A year ago I allowed a neighbor who was building a house next to us access
to electricity in a small building on our property. He had an electrician
put in an outside receptacle. A few weeks after he no longer had any need
for it, I decided to use that as a way to get electricity 100' away as a new
outlet for a pond pump and outdoor light. All the wire is in place and
underground. It took me until now to finish off the connection at the building.

Here's the situation. He connected the receptacle directly to the switch box
in the building, and the wires a ground, red, black and white. I long
ago, 10 months ago, disconnected those wires and taped them. The wiring I
have underground to the pond area uses white, green, and ground. For 120 v,
I believe the whites go together, and the green goes to black, correct? It
appears that the red wire allows for 240v, so I'll just tape it off. I'm
still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have
a socket entirely different than one for 120v?

An oddity about this is that he apparently has the outside outlet on two
switches in the switch box. Unless both are off, then they appear to be
alive when either or both are on. When both are on, I get either 240v or
120v depending on which pair combo I measure. It is possible for me to
contact the electrician, so maybe I can review what he did. Comments?
--
Wayne Watson (Nevada City, CA)

Web Page: speckledwithStars.net
  #2   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 118
Default Red, Green, Black, and White Wires

"W. Watson" writes:

A year ago I allowed a neighbor who was building a house next to us
access to electricity in a small building on our property. He had an
electrician put in an outside receptacle. A few weeks after he no
longer had any need for it, I decided to use that as a way to get
electricity 100' away as a new outlet for a pond pump and outdoor
light. All the wire is in place and underground. It took me until now
to finish off the connection at the building.

Here's the situation. He connected the receptacle directly to the
switch box in the building, and the wires a ground, red, black and
white. I long ago, 10 months ago, disconnected those wires and taped
them. The wiring I have underground to the pond area uses white,
green, and ground. For 120 v, I believe the whites go together, and


Better not. Green should ONLY be using for the (Safety) ground.

White is Neutral
Black or red is Hot.
Green or bare copper is ground.

the green goes to black, correct? It appears that the red wire allows


If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.

for 240v, so I'll just tape it off. I'm still a bit puzzled why the
guy used red at all. Doesn't a 240 v outlet have a socket entirely
different than one for 120v?


There are various versions depending on maximum current but at the very
least, the prongs are oriented differently.

An oddity about this is that he apparently has the outside outlet on
two switches in the switch box. Unless both are off, then they appear
to be alive when either or both are on. When both are on, I get either
240v or 120v depending on which pair combo I measure. It is possible
for me to contact the electrician, so maybe I can review what he
did. Comments?


Note that if it was a 230 VAC circuit, the breakers should have been
ganged so if either tripped, they both went off. However, now, the
way it was hooked up is correct for seprate circuits.

To be sure about all this, it would be a good idea to have a qualitifed
electrician check it over.

--- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/
Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/
+Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm
| Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html

Important: Anything sent to the email address in the message header above is
ignored unless my full name AND either lasers or electronics is included in the
subject line. Or, you can contact me via the Feedback Form in the FAQs.
  #3   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,247
Default Red, Green, Black, and White Wires

On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser
wrote:


If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.


Never, ever, use green for anything other than ground. Period. Say
some idiot comes along in the future and gets killed because you used
green for hot--you're on the hook for that one. Say the building
inspector sees it? Use the wires the way they are intended to be
used...


  #4   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 42
Default Red, Green, Black, and White Wires



Sam Goldwasser wrote:
"W. Watson" writes:

A year ago I allowed a neighbor who was building a house next to us
access to electricity in a small building on our property. He had an
electrician put in an outside receptacle. A few weeks after he no
longer had any need for it, I decided to use that as a way to get
electricity 100' away as a new outlet for a pond pump and outdoor
light. All the wire is in place and underground. It took me until now
to finish off the connection at the building.

