  #1   Report Post  
Bob
 
Posts: n/a
Default Central Heating Problem

Hi,

I have a problem with my central heating system, which I hope someone
could advise me on. I'm not very good with plumbing, so if I am lacking
info, please forgive me and ask for more details.

Anyway, My central heating pipes/rads make quite a lot of noise of
running water, particular upstairs and in the pipes going to upstairs.
The radiators upstairs are a nightmare. One of them is relatively ok,
heat-wise, but it needs bleeding every 2 or 3 days. The other radiators
are cold and appear to be empty. If I open the bleed valves on these
with the thermostat set so the pump and heating is running, then water
drains from the radiator (I can feel suction on the bleed valve.) If I
turn the thermostat so the heating is off, the radiators fill up, but
when they are full, they are still cold (getting full with cold water??)
Sometimes, through bleeding all rads at the same time and then switcing
the bleed valves off, I hear running water, then the header tank
overflow pipe starts spilling water. And that's about it, I'm not sure
where to begin to look.

Does anyone have any ideas or suggestions. I'm quite prepared to call a
plumber out if that's what's necessary, but I'd prefer to know what the
problem is before I did that so he can't try pulling the wool.

Many thanks for reading,
Bob
  #2   Report Post  
Set Square
 
Posts: n/a
Default

In an earlier contribution to this discussion,
Bob wrote:

Hi,

I have a problem with my central heating system, which I hope someone
could advise me on. I'm not very good with plumbing, so if I am
lacking info, please forgive me and ask for more details.

Anyway, My central heating pipes/rads make quite a lot of noise of
running water, particular upstairs and in the pipes going to upstairs.
The radiators upstairs are a nightmare. One of them is relatively ok,
heat-wise, but it needs bleeding every 2 or 3 days. The other
radiators are cold and appear to be empty. If I open the bleed valves
on these with the thermostat set so the pump and heating is running,
then water drains from the radiator (I can feel suction on the bleed
valve.) If I turn the thermostat so the heating is off, the radiators
fill up, but when they are full, they are still cold (getting full
with cold water??) Sometimes, through bleeding all rads at the same
time and then switcing the bleed valves off, I hear running water,
then the header tank overflow pipe starts spilling water. And that's
about it, I'm not sure where to begin to look.

Does anyone have any ideas or suggestions. I'm quite prepared to call
a plumber out if that's what's necessary, but I'd prefer to know what
the problem is before I did that so he can't try pulling the wool.

Many thanks for reading,
Bob


Has it ever worked? Has this problem arisen since someone did some
alterations or repairs to the system?

My first thoughts are that the pump is pumping in the wrong direction - and
needs turning round. But we really need more details of the system type.

Are both heating and hot water pumped, or is HW primary circulation by
gravity (convection)? Are there any motorised valves? If so how many, and
does each one have two or three water connections? [Photos of the pipework
in the airing cupboard - if that's where the valves/pump are - would be
useful].

Which header tank is overflowing - the large cold tank which feeds the
domestic hot water system, or the small tank for the heating system? If it's
the small one, is the ball valve working ok? What is the water level when
the system is cold? [There should be only 2 or 3 inches of water in the
tank - with the level a *long* way below the overflow to allow for
expansion].

That'll do for starters!
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #3   Report Post  
 
Posts: n/a
Default

Set Square, thanks for your time and advice.


Set Square wrote:

Has it ever worked? Has this problem arisen since someone did some
alterations or repairs to the system?


It has worked much better in the past than it does now, although
problems seem to come and go. The upstairs rads have always needed
frequent bleeding, and the system has always been noisy, in terms of
running water. There hasn't been any work done, other than a boiler
service a year or so ago.



My first thoughts are that the pump is pumping in the wrong direction

- and
needs turning round. But we really need more details of the system

type.

Are both heating and hot water pumped, or is HW primary circulation

by
gravity (convection)? Are there any motorised valves? If so how many,

and
does each one have two or three water connections? [Photos of the

pipework
in the airing cupboard - if that's where the valves/pump are - would

be
useful].


My system consists of a Baxi Bermuda located behind my gas fire
downstairs. The pump is under the downstairs floorboards. I think (but
I'm not sure, sorry) that the HW is circulated by gravity. I really
couldn't answer about the motorised valve. I haven't noticed any around
the pump or in the airing cupboard, but this doesn't mean there aren't
any (it's generally inconvenient getting to the pump)



Which header tank is overflowing - the large cold tank which feeds

the
domestic hot water system, or the small tank for the heating system?

