Home |
Search |
Today's Posts |
|
UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
|
#1
|
|||
|
|||
Electrical problem
A mate of mine has completely rewired our house so everything in the
installation is brand new, including the split-load consumer unit. We have an upstairs ring main, downstairs ring main and a kitchen ring main, all of which are protected by the RCD, and the problem is the kitchen ring. As soon as *anything* (portable radio, halogen lamp, electric drill or whatever) is plugged into *any* socket on the kitchen ring, the RCD trips (plugging the same things into either upstairs or downstairs rings does *not* trip it). Splitting the ring at the CU and using a proper Megger (500v insulation resistance tester, not just a multimeter) to test each leg of the ring shows the following: L-N = almost infinity resistance (certainly over 1,000Mohms anyway) L-E = " " " " " " " N-E = " " " " " " " so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) TIA, Mogweed |
#2
|
|||
|
|||
Electrical problem
Mogweed wrote:
A mate of mine has completely rewired our house so everything in the installation is brand new, including the split-load consumer unit. We have an upstairs ring main, downstairs ring main and a kitchen ring main, all of which are protected by the RCD, and the problem is the kitchen ring. As soon as *anything* (portable radio, halogen lamp, electric drill or whatever) is plugged into *any* socket on the kitchen ring, the RCD trips (plugging the same things into either upstairs or downstairs rings does *not* trip it). Splitting the ring at the CU and using a proper Megger (500v insulation resistance tester, not just a multimeter) to test each leg of the ring shows the following: L-N = almost infinity resistance (certainly over 1,000Mohms anyway) L-E = " " " " " " " N-E = " " " " " " " so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) TIA, Mogweed Are you 100% sure you don't have a short? Have you been capping back the cable into chases, Screwed down floor boards? -- Sir Benjamin Middlethwaite |
#3
|
|||
|
|||
Electrical problem
"The3rd Earl Of Derby" wrote in message k... Mogweed wrote: A mate of mine has completely rewired our house so everything in the installation is brand new, including the split-load consumer unit. We have an upstairs ring main, downstairs ring main and a kitchen ring main, all of which are protected by the RCD, and the problem is the kitchen ring. As soon as *anything* (portable radio, halogen lamp, electric drill or whatever) is plugged into *any* socket on the kitchen ring, the RCD trips (plugging the same things into either upstairs or downstairs rings does *not* trip it). Splitting the ring at the CU and using a proper Megger (500v insulation resistance tester, not just a multimeter) to test each leg of the ring shows the following: L-N = almost infinity resistance (certainly over 1,000Mohms anyway) L-E = " " " " " " " N-E = " " " " " " " so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) TIA, Mogweed Are you 100% sure you don't have a short? Have you been capping back the cable into chases, Screwed down floor boards? -- Sir Benjamin Middlethwaite You have to believe your instruments so I can only go on what the megger tells me, and that says that there is no short - tried shorting the test leads and the meter swings right over to 0 ohms so the megger seems to be working OK. Cables capped - and chases plastered over ( Some floorboards screwed back down - but megger shows no shorts. Mogweed. |
#4
|
|||
|
|||
Electrical problem
Mogweed wrote:
"The3rd Earl Of Derby" wrote in message k... Mogweed wrote: A mate of mine has completely rewired our house so everything in the installation is brand new, including the split-load consumer unit. We have an upstairs ring main, downstairs ring main and a kitchen ring main, all of which are protected by the RCD, and the problem is the kitchen ring. As soon as *anything* (portable radio, halogen lamp, electric drill or whatever) is plugged into *any* socket on the kitchen ring, the RCD trips (plugging the same things into either upstairs or downstairs rings does *not* trip it). Splitting the ring at the CU and using a proper Megger (500v insulation resistance tester, not just a multimeter) to test each leg of the ring shows the following: L-N = almost infinity resistance (certainly over 1,000Mohms anyway) L-E = " " " " " " " N-E = " " " " " " " so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) TIA, Mogweed Are you 100% sure you don't have a short? Have you been capping back the cable into chases, Screwed down floor boards? -- Sir Benjamin Middlethwaite You have to believe your instruments so I can only go on what the megger tells me, and that says that there is no short - tried shorting the test leads and the meter swings right over to 0 ohms so the megger seems to be working OK. Cables capped - and chases plastered over ( Some floorboards screwed back down - but megger shows no shorts. Mogweed. Take the kitchen strap out of the CU attach a battery&bulb L to +, - to bulb and bulb to N and see if the bulb lights? do this on the E to L and E to N. If it lights you have a short if not then start looking at CU -- Sir Benjamin Middlethwaite |
