Heat Bank - space heating or not ?
If you're going to fit a heat bank to get the benefit of mains pressure hot
water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store I have this suspicion that if you buffer the radiators via a heat bank you may lose some of the benefit of a condensing boiler since the return temperature will be greater than if you designed the system for radiators, opting for a lower than usual return. Yes, I know it means departing from BS, having bigger rads, adjusting for mean temperature etc. but so what if it achieves the desired effect ? I bet this has been discussed before but I'm taking the easy option |
#2
|
|||
|
|||
"Jeff" wrote in message ... If you're going to fit a heat bank to get the benefit of mains pressure hot water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store I have this suspicion that if you buffer the radiators via a heat bank you may lose some of the benefit of a condensing boiler since the return temperature will be greater than if you designed the system for radiators, opting for a lower than usual return. Yes, I know it means departing from BS, having bigger rads, adjusting for mean temperature etc. but so what if it achieves the desired effect ? I bet this has been discussed before but I'm taking the easy option Get a larger heat bank and run at the lowest temp you canget away with for DHW. Take the rads off the heat banks and use a Grundfos Alpha pump on the rad circuit. Advantages of Heat-Banks - Instant high pressure hot water - When the store has reached temperature water is delivered instantly at the taps. - Very high water flow-rate - The high-end heat-banks have a flow-rate up to 45 litres/min. - Long efficient boiler burn - Reduces boiler on-off cycling increasing efficiency, although inefficient boiler cycling is no longer a major problem as it was with balanced flues. - Maintains optimum boiler temperature range - using a blending valve the flow/return of the boiler can be kept to optimum maintaining greater efficiencies. The boiler operates at optimum performance. - Combines the output of the stored water and the boiler - Cylinder may be smaller for a similar performance - smaller cylinders than unvented cylinders. - Cylinder at low pressure - Unlike an unvented cylinder it does not store water at high pressures. - Fast cylinder recovery rate - When the boiler is connected directly to the heat-bank, and not via an indirect coil, the recovery rate is rapid. Although in some cases a boiler may heat the heat-bank via an indirect coil, reducing the recovery rate. - Legionella bacteria eliminated - The Legionella bacteria cannot survive in the high temperature sealed conditions of a heat-bank. - No scale build-up in heat-bank - Containing primary and not secondary fresh water, there is no scale build-up inside the heat-bank. - Cold water storage eliminated - No need for cold water storage tanks. - Solar heating storage - Water heated via solar panels may be stored in the heat-bank via a solar coil. - Easy maintenance - If an external plate heat exchanger requires cleaning or replacing it is a matter of draining down the heat-bank, or closing isolating vales, and unscrewing the plate heat-exchanger. In some rare instances plate heat-exchangers are fitted directly inside the heat-bank preventing on-site maintenance. - Easy to improve hot water flowrates - By simply adding additional plate heat-exchangers in parallel, hot water flow rates may be improved. Retrofit additions are possible if extra bathrooms or showers are installed. - Stored water vessel need not be cylindrical - As no internal coil is used for hot water heat transfer the stored water vessel may be any shape, as opposed to a thermal store which has to be cylindrical for maximum efficiency. This has advantages where space is limited. - Rads warm up period only a few minutes - The store holds enough hot water for all the rads, so rads instantly hot - If all TVRs Close the Boiler is Not Affected - Flow is always through the boiler Disadvantages of Heat-Banks - The store needs be near fully temperature to supply baths - Before any hot water is drawn off, the store must be up to temperature. Many later versions use a blending valve on the return to the boiler to ensure only up to temperature water is pumped into the store by the boiler. This prevents agitation of the stored water, and aiding heat stratification within the store giving useful water at the top of the store within a shot time. The water is heat only in one pass through the boiler. - Lower water temperatures with fast flow-rates - As with Combi boilers, fast flow-rates through the plate heat-exchanger results in lower water temperatures. This is not so pronounced with heat-banks as with thermal-stores. - Rads may need to be larger - Rads operate at lower temp, so may be larger _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#3
|
|||
|
|||
"Jeff" wrote in message ... If you're going to fit a heat bank to get the benefit of mains pressure hot water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store I have this suspicion that if you buffer the radiators via a heat bank you may lose some of the benefit of a condensing boiler I don't think so - though my boiler isn't condensing. With a heat bank and a programmable thermostat you could set the boiler to kick in and out at whatever is optimal for the boiler, isolating it totally from requirements like not make every radiator scalding hot or stone cold. |
#4
|
|||
|
|||
On Tue, 19 Apr 2005 18:52:20 +0100, "Jeff"
wrote: If you're going to fit a heat bank to get the benefit of mains pressure hot water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store I have this suspicion that if you buffer the radiators via a heat bank you may lose some of the benefit of a condensing boiler since the return temperature will be greater than if you designed the system for radiators, opting for a lower than usual return. Yes, I know it means departing from BS, having bigger rads, adjusting for mean temperature etc. but so what if it achieves the desired effect ? I bet this has been discussed before but I'm taking the easy option If you have a condensing boiler, then it will work optimally and more efficiently at lower temperatures. Especially at this time of year and in the autumn, you can run the radiators at lower temperatures and the boiler will modulate down to match. If you have a heat bank in the middle, in order to heat the hot water, you need to run it at 75 to 80 degrees. You can take heat out of it to run the radiator, of course, but then the problem is that it will have the effect of causing the boiler to run in bursts of full output to replenish the store. This is not as efficient as letting it run continuously or near continuously at lower power to match the radiator requirement. Heating the space with radiators and providing the hot water are two different problems. WIth the space heating, you can achieve optimal efficiency by driving the radiators directly from the boiler. For water heating, the objective is to dump as much heat into the cylinder as quickly as possible and with efficiency as less of a concern. In my system design I have a condensing boiler with weather compensator driving the radiators directly. THe radiator sizing has been arranged such that at the nominal -3 degree outside temperature used as part of UK heating designs, the flow temperature will be 70 degrees and return 50 degrees or less. I achieved exactly this in practice during the winter. Now when just a little heat is required in the evenings, the boiler modulates down to about 3-4 kW and the flow temperature can be around 40 degrees or so. However, when there is hot water demand, the boiler is switched over to driving the cylinder (a fast recovery type) and winds up to full power. The concept of this is to reheat the cylinder quickly and then switch back to running the heating. It works very well. -- ..andy To email, substitute .nospam with .gl |
