Door closers and fire doors
Martin Carroll wrote:
In article , John Rumm writes tony sayer wrote: 1.19 The power supply for a smoke alarm system should be derived from the dwellinghouse's mains electricity supply. The mains supply to the smoke alarm(s) should comprise a single independent circuit at the dwellinghouse's main distribution board (consumer unit) or a single regularly used local lighting circuit. This has the advantage that the circuit is unlikely to be disconnected for any prolonged period. There should be a means of isolating power to the smoke alarms without isolating the lighting. I'm just doing 1st fix on the current job and was reading about this just the other day. I was puzzling over the "There should be a means of isolating power to the smoke alarms without isolating the lighting". I am not sure how this may be achieved? Cheers Martin I know nothing, but have a look he http://www.tlc-direct.co.uk/Products/TLCT100C.html The wording of the description suggests that it could be used in the situation you describe. (I rather hope someone else, someone who knows something, comes along in a minute and agrees or disagrees.) -- Rod Hypothyroidism is a seriously debilitating condition with an insidious onset. Although common it frequently goes undiagnosed. www.thyromind.info www.thyroiduk.org www.altsupportthyroid.org |
#42
Posted to uk.d-i-y
|
|||
|
|||
Door closers and fire doors
Martin Carroll wrote:
In article , John Rumm writes tony sayer wrote: 1.19 The power supply for a smoke alarm system should be derived from the dwellinghouse's mains electricity supply. The mains supply to the smoke alarm(s) should comprise a single independent circuit at the dwellinghouse's main distribution board (consumer unit) or a single regularly used local lighting circuit. This has the advantage that the circuit is unlikely to be disconnected for any prolonged period. There should be a means of isolating power to the smoke alarms without isolating the lighting. I'm just doing 1st fix on the current job and was reading about this just the other day. I was puzzling over the "There should be a means of isolating power to the smoke alarms without isolating the lighting". I am not sure how this may be achieved? If you take your feed to the first alarm via a DP switch close to the CU, and then feed the switch from the same breaker as the lighting circuit then you can meet the requirement. You could also do something similar from a ceiling rose position, again via a DP switch. Subsequent alarms can be powered from the first via a 3&E that also carries the interlink signal. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#43
Posted to uk.d-i-y
|
|||
|
|||
Door closers and fire doors
Rod wrote:
Martin Carroll wrote: In article , John Rumm writes tony sayer wrote: 1.19 The power supply for a smoke alarm system should be derived from the dwellinghouse's mains electricity supply. The mains supply to the smoke alarm(s) should comprise a single independent circuit at the dwellinghouse's main distribution board (consumer unit) or a single regularly used local lighting circuit. This has the advantage that the circuit is unlikely to be disconnected for any prolonged period. There should be a means of isolating power to the smoke alarms without isolating the lighting. I'm just doing 1st fix on the current job and was reading about this just the other day. I was puzzling over the "There should be a means of isolating power to the smoke alarms without isolating the lighting". I am not sure how this may be achieved? Cheers Martin I know nothing, but have a look he http://www.tlc-direct.co.uk/Products/TLCT100C.html The wording of the description suggests that it could be used in the situation you describe. (I rather hope someone else, someone who knows something, comes along in a minute and agrees or disagrees.) It would meet the requirement for isolation, however it would also end up tucked into a ceiling void somewhere and hence would not be that convenient for maintenance purposes. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#44
Posted to uk.d-i-y
|
|||
|
|||
Door closers and fire doors
In article , John Rumm
scribeth thus tony sayer wrote: In the cases where alarms are required (like a loft conversion adding a third storey) then you then must use battery backup alarms if you are powering them from a non dedicated circuit. Is that strictly the case that they MUST be battery backed on anything other then a dedicated circuit?.. That was my experience based on the building regs a the time I did my loft conversion. However I have just had a read through the current version: http://www.planningportal.gov.uk/upl..._ADB1_2006.pdf One of the commented changes is that all alarms should now have a backup power supply. The current wording is: "Power supplies 1.19 The power supply for a smoke alarm system should be derived from the dwellinghouse's mains electricity supply. The mains supply to the smoke alarm(s) should comprise a single independent circuit at the dwellinghouse's main distribution board (consumer unit) or a single regularly used local lighting circuit. This has the advantage that the circuit is unlikely to be disconnected for any prolonged period. There should be a means of isolating power to the smoke alarms without isolating the lighting. So thats an unusual bit of wiring around the CU then?.. 1.20 The electrical installation should comply with Approved Document P (Electrical safety). 