My recent question about problems with my boiler got very knowledgeable
replies (problem now sorted). So now I have another question (google
doesn't get me a clear answer):

I have bought a Wylex 63A 30mA RCD fom Screwfix (wylex shower unit,
product code 90026) to use for my new electric shower. It is not clear
to me how to wire this thing. It sits in its own box, and I imagined I
would put it close to the consumer unit, in the 10mm cable coming from
the CU and going to the shower.

The RCD has 4 connectors, one marked L at the top left hand side, the
others unmarked. The enclosed leaflet says 'The incoming cables to the
RCD may be taken either to the top or the bottom set of terminals,
dependent entirely on the ease of wiring the device'.

That could be read to mean that only 2 out of 4 terminals are used (that
must surely be wrong). As it has 4 terminals, I guess the live in and
out go to the one marked 'L' and the one below that, the neutrals go to
the other 2. What happens to the earth? Do I connect that using a
connector block?

Hope all this makes sense,

Johan
  #2   Report Post  
John Stumbles
 
Posts: n/a
Default

Johan wrote:


My recent question about problems with my boiler got very knowledgeable
replies (problem now sorted). So now I have another question (google
doesn't get me a clear answer):

I have bought a Wylex 63A 30mA RCD fom Screwfix (wylex shower unit,
product code 90026) to use for my new electric shower. It is not clear
to me how to wire this thing. It sits in its own box, and I imagined I
would put it close to the consumer unit, in the 10mm cable coming from
the CU and going to the shower.


It could do but that's not how it's supposed to be installed: it should be
wired as a mini Consumer Unit with its own feed from the meter in parallel
with that to the main CU. You'd use a Henley block to split the meter
tails, and remove the main incoming fuse to isolate the supply while
working unless you hav a meter with an isolating switch.


The RCD has 4 connectors, one marked L at the top left hand side, the
others unmarked. The enclosed leaflet says 'The incoming cables to the
RCD may be taken either to the top or the bottom set of terminals,
dependent entirely on the ease of wiring the device'.

That could be read to mean that only 2 out of 4 terminals are used (that
must surely be wrong).


Yes, that's wrong

As it has 4 terminals, I guess the live in and
out go to the one marked 'L' and the one below that, the neutrals go to
the other 2.


Yup, incoming L & N to top, outgoing to bottom - or vice versa.
Incoming from meter via Henley block
Outgoing N to load
Outgoing L from RCD to MCB, from there to load

What happens to the earth? Do I connect that using a
connector block?


Yes, there should be a 4 way nickel-plated brass terminal block near meter
which you connect in to. If Earths are all connected to sheath clamp on
incoming cable I'd reconnect to a terminal block (you can get 8-way ones
which are handy since sod's law says you'll need 5 ways if you have a 4-way
block). Again reconnect with incoming power off. You should really check
earth loop resistance (and trip time on your RCD) after doing all this but
you need sparkies' test kit for this.

  #3   Report Post  
Johan
 
Posts: n/a
Default

John Stumbles wrote:

Johan wrote:


My recent question about problems with my boiler got very knowledgeable
replies (problem now sorted). So now I have another question (google
doesn't get me a clear answer):

I have bought a Wylex 63A 30mA RCD fom Screwfix (wylex shower unit,
product code 90026) to use for my new electric shower. It is not clear
to me how to wire this thing. It sits in its own box, and I imagined I
would put it close to the consumer unit, in the 10mm cable coming from
the CU and going to the shower.



It could do but that's not how it's supposed to be installed: it should be
wired as a mini Consumer Unit with its own feed from the meter in parallel
with that to the main CU. You'd use a Henley block to split the meter
tails, and remove the main incoming fuse to isolate the supply while
working unless you hav a meter with an isolating switch.


But then it wouldn't be protected by an MCB. Is what you describe not
what is supposed to be done with a MCB/RCD unit? What I bought is only
an RCD.




