(yes I know it's 35 years old and needs replacing - I'm just trying to nurse
it through until spring!)

The boiler is overheating (radiators too hot, HW scalding and boiler
creaking a bit). The room and HW cylinder thermostats are working ok, so I
thought the problem was the boiler thermostat. Replaced it with a new one
last week but problem still persists. If I turn the boiler thermostat down
to zero it clicks off and the boiler shuts down, but putting it to any other
setting from 1 to 6 the boiler just keeps going until the room/cylinder stat
shuts it down. Turning the knob through it's range there's no feel/sound of
it switching as I'm sure the old one used to do. I suppose the new
thermostat could be faulty - any way of testing it?

I have recently flushed the system in anticipation of getting a new boiler,
but then plans delayed so I refilled with new inhibitor. When draining the
system I found both the drain tap on the lowest rad and the one on the
boiler frozen/blocked, so I fitted a new one on the rad but didn't bother
with the boiler one (at the time though at new boiler was imminent). Could
there be an air lock or sludge in the boiler which is somehow affecting the
thermostat but still allowing the boiler to produce (very) hot water?

Grateful for any advice.
David
(remove _notme from email address)


  #2   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
"DavidM" writes:
(yes I know it's 35 years old and needs replacing - I'm just trying to nurse
it through until spring!)

The boiler is overheating (radiators too hot, HW scalding and boiler
creaking a bit). The room and HW cylinder thermostats are working ok, so I
thought the problem was the boiler thermostat. Replaced it with a new one
last week but problem still persists. If I turn the boiler thermostat down
to zero it clicks off and the boiler shuts down, but putting it to any other
setting from 1 to 6 the boiler just keeps going until the room/cylinder stat
shuts it down. Turning the knob through it's range there's no feel/sound of
it switching as I'm sure the old one used to do. I suppose the new
thermostat could be faulty - any way of testing it?


What sort is it? Does it have a phile on the end of a thin
copper tube? If so, test it by dunking the phile in a mug
of hot water with a separate thermometer. The temperature
range from min to max should probably be something like
60C through to 80C or 85C.

--
Andrew Gabriel

  #3   Report Post  
TonyB
 
Posts: n/a
Default

If I turn the boiler thermostat down
to zero it clicks off and the boiler shuts down, but putting it to any

other
setting from 1 to 6 the boiler just keeps going until the room/cylinder

stat
shuts it down. Turning the knob through it's range there's no feel/sound

of
it switching as I'm sure the old one used to do. I suppose the new
thermostat could be faulty - any way of testing it?


Could be faulty, it's not unheard of. I'd be looking for a dodgy connection
to/from the stat in the first instance.

Having just tried mine ( different system altogether ) I realise that the
boiler stat only clicks when the water temp is up. Otherwise the click is
off the scale to the low end all the time, if that makes sense. You could
try running the boiler for say 20 mins and then see if you can get the stat
to click. However, that will only tell you that the stat is sensing
temperature, not that it would be in a position to shut down the system.

At the other end of the circuit from the stat there must be some sort of
valve or servo that actually turns the system off and it may be that end
that's faulty.

TonyB


  #4   Report Post  
Set Square
 
Posts: n/a
Default

In an earlier contribution to this discussion,
DavidM wrote:

(yes I know it's 35 years old and needs replacing - I'm just trying
to nurse it through until spring!)

The boiler is overheating (radiators too hot, HW scalding and boiler
creaking a bit). The room and HW cylinder thermostats are working ok,
so I thought the problem was the boiler thermostat. Replaced it with
a new one last week but problem still persists. If I turn the boiler
thermostat down to zero it clicks off and the boiler shuts down, but
putting it to any other setting from 1 to 6 the boiler just keeps
going until the room/cylinder stat shuts it down. Turning the knob
through it's range there's no feel/sound of it switching as I'm sure
the old one used to do. I suppose the new thermostat could be faulty
- any way of testing it?

