Having a series of problems with a lighting circuit which has been fine for
2 years. Basically the total load according to my calcs is about 875w so "in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than 75%
lights/shower fans are running.

The circuit is wired with 1mm T&E with odd bits in 1.5mm where alterations
were done a couple of years back.

Assuming it is just a loading issue can I put a 10A trip in or is that too
much for the existing wiring?


  #2   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default 5A not enough on lighting circuit?

TonyK wrote:

Having a series of problems with a lighting circuit which has been fine for
2 years. Basically the total load according to my calcs is about 875w so "in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than 75%
lights/shower fans are running.


Does it trip when they have been running for a bit, or the instant when
you switch stuff on?

I think some tests on the circuit would be advised. Even a simple
current measurement would tell you plenty. If you have access to one, a
clamp meter placed round the live wire at the MCB in the CU would let
you see the actual current drawn with no apparent load (ought to be 0)
an then as you switch in each light.

From there you should have a good indication as to the type of fault
you are looking for, which could be a simple as a faulty MCB to a wiring
or appliance problem.

The circuit is wired with 1mm T&E with odd bits in 1.5mm where alterations
were done a couple of years back.

Assuming it is just a loading issue can I put a 10A trip in or is that too
much for the existing wiring?


It sounds like you have a definite problem that needs investigating and
fixing. IMO uprating the protection device is *not* the way to go (even
if the cable can nominally take it in ideal conditions).



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Posted to uk.d-i-y
TonyK
 
Posts: n/a
Default 5A not enough on lighting circuit?


"John Rumm" wrote in message
...
TonyK wrote:

Having a series of problems with a lighting circuit which has been fine

for
2 years. Basically the total load according to my calcs is about 875w so

"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than

75%
lights/shower fans are running.


Does it trip when they have been running for a bit, or the instant when
you switch stuff on?


It can run quite happily for anything up to 30 mins before it trips, it
seems almost random.

I think some tests on the circuit would be advised. Even a simple
current measurement would tell you plenty. If you have access to one, a
clamp meter placed round the live wire at the MCB in the CU would let
you see the actual current drawn with no apparent load (ought to be 0)
an then as you switch in each light.

From there you should have a good indication as to the type of fault
you are looking for, which could be a simple as a faulty MCB to a wiring
or appliance problem.

The circuit is wired with 1mm T&E with odd bits in 1.5mm where

alterations
were done a couple of years back.

Assuming it is just a loading issue can I put a 10A trip in or is that

too
much for the existing wiring?


It sounds like you have a definite problem that needs investigating and
fixing. IMO uprating the protection device is *not* the way to go (even
if the cable can nominally take it in ideal conditions).



Second time in as many weeks I've been told I need a clamp meter. Shall add
one to Mondays shopping list!

Thanks


  #4   Report Post  
Posted to uk.d-i-y
R obbo
 
Posts: n/a
Default 5A not enough on lighting circuit?


"TonyK" wrote in message
...

"John Rumm" wrote in message
...
TonyK wrote:

Having a series of problems with a lighting circuit which has been fine

for
2 years. Basically the total load according to my calcs is about 875w
so

"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than

75%
lights/shower fans are running.


Does it trip when they have been running for a bit, or the instant when
you switch stuff on?


It can run quite happily for anything up to 30 mins before it trips, it
seems almost random.

I think some tests on the circuit would be advised. Even a simple
current measurement would tell you plenty. If you have access to one, a
clamp meter placed round the live wire at the MCB in the CU would let
you see the actual current drawn with no apparent load (ought to be 0)
an then as you switch in each light.

From there you should have a good indication as to the type of fault
you are looking for, which could be a simple as a faulty MCB to a wiring
or appliance problem.

The circuit is wired with 1mm T&E with odd bits in 1.5mm where

alterations
were done a couple of years back.

Assuming it is just a loading issue can I put a 10A trip in or is that

too
much for the existing wiring?


It sounds like you have a definite problem that needs investigating and
fixing. IMO uprating the protection device is *not* the way to go (even
if the cable can nominally take it in ideal conditions).