Here's the situation. He connected the receptacle directly to the
switch box in the building, and the wires a ground, red, black and
white. I long ago, 10 months ago, disconnected those wires and taped
them. The wiring I have underground to the pond area uses white,
green, and ground. For 120 v, I believe the whites go together, and


Better not. Green should ONLY be using for the (Safety) ground.

Yes, bad memory. There is no bare copper.

White is Neutral
Black or red is Hot.
Green or bare copper is ground.

the green goes to black, correct? It appears that the red wire allows


If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.

for 240v, so I'll just tape it off. I'm still a bit puzzled why the
guy used red at all. Doesn't a 240 v outlet have a socket entirely
different than one for 120v?


There are various versions depending on maximum current but at the very
least, the prongs are oriented differently.

Thanks. I think I'll get the the guy's phone number and call him. I have a
feeling he didn't use the red. It was snipped off, but may have been taped.

An oddity about this is that he apparently has the outside outlet on
two switches in the switch box. Unless both are off, then they appear
to be alive when either or both are on. When both are on, I get either
240v or 120v depending on which pair combo I measure. It is possible
for me to contact the electrician, so maybe I can review what he
did. Comments?


Note that if it was a 230 VAC circuit, the breakers should have been
ganged so if either tripped, they both went off. However, now, the
way it was hooked up is correct for seprate circuits.

To be sure about all this, it would be a good idea to have a qualitifed
electrician check it over.

--- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/
Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/
+Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm
| Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html

Important: Anything sent to the email address in the message header above is
ignored unless my full name AND either lasers or electronics is included in the
subject line. Or, you can contact me via the Feedback Form in the FAQs.


--
Wayne Watson (Nevada City, CA)

Web Page: speckledwithStars.net
  #5   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 42
Default Red, Green, Black, and White Wires

Yep, bad memory. There were black, green and white in the conduit.

PeterD wrote:
On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser
wrote:

If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.


Never, ever, use green for anything other than ground. Period. Say
some idiot comes along in the future and gets killed because you used
green for hot--you're on the hook for that one. Say the building
inspector sees it? Use the wires the way they are intended to be
used...



--
Wayne Watson (Nevada City, CA)

Web Page: speckledwithStars.net


  #6   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 533
Default Red, Green, Black, and White Wires

W. Watson wrote:
Yep, bad memory. There were black, green and white in the conduit.

PeterD wrote:
On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser
wrote:

If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.


Never, ever, use green for anything other than ground. Period. Say
some idiot comes along in the future and gets killed because you used
green for hot--you're on the hook for that one. Say the building
inspector sees it? Use the wires the way they are intended to be
used...


That makes more sense, but I like your advice about calling the
electrician. If I were doing this, I'd hook up my voltmeter and simply
verify the original wiring. Likely, what I would measure would be line
voltage from either the red or black wires, to either the bare or the
white wire.

This is an area where you don't want to be 'guessing'. If you don't
have the proper equipment, you either need to get it, borrow it (and
understand how it works) or let someone else do it. A little bit of
knowledge (which you do appear to have) can be very dangerous in these
situations.

As to the wires in the conduit. If you really had just a white, green
and bare wire, my advice would be to use the bare wire to pull in a new
length of black wire. It wouldn't have been all that hard to do, and
would have insured that everything remained legal and kosher.

Thankfully, that issue has been resolved. Are electrical codes
inspections required for new work in your locality?

jak
  #8   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 274
Default Red, Green, Black, and White Wires

On 2/19/08 8:34 AM, in article
, "W. Watson"
wrote:



Sam Goldwasser wrote:
"W. Watson" writes:

A year ago I allowed a neighbor who was building a house next to us
access to electricity in a small building on our property. He had an
electrician put in an outside receptacle. A few weeks after he no
longer had any need for it, I decided to use that as a way to get
electricity 100' away as a new outlet for a pond pump and outdoor
light. All the wire is in place and underground. It took me until now
to finish off the connection at the building.

