Red, Green, Black, and White Wires
A year ago I allowed a neighbor who was building a house next to us access
to electricity in a small building on our property. He had an electrician put in an outside receptacle. A few weeks after he no longer had any need for it, I decided to use that as a way to get electricity 100' away as a new outlet for a pond pump and outdoor light. All the wire is in place and underground. It took me until now to finish off the connection at the building. Here's the situation. He connected the receptacle directly to the switch box in the building, and the wires a ground, red, black and white. I long ago, 10 months ago, disconnected those wires and taped them. The wiring I have underground to the pond area uses white, green, and ground. For 120 v, I believe the whites go together, and the green goes to black, correct? It appears that the red wire allows for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? An oddity about this is that he apparently has the outside outlet on two switches in the switch box. Unless both are off, then they appear to be alive when either or both are on. When both are on, I get either 240v or 120v depending on which pair combo I measure. It is possible for me to contact the electrician, so maybe I can review what he did. Comments? -- Wayne Watson (Nevada City, CA) Web Page: speckledwithStars.net |
#2
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
"W. Watson" writes:
A year ago I allowed a neighbor who was building a house next to us access to electricity in a small building on our property. He had an electrician put in an outside receptacle. A few weeks after he no longer had any need for it, I decided to use that as a way to get electricity 100' away as a new outlet for a pond pump and outdoor light. All the wire is in place and underground. It took me until now to finish off the connection at the building. Here's the situation. He connected the receptacle directly to the switch box in the building, and the wires a ground, red, black and white. I long ago, 10 months ago, disconnected those wires and taped them. The wiring I have underground to the pond area uses white, green, and ground. For 120 v, I believe the whites go together, and Better not. Green should ONLY be using for the (Safety) ground. White is Neutral Black or red is Hot. Green or bare copper is ground. the green goes to black, correct? It appears that the red wire allows If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? There are various versions depending on maximum current but at the very least, the prongs are oriented differently. An oddity about this is that he apparently has the outside outlet on two switches in the switch box. Unless both are off, then they appear to be alive when either or both are on. When both are on, I get either 240v or 120v depending on which pair combo I measure. It is possible for me to contact the electrician, so maybe I can review what he did. Comments? Note that if it was a 230 VAC circuit, the breakers should have been ganged so if either tripped, they both went off. However, now, the way it was hooked up is correct for seprate circuits. To be sure about all this, it would be a good idea to have a qualitifed electrician check it over. --- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/ Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/ +Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm | Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html Important: Anything sent to the email address in the message header above is ignored unless my full name AND either lasers or electronics is included in the subject line. Or, you can contact me via the Feedback Form in the FAQs. |
#3
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser
wrote: If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. Never, ever, use green for anything other than ground. Period. Say some idiot comes along in the future and gets killed because you used green for hot--you're on the hook for that one. Say the building inspector sees it? Use the wires the way they are intended to be used... |
#4
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
Sam Goldwasser wrote: "W. Watson" writes: A year ago I allowed a neighbor who was building a house next to us access to electricity in a small building on our property. He had an electrician put in an outside receptacle. A few weeks after he no longer had any need for it, I decided to use that as a way to get electricity 100' away as a new outlet for a pond pump and outdoor light. All the wire is in place and underground. It took me until now to finish off the connection at the building. Here's the situation. He connected the receptacle directly to the switch box in the building, and the wires a ground, red, black and white. I long ago, 10 months ago, disconnected those wires and taped them. The wiring I have underground to the pond area uses white, green, and ground. For 120 v, I believe the whites go together, and Better not. Green should ONLY be using for the (Safety) ground. Yes, bad memory. There is no bare copper. White is Neutral Black or red is Hot. Green or bare copper is ground. the green goes to black, correct? It appears that the red wire allows If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? There are various versions depending on maximum current but at the very least, the prongs are oriented differently. Thanks. I think I'll get the the guy's phone number and call him. I have a feeling he didn't use the red. It was snipped off, but may have been taped. An oddity about this is that he apparently has the outside outlet on two switches in the switch box. Unless both are off, then they appear to be alive when either or both are on. When both are on, I get either 240v or 120v depending on which pair combo I measure. It is possible for me to contact the electrician, so maybe I can review what he did. Comments? Note that if it was a 230 VAC circuit, the breakers should have been ganged so if either tripped, they both went off. However, now, the way it was hooked up is correct for seprate circuits. To be sure about all this, it would be a good idea to have a qualitifed electrician check it over. --- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/ Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/ +Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm | Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html Important: Anything sent to the email address in the message header above is ignored unless my full name AND either lasers or electronics is included in the subject line. Or, you can contact me via the Feedback Form in the FAQs. -- Wayne Watson (Nevada City, CA) Web Page: speckledwithStars.net |
#5
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
Yep, bad memory. There were black, green and white in the conduit.
