I've spent most of today attempting to get one of these to drive a
wood turning lathe with a 3 ph motor and wonder if anyone here has any
experience of these devices and can help me.

The problem I found was that if I wired the convertor straight to the
motor it would work fine, but if I connected it though the lathe's
supply terminals such that the power to the motor is switched by the
lathe's on /off switches and contactor, the convertor appeared to be
unwilling to work with the low current demand of the contactor coil
(1200 ohms) - the output voltage of the convertor was low and unstable
and the coil would buzz but not pull in.

Are these convertors like switching regulators in that they require a
minimum load to actually work? I could just bypass the lathe switch
wiring but there are two safety microswitches in the circuit and the
on/off switches are a preferable size to those on the convertor, let
alone a better position when using the machine.

Thanks
Rob
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,538
Default Single phase to 3 phase convertor

robgraham coughed up some electrons that declared:

I've spent most of today attempting to get one of these to drive a
wood turning lathe with a 3 ph motor and wonder if anyone here has any
experience of these devices and can help me.

The problem I found was that if I wired the convertor straight to the
motor it would work fine, but if I connected it though the lathe's
supply terminals such that the power to the motor is switched by the
lathe's on /off switches and contactor, the convertor appeared to be
unwilling to work with the low current demand of the contactor coil
(1200 ohms) - the output voltage of the convertor was low and unstable
and the coil would buzz but not pull in.

Are these convertors like switching regulators in that they require a
minimum load to actually work? I could just bypass the lathe switch
wiring but there are two safety microswitches in the circuit and the
on/off switches are a preferable size to those on the convertor, let
alone a better position when using the machine.


Maybe. If so, could you add some dummy load to the converter's output, say 3
60-100W lamps between each phase and neutral?

Cheers

Tim


  #3   Report Post  
Posted to uk.d-i-y
cj cj is offline
external usenet poster
 
Posts: 168
Default Single phase to 3 phase convertor

Hi
Another possibility may be to drive the motor from the inverter directly ,as
you say this works .
Then swap out the contactor coil for a 240v one and use the contactor to
drive the converter.This should then allow the safety switches (usually
emergency stop )to function as they will control the contactor.
Unless of course the switch is the reversing type with 2 contactors.

HTH

CJ


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Single phase to 3 phase convertor

On Aug 19, 11:40*pm, robgraham wrote:
I've spent most of today attempting to get one of these to drive a
wood turning lathe with a 3 ph motor and wonder if anyone here has any
experience of these devices and can help me.

The problem I found was that if I wired the convertor straight to the
motor it would work fine, but if I connected it though the lathe's
supply terminals such that the power to the motor is switched by the
lathe's on /off switches and contactor, the convertor appeared to be
unwilling to work with the low current demand of the contactor coil
(1200 ohms) - the output voltage of the convertor was low and unstable
and the coil would buzz but not pull in.

Are these convertors like switching regulators in that they require a
minimum load to actually work? *I could just bypass the lathe switch
wiring but there are two safety microswitches in the circuit and the
on/off switches are a preferable size to those on the convertor, let
alone a better position when using the machine.

Thanks
Rob



why not put the invertor between the switches and the motor insead of
before the switches.


NT
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,379
Default Single phase to 3 phase convertor

It's not clear which kind of converter you mean - I'm assuming you
mean a VFD?

http://en.wikipedia.org/wiki/Variable-frequency_drive

The most important thing to understand is that the output of a VFD is
*nothing like* a normal sine wave. It's designed to drive a 3 phase
motor and that's it - there should be a (very short) direct connection
and you should not try to switch it in any way. In fact manufacturer
data may well worn you *not* to disconnect the load.

(Remember a VFD fires full voltage narrow pulses from it's output -
but varies the width or density of these pulses to produce the
equivalent drive to sine waves. *Most importantly* remember that the
output *will not show up* on a conventional voltmeter. Also remember
it will probably be necessary to change the motor being driven from
star to delta configuration)

However as VFD's are so commonly used as retrofits on machinery, the
control inputs are usually designed to hook up easily to existing
motor control.

I added an Omron VFD to a 3 phase Startrite bandsaw - the original
incoming mains 3 phase wiring was disconnected from the contactor (and
the wiring rerouted to carry incoming single phase direct to the VFD),
the output of the contactor to the motor disconnected (and rerouted
between motor and VFD) and finally using the manufacturers data the
momentary switch part *only* of the contactor is used as an "on"
signal, whilst the momentary off push button is daisy-chained with the
safety interlocks so any one of them momentarily opening is the "off"
signal to the VFD.