#5
|
|||
|
|||
"Andy Hall" wrote in message ... If you have a heat bank in the middle, in order to heat the hot water, you need to run it at 75 to 80 degrees. Using a heat bank, the temperature only be 10C above DHW temperature. IF you want 50C at the taps, then 60C store temp will do. So a condensing boiler with a 22C flow/return temp differential need only be running at 38C return. Very economical. The store then needs to be larger. You can take heat out of it to run the radiator, of course, but then the problem is that it will have the effect of causing the boiler to run in bursts of full output to replenish the store. Yes, economically so. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#6
|
|||
|
|||
Jeff wrote:
If you're going to fit a heat bank to get the benefit of mains pressure hot water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? With a modern boiler (and hence sophisticated load compensating control system), you will usually be better off letting it drive the rads directly. (Thermal stores are good at improving efficiency on old "all or nothing" boilers, but often just serve to cock up the closed loop control system on modulating boilers) I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store Personally I would connect the rads directly. However there is sure to be someone along shortly to contradict that. ;-) I have this suspicion that if you buffer the radiators via a heat bank you may lose some of the benefit of a condensing boiler since the return temperature will be greater than if you designed the system for radiators, Yup, you can get round some of the problems with extra work (blending valves etc), but it is usually far simpler to avoid creating the problem in the first place than spending lots of money fixing it. A modern modulating boiler will run at its most efficient when it can reduce its output down to a steady low state to match the actual radiator load. If you stick an extra sodding great energy store into the equation then you are introducing extra complexity that will usually prevent the most efficient mode of operating from being reached. opting for a lower than usual return. Yes, I know it means departing from BS, having bigger rads, adjusting for mean temperature etc. but so what if it achieves the desired effect ? Not sure I follow that bit? I bet this has been discussed before but I'm taking the easy option It has, to death ;-) Google will have loads. One of the difficulties is that for many years the thermal store was actually a "good thing" in radiator circuits since it improved boiler efficiency by reducing short cycling etc. Modern boilers and control systems have now rendered that common wisdom less relevant in many cases. However some folks are not so easily separated from their old ways ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#7
|
|||
|
|||
"Doctor Evil" wrote in message ... You can take heat out of it to run the radiator, of course, but then the problem is that it will have the effect of causing the boiler to run in bursts of full output to replenish the store. Yes, economically so. OK, you covered all the pros and cons quite comprehensively, bearing in mind I think a condensing oil boiler can only fire at the rated output, you are saying it's likely to be quite economical to let it dump a load of heat into the store and then let the rads draw it off? |
#8
|
|||
|
|||
"John Rumm" wrote in message ... With a modern boiler (and hence sophisticated load compensating control system), you will usually be better off letting it drive the rads directly. The great thing about a thermal store/heat bank is that a simple none complicated boiler need only be used. This adds reliability, and less service changes as less to go wrong. (Thermal stores are good at improving efficiency on old "all or nothing" boilers, but often just serve to cock up the closed loop control system on modulating boilers) Not so. Modulating boilers work wekll with heat banks. snip misinformation A modern modulating boiler will run at its most efficient when it can reduce its output down to a steady low state to match the actual radiator load. He doesn't need a modulating boiler with sophisticated load compensation control. One of the difficulties is that for many years the thermal store was actually a "good thing" in radiator circuits since it improved boiler efficiency by reducing short cycling etc. Modern boilers and control systems have now rendered that common wisdom less relevant in many cases. However some folks are not so easily separated from their old ways ;-) Old ways? What a joke.Thermal stores never took off and obtained the status it deserves because plumbers couldn't understand them and builders kept putting in silly tanks and cylinders. It is also too new for many people, so much for "old ways". They are becoming more popular now as people realise they have more advantages than unvented cylinders which require annual services. The store is a superb neutral point separating, the boiler, rads, DHW, solar input, etc. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#9
|
|||
|
|||
"Jeff" wrote in message ... I should have mentioned - no gas here, I'll (or probably someone else) will be fitting a condensing oil boiler. AFAIK, they don't modulate. I think it's firing or not firing. Oil condensers are very expensive and don't offer great efficiencies over non-condensers. Yep, just get a normal heat bank. Possibly that would make me lean towards taking the rads off the heat bank, to reduce cycling. Very wise. Get a heat bank with two cylinder stats Otherwise, during not so cold weather the boiler will be oversized and cycling regularly. Would you agree? Yep. I can see the advantage there but then I think that the heat bank will get up to temperature and take the return temp up above the optimum. Pandora says the water in the store is typically 75 degrees. It can be higher. They want lower temps to get the best out of gas condensers. If the rads are off the boiler, I could design the system for a suitable return temperature to try and keep it condensing. But then, that only applies when the system is fully loaded, and how often is that? With a non-condensing oil boiler you don't want low temps. Maybe I worry too much about this efficiency lark. Just have two cylinder stats to prevent boiler cycling and lag the hell out of all exposed pipes. You could fit a blending valve on the flow/return. The likes of DPS would fit one for you. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#10
|
|||
|
|||
"Andy Hall" wrote in message ... If you're going to fit a heat bank to get the benefit of mains pressure hot water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store If you have a condensing boiler, then it will work optimally and more efficiently at lower temperatures. Especially at this time of year and in the autumn, you can run the radiators at lower temperatures and the boiler will modulate down to match. Only if it's a modulating boiler surely. If it can only do full or nothing I'd still suggest putting the heat bank in the middle is a better option. |
#11
|
|||
|
|||