I have recently flushed the system in anticipation of getting a new
boiler, but then plans delayed so I refilled with new inhibitor. When
draining the system I found both the drain tap on the lowest rad and
the one on the boiler frozen/blocked, so I fitted a new one on the
rad but didn't bother with the boiler one (at the time though at new
boiler was imminent). Could there be an air lock or sludge in the
boiler which is somehow affecting the thermostat but still allowing
the boiler to produce (very) hot water?

Grateful for any advice.
David
(remove _notme from email address)


Silly question: I suppose the little bulb on the end of the stat's capillary
tube *is* correctly plugged into its hole in the heat exchanger - so that it
senses the boiler temperature? Is it making good contact. [You used to be
able to get some heat conducting paste to put in the hole to make sure that
it contacts ok. Probably still can!]
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #5   Report Post  
DavidM
 
Posts: n/a
Default


"DavidM" wrote in message
...
(yes I know it's 35 years old and needs replacing - I'm just trying to

nurse
it through until spring!)

The boiler is overheating (radiators too hot, HW scalding and boiler
creaking a bit). The room and HW cylinder thermostats are working ok, so I
thought the problem was the boiler thermostat. Replaced it with a new one
last week but problem still persists. If I turn the boiler thermostat down
to zero it clicks off and the boiler shuts down, but putting it to any

other
setting from 1 to 6 the boiler just keeps going until the room/cylinder

stat
shuts it down. Turning the knob through it's range there's no feel/sound

of
it switching as I'm sure the old one used to do. I suppose the new
thermostat could be faulty - any way of testing it?

I have recently flushed the system in anticipation of getting a new

boiler,
but then plans delayed so I refilled with new inhibitor. When draining the
system I found both the drain tap on the lowest rad and the one on the
boiler frozen/blocked, so I fitted a new one on the rad but didn't bother
with the boiler one (at the time though at new boiler was imminent). Could
there be an air lock or sludge in the boiler which is somehow affecting

the
thermostat but still allowing the boiler to produce (very) hot water?

Grateful for any advice.
David
(remove _notme from email address)


Thanks for replies so far.
I've done some more checks:
1. Removed thermostat and checked it in a pan of hot water and with a
meter - switches correctly between 60 and 80 C. The old thermostat I took
out also works correctly grrrrrrrr - £33 needlessly spent!
2. Checked the electrical connections - the boiler gas valve is only
connected to the bioler thermostat, no where else, so nothing can be
bypassing the thermostat.
3. Checked that the thermostat bulb is pushed fully into the tube in the
boiler.
4. The gas valve turns off if the boiler supply is swithed off or if the
boiler thermostat is turned to the off position, so I'm pretty sure it's not
just the gas valve sticking (the whole gas valve assembly was renewed last
year anyway).

Any more ideas please?
David
(remove _notme from email address)




  #6   Report Post  
Andrew Gabriel
 
Posts: n/a
Default

In article ,
"DavidM" writes:
Thanks for replies so far.
I've done some more checks:
1. Removed thermostat and checked it in a pan of hot water and with a
meter - switches correctly between 60 and 80 C. The old thermostat I took
out also works correctly grrrrrrrr - £33 needlessly spent!
2. Checked the electrical connections - the boiler gas valve is only
connected to the bioler thermostat, no where else, so nothing can be
bypassing the thermostat.
3. Checked that the thermostat bulb is pushed fully into the tube in the
boiler.
4. The gas valve turns off if the boiler supply is swithed off or if the
boiler thermostat is turned to the off position, so I'm pretty sure it's not
just the gas valve sticking (the whole gas valve assembly was renewed last
year anyway).

Any more ideas please?


Would be useful to narrow down a thermal problem or an electrical problem.
If you take the phile out of the tube and dunk it into a mug of nearly
boiling water, does that cut off the gas valve?
(Obviously, take care with mugs of water and mains around.)