The RCD has 4 connectors, one marked L at the top left hand side, the
others unmarked. The enclosed leaflet says 'The incoming cables to the
RCD may be taken either to the top or the bottom set of terminals,
dependent entirely on the ease of wiring the device'.

That could be read to mean that only 2 out of 4 terminals are used (that
must surely be wrong).



Yes, that's wrong


As it has 4 terminals, I guess the live in and
out go to the one marked 'L' and the one below that, the neutrals go to
the other 2.



Yup, incoming L & N to top, outgoing to bottom - or vice versa.
Incoming from meter via Henley block
Outgoing N to load
Outgoing L from RCD to MCB, from there to load


What happens to the earth? Do I connect that using a
connector block?



Yes, there should be a 4 way nickel-plated brass terminal block near meter
which you connect in to. If Earths are all connected to sheath clamp on
incoming cable I'd reconnect to a terminal block (you can get 8-way ones
which are handy since sod's law says you'll need 5 ways if you have a 4-way
block). Again reconnect with incoming power off. You should really check
earth loop resistance (and trip time on your RCD) after doing all this but
you need sparkies' test kit for this.


I intend to get it all checked over by a sparkie when I have finished
all the wiring.
  #4   Report Post  
 
Posts: n/a
Default

Johan wrote:

I intend to get it all checked over by a sparkie when I have finished


all the wiring.


I dont mean to be funny, but if your knowledge is so lacking, what on
earth are you thinking wiring your shower up.

You might dislike me or take offense, but then again you might survive
to be able to take offence!

Why not just run the 10mm and let the spark connect it all up etc,
including equipotential bonding. You probably dont even know what that
is.


NT

  #5   Report Post  
John Stumbles
 
Posts: n/a
Default

Johan wrote:

John Stumbles wrote:

Johan wrote:


I have bought a Wylex 63A 30mA RCD fom Screwfix (wylex shower unit,
product code 90026) to use for my new electric shower. It is not clear
to me how to wire this thing. It sits in its own box, and I imagined I
would put it close to the consumer unit, in the 10mm cable coming from
the CU and going to the shower.



It could do but that's not how it's supposed to be installed: it should
be wired as a mini Consumer Unit with its own feed from the meter in
parallel with that to the main CU. You'd use a Henley block to split the
meter tails, and remove the main incoming fuse to isolate the supply
while working unless you hav a meter with an isolating switch.


But then it wouldn't be protected by an MCB. Is what you describe not
what is supposed to be done with a MCB/RCD unit? What I bought is only
an RCD.



Sorry, I didn't (CBA to) look up the product you gave the code for so when
you said 'shower unit' I just assumed you meant an RCD and an MCB in one
box like this
http://www.screwfix.com/app/sfd/cat/pro.jsp?id=69659

Was there a particular reason to spend £13 more on just the RCD rather than
the combined unit? :-)

I intend to get it all checked over by a sparkie when I have finished
all the wiring.


Do you have a sparks lined up for this? If so could you get him to look over
the installation and bits & bobs you've got and agree what bits he'll do
and what he's happy to have you do?



  #6   Report Post  
Johan
 
Posts: n/a
Default

wrote:
Johan wrote:


I intend to get it all checked over by a sparkie when I have finished



all the wiring.



I dont mean to be funny, but if your knowledge is so lacking, what on
earth are you thinking wiring your shower up.


What makes you think that my intention to get things checked over is
anything to do with lack of knowledge (nothing wrong with asking the
question, but I don't see your logic)? I have read the IEE on-site guide
and lots of stuff on the web, and think I know what the regulations
say. The shower wiring is part of a lot of other wiring to do with an
extension we had built. I want to get an electrician to check things
like the earthing (which I don't have the equipment for) and to get a
certificate. Overly careful? Waste of money? Worth it for my peace of
mind, I think.