"Jeff" wrote in message ... I should have mentioned - no gas here, I'll (or probably someone else) will be fitting a condensing oil boiler. AFAIK, they don't modulate. I think it's firing or not firing. Yes Possibly that would make me lean towards taking the rads off the heat bank, to reduce cycling. Otherwise, during not so cold weather the boiler will be oversized and cycling regularly. Would you agree? Yes. The other problem with direct connection in not so cold weather is you don't really take much heat from the boiler, but it is running flat out so the boiler thermostat operates more often than the control thermostat and you can actually feel the temperature of the radiators going down whilst waiting for the boiler to come on again. A heat store will level out this effect. If the rads are off the boiler, I could design the system for a suitable return temperature to try and keep it condensing. But then, that only applies when the system is fully loaded, and how often is that? You probably won't have the boiler ever fully loaded. Thus keeping it optimal is impossible. Maybe I worry too much about this efficiency lark. No. Do worry about it. But for non-modulating boilers I think a heat store is the best approach. |
#12
|
|||
|
|||
"Mike" wrote in message ... "Jeff" wrote in message ... I should have mentioned - no gas here, I'll (or probably someone else) will be fitting a condensing oil boiler. AFAIK, they don't modulate. I think it's firing or not firing. Yes Possibly that would make me lean towards taking the rads off the heat bank, to reduce cycling. Otherwise, during not so cold weather the boiler will be oversized and cycling regularly. Would you agree? Yes. The other problem with direct connection in not so cold weather is you don't really take much heat from the boiler, but it is running flat out so the boiler thermostat operates more often than the control thermostat and you can actually feel the temperature of the radiators going down whilst waiting for the boiler to come on again. A heat store will level out this effect. If the rads are off the boiler, I could design the system for a suitable return temperature to try and keep it condensing. But then, that only applies when the system is fully loaded, and how often is that? You probably won't have the boiler ever fully loaded. Thus keeping it optimal is impossible. If the boiler is connected directly to a store, it will be fully loaded when reheating. Maybe I worry too much about this efficiency lark. No. Do worry about it. But for non-modulating boilers I think a heat store is the best approach. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#13
|
|||
|
|||
"Doctor Evil" wrote in message ... If the rads are off the boiler, I could design the system for a suitable return temperature to try and keep it condensing. But then, that only applies when the system is fully loaded, and how often is that? You probably won't have the boiler ever fully loaded. Thus keeping it optimal is impossible. If the boiler is connected directly to a store, it will be fully loaded when reheating. That's what I said in the paragraph after |
#14
|
|||
|
|||
On Tue, 19 Apr 2005 22:06:49 +0100, "Jeff"
wrote: "Doctor Evil" wrote in message ... You can take heat out of it to run the radiator, of course, but then the problem is that it will have the effect of causing the boiler to run in bursts of full output to replenish the store. Yes, economically so. OK, you covered all the pros and cons quite comprehensively, bearing in mind I think a condensing oil boiler can only fire at the rated output, you are saying it's likely to be quite economical to let it dump a load of heat into the store and then let the rads draw it off? He may be saying that, but it isn't the case. Most condensing boilers can modulate downwards to match the heating load. If you connect a small load such as radiator space heating during spring and autumn then the boiler can modulate down and operate at lower temperatures which are more efficient for it as well as not needing to fire on and off. If you do this via a heatbank, then the boiler can never enter the lower temperature ranges and probably won't modulate down either. The technique of using a heatbank as intermediary for space heating is useful in two scenarios: - If you have a non-condensing boiler, it will provide a "smoothing" action which will reduce the amount of cycling considerably and improve its efficiency. The non-condensing boiler is designed to run at high temperature anyway. - If you have another source of heat such as solar and need to do combining of some sort. -- ..andy To email, substitute .nospam with .gl |
#15
|
|||
|
|||
On Tue, 19 Apr 2005 23:11:57 +0100, "Mike" wrote:
"Andy Hall" wrote in message .. . If you're going to fit a heat bank to get the benefit of mains pressure hot water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store If you have a condensing boiler, then it will work optimally and more efficiently at lower temperatures. Especially at this time of year and in the autumn, you can run the radiators at lower temperatures and the boiler will modulate down to match. Only if it's a modulating boiler surely. If it can only do full or nothing I'd still suggest putting the heat bank in the middle is a better option. Most new condensing boiler designs are modulating. If it isn't then there could be an advantage in putting a heatbank in the middle to reduce cycling. -- ..andy To email, substitute .nospam with .gl |
#16
|
|||
|
|||
"Andy Hall" wrote in message ... On Tue, 19 Apr 2005 22:06:49 +0100, "Jeff" wrote: "Doctor Evil" wrote in message ... You can take heat out of it to run the radiator, of course, but then the problem is that it will have the effect of causing the boiler to run in bursts of full output to replenish the store. Yes, economically so. OK, you covered all the pros and cons quite comprehensively, bearing in mind I think a condensing oil boiler can only fire at the rated output, you are saying it's likely to be quite economical to let it dump a load of heat into the store and then let the rads draw it off? He may be saying that, but it isn't the case. It is the case. Most condensing boilers can modulate downwards to match the heating load. Most cannot accurately enough. To do it properly you need a boiler can modulate down very low and have load compensation control. They are "expensive" to buy and have more to go wrong. If you do this via a heatbank, then the boiler can never enter the lower temperature ranges and probably won't modulate down either. You can have a weather compensator maintaining the bottom CH zone in the heat bank. The boiler comes in to reheat the mass of water to the settings of the compensator. Simple and effective. Cycling is vastly reduced as a mass of water cools slowly. The technique of using a heatbank as intermediary for space heating is useful in two scenarios: Let's see what wisdom we have here... - If you have a non-condensing boiler, it will provide a "smoothing" action which will reduce the amount of cycling considerably and improve its efficiency. "Eliminate" cycling with another stat. The same also applies to condensing boilers. The non-condensing boiler is designed to run at high temperature anyway. Above condensing point. They run more efficiently when a flow/return blending valve is set to maintian the return at 59C. At 11c delta T that is 70C flow temp. - If you have another source of heat such as solar and need to do combining of some sort. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#17
|
|||
|
|||