#5
|
|||
|
|||
Electrical problem
"The3rd Earl Of Derby" wrote in message k... Mogweed wrote: "The3rd Earl Of Derby" wrote in message k... Mogweed wrote: Are you 100% sure you don't have a short? Have you been capping back the cable into chases, Screwed down floor boards? -- Sir Benjamin Middlethwaite You have to believe your instruments so I can only go on what the megger tells me, and that says that there is no short - tried shorting the test leads and the meter swings right over to 0 ohms so the megger seems to be working OK. Cables capped - and chases plastered over ( Some floorboards screwed back down - but megger shows no shorts. Mogweed. Take the kitchen strap out of the CU attach a battery&bulb L to +, - to bulb and bulb to N and see if the bulb lights? do this on the E to L and E to N. If it lights you have a short if not then start looking at CU -- Sir Benjamin Middlethwaite Cheers Sir Benjamin, I'll give it a go. Mogweed. |
#6
|
|||
|
|||
Electrical problem
The3rd Earl Of Derby wrote:
Take the kitchen strap out of the CU attach a battery&bulb L to +, - to bulb and bulb to N and see if the bulb lights? do this on the E to L and E to N. If it lights you have a short if not then start looking at CU Why would using a battery and bulb be a better tester than a proper instrument? alex |
#7
|
|||
|
|||
Electrical problem
Mogweed wrote:
so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) Have you checked for a misplaced neutral? 'Tis a common mistake on a split load CU... Lee -- Email address is valid, but is unlikely to be read. |
#8
|
|||
|
|||
Electrical problem
"Lee" wrote in message ... Mogweed wrote: so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) Have you checked for a misplaced neutral? 'Tis a common mistake on a split load CU... Lee Ah, now then, I haven't checked for that - mainly because I didn't know that a neutral could be misplaced. They all go to a common bar don't they? Mogweed. |
#9
|
|||
|
|||
Electrical problem
On or around Fri, 11 Nov 2005 19:21:12 -0000, "Mogweed"
mused: "Lee" wrote in message ... Mogweed wrote: so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) Have you checked for a misplaced neutral? 'Tis a common mistake on a split load CU... Lee Ah, now then, I haven't checked for that - mainly because I didn't know that a neutral could be misplaced. They all go to a common bar don't they? Nope, seperate neutral bars for RCD and non-RCD circuits. Did the circuit ever work? If it did, then the misplaced neutral idea is wrong as that would trip the RCD from day one. -- | Stuart @ SJW Electrical. Please Reply to group. | |
#10
|
|||
|
|||
Electrical problem
"Lurch" wrote in message ... On or around Fri, 11 Nov 2005 19:21:12 -0000, "Mogweed" mused: "Lee" wrote in message ... Mogweed wrote: so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) Have you checked for a misplaced neutral? 'Tis a common mistake on a split load CU... Lee Ah, now then, I haven't checked for that - mainly because I didn't know that a neutral could be misplaced. They all go to a common bar don't they? Nope, seperate neutral bars for RCD and non-RCD circuits. Did the circuit ever work? If it did, then the misplaced neutral idea is wrong as that would trip the RCD from day one. I read this as all the time since rewiring |
#11
|
|||
|
|||
Electrical problem
On Fri, 11 Nov 2005 18:58:17 GMT, Lee
wrote: Mogweed wrote: so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) Have you checked for a misplaced neutral? 'Tis a common mistake on a split load CU... That does sound like the problem - possibly a neutral swapped with an earth, otherwise the RCD wouldn't trip with a non-earthed item such as a radio. -- Frank Erskine |
#12
|
|||
|
|||
Electrical problem
In message , Frank Erskine
writes On Fri, 11 Nov 2005 18:58:17 GMT, Lee wrote: Mogweed wrote: so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) Have you checked for a misplaced neutral? 'Tis a common mistake on a split load CU... That does sound like the problem - possibly a neutral swapped with an earth, otherwise the RCD wouldn't trip with a non-earthed item such as a radio. Yes it would, if the kitchen ring neutral has been returned to the non-RCD busbar. A common and easy to make mistake. -- steve |
