Grundfos says their "comfort system" uses "less energy than a 25 watt
light bulb," but it looks like that isn't the whole story. A foot of 3/4"
140 F pipe in 70 F air loses 30 Btu/h, about 10 watts, so when it is
running, their recirc pump might add about 1 kW to the power consumed
by a house with 100' of hot water pipe, or more, since Grundfos uses a
pump and a timer at the water heater and doesn't sense temperature at
the distant fixture. It looks like it pumps hot water continuously into
the cold water pipe at the fixture, thus making a lot of the cold water
piping hot and forcing a person wanting cold water to waste hot water
out of the cold water pipe until it turns hot again.

Taco seems to have a better solution. Their $300 006DM-PK plumbing kit
has a pump with a check valve under the sink, and temperature sensors.
I'd omit the preheat pushbutton and use it with a motion detector.

Nick

  #2   Report Post  
Jeff Wisnia
 
Posts: n/a
Default Hot water recirculation



wrote:

Grundfos says their "comfort system" uses "less energy than a 25 watt
light bulb," but it looks like that isn't the whole story. A foot of 3/4"
140 F pipe in 70 F air loses 30 Btu/h, about 10 watts, so when it is
running, their recirc pump might add about 1 kW to the power consumed
by a house with 100' of hot water pipe, or more, since Grundfos uses a
pump and a timer at the water heater and doesn't sense temperature at
the distant fixture. It looks like it pumps hot water continuously into
the cold water pipe at the fixture, thus making a lot of the cold water
piping hot and forcing a person wanting cold water to waste hot water
out of the cold water pipe until it turns hot again.


Maybe you've been looking at a different Grundfos recirculator Nick.
This one on their website uses a dedicated return pipe. If all the hot
water piping and the return pipe are well insulated, it should provide a
pretty efficient solution.

http://www.grundfos.com/Web/HomeUs.n...256AE9005326AE

However, for existing construction, the cost of installing a return line
and trying to insulate the piping would be a financial nightmare.

Maybe Grundfos has another model which uses the cold water line for a
"return", like the Taco.

Taco seems to have a better solution. Their $300 006DM-PK plumbing kit
has a pump with a check valve under the sink, and temperature sensors.
I'd omit the preheat pushbutton and use it with a motion detector.

Nick


You've analyzed it and figured out the the deficits correctly Nick.
Those systems that pump the hot water back into the cold line are an
expensive solution for what isn't really that big of a problem for most
folks.

Do the numbers yourself Nick. All that "wasted" water the advertisements
blab about really doesn't cost that much, unless your house is located
on the moon.

If water waste bothers you, you can avoid ****ing away a lot more than
that amount of water by developing better washing habits, like not
letting the warer run all the time you are shaving, but turning it on
and off each time you need to rinse the razor. Or, just putting a little
water in the sink and swishing the razor in it. You get the idea...

If the "wait" for hot water and its attendant waste is really bugging
you, the "right way" to correct the problem in an existing structure is
to install an electric "tankless heater" close to the faucets of interest.

Jeff

--

Jeff Wisnia (W1BSV + Brass Rat '57 EE)

"As long as there are exams in public schools there will be prayer in
public schools."

  #3   Report Post  
 
Posts: n/a
Default Hot water recirculation

Jeff Wisnia wrote:

wrote:

Grundfos says their "comfort system" uses "less energy than a 25 watt
light bulb," but it looks like that isn't the whole story. A foot of 3/4"
140 F pipe in 70 F air loses 30 Btu/h, about 10 watts, so when it is
running, their recirc pump might add about 1 kW to the power consumed
by a house with 100' of hot water pipe, or more, since Grundfos uses a
pump and a timer at the water heater and doesn't sense temperature at
the distant fixture. It looks like it pumps hot water continuously into
the cold water pipe at the fixture, thus making a lot of the cold water
piping hot and forcing a person wanting _cold_ water to waste hot water
out of the cold water pipe until it turns hot again.


Maybe you've been looking at a different Grundfos recirculator Nick.


The Grundfos "comfort system" has no dedicated return pipe.