"Andy Hall" wrote in message ... On Tue, 19 Apr 2005 23:11:57 +0100, "Mike" wrote: "Andy Hall" wrote in message .. . If you're going to fit a heat bank to get the benefit of mains pressure hot water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store If you have a condensing boiler, then it will work optimally and more efficiently at lower temperatures. Especially at this time of year and in the autumn, you can run the radiators at lower temperatures and the boiler will modulate down to match. Only if it's a modulating boiler surely. If it can only do full or nothing I'd still suggest putting the heat bank in the middle is a better option. Most new condensing boiler designs are modulating. On temperature, not load. If it isn't then there could be an advantage in putting a heatbank in the middle to reduce cycling. Always an advantage. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#18
|
|||
|
|||
On Tue, 19 Apr 2005 21:55:37 +0100, "Jeff"
wrote: I should have mentioned - no gas here, I'll (or probably someone else) will be fitting a condensing oil boiler. AFAIK, they don't modulate. I think it's firing or not firing. Ah.... you didn't say that. I believe that there are modulating oil boilers on the market, but most are not. Possibly that would make me lean towards taking the rads off the heat bank, to reduce cycling. Otherwise, during not so cold weather the boiler will be oversized and cycling regularly. Would you agree? If the boiler has fixed and high output in relation to the needs of the radiators then yes. I can see the advantage there but then I think that the heat bank will get up to temperature and take the return temp up above the optimum. Pandora says the water in the store is typically 75 degrees. Bear in mind that there will be a range of temperatures from top to bottom. When you have just the radiator load, the return water temperature into the store will probably not be as low as when you are heating cold water and the return water is from the plate heat exchanger. If the rads are off the boiler, I could design the system for a suitable return temperature to try and keep it condensing. Remember that there isn't a Holy Grail that you get to when condensing begins. In reality what happens (if you think of it as a graph) is that efficiency increases with falling return temperature. Below the dew point where condensing begins, the *rate* of efficiency improvement increases. In other words at 53 degrees, it's not hugely better than at 55 degrees. To achieve maximum efficiency, you would need to arrange the temperature to be as low as possible. The problem is that the scenario for the radiators is different to that for the hot water. For the radiators, you would ideally like to let the store get almost cold and then fire up the boiler, simply because for most of the time you are using heat at a lower rate than the boiler can provide. This would result in the boiler firing up and reheating an almost cold store, which, given a fixed output boiler, is the best that you are going to get. For the hot water, you really need to have the store as fully charged for as much of the time as possible. This is because when you make a sudden large demand such as a bath, you are using heat far faster than the boiler can produce, but of course the store can keep up while its heat lasts. If you allow the store to deplete to improve boiler efficiency, then you lose the benefit of storage and the set up becomes limited to boiler ability in terms of HW flow rates. So really the two objectives don't coincide that well. I suppose that one could put more sophisticated temperature sensors and control systems around the store to detect load behaviour and (for example) fire the boiler up sooner if the temperature drop is rapid, but this is becoming complex to do and the return on investment may not be there. But then, that only applies when the system is fully loaded, and how often is that? Probably only when you are starting the store from cold or having a large Maybe I worry too much about this efficiency lark. -- ..andy To email, substitute .nospam with .gl |
#19
|
|||
|
|||
On Wed, 20 Apr 2005 00:21:50 +0100, "Doctor Evil"
wrote: "Andy Hall" wrote in message .. . On Tue, 19 Apr 2005 22:06:49 +0100, "Jeff" wrote: "Doctor Evil" wrote in message ... You can take heat out of it to run the radiator, of course, but then the problem is that it will have the effect of causing the boiler to run in bursts of full output to replenish the store. Yes, economically so. OK, you covered all the pros and cons quite comprehensively, bearing in mind I think a condensing oil boiler can only fire at the rated output, you are saying it's likely to be quite economical to let it dump a load of heat into the store and then let the rads draw it off? He may be saying that, but it isn't the case. It is the case. It depends on the type of boiler. Most condensing boilers can modulate downwards to match the heating load. Most cannot accurately enough. To do it properly you need a boiler can modulate down very low and have load compensation control. They are "expensive" to buy and have more to go wrong. "Accurately" is not an appropriate way to describe it. It is true that some boilers are able to modulate over a greater range than others, but that has to do with a number of factors. There are now some relatively inexpensive ones able to cover a very wide range and drop down to below 5kW. It's a complete nonsense to suggest that a boiler with load compensation control has more to go wrong than one without. There is an additional temperature sensor outside and a more sophisticated control algorithm used in the controller electronics. this does not imply that there is more to go wrong. If you do this via a heatbank, then the boiler can never enter the lower temperature ranges and probably won't modulate down either. You can have a weather compensator maintaining the bottom CH zone in the heat bank. The boiler comes in to reheat the mass of water to the settings of the compensator. Simple and effective. Cycling is vastly reduced as a mass of water cools slowly. You can, but it is still at variance to the required behaviour from the store when heating the DHW. One doesn't really want the behaviour of the hot water heating to change with the weather. The technique of using a heatbank as intermediary for space heating is useful in two scenarios: Let's see what wisdom we have here... - If you have a non-condensing boiler, it will provide a "smoothing" action which will reduce the amount of cycling considerably and improve its efficiency. "Eliminate" cycling with another stat. The same also applies to condensing boilers. ????? The non-condensing boiler is designed to run at high temperature anyway. Above condensing point. They run more efficiently when a flow/return blending valve is set to maintian the return at 59C. At 11c delta T that is 70C flow temp. ????? - If you have another source of heat such as solar and need to do combining of some sort. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account -- ..andy To email, substitute .nospam with .gl |
#20
|
|||
|
|||
Jeff wrote:
I should have mentioned - no gas here, I'll (or probably someone else) will be fitting a condensing oil boiler. AFAIK, they don't modulate. I think it's firing or not firing. Possibly that would make me lean towards taking the rads off the heat bank, to reduce cycling. Otherwise, during not so cold weather the boiler will be oversized and cycling regularly. Would you agree? I can see the advantage Yup if you don't have the modulation then you are back to cycling to achieve less than the max effective output. So being able to consume the maximum output in big lumps (i.e. with a store is better) Many oil fired boilers are fixed output, although you can get some modulating ones. Often the modulation range is not as wide as with gas though. Misteral seem to do quite a number. Grab a copy of the free SEDBUK database of boilers from SDA he http://www.sda.co.uk/qsedbuk.htm If the rads are off the boiler, I could design the system for a suitable return temperature to try and keep it condensing. But then, that only applies when the system is fully loaded, and how often is that? It is unlikely to ever be fully loaded on heating alone. HW water is the place you can sink big outputs in a short amount of time. Remember however that efficiency is better when condensing, but it is not a magic bullet - if you stop condensing there is not a big step change. The condensing boiler will still be more efficient that its conventional sibling simply by virtue of its better heat exchanger design. Maybe I worry too much about this efficiency lark. Possibly, I would focus more efforts on getting the type of system performance you want first, and then the best economy within those parameters second. Otherwise you will always be a bit dissatisfied with the system, and knowing that "at least it is as cheap to run as possible" may not offer much consolation. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#21
|
|||
|
|||
"Andy Hall" wrote in message ... SNIP He may be saying that, but it isn't the case. Most condensing boilers can modulate downwards to match the heating load. If you connect a small load such as radiator space heating during spring and autumn then the boiler can modulate down and operate at lower temperatures which are more efficient for it as well as not needing to fire on and off. Andy Whilst the principles of your argument regarding the system are correct it is not the case that the OPs intended "oil" fired condensing boiler can modulate. To maintain good (efficient) combustion with small oil burners it is neccessary to closely match the oil rate and atomisation through the nozzle with the airflow rate. The economics and the practicalities are such that turning up or down the oil rate will require adjustment of either the oil nozzle hole size or oil pressure. The oil nozzle is a precision bored unit and is effectively non adjustable. The alteration of the oil pressure leads to alteration of the quality of atomisation. Again, alteration of the airflow requires some considerable additional hardware and controls i.e. servo operated air damper or fan speed but the fan is invariably mounted on the same motor shaft as the oil pump (gear type). On some larger (intermediate) oil burners a step modulation is employed by installing twin nozzles in the burner head and a two stage (solenoid operated hydraulic ram positioner) air shutter but these are only found in burners of 100kW and above. I have seen only one progressively modulating oil burner (serving a very large office building and made IIRC by Veissman) but as it was so unusual out in the field I would anticipate its cost was prohibitive. These problems are most likely behind the reasoning to not require condensing boiler installation for oil until 2007 at the present state of affairs? |
#22
|
|||
|
|||
"John" wrote in message ... These problems are most likely behind the reasoning to not require condensing boiler installation for oil until 2007 at the present state of affairs? I think more likely was the fact that almost every oil boiler on the market is 85% efficient so the 86% requirment of part L was a little silly. Non-condensing gas boilers are more inefficient for reasons I'm sure somebody here can explain. |
#23
|
|||
|
|||
This has been very interesting and helpful, thanks all contributors.
Trying to sort out the consistent themes and the most appropriate for me I'm coming to the following conclusions: (From the other thread) I don't need a bypass valve of any sort as long as I have a water path at all times when pumping but I do need a zone with time and temp control per 150 m2 max. 'Bypass' rads to have 2 lockshields. An oil condensing boiler does not have the efficiency benefit over a standard one, in comparison with gas models, and is also likely to be much more expensive (checked out the efficiency on SEDBUK site) A heat bank will usefully buffer the boiler output including for the rad circuits particularly so for a non-condenser. A two-stat model will further reduce cycling. So I'm thinking I'll design for the 'normal' or higher temperature range of boiler output, meaning I won't feel compelled to have slightly larger rads (cost saving), I won't have to specify a condensing boiler so since I'll probably be using an installer for the boiler and tank I should get quotations competitivie with the installer's favoured models. Now, how to size the boiler. Calculated heat loss over 2 floors plus a bit for utility areas is around 29kW but it's unlikely we would ever want every room up to design temperature. It's an old and poorly insulated property but I'm hoping to significantly improve the main living rooms to a high standard. No modulation, should I keep the boiler rating on the low side or should I allow for the heat bank dhw load in addition? "Jeff" wrote in message ... If you're going to fit a heat bank to get the benefit of mains pressure hot water, no tanks, etc. etc., what are the pros and cons of heating the radiators from either the store with the necessary coil and pump or directly from the condensing boiler? I'm wondering if I should just treat the heat bank as a cylinder and connect the rad circuit(s) directly via a zone valve or to feed them from the store I have this suspicion that if you buffer the radiators via a heat bank you may lose some of the benefit of a condensing boiler since the return temperature will be greater than if you designed the system for radiators, opting for a lower than usual return. Yes, I know it means departing from BS, having bigger rads, adjusting for mean temperature etc. but so what if it achieves the desired effect ? I bet this has been discussed before but I'm taking the easy option |
#24
|
|||
|
|||
"Jeff" wrote in message ... This has been very interesting and helpful, thanks all contributors. Trying to sort out the consistent themes and the most appropriate for me I'm coming to the following conclusions: (From the other thread) I don't need a bypass valve of any sort as long as I have a water path at all times when pumping but I do need a zone with time and temp control per 150 m2 max. 