#13
|
|||
|
|||
Electrical problem
|
#15
|
|||
|
|||
Electrical problem
On Fri, 11 Nov 2005 18:36:00 -0000, "Mogweed"
wrote: A mate of mine has completely rewired our house so everything in the installation is brand new, including the split-load consumer unit. We have an upstairs ring main, downstairs ring main and a kitchen ring main, all of which are protected by the RCD, and the problem is the kitchen ring. As soon as *anything* (portable radio, halogen lamp, electric drill or whatever) is plugged into *any* socket on the kitchen ring, the RCD trips (plugging the same things into either upstairs or downstairs rings does *not* trip it). Splitting the ring at the CU and using a proper Megger (500v insulation resistance tester, not just a multimeter) to test each leg of the ring shows the following: L-N = almost infinity resistance (certainly over 1,000Mohms anyway) L-E = " " " " " " " N-E = " " " " " " " so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) TIA, Mogweed Faulty RCD? If they are the same value try swapping two and see if the fault moves. sponix |
#16
|
|||
|
|||
Electrical problem
"--s-p-o-n-i-x--" wrote in message ... On Fri, 11 Nov 2005 18:36:00 -0000, "Mogweed" wrote: A mate of mine has completely rewired our house so everything in the installation is brand new, including the split-load consumer unit. We have an upstairs ring main, downstairs ring main and a kitchen ring main, all of which are protected by the RCD, and the problem is the kitchen ring. As soon as *anything* (portable radio, halogen lamp, electric drill or whatever) is plugged into *any* socket on the kitchen ring, the RCD trips (plugging the same things into either upstairs or downstairs rings does *not* trip it). Splitting the ring at the CU and using a proper Megger (500v insulation resistance tester, not just a multimeter) to test each leg of the ring shows the following: L-N = almost infinity resistance (certainly over 1,000Mohms anyway) L-E = " " " " " " " N-E = " " " " " " " so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) TIA, Mogweed Faulty RCD? If they are the same value try swapping two and see if the fault moves. sponix Thanks sponix but I think you're thinking of the MCBs rather than the RCD ) Mogweed. |
#17
|
|||
|
|||
Electrical problem
On Fri, 11 Nov 2005 19:44:28 -0000, "Mogweed"
wrote: Faulty RCD? If they are the same value try swapping two and see if the fault moves. sponix Thanks sponix but I think you're thinking of the MCBs rather than the RCD ) Well, I have had plug in RCDs that trip when loaded with non-earthed appliances.. sponix |
#18
|
|||
|
|||
Electrical problem
On or around Fri, 11 Nov 2005 19:27:25 +0000, --s-p-o-n-i-x--
mused: Faulty RCD? If they are the same value try swapping two and see if the fault moves. A split load board installed by a mate with 2 identical RCD's in? Stick to whatever it is you do normally. -- | Stuart @ SJW Electrical. Please Reply to group. | |
#19
|
|||
|
|||
Electrical problem
On Fri, 11 Nov 2005 20:19:52 +0000, Lurch
wrote: On or around Fri, 11 Nov 2005 19:27:25 +0000, --s-p-o-n-i-x-- mused: Faulty RCD? If they are the same value try swapping two and see if the fault moves. A split load board installed by a mate with 2 identical RCD's in? Stick to whatever it is you do normally. So you are saying one RCD protects the whole house? That's a pretty stupid idea in addition to the fact it contravenes 16th edition regulations. sponix |
#20
|
|||
|
|||
Electrical problem
On or around Fri, 11 Nov 2005 20:37:35 +0000, --s-p-o-n-i-x--
mused: On Fri, 11 Nov 2005 20:19:52 +0000, Lurch wrote: On or around Fri, 11 Nov 2005 19:27:25 +0000, --s-p-o-n-i-x-- mused: Faulty RCD? If they are the same value try swapping two and see if the fault moves. A split load board installed by a mate with 2 identical RCD's in? Stick to whatever it is you do normally. So you are saying one RCD protects the whole house? That's a pretty stupid idea in addition to the fact it contravenes 16th edition regulations. Dr Dimwit? It doesn't contravene BS7671, under certain circumstances, and a standard slit load board has one RCD covering *some* circuits, not all. I suggest you read up on plit load boards before talking more ********. -- | Stuart @ SJW Electrical. Please Reply to group. | |
#21
|
|||
|
|||
Electrical problem
Lurch wrote:
