Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
I bought a 200,000 BTU pool heater, to be installed outdoors.
The model is Hayward H200FDN. The size of the piping that leads to it is somewhat iffy and appears just a bit undersized according to various tables. Depending on the actual pressure in the system, may be inadequate and not able to supply enough gas. The manual says: ``Based upon an inlet gas pressure of 0.5 psig or less at a pressure drop of 0.5 in-wc'' Later it says: ``Hayward will not be responsible for heaters that soot up due to improper .. natural gas line sizing''. If I cannot provide this heater with adequate gas flow, I can upgrade most of the piping from 3/4" NPT to 1" NPT, it is roughly a day or work and some money. To question is, do I need to do it? So, I thought, I could turn to measurement of the gas pressure right at the inlet of the pool heater. If the gas pressure at the inlet, when the heater is running, is above the recommended value, then I am fine. I do have a pressure gauge that I could use. My question is, and here's where I am not sure, what is that "recommended inlet pressure". Is that 0.5 PSIG when the heater is running? Am I reading that right? thanks |
#2
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
On 5/16/2015 10:29 AM, Ignoramus6769 wrote:
I bought a 200,000 BTU pool heater, to be installed outdoors. The model is Hayward H200FDN. The size of the piping that leads to it is somewhat iffy and appears just a bit undersized according to various tables. Depending on the actual pressure in the system, may be inadequate and not able to supply enough gas. The manual says: ``Based upon an inlet gas pressure of 0.5 psig or less at a pressure drop of 0.5 in-wc'' Later it says: ``Hayward will not be responsible for heaters that soot up due to improper .. natural gas line sizing''. If I cannot provide this heater with adequate gas flow, I can upgrade most of the piping from 3/4" NPT to 1" NPT, it is roughly a day or work and some money. To question is, do I need to do it? So, I thought, I could turn to measurement of the gas pressure right at the inlet of the pool heater. If the gas pressure at the inlet, when the heater is running, is above the recommended value, then I am fine. I do have a pressure gauge that I could use. My question is, and here's where I am not sure, what is that "recommended inlet pressure". Is that 0.5 PSIG when the heater is running? Am I reading that right? thanks I think you are interpreting it correctly. But, 0.5 psig seems high for regular natural gas. Or, is it propane? Either way, 1 psi is 27.7 in-wc. So that would make the inlet pressure almost 14 in-wc. But as most gas appliances have regulators, I guess that might be ok. |
#3
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
On Sat, 16 May 2015 09:29:54 -0500, Ignoramus6769
wrote: I bought a 200,000 BTU pool heater, to be installed outdoors. The model is Hayward H200FDN. The size of the piping that leads to it is somewhat iffy and appears just a bit undersized according to various tables. Depending on the actual pressure in the system, may be inadequate and not able to supply enough gas. The manual says: ``Based upon an inlet gas pressure of 0.5 psig or less at a pressure drop of 0.5 in-wc'' Later it says: ``Hayward will not be responsible for heaters that soot up due to improper .. natural gas line sizing''. If I cannot provide this heater with adequate gas flow, I can upgrade most of the piping from 3/4" NPT to 1" NPT, it is roughly a day or work and some money. To question is, do I need to do it? So, I thought, I could turn to measurement of the gas pressure right at the inlet of the pool heater. If the gas pressure at the inlet, when the heater is running, is above the recommended value, then I am fine. I do have a pressure gauge that I could use. My question is, and here's where I am not sure, what is that "recommended inlet pressure". Is that 0.5 PSIG when the heater is running? Am I reading that right? thanks You are correct. You need the pressure at the appliance when it is running. With the appliance NOT running you would have the correct pressure on even a 1/4" line. |
#4
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
|
#5
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
On 05/16/2015 10:49 AM, Ignoramus6769 wrote:
On 2015-05-16, wrote: On Sat, 16 May 2015 09:29:54 -0500, Ignoramus6769 wrote: I bought a 200,000 BTU pool heater, to be installed outdoors. The model is Hayward H200FDN. The size of the piping that leads to it is somewhat iffy and appears just a bit undersized according to various tables. Depending on the actual pressure in the system, may be inadequate and not able to supply enough gas. The manual says: ``Based upon an inlet gas pressure of 0.5 psig or less at a pressure drop of 0.5 in-wc'' .... My question is, and here's where I am not sure, what is that "recommended inlet pressure". Is that 0.5 PSIG when the heater is running? Am I reading that right? thanks You are correct. You need the pressure at the appliance when it is running. With the appliance NOT running you would have the correct pressure on even a 1/4" line. I agree. It makes sense based on simple physics. The question is, what exactly pressure should I see on the onlet when the heater is running. "...an inlet gas pressure of 0.5 psig or less ..." It's not any _specific_ pressure; it's that it's not too high and that whatever it is can be maintained under flow conditions. -- |