Second time in as many weeks I've been told I need a clamp meter. Shall
add
one to Mondays shopping list!


Loose wires in a socket or to one of the fans.
Could be the result of vibration and causing an intermittent load that trips
the breaker



  #5   Report Post  
Posted to uk.d-i-y
dennis@home
 
Posts: n/a
Default 5A not enough on lighting circuit?


"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been fine
for
2 years. Basically the total load according to my calcs is about 875w so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than 75%
lights/shower fans are running.


Does it only trip when the fan motors are running/starting?




  #6   Report Post  
Posted to uk.d-i-y
TonyK
 
Posts: n/a
Default 5A not enough on lighting circuit?


"dennis@home" wrote in message
. uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been fine
for
2 years. Basically the total load according to my calcs is about 875w so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than

75%
lights/shower fans are running.


Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors, 6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and ajoining
hallway.

You can run everything for a few minutes or a combination of rooms for half
an hour, after than it gives up.

It was perfectly fine for 2 years up until about 3 weeks ago.


  #7   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default 5A not enough on lighting circuit?

TonyK wrote:

Does it trip when they have been running for a bit, or the instant when
you switch stuff on?



It can run quite happily for anything up to 30 mins before it trips, it
seems almost random.


That would suggest a sustained overload then. Remember that a MCB will
pass current significantly above its marked value for some time.
Assuming we are talking about a 6A type B MCB, then table 3.4 of BS7671
would apply. That would indicate a sustained load of some 9A to result
in a trip in that time frame.

Second time in as many weeks I've been told I need a clamp meter. Shall add
one to Mondays shopping list!


It is not essential, but it is a quicker and safer way to make these
sorts of measurements. Some multimeters will measure AC current
(although some that do only go up to 5A or so), but, they need to be
placed in circuit to make a reading. This obviously requires
disconnecting wires and finding a safe way to connect them to the meter
(a good set of shielded probes with insulated croc clips - or failing
that a chockie block to join the circuit wire to either the probe end,
or better still a suitable shrouded banana plug).

With a clamp meter you can place it round any suitable individual
conductor[1] (i.e. you can't just clamp round a whole flex or cable
since the current flowing back through the neutral will exactly cancel
the reading you would get from the current in the live). So for example
placing it round a meter tail will give you a base reading for the whole
houses consumption at that moment without even needing to open the CU.
Assuming this is reasonably static (i.e. no big loads switching in and
out on thermostats etc) you can probably conduct useful tests with just
this.

[1] A useful trick with clamp meters to increase resolution of a reading
is to put the clamp round several turns of the wire under test - then
divide the reading by the number of turns.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #8   Report Post  
Posted to uk.d-i-y
Frank Erskine
 
Posts: n/a
Default 5A not enough on lighting circuit?

On Sat, 31 Dec 2005 17:33:46 +0000, John Rumm
wrote:

TonyK wrote:

Does it trip when they have been running for a bit, or the instant when
you switch stuff on?



It can run quite happily for anything up to 30 mins before it trips, it
seems almost random.


That would suggest a sustained overload then. Remember that a MCB will
pass current significantly above its marked value for some time.
Assuming we are talking about a 6A type B MCB, then table 3.4 of BS7671
would apply. That would indicate a sustained load of some 9A to result
in a trip in that time frame.

Second time in as many weeks I've been told I need a clamp meter. Shall add
one to Mondays shopping list!


It is not essential, but it is a quicker and safer way to make these
sorts of measurements. Some multimeters will measure AC current
(although some that do only go up to 5A or so), but, they need to be
placed in circuit to make a reading. This obviously requires
disconnecting wires and finding a safe way to connect them to the meter
(a good set of shielded probes with insulated croc clips - or failing
that a chockie block to join the circuit wire to either the probe end,
or better still a suitable shrouded banana plug).


An alternative is to connect it across the circuit's switch - with the
switch "off" the meter will be in circuit.

--
Frank Erskine
  #9   Report Post  
Posted to uk.d-i-y
ARWadsworth
 
Posts: n/a
Default 5A not enough on lighting circuit?


"TonyK" wrote in message
...