Anyway, as there is no legal way to switch off the supply before the
consumer unit, I decided to make sure the shower had its own RCD (CU
only has an RCD for the garage/workshop, no space for another one).
Never used one of these, and want to make absolutely sure I use it as
intended. Perhaps my initial post wasn't phrased very well.


You might dislike me or take offense, but then again you might survive
to be able to take offence!


Absolutely!

Why not just run the 10mm and let the spark connect it all up etc,
including equipotential bonding. You probably dont even know what that
is.


Thankfully I do. Then again, all the new plumbing is in speedfit (Yes, I
have read all the 'dicussions' about that on uk.d-i-y as well ;-)




NT

  #7   Report Post  
Andy Wade
 
Posts: n/a
Default

Johann wrote:

What makes you think that my intention to get things checked over is
anything to do with lack of knowledge [...]


Most of your original article actually.

Anyway, as there is no legal way to switch off the supply before the
consumer unit, I decided to make sure the shower had its own RCD


That's a non-sequitur. What has the inability (or otherwise) to isolate
the supply to the CU go to do with the need for the shower to have its
own RCD?

Point 1: there is a legal way to isolate the supply to the CU and that's
to ask via your supplier to have the main fuse withdrawn.

Point 2: why do you think the shower circuit needs to be RCD protected?

Point 3: what device will be providing overcurrent protection in your
proposed wiring scheme?

--
Andy
  #8   Report Post  
Johan
 
Posts: n/a
Default

Andy Wade wrote:

Johann wrote:

What makes you think that my intention to get things checked over is
anything to do with lack of knowledge [...]



Most of your original article actually.

Anyway, as there is no legal way to switch off the supply before the
consumer unit, I decided to make sure the shower had its own RCD



That's a non-sequitur. What has the inability (or otherwise) to isolate
the supply to the CU go to do with the need for the shower to have its
own RCD?

Point 1: there is a legal way to isolate the supply to the CU and that's
to ask via your supplier to have the main fuse withdrawn.

Point 2: why do you think the shower circuit needs to be RCD protected?

Point 3: what device will be providing overcurrent protection in your
proposed wiring scheme?


I've clearly got myself into a mess here. I've been far too inaccurate
in what I wrote. And of course it is possible I have misunderstood
something fundamental here. Let me try to clarify again:

- My CU has one MCB/RCD for the garage, no split load or other RCD
provision; no more space for an MCB/RCD that takes up the space of 2
MCBs. I suppose I could have got a RCBO that takes one module/way.

- Non-sequitur indeed. I was partly replying to someone else's post who
mentioned using a Henley block after the meter/before the CU and an
MCB/RCD unit for the shower. That would have required to get the supply
switched off (at least I realised that ;-) Obviously one can ask the
supplier. Wanted to avoid the hassle.

- The MCB in the CU does the overcurrent protection, surely? My idea was
to go CU (MCB) - RCD - shower. I must admit that I bought the RCD as
part of a larger order from screwfix without being 100% sure what the
connections would be like. Having considered the separate MCD/RCD unit
and the option of putting an RCBO in the CU, I assumed that the
availability of a separate RCD unit implied this was another way of
dealing with this. Hence my original question.

So to summarise again: I would like my shower to be protected by an RCD,
I have considered the options, bought a separate RCD and would love to
know how these things are wired in.
  #9   Report Post  
Johan
 
Posts: n/a
Default

John Stumbles wrote:

snip



Sorry, I didn't (CBA to) look up the product you gave the code for so when
you said 'shower unit' I just assumed you meant an RCD and an MCB in one
box like this
http://www.screwfix.com/app/sfd/cat/pro.jsp?id=69659

Was there a particular reason to spend £13 more on just the RCD rather than
the combined unit? :-)


See my other replies.


I intend to get it all checked over by a sparkie when I have finished
all the wiring.



Do you have a sparks lined up for this?


Not yet

If so could you get him to look over
the installation and bits & bobs you've got and agree what bits he'll do
and what he's happy to have you do?