PeterD wrote: On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser wrote: If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. Never, ever, use green for anything other than ground. Period. Say some idiot comes along in the future and gets killed because you used green for hot--you're on the hook for that one. Say the building inspector sees it? Use the wires the way they are intended to be used... -- Wayne Watson (Nevada City, CA) Web Page: speckledwithStars.net |
#6
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
W. Watson wrote:
Yep, bad memory. There were black, green and white in the conduit. PeterD wrote: On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser wrote: If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. Never, ever, use green for anything other than ground. Period. Say some idiot comes along in the future and gets killed because you used green for hot--you're on the hook for that one. Say the building inspector sees it? Use the wires the way they are intended to be used... That makes more sense, but I like your advice about calling the electrician. If I were doing this, I'd hook up my voltmeter and simply verify the original wiring. Likely, what I would measure would be line voltage from either the red or black wires, to either the bare or the white wire. This is an area where you don't want to be 'guessing'. If you don't have the proper equipment, you either need to get it, borrow it (and understand how it works) or let someone else do it. A little bit of knowledge (which you do appear to have) can be very dangerous in these situations. As to the wires in the conduit. If you really had just a white, green and bare wire, my advice would be to use the bare wire to pull in a new length of black wire. It wouldn't have been all that hard to do, and would have insured that everything remained legal and kosher. Thankfully, that issue has been resolved. Are electrical codes inspections required for new work in your locality? jak |
#7
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
|
#8
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
On 2/19/08 8:34 AM, in article
, "W. Watson" wrote: Sam Goldwasser wrote: "W. Watson" writes: A year ago I allowed a neighbor who was building a house next to us access to electricity in a small building on our property. He had an electrician put in an outside receptacle. A few weeks after he no longer had any need for it, I decided to use that as a way to get electricity 100' away as a new outlet for a pond pump and outdoor light. All the wire is in place and underground. It took me until now to finish off the connection at the building. Here's the situation. He connected the receptacle directly to the switch box in the building, and the wires a ground, red, black and white. I long ago, 10 months ago, disconnected those wires and taped them. The wiring I have underground to the pond area uses white, green, and ground. For 120 v, I believe the whites go together, and Better not. Green should ONLY be using for the (Safety) ground. Yes, bad memory. There is no bare copper. White is Neutral Black or red is Hot. Green or bare copper is ground. the green goes to black, correct? It appears that the red wire allows If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? Yes and No....... If it's for use by 240V equipment, then yes. But it is acceptable to connect each side of a 240V feed to half of a 120V duplex outlet, with the neutral common to both. Kitchens outlets are commonly wired this way. My shop is also wired this way. There are various versions depending on maximum current but at the very least, the prongs are oriented differently. Thanks. I think I'll get the the guy's phone number and call him. I have a feeling he didn't use the red. It was snipped off, but may have been taped. An oddity about this is that he apparently has the outside outlet on two switches in the switch box. Unless both are off, then they appear to be alive when either or both are on. When both are on, I get either 240v or 120v depending on which pair combo I measure. It is possible for me to contact the electrician, so maybe I can review what he did. Comments? Note that if it was a 230 VAC circuit, the breakers should have been ganged so if either tripped, they both went off. However, now, the way it was hooked up is correct for seprate circuits. To be sure about all this, it would be a good idea to have a qualitifed electrician check it over. --- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/ Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/ +Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm | Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html Important: Anything sent to the email address in the message header above is ignored unless my full name AND either lasers or electronics is included in the subject line. Or, you can contact me via the Feedback Form in the FAQs. |