  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,730
Default Single phase to 3 phase convertor

On 20 Aug, 06:57, " wrote:
It's not clear which kind of converter you mean - I'm assuming you
mean a VFD?

http://en.wikipedia.org/wiki/Variable-frequency_drive

The most important thing to understand is that the output of a VFD is
*nothing like* a normal sine wave. It's designed to drive a 3 phase
motor and that's it - there should be a (very short) direct connection
and you should not try to switch it in any way. In fact manufacturer
data may well worn you *not* to disconnect the load.

(Remember a VFD fires full voltage narrow pulses from it's output -
but varies the width or density of these pulses to produce the
equivalent drive to sine waves. *Most importantly* remember that the
output *will not show up* on a conventional voltmeter. Also remember
it will probably be necessary to change the motor being driven from
star to delta configuration)

However as VFD's are so commonly used as retrofits on machinery, the
control inputs are usually designed to hook up easily to existing
motor control.

I added an Omron VFD to a 3 phase Startrite bandsaw - the original
incoming mains 3 phase wiring was disconnected from the contactor (and
the wiring rerouted to carry incoming single phase direct to the VFD),
the output of the contactor to the motor disconnected (and rerouted
between motor and VFD) and finally using the manufacturers data the
momentary switch part *only* of the contactor is used as an "on"
signal, whilst the momentary off push button is daisy-chained with the
safety interlocks so any one of them momentarily opening is the "off"
signal to the VFD.


Many thanks guys, Dom particularly. I'll now need to check the
contactor and convertor to see if they have the same capabilities as
Dom's system has.

The one thing I must admit I didn't try was to see if the contactor
coil works of single phase 240v - it is currently wired between two of
the incoming phases. I think it is reasonable for it to do so.

I didn't check the wiring of the motor but on the basis that the
current incoming cable doesn't contain a neutral, I'm assuming the
motor is star connected - anyway it ran when directly connected to the
convertor, with the speed and direction being controllable.

Many thanks
Rob
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,379
Default Single phase to 3 phase convertor


No - swapping any pair of phases on output should be fine. After all -
the motor coils are just coils.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,379
Default Single phase to 3 phase convertor

You probably want "3 wire control". My device had countless modes and
options, but came pre-configured for 3 wire control, as I guess it's
the most common requirement.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,175
Default Single phase to 3 phase convertor

On 19 Aug, 23:40, robgraham wrote:
I've spent most of today attempting to get one of these to drive a
wood turning lathe with a 3 ph motor and wonder if anyone here has any
experience of these devices and can help me.


What do you mean by "converter"? A solid state inverter? Yes, these
won't be happy driving a contactor coil alone. Your best bet is to
talk to the inverter manufacturer and rig up some sort of "integrated"
contactor switching (they'll have a standard circuit).

You can also run the contactor coils and switchgear from 240V single
phase, or 50V, or whatever else you have handy. No reason at all why
it has to be the motor supply. This assumes that the inverter is happy
if left powered up, merely with its load being switched in and out.


Personally I prefer rotary converters, recycled from big old 3 phase
motors.

http://wiki.owwm.com/Three%20Phase%2...estions.ash x





  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,730
Default Single phase to 3 phase convertor

On 20 Aug, 10:34, Andy Dingley wrote:
On 19 Aug, 23:40, robgraham wrote:

I've spent most of today attempting to get one of these to drive a
wood turning lathe with a 3 ph motor and wonder if anyone here has any
experience of these devices and can help me.


What do you mean by "converter"? *A solid state inverter? *Yes, these
won't be happy driving a contactor coil alone. Your best bet is to
talk to the inverter manufacturer and rig up some sort of "integrated"
contactor switching (they'll have a standard circuit).

You can also run the contactor coils and switchgear from 240V single
phase, or 50V, or whatever else you have handy. No reason at all why
it has to be the motor supply. This assumes that the inverter is happy
if left powered up, merely with its load being switched in and out.

Personally I prefer rotary converters, recycled from big old 3 phase
motors.

http://wiki.owwm.com/Three%20Phase%2...estions.ash x


Just a bit of feedback for anyone else. I phoned ABB, the
manufacturers of the convertor and they pointed out that trying to
operate the system in the way I was doing - ie just firing 3 phase
from the convertor into the 3 phase leads of the lathe would in all
likelihood damage the convertor. If I had got the contactor to close,
the motor would not have been ramped up by the electronics and the
instant load would have quite possibly killed the black box!

So yes I now have to look at operating the thing in Remote mode.

