Earth Bonding cable size
Can anyone confirm this meets wiring regs please?...
I have rewired my house, and have ran a 4mm earth cable from kitchen sink to fuse board, 4mm from cloakroom sink to fuseboard, 4mm from bathroom taps to fuseboard, and 6mm form boiler to fuseboard. I have also used 10mm from gas supply to fuseboard. Are these cable sizes ok (they are indepentantly wired, i.e. they do not loop into each other). Also is it ok to do it this way? Thanks in advance, Toby. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
In article . com,
mkkbb writes: Can anyone confirm this meets wiring regs please?... I have rewired my house, and have ran a 4mm earth cable from kitchen sink to fuse board, Not required. Actually a bad idea if the pipework is plastic. 4mm from cloakroom sink to fuseboard, Not required. Actually a bad idea if the pipework is plastic. 4mm from bathroom taps to fuseboard, Not required. You need to bond all the metal pipework and fittings and earth conductors of circuits in the bathroom together. This is normally done with 4mm cable, but you can use 2.5mm if it is protected from damage. This bonding doesn't need separately connecting back to the main earth terminal and must not be connected back to the main earth terminal instead of connecting to the earth conductors in the circuits locally. and 6mm form boiler to fuseboard. Not required (over and above the earthing in the boiler supply). However, you should earth the associated pipework unless it's plastic. I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Are these cable sizes ok (they are indepentantly wired, i.e. they do not loop into each other). Also is it ok to do it this way? Service bonding should be 10mm. Most of the other bonding you did wasn't required so there is no relevant cable size. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#3
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
In message , Andrew Gabriel
writes I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Er.. What is the thinking behind this? Assuming the gas supply to an external meter box is plastic and the consumer side is copper. Are we protecting the meter reader from shock or is there some other purpose? regards -- Tim Lamb |
#4
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
I have rewired my house, and have ran a 4mm earth cable from kitchen
sink to fuse board, Not required. Actually a bad idea if the pipework is plastic. 4mm from cloakroom sink to fuseboard, Not required. Actually a bad idea if the pipework is plastic. 4mm from bathroom taps to fuseboard, Not required. You need to bond all the metal pipework and fittings and earth conductors of circuits in the bathroom together. This is normally done with 4mm cable, but you can use 2.5mm if it is protected from damage. This bonding doesn't need separately connecting back to the main earth terminal and must not be connected back to the main earth terminal instead of connecting to the earth conductors in the circuits locally. and 6mm form boiler to fuseboard. Not required (over and above the earthing in the boiler supply). However, you should earth the associated pipework unless it's plastic. I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Are these cable sizes ok (they are indepentantly wired, i.e. they do not loop into each other). Also is it ok to do it this way? Service bonding should be 10mm. Most of the other bonding you did wasn't required so there is no relevant cable size. Andrew Gabriel [email address is not usable -- followup in the newsgroup] Thanks for your reply, however i'm a bit more confused. How should I earth the kitchen and bathroom sink taps. Bond the hot and cold together then run one cable back to fuseboard? I have copper all round the house (only plastic, the blue MDPE pipe, from street). I'm just finding it hard to visualise the actual cable runs. Toby. |
#5
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 18 Apr 2007 01:34:45 -0700, mkkbb mused:
I have rewired my house, and have ran a 4mm earth cable from kitchen sink to fuse board, Not required. Actually a bad idea if the pipework is plastic. 4mm from cloakroom sink to fuseboard, Not required. Actually a bad idea if the pipework is plastic. 4mm from bathroom taps to fuseboard, Not required. You need to bond all the metal pipework and fittings and earth conductors of circuits in the bathroom together. This is normally done with 4mm cable, but you can use 2.5mm if it is protected from damage. This bonding doesn't need separately connecting back to the main earth terminal and must not be connected back to the main earth terminal instead of connecting to the earth conductors in the circuits locally. and 6mm form boiler to fuseboard. Not required (over and above the earthing in the boiler supply). However, you should earth the associated pipework unless it's plastic. I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Are these cable sizes ok (they are indepentantly wired, i.e. they do not loop into each other). Also is it ok to do it this way? Service bonding should be 10mm. Most of the other bonding you did wasn't required so there is no relevant cable size. Andrew Gabriel [email address is not usable -- followup in the newsgroup] Thanks for your reply, however i'm a bit more confused. How should I earth the kitchen and bathroom sink taps. Kitchen taps don't need any bonding, as you've been told once already. You don't appear to understand the basics of supplementary earth bonding, it's not about earthing everything, it's about keeping various zones at the same potential by connecting local pipework together, not to connect every bit of pipe in the whole house together. Maybe buy a book, or actually look into what you're doing *before* starting a job, especially one where you can end up injuring people, by killing them. -- Regards, Stuart. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