'Bypass' rads to have 2 lockshields. An oil condensing boiler does not have the efficiency benefit over a standard one, in comparison with gas models, and is also likely to be much more expensive (checked out the efficiency on SEDBUK site) There is an efficiency gain by using a condensing boiler but it becomes less as the load modulates down and the boiler doesn't. You imply you have looked at pricing so I guess you have made the decision? A heat bank will usefully buffer the boiler output including for the rad circuits particularly so for a non-condenser. A two-stat model will further reduce cycling. So I'm thinking I'll design for the 'normal' or higher temperature range of boiler output, meaning I won't feel compelled to have slightly larger rads (cost saving), I won't have to specify a condensing boiler so since I'll probably be using an installer for the boiler and tank I should get quotations competitivie with the installer's favoured models. Personally I would oversize in line with a future swap to condensing and use TRVs for room comfort. In terms of which model of boiler I have a distinct penchant for Firebird non- condensing units. They have a very good build quality and an economic price. The burners Firebird use can vary but I suggest you specify Riello RDB (which is the usual model that comes with the boiler). The boiler is available for balanced flue operation (about under-worktop height) and/or conventional flueing. Both kitchen (white cased) and boilerhouse models are available Now, how to size the boiler. Calculated heat loss over 2 floors plus a bit for utility areas is around 29kW but it's unlikely we would ever want every room up to design temperature. It's an old and poorly insulated property but I'm hoping to significantly improve the main living rooms to a high standard. No modulation, should I keep the boiler rating on the low side or should I allow for the heat bank dhw load in addition? Allow for everything being on-line unless you are absolutely, definitely, certain about not wanting all on at some stage in the future. Also make sure your oil storage facility complies with OFTEC and Environment regulations. |
#25
|
|||
|
|||
"John" wrote in message ... An oil condensing boiler does not have the efficiency benefit over a standard one, in comparison with gas models, and is also likely to be much more expensive (checked out the efficiency on SEDBUK site) There is an efficiency gain by using a condensing boiler but it becomes less as the load modulates down and the boiler doesn't. You imply you have looked at pricing so I guess you have made the decision? No, I haven't looked at pricing or made a decision yet - I could still go either way. I don't have a nominated installer - my feeling was that if I ask for quotations for a specific output of *any* or a small option list of boilers I am likely to get a keener quotation; in my experience once you start asking a given supplier for something that isn't on their 'preferred' stock list it can work aginst you. Of course, I'll be examining what is offered and making any necessary mental adjustments for perceived differences in quality/list price. Or, I could source the boiler myself and see if I can get someone to fit it. Or, fit it myself, but what certification would I need and will someone actually certify my installation? I've never fitted an oil boiler or the associated tank and supply lines. A heat bank will usefully buffer the boiler output including for the rad circuits particularly so for a non-condenser. A two-stat model will further reduce cycling. So I'm thinking I'll design for the 'normal' or higher temperature range of boiler output, meaning I won't feel compelled to have slightly larger rads (cost saving), I won't have to specify a condensing boiler so since I'll probably be using an installer for the boiler and tank I should get quotations competitivie with the installer's favoured models. Personally I would oversize in line with a future swap to condensing and use TRVs for room comfort. In terms of which model of boiler I have a distinct penchant for Firebird non- condensing units. They have a very good build quality and an economic price. The burners Firebird use can vary but I suggest you specify Riello RDB (which is the usual model that comes with the boiler). The boiler is available for balanced flue operation (about under-worktop height) and/or conventional flueing. Both kitchen (white cased) and boilerhouse models are available You mean oversize the rads anyway on the basis the next boiler change will be condensing? I could do this. If so, I would adjust the rad size for the reduced mean temperature if I changed to condensing per the manufacturers' tables. Now, how to size the boiler. Calculated heat loss over 2 floors plus a bit for utility areas is around 29kW but it's unlikely we would ever want every room up to design temperature. It's an old and poorly insulated property but I'm hoping to significantly improve the main living rooms to a high standard. No modulation, should I keep the boiler rating on the low side or should I allow for the heat bank dhw load in addition? Allow for everything being on-line unless you are absolutely, definitely, certain about not wanting all on at some stage in the future. Also make sure your oil storage facility complies with OFTEC and Environment regulations. So would it be say 29kW plus say 6kW (notional guess) for dhw and aim for a 35kW model? |
#26
|
|||
|
|||
In article ,
"John" writes: Allow for everything being on-line unless you are absolutely, definitely, certain about not wanting all on at some stage in the future. If you are zoning with a view to not always having all the heating on (whether by simple use of radiator valves, or by use of multiple heating circuits and zoning valves), remember when doing your heat loss calculations that an adjacent room (sideways, above or below) might be cold, or you'll find you can't get a room up to temperature without all those around it also being heated, defeating the object of what you're aiming to do. (Heating just parts of a house can cause other problems too, such as condensation.) Also, you need some headroom in the boiler output to heat a place up from cold without it taking ages to do so. -- Andrew Gabriel |
#27
|
|||
|
|||
"Jeff" wrote in message ... This has been very interesting and helpful, thanks all contributors. Trying to sort out the consistent themes and the most appropriate for me I'm coming to the following conclusions: (From the other thread) I don't need a bypass valve of any sort as long as I have a water path at all times when pumping but I do need a zone with time and temp control per 150 m2 max. 'Bypass' rads to have 2 lockshields. You can use a Grundfoss Alpha modulating pumps and TRVs on all rads. take CH off heat bank. Over 150 m2 it requires to be split into zones with time control. If you are zoning have the flow and return of each zone off the heat bank. They then will be totally independent of each other coming off a neutral point. Then no zone valves, just a couple of Alpha pumps on each zone. An oil condensing boiler does not have the efficiency benefit over a standard one, in comparison with gas models, and is also likely to be much more expensive (checked out the efficiency on SEDBUK site) Yep. A heat bank will usefully buffer the boiler output including for the rad circuits particularly so for a non-condenser. A two-stat model will further reduce cycling. Yep. So I'm thinking I'll design for the 'normal' or higher temperature range of boiler output, meaning I won't feel compelled to have slightly larger rads (cost saving), I won't have to specify a condensing boiler so since I'll probably be using an installer for the boiler and tank I should get quotations competitivie with the installer's favoured models. Now, how to size the boiler. Calculated heat loss over 2 floors plus a bit for utility areas is around 29kW but it's unlikely we would ever want every room up to design temperature. It's an old and poorly insulated property but I'm hoping to significantly improve the main living rooms to a high standard. No modulation, should I keep the boiler rating on the low side or should I allow for the heat bank dhw load in addition? If the boiler is connected directly to the heat bank, not via a coil, then, as long as the flow and return pipes are sized properly, minimum 28mm, you can have a very large boiler. Size doesn't matter as the boiler is disconnected from the DHW and CH functions. The larger the boiler the quicker the re-heat and still no cycling. Some larger boilers are cheaper than smaller models because of volume sales. This is certainly the case with gas boilers. If your house is very large, then it may be worth your while having two smaller boilers heat the heat bank. The beauty of a heat bank is that boilers can independently heat with their own flow and return from the heat bank. Then you have back up if one is down. The two re-heat pretty quickly and no cycling. Price up two boilers, you may be pleasantly surprised. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#28