If it's
the small one, is the ball valve working ok? What is the water level

when
the system is cold? [There should be only 2 or 3 inches of water in

the
tank - with the level a *long* way below the overflow to allow for
expansion].


It's the small one that is slightly warm that sometimes overflows (but
hasn't done for some time.) The ball valve is fine, and the water level
is normally well below the outlet.)

I used to be able to bleed the radiators with the pump running in the
past, but like I said, if I do that at the moment, the rads appear to
drain. Where could the water be going? I haven't spotted a leak
anywhere (and I did look under the floorboards too


That'll do for starters!
--


I appreciate the help, if there's any more info I can give, I'll gladly
do so.
Many Thanks,
Bob.

  #4   Report Post  
Set Square
 
Posts: n/a
Default

In an earlier contribution to this discussion,
wrote:

Set Square, thanks for your time and advice.



My system consists of a Baxi Bermuda located behind my gas fire
downstairs. The pump is under the downstairs floorboards. I think (but
I'm not sure, sorry) that the HW is circulated by gravity. I really
couldn't answer about the motorised valve. I haven't noticed any
around the pump or in the airing cupboard, but this doesn't mean
there aren't any (it's generally inconvenient getting to the pump)

It's the small one that is slightly warm that sometimes overflows (but
hasn't done for some time.) The ball valve is fine, and the water
level is normally well below the outlet.)

I used to be able to bleed the radiators with the pump running in the
past, but like I said, if I do that at the moment, the rads appear to
drain. Where could the water be going? I haven't spotted a leak
anywhere (and I did look under the floorboards too

OK, it's almost certainly gravity HW circulation (two 1" or 28mm pipes
connected to one side of the boiler and going to the indirect coil in the
hot water cylinder in the airing cupboard) and pumped CH (two 3/4" or 22mm
pipes connected to the other side of the boiler). Presumably there's no
cylinder stat, and the DHW gets hot whenever either HW or CH are switched
on, and sometimes gets *too* hot?

I would guess from your further information that you have no corrosion
inhibitor in your system - with the result that a lot of sludge has built
up, partially (or even completely!) blocking some of the radiators. I would
also guess that what you are bleeding out is hydrogen caused by the
corrosion rather than air. [You can test for this by holding a lighted taper
in the stream of gas coming out of the bleed valve. If it burns, it's
hydrogen!]

Sludged-up radiators would probably explain what happens when you try to
bleed with the pump running. The pump is probably installed in the boiler
return - so that it's in effect sucking the water through the radiators. If
the inlet of a radiator is blocked, and you suck on the outlet with the
bleed valve open, you're going to suck the water out. This will end up in
the header tank, with a resulting rise in level.

It seems to me that your system needs a really good flush out, and then
needs to have inhibitor added. By far the best way to flush it out -
particularly with summer coming on - is to remove the rads and take them
outside and give then a good flush out with a hosepipe. While they're off,
flush the flow and return pipes by keeping the header tank full and opening
each radiator valve in turn (with a bowl under it to catch the water!).
Incidentally, take great care not to spill any black sludge from the
radiators on your carpets - it makes a pretty indellible dye!

If you get a plumber in, he'll probably want to charge you an arm and a leg
for doing a power flush. However, the method I have described is far
cheaper - and probably more effective.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #5   Report Post  
Steve
 
Posts: n/a
Default

Set Square wrote:
It seems to me that your system needs a really good flush out, and then
needs to have inhibitor added. By far the best way to flush it out -
particularly with summer coming on - is to remove the rads and take them
outside and give then a good flush out with a hosepipe. While they're off,
flush the flow and return pipes by keeping the header tank full and opening
each radiator valve in turn (with a bowl under it to catch the water!).
Incidentally, take great care not to spill any black sludge from the
radiators on your carpets - it makes a pretty indellible dye!

If you get a plumber in, he'll probably want to charge you an arm and a leg
for doing a power flush. However, the method I have described is far
cheaper - and probably more effective.


That's fantastic information, many thanks Set Square, I'll give that a
go. Incidentally, with me being a complete newbie, where does one put
the corrosion inhibitor? Does it simply pour into the header tank?