  #11   Report Post  
Dave Plowman (News)
 
Posts: n/a
Default

In article ,
Johan wrote:
I have bought a Wylex 63A 30mA RCD fom Screwfix (wylex shower unit,
product code 90026) to use for my new electric shower. It is not clear
to me how to wire this thing. It sits in its own box, and I imagined I
would put it close to the consumer unit, in the 10mm cable coming from
the CU and going to the shower.


The RCD has 4 connectors, one marked L at the top left hand side, the
others unmarked. The enclosed leaflet says 'The incoming cables to the
RCD may be taken either to the top or the bottom set of terminals,
dependent entirely on the ease of wiring the device'.


Sounds pretty clear to me.

That could be read to mean that only 2 out of 4 terminals are used (that
must surely be wrong).


Well, yes, you are wrong. An RCD needs both line and neutral to work
unlike an MCB which is just in the line.

As it has 4 terminals, I guess the live in and
out go to the one marked 'L' and the one below that, the neutrals go to
the other 2. What happens to the earth? Do I connect that using a
connector block?


No. Feed to one pair of terminals - either top or bottom - and load to the
other pair. If there's also an MCB, the load line should go to that with a
link between the MCB and RCD. Although I'd have expected this to be
pre-wired. I'd also expect an earth bus bar.


Something like this:-


Feed
L N
| |
| |
| |
------------
| L |
| |
| RCD |
------------
| |
L| |N
| |
-------- |
| | |
| MCB | |
| | |
-------- |
| |
| |
L N
to shower

--
*Middle age is when it takes longer to rest than to get tired.

Dave Plowman London SW
To e-mail, change noise into sound.
  #12   Report Post  
Johan
 
Posts: n/a
Default

wrote:

Johan wrote:

wrote:



I intend to get it all checked over by a sparkie when I have


finished

all the wiring.



I dont mean to be funny, but if your knowledge is so lacking, what


on

earth are you thinking wiring your shower up.



What makes you think that my intention to get things checked over is
anything to do with lack of knowledge (nothing wrong with asking the
question, but I don't see your logic)?



I dont think that. Its your assorted basic errors that leave me wanting
to stay away from your shower.


?? what errors?




I have read the IEE on-site guide
and lots of stuff on the web, and think I know what the regulations



say.



I'm doubtful. Take your reason for installing an RCD.


That's ok (being doubtful). But I haven't given a reason, other than 'I
want my shower to have one'.



Anyway, as there is no legal way to switch off the supply before the
consumer unit,



pull the supply fuse.


Not legal if I were to do it. As I said elsewhere, didn't want the
hassle of asking the supplier.




I decided to make sure the shower had its own RCD



a necessity, but for entirely different reasons.



Are you not confusing a reply from someone with my original posting? I
never gave a real reason.


(CU
only has an RCD for the garage/workshop, no space for another one).



usually easy to get round compliantly, eg by turning 2 lighting
circuits into one.


Only two lighting circuits (as usual) and combining them would make the
cable run too long.

Why not forget about whether other solutions would have been possible?
Now that I have the RCD, I might as well use it (unless there is a
_clear_ reason not to). Question remains, how?

Johan
  #13   Report Post  
Andy Wade
 
Posts: n/a
Default

Johan wrote:

- My CU has one MCB/RCD for the garage,


If you mean a combined MCB and RCD for one circuit, that's called an RCBO.

- The MCB in the CU does the overcurrent protection, surely? My idea was
to go CU (MCB) - RCD - shower.


Oh yes, that's OK. It wasn't clear to me before how you were intending
to feed the RCD. Some people wrongly think that an RCD provides
overcurrent protection too and I just wanted to eliminate the
possibility that you were going to wire straight off the meter tails via
the RCD to the shower, giving no overcurrent protection (other than the
supplier's fuse).