#10
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
On 2/19/08 12:08 PM, in article
, "jakdedert" wrote: Don Bowey wrote: On 2/19/08 6:03 AM, in article , "PeterD" wrote: On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser wrote: If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. Never, ever, use green for anything other than ground. Period. Say some idiot comes along in the future and gets killed because you used green for hot--you're on the hook for that one. Say the building inspector sees it? Use the wires the way they are intended to be used... While you offer some good cautious advice, we do have a NEC case where a white wire can be designated as a hot wire by taping the ends black or red. IMO, if the green wire is *verified* at the breaker to be a hot lead AND the gauge and insulation types are valid, then I don't see a problem with color-taping *BOTH* ends black or red and using it as a hot wire. I guess I'm a little more cautious in my old age. I could 'maybe' get behind color-taping a wire with red tape. While probably legal, I'm dead-set against doing it with black. Trouble is, IMM, that black tape is so common that it could easily be overlooked or discounted at a casual glance. Red is a little different in that--being red--it might inspire at least caution, if not a full-stop and verification before going further. I've done it with Cam-loc (Cleco) connectors, but in those situations, the entire connector was covered with the correct color tape; and *all* of the conductors were black anyway. In any case, since the OP stated all the wires go through a conduit, I think I'd just replace the offending wire to code. jak Both red and black should raise one's awareness while working around hot, or even questionable, services. Thinking more on this though, I don't recall ever seeing green "power" wire. I wonder if the wire in the conduit is appliance wire (rubber outer cover with white, black, red, green stranded wires). If so, without checking the NEC, I don't think this wire correct at all for how it's being used. |
#11
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
Both red and black should raise one's awareness while working around hot, or even questionable, services. Thinking more on this though, I don't recall ever seeing green "power" wire. I wonder if the wire in the conduit is appliance wire (rubber outer cover with white, black, red, green stranded wires). If so, without checking the NEC, I don't think this wire correct at all for how it's being used. Red and black are both perfectly acceptable to use as hot. White may also be used in some circumstances but it must be marked with either red or black. Properly applied wire nuts do not normally need to be taped, so the only reason tape would be on a wire in a box is to mark the color. I'd have to check, but I seem to recall that it's forbidden to use a green wire for anything but ground, it's certainly not advisable. That said, the OP responded to say that he got the colors wrong and that black, white, and green are what he has, which is precisely what I'd expect for a 120V branch wired with THHN in conduit. I guess people missed that. |
#12
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
Don Bowey wrote:
On 2/19/08 12:08 PM, in article , "jakdedert" wrote: Don Bowey wrote: On 2/19/08 6:03 AM, in article , "PeterD" wrote: On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser wrote: If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. Never, ever, use green for anything other than ground. Period. Say some idiot comes along in the future and gets killed because you used green for hot--you're on the hook for that one. Say the building inspector sees it? Use the wires the way they are intended to be used... While you offer some good cautious advice, we do have a NEC case where a white wire can be designated as a hot wire by taping the ends black or red. IMO, if the green wire is *verified* at the breaker to be a hot lead AND the gauge and insulation types are valid, then I don't see a problem with color-taping *BOTH* ends black or red and using it as a hot wire. I guess I'm a little more cautious in my old age. I could 'maybe' get behind color-taping a wire with red tape. While probably legal, I'm dead-set against doing it with black. Trouble is, IMM, that black tape is so common that it could easily be overlooked or discounted at a casual glance. Red is a little different in that--being red--it might inspire at least caution, if not a full-stop and verification before going further. I've done it with Cam-loc (Cleco) connectors, but in those situations, the entire connector was covered with the correct color tape; and *all* of the conductors were black anyway. In any case, since the OP stated all the wires go through a conduit, I think I'd just replace the offending wire to code. jak Both red and black should raise one's awareness while