trader_4 October 11th 20 03:39 PM

NIMA 14-50
 
On Sunday, October 11, 2020 at 6:38:22 AM UTC-4, gary wrote:
On 10/11/20 1:52 AM, Eli Sidwell Iii wrote:
Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral.



Using the conduit as a neutral is dangerous.Â* I'd fire that clowntractor and do it right.


That about sums that up. After all the discussion here about how to do it
right, this is how it winds up. It's a clear and major code violation to
be using the conduit as the neutral, surprising a licensed electrician
would ever do it.




Ralph Mowery October 11th 20 03:42 PM

NIMA 14-50
 
In article , says...
On 10/11/20 1:52 AM, Eli Sidwell Iii wrote:
Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral.



Using the conduit as a neutral is dangerous.* I'd fire that clowntractor and do it right.





It is bad enough to use conduit as a ground, but crazy to use it for the
neutral.

Not sure who to report the contractor to,but I think I would try to
find someone to report that to. Maybe get a building inspector out to
look at it.


It sounds like a fellow I worked with. He got his electrical license on
the third try to do some work to make extra money . From some of the
stuff he tells on himself, I would not let him change a battery in a one
cell flashlight. He always complains on how the inspector is always
turning his word down.


[email protected] October 11th 20 09:27 PM

NIMA 14-50
 
On Sat, 10 Oct 2020 22:52:52 -0700 (PDT), Eli Sidwell Iii
wrote:

On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks

Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850

I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?


I doubt it really uses the neutral so you are probably good to go. It
should still be a 3 wire receptacle tho.

[email protected] October 11th 20 09:33 PM

NIMA 14-50
 
On Sun, 11 Oct 2020 10:42:44 -0400, Ralph Mowery
wrote:

In article , says...
On 10/11/20 1:52 AM, Eli Sidwell Iii wrote:
Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral.



Using the conduit as a neutral is dangerous.Â* I'd fire that clowntractor and do it right.





It is bad enough to use conduit as a ground, but crazy to use it for the
neutral.

Not sure who to report the contractor to,but I think I would try to
find someone to report that to. Maybe get a building inspector out to
look at it.


It sounds like a fellow I worked with. He got his electrical license on
the third try to do some work to make extra money . From some of the
stuff he tells on himself, I would not let him change a battery in a one
cell flashlight. He always complains on how the inspector is always
turning his word down.


If an inspector looks at it he will fail it because of the neutral. A
am still not sure a Tesla Charger really needs a neutral tho. The ones
I looked at were pure 240v loads. I would look into that before I did
anything else. Then just find the appropriate 3 wire receptacle.
(6-50r or 10-50r)

dpb[_3_] October 11th 20 10:28 PM

NIMA 14-50
 
On 10/11/2020 3:27 PM, wrote:
On Sat, 10 Oct 2020 22:52:52 -0700 (PDT), Eli Sidwell Iii
wrote:

....

I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?


I doubt it really uses the neutral so you are probably good to go. It
should still be a 3 wire receptacle tho.


Presuming the conduit is actually tied to a real ground...

--

rbowman October 12th 20 12:56 AM

NIMA 14-50
 
On 10/11/2020 03:28 PM, dpb wrote:
On 10/11/2020 3:27 PM, wrote:
On Sat, 10 Oct 2020 22:52:52 -0700 (PDT), Eli Sidwell Iii
wrote:

...

I got a text from my tenant on Friday stating the receptacle was in
and working. Contractor stated that he only needed 2 #6 wires and
use the conduit as a ground for the ground and neutral. Don't know
I have not seen it yet. May end up ripping it out and re-doing it
myself.

Any thoughts ?


I doubt it really uses the neutral so you are probably good to go. It
should still be a 3 wire receptacle tho.


Presuming the conduit is actually tied to a real ground...

--


It should be easy to find where it's bonded. Or not.

Clare Snyder October 12th 20 09:01 PM

NIMA 14-50
 
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:

On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850

I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.

Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.

Sid 03 November 25th 20 03:50 AM

NIMA 14-50
 
On Monday, October 12, 2020 at 3:01:10 PM UTC-5, Clare Snyder wrote:
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:
On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850
I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.

Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.


