I just bought a new Siemens/Landis 3 port diverter valve to replace the Switchmaster valve in our heating system that has finally expired after 20 years. I thought I would check it works OK before installing it, so after wiring it in I observed the position of the valve ( its like a rubber wedge) while changing the demand for heating and hot water. With CH demand but no HW demand the CH port is fully open. With HW demand but no CH demand the HW port is fully open. So far so good. But with CH demand AND HW demand the valve does not go to exactly mid point. I would estimate the valve goes to a position that is 60% CH and 40% HW. Is this how these vlves are set up normally or is the valve faulty? I can imagine that it would be an advantage to operate like this because the CH loop will require greater flow than the HW loop. But is this how it should be? I believe the 'mid' position is set by microswitches, are these adjustable? Thanks Mark |
#2
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
In message , LaserMark
writes Hi I just bought a new Siemens/Landis 3 port diverter valve to replace the Switchmaster valve in our heating system that has finally expired after 20 years. I thought I would check it works OK before installing it, so after wiring it in I observed the position of the valve ( its like a rubber wedge) while changing the demand for heating and hot water. With CH demand but no HW demand the CH port is fully open. With HW demand but no CH demand the HW port is fully open. So far so good. But with CH demand AND HW demand the valve does not go to exactly mid point. I would estimate the valve goes to a position that is 60% CH and 40% HW. Is this how these vlves are set up normally or is the valve faulty? I can imagine that it would be an advantage to operate like this because the CH loop will require greater flow than the HW loop. But is this how it should be? I believe the 'mid' position is set by microswitches, are these adjustable? No, the switching position of the microswitches is fixed, the switches are not adjustable and the opening position is set by a cam I can only think that you have the wrong actuator head for the valve (unless you have not diagnosed the problem correctly) -- geoff |
#3
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
On Fri, 30 Mar 2007 23:10:06 GMT, raden wrote:
In message , LaserMark writes Hi I just bought a new Siemens/Landis 3 port diverter valve to replace the Switchmaster valve in our heating system that has finally expired after 20 years. I thought I would check it works OK before installing it, so after wiring it in I observed the position of the valve ( its like a rubber wedge) while changing the demand for heating and hot water. With CH demand but no HW demand the CH port is fully open. With HW demand but no CH demand the HW port is fully open. So far so good. But with CH demand AND HW demand the valve does not go to exactly mid point. I would estimate the valve goes to a position that is 60% CH and 40% HW. Is this how these vlves are set up normally or is the valve faulty? I can imagine that it would be an advantage to operate like this because the CH loop will require greater flow than the HW loop. But is this how it should be? I believe the 'mid' position is set by microswitches, are these adjustable? No, the switching position of the microswitches is fixed, the switches are not adjustable and the opening position is set by a cam I can only think that you have the wrong actuator head for the valve (unless you have not diagnosed the problem correctly) No, this is a complete new actuator head and valve assembly straight out of the box, i'm not mixing and matching. |
#4
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
On 30 Mar, 23:51, LaserMark wrote:
Hi I just bought a new Siemens/Landis 3 port diverter valve to replace the Switchmaster valve in our heating system that has finally expired after 20 years. I thought I would check it works OK before installing it, so after wiring it in I observed the position of the valve ( its like a rubber wedge) while changing the demand for heating and hot water. With CH demand but no HW demand the CH port is fully open. With HW demand but no CH demand the HW port is fully open. So far so good. But with CH demand AND HW demand the valve does not go to exactly mid point. I would estimate the valve goes to a position that is 60% CH and 40% HW. Is this how these vlves are set up normally or is the valve faulty? Should not be a problem - it means the heating circuit will have a bigger share of the available flow from the pump. I can imagine that it would be an advantage to operate like this because the CH loop will require greater flow than the HW loop. But is this how it should be? I believe the 'mid' position is set by microswitches, are these adjustable? No |
#5
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
In an earlier contribution to this discussion,
LaserMark wrote: Hi I just bought a new Siemens/Landis 3 port diverter valve to replace the Switchmaster valve in our heating system that has finally expired after 20 years. I thought I would check it works OK before installing it, so after wiring it in I observed the position of the valve ( its like a rubber wedge) while changing the demand for heating and hot water. With CH demand but no HW demand the CH port is fully open. With HW demand but no CH demand the HW port is fully open. So far so good. But with CH demand AND HW demand the valve does not go to exactly mid point. I would estimate the valve goes to a position that is 60% CH and 40% HW. Is this how these vlves are set up normally or is the valve faulty? I can imagine that it would be an advantage to operate like this because the CH loop will require greater flow than the HW loop. But is this how it should be? I believe the 'mid' position is set by microswitches, are these adjustable? Thanks Mark All the valves I've seen move through 90 degrees from HW to CH - with the mid-position being at 45 degrees. Sounds like someone has designed an 'improvement' into yours which gives a bit more flow to the CH than to the HW when both are demanded at the same time. I doubt whether it's a fault - it actually sounds like quite a good idea. Did it come with a leaflet which describes its operation? If so, what does *that* say? -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#6