--
Andrew Gabriel

  #7   Report Post  
Set Square
 
Posts: n/a
Default

In an earlier contribution to this discussion,
DavidM wrote:


Thanks for replies so far.
I've done some more checks:
1. Removed thermostat and checked it in a pan of hot water and with a
meter - switches correctly between 60 and 80 C. The old thermostat I
took out also works correctly grrrrrrrr - £33 needlessly spent!
2. Checked the electrical connections - the boiler gas valve is only
connected to the bioler thermostat, no where else, so nothing can be
bypassing the thermostat.
3. Checked that the thermostat bulb is pushed fully into the tube in
the boiler.
4. The gas valve turns off if the boiler supply is swithed off or if
the boiler thermostat is turned to the off position, so I'm pretty
sure it's not just the gas valve sticking (the whole gas valve
assembly was renewed last year anyway).

Any more ideas please?
David


So the thermostat works when you test it in water. The output from the stat
is the only thing connected to the gas valve - but when the boiler gets hot,
the stat doesn't switch off when it should. Is that correct?

If so, it can *only* be that the stat is not sensing the temperature of the
boiler for some reason. Try cleaning out its pocket with a suitable sized
drill bit (operated by hand!) to make sure there's no gunge in there that's
providing insulation and preventing proper contact. Then use some heat
conducting paste.

It that doesn't work, it sounds like there could be some sludge inside the
heat exchanger which is stopping the hot water from getting to the area of
the thermostat pocket.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #8   Report Post  
TonyB
 
Posts: n/a
Default

Would be useful to narrow down a thermal problem or an electrical problem.
If you take the phile out of the tube and dunk it into a mug of nearly
boiling water, does that cut off the gas valve?
(Obviously, take care with mugs of water and mains around.)



Andrew's idea sounds like a good test, can you do that one?
TonyB


  #9   Report Post  
Ed Sirett
 
Posts: n/a
Default

On Sun, 02 Oct 2005 13:01:57 +0100, Set Square wrote:

In an earlier contribution to this discussion,
DavidM wrote:


Thanks for replies so far.
I've done some more checks:
1. Removed thermostat and checked it in a pan of hot water and with a
meter - switches correctly between 60 and 80 C. The old thermostat I
took out also works correctly grrrrrrrr - £33 needlessly spent!
2. Checked the electrical connections - the boiler gas valve is only
connected to the bioler thermostat, no where else, so nothing can be
bypassing the thermostat.
3. Checked that the thermostat bulb is pushed fully into the tube in
the boiler.
4. The gas valve turns off if the boiler supply is swithed off or if
the boiler thermostat is turned to the off position, so I'm pretty
sure it's not just the gas valve sticking (the whole gas valve
assembly was renewed last year anyway).

Any more ideas please?
David


So the thermostat works when you test it in water. The output from the stat
is the only thing connected to the gas valve - but when the boiler gets hot,
the stat doesn't switch off when it should. Is that correct?

If so, it can *only* be that the stat is not sensing the temperature of the
boiler for some reason. Try cleaning out its pocket with a suitable sized
drill bit (operated by hand!) to make sure there's no gunge in there that's
providing insulation and preventing proper contact. Then use some heat
conducting paste.

It that doesn't work, it sounds like there could be some sludge inside the
heat exchanger which is stopping the hot water from getting to the area of
the thermostat pocket.


The only other possibility is that the capiliary tube is kinked so that
when the thermostat is in position it does not work correctly?



--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #10   Report Post  
DavidM
 
Posts: n/a
Default


"Ed Sirett" wrote in message
news
On Sun, 02 Oct 2005 13:01:57 +0100, Set Square wrote:

In an earlier contribution to this discussion,
DavidM wrote:


Thanks for replies so far.
I've done some more checks:
1. Removed thermostat and checked it in a pan of hot water and with a
meter - switches correctly between 60 and 80 C. The old thermostat I
took out also works correctly grrrrrrrr - £33 needlessly spent!
2. Checked the electrical connections - the boiler gas valve is only
connected to the bioler thermostat, no where else, so nothing can be
bypassing the thermostat.
3. Checked that the thermostat bulb is pushed fully into the tube in
the boiler.
4. The gas valve turns off if the boiler supply is swithed off or if
the boiler thermostat is turned to the off position, so I'm pretty
sure it's not just the gas valve sticking (the whole gas valve
assembly was renewed last year anyway).