Thanks again,

Bob


  #6   Report Post  
Steve
 
Posts: n/a
Default

Oops, using my brother's machine, hence the Steve!!

Bob
  #7   Report Post  
Set Square
 
Posts: n/a
Default

In an earlier contribution to this discussion,
Steve wrote:


That's fantastic information, many thanks Set Square, I'll give that a
go. Incidentally, with me being a complete newbie, where does one put
the corrosion inhibitor? Does it simply pour into the header tank?


Yes. After flushing it out, drain and re-fill the system. Part-way through
the fill process, pour in the inhibitor. It will then get thoroughly mixed
in.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #8   Report Post  
Bob
 
Posts: n/a
Default

Set Square wrote:

It seems to me that your system needs a really good flush out, and then
needs to have inhibitor added. By far the best way to flush it out -
particularly with summer coming on - is to remove the rads and take them
outside and give then a good flush out with a hosepipe. While they're off,
flush the flow and return pipes by keeping the header tank full and opening
each radiator valve in turn (with a bowl under it to catch the water!).
Incidentally, take great care not to spill any black sludge from the
radiators on your carpets - it makes a pretty indellible dye!


Hi Set Square,

Right, finally had a go at the first radiator....unfortunately the
results weren't as I was expecting from your description.

I took a rad off and flushed it out, and as expected was a bit mucky,
although not really sludgy. I then opened a valve on the pipes (not sure
which is flow and return, so did each separately.) Anyway, when the pump
was off, I got water flowing, which I let run until it ran clear.
However, when I switched the pump back on (by turning up thermostat) the
water stopped flowing and I could feel the suction at the valve again.
The same symptoms occurred at both valves. By the way, I closed the
valves on all other upstairs rads.

Is this what you would expect or is something else wrong. Additionally,
is there anything else I can try?

Many thanks for your assistance.
Bob
  #9   Report Post  
Set Square
 
Posts: n/a
Default

In an earlier contribution to this discussion,
Bob wrote:

Set Square wrote:

It seems to me that your system needs a really good flush out, and
then needs to have inhibitor added. By far the best way to flush it
out - particularly with summer coming on - is to remove the rads and
take them outside and give then a good flush out with a hosepipe.
While they're off, flush the flow and return pipes by keeping the
header tank full and opening each radiator valve in turn (with a
bowl under it to catch the water!). Incidentally, take great care
not to spill any black sludge from the radiators on your carpets -
it makes a pretty indellible dye!


Hi Set Square,

Right, finally had a go at the first radiator....unfortunately the
results weren't as I was expecting from your description.

I took a rad off and flushed it out, and as expected was a bit mucky,
although not really sludgy. I then opened a valve on the pipes (not
sure which is flow and return, so did each separately.) Anyway, when
the pump was off, I got water flowing, which I let run until it ran
clear. However, when I switched the pump back on (by turning up
thermostat) the water stopped flowing and I could feel the suction at
the valve again. The same symptoms occurred at both valves. By the
way, I closed the valves on all other upstairs rads.

Is this what you would expect or is something else wrong.
Additionally, is there anything else I can try?

Many thanks for your assistance.
Bob


Remind me of the original problem - it seems a long time since I wrote the
above!

A description of the system - including the relative position of boiler,
pump, zone valves, etc. would help. Even better if you can take some photos
and upload them to a website and post a reference to them.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #10   Report Post  
Bob
 
Posts: n/a
Default



Remind me of the original problem - it seems a long time since I wrote the
above!


Aye, just about a month ago now

A description of the system - including the relative position of boiler,
pump, zone valves, etc. would help. Even better if you can take some photos
and upload them to a website and post a reference to them.