"dennis@home" wrote in message
. uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been fine
for
2 years. Basically the total load according to my calcs is about 875w
so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than

75%
lights/shower fans are running.


Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors,
6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined
shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and ajoining
hallway.

You can run everything for a few minutes or a combination of rooms for
half
an hour, after than it gives up.

It was perfectly fine for 2 years up until about 3 weeks ago.


If you have two 5 amp MCBs on the CU then swap them over to see if the MCB
is faulty.

Adam


  #10   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default 5A not enough on lighting circuit?

Frank Erskine wrote:

An alternative is to connect it across the circuit's switch - with the
switch "off" the meter will be in circuit.


Yes, good point! handy for narrowing down likely culprits if it turns
out to not be the wiring itself.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #11   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default 5A not enough on lighting circuit?

TonyK wrote:

It was perfectly fine for 2 years up until about 3 weeks ago.


What else has happened in the last two weeks? Any DIY going on that
required holes in walls? Changed any bulbs or fittings?



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #12   Report Post  
Posted to uk.d-i-y
Tim \(remove obvious\)
 
Posts: n/a
Default 5A not enough on lighting circuit?


"TonyK" wrote in message
...

"dennis@home" wrote in message
. uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been

fine
for
2 years. Basically the total load according to my calcs is about 875w

so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than

75%
lights/shower fans are running.


Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors,

6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined

shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and ajoining
hallway.


Jeuss, thats some hall way / bathroom! Are you sure you dont live in a
hotel?!

Tim..


  #13   Report Post  
Posted to uk.d-i-y
TonyK
 
Posts: n/a
Default 5A not enough on lighting circuit?


"Tim (remove obvious)" wrote in
message ...

"TonyK" wrote in message
...

"dennis@home" wrote in message
. uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been

fine
for
2 years. Basically the total load according to my calcs is about

875w
so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more

than
75%
lights/shower fans are running.

Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors,

6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined

shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and ajoining
hallway.


Jeuss, thats some hall way / bathroom! Are you sure you dont live in a
hotel?!

Tim..



Not far from the truth! A Youth Hostel. Bear in mind this circuit only
covers about 40% of one of three floors.

Now you begin to understand my problem!


  #14   Report Post  
Posted to uk.d-i-y
TonyK
 
Posts: n/a
Default 5A not enough on lighting circuit?


"John Rumm" wrote in message
...
TonyK wrote:

It was perfectly fine for 2 years up until about 3 weeks ago.


What else has happened in the last two weeks? Any DIY going on that
required holes in walls? Changed any bulbs or fittings?



AFAIK nothing has changed. :-?


  #15   Report Post  
Posted to uk.d-i-y
raden
 
Posts: n/a
Default 5A not enough on lighting circuit?

In message , TonyK
writes

"John Rumm" wrote in message
...
TonyK wrote:

It was perfectly fine for 2 years up until about 3 weeks ago.


What else has happened in the last two weeks? Any DIY going on that
required holes in walls? Changed any bulbs or fittings?



AFAIK nothing has changed. :-?


In that case upping the current rating is only going to allow whatever
has gone faulty to burn / go bang better

--
geoff


  #16   Report Post  
Posted to uk.d-i-y
TonyK
 
Posts: n/a
Default 5A not enough on lighting circuit?


"raden" wrote in message
...
In message , TonyK
writes

"John Rumm" wrote in message
...
TonyK wrote:

It was perfectly fine for 2 years up until about 3 weeks ago.

What else has happened in the last two weeks? Any DIY going on that
required holes in walls? Changed any bulbs or fittings?



AFAIK nothing has changed. :-?


In that case upping the current rating is only going to allow whatever
has gone faulty to burn / go bang better

--
geoff


Yep, I'll wait until I've got a meter and can track thr problem down.


  #17   Report Post  
Posted to uk.d-i-y
Steven Briggs
 
Posts: n/a
Default 5A not enough on lighting circuit?

In message , TonyK
writes

"dennis@home" wrote in message
.uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been fine
for
2 years. Basically the total load according to my calcs is about 875w so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than

75%
lights/shower fans are running.


Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors, 6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and ajoining
hallway.

You can run everything for a few minutes or a combination of rooms for half
an hour, after than it gives up.

It was perfectly fine for 2 years up until about 3 weeks ago.


Something may have changed, but I think you've got a lot of low power
factor loads, particularly all the 2D fittings if they're magnetic
ballasts.

Before these calculations get torn apart, I've made a guesstimate at the
typical PF of these loads. Particularly the motor loads I'm not sure of.
Anyway,
Qty x Wattage / PF = VA
4 x 58 / 0.7 = 331
3 x 20 / 0.7 = 85
6 x 35 / 0.98 = 215 (transformer efficiency rather than pf)
13 x 16 / 0.7 = 297
2 x 36 / 0.7 = 103
4 x 60 / 1 = 240 (assuming 60W strip lights?)
4 x 16 /.55 = 116

Total VA = 1387, or 5.78A.

So the circuit _may_ be on marginal overload anyway, although as pointed
out previously a typical B breaker would take that lot pretty
indefinitely.
I think some actual current measurements are in order, and check any
magnetic ballasts for signs of over heating (although you'd have smelt
them by now if they were on their death bed and cooking).


--
steve
  #18   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default 5A not enough on lighting circuit?

Steven Briggs wrote:
In message , TonyK
writes

"dennis@home" wrote in message
.uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been fine
for
2 years. Basically the total load according to my calcs is about 875w so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more than

75%
lights/shower fans are running.

Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors, 6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and ajoining
hallway.

You can run everything for a few minutes or a combination of rooms for half
an hour, after than it gives up.

It was perfectly fine for 2 years up until about 3 weeks ago.


Something may have changed, but I think you've got a lot of low power
factor loads, particularly all the 2D fittings if they're magnetic
ballasts.

Before these calculations get torn apart, I've made a guesstimate at the
typical PF of these loads. Particularly the motor loads I'm not sure of.
Anyway,
Qty x Wattage / PF = VA
4 x 58 / 0.7 = 331
3 x 20 / 0.7 = 85
6 x 35 / 0.98 = 215 (transformer efficiency rather than pf)
13 x 16 / 0.7 = 297
2 x 36 / 0.7 = 103
4 x 60 / 1 = 240 (assuming 60W strip lights?)
4 x 16 /.55 = 116

Total VA = 1387, or 5.78A.

So the circuit _may_ be on marginal overload anyway, although as pointed
out previously a typical B breaker would take that lot pretty
indefinitely.


Diversity should see that lot run indefinitely.

FWIW the halogen transformers and CFLs will have much worse pf than
that, they will only take current at v peaks. But diversity still
applies.


NT

  #19   Report Post  
Posted to uk.d-i-y
The Natural Philosopher
 
Posts: n/a
Default 5A not enough on lighting circuit?

On Sat, 31 Dec 2005 21:41:32 +0000, Steven Briggs wrote:

So the circuit _may_ be on marginal overload anyway, although as pointed
out previously a typical B breaker would take that lot pretty
indefinitely.
I think some actual current measurements are in order, and check any
magnetic ballasts for signs of over heating (although you'd have smelt
them by now if they were on their death bed and cooking).


I agree, I'd say you are close to the limit, and possibly the circuit
breaker has started to go 'sensitive'.

Given the cost, I'd go for a new one of the correct rating for the wiring,
before doing anything else.

Its cheaper than a meter.

  #20   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default 5A not enough on lighting circuit?

The Natural Philosopher wrote:

I agree, I'd say you are close to the limit, and possibly the circuit
breaker has started to go 'sensitive'.

Given the cost, I'd go for a new one of the correct rating for the wiring,
before doing anything else.

Its cheaper than a meter.


I'd make it a type C as well

NT



  #21   Report Post  
Posted to uk.d-i-y
Andy Wade
 
Posts: n/a
Default 5A not enough on lighting circuit?

Steven Briggs wrote:

Something may have changed, but I think you've got a lot of low power
factor loads, particularly all the 2D fittings if they're magnetic
ballasts.


Just what I was thinking ...

Anyway,
Qty x Wattage / PF = VA


I suspect you may have overestimated some of the PFs.