So to summarise again: I would like my shower to be protected by an RCD,


But you haven't said why. There's not usually any need to use an RCD
for a shower - unless the installation is TT-earthed of course, but I
don't think that applies here. What type of earthing do you have?

The important things when wiring a shower circuit are these:

(a) not to use an undersized cable - you mentioned 10mm^2m so that's
probably OK - refer to Table 7 in the OSG for maximum circuit lengths;

(b) not to use an under-rated fuse or MCB; (c) to ensure that all
connections are sound, with all terminal screws done up really tight;

(d) to ensure that the circuit protective (earth) conductor is also
soundly connected and to verify this by doing a loop test at the shower
appliance's supply terminals with any supplementary bonding temporarily
disconnected - see Appendix 2 of the OSG for the maximum permissible
measured Zs value;

(e) to ensure that any and all supplementary bonding required in the
bath/shower room is in place, properly sized and soundly connected.

Of these the most important, in terms of risk of being electrocuted in
the shower, is (e), closely followed by (d). Use of an RCD is not in
any way a substitute for doing (a) to (e) properly.

I have considered the options, bought a separate RCD and would love to
know how these things are wired in.


L & N in side-by-side at the top or bottom and out at the bottom or top,
observing any polarity markings on the device. Earth straight to the
earth bar in the CU. Some electronic RCDs require a separate earth
connection (single wire).

--
Andy
  #14   Report Post  
Johan
 
Posts: n/a
Default

Andy Wade wrote:

Johan wrote:

- My CU has one MCB/RCD for the garage,



If you mean a combined MCB and RCD for one circuit, that's called an RCBO.


Indeed. Is there a difference between RCBOs and what toolstation calls a
'MCB/RCD Combined' (part number 58556) in what they do? I can see that
the toolstation one only takes up the space of 1 module, while RCBOs
usually take the space of two. Just asking out of curiosity, might as
well learn a little more now......

- The MCB in the CU does the overcurrent protection, surely? My idea
was to go CU (MCB) - RCD - shower.



Oh yes, that's OK. It wasn't clear to me before how you were intending
to feed the RCD. Some people wrongly think that an RCD provides
overcurrent protection too and I just wanted to eliminate the
possibility that you were going to wire straight off the meter tails via
the RCD to the shower, giving no overcurrent protection (other than the
supplier's fuse).


Thanks for making sure. I should have been clearer.

So to summarise again: I would like my shower to be protected by an RCD,



But you haven't said why.


Bigcat, please take note ;-)
I have an (irrational) aversion of electric showers as they bring
electricity and water in very close proximity. An RCD would give me (if
I get everything else about the installation right :-) ) a little more
peace of mind.

There's not usually any need to use an RCD
for a shower - unless the installation is TT-earthed of course, but I
don't think that applies here. What type of earthing do you have?


TN-S (via the sheath of the incoming cable).

The important things when wiring a shower circuit are these:

(a) not to use an undersized cable - you mentioned 10mm^2m so that's
probably OK - refer to Table 7 in the OSG for maximum circuit lengths;


should be ok, about 6 meters, but I realise this depends on the kW of
the shower.


(b) not to use an under-rated fuse or MCB;


not bought the shower yet, will make sure this is ok.

(c) to ensure that all
connections are sound, with all terminal screws done up really tight;


will do


(d) to ensure that the circuit protective (earth) conductor is also
soundly connected and to verify this by doing a loop test at the shower
appliance's supply terminals with any supplementary bonding temporarily
disconnected - see Appendix 2 of the OSG for the maximum permissible
measured Zs value;


this is where I need an electrician to come and check


(e) to ensure that any and all supplementary bonding required in the
bath/shower room is in place, properly sized and soundly connected.


diagrams in IEE ons-site guide are very clear for this, in my opinion,
so should get that right.

Of these the most important, in terms of risk of being electrocuted in
the shower, is (e), closely followed by (d). Use of an RCD is not in
any way a substitute for doing (a) to (e) properly.