Follow UP: I went over and inspected what the contractor had done, what I found was that they installed a "NEMA 6-50" outlet that only has two hots and a neutral, and the neutral was terminated at a ground block in the receptacle box.
So: 1/2" Conduit w/2 #6 wires and the ground from the 6-50 terminated in the receptacle box.

I figure Its on the edge of the building code, but probably not unsafe ?
Thanks
Sid.




Dean Hoffman[_17_] November 25th 20 09:43 AM

NIMA 14-50
 
On 11/24/20 9:50 PM, Sid 03 wrote:
On Monday, October 12, 2020 at 3:01:10 PM UTC-5, Clare Snyder wrote:
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:
On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850
I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.

Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.


Follow UP: I went over and inspected what the contractor had done, what I found was that they installed a "NEMA 6-50" outlet that only has two hots and a neutral, and the neutral was terminated at a ground block in the receptacle box.
So: 1/2" Conduit w/2 #6 wires and the ground from the 6-50 terminated in the receptacle box.

I figure Its on the edge of the building code, but probably not unsafe ?
Thanks
Sid.


So the neutral isn't actually connected to the 3rd prong
of the
receptacle?




[email protected] November 25th 20 12:54 PM

NIMA 14-50
 
On Tue, 24 Nov 2020 19:50:04 -0800 (PST), Sid 03
wrote:

On Monday, October 12, 2020 at 3:01:10 PM UTC-5, Clare Snyder wrote:
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:
On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850
I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.

Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.


Follow UP: I went over and inspected what the contractor had done, what I found was that they installed a "NEMA 6-50" outlet that only has two hots and a neutral, and the neutral was terminated at a ground block in the receptacle box.
So: 1/2" Conduit w/2 #6 wires and the ground from the 6-50 terminated in the receptacle box.

I figure Its on the edge of the building code, but probably not unsafe ?
Thanks
Sid.


Legal but not desirable. You can use the conduit for ground if
everything is made up properly but a #10 grounding conductor would
have been better. There is still no neutral present. If you need that,
this is not going to be legal.


Sid 03 November 25th 20 05:01 PM

NIMA 14-50
 
On Wednesday, November 25, 2020 at 6:54:30 AM UTC-6, wrote:
On Tue, 24 Nov 2020 19:50:04 -0800 (PST), Sid 03
wrote:
On Monday, October 12, 2020 at 3:01:10 PM UTC-5, Clare Snyder wrote:
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:
On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850
I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.
Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.


Follow UP: I went over and inspected what the contractor had done, what I found was that they installed a "NEMA 6-50" outlet that only has two hots and a neutral, and the neutral was terminated at a ground block in the receptacle box.
So: 1/2" Conduit w/2 #6 wires and the ground from the 6-50 terminated in the receptacle box.

I figure Its on the edge of the building code, but probably not unsafe ?
Thanks
Sid.


Legal but not desirable. You can use the conduit for ground if
everything is made up properly but a #10 grounding conductor would
have been better. There is still no neutral present. If you need that,
this is not going to be legal.


My Bad, I stated it wrong, NO Neutral, just the ground terminated in the receptacle box ! (plug has 3 wires)
Should I leave it or have it changed ? (If it is to be changed, this would be the time, because I want to finish the walls in the garage.)

The Contractor stated that he wanted to use 1/2" conduit because he couldn't get 3/4" to bend around the corner w/o showing.
I figure there are ways of doing it, you just need to think outside the box ?!
Can't just run your conduit bend down into the corner and then another bend down into the other wall so that you get a 90 and no part of the radius showing ?
May look a little crazy, but seems like it would work on paper ?!

Thanks









[email protected] November 25th 20 06:53 PM

NIMA 14-50
 
On Wed, 25 Nov 2020 09:01:53 -0800 (PST), Sid 03
wrote:

On Wednesday, November 25, 2020 at 6:54:30 AM UTC-6, wrote:
On Tue, 24 Nov 2020 19:50:04 -0800 (PST), Sid 03
wrote:
On Monday, October 12, 2020 at 3:01:10 PM UTC-5, Clare Snyder wrote:
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:
On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850
I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.
Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.

Follow UP: I went over and inspected what the contractor had done, what I found was that they installed a "NEMA 6-50" outlet that only has two hots and a neutral, and the neutral was terminated at a ground block in the receptacle box.
So: 1/2" Conduit w/2 #6 wires and the ground from the 6-50 terminated in the receptacle box.

