Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Ray
 
Posts: n/a
Default Grounding Metal Building

I erected a 30 x 24 foot metal building and I've read somewhere that it may
need to be grounded. If so, how would I go about this.

Thanks in advance....


  #2   Report Post  
Edwin Pawlowski
 
Posts: n/a
Default


"Ray" wrote in message
news:yAeSd.10812$Ps.5172@okepread06...
I erected a 30 x 24 foot metal building and I've read somewhere that it may
need to be grounded. If so, how would I go about this.

Thanks in advance....


Your building inspector will have the specifications for your town. In
general, it is driving a grounding stake into the earth and wiring it to the
building.


  #3   Report Post  
HorneTD
 
Posts: n/a
Default

Ray wrote:
I erected a 30 x 24 foot metal building and I've read somewhere that it may
need to be grounded. If so, how would I go about this.

Thanks in advance....


Is the building merely metal skinned or does it have a metal frame as
well? What is the foundation for the building and is it steel
reinforced with reinforcing bars? Were is the building located? I
don't want the street address but I need the state in order to gage the
lightning exposure.

Under the US NEC the metal frame of the building must be bonded to the
grounded current carrying conductor of the electrical service that most
of us call the neutral. If the building has a metal frame that is
bolted to a concrete foundation it may be grounded already by the
reinforcing steel in the footing. If the footer does not contain any
rebar and the frame is therefore not effectively grounded then a three
foot trench should be dug around the entire periphery of the building to
permit installation of a ground ring. A ground ring is a number two
American Wire Gage or larger conductor that is buried around a building
at a depth of at least thirty inches. Best practice is to bury it below
the permanent moisture level. From the ground ring a Grounding
Electrode Conductor would be run to the service disconnecting means
enclosure as well as to each major column of the frame of the building.
If the permanent moisture level is well below the surface of the earth
then sectional ground rods should be driven at each corner of the
building to below the permanent moisture level if the building is in a
lightning prone area. These rods would then be bonded to the ground ring.
--
Tom H
  #4   Report Post  
SQLit
 
Posts: n/a
Default


"Ray" wrote in message
news:yAeSd.10812$Ps.5172@okepread06...
I erected a 30 x 24 foot metal building and I've read somewhere that it

may
need to be grounded. If so, how would I go about this.

Thanks in advance....


Depending on how you constructed the foundation the building might be
considered grounded now. Electrical circuits excluded.


  #5   Report Post  
tom
 
Posts: n/a
Default

On Mon, 21 Feb 2005 15:23:08 GMT, HorneTD
wrote:

Ray wrote:
I erected a 30 x 24 foot metal building and I've read somewhere that it may
need to be grounded. If so, how would I go about this.

Thanks in advance....


Is the building merely metal skinned or does it have a metal frame as
well? What is the foundation for the building and is it steel
reinforced with reinforcing bars? Were is the building located? I
don't want the street address but I need the state in order to gage the
lightning exposure.

Under the US NEC the metal frame of the building must be bonded to the
grounded current carrying conductor of the electrical service that most
of us call the neutral. If the building has a metal frame that is
bolted to a concrete foundation it may be grounded already by the
reinforcing steel in the footing. If the footer does not contain any
rebar and the frame is therefore not effectively grounded then a three
foot trench should be dug around the entire periphery of the building to
permit installation of a ground ring. A ground ring is a number two
American Wire Gage or larger conductor that is buried around a building
at a depth of at least thirty inches. Best practice is to bury it below
the permanent moisture level. From the ground ring a Grounding
Electrode Conductor would be run to the service disconnecting means
enclosure as well as to each major column of the frame of the building.
If the permanent moisture level is well below the surface of the earth
then sectional ground rods should be driven at each corner of the
building to below the permanent moisture level if the building is in a
lightning prone area. These rods would then be bonded to the ground ring.



Good Post, I've noticed many people use the word 'grounded' and
'bonded' the same when they are actually different.

thanks,

tom @ www.BookmarkAdmin.com





  #6   Report Post  
Ray
 
Posts: n/a
Default

Tom H,

I live in South Louisiana and the building is metal framed and skinned with
the frames being bolted to anchor bolts that were placed in the concrete
slab. Rebar was used in the footer perimeter. (Would the anchor bolts need
to be touching the rebar to be considered grounded as per your explanation
??)

If I satisfy the grounding requirements, does that mean that I will still
need to "bond" the building to the ground rod ?? Could you explain how to
bond to the frames ??

