David:
DD I would like to put my computer equipment on its own circuit. Would I need DD a 15 or 20 amp breaker to do this? Are there any restrictions as far as ho DD many breakers can be in the box? I know there is room for more. What gaug DD wiring would this require? I'd go with the 20 Amp circuit "just because" it's a little more robust in case you need more current later. Maybe it's a little cool in the Computer Room and you need to take the chill out by running an electric heater. And for your next question, no, you do not have to use 20A rated outlets on a 20 Amp circuit - the 15 Amp duplex outlets are fine. BTW, speaking of outlets, you might want to have a few more than one or two per wall for the equipment. Also plan ahead to position the outlets where you need them now and where you may need them int he future should you re-arrange things. Easier and cheaper to plan ahead for the future now. - ¯ barry.martinþATþthesafebbs.zeppole.com ® * A horse may go freely to water, but a pencil must be lead. --- þ RoseReader 2.52á P003186 þ The Safe BBS þ Bettendorf, IA 563-359-1971 --- þ RIMEGate(tm)/RGXMod V1.13 at BBSWORLD * |
#2
![]() |
|||
|
|||
![]()
The bull**** is certainly flying around here.
Take a look at 310-16 in the NEC and you will see that 14ga wire is really rated at 20a. . Article 240.4(D) limits the O/C device to 15a so people who try these "run it till it trips" experiments or lifestyles are not really creating a hazard. If you can load a 15a breaker/14ga copper circuit enought to warm the wire you have a defective breaker. |
#3
![]() |
|||
|
|||
![]()
If you can load a 15a breaker/14ga copper circuit enought to warm the
wire you have a defective breaker. Breakers are NEVER defective? That's good to know! Thanks!!! If you have a defective breaker it doesn't matter how big your wire is. Available fault current in a home is in the thousands of amps. (only limited by the size of the service drop) That was not the discussion. |
#4
![]() |
|||
|
|||
![]()
And for your next question, no, you do not have to use 20A rated
outlets on a 20 Amp circuit - the 15 Amp duplex outlets are fine. Check your local building code. Up here in Ontario, you _must_ use 20A rated outlets if you have a 20A breaker. Hmmm... Hold on... I've said that a few times but now that I think about it, the part of the code I'm thinking was dealing with a kitchen countertop where you ether had to have a split-circuit recepticle or a single 20A circuit (complete with 20A outlet). It's possible that it's not required to have a 20A outlet on a 20A circuit in other situations. But why take the chance? It doesn't make good sense to use a 15A rated part in one place when the your only piece of protection (the breaker) is rated at 20A. Plus, if you ever had a 20A piece of equipment, at least you'd have a recepticle that would take it. Brian ( ) ------------------------------------------------------------------------------- Good encryption is not sufficient for good security. http://www.freeswan.org/ ------------------------------------------------------------------------------- ( Couldn't verify my signature? Use http://www.precidia.com/precidia.crt ) |
#5
![]() |
|||
|
|||
![]() "Brian White" wrote in message ... And for your next question, no, you do not have to use 20A rated outlets on a 20 Amp circuit - the 15 Amp duplex outlets are fine. Check your local building code. Up here in Ontario, you _must_ use 20A rated outlets if you have a 20A breaker. Maybe so in Canada, but in the USA we are certainly allowed to install 15 amp outlets on 20 amp circuits. In fact, you can install as many on a circuit as you wish. Homebuilders do it all the time. In fact, we get our electrical jollies doing it. Hmmm... Hold on... I've said that a few times but now that I think about it, the part of the code I'm thinking was dealing with a kitchen countertop where you ether had to have a split-circuit recepticle or a single 20A circuit (complete with 20A outlet). Again, maybe in Canada, not in USA. There are 20 amp wiring requirements for kitchens, but no requirement for a 20 amp outlet. Last time I checked, my toaster, blender, coffe maker, electric skillet, and anything else I am likely to plug in my kitchen doesn't have the kind of plug that requires a 20 amp outlet. It's possible that it's not required to have a 20A outlet on a 20A circuit in other situations. In mainstream house wiring it's really not required anywhere, with the possible exception for a dedicated circuit for something like an air compressor or other high draw device. Again, that's NEC. Things up there may be different. But why take the chance? What chance? There is absolutely NO DANGER IN PUTTING 15 AMP OUTLETS ON 20 AMP WIRING. NONE, NADA, ZILCH. Keep in mind that a 15 amp outlet won't allow anything to be plugged into it that will draw over 15 amps. For that very reason, it is not allowed to put a 20 amp outlet on a 15 amp circuit. This is where you could potentially plug something in that would over draw the wiring. It doesn't make good sense to use a 15A rated part in one place when the your only piece of protection (the breaker) is rated at 20A. You clearly don't understand the concept. Let me repeat myself. A 15 amp outlet will not allow anything to be plugged into it that would allow the wiring, outlet, and breaker. Power is drawn from the load, not pushed from the supply. A 15 amp outlet is fine on a 20 amp circuit. The outlet wont melt, explode, or anything, because nothing that will draw too much current will be plugged into it. Get it yet? Plus, if you ever had a 20A piece of equipment, at least you'd have a recepticle that would take it. Please take inventory of everything you own, and list what you have that has the special plug configuration that requires a 20 amp outlet. I'm not even sure what type of appliance, tool, or widget this would be. By the way, your other post was really amusing. Where did you get that 240 amp kitchen code requirement? Brian I don't know about the Canadian electrical code, but here in the USA, it's And you'd be taking ABSOLUTELY NO CHANCES by doing this. All you'd be doing is what home builders do all over the place. I'm not even sure what kind of appliance even has the plug configuration that requires a 20 amp outlet. What makes no sense is spending a pile of money on 20 amp outlets when you don't need them. |