I figure Its on the edge of the building code, but probably not unsafe ?
Thanks
Sid.


Legal but not desirable. You can use the conduit for ground if
everything is made up properly but a #10 grounding conductor would
have been better. There is still no neutral present. If you need that,
this is not going to be legal.


My Bad, I stated it wrong, NO Neutral, just the ground terminated in the receptacle box ! (plug has 3 wires)
Should I leave it or have it changed ? (If it is to be changed, this would be the time, because I want to finish the walls in the garage.)

The Contractor stated that he wanted to use 1/2" conduit because he couldn't get 3/4" to bend around the corner w/o showing.
I figure there are ways of doing it, you just need to think outside the box ?!
Can't just run your conduit bend down into the corner and then another bend down into the other wall so that you get a 90 and no part of the radius showing ?
May look a little crazy, but seems like it would work on paper ?!

Thanks


Yours is actually a fairly elegant geometric solution if you don't end
up with too many bends (360 degrees total).
It is likely your car charger is just a line to line load (240 only)
and if that is true, what you have, works. If you want a belt and
suspenders approach to your ground you could get some green #10 solid
and tywrap it to the outside of the conduit and tie the boxes
together. HD/Lowes sells it by the foot.
It is sort of legal since the conductors are all run together and
physical damage potential inside a wall is minimal.

Before I closed up the wall I would verify what type of plugs are
available on the charger.

trader_4 November 25th 20 07:43 PM

NIMA 14-50
 
On Wednesday, November 25, 2020 at 7:54:30 AM UTC-5, wrote:
On Tue, 24 Nov 2020 19:50:04 -0800 (PST), Sid 03
wrote:
On Monday, October 12, 2020 at 3:01:10 PM UTC-5, Clare Snyder wrote:
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:
On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850
I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.
Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.


Follow UP: I went over and inspected what the contractor had done, what I found was that they installed a "NEMA 6-50" outlet that only has two hots and a neutral, and the neutral was terminated at a ground block in the receptacle box.
So: 1/2" Conduit w/2 #6 wires and the ground from the 6-50 terminated in the receptacle box.

I figure Its on the edge of the building code, but probably not unsafe ?
Thanks
Sid.


Legal but not desirable



Since when is it code compliant to use the ground at a receptacle for the neutral?





.. You can use the conduit for ground if
everything is made up properly but a #10 grounding conductor would
have been better. There is still no neutral present. If you need that,
this is not going to be legal.


I guess you missed the part where he said the neutral is tied to the ground at the
receptacle. The conduit is not only the ground, it's the neutral too.





trader_4 November 25th 20 07:47 PM

NIMA 14-50
 
On Wednesday, November 25, 2020 at 12:02:02 PM UTC-5, wrote:
On Wednesday, November 25, 2020 at 6:54:30 AM UTC-6, wrote:
On Tue, 24 Nov 2020 19:50:04 -0800 (PST), Sid 03
wrote:
On Monday, October 12, 2020 at 3:01:10 PM UTC-5, Clare Snyder wrote:
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:
On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850
I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.
Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.

Follow UP: I went over and inspected what the contractor had done, what I found was that they installed a "NEMA 6-50" outlet that only has two hots and a neutral, and the neutral was terminated at a ground block in the receptacle box.
So: 1/2" Conduit w/2 #6 wires and the ground from the 6-50 terminated in the receptacle box.

I figure Its on the edge of the building code, but probably not unsafe ?
Thanks
Sid.


Legal but not desirable. You can use the conduit for ground if
everything is made up properly but a #10 grounding conductor would
have been better. There is still no neutral present. If you need that,
this is not going to be legal.

My Bad, I stated it wrong, NO Neutral, just the ground terminated in the receptacle box ! (plug has 3 wires)


Big difference. Then what you have is code compliant.





Should I leave it or have it changed ? (If it is to be changed, this would be the time, because I want to finish the walls in the garage.)

The Contractor stated that he wanted to use 1/2" conduit because he couldn't get 3/4" to bend around the corner w/o showing.
I figure there are ways of doing it, you just need to think outside the box ?!
Can't just run your conduit bend down into the corner and then another bend down into the other wall so that you get a 90 and no part of the radius showing ?
May look a little crazy, but seems like it would work on paper ?!