This one on their website uses a dedicated return pipe. If all the hot
water piping and the return pipe are well insulated, it should provide a
pretty efficient solution.


Chapter 44 of the ASHRAE Applications Handbook says 1/2" fiberglass
insulation lowers the pipe heat loss from 30 to 17.7 Btu/h per foot.

Maybe Grundfos has another model which uses the cold water line for a
"return", like the Taco.


Yes.

Taco seems to have a better solution. Their $300 006DM-PK plumbing kit
has a pump with a check valve under the sink, and temperature sensors.
I'd omit the preheat pushbutton and use it with a motion detector.


...Those systems that pump the hot water back into the cold line are an
expensive solution for what isn't really that big of a problem for most folks.


Taco wastes less energy than Grundfos, for cold-line systems.

If the "wait" for hot water and its attendant waste is really bugging
you, the "right way" to correct the problem in an existing structure is
to install an electric "tankless heater" close to the faucets of interest.


That would cost more and waste more energy, without a motion detector.

Nick

  #4   Report Post  
Childfree Scott
 
Posts: n/a
Default Hot water recirculation

Personally, I think what you want to do is a silly waste of energy and
money. You've got more important things to worry about. Having said
that, if you have to have this, I'd add a tankless unit in the
bathroom.
  #5   Report Post  
 
Posts: n/a
Default Hot water recirculation

Childfree Scott wrote:

...if you have to have this, I'd add a tankless unit in the bathroom.


They cost a lot and keep a small amount of water hot all the time.
You might compare the capital and energy costs of the tankless and
Taco solutions, with a motion detector that moves hot water for 30
seconds, using actual numbers.

Nick



  #7   Report Post  
 
Posts: n/a
Default Hot water recirculation

Jeff Wisnia wrote

...if you have to have this, I'd add a tankless unit in the bathroom.


They cost a lot and keep a small amount of water hot all the time.
You might compare the capital and energy costs of the tankless and
Taco solutions, with a motion detector that moves hot water for 30
seconds, using actual numbers.


Yes, but if it's in a john, howya gonna keep that motion detector from
causing it to waste energy for 30 seconds every time you go in the to
take a leak?


You aren't, and the pump would only run long enough to warm the pipe
to the distant fixture, which might be less than 30 seconds. I suggest
you compare that energy to the standby energy used by a typical tankless,
over a day, using actual numbers. This might require an actual phone call
to an actual tankless manufacturer. It's my impression that most tankless
heaters keep a small volume of water hot 100% of the time, so the standby
loss is not zero, and it may be more than the energy lost by pumping a
half-gallon of hot water 6X(?) per day.

Then, you might compare the non-recurring costs.

Nick

  #8   Report Post  
Jeff Wisnia
 
Posts: n/a
Default Hot water recirculation

wrote:
Jeff Wisnia wrote

...if you have to have this, I'd add a tankless unit in the bathroom.

They cost a lot and keep a small amount of water hot all the time.
You might compare the capital and energy costs of the tankless and
Taco solutions, with a motion detector that moves hot water for 30
seconds, using actual numbers.


Yes, but if it's in a john, howya gonna keep that motion detector from
causing it to waste energy for 30 seconds every time you go in the to
take a leak?



You aren't, and the pump would only run long enough to warm the pipe
to the distant fixture, which might be less than 30 seconds. I suggest
you compare that energy to the standby energy used by a typical tankless,
over a day, using actual numbers. This might require an actual phone call
to an actual tankless manufacturer. It's my impression that most tankless
heaters keep a small volume of water hot 100% of the time, so the standby
loss is not zero, and it may be more than the energy lost by pumping a
half-gallon of hot water 6X(?) per day.



Well, you are wrong about that Nick, or Bosch is guilty of saying what
the native americans used to call, "that which is not so".

Take the "Interactive tour" and you'll see that they confirm there's NO
standby energy use.

http://www.globecomsoftware.com/vend...ess/index.html

They use FLOW to trigger the heating, so, except for the little bit of
heated water left in the coils when you close the faucet, there's
minimal "standby losses".