In article , Lurch
writes On 18 Apr 2007 01:34:45 -0700, mkkbb mused: I have rewired my house, and have ran a 4mm earth cable from kitchen sink to fuse board, Not required. Actually a bad idea if the pipework is plastic. 4mm from cloakroom sink to fuseboard, Not required. Actually a bad idea if the pipework is plastic. 4mm from bathroom taps to fuseboard, Not required. You need to bond all the metal pipework and fittings and earth conductors of circuits in the bathroom together. This is normally done with 4mm cable, but you can use 2.5mm if it is protected from damage. This bonding doesn't need separately connecting back to the main earth terminal and must not be connected back to the main earth terminal instead of connecting to the earth conductors in the circuits locally. and 6mm form boiler to fuseboard. Not required (over and above the earthing in the boiler supply). However, you should earth the associated pipework unless it's plastic. I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Are these cable sizes ok (they are indepentantly wired, i.e. they do not loop into each other). Also is it ok to do it this way? Service bonding should be 10mm. Most of the other bonding you did wasn't required so there is no relevant cable size. Andrew Gabriel [email address is not usable -- followup in the newsgroup] Thanks for your reply, however i'm a bit more confused. How should I earth the kitchen and bathroom sink taps. Kitchen taps don't need any bonding, as you've been told once already. You don't appear to understand the basics of supplementary earth bonding, it's not about earthing everything, it's about keeping various zones at the same potential by connecting local pipework together, not to connect every bit of pipe in the whole house together. Maybe buy a book, or actually look into what you're doing *before* starting a job, especially one where you can end up injuring people, by killing them. You might find this interesting reading.... http://www.iee.org/Publish/WireRegs/EarthingPlasticPipes.pdf -- Tony Sayer |
#7
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On Wed, 18 Apr 2007 10:04:24 +0100, tony sayer
mused: In article , Lurch writes On 18 Apr 2007 01:34:45 -0700, mkkbb mused: I have rewired my house, and have ran a 4mm earth cable from kitchen sink to fuse board, Not required. Actually a bad idea if the pipework is plastic. 4mm from cloakroom sink to fuseboard, Not required. Actually a bad idea if the pipework is plastic. 4mm from bathroom taps to fuseboard, Not required. You need to bond all the metal pipework and fittings and earth conductors of circuits in the bathroom together. This is normally done with 4mm cable, but you can use 2.5mm if it is protected from damage. This bonding doesn't need separately connecting back to the main earth terminal and must not be connected back to the main earth terminal instead of connecting to the earth conductors in the circuits locally. and 6mm form boiler to fuseboard. Not required (over and above the earthing in the boiler supply). However, you should earth the associated pipework unless it's plastic. I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Are these cable sizes ok (they are indepentantly wired, i.e. they do not loop into each other). Also is it ok to do it this way? Service bonding should be 10mm. Most of the other bonding you did wasn't required so there is no relevant cable size. Andrew Gabriel [email address is not usable -- followup in the newsgroup] Thanks for your reply, however i'm a bit more confused. How should I earth the kitchen and bathroom sink taps. Kitchen taps don't need any bonding, as you've been told once already. You don't appear to understand the basics of supplementary earth bonding, it's not about earthing everything, it's about keeping various zones at the same potential by connecting local pipework together, not to connect every bit of pipe in the whole house together. Maybe buy a book, or actually look into what you're doing *before* starting a job, especially one where you can end up injuring people, by killing them. You might find this interesting reading.... http://www.iee.org/Publish/WireRegs/EarthingPlasticPipes.pdf Why? Which bit did I get wrong? -- Regards, Stuart. |
#8
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
In article , Lurch