Here's the situation. He connected the receptacle directly to the
switch box in the building, and the wires a ground, red, black and
white. I long ago, 10 months ago, disconnected those wires and taped
them. The wiring I have underground to the pond area uses white,
green, and ground. For 120 v, I believe the whites go together, and


Better not. Green should ONLY be using for the (Safety) ground.

Yes, bad memory. There is no bare copper.

White is Neutral
Black or red is Hot.
Green or bare copper is ground.

the green goes to black, correct? It appears that the red wire allows


If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.

for 240v, so I'll just tape it off. I'm still a bit puzzled why the
guy used red at all. Doesn't a 240 v outlet have a socket entirely
different than one for 120v?


Yes and No....... If it's for use by 240V equipment, then yes. But it is
acceptable to connect each side of a 240V feed to half of a 120V duplex
outlet, with the neutral common to both. Kitchens outlets are commonly
wired this way. My shop is also wired this way.



There are various versions depending on maximum current but at the very
least, the prongs are oriented differently.

Thanks. I think I'll get the the guy's phone number and call him. I have a
feeling he didn't use the red. It was snipped off, but may have been taped.

An oddity about this is that he apparently has the outside outlet on
two switches in the switch box. Unless both are off, then they appear
to be alive when either or both are on. When both are on, I get either
240v or 120v depending on which pair combo I measure. It is possible
for me to contact the electrician, so maybe I can review what he
did. Comments?


Note that if it was a 230 VAC circuit, the breakers should have been
ganged so if either tripped, they both went off. However, now, the
way it was hooked up is correct for seprate circuits.

To be sure about all this, it would be a good idea to have a qualitifed
electrician check it over.

--- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/
Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/
+Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm
| Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html

Important: Anything sent to the email address in the message header above is
ignored unless my full name AND either lasers or electronics is included in
the
subject line. Or, you can contact me via the Feedback Form in the FAQs.


  #9   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 533
Default Red, Green, Black, and White Wires

Don Bowey wrote:
On 2/19/08 6:03 AM, in article ,
"PeterD" wrote:

On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser
wrote:

If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.

Never, ever, use green for anything other than ground. Period. Say
some idiot comes along in the future and gets killed because you used
green for hot--you're on the hook for that one. Say the building
inspector sees it? Use the wires the way they are intended to be
used...



While you offer some good cautious advice, we do have a NEC case where a
white wire can be designated as a hot wire by taping the ends black or red.

IMO, if the green wire is *verified* at the breaker to be a hot lead AND the
gauge and insulation types are valid, then I don't see a problem with
color-taping *BOTH* ends black or red and using it as a hot wire.


I guess I'm a little more cautious in my old age. I could 'maybe' get
behind color-taping a wire with red tape. While probably legal, I'm
dead-set against doing it with black. Trouble is, IMM, that black tape
is so common that it could easily be overlooked or discounted at a
casual glance. Red is a little different in that--being red--it might
inspire at least caution, if not a full-stop and verification before
going further.

I've done it with Cam-loc (Cleco) connectors, but in those situations,
the entire connector was covered with the correct color tape; and *all*
of the conductors were black anyway.

In any case, since the OP stated all the wires go through a conduit, I
think I'd just replace the offending wire to code.

jak
  #10   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 274
Default Red, Green, Black, and White Wires

On 2/19/08 12:08 PM, in article
, "jakdedert"
wrote:

Don Bowey wrote:
On 2/19/08 6:03 AM, in article ,
"PeterD" wrote:

On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser
wrote:

If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.
Never, ever, use green for anything other than ground. Period. Say
some idiot comes along in the future and gets killed because you used
green for hot--you're on the hook for that one. Say the building
inspector sees it? Use the wires the way they are intended to be
used...



While you offer some good cautious advice, we do have a NEC case where a
white wire can be designated as a hot wire by taping the ends black or red.