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
On Sat, 31 Mar 2007 13:51:11 +0100, "Roger Mills"
wrote: In an earlier contribution to this discussion, LaserMark wrote: Hi I just bought a new Siemens/Landis 3 port diverter valve to replace the Switchmaster valve in our heating system that has finally expired after 20 years. I thought I would check it works OK before installing it, so after wiring it in I observed the position of the valve ( its like a rubber wedge) while changing the demand for heating and hot water. With CH demand but no HW demand the CH port is fully open. With HW demand but no CH demand the HW port is fully open. So far so good. But with CH demand AND HW demand the valve does not go to exactly mid point. I would estimate the valve goes to a position that is 60% CH and 40% HW. Is this how these vlves are set up normally or is the valve faulty? I can imagine that it would be an advantage to operate like this because the CH loop will require greater flow than the HW loop. But is this how it should be? I believe the 'mid' position is set by microswitches, are these adjustable? Thanks Mark All the valves I've seen move through 90 degrees from HW to CH - with the mid-position being at 45 degrees. Sounds like someone has designed an 'improvement' into yours which gives a bit more flow to the CH than to the HW when both are demanded at the same time. I doubt whether it's a fault - it actually sounds like quite a good idea. Did it come with a leaflet which describes its operation? If so, what does *that* say? Unfortunately the instruction leaflet is rather vague and just has the wiring diagram and port positions. Can't find it on the web either the box says Landis & Staefa but the valve itself is branded Siemens. Model no appears to be MA-V322C. Think I'll just give it a try, should soon be apparent if the HW is starved of flow. |
#7
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
On Sat, 31 Mar 2007 07:59:14 +0100, LaserMark wrote:
No, this is a complete new actuator head and valve assembly straight out of the box, i'm not mixing and matching. I suppose you have rewired the system from the Switchmaster non-spring-return wiring to the standard Y-plan? http://wiki.diyfaq.org.uk/index.php?...torised_Valves |
#8
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
On Sat, 31 Mar 2007 14:59:59 GMT, John Stumbles
wrote: On Sat, 31 Mar 2007 07:59:14 +0100, LaserMark wrote: No, this is a complete new actuator head and valve assembly straight out of the box, i'm not mixing and matching. I suppose you have rewired the system from the Switchmaster non-spring-return wiring to the standard Y-plan? http://wiki.diyfaq.org.uk/index.php?...torised_Valves Yes I've rewired it as per the conversion table in the faq. As I say, it appears to function correctly but for the fact that the mid position isn't in fact mid position. Of course whether the position it takes up would give equal flow remains to be seen? |
#9
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
On Sat, 31 Mar 2007 15:32:52 +0100, in uk.d-i-y LaserMark
wrote: On Sat, 31 Mar 2007 13:51:11 +0100, "Roger Mills" wrote: In an earlier contribution to this discussion, LaserMark wrote: Hi I just bought a new Siemens/Landis 3 port diverter valve to replace the Switchmaster valve in our heating system that has finally expired after 20 years. I thought I would check it works OK before installing it, so after wiring it in I observed the position of the valve ( its like a rubber wedge) while changing the demand for heating and hot water. With CH demand but no HW demand the CH port is fully open. With HW demand but no CH demand the HW port is fully open. So far so good. But with CH demand AND HW demand the valve does not go to exactly mid point. I would estimate the valve goes to a position that is 60% CH and 40% HW. Is this how these vlves are set up normally or is the valve faulty? I can imagine that it would be an advantage to operate like this because the CH loop will require greater flow than the HW loop. But is this how it should be? I believe the 'mid' position is set by microswitches, are these adjustable? Thanks Mark All the valves I've seen move through 90 degrees from HW to CH - with the mid-position being at 45 degrees. Sounds like someone has designed an 'improvement' into yours which gives a bit more flow to the CH than to the HW when both are demanded at the same time. I doubt whether it's a fault - it actually sounds like quite a good idea. Did it come with a leaflet which describes its operation? If so, what does *that* say? Unfortunately the instruction leaflet is rather vague and just has the wiring diagram and port positions. Can't find it on the web either the box says Landis & Staefa but the valve itself is branded Siemens. Model no appears to be MA-V322C. Think I'll just give it a try, should soon be apparent if the HW is starved of flow. Landis & Staefa is now part of Siemens Building Technologies, and not too easy to find. There is what might be a similar model to yours here; CMV… 22 and 28mm 3-port motorised valves. http://preview.tinyurl.com/383vup or long url http://www.eci.siemens.com/index.jsp...id=8599288962& and a diagram showing a CMV322 here http://preview.tinyurl.com/2u35xs http://www.eci.siemens.com/index.jsp...=85 99288962& Couldnt see much data, but there are phone numbers Residential Technical Helpdesk: 0870 850 0184 General enquiries: 01784 412564 Phil |
#10
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
In an earlier contribution to this discussion,