Thanks


[email protected] November 26th 20 05:13 PM

NIMA 14-50
 
On Wed, 25 Nov 2020 11:43:59 -0800 (PST), trader_4
wrote:

On Wednesday, November 25, 2020 at 7:54:30 AM UTC-5, wrote:
On Tue, 24 Nov 2020 19:50:04 -0800 (PST), Sid 03
wrote:
On Monday, October 12, 2020 at 3:01:10 PM UTC-5, Clare Snyder wrote:
On Sun, 11 Oct 2020 05:21:30 -0500, Dean Hoffman
wrote:
On 10/11/20 12:52 AM, Eli Sidwell Iii wrote:
On Monday, September 28, 2020 at 11:06:34 PM UTC-5, wrote:
On Monday, September 28, 2020 at 9:34:14 PM UTC-5, Eli Sidwell wrote:
On Sunday, September 20, 2020 at 2:20:57 PM UTC-5, Clare Snyder wrote:
On Sun, 20 Sep 2020 13:16:26 -0500, dpb wrote:

On 9/18/2020 11:26 AM, wrote:
On Sunday, August 2, 2020 at 7:30:11 PM UTC-5, Sid wrote:
Can a NIMA 14-50 receptacle be wired up with #10 wire ?
What if you doubled up each wire ?

Would that meet code ?
what if you found one wired up that way ?

Any help appreciated.
Thanks

I ask the contractor about using 3/4" conduit and he stated that the radius was too big to hide in the wall. He said he may use 3/4" but use a 1/2" piece to get around the corner.

Call your local building inspector office and check that you can't just
run Romex...

Then you'll know if the contractor is just stuck in old Chicago or your
jurisdiction hasn't changed to match the times yet, either.

I'd guess odds are 50:50 it would meet your locality's code and
eliminate all the hassle.

Or, if it's so difficult a run to make a bend in the wall (and I can't
see why that should be so -- he might have to make a bigger hole to feed
one end through a joist if it won't fit in one 16" joist bay, but that
shouldn't be any big deal), just do the overhead to the joist cavity
that wants to hit and come in the top of the box and the elbow is above
or could use the pull box in the attic in Code as wouldn't be covered there.

But, going Romex is the smart thing to do -- check with your
municipality to find out what the pertinent Code really is.
Or "BX" if protection is rerquired?
The work was supposed to be done this wknd, but the contractor called on the day of and said he had a family emergency.
If we start having problems like that , I will look around for another contractor.

The corner is an inside corner. Here is a pic from Menards:
https://www.menards.com/main/electri...4430897073.htm

Thanks
Here is the HD link: https://www.homedepot.com/p/Halex-3-...4607/100210850
I got a text from my tenant on Friday stating the receptacle was in and working. Contractor stated that he only needed 2 #6 wires and use the conduit as a ground for the ground and neutral. Don't know I have not seen it yet. May end up ripping it out and re-doing it myself.

Any thoughts ?

There's at least a possibility that the conduit will be routinely
carrying current. The elbow isn't threaded. That would make it easier
to get a bad connection.
I'd vote no. I'm curious what Fretwell has to say.
Fon't know about where the OP is, but up here in Ontario the conduit
can NOT be used as the neutral and in many cases cannot be used as the
"safety ground" either.

Follow UP: I went over and inspected what the contractor had done, what I found was that they installed a "NEMA 6-50" outlet that only has two hots and a neutral, and the neutral was terminated at a ground block in the receptacle box.
So: 1/2" Conduit w/2 #6 wires and the ground from the 6-50 terminated in the receptacle box.

I figure Its on the edge of the building code, but probably not unsafe ?
Thanks
Sid.


Legal but not desirable



Since when is it code compliant to use the ground at a receptacle for the neutral?


I was referring to using the raceway as the grounding conductor.


. You can use the conduit for ground if
everything is made up properly but a #10 grounding conductor would
have been better. There is still no neutral present. If you need that,
this is not going to be legal.


I guess you missed the part where he said the neutral is tied to the ground at the
receptacle. The conduit is not only the ground, it's the neutral too.




A 6-50 only has 2 ungrounded conductors and an equipment grounding
conductor. There was never a legal 6-50 using the neutral as a ground.
It was common on the 14-50 before the 96 code change.