Robin 1651 (calibrated) insulation test readings, 500V-DC, L/N shorted
v E.

Final circuit consists of 8m FTE2.5, 13m SWA-PVC-2.5-2-core to
a CU with 12m of FTE2.5 & 20m FTE1.5 for power & lighting ring.
All bulbs removed, all switches on, lighting switches are 1-way.
Cable tested at source with RCD removed (ie, whole cable run).

After removing the tell-tale neon (0.32Mohm) I get an insulation
resistance of 1651Mohms which seems unusually high/good.

Is the calibration stuffed or is this reading correct?
Set to 2000Mohm, 500VDC (200Mohm & 20Mohm range all OR).

IIRC PVC typically has insulation resistance of 200Mohms/km,
and resistance halves with every doubling of distance. So the
figure is not untoward - I expected 15-25 for a 1980 final circuit.
This is fully wired up, all fittings, bulbs removed, not bare reels.

Testing the meter on 3ft of shagged (technical term) butyl cable
from 1947, crumbling & disintegrated insulation, showed infinity
as the IR even on the 1000V-DC test. That I think is complete
******** because it should carbon track - it could not pass.


Doing basic IR tests before a BCO outsources same and we
get a PIR done generally. I have to replace a surface run of
SWA elsewhere (2-core, armour exported earth) due to a nick
in the sheath showing flaking rust. Conventional wisdom is
not to export the earth even if no Class-1 devices (in garage).
However with many 24" railway drains just 3-4ft below ground
I do not feel like SDSing 4ft earth rods at random. Last person
who damaged one found knee deep water & a £7k repair bill.

Thanks.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
ESR readings Mike Electronics Repair 9 December 3rd 06 06:46 PM
Timer for 400-500V line pt Home Repair 3 April 29th 06 01:37 AM
Why do Fluke multimeter LCD displays fade? Any Fluke model immune? fancy nospam tunes Electronics Repair 6 February 2nd 05 08:09 PM
WTD: Service info for Fluke 900 test fixture John Robertson Electronics Repair 0 December 15th 04 06:58 PM


All times are GMT +1. The time now is 12:56 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"