Hi

Turned on the Central Heating for the 1st time last night & nothing
happens, The bolier doesn't fire up and nor does the pump. I know the
boiler's fine as the hot water works ok - any suggestions as where to
start ? I was thinking the Thermostat - It clicks as you move the
temperature up past ambient could it be anything else ?

Jim
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 568
Default CH Doesn't Fire Up


Jim Burrows wrote:
Hi

Turned on the Central Heating for the 1st time last night & nothing
happens, The bolier doesn't fire up and nor does the pump. I know the
boiler's fine as the hot water works ok - any suggestions as where to
start ? I was thinking the Thermostat - It clicks as you move the
temperature up past ambient could it be anything else ?

Jim


oil or gas?

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,488
Default CH Doesn't Fire Up

In an earlier contribution to this discussion,
Jim Burrows rakkor at hotmail dot com wrote:

Hi

Turned on the Central Heating for the 1st time last night & nothing
happens, The bolier doesn't fire up and nor does the pump. I know the
boiler's fine as the hot water works ok - any suggestions as where to
start ? I was thinking the Thermostat - It clicks as you move the
temperature up past ambient could it be anything else ?

Jim


I'm assuming that it's a fully pumped system with a conventional (not combi)
boiler, which is supposed to heat both the HW and the CH, and that it has
one or more motorised valves to direct the water to the right place. Is this
correct?

If so, you have a problem either a valve or with the room thermostat which
drives it. Assuming that the HW demand is already satisfied, the 2-port
(S-Plan) or 3-port (Y-Plan) valve needs to motor to the CH position before
an internal switch closes and turns on the boiler and pump.

If a motorised valve isn't exercised for several months, it can easily seize
up - which is what has most likely happened.

Tell us a bit more about what type of system you have.
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6
Default CH Doesn't Fire Up

On Thu, 19 Oct 2006 19:07:32 +0100, "Roger Mills"
wrote:


If so, you have a problem either a valve or with the room thermostat which
drives it. Assuming that the HW demand is already satisfied, the 2-port
(S-Plan) or 3-port (Y-Plan) valve needs to motor to the CH position before
an internal switch closes and turns on the boiler and pump.

If a motorised valve isn't exercised for several months, it can easily seize
up - which is what has most likely happened.

Tell us a bit more about what type of system you have.


It's a gas fired sytem - cold water tank, hot water tank, Spartan
recovery tank ? and a boiler on the wall.

The motorised valve doesn't move when I switch on the CH - HW works
just fine

Jim
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,466
Default CH Doesn't Fire Up

In message , Jim Burrows
writes

Hi

Turned on the Central Heating for the 1st time last night & nothing
happens, The bolier doesn't fire up and nor does the pump. I know the
boiler's fine as the hot water works ok - any suggestions as where to
start ? I was thinking the Thermostat - It clicks as you move the
temperature up past ambient could it be anything else ?

Pump seized through lack of use ?

--
geoff


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 568
Default CH Doesn't Fire Up


raden wrote:
In message , Jim Burrows
writes

Hi

Turned on the Central Heating for the 1st time last night & nothing
happens, The bolier doesn't fire up and nor does the pump. I know the
boiler's fine as the hot water works ok - any suggestions as where to
start ? I was thinking the Thermostat - It clicks as you move the
temperature up past ambient could it be anything else ?

Pump seized through lack of use ?

--
geoff


Tap it to see if it'll spin up, worked for me a few times, or as told
on here open the chrome nut on the pump and turn it with a screwdriver

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,488
Default CH Doesn't Fire Up

In an earlier contribution to this discussion,
Jim Burrows rakkor at hotmail dot com wrote:

On Thu, 19 Oct 2006 19:07:32 +0100, "Roger Mills"
wrote:


If so, you have a problem either a valve or with the room thermostat
which drives it. Assuming that the HW demand is already satisfied,
the 2-port (S-Plan) or 3-port (Y-Plan) valve needs to motor to the
CH position before an internal switch closes and turns on the boiler
and pump.

If a motorised valve isn't exercised for several months, it can
easily seize up - which is what has most likely happened.

Tell us a bit more about what type of system you have.


It's a gas fired sytem - cold water tank, hot water tank, Spartan
recovery tank ? and a boiler on the wall.