Any more ideas please?
David


So the thermostat works when you test it in water. The output from the

stat
is the only thing connected to the gas valve - but when the boiler gets

hot,
the stat doesn't switch off when it should. Is that correct?

If so, it can *only* be that the stat is not sensing the temperature of

the
boiler for some reason. Try cleaning out its pocket with a suitable

sized
drill bit (operated by hand!) to make sure there's no gunge in there

that's
providing insulation and preventing proper contact. Then use some heat
conducting paste.

It that doesn't work, it sounds like there could be some sludge inside

the
heat exchanger which is stopping the hot water from getting to the area

of
the thermostat pocket.


The only other possibility is that the capiliary tube is kinked so that
when the thermostat is in position it does not work correctly?



--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


Am continuing to investigate - thanks for advice so far.
David




  #11   Report Post  
DavidM
 
Posts: n/a
Default


"DavidM" wrote in message
...

"Ed Sirett" wrote in message
news
On Sun, 02 Oct 2005 13:01:57 +0100, Set Square wrote:

In an earlier contribution to this discussion,
DavidM wrote:


Thanks for replies so far.
I've done some more checks:
1. Removed thermostat and checked it in a pan of hot water and with a
meter - switches correctly between 60 and 80 C. The old thermostat I
took out also works correctly grrrrrrrr - £33 needlessly spent!
2. Checked the electrical connections - the boiler gas valve is only
connected to the bioler thermostat, no where else, so nothing can be
bypassing the thermostat.
3. Checked that the thermostat bulb is pushed fully into the tube in
the boiler.
4. The gas valve turns off if the boiler supply is swithed off or if
the boiler thermostat is turned to the off position, so I'm pretty
sure it's not just the gas valve sticking (the whole gas valve
assembly was renewed last year anyway).

Any more ideas please?
David

So the thermostat works when you test it in water. The output from the

stat
is the only thing connected to the gas valve - but when the boiler

gets
hot,
the stat doesn't switch off when it should. Is that correct?

If so, it can *only* be that the stat is not sensing the temperature

of
the
boiler for some reason. Try cleaning out its pocket with a suitable

sized
drill bit (operated by hand!) to make sure there's no gunge in there

that's
providing insulation and preventing proper contact. Then use some heat
conducting paste.

It that doesn't work, it sounds like there could be some sludge inside

the
heat exchanger which is stopping the hot water from getting to the

area
of
the thermostat pocket.


The only other possibility is that the capiliary tube is kinked so that
when the thermostat is in position it does not work correctly?



--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


Am continuing to investigate - thanks for advice so far.
David


Update:
The thermostat tube did have a couple of rather tight bends, so straightened
it out and rerouted it a bit (new hole drilled in control box). Also cleaned
out the tube in the heat exchanger into which the bulb fits, and it now
seems to be working ok.
Radiators still get a bit hot, but given all the changes/replacements over
the years it's probably overdue for rebalancing the whole setup, so that's
the next job on the list.
Sods law says that next week I'll get a sensible quote arrive for fitting a
new boiler
Many thanks for all the advice!
David.
(remove the _notme from email address)


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Non-modulating condensing boilers? Egremont UK diy 34 July 22nd 05 07:02 PM
Condensing Boiler News RedOnRed UK diy 0 April 9th 05 05:37 PM
Ariston microGenus Boiler problem, totally non D.I.Y savvy! [email protected] UK diy 3 March 12th 05 04:41 PM
11degC across Boiler, why? Tom UK diy 54 September 24th 04 07:32 AM
Near death boiler + replacing a boiler David Hearn UK diy 9 January 26th 04 12:44 PM


All times are GMT +1. The time now is 04:49 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"