Here's the description I posted first time, aswell some other bits I posted:


Quote
My system consists of a Baxi Bermuda located behind my gas fire
downstairs. The pump is under the downstairs floorboards. I think (but
I'm not sure, sorry) that the HW is circulated by gravity. I really
couldn't answer about the motorised valve. I haven't noticed any around
the pump or in the airing cupboard, but this doesn't mean there aren't
any (it's generally inconvenient getting to the pump)
Unquote

Quote
Anyway, My central heating pipes/rads make quite a lot of noise of
running water, particular upstairs and in the pipes going to upstairs.
The radiators upstairs are a nightmare. One of them is relatively ok,
heat-wise, but it needs bleeding every 2 or 3 days. The other radiators
are cold and appear to be empty. If I open the bleed valves on these
with the thermostat set so the pump and heating is running, then water
drains from the radiator (I can feel suction on the bleed valve.) If I
turn the thermostat so the heating is off, the radiators fill up, but
when they are full, they are still cold (getting full with cold water??)
Sometimes, through bleeding all rads at the same time and then switcing
the bleed valves off, I hear running water, then the header tank
overflow pipe starts spilling water. And that's about it, I'm not sure
where to begin to look.
Unquote

Your original reply read:

Quote
I would guess from your further information that you have no corrosion
inhibitor in your system - with the result that a lot of sludge has built
up, partially (or even completely!) blocking some of the radiators. I would
also guess that what you are bleeding out is hydrogen caused by the
corrosion rather than air. [You can test for this by holding a lighted taper
in the stream of gas coming out of the bleed valve. If it burns, it's
hydrogen!]

Sludged-up radiators would probably explain what happens when you try to
bleed with the pump running. The pump is probably installed in the boiler
return - so that it's in effect sucking the water through the radiators. If
the inlet of a radiator is blocked, and you suck on the outlet with the
bleed valve open, you're going to suck the water out. This will end up in
the header tank, with a resulting rise in level.

It seems to me that your system needs a really good flush out, and then
needs to have inhibitor added. By far the best way to flush it out -
particularly with summer coming on - is to remove the rads and take them
outside and give then a good flush out with a hosepipe. While they're off,
flush the flow and return pipes by keeping the header tank full and opening
each radiator valve in turn (with a bowl under it to catch the water!).
Incidentally, take great care not to spill any black sludge from the
radiators on your carpets - it makes a pretty indellible dye!
Unquote

Sorry to make the post so long, I just thought as most of the info was
there, I'd just cut and paste.

I'm not sure what to take pictures of to be honest, as I said, the
boiler is behind the fire, and the pump is under the floor. That only
leaves the airing cupboard & header tank...

Thanks again for your assistance,
Bob


  #11   Report Post  
Set Square
 
Posts: n/a
Default

In an earlier contribution to this discussion,
Bob wrote:

Remind me of the original problem - it seems a long time since I
wrote the above!


Aye, just about a month ago now

A description of the system - including the relative position of
boiler, pump, zone valves, etc. would help. Even better if you can
take some photos and upload them to a website and post a reference
to them.


Here's the description I posted first time, aswell some other bits I
posted:
SNIP


Ah, I remember the one. With a Bermuda and gravity hot water there won't be
any motorised valves - so don't waste time looking for them.

It still sounds as if there is a blockage on the flow side of the CH
circuit. Are the downstairs rads ok? When you flush the pipes out with an
upstairs rad removed by opening each valve in turn (with the pump off, of
course) do you get a good flow from *both* valves?

Are the HW and CH circuits separate, or do they share any pipework? If it's
like the Bermudas which I used to own, the boiler casting will have 4
connection points - 2 on each side. It works best if the HW circuit is
connected to one side and the CH circuit to the other - but you sometimes
find them both connected to the same side, and then splitting into 2
circuits.

Is this a recent problem, or has it *never* worked properly?
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #12   Report Post  
John
 
Posts: n/a
Default


"Set Square" wrote in message
...
In an earlier contribution to this discussion,
Bob wrote:

Remind me of the original problem - it seems a long time since I
wrote the above!


Aye, just about a month ago now

A description of the system - including the relative position of
boiler, pump, zone valves, etc. would help. Even better if you can
take some photos and upload them to a website and post a reference
to them.


Here's the description I posted first time, aswell some other bits I
posted:
SNIP


Ah, I remember the one. With a Bermuda and gravity hot water there won't
be
any motorised valves - so don't waste time looking for them.

It still sounds as if there is a blockage on the flow side of the CH
circuit. Are the downstairs rads ok? When you flush the pipes out with an
upstairs rad removed by opening each valve in turn (with the pump off, of
course) do you get a good flow from *both* valves?

Are the HW and CH circuits separate, or do they share any pipework? If
it's
like the Bermudas which I used to own, the boiler casting will have 4
connection points - 2 on each side. It works best if the HW circuit is
connected to one side and the CH circuit to the other - but you sometimes
find them both connected to the same side, and then splitting into 2
circuits.

