Default I am installing a subpanel in the garage.

You might want to consider #4 wire with a 70 amp main breaker. I don't know
what you will be using the 50 amp receptacle for, but if you draw 40 amps
the 60 amp main will be at its maximum continuous load. Circuit breakers
are only rated for 80% continuous load.

John Grabowski
http://www.mrelectrician.tv



"Ignoramus14233" wrote in message
...
Thanks to all gentlemen who steered me in the right direction.

I am going to install a real subpanel in the garage, I will use
3/4" metallic conduit, 6 gauge wires.

The subpanel will be protected by a 60 amp breaker on the main
panel. It will have the following outlets attached to it, with
appropriate breakers:

1. 50A 220V range receptacle
2. Regular 20A 220V receptacle
3. Two regular 20 A 110V outlets.

i


  #2   Report Post  
HorneTD
 
Posts: n/a
Default

John Grabowski wrote:
"Ignoramus14233" wrote in message
...

Thanks to all gentlemen who steered me in the right direction.

I am going to install a real subpanel in the garage, I will use
3/4" metallic conduit, 6 gauge wires.

The subpanel will be protected by a 60 amp breaker on the main
panel. It will have the following outlets attached to it, with
appropriate breakers:

1. 50A 220V range receptacle
2. Regular 20A 220V receptacle
3. Two regular 20 A 110V outlets.

i

You might want to consider #4 wire with a 70 amp main breaker. I
don't know what you will be using the 50 amp receptacle for, but if
you draw 40 amps the 60 amp main will be at its maximum continuous
load. Circuit breakers are only rated for 80% continuous load.

John Grabowski
http://www.mrelectrician.tv

[Continuous Load. A load where the maximum current is expected to
continue for 3 hours or more.] Copyright 2002 National Fire Protection
Association

As you can see the definition of continuous is three hours or more.
--
Tom H
  #3   Report Post  
HorneTD
 
Posts: n/a
Default

On Mon, 3 Jan 2005 10:32:32 -0500, John Grabowski
wrote:

You might want to consider #4 wire with a 70 amp main breaker. I
don't know what you will be using the 50 amp receptacle for, but
if you draw 40 amps the 60 amp main will be at its maximum
continuous load. Circuit breakers are only rated for 80%
continuous load.



50 amp receptacle will be used for testing military surplus stuff,
or, alternatively, later, for a phase converter or some such.
Supposedly, #6 wires are rated for 75 amps.


i

You need to be aware that the 75 ampere value given in table 310.16
Allowable Ampacities of Insulated Conductors Rated 0 Through 2000 Volts,
60°C Through 90°C are not achievable in actual practice. This is because
everything that the conductor connects to has to be listed to be used at
the ninety degree centigrade temperature. In general such terminals are
not readily available in the market place and that column is used as a
starting point for derating the wire for high ambient temperatures or
for more than three current carrying conductors in a raceway or cable.
The values in the seventy five degree column of the table are the actual
maximums that can be practically achieved. Since the 65 ampere value is
not a standard size of Over Current Protective Device (OCPD) you are
allowed to use a seventy ampere breaker but the idea is that the circuit
will only draw sixty five amperes under the designed operating
conditions. If you were actually going to draw the full seventy amperes
you would go up to the next wire size.
--
Tom H
  #4   Report Post  
SQLit
 
Posts: n/a
Default


"HorneTD" wrote in message
nk.net...
On Mon, 3 Jan 2005 10:32:32 -0500, John Grabowski
wrote:

You might want to consider #4 wire with a 70 amp main breaker. I
don't know what you will be using the 50 amp receptacle for, but
if you draw 40 amps the 60 amp main will be at its maximum
continuous load. Circuit breakers are only rated for 80%
continuous load.



50 amp receptacle will be used for testing military surplus stuff,
or, alternatively, later, for a phase converter or some such.
Supposedly, #6 wires are rated for 75 amps.


i

You need to be aware that the 75 ampere value given in table 310.16
Allowable Ampacities of Insulated Conductors Rated 0 Through 2000 Volts,
60°C Through 90°C are not achievable in actual practice. This is because
everything that the conductor connects to has to be listed to be used at
the ninety degree centigrade temperature. In general such terminals are
not readily available in the market place and that column is used as a
starting point for derating the wire for high ambient temperatures or
for more than three current carrying conductors in a raceway or cable.
The values in the seventy five degree column of the table are the actual
maximums that can be practically achieved. Since the 65 ampere value is
not a standard size of Over Current Protective Device (OCPD) you are
allowed to use a seventy ampere breaker but the idea is that the circuit
will only draw sixty five amperes under the designed operating
conditions. If you were actually going to draw the full seventy amperes
you would go up to the next wire size.
--
Tom H



Absolutely great answer Tom...



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installing power sockets and light into an adjacent garage Andy Hide UK diy 0 July 21st 03 10:00 AM


All times are GMT +1. The time now is 11:38 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"