Here's another one for you if you are still a disbeliever.


Then, you might compare the non-recurring costs.


That probably would tip it in favor of the cheapo "jam it down the cold
pipe" designs from an overall cost perspective, but that wasn't my
original point. I was saying that I think those cheap systems are a
stupid way to solve what isn't a very big problem anyway. And, that if
you want to do it "right" then a separate return pipe with insulation or
a tankless heater is the proper engineering solution.

Nice meeting you,

Jeff

Nick



--
Jeff Wisnia (W1BSV + Brass Rat '57 EE)

"As long as there are final exams, there will be prayer in public
schools"

  #9   Report Post  
 
Posts: n/a
Default Hot water recirculation

Jeff Wisnia wrote:

...if you have to have this, I'd add a tankless unit in the bathroom.


I don't have to or want to, but if I did, I'd want a lower-energy solution.

They cost a lot and keep a small amount of water hot all the time.
You might compare the capital and energy costs of the tankless and
Taco solutions, with a motion detector that moves hot water for 30
seconds, using actual numbers.

Yes, but if it's in a john, howya gonna keep that motion detector from
causing it to waste energy for 30 seconds every time you go in the to
take a leak?


You aren't, and the pump would only run long enough to warm the pipe
to the distant fixture, which might be less than 30 seconds. I suggest
you compare that energy to the standby energy used by a typical tankless,
over a day, using actual numbers. This might require an actual phone call
to an actual tankless manufacturer. It's my impression that most tankless
heaters keep a small volume of water hot 100% of the time, so the standby
loss is not zero, and it may be more than the energy lost by pumping a
half-gallon of hot water 6X(?) per day.


Well, you are wrong about that Nick, or Bosch is guilty of saying what
the native americans used to call, "that which is not so".


Maybe the latter. I see a number of Bosch units have standing pilots.

Take the "Interactive tour" and you'll see that they confirm there's NO
standby energy use.


That's what they say...

http://www.globecomsoftware.com/vend...ess/index.html

They use FLOW to trigger the heating, so, except for the little bit of
heated water left in the coils when you close the faucet, there's
minimal "standby losses".


There's one loss. The Bosch distributor CEC also mentioned a "5 to 10
second delay" between the start of water flow and actual hot water in
the HX water ignition system.

The closest thing I found to a zero-standby-loss instant heater was
the $200 Powerstream RP12T... 240 V at 50 amps to heat 1.5 gpm "in
a cold climate." But that seemed to have other problems, eg poor temp
control with varying pressure, eg in a house with a well vs city water.

That probably would tip it in favor of the cheapo "jam it down the cold
pipe" designs from an overall cost perspective, but that wasn't my
original point. I was saying that I think those cheap systems are a
stupid way to solve what isn't a very big problem anyway. And, that if
you want to do it "right" then a separate return pipe with insulation or
a tankless heater is the proper engineering solution.


In my opinion, that's "not proven," and likely untrue.

Nice meeting you,


Likewise.

Nick (ex K3VZW, BSEE '68, MSEE '87)

  #10   Report Post  
Jeff Wisnia
 
Posts: n/a
Default Hot water recirculation

wrote:
Jeff Wisnia wrote:


...if you have to have this, I'd add a tankless unit in the bathroom.



I don't have to or want to, but if I did, I'd want a lower-energy solution.


They cost a lot and keep a small amount of water hot all the time.
You might compare the capital and energy costs of the tankless and
Taco solutions, with a motion detector that moves hot water for 30
seconds, using actual numbers.

Yes, but if it's in a john, howya gonna keep that motion detector from
causing it to waste energy for 30 seconds every time you go in the to
take a leak?

You aren't, and the pump would only run long enough to warm the pipe
to the distant fixture, which might be less than 30 seconds. I suggest
you compare that energy to the standby energy used by a typical tankless,
over a day, using actual numbers. This might require an actual phone call
to an actual tankless manufacturer. It's my impression that most tankless
heaters keep a small volume of water hot 100% of the time, so the standby
loss is not zero, and it may be more than the energy lost by pumping a
half-gallon of hot water 6X(?) per day.


