-

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,683
Default New consumer unit, does sparky issue full certs.

On Jul 28, 4:51*pm, "gb" wrote:
My old mother has just had a new consumer unit fitted
(old one was rewireable fuses).


What are her cables - Lead-sheathed, Rubber or PVC?

The old cables were not long enough, so some had to be lengthened via a block.


I know who wired the house - "cables as short n taut as the crow
flies" :-)


Does the sparky have to issue a full test cert for all circuits,
as the cables were lengthened.


Consumer unit change requires an EIC, typical info is...
a - IR test & continuity test of any rings
b - CPC present (Yes or No)
c - Ze measured or assumed from type of supply / DNO enquiry
d - Zs limit (80%) from tables for that circuit breaker type (B) &
rating (20A)
e - Zs measured / calculated for each circuit and within Zs limit (d)
f - RCD actual measured trip times are absolutely vital

In replacing the CU, any spark should at least check...
a - There is no borrowed live/neutral condition (eg, on hall 2-way
lights). A giveaway that there is would be both Lights-UP & Lights-
DOWN on the same RCD rather than split between 2 RCD as 17th reg 314.1
would require.

This check takes 5 min.

b - That Light-UP & Light-DOWN have CPC (earth) present in the cable.
If not she should have at least been advised plus a quick check that
all lights are Class-II, backboxes are plaster or earthed-metal
(separate 4mm 6491X earth) or plastic (Class-II), wiring accessories
are plastic or M3.5 plastic screws used (not easy to find).

This check takes 5 min.

c - That MEB (Main Equipotential Bonding) is in place to Gas & Water
if necessary, plus 17th bathroom requirements met
- Verification that no class-1 lights are in use without a CPC on the
lighting circuit. The Green/Yellow 6491X bonding cable. Addtional work
is required if the supply is TT (ie, she has her own earth rod).

This check takes 15 min. Earth rod tests & validation can take about
2hrs.

d - There are no obviously unsafe circuits, ie, insulation falling
off, blackened & broken kitchen socket, 2-pin cord plug into light
fitting (still have one of those myself, predates RCDs too :-)

There are a few more checks, but you get the idea.
Most electricians would check for a-b-c before changing the CU as part
of a "PIR" or Periodic Inspection Report, or check for them on their
own. It is pretty "no-brainer" stuff for any spark as they do it day-
in-day-out.

CU type.
a - All circuits require RCD protection unless cables are surface run,
50mm from the surface, in steel conduit or BS8436 cable. For your

mother everything would require RCD protection almost certainly.

b - CU should be a minimum of Split Load with at least 2x RCD. Lights
UP should be on RCD #1, Lights DOWN on RCD #2. That is to say not all
lights should be on one RCD - if they are I would suspect there is a
borrowed neutral/live which has not been corrected and really needs to
be re "all lights out and mother down the stairs".


Was he right originally in saying that he could not install
a new circuit, without a new consumer box being fitted.


Depends on what was there previously.

If your new circuit was a single socket (outdoor) or light (kitchen)
he could run that off an existing final circuit if that circuit would
then not be overloaded (by that I mean its functionality not reduced).
He would have to run surface wiring from that fuseholder to an
external RCD such as a 13A RCD protected fused spur or 20A RCD
protected enclosure etc.

If the new circuit was for something like a cooker, the meter tails
could have been Henley Block split to a new CU with 32A RCBO
protection, then check MEB is correct. There may not have been space
in the CU location for this.


CU Change is notifiable to Building Control under Part P.
- Some DIYers do ignore this part, preferring to fix something unsafe
and spend the £200 notification fee saved on RCBO or smoke alarm or
fixing an otherwise unsafe install - but if they break BS7671 or
equivalent named standard it is on their head re any faults introduced
or potentially not rectified.
- Electricians ignoring it are another matter, not so much re breaking
the law but the work *might* not be up to scratch. Realise an
industrial spark with C&G 2382 2392 can not legally do a CU change
unless he is a member of a competent body such as NICEIC ESC BSI
(Electra?) and so on, whereas a 5-day trained NICEIC Domestic
Installer can do it and need not actually comply with BS7671 or
equivalent named standard in doing so, just be "reasonably safe".

A CU change to 17th should be about £450-650 depending on the work
(and extending CU tails can be a fair bit of work and added cost re
enclosures, checking circuits and so on).

Bottom-line.
Do you have a piece of paper with the proper RCD test results on it?
Does the CU have at least 2x RCD? Is the persons name on the Part P
Competent Installer list? Are the lights on 1 RCD or split between 2
RCD? Is there a green/yellow wire running to the gas & cold water
pipes if they are copper (or lead) in the house?
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,307
Default New consumer unit, does sparky issue full certs.

js.b1 wrote:

whereas a 5-day trained NICEIC Domestic
Installer can do it and need not actually comply with BS7671 or
equivalent named standard in doing so, just be "reasonably safe".