writes On Wed, 18 Apr 2007 10:04:24 +0100, tony sayer mused: In article , Lurch writes On 18 Apr 2007 01:34:45 -0700, mkkbb mused: I have rewired my house, and have ran a 4mm earth cable from kitchen sink to fuse board, Not required. Actually a bad idea if the pipework is plastic. 4mm from cloakroom sink to fuseboard, Not required. Actually a bad idea if the pipework is plastic. 4mm from bathroom taps to fuseboard, Not required. You need to bond all the metal pipework and fittings and earth conductors of circuits in the bathroom together. This is normally done with 4mm cable, but you can use 2.5mm if it is protected from damage. This bonding doesn't need separately connecting back to the main earth terminal and must not be connected back to the main earth terminal instead of connecting to the earth conductors in the circuits locally. and 6mm form boiler to fuseboard. Not required (over and above the earthing in the boiler supply). However, you should earth the associated pipework unless it's plastic. I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Are these cable sizes ok (they are indepentantly wired, i.e. they do not loop into each other). Also is it ok to do it this way? Service bonding should be 10mm. Most of the other bonding you did wasn't required so there is no relevant cable size. Andrew Gabriel [email address is not usable -- followup in the newsgroup] Thanks for your reply, however i'm a bit more confused. How should I earth the kitchen and bathroom sink taps. Kitchen taps don't need any bonding, as you've been told once already. You don't appear to understand the basics of supplementary earth bonding, it's not about earthing everything, it's about keeping various zones at the same potential by connecting local pipework together, not to connect every bit of pipe in the whole house together. Maybe buy a book, or actually look into what you're doing *before* starting a job, especially one where you can end up injuring people, by killing them. You might find this interesting reading.... http://www.iee.org/Publish/WireRegs/EarthingPlasticPipes.pdf Why? Which bit did I get wrong? No suggestion of getting anything wrong ..just given for general advice and reading!...... -- Tony Sayer |
#9
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 17 Apr, 19:48, (Andrew Gabriel) wrote:
In article . com, mkkbb writes: Can anyone confirm this meets wiring regs please?... snip I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Clarification here might help the OP (& me too). Oil supply pipe(s) coming into the house are usually 10mm outside diameter. Standard bonding clamps with the proper regulation stamped tag do not fit pipes 15mm dia very well & always appear to me to present some danger that a really tight screwing on could damage an oil pipe. What is the correct clamp to use for 10mm oil pipe? Perhaps a pointer into the TLC catalog would help. |
#10
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 18 Apr 2007 01:34:45 -0700 someone who may be mkkbb
wrote this:- Thanks for your reply, however i'm a bit more confused. How should I earth the kitchen and bathroom sink taps. Bond the hot and cold together then run one cable back to fuseboard? I have copper all round the house (only plastic, the blue MDPE pipe, from street). I'm just finding it hard to visualise the actual cable runs. To add to what the others have said. Copper pipe generally conducts electricity just as well, if not better, than copper cable, as it has a similar, or larger, cross sectional area compared to copper cable. If there is reliable metal to metal contact along the length of a metal pipe then running a bit of copper covered in green and yellow plastic alongside it adds almost nothing to electrical safety. Of far more importance is to bridge plastic inserts. For example a plastic water tank may mean some pipes are not earthed properly. This is easily solved by a few clamps and a short length of earth cable. In rooms containing a bath and shower the aim is to ensure that all pipes and metalwork that may introduce a potential into the room are at the same potential. It doesn't particularly matter what this potential is, so long as there is not a difference between the potential of different pipes. That is what supplementary bonding is for. This is explained well in the usual books on the subject, which may be borrowed from your local library before starting to do some work. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54 |
#11
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On Wed, 18 Apr 2007 11:18:29 +0100, tony sayer
mused: You might find this interesting reading.... http://www.iee.org/Publish/WireRegs/...asticPipes.pdf Why? Which bit did I get wrong? No suggestion of getting anything wrong ..just given for general advice and reading!...... Right, it's just that as you replied to my post I assumed you were telling me I should read the guide. -- Regards, Stuart. |
#12
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 18 Apr 2007 05:49:39 -0700, jim mused:
On 17 Apr, 19:48, (Andrew Gabriel) wrote: In article . com, mkkbb writes: Can anyone confirm this meets wiring regs please?... snip I have also used 10mm from gas supply to fuseboard. That's good. You need to do this with all metalic services into the house (e.g. water, oil) too. Clarification here might help the OP (& me too). Oil supply pipe(s) coming into the house are usually 10mm outside diameter. Standard bonding clamps with the proper regulation stamped tag do not fit pipes 15mm dia very well & always appear to me to present some danger that a really tight screwing on could damage an oil pipe. What is the correct clamp to use for 10mm oil pipe? Perhaps a pointer into the TLC catalog would help. Although I've never looked into small pipe clamp sizes I have found that the cheap clamps are useless on most pipes. I tend to stick to the Tenby clamps as you don't have to tighten the screw up with a huge amount of force to tighten the strap up as you do with the cheap ones. -- Regards, Stuart. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On Wed, 18 Apr 2007 15:32:55 UTC, Lurch
wrote: Although I've never looked into small pipe clamp sizes I have found that the cheap clamps are useless on most pipes. I tend to stick to the Tenby clamps as you don't have to tighten the screw up with a huge amount of force to tighten the strap up as you do with the cheap ones. One thing not mentioned in terms of bonding is the bonding of the three pipes at the boiler. We had to do that with ours, and I guess it's a general requirement. -- The information contained in this post is copyright the poster, and specifically may not be published in, or used by http://www.diybanter.com |
#14
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 18 Apr 2007 15:42:35 GMT, "Bob Eager" mused:
On Wed, 18 Apr 2007 15:32:55 UTC, Lurch wrote: Although I've never looked into small pipe clamp sizes I have found that the cheap clamps are useless on most pipes. I tend to stick to the Tenby clamps as you don't have to tighten the screw up with a huge amount of force to tighten the strap up as you do with the cheap ones. One thing not mentioned in terms of bonding is the bonding of the three pipes at the boiler. We had to do that with ours, and I guess it's a general requirement. Well, I think it was, but that may have been in one of the other 56 bonding threads from this week. I will generally only bond all the pipes at a boiler if it's close to a bathroom or if the existing supplementary and\or equipotential bonding is a bit suspect. -- Regards, Stuart. |
#15
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
"Bob Eager" wrote in message ... On Wed, 18 Apr 2007 15:32:55 UTC, Lurch wrote: Although I've never looked into small pipe clamp sizes I have found that the cheap clamps are useless on most pipes. I tend to stick to the Tenby clamps as you don't have to tighten the screw up with a huge amount of force to tighten the strap up as you do with the cheap ones. One thing not mentioned in terms of bonding is the bonding of the three pipes at the boiler. We had to do that with ours, and I guess it's a general requirement. There is no such rule that I am aware of. As long as the main equipotential bonding is done correctly along with the supplementary bonding in bath/shower rooms why would the boiler need x-bonding? A lot of plumbers ask for this to be done and say CORGI ask fot it doing, but many other CORGI plumbers do not ask for this doing. Adam |
#16
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On Wed, 18 Apr 2007 16:03:44 UTC, Lurch
wrote: On 18 Apr 2007 15:42:35 GMT, "Bob Eager" mused: On Wed, 18 Apr 2007 15:32:55 UTC, Lurch wrote: Although I've never looked into small pipe clamp sizes I have found that the cheap clamps are useless on most pipes. I tend to stick to the Tenby clamps as you don't have to tighten the screw up with a huge amount of force to tighten the strap up as you do with the cheap ones. One thing not mentioned in terms of bonding is the bonding of the three pipes at the boiler. We had to do that with ours, and I guess it's a general requirement. Well, I think it was, but that may have been in one of the other 56 bonding threads from this week. I will generally only bond all the pipes at a boiler if it's close to a bathroom or if the existing supplementary and\or equipotential bonding is a bit suspect. Fair enough. Our WB 24Ri installation manual explicitly states that it should be so bonded. So I did! -- The information contained in this post is copyright the poster, and specifically may not be published in, or used by http://www.diybanter.com |
#17
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
ARWadsworth wrote:
There is no such rule that I am aware of. As long as the main equipotential bonding is done correctly along with the supplementary bonding in bath/shower rooms why would the boiler need x-bonding? A lot of plumbers ask for this to be done and say CORGI ask fot it doing, but many other CORGI plumbers do not ask for this doing. Would be worth doing if the boiler was in the bathroom... ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#18
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On Wed, 18 Apr 2007 16:09:39 GMT someone who may be "ARWadsworth"