Well, you are wrong about that Nick, or Bosch is guilty of saying what
the native americans used to call, "that which is not so".



Maybe the latter. I see a number of Bosch units have standing pilots.


Take the "Interactive tour" and you'll see that they confirm there's NO
standby energy use.



That's what they say...


http://www.globecomsoftware.com/vend...ess/index.html

They use FLOW to trigger the heating, so, except for the little bit of
heated water left in the coils when you close the faucet, there's
minimal "standby losses".



There's one loss. The Bosch distributor CEC also mentioned a "5 to 10
second delay" between the start of water flow and actual hot water in
the HX water ignition system.

The closest thing I found to a zero-standby-loss instant heater was
the $200 Powerstream RP12T... 240 V at 50 amps to heat 1.5 gpm "in
a cold climate." But that seemed to have other problems, eg poor temp
control with varying pressure, eg in a house with a well vs city water.


That probably would tip it in favor of the cheapo "jam it down the cold
pipe" designs from an overall cost perspective, but that wasn't my
original point. I was saying that I think those cheap systems are a
stupid way to solve what isn't a very big problem anyway. And, that if
you want to do it "right" then a separate return pipe with insulation or
a tankless heater is the proper engineering solution.



In my opinion, that's "not proven," and likely untrue.



Well Nick, since you encouraged me to "do the numbers", I just did.

We'll use your 6 times a day "waiting for hot water" figure.

Our city water (combined with a sewage charge that's more than the water
charge!) costs us very close to $5.00 per hundred cubic feet. I know
that's high, but we live in one of the 40 cities and towns that is still
paying for the cleanup of Boston Harbor, claimed to have been polluted
by over a hundred years of those 40 municipalities depositing their
sewage into it.

I just used a gallon milk jug to check what it took to "get hot water"
in the bathroom in our home furthest from the water heater. The jug was
nearly filled when the water got "as hot as she gets" and it took 25
seconds to get there. Normally, I'd find the water was warm enough to
start using in about half that time, but let's play it conservative.
BTW, no one had been there to run any water for at least six hours
before my great experiment.

That computes Captain, because that bathroom is maybe 50 linear feet
from the heater, and assuming maybe 30 feet of 3/4" pipe and 20 feet of
1/2" pipe worst case, there's about 0.8 gallons of water in the hot
water piping to sweep out, and the pipe itself needs to get heated in
the process.

So, if we "waste" that one gallon of water down the drain six times a
day, 365 days a year, the cost to do that, even at my outrageous water
rates, will be less than $15 per year. If you live where water costs
less than $5.00 per hundred cubic feet the cost will obviously be
proportionally lower.

That's gonna take a long time to pay off the purchase and installation
costs of an undersink unit. Say Nick, how many vanity cabinets have you
seen with a power outlets inside 'em? Have you priced what an
electrician would charge to install one there for you?

All the other factors cancel out, save for the cost of power to run the
circulating pump and the cost of the water you "waste" waiting to get a
glass of "cool" water to drink because warm water has just been pushed
into the cold line. Of course, there's also some additional savings from
decreased waiting times for hot water at other nearby faucets IF the
motion detectored pump had recently been activated.

The pump power cost, if it really only draws 25 watts, is negligible. I
figured it out to about half a kilowatt hour a year running for 30
seconds 6 times a day. That's nuttin' to worry about.

The "cold water waste" is a function of your thirst and taste of course,
but it's gotta take something away the water you save by not wasting
that water from the hot water faucet.

I suppose that if you're an impatient type and put a price on your
discretionary time then the total waiting time for the hot water to warm
up enough to use, which I make to be about 10 hours a year, would easily
swamp all the other cost calculations. But, I try hard not to think
about stuff like that while I'm waiting for traffic lights to change and
supermarket checkout lines to move.

I think I've about "saucered and blowed" this one, Nick. Do what you
want about it, Thank G-d it's a free country.