[Fans]
4 x 58 / 0.7 = 331
3 x 20 / 0.7 = 85

I'd guess 0.65, so 450 VA.

[Halogens]
6 x 35 / 0.98 = 215 (transformer efficiency rather than pf)

Efficiency would be about 95% if they're iron-cored transformers (so 220
VA), but electronic xfmrs could have a much lower PF (due to waveform
distortion), so in worst case the loading might be as high as ~400 VA.

[2Ds]
13 x 16 / 0.7 = 297

PF of these, unless corrected, is close to 0.5, so 410 VA, say.

[Linear fluorescents]
2 x 36 / 0.7 = 103

Ditto 0.55, so 130 VA.

[Shaver lights]
4 x 60 / 1 = 240 (assuming 60W strip lights?)

They might be fluorescents, but let's stick to worst-case.

CFLs
4 x 16 /.55 = 116

PF closer to 0.5, say 130 VA.

Total VA = 1387, or 5.78A.


Worst case total VA = 1760, or 7.6 A - enough to trip an old 5 A MCB (if
that's what it is), but probably not a 6 A one.

So the circuit _may_ be on marginal overload anyway, although as pointed
out previously a typical B breaker would take that lot pretty indefinitely.
I think some actual current measurements are in order, and check any
magnetic ballasts for signs of over heating (although you'd have smelt
them by now if they were on their death bed and cooking).


The circuit is certainly capable of being overloaded and should either
be spit into two, or uprated to 10 A, if the cable installation
conditions allow. As has been said, test and inspect first before,
uprating the breaker. And make sure that the clamp meter reads true RMS
amps, otherwise the results will be fairly meaningless (even for the
iron-cored loads harmonic currents will contribute significantly to the
lower power factors).

--
Andy
  #22   Report Post  
Posted to uk.d-i-y
Rumble
 
Posts: n/a
Default 5A not enough on lighting circuit?

TonyK said the following on 31/12/2005 14:39:

Assuming it is just a loading issue can I put a 10A trip in or is that too
much for the existing wiring?



BS7671 Regulation 553-03-01 (Table 55B) applies. Overcurrent protection
of lampholders (under certain circumstances) is limited to 6 Amp for
SBC and SES lampholders. This is why domestic lighting circuits are
always rated at 5/6A. Even if you don't have any light fittings with
SBC (small bayonet) or SES (small edison screw) lamps IMHO it would
still be considered bad practice to upgrade the MCB to 10A.

If it turns out that you have an overloaded circuit, you should split
the load onto two or more separate 5/6A MCBs.

HTH
  #23   Report Post  
Posted to uk.d-i-y
Stephen Dawson
 
Posts: n/a
Default 5A not enough on lighting circuit?


"TonyK" wrote in message
...

"Tim (remove obvious)" wrote in
message ...

"TonyK" wrote in message
...

"dennis@home" wrote in message
. uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been

fine
for
2 years. Basically the total load according to my calcs is about

875w
so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more

than
75%
lights/shower fans are running.

Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors,

6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined

shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and
ajoining
hallway.


Jeuss, thats some hall way / bathroom! Are you sure you dont live in a
hotel?!

Tim..



Not far from the truth! A Youth Hostel. Bear in mind this circuit only
covers about 40% of one of three floors.

Now you begin to understand my problem!



I feel that you have a duty of care to get a professional in to locate the
problem. That is unless you are a competent electrician and appropriately
insuredfor the work you will be carrying out.

Regards

Steve Dawson


  #24   Report Post  
Posted to uk.d-i-y
John
 
Posts: n/a
Default 5A not enough on lighting circuit?

In article , Stephen Dawson
writes

"TonyK" wrote in message
...

"Tim (remove obvious)" wrote in
message ...

"TonyK" wrote in message
...

"dennis@home" wrote in message
. uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has been
fine
for
2 years. Basically the total load according to my calcs is about

875w
so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more

than
75%
lights/shower fans are running.

Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors,
6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined
shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and
ajoining
hallway.

Jeuss, thats some hall way / bathroom! Are you sure you dont live in a
hotel?!