#6
![]() |
|||
|
|||
![]()
And for your next question, no, you do not have to use 20A rated
outlets on a 20 Amp circuit - the 15 Amp duplex outlets are fine. Check your local building code. Up here in Ontario, you _must_ use 20A rated outlets if you have a 20A breaker. Maybe so in Canada, but in the USA we are certainly allowed to install 15 amp outlets on 20 amp circuits. In fact, you can install as many on a circuit as you wish. Homebuilders do it all the time. In fact, we get our electrical jollies doing it. As somebody pointed out, even "15A" recepticles are rated for 20A feed- through. That's what is important. They're not not configured/rated for 20A appliances. Hmmm... Hold on... I've said that a few times but now that I think about it, the part of the code I'm thinking was dealing with a kitchen countertop where you ether had to have a split-circuit recepticle or a single 20A circuit (complete with 20A outlet). Again, maybe in Canada, not in USA. There are 20 amp wiring requirements for kitchens, but no requirement for a 20 amp outlet. Last time I checked, my toaster, blender, coffe maker, electric skillet, and anything else I am likely to plug in my kitchen doesn't have the kind of plug that requires a 20 amp outlet. I know. I didn't understand why a 20A outlet was necessary either, but it's "code" and if I wanted to pass my inspection... In mainstream house wiring it's really not required anywhere, with the possible exception for a dedicated circuit for something like an air compressor or other high draw device. Again, that's NEC. Things up there may be different. And those devices should have 20A plugs if they're going to draw a 20A surge. But why take the chance? What chance? There is absolutely NO DANGER IN PUTTING 15 AMP OUTLETS ON 20 AMP WIRING. NONE, NADA, ZILCH. Keep in mind that a 15 amp outlet won't allow anything to be plugged into it that will draw over 15 amps. For that very reason, it is not allowed to put a 20 amp outlet on a 15 amp circuit. This is where you could potentially plug something in that would over draw the wiring. Yes, there IS A DANGER _if_ at outlet were only rated for 15A. However, since a 15A outlet is still rated to handle 20A of current (though not to a single device), then you're still okay. We're in violent agreement here. grin It doesn't make good sense to use a 15A rated part in one place when the your only piece of protection (the breaker) is rated at 20A. You clearly don't understand the concept. Let me repeat myself. A 15 amp outlet will not allow anything to be plugged into it that would allow the wiring, outlet, and breaker. Power is drawn from the load, not pushed from the supply. A 15 amp outlet is fine on a 20 amp circuit. The outlet wont melt, explode, or anything, because nothing that will draw too much current will be plugged into it. Note that what you say here is technically wrong. NO simple outlet protects against things being plugged in to it. I could easily add a power bar or string Christmas lights together and try to draw more than 15A from a single socket. It may make things more difficult (for example not allowing a 20A plug to fit) but _all_ protection comes from the CB in the panel, not the outlet (at least, not a standard simple one). But, since a 15A outlet is actually rated for 20A current it's fine to use on a 20A circuit. I did not know this when I made my original post. Get it yet? I do. Do you? Plus, if you ever had a 20A piece of equipment, at least you'd have a recepticle that would take it. Please take inventory of everything you own, and list what you have that has the special plug configuration that requires a 20 amp outlet. I'm not even sure what type of appliance, tool, or widget this would be. Mostly shop equipment; a lathe for example might require 20A. By the way, your other post was really amusing. Where did you get that 240 amp kitchen code requirement? - every appliance has to have it's own 15A circuit: dishwasher, garbage disposal, fridge, microwave 60A - countertop: split circuit or 20A, every 6 feet, adjacent must be on different circuits, next to sink must be GFI: 1 x 15A@240V-split, 2 x 20A (GFI outlets) 70A @ 120V - stove/oven: 40A (required present even if using gas) oven doesn't draw that much, cooktop is gas 40A @ 240V - lights: must be on separate circuit one circuit for all lights 15A - smoke / explosive gas detector separate circuit if running 3-wire "ring all" config 15A ============ 240A @ 120V The panel in the basement is 100A @ 240V. You can see the history of the renovation he http://pobox.com/~bcwhite/beaumaris/kitchen/ It _is_ actually finished now... I just haven't finished the write-up. Brian ( ) ------------------------------------------------------------------------------- Leave it to the computer industry to shorten "Year 2000" to "Y2K". It's that sort of thinking that led to the problem in the first place. ------------------------------------------------------------------------------- ( Couldn't verify my signature? Use http://www.precidia.com/precidia.crt ) |
#7
![]() |
|||
|
|||
![]()
same gauge may have quite different specs as far as resistance. The type of
configuration, flexibility, flex fatigue, and the cover also make a difference. how does the cover make a differance? |
#8
![]() |
|||
|
|||
![]()
Power is drawn from the load, not pushed from the supply.
It occurred to me later that this is incorrect. Power _is_ pushed from the supply (with a force of approximately 120V). It's how well the load resists this push that determines how much current it will pass. Open air resists it very well; copper wire does not. Voltage is a potential energy, much like (to use a frequent analogy) a lake at the top of a waterfall. As it falls, the potential is converted to heat, motion, whatever by the mechanisim through which the current passes. Brian ( ) ------------------------------------------------------------------------------- Making a living is not the same as making a life. ------------------------------------------------------------------------------- ( Couldn't verify my signature? Use http://www.precidia.com/precidia.crt ) |