The Boiler is some 10 years old, and has developed a intermittent fault
... Functions normally most of the time, then started to fail to supply hot water for heating system.....This seems to happen if its been on for a long period of time .. ie over night with the house stat turned down (normal would be shut down 1200 till 0730) When heating has failed -over night- Symptom's are :- House thermostat demanding heat , (Radiators fully cold) circulation pump running, Boiler 'gas' fan running No flame No green light No orange light. This situation will remain so indefinitely Found to cure problem. Turning on house hot water tap Fan remains running Can here light 'click' from control box (relay operating) Can hear (primary water circuit) diverter valve operate Ignition system fires Gas valve activates Boiler lights Green lamp lights Orange lights Hot water will run until tap closed .. normal operation . Close hot tap Diverter valve operates (can hear) Boiler remains lit / re-lights flame height rises to full then backs off - normal- Heating functions normally Till at some point the house thermostat shuts boiler down, then randomly the heating fails.to re-start when demanded by thermostat. I have changed the micro-switch on the hot water demand 'detector' this at first seemed to of cleared the problem .. however this morning ... heating had failed .. open hot tap and close .. heating operated as normal and has remained on all day .. I don't have a circuit for the flame control module, I only have the user documentation that came with the appliance..The schematic, only shows the inter connections. I can only assume its the part that the water demand sensor feeds that's developed the fault .. may be a 'dry joint' on the board as its seems only to happen after long periods of use ?.... as the hot water function is 100 p/c reliable all of the main parts of the boiler are functioning normally .. its got be a electronic fail ..has anyone got the circuit ? Sorry for the long post .. but that about describes the problem Any one seen this problem ? Tnx - Graham. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
In message .com,
Graham writes The Boiler is some 10 years old, and has developed a intermittent fault .. Functions normally most of the time, then started to fail to supply hot water for heating system.....This seems to happen if its been on for a long period of time .. ie over night with the house stat turned down (normal would be shut down 1200 till 0730) When heating has failed -over night- Symptom's are :- House thermostat demanding heat , (Radiators fully cold) circulation pump running, Boiler 'gas' fan running No flame No green light No orange light. This situation will remain so indefinitely Found to cure problem. Turning on house hot water tap Fan remains running Can here light 'click' from control box (relay operating) Can hear (primary water circuit) diverter valve operate Ignition system fires Gas valve activates Boiler lights Green lamp lights Orange lights Hot water will run until tap closed .. normal operation . Close hot tap Diverter valve operates (can hear) But is it actually moving far enough to operate the microswitches Boiler remains lit / re-lights flame height rises to full then backs off - normal- Heating functions normally Till at some point the house thermostat shuts boiler down, then randomly the heating fails.to re-start when demanded by thermostat. I have changed the micro-switch on the hot water demand 'detector' this at first seemed to of cleared the problem .. however this morning .. heating had failed .. open hot tap and close .. heating operated as normal and has remained on all day .. I don't have a circuit for the flame control module, Why should it be the flame sup cct ? - I thought it worked in CH mode It could be the thermostatic ctrl board I only have the user documentation that came with the appliance..The schematic, only shows the inter connections. I can only assume its the part that the water demand sensor feeds that's developed the fault .. may be a 'dry joint' on the board as its seems only to happen after long periods of use ?.... as the hot water function is 100 p/c reliable all of the main parts of the boiler are functioning normally .. its got be a electronic fail ..has anyone got the circuit ? Sorry for the long post .. but that about describes the problem Any one seen this problem ? Tnx - Graham. -- geoff |
#3
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
Ok well i checked the micro switch opreation .. and it functions fine
with low/medium hot water flow ..hot water supply is fine - 100 p/c ... flame control module, well i mean the cct for the whole control box - there are a few boards in there .. it must be something that the direct hot water over-rides as once you have run the hot water .. dam thing works fine again .. also a slight tap on the box has the same affect .heating come back on .. hence i think its a joint on one of the boards ... but which one .. when it clears .. you can here the relay 'click' in the control box prior to the gas opeing .. so what drives the relay ? Tnx - G . |
#4
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