Phil Addison wrote: Landis & Staefa is now part of Siemens Building Technologies, and not too easy to find. There is what might be a similar model to yours here; CMV. 22 and 28mm 3-port motorised valves. http://preview.tinyurl.com/383vup or long url http://www.eci.siemens.com/index.jsp...id=8599288962& and a diagram showing a CMV322 here http://preview.tinyurl.com/2u35xs http://www.eci.siemens.com/index.jsp...=85 99288962& Couldnt see much data, but there are phone numbers Residential Technical Helpdesk: 0870 850 0184 General enquiries: 01784 412564 Phil The literature refers to a 'wedge' type actuator. Anyone know what that means? -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#11
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
On Sun, 1 Apr 2007 11:32:59 +0100, in uk.d-i-y "Roger Mills"
wrote: In an earlier contribution to this discussion, Phil Addison wrote: Landis & Staefa is now part of Siemens Building Technologies, and not too easy to find. There is what might be a similar model to yours here; CMV. 22 and 28mm 3-port motorised valves. http://preview.tinyurl.com/383vup or long url http://www.eci.siemens.com/index.jsp...id=8599288962& and a diagram showing a CMV322 here http://preview.tinyurl.com/2u35xs http://www.eci.siemens.com/index.jsp...=85 99288962& Couldnt see much data, but there are phone numbers Residential Technical Helpdesk: 0870 850 0184 General enquiries: 01784 412564 Phil The literature refers to a 'wedge' type actuator. Anyone know what that means? Where did you find that literature Roger? I couldn't find anything further on that site. Mark says of his "its like a rubber wedge". Phil Phil The uk.d-i-y FAQ is at http://www.diyfaq.org.uk/ The Google uk.d-i-y archive is at http://tinyurl.com/65kwq Remove NOSPAM from address to email me |
#12
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
In message , Phil Addison
writes The literature refers to a 'wedge' type actuator. Anyone know what that means? Where did you find that literature Roger? I couldn't find anything further on that site. Mark says of his "its like a rubber wedge". There is a style of valve with a triangular (like a cheese) section This is to make the rubber perpendicular to each port as it swings from one side to the other (badly explained, but YKWIM) -- geoff |
#13
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
In an earlier contribution to this discussion,
Phil Addison wrote: On Sun, 1 Apr 2007 11:32:59 +0100, in uk.d-i-y "Roger Mills" wrote: The literature refers to a 'wedge' type actuator. Anyone know what that means? Where did you find that literature Roger? I couldn't find anything further on that site. Mark says of his "its like a rubber wedge". I was referring to the second reference which you gave. If you click on the Flow Control bit, it shows pictures of 2 and 3 port valves, with a list of features. 'Wedge type adtuator' is one of the features listed. -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#14
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
In an earlier contribution to this discussion,
raden wrote: In message , Phil Addison writes The literature refers to a 'wedge' type actuator. Anyone know what that means? Where did you find that literature Roger? I couldn't find anything further on that site. Mark says of his "its like a rubber wedge". There is a style of valve with a triangular (like a cheese) section This is to make the rubber perpendicular to each port as it swings from one side to the other (badly explained, but YKWIM) So they're referring to the paddle inside the wet bit of the valve? That's confusing 'cos, to most of us, 'actuator' means the dry bit containing the electric motor! -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#15
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
In message , Roger Mills
writes In an earlier contribution to this discussion, raden wrote: In message , Phil Addison writes The literature refers to a 'wedge' type actuator. Anyone know what that means? Where did you find that literature Roger? I couldn't find anything further on that site. Mark says of his "its like a rubber wedge". There is a style of valve with a triangular (like a cheese) section This is to make the rubber perpendicular to each port as it swings from one side to the other (badly explained, but YKWIM) So they're referring to the paddle inside the wet bit of the valve? That's confusing 'cos, to most of us, 'actuator' means the dry bit containing the electric motor! Me too ... My brain filtered out the actuator and went for the paddle, as it seemed the obvious thing being referred to, as I couldn't think of anything else either -- geoff |
#16
Posted to uk.d-i-y
|
|||
|
|||
3 port diverter valve - is this correct?
On Sun, 1 Apr 2007 18:34:42 +0100, in uk.d-i-y "Roger Mills"
wrote: In an earlier contribution to this discussion, Phil Addison wrote: On Sun, 1 Apr 2007 11:32:59 +0100, in uk.d-i-y "Roger Mills" wrote: The literature refers to a 'wedge' type actuator. Anyone know what that means? Where did you find that literature Roger? I couldn't find anything further on that site. Mark says of his "its like a rubber wedge". I was referring to the second reference which you gave. If you click on the Flow Control bit, it shows pictures of 2 and 3 port valves, with a list of features. 'Wedge type adtuator' is one of the features listed. Ahh, right. Saw those... just glanced and went looking for the detailed download - nowt there!! Siemens have seriously dumbed down the old Landis & Gyr/Staefa site. Phil |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Boiler faults - air bleed valve and diverter valve? | UK diy | |||
Valve,Butterfly valve,Globe valve,Check valve,Ball valve,Plug valve,Marine valve,Gate valve,Flow control valve | UK diy | |||
I need circuit diagram of keyboard and mouse port, USB port, DDR port, IDE port,... | Electronics Repair | |||
3-port head on 2-port valve body??? | UK diy | |||
diverter valve again | UK diy |