wrote this:- There is no such rule that I am aware of. As long as the main equipotential bonding is done correctly along with the supplementary bonding in bath/shower rooms why would the boiler need x-bonding? A lot of plumbers ask for this to be done and say CORGI ask fot it doing, but many other CORGI plumbers do not ask for this doing. The flow and return pipes of heating systems are amongst those the relevant books indicate should be bonded, along with metal ductwork and a number of other things. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54 |
#19
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
In message , tony sayer
writes You might find this interesting reading.... http://www.iee.org/Publish/WireRegs/...asticPipes.pdf Yes. Clear enough. The reason I am interested is that a recent gas meter change for my Aunt was accompanied by a warning that the installation might not meet the regulations in respect of electrical bonding. A local electrician has quoted for running 10mm earth cable from the service earth to the gas supply entry point. I have only heard my wife's version of the proposed route so may easily have misunderstood but, with continuous copper gas piping to the meter and plastic beyond: underground, I could not see any benefit to carrying the earth beyond the nearest convenient bonding point (at the boiler). regards -- Tim Lamb |
#20
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
David Hansen wrote:
The flow and return pipes of heating systems are amongst those the relevant books indicate should be bonded, along with metal ductwork and a number of other things. Which "relevant books" are those? Or is this like Whitfield claiming that sinks should be bonded? BS7671 only mentions bonding of CH flow and return pipes in relation to locations containing a bath or shower [601-04-01] -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#21
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On Thu, 19 Apr 2007 09:18:58 +0100 someone who may be Tim Lamb
wrote this:- A local electrician has quoted for running 10mm earth cable from the service earth to the gas supply entry point. I have only heard my wife's version of the proposed route so may easily have misunderstood but, with continuous copper gas piping to the meter and plastic beyond: underground, I could not see any benefit to carrying the earth beyond the nearest convenient bonding point (at the boiler). Whether you, or I, can see any benefit the IEE/IET committee, in their wisdom, have decided that the bond should be as close to the point of entry as practical. The result is a green and yellow striped bit of copper running alongside a gas pipe for many metres in several houses I keep an eye on. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54 |
#22
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
In message , David Hansen
writes On Thu, 19 Apr 2007 09:18:58 +0100 someone who may be Tim Lamb wrote this:- A local electrician has quoted for running 10mm earth cable from the service earth to the gas supply entry point. I have only heard my wife's version of the proposed route so may easily have misunderstood but, with continuous copper gas piping to the meter and plastic beyond: underground, I could not see any benefit to carrying the earth beyond the nearest convenient bonding point (at the boiler). Whether you, or I, can see any benefit the IEE/IET committee, in their wisdom, have decided that the bond should be as close to the point of entry as practical. The result is a green and yellow striped bit of copper running alongside a gas pipe for many metres in several houses I keep an eye on. OK. That sounds like the last word. Thanks. regards -- Tim Lamb |
#23
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
"John Rumm" wrote in message ... ARWadsworth wrote: There is no such rule that I am aware of. As long as the main equipotential bonding is done correctly along with the supplementary bonding in bath/shower rooms why would the boiler need x-bonding? A lot of plumbers ask for this to be done and say CORGI ask fot it doing, but many other CORGI plumbers do not ask for this doing. Would be worth doing if the boiler was in the bathroom... ;-) I agree. The WB site gives this approach to the subject http://www.worcester-bosch.co.uk/index.php?fuseaction=site.viewFile&id=190261 I think that WB mix the words extraneous and exposed up. They also suggest that "earth bonding" which is a made up phrase and means nothing needs 10mm cable Adam |
#24
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
snip
Although I've never looked into small pipe clamp sizes I have found that the cheapclampsare useless on most pipes. I tend to stick to theTenbyclamps any chance of a pointer (eg into Screwfix or TLC or other picture or catalog listing) to a 'Tenby' clamp please? TIA |
#25
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 22 Apr 2007 15:41:46 -0700, jim mused:
snip Although I've never looked into small pipe clamp sizes I have found that the cheapclampsare useless on most pipes. I tend to stick to theTenbyclamps any chance of a pointer (eg into Screwfix or TLC or other picture or catalog listing) to a 'Tenby' clamp please? Can't seem to see any in any online stores. Tenby is a manufacturer, not a type. Manufacturers page - http://www.electrika.com/products/itemdetail.asp?MANU=0550&C=ABF&D=AAA&E=AAC -- Regards, Stuart. |
#26