I dont think you are right about that.
I am currently revising to take my 2382, and when passed, will not be
able to change a CU,or fit a new circuit, but will be able to do minor
works such as moving/adding sockets to an existing circuit.

Alan.

--
To reply by e-mail, change the ' + ' to 'plus'.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default New consumer unit, does sparky issue full certs.


"A.Lee" wrote in message
...
js.b1 wrote:

whereas a 5-day trained NICEIC Domestic
Installer can do it and need not actually comply with BS7671 or
equivalent named standard in doing so, just be "reasonably safe".



I dont think you are right about that.
I am currently revising to take my 2382, and when passed, will not be
able to change a CU,or fit a new circuit, but will be able to do minor
works such as moving/adding sockets to an existing circuit.

Alan.


Alan

Start with

http://www.niceic.com/Uploads/File1950.pdf

Changing a CU is usually trouble.

Cheers

Adam


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,683
Default New consumer unit, does sparky issue full certs.

DI can be defined-scope or full-scope.

a) Full-scope means they can do a rewire - - without notifying BC by
the DIY-route (£200 fee).
b) Defined-scope means they can wire up a boiler etc - without
notifying BC by the DIY-route (£200 fee).

I suspect a typical BG boiler servicing bod is defined scope DI for
example.

Put simply...
- Domestic - you need to be Competent Scheme member OR pay BC fee for
notifiable works.
- Industrial - you need to be Competent with Insurance. Most companies
want to see C&G 2382 (2392) etc and a whole lot more if it is say a
petrol station.

The former was about a paper trail for dead bodies & undeclared
earnings. Sadly domestic cowboys tend to be long gone and a receipt is
as scarce as "cheque will do". (The Cash Economy from this weeks
experience must be freakin huge :-))


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,175
Default New consumer unit, does sparky issue full certs.

On 28 July, 18:24, "js.b1" wrote:

In replacing the CU, any spark should at least check...
a - There is no borrowed live/neutral condition (eg, on hall 2-way
lights). A giveaway that there is would be both Lights-UP & Lights-
DOWN on the same RCD rather than split between 2 RCD as 17th reg 314.1
would require.

This check takes 5 min.


Whilst splitting the circuits by floors might be a separate
requirement of the regs, and a shared circuit is thus a bad thing,
does this necessarily indicate a borrowed neutral? In particular,
can't a borrowed neutral exist anyway, even if the stair lighting is
supplied (live anyway) correctly? (i.e. absence of the obvious shared
circuit doesn't indicate that there isn't a borrowed neutral).

Last house of mine where I encountered this did have separate circuits
for ground and first, but the two stair lights had neutrals from two
different circuits. The middle landing's came from the ground floor
(actually the rear extension which included both kitchen & bathroom),
the upper landing's was from the first floor circuit that supplied the
bedrooms.

What's the approved method of checking for a borrowed neutral, and
proving that there isn't one?
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default New consumer unit, does sparky issue full certs.


"Andy Dingley" wrote in message
...
On 28 July, 18:24, "js.b1" wrote:

In replacing the CU, any spark should at least check...
a - There is no borrowed live/neutral condition (eg, on hall 2-way
lights). A giveaway that there is would be both Lights-UP & Lights-
DOWN on the same RCD rather than split between 2 RCD as 17th reg 314.1
would require.

This check takes 5 min.


Whilst splitting the circuits by floors might be a separate
requirement of the regs, and a shared circuit is thus a bad thing,
does this necessarily indicate a borrowed neutral? In particular,
can't a borrowed neutral exist anyway, even if the stair lighting is
supplied (live anyway) correctly? (i.e. absence of the obvious shared
circuit doesn't indicate that there isn't a borrowed neutral).

Last house of mine where I encountered this did have separate circuits
for ground and first, but the two stair lights had neutrals from two
different circuits. The middle landing's came from the ground floor
(actually the rear extension which included both kitchen & bathroom),
the upper landing's was from the first floor circuit that supplied the
bedrooms.

What's the approved method of checking for a borrowed neutral, and
proving that there isn't one?


Turning the lights on and sticking a clamp meter over the cables in the CU
is one way.

I always check the landing light before swapping a CU.

Cheers

Adam


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Consumer Unit Fredrick Skoog UK diy 6 May 18th 08 09:12 AM
Consumer unit Capt T UK diy 25 May 17th 08 04:56 PM
New consumer unit Terry D[_2_] UK diy 9 December 2nd 07 02:34 PM
Consumer unit ΠDavid Love UK diy 10 October 24th 06 03:39 PM
new consumer unit-do i need an RCD? tarquinlinbin UK diy 16 October 19th 04 10:52 AM


All times are GMT +1. The time now is 10:19 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"