Thanks,
Ray

"HorneTD" wrote in message
nk.net...
Ray wrote:
I erected a 30 x 24 foot metal building and I've read somewhere that it

may
need to be grounded. If so, how would I go about this.

Thanks in advance....


Is the building merely metal skinned or does it have a metal frame as
well? What is the foundation for the building and is it steel
reinforced with reinforcing bars? Were is the building located? I
don't want the street address but I need the state in order to gage the
lightning exposure.

Under the US NEC the metal frame of the building must be bonded to the
grounded current carrying conductor of the electrical service that most
of us call the neutral. If the building has a metal frame that is
bolted to a concrete foundation it may be grounded already by the
reinforcing steel in the footing. If the footer does not contain any
rebar and the frame is therefore not effectively grounded then a three
foot trench should be dug around the entire periphery of the building to
permit installation of a ground ring. A ground ring is a number two
American Wire Gage or larger conductor that is buried around a building
at a depth of at least thirty inches. Best practice is to bury it below
the permanent moisture level. From the ground ring a Grounding
Electrode Conductor would be run to the service disconnecting means
enclosure as well as to each major column of the frame of the building.
If the permanent moisture level is well below the surface of the earth
then sectional ground rods should be driven at each corner of the
building to below the permanent moisture level if the building is in a
lightning prone area. These rods would then be bonded to the ground ring.
--
Tom H



  #7   Report Post  
DanG
 
Posts: n/a
Default

I don't know how fancy you want to get. I built a couple of
buildings for a major gas pumping outfit here. They required the
full ground ring around the perimeter buried 4' minimum with a
grounding stinger cad welded to the building ring and to each
column. Cad welding is explained he
http://www.erico.com/products.asp?folderid=138
but is basically a molten metal connection that uses powdered
copper oxide and aluminum that is ignited. Your electrician
should be familiar with the system.

These things can be accomplished with mechanical fasteners.

(top posted for your convenience)
^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
Keep the whole world singing . . . .
DanG (remove the sevens)




"Ray" wrote in message
news:rTxSd.10896$Ps.3265@okepread06...
Tom H,

I live in South Louisiana and the building is metal framed and
skinned with
the frames being bolted to anchor bolts that were placed in the
concrete
slab. Rebar was used in the footer perimeter. (Would the
anchor bolts need
to be touching the rebar to be considered grounded as per your
explanation
??)

If I satisfy the grounding requirements, does that mean that I
will still
need to "bond" the building to the ground rod ?? Could you
explain how to
bond to the frames ??

Thanks,
Ray

"HorneTD" wrote in message
nk.net...
Ray wrote:
I erected a 30 x 24 foot metal building and I've read
somewhere that it

may
need to be grounded. If so, how would I go about this.

Thanks in advance....


Is the building merely metal skinned or does it have a metal
frame as
well? What is the foundation for the building and is it steel
reinforced with reinforcing bars? Were is the building
located? I
don't want the street address but I need the state in order to
gage the
lightning exposure.

Under the US NEC the metal frame of the building must be bonded
to the
grounded current carrying conductor of the electrical service
that most
of us call the neutral. If the building has a metal frame that
is
bolted to a concrete foundation it may be grounded already by
the
reinforcing steel in the footing. If the footer does not
contain any
rebar and the frame is therefore not effectively grounded then
a three
foot trench should be dug around the entire periphery of the
building to
permit installation of a ground ring. A ground ring is a
number two
American Wire Gage or larger conductor that is buried around a
building
at a depth of at least thirty inches. Best practice is to bury
it below
the permanent moisture level. From the ground ring a Grounding
Electrode Conductor would be run to the service disconnecting
means
enclosure as well as to each major column of the frame of the
building.
If the permanent moisture level is well below the surface of
the earth
then sectional ground rods should be driven at each corner of
the
building to below the permanent moisture level if the building
is in a
lightning prone area. These rods would then be bonded to the
ground ring.
--
Tom H





Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Dryer Old Cord RCAlford Home Repair 9 October 3rd 04 02:11 AM
Building a pole barn shop Don Home Repair 13 April 15th 04 05:51 PM
Earth Bondng Adrian Simpson UK diy 8 March 21st 04 11:58 PM
Comments on Steel Buildings for Workshop Pops Woodworking 12 November 6th 03 03:35 PM
Building Warrants - Buying Flat Without L Reid UK diy 6 July 16th 03 03:54 PM


All times are GMT +1. The time now is 04:41 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"