Tim..



Not far from the truth! A Youth Hostel. Bear in mind this circuit only
covers about 40% of one of three floors.

Now you begin to understand my problem!



I feel that you have a duty of care to get a professional in to locate the
problem. That is unless you are a competent electrician and appropriately
insuredfor the work you will be carrying out.

Regards

Steve Dawson


Does it trip when the "extra" switch is turned on, or just with 75%
running? Fans and extractors can have quite a switch on surge, as can
fluorescent and halogens. I would guess that it is the surge which is
the problem and Steve is right - you need an expert.
--
John Alexander,

Remove NOSPAM if replying by e-mail
  #25   Report Post  
Posted to uk.d-i-y
Steven Briggs
 
Posts: n/a
Default 5A not enough on lighting circuit?

In message , Andy Wade
writes
Steven Briggs wrote:

Something may have changed, but I think you've got a lot of low power
factor loads, particularly all the 2D fittings if they're magnetic
ballasts.


Just what I was thinking ...

Anyway,
Qty x Wattage / PF = VA


I suspect you may have overestimated some of the PFs.


Yeah, I was being generous, there's a lot of detail we don't know.

Efficiency would be about 95% if they're iron-cored transformers (so
220 VA), but electronic xfmrs could have a much lower PF (due to
waveform distortion), so in worst case the loading might be as high as
~400 VA.


FWIW, I thought electronic halogen transformers were pretty good on PF,
certainly the ones I played with a while back just rectified the mains
and chopped the power across a small toroidal ferrite transformer at HF.
No storage capacitor to bugger up the input waveform.

CFL's are crap, due to a rectifier-cap input circuit. ISTR a 20W Philips
one was PF=.515, 11W was 0.575 when I measured some (Voltech power
analyser).

Proper electronic ballasts for linear FL's should have active power
factor correction, and be pretty close to unity.

Anyway, we should have added that lot up vector wise, accounted for the
low PFs due to distortion rather than phase shift, etc, etc.
But for a "back of the envelope" calculation, we've shown that there may
be an overload problem that the original sparks toting up the bare watts
figures didn't account for.


--
steve


  #26   Report Post  
Posted to uk.d-i-y
Andrew Gabriel
 
Posts: n/a
Default 5A not enough on lighting circuit?

In article ,
Andy Wade writes:

Just what I was thinking ...

Anyway,
Qty x Wattage / PF = VA


I suspect you may have overestimated some of the PFs.


[2Ds]
13 x 16 / 0.7 = 297

PF of these, unless corrected, is close to 0.5, so 410 VA, say.


It's difficult to find specs of 2D lamps, but I suspect the tube
voltage will be around 50V, which would make the uncorrected PF
more like 0.25, which is 810 VA.

[Linear fluorescents]
2 x 36 / 0.7 = 103

Ditto 0.55, so 130 VA.


Again, tube voltage is something like 110V, which would make
uncorrected PF less than 0.5, so VA could be more like 150.

One possibility could be progressive failure of PF correction
capacitors (if the fittings ever had them), resulting in a
progressive increase in the circuit current. It's not uncommon
to find PF correction capacitors going open circuit in strings
of fluorescent luminares as they age (or more strictly, they
short out and an internal fuse opens).

--
Andrew Gabriel
  #27   Report Post  
Posted to uk.d-i-y
TonyK
 
Posts: n/a
Default 5A not enough on lighting circuit?


"Stephen Dawson" wrote in message
...

"TonyK" wrote in message
...

"Tim (remove obvious)" wrote in
message ...

"TonyK" wrote in message
...

"dennis@home" wrote in message
. uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has

been
fine
for
2 years. Basically the total load according to my calcs is about

875w
so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever more

than
75%
lights/shower fans are running.

Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower extractors,
6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined
shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and
ajoining
hallway.

Jeuss, thats some hall way / bathroom! Are you sure you dont live in a
hotel?!

Tim..



Not far from the truth! A Youth Hostel. Bear in mind this circuit only
covers about 40% of one of three floors.

Now you begin to understand my problem!



