Hello,

Looking at table 6D1 in the OSG (17th) am I right to read that 6mm^2
T&E clipped direct is rated at 47 Amps but enclosed in conduit the
rating drops to 41 Amps?

Is the length of conduit relevant? I thought I read elsewhere in the
guide that derating where the cable runs through insulation was
dependent on how much cable ran through the insulation.

I would like to run 6mm^2 T&E to the garage. I could clip direct but
does T&E agree with sunlight? I though that conduit might protect it
from UV and impact?

The cable would be protected by a 40A RCBO in the house and terminate
in a CU in the garage. I figure that 32A for sockets plus 6A for
lights = 38A, which is below the 41A limit. But for a couple of
sockets is it worth using a ring; I could use a 16A MCB and have them
as spurs, meaning the maximum load would be 16+6=22A.

Subject to other considerations: earth impedance, voltage drop, etc.
does this sound ok so far? (No burying or overhead cables involved).

Thanks.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,341
Default 6mm^2 T&E ratings

On Wed, 07 Oct 2009 14:40:57 +0100, Stephen wrote:

Hello,

Looking at table 6D1 in the OSG (17th) am I right to read that 6mm^2
T&E clipped direct is rated at 47 Amps but enclosed in conduit the
rating drops to 41 Amps?

Is the length of conduit relevant? I thought I read elsewhere in the
guide that derating where the cable runs through insulation was
dependent on how much cable ran through the insulation.

I would like to run 6mm^2 T&E to the garage. I could clip direct but
does T&E agree with sunlight? I though that conduit might protect it
from UV and impact?


Had 2.5mm outside for ~40 years and it's still flexible (to some extent)
and not cracked. It gets sun on it for about 4 -h/day in the 'Summer'.

This proves that T&E was OK back then.

The cable would be protected by a 40A RCBO in the house and terminate
in a CU in the garage. I figure that 32A for sockets plus 6A for
lights = 38A, which is below the 41A limit. But for a couple of
sockets is it worth using a ring; I could use a 16A MCB and have them
as spurs, meaning the maximum load would be 16+6=22A.

Subject to other considerations: earth impedance, voltage drop, etc.
does this sound ok so far? (No burying or overhead cables involved).

Thanks.



--
Peter.
The head of a pin will hold more angels if
it's been flattened with an angel-grinder.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default 6mm^2 T&E ratings


"Stephen" wrote in message
...
Hello,

Looking at table 6D1 in the OSG (17th) am I right to read that 6mm^2
T&E clipped direct is rated at 47 Amps but enclosed in conduit the
rating drops to 41 Amps?

Is the length of conduit relevant? I thought I read elsewhere in the
guide that derating where the cable runs through insulation was
dependent on how much cable ran through the insulation.

I would like to run 6mm^2 T&E to the garage. I could clip direct but
does T&E agree with sunlight? I though that conduit might protect it
from UV and impact?

The cable would be protected by a 40A RCBO in the house and terminate
in a CU in the garage. I figure that 32A for sockets plus 6A for
lights = 38A, which is below the 41A limit. But for a couple of
sockets is it worth using a ring; I could use a 16A MCB and have them
as spurs, meaning the maximum load would be 16+6=22A.

Subject to other considerations: earth impedance, voltage drop, etc.
does this sound ok so far? (No burying or overhead cables involved).

Thanks.


What sort of load do you want to run in the garage? If you want to use arc
welders or 110V transformers then you will need a 32 MCB as they often trip
16A MCBs.

Adam

  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 551
Default 6mm^2 T&E ratings

On Thu, 08 Oct 2009 06:46:31 GMT, "ARWadsworth"
wrote:

What sort of load do you want to run in the garage? If you want to use arc
welders or 110V transformers then you will need a 32 MCB as they often trip
16A MCBs.


