Thought I'd start a new thread.

I spent about five hours yesterday taking apart and cleaning the a/c
condenser. It didn't help.

When I arrived on scene, the a/c was working fine. Cold air was blowing
out of the vents. The refrigerant drier cannister happens to be located
on the small line outside the evaporator. This line was very slightly
warm to the touch. The larger copper line going into the evaporator was
cold to the touch. The outside of the plenum was also cold (not
freezing).

After about 30 minutes, the a/c unit's fan turned off, the furnace fan
remained on, and the evaporator line outside the plenum, and the plenum,
got warmer.

Time to clean the condenser. I turned off the thermostat, pilled the 40
amp fuse at the a/c unit, and disassembled the side panels, the fan, and
any wiring as necessary. The compressor had an orange vinyl insulated
sort of pull down 'hat' over it. I took that off, too, to get the
compressor specs, if needed, and I put my hand on top of the compressor.
It was hot enough that I couldn't keep my hand on it for more than a
second or so, but not hot enough to cause immediate burns.

There were lots of leaves in the drip pan, but not much came out of the
condenser. I first vacuumed both sides of the entire consenser, and
there was not much debris at all. I then wetted and sprayed foam on the
outside, and rinsed from both the outside and inside, until all runoff
water was clear. Actually, I was surprised at how little dust/dirt there
was. The only thing that was really dirty was the temp sensing unit that
sits on the small copper line, right where it enters the compressor. I
removed it and cleaned it off good.

I got it put back together, turned it on. The outside temp was now 100
degrees. The indoor temp was 77, and I called for 66 at the thermostat.
Cool air started coming out, measured at 64 degrees (I guess the attic
ductwork was really hot) and it ran fine for about 40 minutes. Then,
warm air came out. The a/c fan stopped. I hand checked hand temps at
the plenum, and it was warming up again.

Crap.

I'm calling another company out for a another look before I replace
anyting major.



  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Cleaned A/C Condenser, No Joy

On Monday, June 8, 2015 at 12:07:34 PM UTC-4, Boris wrote:
Thought I'd start a new thread.

I spent about five hours yesterday taking apart and cleaning the a/c
condenser. It didn't help.

When I arrived on scene, the a/c was working fine. Cold air was blowing
out of the vents. The refrigerant drier cannister happens to be located
on the small line outside the evaporator. This line was very slightly
warm to the touch. The larger copper line going into the evaporator was
cold to the touch. The outside of the plenum was also cold (not
freezing).

After about 30 minutes, the a/c unit's fan turned off, the furnace fan
remained on, and the evaporator line outside the plenum, and the plenum,
got warmer.

Time to clean the condenser. I turned off the thermostat, pilled the 40
amp fuse at the a/c unit, and disassembled the side panels, the fan, and
any wiring as necessary. The compressor had an orange vinyl insulated
sort of pull down 'hat' over it. I took that off, too, to get the
compressor specs, if needed, and I put my hand on top of the compressor.
It was hot enough that I couldn't keep my hand on it for more than a
second or so, but not hot enough to cause immediate burns.

There were lots of leaves in the drip pan, but not much came out of the
condenser. I first vacuumed both sides of the entire consenser, and
there was not much debris at all. I then wetted and sprayed foam on the
outside, and rinsed from both the outside and inside, until all runoff
water was clear. Actually, I was surprised at how little dust/dirt there
was. The only thing that was really dirty was the temp sensing unit that
sits on the small copper line, right where it enters the compressor. I
removed it and cleaned it off good.

I got it put back together, turned it on. The outside temp was now 100
degrees. The indoor temp was 77, and I called for 66 at the thermostat.
Cool air started coming out, measured at 64 degrees (I guess the attic
ductwork was really hot) and it ran fine for about 40 minutes. Then,
warm air came out. The a/c fan stopped. I hand checked hand temps at
the plenum, and it was warming up again.

Crap.

I'm calling another company out for a another look before I replace
anyting major.