I feel that you have a duty of care to get a professional in to locate the
problem. That is unless you are a competent electrician and appropriately
insuredfor the work you will be carrying out.

Regards

Steve Dawson



Yep, from the sound of the problem it doesn't look like its a simple one. I
suspect the electricians that did all the work a few years back weren't
"competent".

It'll just have to wait until people are back at work next week.


  #28   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default 5A not enough on lighting circuit?

I feel that you have a duty of care to get a professional in to locate the
problem. That is unless you are a competent electrician and appropriately
insuredfor the work you will be carrying out.


Does it trip when the "extra" switch is turned on, or just with 75%
running? Fans and extractors can have quite a switch on surge, as can
fluorescent and halogens. I would guess that it is the surge which is
the problem and Steve is right - you need an expert.



What am I missing:
1. the circuit is loaded up to its max rating and likely beyond
2. its behaving exactly as would be expected
3. Type C breakers are known to be better suited for lighting circuits,
and would help with the switch on surge currents that are the
(non-safety) problem.

AFAICS there is no reason to believe anything is unsafely amiss, beyond
switch on surges popping the breaker.

OTOH I forget what the level of expertise of the OP is.


NT

  #29   Report Post  
Posted to uk.d-i-y
 
Posts: n/a
Default 5A not enough on lighting circuit?

Andy Wade wrote:
Steven Briggs wrote:

Something may have changed, but I think you've got a lot of low power
factor loads, particularly all the 2D fittings if they're magnetic
ballasts.


Just what I was thinking ...

Anyway,
Qty x Wattage / PF = VA


I suspect you may have overestimated some of the PFs.

[Fans]
4 x 58 / 0.7 = 331
3 x 20 / 0.7 = 85

I'd guess 0.65, so 450 VA.

[Halogens]
6 x 35 / 0.98 = 215 (transformer efficiency rather than pf)

Efficiency would be about 95% if they're iron-cored transformers (so 220
VA), but electronic xfmrs could have a much lower PF (due to waveform
distortion), so in worst case the loading might be as high as ~400 VA.

[2Ds]
13 x 16 / 0.7 = 297

PF of these, unless corrected, is close to 0.5, so 410 VA, say.

[Linear fluorescents]
2 x 36 / 0.7 = 103

Ditto 0.55, so 130 VA.

[Shaver lights]
4 x 60 / 1 = 240 (assuming 60W strip lights?)

They might be fluorescents, but let's stick to worst-case.

CFLs
4 x 16 /.55 = 116

PF closer to 0.5, say 130 VA.

Total VA = 1387, or 5.78A.


Worst case total VA = 1760, or 7.6 A - enough to trip an old 5 A MCB (if
that's what it is), but probably not a 6 A one.

So the circuit _may_ be on marginal overload anyway, although as pointed
out previously a typical B breaker would take that lot pretty indefinitely.
I think some actual current measurements are in order, and check any
magnetic ballasts for signs of over heating (although you'd have smelt
them by now if they were on their death bed and cooking).


The circuit is certainly capable of being overloaded and should either
be spit into two, or uprated to 10 A, if the cable installation
conditions allow. As has been said, test and inspect first before,
uprating the breaker. And make sure that the clamp meter reads true RMS
amps, otherwise the results will be fairly meaningless (even for the
iron-cored loads harmonic currents will contribute significantly to the
lower power factors).



While I can happily accept the numbers, I'm not so sure I'd interpret
them the same way. 7.6A of loads on a 5A circuit would not normally be
a problem, due to diversity. The problem I think is less liekly the
continuous ratings, more likely the surges, and the poor surge
tolerance of type Bs.


NT

  #32   Report Post  
Posted to uk.d-i-y
Stephen Dawson
 
Posts: n/a
Default 5A not enough on lighting circuit?


"TonyK" wrote in message
news

"Stephen Dawson" wrote in message
...

"TonyK" wrote in message
...

"Tim (remove obvious)" wrote in
message ...

"TonyK" wrote in message
...

"dennis@home" wrote in message
. uk...