#6
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
|
#7
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
|
#8
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
On Saturday, May 16, 2015 at 9:29:57 AM UTC-5, Ignoramus6769 wrote:
I bought a 200,000 BTU pool heater, to be installed outdoors. The model is Hayward H200FDN. The size of the piping that leads to it is somewhat iffy and appears just a bit undersized according to various tables. Depending on the actual pressure in the system, may be inadequate and not able to supply enough gas. The manual says: ``Based upon an inlet gas pressure of 0.5 psig or less at a pressure drop of 0.5 in-wc'' Later it says: ``Hayward will not be responsible for heaters that soot up due to improper .. natural gas line sizing''. If I cannot provide this heater with adequate gas flow, I can upgrade most of the piping from 3/4" NPT to 1" NPT, it is roughly a day or work and some money. To question is, do I need to do it? So, I thought, I could turn to measurement of the gas pressure right at the inlet of the pool heater. If the gas pressure at the inlet, when the heater is running, is above the recommended value, then I am fine. I do have a pressure gauge that I could use. My question is, and here's where I am not sure, what is that "recommended inlet pressure". Is that 0.5 PSIG when the heater is running? Am I reading that right? thanks Check with your gas company to see if you can get 2 psi service. When I was doing work on HVAC systems especially remodeling, we would get 2 psi service and run 1/2 inch copper or corrugated stainless steel tubing to each appliance where a regulator was installed at each appliance to drop the pressure down to what the appliance required. I think 1/2 inch line at 2 psi could work but it's best to check the tables for the right size for the length of the pipe run. 8-) http://preview.tinyurl.com/l9hlhoy http://www.gastite.com/us/products/gastite.html http://preview.tinyurl.com/klwfswq [8~{} Uncle Gassy Monster |
#9
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
On 2015-05-16, dpb wrote:
"...an inlet gas pressure of 0.5 psig or less ..." It's not any _specific_ pressure; it's that it's not too high and that whatever it is can be maintained under flow conditions. OK, an update: I have decided that 1) This is a very good heater because it can heat the pool quickly before use, and thus I do not need to waste energy "maintaining" temperature when the pool is not in use. 2) I need to hook it up correctly and will install proper gas piping comprised of about 40' of 1" pipe. i |
#10
Posted to alt.home.repair
|
|||
|
|||
Natural gas pressure drop, pipe sizing and pressure
On Sunday, May 17, 2015 at 4:37:03 PM UTC-4, Ignoramus4261 wrote:
On 2015-05-16, dpb wrote: "...an inlet gas pressure of 0.5 psig or less ..." It's not any _specific_ pressure; it's that it's not too high and that whatever it is can be maintained under flow conditions. OK, an update: I have decided that 1) This is a very good heater because it can heat the pool quickly before use, and thus I do not need to waste energy "maintaining" temperature when the pool is not in use. 2) I need to hook it up correctly and will install proper gas piping comprised of about 40' of 1" pipe. i Before you plumb it all in, have you figured out how much it's going to cost to heat the pool? Around here, NJ, almost no one uses them because of the huge operating cost. They have them sitting there, because they were installed with the pool, but they rarely if ever use them. I guess if it's small, it might not be too bad. But for an inground one that's 30 or 40K gallons, which isn't unusual, it costs a lot of money. The fact that it's 200K BTUs tells you something. The largest home gas furnace is 120K btus. If you have some room for a solar array, you can operate it for close to free. But they have drawbacks too, the large size needed being one. Whether you want one on the roof or have a space out of sight in the yard is another. You can use a pool cover with either, which helps a lot. But that's a pain and some folks won't put up with it, don't like the look, etc. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Nat gas pressure drop vs. pipe length | Home Repair | |||
Gas Pipe - How do I caculate pressure drop? | UK diy | |||
Natural Gas Pipe Sizing | Home Repair | |||
Natural gas pipe sizing (or "how can this ever work??") | Home Repair | |||
Help sizing a pressure tank | Home Repair |