Thanks all

Rob
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,158
Default Single phase to 3 phase convertor


"robgraham" wrote in message
...
I've spent most of today attempting to get one of these to drive a
wood turning lathe with a 3 ph motor and wonder if anyone here has

any
experience of these devices and can help me.

The problem I found was that if I wired the convertor straight to

the
motor it would work fine, but if I connected it though the lathe's
supply terminals such that the power to the motor is switched by the
lathe's on /off switches and contactor, the convertor appeared to be
unwilling to work with the low current demand of the contactor coil
(1200 ohms) - the output voltage of the convertor was low and

unstable
and the coil would buzz but not pull in.

Are these convertors like switching regulators in that they require

a
minimum load to actually work? I could just bypass the lathe switch
wiring but there are two safety microswitches in the circuit and the
on/off switches are a preferable size to those on the convertor, let
alone a better position when using the machine.

Thanks
Rob


Most static 3 phase converters (rather than inverters) generate an
'artificial leg' that relies on the motor load to actually produce the
voltage by transformer action as it starts to spin on two phases. If
you happen to have used this phase for the control electrics then
things don't start to happen - as you note.

Rotary converters usually are simply static one with a pony motor
added to avoid the problems noted above and also allow the use of a
wider range (particularly smaller) motors without over volting one
phase (typically the small suds pump motor of a lathe)

AWEM

  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 88
Default Single phase to 3 phase convertor


"robgraham" wrote in message
...
I've spent most of today attempting to get one of these to drive a
wood turning lathe with a 3 ph motor and wonder if anyone here has any
experience of these devices and can help me.

The problem I found was that if I wired the convertor straight to the
motor it would work fine, but if I connected it though the lathe's
supply terminals such that the power to the motor is switched by the
lathe's on /off switches and contactor, the convertor appeared to be
unwilling to work with the low current demand of the contactor coil
(1200 ohms) - the output voltage of the convertor was low and unstable
and the coil would buzz but not pull in.

Are these convertors like switching regulators in that they require a
minimum load to actually work? I could just bypass the lathe switch
wiring but there are two safety microswitches in the circuit and the
on/off switches are a preferable size to those on the convertor, let
alone a better position when using the machine.


You should not interupt the convertor's output before the motor, as you are
attempting with the lathe's inbuilt controls. As you say they must see a
balanced load across the 3 phases "to work properly".

Re-wire the lathe controls as remote's for the convertor on/off - the
instruction book will tell you how.

Tim..


  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,730
Default Single phase to 3 phase convertor

On 21 Aug, 08:39, "Tim.." wrote:
"robgraham" wrote in message

...



I've spent most of today attempting to get one of these to drive a
wood turning lathe with a 3 ph motor and wonder if anyone here has any
experience of these devices and can help me.


The problem I found was that if I wired the convertor straight to the
motor it would work fine, but if I connected it though the lathe's
supply terminals such that the power to the motor is switched by the
lathe's on /off switches and contactor, the convertor appeared to be
unwilling to work with the low current demand of the contactor coil
(1200 ohms) - the output voltage of the convertor was low and unstable
and the coil would buzz but not pull in.


Are these convertors like switching regulators in that they require a
minimum load to actually work? *I could just bypass the lathe switch
wiring but there are two safety microswitches in the circuit and the
on/off switches are a preferable size to those on the convertor, let
alone a better position when using the machine.


You should not interupt the convertor's output before the motor, as you are
attempting with the lathe's inbuilt controls. As you say they must see a
balanced load across the 3 phases "to work properly".

Re-wire the lathe controls as remote's for the convertor on/off - the
instruction book will tell you how.

Tim..


Tim - I didn't actually mention a balanced load, but I can see that
that might be a requirement. In fact I'll put that as a definite
question as I did have thoughts of using one of these to vary the
speed of a single speed induction motor - is that not going to
work ?

Rob
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rotary phase converter versus trying to run a VMC straight from single phase Jeffrey Lebowski[_2_] Metalworking 0 February 21st 08 06:44 AM
Rotary phase converter versus trying to run a VMC straight from single phase Wes[_2_] Metalworking 0 February 19th 08 06:31 PM
Single Phase Backup Generator to Three Phase Mains Supply? [email protected] Home Repair 3 January 24th 08 02:30 AM
Single Phase Backup Generator to Three Phase Mains Supply? [email protected] UK diy 5 January 22nd 08 10:08 PM
profit-motive question: single phase adapter for 3-phase motor drives gwes Metalworking 8 October 5th 07 08:33 PM


All times are GMT +1. The time now is 09:01 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"