dave wrote:
I have some questions regarding domestic electrical earthing - and would appreciate some enlightnment. Yes, you seem mighty confused... http://www.diyfaq.org.uk/electrical/....html#earthing may shed some light. The house is a 50's semi. Earthing is provided by a conductor bonded to the cold water supply where it enters the house. There is an RCD fitted in the CU. Both rings and lighting circuits have mcb's. Are you sure you're not confusing the "means of earthing" with the (required) main bonding connection to the water pipe? Is there any other connection to the main earth terminal? Is your supply from an underground cable, or overhead wires? A photo of the supply intake, meter and consumer unit would help if you have a digital camera and some Web space. Q1: Is this an illegal installation because of the earthing? If the water pipe is the only means of earthing it would certainly be illegal to install now. Right now it requires urgent investigation and possibly remedial work. Q2: Is this a TTS system? TTS? There's TN-S (cable sheath earth), TN-C-S (PME) and TT (own earth rod). These are explained in the above-cited FAQ article. Several years ago we had a quote from the electricity company to rewire the house (which we should have got around to but didn't). In that quote they say (under comments), "PME Earthing". I'm not sure if that meant they intended to provide PME earthing as part of the quote - or that (for some reason) they thought we already had it. I think the former. Anyway... Perhaps. On a 50s property PME will only be possible if the service cable has been replaced, or an overhead network upgraded. Q3: Given that (afai can see) the only conductors into the house a single phase and neutral cable, how/where would they have obtained that earth from? From the neutral - that's what PME is - or from a local earth electrode (TT system). TT is a non-preferred option now and you should use it only if the supplier cannot give you PME, or TN-S. What does the cable look like, by the way? I'd like to install an earthing rod. If I do, Before you do that, let's be sure it's necessary. Q4: Is this still TTS? It would still be TT, yes, provided there was no supplier's earth connection. (The bond to the water pipe doesn't affect this, and is still necessary.) Q5: If I do install the earthing rod, can/should the bond to the cold water supply remain *as well*. Would it do any harm to leave it in place (electrically) anyway? Yes, it's a requirement - main equipotential bonding. There should be one to any gas pipe too, and any other incoming metallic services. Q6: Is it possible, and is there any virtue in, asking the electricity company to provided PME earthing to the property? (How they would get that to the house I have no idea - maybe is expensive). Yes, use PME if available. If necessary, you will need to bring the earth bonding, both main and supplementary, up to modern standards before the supplier will connect a PME earth. Q7: If PME is installed, would the installation then be TN-S? Thanks No, it would be TN-C-S. If you're going to DIY this you need to learn an awful lot more. Could I suggest using a qualified electrician? Start by getting a PIR (periodic inspection report) done, as there may well be other nasties lurking in your old wiring. -- Andy |
#2
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
Andy Wade wrote:
TTS? There's TN-S (cable sheath earth), TN-C-S (PME) and TT (own earth rod). Another decent article with helpful explanations and diagrams http://www.iee.org/Publish/WireRegs/...s_answered.pdf |
#3
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In message , Andy Wade
writes dave wrote: The house is a 50's semi. Earthing is provided by a conductor bonded to the cold water supply where it enters the house. There is an RCD fitted in the CU. Both rings and lighting circuits have mcb's. Are you sure you're not confusing the "means of earthing" with the (required) main bonding connection to the water pipe? Is there any other connection to the main earth terminal? Is your supply from an underground cable, or overhead wires? A photo of the supply intake, meter and consumer unit would help if you have a digital camera and some Web space. I don't think it's that uncommon Andy, it older properties not recently rewired. Our last house - 1938 semi, some wiring done in the 1960's ish probably, but still old rubber stuff on the lighting circuit. Our only earth was via the lead water main. -- Chris French |
#4
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
chris French wrote:
still old rubber stuff on the lighting circuit. and you're practically *boasting* about that? |
#5
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
chris French wrote:
I don't think it's that uncommon Andy, it older properties not recently rewired. Our last house - 1938 semi, some wiring done in the 1960's ish probably, but still old rubber stuff on the lighting circuit. Our only earth was via the lead water main. Yes, I've never doubted that that used to be quite common practice. OTOH confusion has often arisen between the earthing conductor and the main bonding connection to the water service in threads such as this in the past, hence I felt that the possibility should be considered and eliminated (or otherwise) at an early stage in the discussion. -- Andy |