IMO, if the green wire is *verified* at the breaker to be a hot lead AND the
gauge and insulation types are valid, then I don't see a problem with
color-taping *BOTH* ends black or red and using it as a hot wire.


I guess I'm a little more cautious in my old age. I could 'maybe' get
behind color-taping a wire with red tape. While probably legal, I'm
dead-set against doing it with black. Trouble is, IMM, that black tape
is so common that it could easily be overlooked or discounted at a
casual glance. Red is a little different in that--being red--it might
inspire at least caution, if not a full-stop and verification before
going further.

I've done it with Cam-loc (Cleco) connectors, but in those situations,
the entire connector was covered with the correct color tape; and *all*
of the conductors were black anyway.

In any case, since the OP stated all the wires go through a conduit, I
think I'd just replace the offending wire to code.

jak


Both red and black should raise one's awareness while working around hot, or
even questionable, services.

Thinking more on this though, I don't recall ever seeing green "power" wire.
I wonder if the wire in the conduit is appliance wire (rubber outer cover
with white, black, red, green stranded wires). If so, without checking the
NEC, I don't think this wire correct at all for how it's being used.



  #11   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,572
Default Red, Green, Black, and White Wires



Both red and black should raise one's awareness while working around hot,
or
even questionable, services.

Thinking more on this though, I don't recall ever seeing green "power"
wire.
I wonder if the wire in the conduit is appliance wire (rubber outer cover
with white, black, red, green stranded wires). If so, without checking
the
NEC, I don't think this wire correct at all for how it's being used.



Red and black are both perfectly acceptable to use as hot. White may also be
used in some circumstances but it must be marked with either red or black.
Properly applied wire nuts do not normally need to be taped, so the only
reason tape would be on a wire in a box is to mark the color. I'd have to
check, but I seem to recall that it's forbidden to use a green wire for
anything but ground, it's certainly not advisable.

That said, the OP responded to say that he got the colors wrong and that
black, white, and green are what he has, which is precisely what I'd expect
for a 120V branch wired with THHN in conduit. I guess people missed that.


  #12   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 533
Default Red, Green, Black, and White Wires

Don Bowey wrote:
On 2/19/08 12:08 PM, in article
, "jakdedert"
wrote:

Don Bowey wrote:
On 2/19/08 6:03 AM, in article ,
"PeterD" wrote:

On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser
wrote:

If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.
Never, ever, use green for anything other than ground. Period. Say
some idiot comes along in the future and gets killed because you used
green for hot--you're on the hook for that one. Say the building
inspector sees it? Use the wires the way they are intended to be
used...


While you offer some good cautious advice, we do have a NEC case where a
white wire can be designated as a hot wire by taping the ends black or red.

IMO, if the green wire is *verified* at the breaker to be a hot lead AND the
gauge and insulation types are valid, then I don't see a problem with
color-taping *BOTH* ends black or red and using it as a hot wire.


I guess I'm a little more cautious in my old age. I could 'maybe' get
behind color-taping a wire with red tape. While probably legal, I'm
dead-set against doing it with black. Trouble is, IMM, that black tape
is so common that it could easily be overlooked or discounted at a
casual glance. Red is a little different in that--being red--it might
inspire at least caution, if not a full-stop and verification before
going further.

I've done it with Cam-loc (Cleco) connectors, but in those situations,
the entire connector was covered with the correct color tape; and *all*
of the conductors were black anyway.

In any case, since the OP stated all the wires go through a conduit, I
think I'd just replace the offending wire to code.

jak


Both red and black should raise one's awareness while working around hot, or
even questionable, services.

Thinking more on this though, I don't recall ever seeing green "power" wire.
I wonder if the wire in the conduit is appliance wire (rubber outer cover
with white, black, red, green stranded wires). If so, without checking the
NEC, I don't think this wire correct at all for how it's being used.