1.21 Any cable suitable for domestic wiring may be used for the power supply and interconnection to smoke alarm systems. It does not need any particular fire survival properties except in large houses (BS 5839-6:2004 specifies fire resisting cables for Grade A and B systems). Any conductors used for interconnecting alarms (signalling) should be readily distinguishable from those supplying mains power, e.g. by colour coding. Now what way do they want that done and what colour?.. Note: Mains-powered smoke alarms may be interconnected using radio-links, Scary .. absolutely scary... provided that this does not reduce the lifetime or duration of any standby power supply below 72 hours. In this case, the smoke alarms may be connected to separate power circuits (see paragraph 1.19) 1.22 Other effective options exist and are described in BS 5839-1:2002 and BS 5839-6:2004. For example, the mains supply may be reduced to extra low voltage in a control unit incorporating a standby trickle-charged battery, before being distributed at that voltage to the alarms." The logic being that alarms alone are highly unlikely to trip a circuit, No I very much doubt they would, and seeing there're not earthed even.. Indeed. whereas a shared circuit might be tripped by something else and lose the alarms. Yes but that would be noticed very quickly.. Perhaps, although on a summers day you could go many hours unprotected... Most mains powered alarms also have a "mains on" LED so you can see at a glance if they are not powered. Yep so they might .. but take the case of a HIMO do you really think that say some 20 odd year old house sharers would even look?.. Under the 16th edition regs one would have likely placed alarms on a non RCD protected circuit. IMO they are probably still better powered that way when a dedicated circuit is in use, but with a suitably screened cable. Screened against what?.. Screened so as to provide earthed enclosure of the cable. i.e. to meet 17th edition requirements for the protection of cables, where you can only have a non RCD protected cable hidden in the fabric of the building if it =50mm from the surface, or run in a cable like MICC, Earthshield, SWA etc. Hummmm..... I don't think they have thought this out all that carefully... -- Tony Sayer |
#45
Posted to uk.d-i-y
|
|||
|
|||
Door closers and fire doors
tony sayer wrote:
The current wording is: "Power supplies 1.19 The power supply for a smoke alarm system should be derived from the dwellinghouse's mains electricity supply. The mains supply to the smoke alarm(s) should comprise a single independent circuit at the dwellinghouse's main distribution board (consumer unit) or a single regularly used local lighting circuit. This has the advantage that the circuit is unlikely to be disconnected for any prolonged period. There should be a means of isolating power to the smoke alarms without isolating the lighting. So thats an unusual bit of wiring around the CU then?.. Not especially - its not uncommon to provide isolating switches for all sorts of appliances of even clusters of appliances. For example you may have all your outside lights powered from the downstairs lighting circuit, but with an isolator that enables them to be independently turned off. As long as you label the switch, all should be clear. (in fact a keyswitch might be a good idea here) The intention being that you can work on the alarm circuit and not have to turn off all the lights to do so. 1.20 The electrical installation should comply with Approved Document P (Electrical safety). 1.21 Any cable suitable for domestic wiring may be used for the power supply and interconnection to smoke alarm systems. It does not need any particular fire survival properties except in large houses (BS 5839-6:2004 specifies fire resisting cables for Grade A and B systems). Any conductors used for interconnecting alarms (signalling) should be readily distinguishable from those supplying mains power, e.g. by colour coding. Now what way do they want that done and what colour?.. Personally I would treat the interlink wire as a switched live[1] - much as you would treat the return from a switch. Hence flag it with brown sleeve on a harmonised colour 3&E, or red on a old colour one. [1] Which for most alarms it probably is - although one should allow for the possibility that it may carry proprietary signalling with some brands of alarm. Note: Mains-powered smoke alarms may be interconnected using radio-links, Scary .. absolutely scary... Seems to work ok for thermostats... ;-) Screened against what?.. Screened so as to provide earthed enclosure of the cable. i.e. to meet 17th edition requirements for the protection of cables, where you can only have a non RCD protected cable hidden in the fabric of the building if it =50mm from the surface, or run in a cable like MICC, Earthshield, SWA etc. Hummmm..... I don't think they have thought this out all that carefully... Why so? -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#46
Posted to uk.d-i-y
|
|||
|
|||
Door closers and fire doors
We are doing a similar project and on certain doors have added
electromagnetic catches linked to the detectors, so that the doors can be kept open but will automatically close if the alarm is triggered. The weirdest side effect is that the first indication I had of a day- time power cut was the sound of doors slamming shut. Jonathan |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Self-Closers on Fire Doors | UK diy | |||
Concealed door closers | UK diy | |||
Door Closers | Home Repair | |||
Interior doors in-between 'featherweight' and 'fire door' quality? | UK diy | |||
Door closers on every internal door - normal? | UK diy |