I would look at a wiring diagram for the unit and see what
it takes for the condenser fan to stop running. IDK how they
are wired, but my first thought would be that the thermal
protection for the compressor would stop just the compressor,
not the fan too. If that's true, then something else is
wrong, eg bad contactor, that is stopping both the compressor
and the fan......
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,115
Default Cleaned A/C Condenser, No Joy

trader_4 wrote:
On Monday, June 8, 2015 at 12:07:34 PM UTC-4, Boris wrote:
Thought I'd start a new thread.

I spent about five hours yesterday taking apart and cleaning the a/c
condenser. It didn't help.

When I arrived on scene, the a/c was working fine. Cold air was
blowing out of the vents. The refrigerant drier cannister happens
to be located on the small line outside the evaporator. This line
was very slightly warm to the touch. The larger copper line going
into the evaporator was cold to the touch. The outside of the
plenum was also cold (not freezing).

After about 30 minutes, the a/c unit's fan turned off, the furnace
fan remained on, and the evaporator line outside the plenum, and the
plenum, got warmer.

Time to clean the condenser. I turned off the thermostat, pilled
the 40 amp fuse at the a/c unit, and disassembled the side panels,
the fan, and any wiring as necessary. The compressor had an orange
vinyl insulated sort of pull down 'hat' over it. I took that off,
too, to get the compressor specs, if needed, and I put my hand on
top of the compressor. It was hot enough that I couldn't keep my
hand on it for more than a second or so, but not hot enough to cause
immediate burns.

There were lots of leaves in the drip pan, but not much came out of
the condenser. I first vacuumed both sides of the entire consenser,
and there was not much debris at all. I then wetted and sprayed
foam on the outside, and rinsed from both the outside and inside,
until all runoff water was clear. Actually, I was surprised at how
little dust/dirt there was. The only thing that was really dirty
was the temp sensing unit that sits on the small copper line, right
where it enters the compressor. I removed it and cleaned it off
good.

I got it put back together, turned it on. The outside temp was now
100 degrees. The indoor temp was 77, and I called for 66 at the
thermostat. Cool air started coming out, measured at 64 degrees (I
guess the attic ductwork was really hot) and it ran fine for about
40 minutes. Then, warm air came out. The a/c fan stopped. I hand
checked hand temps at the plenum, and it was warming up again.

Crap.

I'm calling another company out for a another look before I replace
anyting major.


I would look at a wiring diagram for the unit and see what
it takes for the condenser fan to stop running. IDK how they
are wired, but my first thought would be that the thermal
protection for the compressor would stop just the compressor,
not the fan too. If that's true, then something else is
wrong, eg bad contactor, that is stopping both the compressor
and the fan......


If the condenser fan stops , the compressor will overheat and shut down too
.... try it again , and when the fan turns off check the compressor , if it's
still running replace the fan motor .

--
Snag


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Cleaned A/C Condenser, No Joy

On Monday, June 8, 2015 at 1:17:24 PM UTC-4, Terry Coombs wrote:
trader_4 wrote:
On Monday, June 8, 2015 at 12:07:34 PM UTC-4, Boris wrote:
Thought I'd start a new thread.

I spent about five hours yesterday taking apart and cleaning the a/c
condenser. It didn't help.

When I arrived on scene, the a/c was working fine. Cold air was
blowing out of the vents. The refrigerant drier cannister happens
to be located on the small line outside the evaporator. This line
was very slightly warm to the touch. The larger copper line going
into the evaporator was cold to the touch. The outside of the
plenum was also cold (not freezing).

After about 30 minutes, the a/c unit's fan turned off, the furnace
fan remained on, and the evaporator line outside the plenum, and the
plenum, got warmer.

Time to clean the condenser. I turned off the thermostat, pilled
the 40 amp fuse at the a/c unit, and disassembled the side panels,
the fan, and any wiring as necessary. The compressor had an orange
vinyl insulated sort of pull down 'hat' over it. I took that off,
too, to get the compressor specs, if needed, and I put my hand on
top of the compressor. It was hot enough that I couldn't keep my
hand on it for more than a second or so, but not hot enough to cause
immediate burns.