In message .com,
Graham writes Ok well i checked the micro switch opreation .. and it functions fine with low/medium hot water flow ..hot water supply is fine - 100 p/c ... flame control module, well i mean the cct for the whole control box - there are a few boards in there .. it must be something that the direct hot water over-rides as once you have run the hot water .. dam thing works fine again .. also a slight tap on the box has the same affect .heating come back on . hence i think its a joint on one of the boards ... but which one .. when it clears .. you can here the relay 'click' in the control box prior to the gas opeing .. so what drives the relay ? Top board - fl sup board bottom board - fan ctrl board neither are interested in what mode it's in it's either the motherboard or the thermostatic board - the middle one .... if that is indeed the problem -- geoff |
#5
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
On Sun, 12 Mar 2006 09:02:25 -0800, Graham wrote:
The Boiler is some 10 years old, and has developed a intermittent fault .. Functions normally most of the time, then started to fail to supply hot water for heating system.....This seems to happen if its been on for a long period of time .. ie over night with the house stat turned down (normal would be shut down 1200 till 0730) When heating has failed -over night- Symptom's are :- House thermostat demanding heat , (Radiators fully cold) circulation pump running, Boiler 'gas' fan running No flame No green light No orange light. This situation will remain so indefinitely Found to cure problem. Turning on house hot water tap Fan remains running Can here light 'click' from control box (relay operating) Can hear (primary water circuit) diverter valve operate Ignition system fires Gas valve activates Boiler lights Green lamp lights Orange lights Hot water will run until tap closed .. normal operation . Close hot tap Diverter valve operates (can hear) Boiler remains lit / re-lights flame height rises to full then backs off - normal- Heating functions normally Till at some point the house thermostat shuts boiler down, then randomly the heating fails.to re-start when demanded by thermostat. I have changed the micro-switch on the hot water demand 'detector' this at first seemed to of cleared the problem .. however this morning .. heating had failed .. open hot tap and close .. heating operated as normal and has remained on all day .. I don't have a circuit for the flame control module, I only have the user documentation that came with the appliance..The schematic, only shows the inter connections. I can only assume its the part that the water demand sensor feeds that's developed the fault .. may be a 'dry joint' on the board as its seems only to happen after long periods of use ?.... as the hot water function is 100 p/c reliable all of the main parts of the boiler are functioning normally .. its got be a electronic fail ..has anyone got the circuit ? Sorry for the long post .. but that about describes the problem Any one seen this problem ? This seems like it's the diverter valve or the servo valve or diverter valve micro switches. When the CH demand is applied the pump moves the diverter valve from neutral to the left to going to CH mode. When the diverter valve arrives at the full left position one or two micro switches are made to initiate ignition. IME a good many of the problems with the boiler (which is a generally very reliable unit) are with the water flow detector and/or servo valve assembly. This is the gadget at the low front middle on the boiler. The piston from the water flow diaphragm get sticky at the beginning or end of its travel. as it works the servo valve and DHW microswitch. However YMMV. This problem is marginal/intermittent and exercising the valve gear by turning on a tap temporarily clears the problem. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at http://www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html |
#6
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
In message .uk, Ed
Sirett writes On Sun, 12 Mar 2006 09:02:25 -0800, Graham wrote: I don't have a circuit for the flame control module, I only have the user documentation that came with the appliance..The schematic, only shows the inter connections. I can only assume its the part that the water demand sensor feeds that's developed the fault .. may be a 'dry joint' on the board as its seems only to happen after long periods of use ?.... as the hot water function is 100 p/c reliable all of the main parts of the boiler are functioning normally .. its got be a electronic fail ..has anyone got the circuit ? Sorry for the long post .. but that about describes the problem Any one seen this problem ? This seems like it's the diverter valve or the servo valve or diverter valve micro switches. That's what I said in the first place -- geoff |
#7
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
......, this mean ive changed the wrong micro switch ... ? the one i
suspected was on the back of the hot water flow sensor .. for want of a better cescription ..ther is only 1 microw switch on this item driven by a rotating cam, that has a return spring .. are the other 2 switches on the valve assembly directly over that one ... ? seem to be locked with locking wire .. Tnx G. |