I have considered the options, bought a separate RCD and would love to
know how these things are wired in.



L & N in side-by-side at the top or bottom and out at the bottom or top,
observing any polarity markings on the device. Earth straight to the
earth bar in the CU. Some electronic RCDs require a separate earth
connection (single wire).

thanks, that sounds reassuringly how I assumed it would work, and tells
me how to deal with the earth connection.

Johan
  #15   Report Post  
Johan
 
Posts: n/a
Default

Dave Plowman (News) wrote:

In article ,
Johan wrote:

I have bought a Wylex 63A 30mA RCD fom Screwfix (wylex shower unit,
product code 90026) to use for my new electric shower. It is not clear
to me how to wire this thing. It sits in its own box, and I imagined I
would put it close to the consumer unit, in the 10mm cable coming from
the CU and going to the shower.



The RCD has 4 connectors, one marked L at the top left hand side, the
others unmarked. The enclosed leaflet says 'The incoming cables to the
RCD may be taken either to the top or the bottom set of terminals,
dependent entirely on the ease of wiring the device'.



Sounds pretty clear to me.


Hmmmm. I initially thought it was clear, then started to worry that it
_could_ mean what I describe in the next sentence of my original
message. Exactly because electrical installations _can_ be dangerous if
not installed properly (as others have pointed out), I decided to ask
first.



That could be read to mean that only 2 out of 4 terminals are used (that
must surely be wrong).



Well, yes, you are wrong.


It would have been very odd, but better safe than sorry.

An RCD needs both line and neutral to work
unlike an MCB which is just in the line.


As it has 4 terminals, I guess the live in and
out go to the one marked 'L' and the one below that, the neutrals go to
the other 2. What happens to the earth? Do I connect that using a
connector block?



No. Feed to one pair of terminals - either top or bottom - and load to the
other pair.


That's what my woeful description says, but clearly not in a helpful way.

If there's also an MCB, the load line should go to that with a
link between the MCB and RCD. Although I'd have expected this to be
pre-wired. I'd also expect an earth bus bar.


Something like this:-


Feed
L N
| |
| |
| |
------------
| L |
| |
| RCD |
------------
| |
L| |N
| |
-------- |
| | |
| MCB | |
| | |
-------- |
| |
| |
L N
to shower


Just to be clear: in my case the MCB would be on the feed side of the RCD.

Johan



  #16   Report Post  
Dave Plowman (News)
 
Posts: n/a
Default

In article ,
Johan wrote:
I have an (irrational) aversion of electric showers as they bring
electricity and water in very close proximity. An RCD would give me (if
I get everything else about the installation right :-) ) a little more
peace of mind.


So does a kettle. Coffee maker. Immersion heater. Etc.

--
*(on a baby-size shirt) "Party -- my crib -- two a.m

Dave Plowman London SW
To e-mail, change noise into sound.
  #17   Report Post  
Stefek Zaba
 
Posts: n/a
Default

Johan wrote:

Just to be clear: in my case the MCB would be on the feed side of the RCD.

No problem there.

I was about to ask whether your RCD came with an enclosure, but since
you provided the Screwfix partnum I can see that it does - so that's OK
too. As the estimable Mr Stumbles noted, S-fix also carry a
more-for-less RCD+MCB-in-one-enclosure - Volex rather'n Wylex, reputable
enough. With the combined part, you'd use a Henley block to feed your
existing CU and the shower unit in parallel from the main fuse; with
your RCD-only, you need to take the feed from a suitable (typicalluy
40A) MCB in the main CU.

And as Andy Wade mentioned, for the higher currents your electric shower
pulls, you really do want to do up the connections tighter than you
might think (and it's a good idea to recheck them after a month or so,
as the strands settle/deform). We're not talking gorrilla-level
6ft-scaff-pole-on-the-end-of-ratchet torques, but "well firm with
ordinary screwdriver"...