There were lots of leaves in the drip pan, but not much came out of
the condenser. I first vacuumed both sides of the entire consenser,
and there was not much debris at all. I then wetted and sprayed
foam on the outside, and rinsed from both the outside and inside,
until all runoff water was clear. Actually, I was surprised at how
little dust/dirt there was. The only thing that was really dirty
was the temp sensing unit that sits on the small copper line, right
where it enters the compressor. I removed it and cleaned it off
good.

I got it put back together, turned it on. The outside temp was now
100 degrees. The indoor temp was 77, and I called for 66 at the
thermostat. Cool air started coming out, measured at 64 degrees (I
guess the attic ductwork was really hot) and it ran fine for about
40 minutes. Then, warm air came out. The a/c fan stopped. I hand
checked hand temps at the plenum, and it was warming up again.

Crap.

I'm calling another company out for a another look before I replace
anyting major.


I would look at a wiring diagram for the unit and see what
it takes for the condenser fan to stop running. IDK how they
are wired, but my first thought would be that the thermal
protection for the compressor would stop just the compressor,
not the fan too. If that's true, then something else is
wrong, eg bad contactor, that is stopping both the compressor
and the fan......


If the condenser fan stops , the compressor will overheat and shut down too
... try it again , and when the fan turns off check the compressor , if it's
still running replace the fan motor .

--
Snag


That's an excellent observation. He could check for voltage at
the fan when it quits.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 119
Default Cleaned A/C Condenser, No Joy

"Terry Coombs" wrote in
:

trader_4 wrote:
On Monday, June 8, 2015 at 12:07:34 PM UTC-4, Boris wrote:
Thought I'd start a new thread.

I spent about five hours yesterday taking apart and cleaning the a/c
condenser. It didn't help.

When I arrived on scene, the a/c was working fine. Cold air was
blowing out of the vents. The refrigerant drier cannister happens
to be located on the small line outside the evaporator. This line
was very slightly warm to the touch. The larger copper line going
into the evaporator was cold to the touch. The outside of the
plenum was also cold (not freezing).

After about 30 minutes, the a/c unit's fan turned off, the furnace
fan remained on, and the evaporator line outside the plenum, and the
plenum, got warmer.

Time to clean the condenser. I turned off the thermostat, pilled
the 40 amp fuse at the a/c unit, and disassembled the side panels,
the fan, and any wiring as necessary. The compressor had an orange
vinyl insulated sort of pull down 'hat' over it. I took that off,
too, to get the compressor specs, if needed, and I put my hand on
top of the compressor. It was hot enough that I couldn't keep my
hand on it for more than a second or so, but not hot enough to cause
immediate burns.

There were lots of leaves in the drip pan, but not much came out of
the condenser. I first vacuumed both sides of the entire consenser,
and there was not much debris at all. I then wetted and sprayed
foam on the outside, and rinsed from both the outside and inside,
until all runoff water was clear. Actually, I was surprised at how
little dust/dirt there was. The only thing that was really dirty
was the temp sensing unit that sits on the small copper line, right
where it enters the compressor. I removed it and cleaned it off
good.

I got it put back together, turned it on. The outside temp was now
100 degrees. The indoor temp was 77, and I called for 66 at the
thermostat. Cool air started coming out, measured at 64 degrees (I
guess the attic ductwork was really hot) and it ran fine for about
40 minutes. Then, warm air came out. The a/c fan stopped. I hand
checked hand temps at the plenum, and it was warming up again.

Crap.

I'm calling another company out for a another look before I replace
anyting major.


I would look at a wiring diagram for the unit and see what
it takes for the condenser fan to stop running. IDK how they
are wired, but my first thought would be that the thermal
protection for the compressor would stop just the compressor,

good point

not the fan too. If that's true, then something else is
wrong, eg bad contactor,


I've heard 'contactor' used, but not sure what that is. Is it some sort
of wiring block where many of the that is stopping both the compressor
and the fan......