Cheers,

Jeff

--
Jeff Wisnia (W1BSV + Brass Rat '57 EE)

http://home.comcast.net/~jwisnia18/jeff/

"As long as there are final exams, there will be prayer in public
schools"



  #11   Report Post  
Jedd Haas
 
Posts: n/a
Default Hot water recirculation

I have been interested in building a new plumbing system with hot water
recirculation. I just found this install guide from Grundfos that has some
good information (PDF file)

http://www.us.grundfos.com/web/Download.nsf/Pages/D6774D5BEBD2117B8825652200650E2C/$File/Uprec-gd.pdf

--
Jedd Haas - Artist
http://www.gallerytungsten.com
http://www.epsno.com
  #12   Report Post  
Rich
 
Posts: n/a
Default Hot water recirculation

The way that they have it drawn it will work without the pump. Heat
rises and cold falls so all you need to do is bring a return from the
last hot water connection to the water heater drain with an extension,
put a flap type check valve installed at a very slight angle so the flap
hangs open on the return line. Then when you turn the hot water on the
flap closes and you don't pull cooler water into the loop.

I did this in my ranch type house and it worked great, but used energy
as you have a constant loss. But its a trade off for convenience.

Rich






"Jedd Haas" wrote in message
...
I have been interested in building a new plumbing system with hot water
recirculation. I just found this install guide from Grundfos that has
some
good information (PDF file)

http://www.us.grundfos.com/web/Download.nsf/Pages/D6774D5BEBD2117B8825652200650E2C/$File/Uprec-gd.pdf

--
Jedd Haas - Artist
http://www.gallerytungsten.com
http://www.epsno.com



  #13   Report Post  
m Ransley
 
Posts: n/a
Default Hot water recirculation

Bosch Aquastar has many units, you can get an old pilot model if you
wish to waste energy or one of the newer models most people buy. 2 of
them require no outside electricity supply, one has battery ignition ,
which I have, and one has a mini hydro generator. I dont see any more
delay than with a tank.

Recirculators waste energy.

Electric tankless heaters for most of the US cost double to operate
than gas and easily require you to upgrade your main as a good Bosch
unit takes apx 120 amp itself to operate.

  #14   Report Post  
 
Posts: n/a
Default Hot water recirculation

Jeff Wisnia wrote:

...since you encouraged me to "do the numbers", I just did.


Good.

We'll use your 6 times a day "waiting for hot water" figure.


OK.

Our city water (combined with a sewage charge that's more than the water
charge!) costs us very close to $5.00 per hundred cubic feet...
I just used a gallon milk jug to check what it took to "get hot water"
in the bathroom in our home furthest from the water heater. The jug was
nearly filled when the water got "as hot as she gets" and it took 25
seconds to get there...


At about 2 gpm? Not much...

that bathroom is maybe 50 linear feet from the heater, and assuming maybe
30 feet of 3/4" pipe and 20 feet of1/2" pipe worst case, there's about
0.8 gallons of water in the hot water piping to sweep out...


OK.

So, if we "waste" that one gallon of water down the drain six times a
day, 365 days a year, the cost to do that, even at my outrageous water
rates, will be less than $15 per year.


....O.8x6x365 = 1752 gal or 219 ft^3/year, about $11. Heating it takes
1752x8(120-60) = 841K Btu or 247kWh/year, about $25 at 10 cents/kWh.

That's gonna take a long time to pay off the purchase and installation
costs of an undersink unit...


IMO, the question is" "If a body desired instant hot water,
which is cheaper, a) Grundfos, b) Taco, or c) Bosch?

Bosch may not be a good solution, with standing pilots or 5-10 sec delays.
Taco is a better solution than Grundfos, with temp sensing and a motion
detector vs a timer.

The pump power cost, if it really only draws 25 watts, is negligible. I
figured it out to about half a kilowatt hour a year running for 30
seconds 6 times a day. That's nuttin' to worry about.


The Grundfos pump on a timer with no temp sensing would run a lot more
than that. Running for a mere 2 hours per day, eg 8-9 AM and 9-10 PM,
it might use 50 Wh of electricity plus about 2 kWh for pipe heat losses,
totaling 2.05 kWh/day or 749 kWh/year, ie $75 at 10 cents/kWh. The Taco
system might run for 3 minutes per day, filling half the pipe (only the
hot pipe) at a cost of $36/year, about the same as the manual method,
ignoring trips to the loo or the kitchen without hot water use.