|
|||
|
|||
"Jeff" wrote in message ... "Doctor Evil" wrote in message ... You can take heat out of it to run the radiator, of course, but then the problem is that it will have the effect of causing the boiler to run in bursts of full output to replenish the store. Yes, economically so. OK, you covered all the pros and cons quite comprehensively, bearing in mind I think a condensing oil boiler can only fire at the rated output, you are saying it's likely to be quite economical to let it dump a load of heat into the store and then let the rads draw it off? Yep. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#29
|
|||
|
|||
"Andy Hall" wrote in message ... If you do this via a heatbank, then the boiler can never enter the lower temperature ranges and probably won't modulate down either. You can have a weather compensator maintaining the bottom CH zone in the heat bank. The boiler comes in to reheat the mass of water to the settings of the compensator. Simple and effective. Cycling is vastly reduced as a mass of water cools slowly. You can, but it is still at variance to the required behaviour from the store when heating the DHW. One doesn't really want the behaviour of the hot water heating to change with the weather. Read what I wrote. The bottom CH zone. This will be at a different temperature to the hotter upper DHW zone. The DHW zone is priority in that if it calls for heat, say 75-80C then the boiler only sends heat to that upper zone. then it reverts to weather compensator control of the lower CH zone. All the same body of water. The technique of using a heatbank as intermediary for space heating is useful in two scenarios: Let's see what wisdom we have here... - If you have a non-condensing boiler, it will provide a "smoothing" action which will reduce the amount of cycling considerably and improve its efficiency. "Eliminate" cycling with another stat. The same also applies to condensing boilers. ????? Quite clear. The non-condensing boiler is designed to run at high temperature anyway. Above condensing point. They run more efficiently when a flow/return blending valve is set to maintian the return at 59C. At 11c delta T that is 70C flow temp. ????? Quite clear. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#30
|
|||
|
|||
"Jeff" wrote in message ... This has been very interesting and helpful, thanks all contributors. Trying to sort out the consistent themes and the most appropriate for me I'm coming to the following conclusions: (From the other thread) I don't need a bypass valve of any sort as long as I have a water path at all times when pumping but I do need a zone with time and temp control per 150 m2 max. 'Bypass' rads to have 2 lockshields. An oil condensing boiler does not have the efficiency benefit over a standard one, in comparison with gas models, and is also likely to be much more expensive (checked out the efficiency on SEDBUK site) A heat bank will usefully buffer the boiler output including for the rad circuits particularly so for a non-condenser. A two-stat model will further reduce cycling. So I'm thinking I'll design for the 'normal' or higher temperature range of boiler output, meaning I won't feel compelled to have slightly larger rads (cost saving), I won't have to specify a condensing boiler so since I'll probably be using an installer for the boiler and tank I should get quotations competitivie with the installer's favoured models. Now, how to size the boiler. Calculated heat loss over 2 floors plus a bit for utility areas is around 29kW but it's unlikely we would ever want every room up to design temperature. It's an old and poorly insulated property but I'm hoping to significantly improve the main living rooms to a high standard. No modulation, should I keep the boiler rating on the low side or should I allow for the heat bank dhw load in addition? I'd go for one with the Riello RDB 90 burner - Grant Euroflame boiler house is the one I chose - which can be easily jetted down if you find you need less poke. As you say, with a non-condensing oil boiler you can run the radiators hotter and so have smaller sizes. This is especially useful in older houses where the easiest place to put the rad isn't always the biggest. And as you say - insulate. Then insulate some more. From the calculations our house as we bought it was unheatable - unless we bought a commercial boiler anyway - whereas several lorryloads of Kingspan/Celotex later we used under 1000 litres this winter. |
#31
|
|||
|
|||
"Doctor Evil" wrote in message ... ...... If your house is very large, then it may be worth your while having two smaller boilers heat the heat bank. You were doing well until this. Remember it's oil, not gas. Oil boilers get better with size. Small ones are inefficient, big ones are much better. And really big ones can put out serious amounts of poke efficiently if you have something like a heat bank to actually take the energy and store it for later use. |
#32
|
|||
|
|||
"Mike" wrote in message ... "Jeff" wrote in message ... This has been very interesting and helpful, thanks all contributors. Trying to sort out the consistent themes and the most appropriate for me I'm coming to the following conclusions: (From the other thread) I don't need a bypass valve of any sort as long as I have a water path at all times when pumping but I do need a zone with time and temp control per 150 m2 max. 'Bypass' rads to have 2 lockshields. An oil condensing boiler does not have the efficiency benefit over a standard one, in comparison with gas models, and is also likely to be much more expensive (checked out the efficiency on SEDBUK site) A heat bank will usefully buffer the boiler output including for the rad circuits particularly so for a non-condenser. A two-stat model will further reduce cycling. So I'm thinking I'll design for the 'normal' or higher temperature range of boiler output, meaning I won't feel compelled to have slightly larger rads (cost saving), I won't have to specify a condensing boiler so since I'll probably be using an installer for the boiler and tank I should get quotations competitivie with the installer's favoured models. Now, how to size the boiler. Calculated heat loss over 2 floors plus a bit for utility areas is around 29kW but it's unlikely we would ever want every room up to design temperature. It's an old and poorly insulated property but I'm hoping to significantly improve the main living rooms to a high standard. No modulation, should I keep the boiler rating on the low side or should I allow for the heat bank dhw load in addition? I'd go for one with the Riello RDB 90 burner - Grant Euroflame boiler house is the one I chose - which can be easily jetted down if you find you need less poke. Coupling the boiler "directly" to a heat bank, the size doesn't matter. You can't oversize a boiler, as long as the flow and return pipes are sized up properly, You can oversize a boiler if it is coupled directly onto a rad circuit; it will cycle far too much, be inefficient and wear out the controls pronto. As you say, with a non-condensing oil boiler you can run the radiators hotter and so have smaller sizes. This is especially useful in older houses where the easiest place to put the rad isn't always the biggest. And as you say - insulate. Then insulate some more. From the calculations our house as we bought it was unheatable - unless we bought a commercial boiler anyway - whereas several lorryloads of Kingspan/Celotex later we used under 1000 litres this winter. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#33