Sorry, I was looking for slightly more than that. Is there just one
motorised valve? Does it have 3 water connections - an inlet coming from the
pump, and 2 outlets - one going to the HW cylinder and the other to the CH
radiators? When the HW is heating up, does the pump run?

The motorised valve doesn't move when I switch on the CH - HW works
just fine

Jim


Assuming it's a fully pumped system (still awaiting confirmation of that!)
the valve certainly *should* move when the heating is turned on if it has
previously been in HW-only mode. You should be able to remove the actuator
(the electrical bit) from the valve by undoing a couple of screws (but don't
disconnect the wires). See whether the socket in the actuator which fits
over the shaft of the 'wet' part of the valve rotates when you turn the
heating on. If it *does*, it means that the valve is seized. You should be
able to rotate the shaft of the valve to and fro by gripping it between
finger and thumb. If you can't, see if you can free it with a pair of
pliers. Once it moves freely, fix the actuator back on, and all should be
well. If you *can't* free the valve, it will have to be replaced.

If the actuator *doesn't* move when detached from the valve, it's either got
a duff motor or it's not receiving a signal from the room thermostat. You'd
need to use a mains voltmeter, or a multimeter on its 250vAC range to find
out which.
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!


  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,466
Default CH Doesn't Fire Up

In message om,
Staffbull writes

raden wrote:
In message , Jim Burrows
writes

Hi

Turned on the Central Heating for the 1st time last night & nothing
happens, The bolier doesn't fire up and nor does the pump. I know the
boiler's fine as the hot water works ok - any suggestions as where to
start ? I was thinking the Thermostat - It clicks as you move the
temperature up past ambient could it be anything else ?

Pump seized through lack of use ?

--
geoff


Tap it to see if it'll spin up, worked for me a few times, or as told
on here open the chrome nut on the pump and turn it with a screwdriver

Watered down the "whack it wi'a sledgehammer" approach then ?

--
geoff
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6
Default CH Doesn't Fire Up

Got home tonight & the place is like a sauna - looks like a couple of
cycles of the timer has freed up whatever was stuck.

Thanks for all the advice

Jim
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 568
Default CH Doesn't Fire Up


raden wrote:
In message om,
Staffbull writes

raden wrote:
In message , Jim Burrows
writes

Hi

Turned on the Central Heating for the 1st time last night & nothing
happens, The bolier doesn't fire up and nor does the pump. I know the
boiler's fine as the hot water works ok - any suggestions as where to
start ? I was thinking the Thermostat - It clicks as you move the
temperature up past ambient could it be anything else ?

Pump seized through lack of use ?

--
geoff


Tap it to see if it'll spin up, worked for me a few times, or as told
on here open the chrome nut on the pump and turn it with a screwdriver

Watered down the "whack it wi'a sledgehammer" approach then ?

--
geoff


If in doubt gi it a clout !!!



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,120
Default CH Doesn't Fire Up

The message .com
from "Staffbull" contains these words:

If in doubt gi it a clout !!!


Come on chaps, stick to the proper terminology or we'll have any old
twit thinking they can fix things. It's "Percussive maintenance" and
that's final.

--
Skipweasel
Pay no attention to that man behind the curtain.
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 568
Default CH Doesn't Fire Up


Guy King wrote:
The message .com
from "Staffbull" contains these words:

If in doubt gi it a clout !!!


Come on chaps, stick to the proper terminology or we'll have any old
twit thinking they can fix things. It's "Percussive maintenance" and
that's final.

--
Skipweasel
Pay no attention to that man behind the curtain.


Now then, thats Foreman speak, I'm most certainly a Layman :-)

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
inspection issues with fire wall jackpara Home Repair 2 September 1st 06 04:48 AM
Replacement of Back Boiler with ILFE Gas Fire from B&Q [email protected] UK diy 1 May 25th 06 11:41 PM
Fire doors+frames in rented flats Tom UK diy 7 May 11th 06 09:35 PM
Replacement Baxi coal fire ash box and 'grill' ljmeek UK diy 3 March 5th 06 08:12 PM
OT- Site Yields Early Evidence of Fire Gunner Metalworking 2 May 3rd 04 05:16 AM


All times are GMT +1. The time now is 06:19 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"