He's already stated his error in the colors. The conductors pulled were
correct; white/black/green. I imagine all else is kosher as well. I
don't know who pulled the wires, or why they weren't hooked up at the time.

My reservation about color-taping was not directed at professionals, but
at the odd homeowner 15 or 20 years down the line. The practice is
apparently more common than I imagined, and--red or black--would flag
itself to a pro.

jak
  #13   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,572
Default Red, Green, Black, and White Wires



My reservation about color-taping was not directed at professionals, but
at the odd homeowner 15 or 20 years down the line. The practice is
apparently more common than I imagined, and--red or black--would flag
itself to a pro.




The most common place you see this is in switch legs where power is supplied
directly to the ceiling box where the light fixture is mounted and then a
separate drop goes from that to the switch. In that case both wires in that
drop are technically hot, so the white one gets taped black and connects to
the light fixture.


The ones that get me are those houses where someone used whatever color wire
they had on hand for whatever, I see that in cars a lot of times too. Always
verify, and never underestimate the crazy things that some previous person
may have done. When I bought my house, all the switches downstairs were on
the neutral side which caused me to get bit pretty good once. Yes, I should
have shut off the breaker.


  #14   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 118
Default Red, Green, Black, and White Wires

"W. Watson" writes:

Yep, bad memory. There were black, green and white in the conduit.


So, black-black, white-white, bare copper to bare copper (or green).

And, of course, splices using proper size solderless connectors ("Wire
Nuts") or other acceptable means, inside proper elecrical boxes!

--- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/
Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/
+Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm
| Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html

Important: Anything sent to the email address in the message header above is
ignored unless my full name AND either lasers or electronics is included in the
subject line. Or, you can contact me via the Feedback Form in the FAQs.

PeterD wrote:
On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser
wrote:

If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.

Never, ever, use green for anything other than ground. Period. Say
some idiot comes along in the future and gets killed because you used
green for hot--you're on the hook for that one. Say the building
inspector sees it? Use the wires the way they are intended to be
used...


--
Wayne Watson (Nevada City, CA)

Web Page: speckledwithStars.net

  #15   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 118
Default Red, Green, Black, and White Wires

Don Bowey writes:

On 2/19/08 8:34 AM, in article
, "W. Watson"
wrote:



Sam Goldwasser wrote:
"W. Watson" writes:

A year ago I allowed a neighbor who was building a house next to us
access to electricity in a small building on our property. He had an
electrician put in an outside receptacle. A few weeks after he no
longer had any need for it, I decided to use that as a way to get
electricity 100' away as a new outlet for a pond pump and outdoor
light. All the wire is in place and underground. It took me until now
to finish off the connection at the building.

Here's the situation. He connected the receptacle directly to the
switch box in the building, and the wires a ground, red, black and
white. I long ago, 10 months ago, disconnected those wires and taped
them. The wiring I have underground to the pond area uses white,
green, and ground. For 120 v, I believe the whites go together, and

Better not. Green should ONLY be using for the (Safety) ground.

Yes, bad memory. There is no bare copper.

White is Neutral
Black or red is Hot.
Green or bare copper is ground.

the green goes to black, correct? It appears that the red wire allows

If all you have in the conduit is white, green, and bare copper, then
that is your only choice but that green wire has to be unambiguously
labeled as Hot by painting the insulation near the ends black.
And, it had better be the proper gauge.

for 240v, so I'll just tape it off. I'm still a bit puzzled why the
guy used red at all. Doesn't a 240 v outlet have a socket entirely
different than one for 120v?


Yes and No....... If it's for use by 240V equipment, then yes. But it is
acceptable to connect each side of a 240V feed to half of a 120V duplex
outlet, with the neutral common to both. Kitchens outlets are commonly
wired this way. My shop is also wired this way.


But this is a 115 VAC outlet providing 115 VAC, not a 230 VAC outlet.