working around hot, or even questionable, services. Thinking more on this though, I don't recall ever seeing green "power" wire. I wonder if the wire in the conduit is appliance wire (rubber outer cover with white, black, red, green stranded wires). If so, without checking the NEC, I don't think this wire correct at all for how it's being used. He's already stated his error in the colors. The conductors pulled were correct; white/black/green. I imagine all else is kosher as well. I don't know who pulled the wires, or why they weren't hooked up at the time. My reservation about color-taping was not directed at professionals, but at the odd homeowner 15 or 20 years down the line. The practice is apparently more common than I imagined, and--red or black--would flag itself to a pro. jak |
#13
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
My reservation about color-taping was not directed at professionals, but at the odd homeowner 15 or 20 years down the line. The practice is apparently more common than I imagined, and--red or black--would flag itself to a pro. The most common place you see this is in switch legs where power is supplied directly to the ceiling box where the light fixture is mounted and then a separate drop goes from that to the switch. In that case both wires in that drop are technically hot, so the white one gets taped black and connects to the light fixture. The ones that get me are those houses where someone used whatever color wire they had on hand for whatever, I see that in cars a lot of times too. Always verify, and never underestimate the crazy things that some previous person may have done. When I bought my house, all the switches downstairs were on the neutral side which caused me to get bit pretty good once. Yes, I should have shut off the breaker. |
#14
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
"W. Watson" writes:
Yep, bad memory. There were black, green and white in the conduit. So, black-black, white-white, bare copper to bare copper (or green). And, of course, splices using proper size solderless connectors ("Wire Nuts") or other acceptable means, inside proper elecrical boxes! --- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/ Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/ +Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm | Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html Important: Anything sent to the email address in the message header above is ignored unless my full name AND either lasers or electronics is included in the subject line. Or, you can contact me via the Feedback Form in the FAQs. PeterD wrote: On 19 Feb 2008 08:22:42 -0500, Sam Goldwasser wrote: If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. Never, ever, use green for anything other than ground. Period. Say some idiot comes along in the future and gets killed because you used green for hot--you're on the hook for that one. Say the building inspector sees it? Use the wires the way they are intended to be used... -- Wayne Watson (Nevada City, CA) Web Page: speckledwithStars.net |
#15
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
Don Bowey writes:
On 2/19/08 8:34 AM, in article , "W. Watson" wrote: Sam Goldwasser wrote: "W. Watson" writes: A year ago I allowed a neighbor who was building a house next to us access to electricity in a small building on our property. He had an electrician put in an outside receptacle. A few weeks after he no longer had any need for it, I decided to use that as a way to get electricity 100' away as a new outlet for a pond pump and outdoor light. All the wire is in place and underground. It took me until now to finish off the connection at the building. Here's the situation. He connected the receptacle directly to the switch box in the building, and the wires a ground, red, black and white. I long ago, 10 months ago, disconnected those wires and taped them. The wiring I have underground to the pond area uses white, green, and ground. For 120 v, I believe the whites go together, and Better not. Green should ONLY be using for the (Safety) ground. Yes, bad memory. There is no bare copper. White is Neutral Black or red is Hot. Green or bare copper is ground. the green goes to black, correct? It appears that the red wire allows If all you have in the conduit is white, green, and bare copper, then that is your only choice but that green wire has to be unambiguously labeled as Hot by painting the insulation near the ends black. And, it had better be the proper gauge. for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? Yes and No....... If it's for use by 240V equipment, then yes. But it is acceptable to connect each side of a 240V feed to half of a 120V duplex outlet, with the neutral common to both. Kitchens outlets are commonly wired this way. My shop is also wired this way. But this is a 115 VAC outlet providing 115 VAC, not a 230 VAC outlet. Only those with Frankstein tendencies will jerryrig a 230 VAC appliance into a split duplex outlet!!! --- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/ Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/ +Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm | Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html Important: Anything sent to the email address in the message header above is ignored unless my full name AND either lasers or electronics is included in the subject line. Or, you can contact me via the Feedback Form in the FAQs. |