#8
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
Just had a look at the boiler .. can the swiches be changed on that
unit .. looks like a sealed assembly .. need to change the whole thing ? Tnx for your help Graham . |
#9
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
In message .com,
Graham writes ....., this mean ive changed the wrong micro switch ... ? the one i suspected was on the back of the hot water flow sensor .. for want of a better cescription ..ther is only 1 microw switch on this item driven by a rotating cam, that has a return spring .. are the other 2 switches on the valve assembly directly over that one .. ? seem to be locked with locking wire .. The diverter valve has two microswitches on top - as the shaft moves up, one changes from NC to NO, the other from NO to NC You need to make sure that the they're changing over properly -- geoff |
#10
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
where is this located in the boiler ... i dont think im looking a the
right assembly .. the only thing i can see .. looks sealed to me .. may be gas valve directly over the hot water sensor ? G .. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
In message .com,
Graham writes where is this located in the boiler ... i dont think im looking a the right assembly .. the only thing i can see .. looks sealed to me .. may be gas valve directly over the hot water sensor ? RHS near the bottom IIRC -- geoff |
#12
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
Ok finally on track .. boiler dead again this moring .. slight tap on
microswitch part of - diaphragm switch and boiler lit .. working normally again Operating hall thermostat .. can see the actuator arms moving .one had a barral on the end and the other seems to have a 1 inch tapped rod with coil spring , part of switch .. .. seems the 'far' one ie the one that had no spring . moves initially full travel then returns slightly in a slow 'damped motion' the sprung one simply moves leaving the actuation arm behind .. the question is .. there seems to be adjustment for travel .. but what is the criteria ? i assume the switches actuators are just on the edge and slightly reducing the travel clearance will solve the problem .. ? Tnx G . |
#13
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
On Mon, 13 Mar 2006 04:41:26 -0800, Graham wrote:
Ok finally on track .. boiler dead again this moring .. slight tap on microswitch part of - diaphragm switch and boiler lit .. working normally again Operating hall thermostat .. can see the actuator arms moving .one had a barral on the end and the other seems to have a 1 inch tapped rod with coil spring , part of switch .. . seems the 'far' one ie the one that had no spring . moves initially full travel then returns slightly in a slow 'damped motion' the sprung one simply moves leaving the actuation arm behind .. the question is .. there seems to be adjustment for travel .. but what is the criteria ? i assume the switches actuators are just on the edge and slightly reducing the travel clearance will solve the problem .. ? I would say that the 'cam' is not returning fully to CH position under spring pressure. When you tap it things are moved enough for correct operation. Forget the main diverter valve and its microswitches for the moment they are _probably_ working fine. The problem is that the water flow piston isn't fully letting the cam go back to the CH position under spring pressure. The part that needs overhauling is the gadget at the bottom front middle. If you dismantle the boiler (it requires a fair bit of work! you can extract the water flow diaphragm unit together with its servo valve (4x 4mm pipes to be disconnected and kept track of) and the DHW microswitch. Overhaul it - but don't open the diaphragm unit as it's clearly working. The nice things about this fault is that it only requires patience and a little silicone grease. Note that the servo valve only requires a very slight movement from the CH position to greatly reduce or even cut off the flow in the CH direction to the diverter-valve. HTH -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at http://www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html |
#14
Posted to uk.d-i-y
|
|||
|
|||
Vaillant VCW GB 242E Heating failing after long operting period 'intermittently'
Ok Ed
Well final check this moring .. same problem . boiler running .. no heat .. cheched travel of 'D H W' sensor spring had returned it fully clockwise .. rotated by hand . returned freely .. applied 'gental upwards tap' to diverter microswitch assemby .. from below .. boiler lit . heating running .. so looks like down to the right part .. but can i do anything with the valve in place .. like change the switches .. seems to be a adjustment possible .. but the actuator arm's would appeare to leave the switches .. so may be just a sticking switch ? taking the thing appart is not really a option at the moment .. may be a good clean with a spray and wd40 might help .looks a bit dusty Tnx - G .. |