I don't have anything that clever (yet)

There might be a freezer if I can't make room for it in the kitchen. I
know it ought to be on a separate circuit but with 40A limit that
won't be possible. That would be the only always-on load. Other than
that it would be the occasional use of tools such as lawn mower,
circular saw, etc.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default 6mm^2 T&E ratings


"Stephen" wrote in message
...
On Thu, 08 Oct 2009 06:46:31 GMT, "ARWadsworth"
wrote:

What sort of load do you want to run in the garage? If you want to use arc
welders or 110V transformers then you will need a 32 MCB as they often
trip
16A MCBs.


I don't have anything that clever (yet)

There might be a freezer if I can't make room for it in the kitchen. I
know it ought to be on a separate circuit but with 40A limit that
won't be possible. That would be the only always-on load. Other than
that it would be the occasional use of tools such as lawn mower,
circular saw, etc.


The limit is not a total sum of the MCBs in the CU. If it was then most
houses would blow the main fuse if you added up all the MCB ratings! There
is no point putting your freezer on its own supply if the incoming supply is
protected by an RCBO.

Even if you somehow maxed out your garage ring to 32A and installed 6A worth
of lighting you are still below the 41 amps maximum load that you are
allowed.

As I am a lazy sod I often wire garage sockets using a 4mm radial setup with
a 32A MCB instead of a ring.

Other options are to use 10mm T&E for the supply or use armoured cable if
you really want a bigger supply.

Adam



  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,565
Default 6mm^2 T&E ratings

On Oct 7, 2:40*pm, Stephen wrote:
Hello,

Looking at table 6D1 in the OSG (17th) am I right to read that 6mm^2
T&E clipped direct is rated at 47 Amps but enclosed in conduit the
rating drops to 41 Amps?

Is the length of conduit relevant? I thought I read elsewhere in the
guide that derating where the cable runs through insulation was
dependent on how much cable ran through the insulation.

I would like to run 6mm^2 T&E to the garage. I could clip direct but
does T&E agree with sunlight? I though that conduit might protect it
from UV and impact?


Its fine, there's loads of exterior T&E in service. But I dont think
its permitted any more.


The cable would be protected by a 40A RCBO in the house and terminate
in a CU in the garage. I figure that 32A for sockets plus 6A for
lights = 38A, which is below the 41A limit. But for a couple of
sockets is it worth using a ring; I could use a 16A MCB and have them
as spurs, meaning the maximum load would be 16+6=22A.


either's good, but rings have safety and reliability advantages.
http://wiki.diyfaq.org.uk/index.php?title=Ring_circuit

NT

Subject to other considerations: earth impedance, voltage drop, etc.
does this sound ok so far? (No burying or overhead cables involved).

Thanks.


Only thing to note is if you have a freezer in there I personally
would give it either its own RCD or no RCD, so put your RCD in the
garage CU, leaving the exterior cable not RCD protected. Why? Food
poisoning kills people, RCDless electric freezers dont to any
significant extent. Plus an unnoticed trip is just an unnecessary
waste of food worth money.


NT
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 551
Default 6mm^2 T&E ratings

On Thu, 08 Oct 2009 16:44:31 GMT, "ARWadsworth"
wrote:

The limit is not a total sum of the MCBs in the CU. If it was then most
houses would blow the main fuse if you added up all the MCB ratings!


You are quite right, I would be unlikely to be pulling 32A through the
sockets and 6A through the lights at the same time, so I do not need
to worry about the MCBs added together: diversity and all that. I
guess if someone fitted too many 500W PIRs the 6A MCB could trip but I
don't use 500W PIRs myself so that won't be a problem for us.

There is no point putting your freezer on its own supply if the incoming supply is
protected by an RCBO.


Oops. I forgot I was in the garage, but on the house CU it is a good
idea to have a separate freezer ring.

As I am a lazy sod I often wire garage sockets using a 4mm radial setup with
a 32A MCB instead of a ring.


If it was a workshop with dozens of sockets I would use a ring but it
isn't and I may just have two sockets. I wonder about using a radial.
I was going to use 2.5mm T&E and a 16A MCB, though I note your
previous comments about certain appliances wanting a 32A MCB.

Other options are to use 10mm T&E for the supply or use armoured cable if
you really want a bigger supply.