#16
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
|
#17
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
Don Bowey writes:
On 2/19/08 4:55 PM, in article , "Sam Goldwasser" wrote: Don Bowey writes: On 2/19/08 8:34 AM, in article , "W. Watson" wrote: (snip) for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? Yes and No....... If it's for use by 240V equipment, then yes. But it is acceptable to connect each side of a 240V feed to half of a 120V duplex outlet, with the neutral common to both. Kitchens outlets are commonly wired this way. My shop is also wired this way. But this is a 115 VAC outlet providing 115 VAC, not a 230 VAC outlet. It isn't used to provide 240V service. It provides two 120V outlets, each with it's own 120V feed from opposite sides of the breaker box (separate phase). Only those with Frankstein tendencies will jerryrig a 230 VAC appliance into a split duplex outlet!!! You're entitled to your opinion, but it's a standard wiring configuration straight out of the NEC. You're saying that NEC recommends jerryrigging a special cord with two plugs to get 230 VAC from a split 115 VAC outlet? --- sam | Sci.Electronics.Repair FAQ: http://www.repairfaq.org/ Repair | Main Table of Contents: http://www.repairfaq.org/REPAIR/ +Lasers | Sam's Laser FAQ: http://www.repairfaq.org/sam/lasersam.htm | Mirror Sites: http://www.repairfaq.org/REPAIR/F_mirror.html Important: Anything sent to the email address in the message header above is ignored unless my full name AND either lasers or electronics is included in the subject line. Or, you can contact me via the Feedback Form in the FAQs. |
#18
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
On 2/20/08 5:25 AM, in article , "Sam
Goldwasser" wrote: Don Bowey writes: On 2/19/08 4:55 PM, in article , "Sam Goldwasser" wrote: Don Bowey writes: On 2/19/08 8:34 AM, in article , "W. Watson" wrote: (snip) for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? Yes and No....... If it's for use by 240V equipment, then yes. But it is acceptable to connect each side of a 240V feed to half of a 120V duplex outlet, with the neutral common to both. Kitchens outlets are commonly wired this way. My shop is also wired this way. But this is a 115 VAC outlet providing 115 VAC, not a 230 VAC outlet. It isn't used to provide 240V service. It provides two 120V outlets, each with it's own 120V feed from opposite sides of the breaker box (separate phase). Only those with Frankstein tendencies will jerryrig a 230 VAC appliance into a split duplex outlet!!! You're entitled to your opinion, but it's a standard wiring configuration straight out of the NEC. You're saying that NEC recommends jerryrigging a special cord with two plugs to get 230 VAC from a split 115 VAC outlet? No the NEC doesn't, but you apparently can't get past what you think. It is not jerryrigging to provide two 120V feeds using a 3-wire with ground (Bk, Red, Wht, & bare copper) cable. The NEC does not describe all the ways a configuration might be used; that is left to you, which you have done well. |
#19
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
No the NEC doesn't, but you apparently can't get past what you think. It is not jerryrigging to provide two 120V feeds using a 3-wire with ground (Bk, Red, Wht, & bare copper) cable. The NEC does not describe all the ways a configuration might be used; that is left to you, which you have done well. He never did say that wiring of the outlet was incorrect, just that use. You guys are on the same page and arguing about different things. |
#20
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
On 2/20/08 10:24 AM, in article ,