"TonyK" wrote in message
...
Having a series of problems with a lighting circuit which has

been
fine
for
2 years. Basically the total load according to my calcs is about
875w
so
"in
theory" is okay on a 5A MCB. But, it keeps tripping whenever
more
than
75%
lights/shower fans are running.

Does it only trip when the fan motors are running/starting?



Not always... there are 4x58w inline fans plus 3 x shower
extractors,
6x35W
12V halogens,13x16w 2D fittings, 2x4' flourescents, 4xcombined
shaver/lamps
plus 4x "normal" 16w CFL lamps. This is spread over 6 rooms and
ajoining
hallway.

Jeuss, thats some hall way / bathroom! Are you sure you dont live in a
hotel?!

Tim..



Not far from the truth! A Youth Hostel. Bear in mind this circuit only
covers about 40% of one of three floors.

Now you begin to understand my problem!



I feel that you have a duty of care to get a professional in to locate
the
problem. That is unless you are a competent electrician and appropriately
insuredfor the work you will be carrying out.

Regards

Steve Dawson



Yep, from the sound of the problem it doesn't look like its a simple one.
I
suspect the electricians that did all the work a few years back weren't
"competent".

It'll just have to wait until people are back at work next week.



Where is your youth hostel??


  #33   Report Post  
Posted to uk.d-i-y
Andy Wade
 
Posts: n/a
Default 5A not enough on lighting circuit?

Andrew Gabriel wrote:

It's difficult to find specs of 2D lamps, but I suspect the tube
voltage will be around 50V, which would make the uncorrected PF
more like 0.25, which is 810 VA.


I'm not sure it's quite that bad. I have a Thorn Lighting data book
(early 90s vintage) which gives the following data for the 16 W 2D:

tube volts 97 V
running current 0.2 A
circuit watts 21 W
total VA 48 VA
circuit power factor 0.44 (uncorrected, lagging)
3rd harmonic current 17%

This brings into focus the fact that the sums should be based on circuit
watts (not tube watts) as the ballast losses are not negligible,
especially for these small lamps. 5 watts ballast loss for a 16 W lamp
is not exactly high efficiency.

Anyway, 13 luminaires at 48 VA each is 624 VA total, or 2.6 amps.

[Linear fluorescents]
2 x 36 / 0.7 = 103

Ditto 0.55, so 130 VA.


Again, tube voltage is something like 110V, which would make
uncorrected PF less than 0.5, so VA could be more like 150.


Same Thorn book says 103 volts (tube), 0.43 A, 47 circuit watts. If
uncorrected that would be ~100 VA each, 200 VA total (PF = 0.455).

One possibility could be progressive failure of PF correction
capacitors (if the fittings ever had them),


The 13 2Ds are very unlikely to be corrected. The default fittings
aren't, you have to select the HPF special order option (high power
factor, not highpass filter!) to get a capacitor.

progressive increase in the circuit current. It's not uncommon
to find PF correction capacitors going open circuit in strings
of fluorescent luminares as they age (or more strictly, they
short out and an internal fuse opens).


Certainly a possibility, although I think that's less common with modern
polypropylene capacitors, compared to the old impregnated paper things.

--
Andy
  #34   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default 5A not enough on lighting circuit?

Stephen Dawson wrote:

I feel that you have a duty of care to get a professional in to locate the
problem. That is unless you are a competent electrician and appropriately
insuredfor the work you will be carrying out.


I can't see any problem with the OP at least diagnosing and locating the
problem, even if he leaves fixing it to a "pro". So long as he is
confident that he will not cause harm to himself (or others) in the
process, there is plenty of advice available here from suitably skilled
people.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lighting circuit earth at 120V Martin Brook UK diy 26 October 21st 17 12:44 PM
Lighting circuit: spur to electrical socket [email protected] UK diy 17 January 18th 05 11:16 PM
Lighting circuit - loop through in switch Dan Sloane UK diy 5 November 12th 03 03:02 PM
Case of the unknown circuit David Hearn UK diy 4 November 10th 03 04:12 PM
Is it a radial or ring circuit? Paul UK diy 14 September 4th 03 04:48 PM


All times are GMT +1. The time now is 07:59 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"