Is this a recent problem, or has it *never* worked properly?


From the "suction" with the pump running I'd be immediately suspicious of a
pump installed in the return from the radiators. The suction will lead to
air being drawn into any weakness point (valve glands, pipe joints etc). To
the OP can you see an arrow on the body of the pump or identify which way
the water flows through it and see if it is pulling water away from the
boiler or pushing it back towards it?
A continuous slow ingress of air (oxygen) will lead to corrosion and the
production of sludge which will settle out at points of low velocity and
eventually cause circulation difficulties.

Flushing out everything and then a dose with Sentinel Ferroquest and a hot
circulating flush will help no end

Dont spill anything on soft furnishing or Set Squares prophesy will come
trueg


  #13   Report Post  
Bob
 
Posts: n/a
Default


It still sounds as if there is a blockage on the flow side of the CH
circuit. Are the downstairs rads ok? When you flush the pipes out with an
upstairs rad removed by opening each valve in turn (with the pump off, of
course) do you get a good flow from *both* valves?


Downstairs rads are fine, never need bleeding, and kicking out plenty of
heat. I'll have to get back to you on the flow from both valves
question....all rads are back in place for the moment.


Are the HW and CH circuits separate, or do they share any pipework?


As far as I can tell, they are separate. There are four pipes coming out
of the side of the chimney breast running to upstairs (HW F/R & CH
F/R???). I only know that all pipes come out of one side of the chimney
breast, not sure how they are configured at the boiler itself.


Is this a recent problem, or has it *never* worked properly?


The upstairs rads have always needed bleeding very regularly, and have
always been quite noisy. It's only recently (12-18mnths) that they
appear to empty with the pump running.

Again, thanks for the assistance. It's much appreciated.
Bob
  #14   Report Post  
Set Square
 
Posts: n/a
Default

In an earlier contribution to this discussion,
Bob wrote:


The upstairs rads have always needed bleeding very regularly, and have
always been quite noisy. It's only recently (12-18mnths) that they
appear to empty with the pump running.

Has the pump ever been removed/replaced? Could it have been put back the
opposite way round from how it was when it worked reasonably well?
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #15   Report Post  
Bob
 
Posts: n/a
Default

Set Square wrote:
Has the pump ever been removed/replaced? Could it have been put back the
opposite way round from how it was when it worked reasonably well?


As long as we've lived in the house, the pump has never been removed or
replaced. I will do what John suggested and get under the floor to check
the flow direction and report back. I'll also flush all the upstairs
rads, and let you know about the flow rate from each valve.

Thanks again and regards,
Bob


  #16   Report Post  
Bob
 
Posts: n/a
Default

John wrote:

From the "suction" with the pump running I'd be immediately suspicious of a
pump installed in the return from the radiators. The suction will lead to
air being drawn into any weakness point (valve glands, pipe joints etc). To
the OP can you see an arrow on the body of the pump or identify which way
the water flows through it and see if it is pulling water away from the
boiler or pushing it back towards it?
A continuous slow ingress of air (oxygen) will lead to corrosion and the
production of sludge which will settle out at points of low velocity and
eventually cause circulation difficulties.

Flushing out everything and then a dose with Sentinel Ferroquest and a hot
circulating flush will help no end

Dont spill anything on soft furnishing or Set Squares prophesy will come
trueg



Thanks for the reply John, I'll flush the other rads, and check for the
arrow on the pump....it's pretty inaccessible, under the floor,
unfortunately.

Incidentally, you mention air being drawn into weak spots in the
pipework if the pump is pulling rather than pushing. If it were pushing,
would I notice water coming *out* of these weak spots?

Many thanks,
Bob
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Problem with Central Heating since changing programmer [email protected] UK diy 21 January 7th 07 11:50 PM
central heating problem.. radiators stay cold Martin UK diy 4 February 16th 05 10:53 PM
Central Heating Problem Duncan Lally UK diy 2 February 22nd 04 09:22 PM
"Sludge Problem" with central heating radiators discoverer UK diy 11 November 17th 03 10:07 PM
Central Heating valve problem. TerenceBooth UK diy 2 October 21st 03 12:34 PM


All times are GMT +1. The time now is 11:29 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"