HTH - Stefek
  #18   Report Post  
Dave Plowman (News)
 
Posts: n/a
Default

In article ,
Stefek Zaba wrote:
And as Andy Wade mentioned, for the higher currents your electric shower
pulls, you really do want to do up the connections tighter than you
might think (and it's a good idea to recheck them after a month or so,
as the strands settle/deform). We're not talking gorrilla-level
6ft-scaff-pole-on-the-end-of-ratchet torques, but "well firm with
ordinary screwdriver"...


IMHO, all permanent wiring connectors should be done up until they 'groan'
- using a screwdriver with a blade the same width as the screw. I've yet
to break a screw or strip a thread, but I've come across lots of problems
on installations where they simply haven't been tightened enough.

Of course if you're a gorilla you might need to be careful. ;-)

--
*Generally speaking, you aren't learning much if your lips are moving.*

Dave Plowman London SW
To e-mail, change noise into sound.
  #19   Report Post  
Mark Carver
 
Posts: n/a
Default

Dave Plowman (News) wrote:


IMHO, all permanent wiring connectors should be done up until they 'groan'
- using a screwdriver with a blade the same width as the screw. I've yet
to break a screw or strip a thread, but I've come across lots of problems
on installations where they simply haven't been tightened enough.


Almost every socket in our kitchen has had loose terminals. This came to
light about a week after moving in. My wife had the iron plugged in to a
socket. She called me because she could hear 'sparking' from behind the
socket. I tapped it, there was indeed a cracking sound from behind.

I killed the breaker and removed the socket, as I undid the fixing
screws the entire socket virtually fell away from the wall ! The two
T&E L and N tails were so short (probably because the wall had been
tiled as part of a kitchen re-build) that it would have been impossible
to have screwed the terminals down. Thankfully the Earth tails were at
least still twisted together and connected. The L and N terminals were
black with arcing. The sparky must have simply positioned all the wires
in the 'correct' place, opened up the terminals and pushed the whole
socket home. It must have taken ages to get that 'right', far longer
than it took me to extend the tails, replace the socket, and do the job
properly.

I checked the other sockets, some had loose terminals, some had cross
threaded fixing screws, so I had to drill those out and start again.
An FCU had been fitted on the wall behind the back of a kitchen cabinet,
but the hole in the back of the cabinet is too small to allow removal of
the FCU.

Hopeless. The plumbing in the kitchen is better, except you need to be a
contortionist (and have a crystal ball) to find and operate the main
stop cock.


--
Mark
Please replace invalid and invalid with gmx and net to reply.
  #20   Report Post  
 
Posts: n/a
Default

Johan wrote:
Andy Wade wrote:


So to summarise again: I would like my shower to be protected by

an RCD,

But you haven't said why.


Bigcat, please take note ;-)
I have an (irrational) aversion of electric showers as they bring
electricity and water in very close proximity. An RCD would give me

(if
I get everything else about the installation right :-) ) a little

more
peace of mind.


You do need an RCD, why is another matter.

10mm2 is OTT unless you've found an unusually heavy duty shower, and
have the supply capability to match.


TN-S (via the sheath of the incoming cable).


dont miss anything out on your equi bonding then! BTW if you dont bond
the plughole on a PME system you're creating a problem.


If you had an electric immersion tank plus mixer shower, your leccy
would not just come close to the water, but would be running right
through it as you shower.


NT



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
gas fireplace - wiring question Hamilton Audio Home Repair 6 January 6th 05 01:33 AM
Cloth covered wiring barry martin Home Repair 0 October 20th 04 02:32 AM
telephone wiring question barry martin Home Repair 0 August 11th 04 02:43 AM
peculiar wiring in residential switch box? David Jones Home Repair 6 July 19th 04 11:25 PM
connecting aluminum to copper wiring Mr. Bill Home Repair 12 May 5th 04 02:33 PM


All times are GMT +1. The time now is 09:17 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"