Hello, I have a problem with my Baxi Solo 3. The sysytem its self is
working correctly, the problem appears after the boiler shuts down;the
pump runs for another 10 minutes as it should, however when it is due
to switch off, the relay controlling the pump "pulses" around once per
second, this causes the pump to pulse, however the time between the
pulses slowly increases until it switches off properley after around 30
seconds.I am experienced in fault finding. I examined the PCB and
re-made a few dry joints, and did some cold checks around the pump
relay but with no success.I don't wont to buy a PCB !. All help is
appreciated.

  #2   Report Post  
Posted to uk.d-i-y
Ed Sirett
 
Posts: n/a
Default Baxi Solo 3 Boiler clicking relay after pump overrun

On Sat, 20 May 2006 06:55:52 -0700, MARTINHOG wrote:

Hello, I have a problem with my Baxi Solo 3. The sysytem its self is
working correctly, the problem appears after the boiler shuts down;the
pump runs for another 10 minutes as it should, however when it is due
to switch off, the relay controlling the pump "pulses" around once per
second, this causes the pump to pulse, however the time between the
pulses slowly increases until it switches off properley after around 30
seconds.I am experienced in fault finding. I examined the PCB and
re-made a few dry joints, and did some cold checks around the pump
relay but with no success.I don't wont to buy a PCB !. All help is
appreciated.


There is a time not to reinvent the wheel and this may be it.
If you really want to diagnose the electronics yourself and your time is
worthless then sci.electronics.repair FAQs might help.

otherwise...
This is some sort of fault with the PCB.
I expect raden who is cetltd.com may be able to help.
I believe pump (over)running problems with this PCB are 'normal'.


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
Gas Fitting Standards Docs he http://www.makewrite.demon.co.uk/GasFittingStandards

  #3   Report Post  
Posted to uk.d-i-y
raden
 
Posts: n/a
Default Baxi Solo 3 Boiler clicking relay after pump overrun

In message .uk, Ed
Sirett writes
On Sat, 20 May 2006 06:55:52 -0700, MARTINHOG wrote:

Hello, I have a problem with my Baxi Solo 3. The sysytem its self is
working correctly, the problem appears after the boiler shuts down;the
pump runs for another 10 minutes as it should, however when it is due
to switch off, the relay controlling the pump "pulses" around once per
second, this causes the pump to pulse, however the time between the
pulses slowly increases until it switches off properley after around 30
seconds.I am experienced in fault finding. I examined the PCB and
re-made a few dry joints, and did some cold checks around the pump
relay but with no success.I don't wont to buy a PCB !. All help is
appreciated.


There is a time not to reinvent the wheel and this may be it.
If you really want to diagnose the electronics yourself and your time is
worthless then sci.electronics.repair FAQs might help.

otherwise...
This is some sort of fault with the PCB.
I expect raden who is cetltd.com may be able to help.
I believe pump (over)running problems with this PCB are 'normal'.

Yes, it sounds like it has to be a pcb fault, but it's not what might be
called a common one

--
geoff
  #4   Report Post  
Posted to uk.d-i-y
MARTINHOG
 
Posts: n/a
Default Baxi Solo 3 Boiler clicking relay after pump overrun

Hi,Discovered that capacitors C12 and C13 (100uF) had failed and that
C20 was about to die. Changed all 3 and now it works a treat !.

Only do this job if you are experienced in PCB component replacement,
the PCB is at mains potential.

  #5   Report Post  
Posted to uk.d-i-y
Roger Mills
 
Posts: n/a
Default Baxi Solo 3 Boiler clicking relay after pump overrun

In an earlier contribution to this discussion,
MARTINHOG wrote:

Hi,Discovered that capacitors C12 and C13 (100uF) had failed and that
C20 was about to die. Changed all 3 and now it works a treat !.

Only do this job if you are experienced in PCB component replacement,
the PCB is at mains potential.


You surely didn't do this in situ, with the boiler/PCB powered up?!
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!




  #6   Report Post  
Posted to uk.d-i-y
raden
 
Posts: n/a
Default Baxi Solo 3 Boiler clicking relay after pump overrun

In message om,
MARTINHOG writes
Hi,Discovered that capacitors C12 and C13 (100uF) had failed and that
C20 was about to die. Changed all 3 and now it works a treat !.


Ah, but you have one of six versions of this pcb


Only do this job if you are experienced in PCB component replacement,
the PCB is at mains potential.

How else is it going to run pump, fan and gas valves ?

What a strange thing to say

--
geoff
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Non-modulating condensing boilers? Egremont UK diy 34 July 22nd 05 07:02 PM
Baxi Solo 50/4 Wm Clicking Main Valve Solenoid Jonathan Stuart UK diy 8 April 5th 05 09:47 AM
Noisy banging boiler what is the cause? Tim UK diy 8 November 3rd 04 09:36 PM
11degC across Boiler, why? Tom UK diy 54 September 24th 04 07:32 AM
Baxi Solo 2 PF 80 boiler won't fire up Dave Burleigh UK diy 3 August 11th 03 04:24 PM


All times are GMT +1. The time now is 07:05 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"