Nick

  #15   Report Post  
 
Posts: n/a
Default Hot water recirculation

m Ransley wrote:

Bosch Aquastar has many units, you can get an old pilot model if you
wish to waste energy or one of the newer models most people buy. 2 of
them require no outside electricity supply, one has battery ignition ,
which I have, and one has a mini hydro generator. I dont see any more
delay than with a tank.


No more delay? :-)

Recirculators waste energy.


The Taco system is close to the manual method, with less water use.

Nick



  #16   Report Post  
m Ransley
 
Posts: n/a
Default Hot water recirculation

My Bosch pilotless has a 4 second delay from faucet turn on till full
fire. Not a delay worth considering. My 2 d cells are 2.7 yrs old ,
maybe new batteries would get it down, but still not worth mentioning at
4 seconds, and zero standby loss, it is pilotless.

  #17   Report Post  
m Ransley
 
Posts: n/a
Default Hot water recirculation

Correction, I just went back and took off my Waterpick restrictive tap
filter and got a 3 second delay.

  #18   Report Post  
 
Posts: n/a
Default Hot water recirculation

The Taco system might use about the same energy and less water than the
manual (run water until it gets hot) method. A cleverer system might pump
cold water back into the hot water pipe at the sink, after water usage has
stopped, until the cold water reaches the water heater output, leaving the
hot pipe filled with cold water between usage bursts, allowing house air
to heat cold water in the hot water pipe, vs allowing stagnant hot water
to lose heat in the hot water pipe...

Nick

  #19   Report Post  
chuck yerkes
 
Posts: n/a
Default Hot water recirculation

wrote:
Jeff Wisnia wrote:

....
The Grundfos pump on a timer with no temp sensing would run a lot more
than that. Running for a mere 2 hours per day, eg 8-9 AM and 9-10 PM,
it might use 50 Wh of electricity plus about 2 kWh for pipe heat losses,
totaling 2.05 kWh/day or 749 kWh/year, ie $75 at 10 cents/kWh. The Taco
system might run for 3 minutes per day, filling half the pipe (only the
hot pipe) at a cost of $36/year, about the same as the manual method,
ignoring trips to the loo or the kitchen without hot water use.


I looked at these recirc pumps before I had replaced a dip tube that
incidentally made a hot water problem moot.

I looked at a "chillipepper" brand. One thing it did was get turned on
via X10 (perhaps with a timer).

If you run the hot down the hot and the warm/hot back up the cold for
30-60 seconds, when you turn on the tap, you get warm to hot water.

This makes my sleepy face happy.

Now, there's warm water backed into the cool a little bit with this.

But frankly, I'm washing my face, dealing with the AM. By the time
I get to the bathroom, the hot water should be actually hot, so the
device is now off. If I hit the cold water to get warm, as the cold
pipe empties of lukewarm water to become cold (lets say 15 seconds of
use, it's filled with cold).

Bottom line, the device turns on just enough to get hot water to the
tap with about 30 seconds of advance warning.

If you do stuff and use NO cold water, then yeah, you leave some
warm water in the cold pipe. Most of the time, people mix.


They also advertise that they draw the water fast enough to turn on
a tankless waterheater.

So you're "6 times a day" means that you run this sucker 3-5 minutes a
day at a few pump watts.

No special return pipe (which would be a pain in my existing bathrooms).
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Copper pipe sizing. Is bigger better? Paul J Home Repair 19 February 29th 04 08:52 PM
need hot water FAST PV Home Repair 38 January 30th 04 02:15 AM
NO MORE hot water problems [email protected] Home Repair 9 January 29th 04 07:15 PM
Thankless or Tankless hot water heaters [email protected] Home Repair 6 January 29th 04 04:01 AM
Why is this a bad idea? Mike Hibbert UK diy 18 August 29th 03 12:59 AM


All times are GMT +1. The time now is 03:27 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"