"Thor" wrote: On Wed, 20 Feb 2008 07:41:49 -0800, Don Bowey wrote: On 2/20/08 5:25 AM, in article , "Sam Goldwasser" wrote: Don Bowey writes: On 2/19/08 4:55 PM, in article , "Sam Goldwasser" wrote: Don Bowey writes: On 2/19/08 8:34 AM, in article , "W. Watson" wrote: (snip) for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? Yes and No....... If it's for use by 240V equipment, then yes. But it is acceptable to connect each side of a 240V feed to half of a 120V duplex outlet, with the neutral common to both. Kitchens outlets are commonly wired this way. My shop is also wired this way. But this is a 115 VAC outlet providing 115 VAC, not a 230 VAC outlet. It isn't used to provide 240V service. It provides two 120V outlets, each with it's own 120V feed from opposite sides of the breaker box (separate phase). Only those with Frankstein tendencies will jerryrig a 230 VAC appliance into a split duplex outlet!!! You're entitled to your opinion, but it's a standard wiring configuration straight out of the NEC. You're saying that NEC recommends jerryrigging a special cord with two plugs to get 230 VAC from a split 115 VAC outlet? No the NEC doesn't, but you apparently can't get past what you think. It is not jerryrigging to provide two 120V feeds using a 3-wire with ground (Bk, Red, Wht, & bare copper) cable. The NEC does not describe all the ways a configuration might be used; that is left to you, which you have done well. I am sure you can not feed a split duplex outlet with 240 volts if the outlet is only rated for 125 volts. Article 410-56(a) Article 110-3 Each outlet of the pair is fed 120V NOT 240V. Only the grounded conductor and the grounding conductor have specified colors. Article 200-6 It is covered in other Articles, also. |
#21
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
Thor wrote:
I am sure you can not feed a split duplex outlet with 240 volts if the outlet is only rated for 125 volts. Article 410-56(a) Article 110-3 You are feeding 120 VAC to each outlet, with a common neutral. It's called a split outlet. There are also combo duplex outlets with a 240 VAC and a 120 VAC receptacle used in commercial buildings to plug in large floor buffers and vacs. http://www.hubbellcatalog.com/wiring/catalogpages/Page-A24.pdf part numbers HBL5492 & HBL5492I at: http://www.hubbellcatalog.com/wiring/section-a-ss.asp?FAM=Straight_Blade&SORD=102+822&FT_102=1350 8&FT_822=7663&SUBMIT.x=28&SUBMIT.y=13 Leviton has their 5031-I, 5842-I, 5844 on page 51 of http://www.leviton.com/OA_HTML/ibcGetAttachment.jsp?cItemId=u4XWH2gnFVIs9yeepxlPk w&label=IBE&appName=IBE which is a 30.691 Mbyte download. Only the grounded conductor and the grounding conductor have specified colors. Article 200-6 -- Service to my country? Been there, Done that, and I've got my DD214 to prove it. Member of DAV #85. Michael A. Terrell Central Florida |
#22
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
"W. Watson" wrote in message ... For 120 v, I believe the whites go together, and the green goes to black, correct? Unless you are DAMN SURE you're the only one who will EVER touch this wiring, and that you will 100% REMEMBER that the green is hot, then bite the bullet and pull a black strand through the conduit. Green means safe to electricians, you don't want somebody down the road to shock and potentially injure themselves because of the ambiguous color coding. It appears that the red wire allows for 240v, so I'll just tape it off. I'm still a bit puzzled why the guy used red at all. Doesn't a 240 v outlet have a socket entirely different than one for 120v? The red strand is often used to run a 2nd hot, so that you can run two circuits with one run of 4-strand wire. On a 240V 4-wire circuit, red and black are opposite poles, with 240v between them. white is neutral. red to white and/or black to white would both give you 120v. Red to black gives 240v. An oddity about this is that he apparently has the outside outlet on two switches in the switch box. Unless both are off, then they appear to be alive when either or both are on. When both are on, I get either 240v or 120v depending on which pair combo I measure. It is possible for me to contact the electrician, so maybe I can review what he did. Comments? -- It's so that you can run a separate circuit to each plug-in on the receptacle. Four conductors must have been run from the main panel in the house to the subpanel. This is good. It means you can wire up a 240v circuit if you need it. Wayne Watson (Nevada City, CA) Web Page: speckledwithStars.net |
#23
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
|
#24
Posted to sci.electronics.repair
|
|||
|
|||
Red, Green, Black, and White Wires
PeterD wrote:
drivelsnip You are a record moron... And for that matter, is green wire capable of passing hot AC voltage? Do the electrons in green coated wire function in the same manner as the electrons in a black or white coated wire? Do the electrons change if you take black spray paint and paint a green wire black, or white? OOPS, how DO you paint a wire white with black spray paint? Hey, Phil, you are so much better than I am at this, please add to my comments! ....or just don't feed the trolls. They starve. Problem solved. jak |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
White, Black, Green, Blue and RED lighting wire ? | Home Repair | |||
gfci three black and two white wires?? | Home Repair | |||
Junction Box has no white wires celing light help needed | Home Repair | |||
Grounding Of Ground Wires In An Electrical Gang Box (how to handle the green ground wires) | Home Repair | |||
Help! What are the black wires for? | UK diy |