On or around Fri, 11 Nov 2005 20:37:35 +0000, --s-p-o-n-i-x-- mused: So you are saying one RCD protects the whole house? That's a pretty stupid idea in addition to the fact it contravenes 16th edition regulations. It doesn't contravene BS7671, under certain circumstances, and a standard slit load board has one RCD covering *some* circuits, not all. I suggest you read up on plit load boards before talking more ********. I've seen plenty of non-split-load CU's for sale complete with RCDs at the likes of Screwfix (eg http://tinyurl.com/bb2ej); I understand it's not a good idea to have all circuits protected by an RCD, but when/why would it be actually against regs to fit one of these as a whole-house CU? David |
#22
|
|||
|
|||
Electrical problem
Lurch wrote:
and a standard slit load board has one RCD covering *some* circuits, not all. I suggest you read up on plit load boards before talking more ********. Might be worth adding that you will need RCD protection for *all* circuits if you have TT earthing. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#23
|
|||
|
|||
Electrical problem
Mogweed was thinking very hard :
A mate of mine has completely rewired our house so everything in the installation is brand new, including the split-load consumer unit. We have an upstairs ring main, downstairs ring main and a kitchen ring main, all of which are protected by the RCD, and the problem is the kitchen ring. As soon as *anything* (portable radio, halogen lamp, electric drill or whatever) is plugged into *any* socket on the kitchen ring, the RCD trips (plugging the same things into either upstairs or downstairs rings does *not* trip it). Splitting the ring at the CU and using a proper Megger (500v insulation resistance tester, not just a multimeter) to test each leg of the ring shows the following: L-N = almost infinity resistance (certainly over 1,000Mohms anyway) L-E = " " " " " " " N-E = " " " " " " " so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) It sounds as if you/he have managed to mix up the ring circuits, such that - one of the circuits protected by RCD is mixed up with one not on the RCD. Thus causing an unbalanced load on the RCD, hence it tripping. Try disconnecting each pair of 2.5mm in turn and make sure you have continuity between each pair of both reds and blacks. -- Regards, Harry (M1BYT) (L) http://www.ukradioamateur.co.uk |
#24
|
|||
|
|||
Electrical problem
On Fri, 11 Nov 2005 19:58:08 GMT, "Harry Bloomfield"
wrote: Try disconnecting each pair of 2.5mm in turn and make sure you have continuity between each pair of both reds and blacks. Or even browns and blues :-) -- Frank Erskine |
#25
|
|||
|
|||
Electrical problem
Frank Erskine has brought this to us :
On Fri, 11 Nov 2005 19:58:08 GMT, "Harry Bloomfield" wrote: Try disconnecting each pair of 2.5mm in turn and make sure you have continuity between each pair of both reds and blacks. Or even browns and blues :-) Not if he is trying to circumvent 'Part P' :-) -- Regards, Harry (M1BYT) (L) http://www.ukradioamateur.co.uk |
#26
|
|||
|
|||
Electrical problem
Harry Bloomfield wrote: Frank Erskine has brought this to us : On Fri, 11 Nov 2005 19:58:08 GMT, "Harry Bloomfield" wrote: Try disconnecting each pair of 2.5mm in turn and make sure you have continuity between each pair of both reds and blacks. Or even browns and blues :-) Not if he is trying to circumvent 'Part P' :-) -- Regards, Harry (M1BYT) (L) http://www.ukradioamateur.co.uk Not necessarily - brown and blue cable was on sale before Part P was in force. CRB |
#27
|
|||
|
|||
Electrical problem
"Mogweed" wrote in message ... A mate of mine has completely rewired our house so everything in the installation is brand new, including the split-load consumer unit. We have an upstairs ring main, downstairs ring main and a kitchen ring main, all of which are protected by the RCD, and the problem is the kitchen ring. As soon as *anything* (portable radio, halogen lamp, electric drill or whatever) is plugged into *any* socket on the kitchen ring, the RCD trips (plugging the same things into either upstairs or downstairs rings does *not* trip it). Splitting the ring at the CU and using a proper Megger (500v insulation resistance tester, not just a multimeter) to test each leg of the ring shows the following: L-N = almost infinity resistance (certainly over 1,000Mohms anyway) L-E = " " " " " " " N-E = " " " " " " " so no short-circuits, but yet the RCD trips. What's the problem - more importantly, what's the solution to the problem? ) He has somehow managed to get one or more neutrals wire to the "wrong" neutral bar in the Consumer Unit. This has been covered many times before so google is your friend |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Tough electrical problem! | Home Repair | |||
HELP! Electrical problem. | Metalworking | |||
electrical problem | Home Repair | |||
Problem with retrace lines on EIZO F55S... | Electronics Repair | |||
New Electrical Regs | UK diy |