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 22 Apr, 23:46, Lurch wrote:
On 22 Apr 2007 15:41:46 -0700, jim mused: snip Although I've never looked into small pipe clamp sizes I have found that the cheapclampsare useless on most pipes. I tend to stick to theTenbyclamps any chance of a pointer (eg into Screwfix or TLC or other picture or catalog listing) to a 'Tenby' clamp please? Can't seem to see any in any online stores.Tenbyis a manufacturer, not a type. Manufacturers page - http://www.electrika.com/products/itemdetail.asp?MANU=0550&C=ABF&D=AA... TFT but unfortunately the smallest dia pipe that Tenby's BS style clamps fit is 12mm, though they do make an 'earthing clip' to fit 10mm dia, these aren't in the standard BS style & don't have the official warning label attached. So what is the right way of main bonding to the incoming 10mm dia Cu oil pipes? Should one of the Tenby 10mm clips be used, fixng the 10mm bond wire to it with Cu washers & nuts & adding a label from a BS style clamp? BTW it isn't just matching the diameter that bothers me, it's also possible damage when a quite hard BS clamp is pressed onto a rather soft Cu pipe. |
#27
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 23 Apr, 10:15, jim wrote:
Although I've never looked into small pipe clamp sizes I have found that the cheapclampsare useless on most pipes. I tend to stick to theTenbyclamps I had no prob with the basic clamps, but I remember there was a knack to it. IIRC I think it was a case of pull the strap tight with pliers before tightening it all up. NT |
#28
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On 23 Apr 2007 02:15:10 -0700, jim mused:
On 22 Apr, 23:46, Lurch wrote: On 22 Apr 2007 15:41:46 -0700, jim mused: snip Although I've never looked into small pipe clamp sizes I have found that the cheapclampsare useless on most pipes. I tend to stick to theTenbyclamps any chance of a pointer (eg into Screwfix or TLC or other picture or catalog listing) to a 'Tenby' clamp please? Can't seem to see any in any online stores.Tenbyis a manufacturer, not a type. Manufacturers page - http://www.electrika.com/products/itemdetail.asp?MANU=0550&C=ABF&D=AA... TFT but unfortunately the smallest dia pipe that Tenby's BS style clamps fit is 12mm, Never had a problem with them on 10mm pipes, fitted loads. Some people read the instructions and dwell on it too much, just fit it. though they do make an 'earthing clip' to fit 10mm dia, these aren't in the standard BS style & don't have the official warning label attached. I think they're probably for earth rods, and would just flatten the 10mm pipe. So what is the right way of main bonding to the incoming 10mm dia Cu oil pipes? Should one of the Tenby 10mm clips be used, fixng the 10mm bond wire to it with Cu washers & nuts & adding a label from a BS style clamp? BTW it isn't just matching the diameter that bothers me, it's also possible damage when a quite hard BS clamp is pressed onto a rather soft Cu pipe. That's why I use the Tenby ones as they're quite soft, some are very rigid and deform anything below 28mm. -- Regards, Stuart. |
#29
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
|
#30
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
"Lurch" wrote in message ... On 23 Apr 2007 05:09:27 -0700, mused: On 23 Apr, 10:15, jim wrote: Although I've never looked into small pipe clamp sizes I have found that the cheapclampsare useless on most pipes. I tend to stick to theTenbyclamps I had no prob with the basic clamps, but I remember there was a knack to it. IIRC I think it was a case of pull the strap tight with pliers before tightening it all up. Probably with cheap stiff crap clamps but the Tenby ones are much better, you don't need to tug them with pliers. And the Tenby ones allow a 10mm earth cable to be clamped nicely and quickly without any of the earth cable strands falling out from behind the clamp's washer. They have a nice fitting rectangle washer not a **** awfull round one with gaps around it. Adam |
#31
Posted to uk.d-i-y
|
|||
|
|||
Earth Bonding cable size
On Mon, 23 Apr 2007 20:09:50 GMT, "ARWadsworth"
mused: "Lurch" wrote in message .. . On 23 Apr 2007 05:09:27 -0700, mused: On 23 Apr, 10:15, jim wrote: Although I've never looked into small pipe clamp sizes I have found that the cheapclampsare useless on most pipes. I tend to stick to theTenbyclamps I had no prob with the basic clamps, but I remember there was a knack to it. IIRC I think it was a case of pull the strap tight with pliers before tightening it all up. Probably with cheap stiff crap clamps but the Tenby ones are much better, you don't need to tug them with pliers. And the Tenby ones allow a 10mm earth cable to be clamped nicely and quickly without any of the earth cable strands falling out from behind the clamp's washer. They have a nice fitting rectangle washer not a **** awfull round one with gaps around it. That's the other thing that helps. -- Regards, Stuart. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Cross-bonding/earth bonding gas meter | UK diy | |||
Earth bonding on armoured mains cable | UK diy | |||
Earth Bonding | UK diy | |||
Earth bonding cable - minimum size? | UK diy | |||
Earth bonding cable? | UK diy |