If the condenser fan stops , the compressor will overheat and shut
down too ... try it again , and when the fan turns off check the
compressor , if it's still running replace the fan motor .


Yeah, that was my thought. But three weeks ago, I had the fan
motor/capacitor replaced because fan motor bearing was bad and the thing
was howling loudly.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 119
Default Cleaned A/C Condenser, No Joy

trader_4 wrote in
:

On Monday, June 8, 2015 at 12:07:34 PM UTC-4, Boris wrote:
Thought I'd start a new thread.

I spent about five hours yesterday taking apart and cleaning the a/c
condenser. It didn't help.

When I arrived on scene, the a/c was working fine. Cold air was
blowing out of the vents. The refrigerant drier cannister happens to
be located on the small line outside the evaporator. This line was
very slightly warm to the touch. The larger copper line going into
the evaporator was cold to the touch. The outside of the plenum was
also cold (not freezing).

After about 30 minutes, the a/c unit's fan turned off, the furnace
fan remained on, and the evaporator line outside the plenum, and the
plenum, got warmer.

Time to clean the condenser. I turned off the thermostat, pilled the
40 amp fuse at the a/c unit, and disassembled the side panels, the
fan, and any wiring as necessary. The compressor had an orange vinyl
insulated sort of pull down 'hat' over it. I took that off, too, to
get the compressor specs, if needed, and I put my hand on top of the
compressor. It was hot enough that I couldn't keep my hand on it for
more than a second or so, but not hot enough to cause immediate
burns.

There were lots of leaves in the drip pan, but not much came out of
the condenser. I first vacuumed both sides of the entire consenser,
and there was not much debris at all. I then wetted and sprayed foam
on the outside, and rinsed from both the outside and inside, until
all runoff water was clear. Actually, I was surprised at how little
dust/dirt there was. The only thing that was really dirty was the
temp sensing unit that sits on the small copper line, right where it
enters the compressor. I removed it and cleaned it off good.

I got it put back together, turned it on. The outside temp was now
100 degrees. The indoor temp was 77, and I called for 66 at the
thermostat. Cool air started coming out, measured at 64 degrees (I
guess the attic ductwork was really hot) and it ran fine for about 40
minutes. Then, warm air came out. The a/c fan stopped. I hand
checked hand temps at the plenum, and it was warming up again.

Crap.

I'm calling another company out for a another look before I replace
anyting major.


I would look at a wiring diagram for the unit and see what
it takes for the condenser fan to stop running. IDK how they
are wired, but my first thought would be that the thermal
protection for the compressor would stop just the compressor,
not the fan too. If that's true, then something else is
wrong, eg bad contactor, that is stopping both the compressor
and the fan......


I did find all the specs and wiring diagrams inside the unit when I took
it apart.

The schematic will help someone more knowledgeable than I.

When I'm inside the house and I notice the vent air no longer cool,
that's when I look outside and see that the a/c fan is not running. So,
I don't know if the compressor got hot and turned off itself and fan, or
the fan turned off, and the compressor then got hot and turned off.
Yesterday, there was one time when as soon as the vent air got warm, I
ran to the a/c unit, and the fan was still on, but then within a few
minutes, stopped.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Landlord is saying you have not cleaned enough Dave Smith[_7_] UK diy 13 July 3rd 13 08:17 PM
Need to Have My Air Ducts Cleaned ABSteamatic Carpet Cleaning Services Home Repair 7 February 16th 11 06:42 AM
Getting the Ducts Cleaned Lexis Home Repair 7 December 12th 07 04:25 AM
Central Air needs to be cleaned every other year? NJ Home Ownership 6 December 23rd 04 11:31 AM
Central Air needs to be cleaned every other year? NJ Electronics Repair 6 December 23rd 04 11:31 AM


All times are GMT +1. The time now is 06:38 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"