Only those with Frankstein tendencies will jerryrig a 230 VAC appliance
into a split duplex outlet!!!

--- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/
Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/
+Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm
| Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html

Important: Anything sent to the email address in the message header above is
ignored unless my full name AND either lasers or electronics is included in the
subject line. Or, you can contact me via the Feedback Form in the FAQs.


  #17   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 118
Default Red, Green, Black, and White Wires

Don Bowey writes:

On 2/19/08 4:55 PM, in article , "Sam
Goldwasser" wrote:

Don Bowey writes:

On 2/19/08 8:34 AM, in article
, "W. Watson"
wrote:


(snip)

for 240v, so I'll just tape it off. I'm still a bit puzzled why the
guy used red at all. Doesn't a 240 v outlet have a socket entirely
different than one for 120v?

Yes and No....... If it's for use by 240V equipment, then yes. But it is
acceptable to connect each side of a 240V feed to half of a 120V duplex
outlet, with the neutral common to both. Kitchens outlets are commonly
wired this way. My shop is also wired this way.


But this is a 115 VAC outlet providing 115 VAC, not a 230 VAC outlet.


It isn't used to provide 240V service. It provides two 120V outlets, each
with it's own 120V feed from opposite sides of the breaker box (separate
phase).


Only those with Frankstein tendencies will jerryrig a 230 VAC appliance
into a split duplex outlet!!!


You're entitled to your opinion, but it's a standard wiring configuration
straight out of the NEC.


You're saying that NEC recommends jerryrigging a special cord with two
plugs to get 230 VAC from a split 115 VAC outlet?

--- sam | Sci.Electronics.Repair FAQ:
http://www.repairfaq.org/
Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/
+Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm
| Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html

Important: Anything sent to the email address in the message header above is
ignored unless my full name AND either lasers or electronics is included in the
subject line. Or, you can contact me via the Feedback Form in the FAQs.
  #18   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 274
Default Red, Green, Black, and White Wires

On 2/20/08 5:25 AM, in article , "Sam
Goldwasser" wrote:

Don Bowey writes:

On 2/19/08 4:55 PM, in article
, "Sam
Goldwasser" wrote:

Don Bowey writes:

On 2/19/08 8:34 AM, in article
, "W. Watson"
wrote:


(snip)

for 240v, so I'll just tape it off. I'm still a bit puzzled why the
guy used red at all. Doesn't a 240 v outlet have a socket entirely
different than one for 120v?

Yes and No....... If it's for use by 240V equipment, then yes. But it is
acceptable to connect each side of a 240V feed to half of a 120V duplex
outlet, with the neutral common to both. Kitchens outlets are commonly
wired this way. My shop is also wired this way.

But this is a 115 VAC outlet providing 115 VAC, not a 230 VAC outlet.


It isn't used to provide 240V service. It provides two 120V outlets, each
with it's own 120V feed from opposite sides of the breaker box (separate
phase).


Only those with Frankstein tendencies will jerryrig a 230 VAC appliance
into a split duplex outlet!!!


You're entitled to your opinion, but it's a standard wiring configuration
straight out of the NEC.


You're saying that NEC recommends jerryrigging a special cord with two
plugs to get 230 VAC from a split 115 VAC outlet?


No the NEC doesn't, but you apparently can't get past what you think.

It is not jerryrigging to provide two 120V feeds using a 3-wire with ground
(Bk, Red, Wht, & bare copper) cable.

The NEC does not describe all the ways a configuration might be used; that
is left to you, which you have done well.

  #19   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,572
Default Red, Green, Black, and White Wires



No the NEC doesn't, but you apparently can't get past what you think.

It is not jerryrigging to provide two 120V feeds using a 3-wire with
ground
(Bk, Red, Wht, & bare copper) cable.

The NEC does not describe all the ways a configuration might be used; that
is left to you, which you have done well.


He never did say that wiring of the outlet was incorrect, just that use. You
guys are on the same page and arguing about different things.