I don't think armoured is necessary as it's not overhead or
underground. I agree 10mm would give more capacity but I think I
already have some 6mm, hence I was going to use that. I am sure 40A is
more than I could need.

Thanks again.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default 6mm^2 T&E ratings


"Stephen" wrote in message
...
On Thu, 08 Oct 2009 16:44:31 GMT, "ARWadsworth"
wrote:

The limit is not a total sum of the MCBs in the CU. If it was then most
houses would blow the main fuse if you added up all the MCB ratings!


You are quite right, I would be unlikely to be pulling 32A through the
sockets and 6A through the lights at the same time, so I do not need
to worry about the MCBs added together: diversity and all that. I
guess if someone fitted too many 500W PIRs the 6A MCB could trip but I
don't use 500W PIRs myself so that won't be a problem for us.

There is no point putting your freezer on its own supply if the incoming
supply is
protected by an RCBO.


Oops. I forgot I was in the garage, but on the house CU it is a good
idea to have a separate freezer ring.

As I am a lazy sod I often wire garage sockets using a 4mm radial setup
with
a 32A MCB instead of a ring.


If it was a workshop with dozens of sockets I would use a ring but it
isn't and I may just have two sockets. I wonder about using a radial.
I was going to use 2.5mm T&E and a 16A MCB, though I note your
previous comments about certain appliances wanting a 32A MCB.

Other options are to use 10mm T&E for the supply or use armoured cable if
you really want a bigger supply.


I don't think armoured is necessary as it's not overhead or
underground. I agree 10mm would give more capacity but I think I
already have some 6mm, hence I was going to use that. I am sure 40A is
more than I could need.

Thanks again.


I do believe that the 500W lamps are now part of our history.

Adam

  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 551
Default 6mm^2 T&E ratings

On Thu, 8 Oct 2009 13:22:41 -0700 (PDT), NT
wrote:

Its fine, there's loads of exterior T&E in service. But I dont think
its permitted any more.


Sorry for the late reply, I've been painting (see other thread). Why
is it not permitted any more and what has replaced it?
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 551
Default 6mm^2 T&E ratings

On Sun, 11 Oct 2009 09:33:52 GMT, "ARWadsworth"
wrote:

I do believe that the 500W lamps are now part of our history.


Sorry for the late reply. Do you mean they are no longer sold? The
problem always was that 500w lights were available for £4.99 from
almost everywhere whereas the more appropriate (IMHO) 150w ones were
less readily available and cost more to buy; I don't think people
thought about running costs.


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default 6mm^2 T&E ratings

In article ,
Stephen writes:
On Sun, 11 Oct 2009 09:33:52 GMT, "ARWadsworth"
wrote:

I do believe that the 500W lamps are now part of our history.


They aren't banned yet, but are due to be at a future date by
the minimum efficiency rules imposed by the EU. The GE 375W
retrofit will survive longer, being more efficient by using an
infra-red reflective coating inside the tube. (There's a 225W
replacement for 300W version too.)

Sorry for the late reply. Do you mean they are no longer sold? The
problem always was that 500w lights were available for £4.99 from
almost everywhere whereas the more appropriate (IMHO) 150w ones were
less readily available and cost more to buy; I don't think people
thought about running costs.


500W lamps have been 3 for £1 in B&Q for some time. More recently,
they have been 3 for 10p. I don't suppose they're top quality, but I
haven't tried them.

B&Q also sell the GE 375W and 225W versions, which can be hard to find.
They are expensive, until you take account of the electricity cost, in
which case they're cheaper than even a free 500W lamp.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
transformer ratings ?? nitro2 Electronics Repair 8 September 28th 06 12:50 PM
PH-17D diode ratings? g. beat Electronics Repair 3 June 15th 06 01:38 AM
5 Star ratings Wally Woodturning 4 May 13th 06 05:46 AM
Hob power ratings Syke UK diy 4 March 8th 05 07:54 PM
Relay ratings Rylos Electronics 1 September 20th 04 10:44 PM


All times are GMT +1. The time now is 04:03 AM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"