|
|||
|
|||
"Mike" wrote in message ... "Doctor Evil" wrote in message ... ..... If your house is very large, then it may be worth your while having two smaller boilers heat the heat bank. You were doing well until this. As I know more about this field than anyone here and I aways do well. I don't know the size of his house. He could get a better deal with two boilers (buy two at a discount) than buying one big one. I know one v country large house had a large Viessmann installed. It broke down, occasionally they do. the whole place was freezing until repaired. They Viessmann because it was the best and reliable, etc. Two mid priced boilers would have been a far better way. Remember it's oil, not gas. Oil boilers get better with size. Small ones are inefficient, big ones are much better. And really big ones can put out serious amounts of poke efficiently if you have something like a heat bank to actually take the energy and store it for later use. Look at sedbuk. You will find that is not the case in small v large = efficiency. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
#34
|
|||
|
|||
On Wed, 20 Apr 2005 07:46:48 +0000 (UTC), "John"
wrote: "Andy Hall" wrote in message .. . SNIP He may be saying that, but it isn't the case. Most condensing boilers can modulate downwards to match the heating load. If you connect a small load such as radiator space heating during spring and autumn then the boiler can modulate down and operate at lower temperatures which are more efficient for it as well as not needing to fire on and off. Andy Whilst the principles of your argument regarding the system are correct it is not the case that the OPs intended "oil" fired condensing boiler can modulate. To maintain good (efficient) combustion with small oil burners it is neccessary to closely match the oil rate and atomisation through the nozzle with the airflow rate. The economics and the practicalities are such that turning up or down the oil rate will require adjustment of either the oil nozzle hole size or oil pressure. The oil nozzle is a precision bored unit and is effectively non adjustable. The alteration of the oil pressure leads to alteration of the quality of atomisation. Again, alteration of the airflow requires some considerable additional hardware and controls i.e. servo operated air damper or fan speed but the fan is invariably mounted on the same motor shaft as the oil pump (gear type). On some larger (intermediate) oil burners a step modulation is employed by installing twin nozzles in the burner head and a two stage (solenoid operated hydraulic ram positioner) air shutter but these are only found in burners of 100kW and above. I have seen only one progressively modulating oil burner (serving a very large office building and made IIRC by Veissman) but as it was so unusual out in the field I would anticipate its cost was prohibitive. These problems are most likely behind the reasoning to not require condensing boiler installation for oil until 2007 at the present state of affairs? Point taken. In the first post we didn't know that it was oil or that it was (probably by implication) non modulating, though, John. -- ..andy To email, substitute .nospam with .gl |
#35
|
|||
|
|||
On Wed, 20 Apr 2005 12:09:13 +0100, "Doctor Evil"
wrote: "Andy Hall" wrote in message .. . If you do this via a heatbank, then the boiler can never enter the lower temperature ranges and probably won't modulate down either. You can have a weather compensator maintaining the bottom CH zone in the heat bank. The boiler comes in to reheat the mass of water to the settings of the compensator. Simple and effective. Cycling is vastly reduced as a mass of water cools slowly. You can, but it is still at variance to the required behaviour from the store when heating the DHW. One doesn't really want the behaviour of the hot water heating to change with the weather. Read what I wrote. The bottom CH zone. This will be at a different temperature to the hotter upper DHW zone. The DHW zone is priority in that if it calls for heat, say 75-80C then the boiler only sends heat to that upper zone. then it reverts to weather compensator control of the lower CH zone. All the same body of water. This sounds like waffle. Are you suggesting thermostats on different heights on the cylinder, or more than one indirect coil or what? The technique of using a heatbank as intermediary for space heating is useful in two scenarios: Let's see what wisdom we have here... - If you have a non-condensing boiler, it will provide a "smoothing" action which will reduce the amount of cycling considerably and improve its efficiency. "Eliminate" cycling with another stat. The same also applies to condensing boilers. ????? Quite clear. Come on, it's waffle and you know it. The non-condensing boiler is designed to run at high temperature anyway. Above condensing point. They run more efficiently when a flow/return blending valve is set to maintian the return at 59C. At 11c delta T that is 70C flow temp. ????? Quite clear. 70-59 = 11 is clear, as is 59 degrees being above the dew point. However, what was the point that you were trying to make? -- ..andy To email, substitute .nospam with .gl |
#36
|
|||
|
|||
"Doctor Evil" wrote in message ... Remember it's oil, not gas. Oil boilers get better with size. Small ones are inefficient, big ones are much better. And really big ones can put out serious amounts of poke efficiently if you have something like a heat bank to actually take the energy and store it for later use. Look at sedbuk. You will find that is not the case in small v large = efficiency. That's a somewhat biased test I'm afraid. Bit like urban mpg figures for cars. In real life a bigger oil boiler operating for a shorter time will always be more efficient. |
#37
|
|||
|
|||
"Mike" wrote in message ... "Doctor Evil" wrote in message ... Remember it's oil, not gas. Oil boilers get better with size. Small ones are inefficient, big ones are much better. And really big ones can put out serious amounts of poke efficiently if you have something like a heat bank to actually take the energy and store it for later use. Look at sedbuk. You will find that is not the case in small v large = efficiency. That's a somewhat biased test I'm afraid. Bit like urban mpg figures for cars. In real life a bigger oil boiler operating for a shorter time will always be more efficient. I would have agreed with you 20 years ago. _________________________________________ Usenet Zone Free Binaries Usenet Server More than 120,000 groups Unlimited download http://www.usenetzone.com to open account |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
AquaTherm Furnace - No Hot Water Issue | Home Repair | |||
Evaporative cooler question | Home Repair | |||
heat pump/secondary propane furnace questions | Home Ownership | |||
Contemplating unvented Indirect hot water upgrade | UK diy | |||
Central heating bypass circuit | UK diy |