  #20   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 274
Default Red, Green, Black, and White Wires

On 2/20/08 10:24 AM, in article ,
"Thor" wrote:

On Wed, 20 Feb 2008 07:41:49 -0800, Don Bowey wrote:

On 2/20/08 5:25 AM, in article
, "Sam
Goldwasser" wrote:

Don Bowey writes:

On 2/19/08 4:55 PM, in article
, "Sam
Goldwasser" wrote:

Don Bowey writes:

On 2/19/08 8:34 AM, in article
, "W. Watson"
wrote:

(snip)

for 240v, so I'll just tape it off. I'm still a bit puzzled why the
guy used red at all. Doesn't a 240 v outlet have a socket entirely
different than one for 120v?

Yes and No....... If it's for use by 240V equipment, then yes. But it
is
acceptable to connect each side of a 240V feed to half of a 120V duplex
outlet, with the neutral common to both. Kitchens outlets are commonly
wired this way. My shop is also wired this way.

But this is a 115 VAC outlet providing 115 VAC, not a 230 VAC outlet.

It isn't used to provide 240V service. It provides two 120V outlets, each
with it's own 120V feed from opposite sides of the breaker box (separate
phase).


Only those with Frankstein tendencies will jerryrig a 230 VAC appliance
into a split duplex outlet!!!

You're entitled to your opinion, but it's a standard wiring configuration
straight out of the NEC.

You're saying that NEC recommends jerryrigging a special cord with two
plugs to get 230 VAC from a split 115 VAC outlet?


No the NEC doesn't, but you apparently can't get past what you think.

It is not jerryrigging to provide two 120V feeds using a 3-wire with ground
(Bk, Red, Wht, & bare copper) cable.

The NEC does not describe all the ways a configuration might be used; that
is left to you, which you have done well.



I am sure you can not feed a split duplex outlet with 240 volts if the outlet
is
only rated for 125 volts. Article 410-56(a) Article 110-3


Each outlet of the pair is fed 120V NOT 240V.


Only the grounded conductor and the grounding conductor have specified
colors.
Article 200-6



It is covered in other Articles, also.



  #21   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 12,924
Default Red, Green, Black, and White Wires

Thor wrote:

I am sure you can not feed a split duplex outlet with 240 volts if the outlet is
only rated for 125 volts. Article 410-56(a) Article 110-3


You are feeding 120 VAC to each outlet, with a common neutral. It's
called a split outlet. There are also combo duplex outlets with a 240
VAC and a 120 VAC receptacle used in commercial buildings to plug in
large floor buffers and vacs.



http://www.hubbellcatalog.com/wiring/catalogpages/Page-A24.pdf part
numbers HBL5492 & HBL5492I at:
http://www.hubbellcatalog.com/wiring/section-a-ss.asp?FAM=Straight_Blade&SORD=102+822&FT_102=1350 8&FT_822=7663&SUBMIT.x=28&SUBMIT.y=13


Leviton has their 5031-I, 5842-I, 5844 on page 51 of
http://www.leviton.com/OA_HTML/ibcGetAttachment.jsp?cItemId=u4XWH2gnFVIs9yeepxlPk w&label=IBE&appName=IBE
which is a 30.691 Mbyte download.


Only the grounded conductor and the grounding conductor have specified colors.
Article 200-6



--
Service to my country? Been there, Done that, and I've got my DD214 to
prove it.
Member of DAV #85.

Michael A. Terrell
Central Florida
  #22   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 91
Default Red, Green, Black, and White Wires


"W. Watson" wrote in message
...
For 120 v,
I believe the whites go together, and the green goes to black, correct?


Unless you are DAMN SURE you're the only one who will EVER touch this
wiring, and that you will 100% REMEMBER that the green is hot, then bite the
bullet and pull a black strand through the conduit. Green means safe to
electricians, you don't want somebody down the road to shock and potentially
injure themselves because of the ambiguous color coding.

It
appears that the red wire allows for 240v, so I'll just tape it off. I'm
still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet
have a socket entirely different than one for 120v?


The red strand is often used to run a 2nd hot, so that you can run two
circuits with one run of 4-strand wire. On a 240V 4-wire circuit, red and
black are opposite poles, with 240v between them. white is neutral. red to
white and/or black to white would both give you 120v. Red to black gives
240v.

An oddity about this is that he apparently has the outside outlet on two
switches in the switch box. Unless both are off, then they appear to be
alive when either or both are on. When both are on, I get either 240v or
120v depending on which pair combo I measure. It is possible for me to
contact the electrician, so maybe I can review what he did. Comments?
--


It's so that you can run a separate circuit to each plug-in on the
receptacle. Four conductors must have been run from the main panel in the
house to the subpanel. This is good. It means you can wire up a 240v
circuit if you need it.


Wayne Watson (Nevada City, CA)

Web Page: speckledwithStars.net



  #23   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,247
Default Red, Green, Black, and White Wires

On Tue, 11 Mar 2008 03:56:34 -0600, wrote:

On Tue, 19 Feb 2008 12:38:58 -0600, jakdedert
wrote:

Never, ever, use green for anything other than ground. Period. Say


What if your mother is connected to a life support machine. The power
suddenly goes out. You hear the generator kick in, but you dont get
any power. You pop open the generator panel and discover one of the
hot wires (black) has a bare spot and is shorted. You run to the
garage and find that all you have is green wire. Do you abide by the
code and let your mother die, or do you violate the code and save her
life?


You are a moron...


Or, it's 50 below zero and your furnace quits. You use your
miltimeter and discover there is no power to the furnace. You run to
the breaker box and find that there's power and the breakers are fine.
You know that there must be a broken wire somewhere in the walls of
your home. The indoor temperature is dropping quickly. You rush to
the basement and find you do not have any romex, just a spool of
single strand green wire. (Ya know that always happens). You're
faced with a major decision in life. Do you run two strands of green
wire from the breaker box to the furnace (one for the hot and one for
the neutral), or do you just freeze to death?


You are more than a moron...


Of course as we all know, there's always a building inspector sitting
outside in a snow bank with binoculars and a video camera just waiting
for someone like you to violate the code !!!!


You are a record moron...


And for that matter, is green wire capable of passing hot AC voltage?
Do the electrons in green coated wire function in the same manner as
the electrons in a black or white coated wire? Do the electrons
change if you take black spray paint and paint a green wire black, or
white?
OOPS, how DO you paint a wire white with black spray paint?


Hey, Phil, you are so much better than I am at this, please add to my
comments!
  #24   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 533
Default Red, Green, Black, and White Wires

PeterD wrote:
drivelsnip

You are a record moron...

And for that matter, is green wire capable of passing hot AC voltage?
Do the electrons in green coated wire function in the same manner as
the electrons in a black or white coated wire? Do the electrons
change if you take black spray paint and paint a green wire black, or
white?
OOPS, how DO you paint a wire white with black spray paint?


Hey, Phil, you are so much better than I am at this, please add to my
comments!


....or just don't feed the trolls. They starve. Problem solved.

jak
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
White, Black, Green, Blue and RED lighting wire ? [email protected] Home Repair 4 December 10th 07 05:28 PM
gfci three black and two white wires?? irishspring Home Repair 12 July 26th 06 02:01 AM
Junction Box has no white wires celing light help needed [email protected] Home Repair 4 August 13th 05 04:28 PM
Grounding Of Ground Wires In An Electrical Gang Box (how to handle the green ground wires) Robert11 Home Repair 7 March 8th 05 03:45 PM
Help! What are the black wires for? Kris UK diy 8 November 14th 03 10:58 PM


All times are GMT +1. The time now is 05:52 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"