I own a 6 family apartment building in Brooklyn, and the electric was upgraded back in 2000.
I noticed on these panels in the basement, the feed coming straight from the meter to the panel, there is no main disconnect. Only way to disconnect the electric to the apt is to shut off the individual breakers ( see pic), or in the more recent renovations, shut off the main breaker in the basement panel feeding the sub-panel in the apartment.

https://plus.google.com/118428219834...ts/F9zvftJ7EvL

(Only the 2 apartments on the first floor do not have a sub-panel within the apartment).
All of the panels in the basement are main lug.
There is a main 200A disconnect for the entire building.

Is this correct? Isn't it necessary to protect the wiring or provide a means of disconnect from the meter to the panel?

I'm asking because we are doing a bathroom reno on the first floor, and I ran a new 12/2 BX just for the bathroom. And when I installed in the panel, to be safe I wanted to de-energize the entire panel, but the only way to do that was to turn off the entire building.

I managed to install it anyway while the panel was live.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Question on 6 family apt building electric panels

On Sunday, December 14, 2014 8:34:22 AM UTC-5, Mikepier wrote:
I own a 6 family apartment building in Brooklyn, and the electric was upgraded back in 2000.
I noticed on these panels in the basement, the feed coming straight from the meter to the panel, there is no main disconnect. Only way to disconnect the electric to the apt is to shut off the individual breakers ( see pic), or in the more recent renovations, shut off the main breaker in the basement panel feeding the sub-panel in the apartment.

https://plus.google.com/118428219834...ts/F9zvftJ7EvL

(Only the 2 apartments on the first floor do not have a sub-panel within the apartment).
All of the panels in the basement are main lug.
There is a main 200A disconnect for the entire building.

Is this correct? Isn't it necessary to protect the wiring or provide a means of disconnect from the meter to the panel?


IDK about NYC, but here in NJ there is generally no disconnect or
protection between the meter and the panel main breaker. I've never
seen one.



I'm asking because we are doing a bathroom reno on the first floor, and I ran a new 12/2 BX just for the bathroom. And when I installed in the panel, to be safe I wanted to de-energize the entire panel, but the only way to do that was to turn off the entire building.

I managed to install it anyway while the panel was live.


I think what you're saying is really lacking here is a main breaker
in the panel. I agree, that is unusual and almost certainly not code.
  #3   Report Post  
Senior Member
 
Posts: 2,498
Default

Mike:

I own a 21 unit apartment building in Winnipeg, Manitoba.

I have a 600 amp "panel" with no breakers on it, just a large handle that shuts off the power to the whole building.

Coming out of that 600 amp "panel" are cables that go to 21 different main breaker boxes that shut off power to each of the individual apartments. Power goes through those breaker boxes, then through a meter for each apartment. There are also two main breaker boxes and two meters for the common areas of the building (like hallway lights and electrical receptacles where I can plug in the vaccuum cleaner for cleaning the hallway carpets) as well as the parking fence outdoors where tenants plug in their block heaters during the winter.

Each apartment has it's own fuse box. That fuse box contains a fuse holder for the stove and anywhere from two to six plug (or "screw-in" style) fuses. The fuse holder for the stove holds two 40 amp cartridge style fuses in it, and each of the plug fuse sockets contains a plastic 15 amp fuse rejector. When I first took over this building, I found 20, 25 and 30 amp fuses in the suite fuse boxes that were put in by tenants because the fuses on the circuits they had plugged their window air conditioners into would blow. So, instead of installing 15 amp slo-blo fuses on those circuits, they installed 20, 25 and 30 amp fuses instead.

Anyhow, all my building has is a main switch to turn off the power to the entire building, breaker panels with one switch each for each apartment and two breaker panels for the common areas, meters for each apartment and two meters for the common areas, and a fuse box in each apartment that has the fuses for the stove and individual 15 amp circuits within each apartment.

Last edited by nestork : December 14th 14 at 08:53 PM
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 148
Default Question on 6 family apt building electric panels

I own a 6 family apartment building in Brooklyn, and the electric was upgraded back in 2000.
I noticed on these panels in the basement, the feed coming straight from the meter to the panel, there is no main disconnect. Only way to disconnect the electric to the apt is to shut off the individual breakers ( see pic), or in the more recent renovations, shut off the main breaker in the basement panel feeding the sub-panel in the apartment.

https://plus.google.com/118428219834...ts/F9zvftJ7EvL

(Only the 2 apartments on the first floor do not have a sub-panel within the apartment).
All of the panels in the basement are main lug.
There is a main 200A disconnect for the entire building.

Is this correct? Isn't it necessary to protect the wiring or provide a means of disconnect from the meter to the panel?

I'm asking because we are doing a bathroom reno on the first floor, and I ran a new 12/2 BX just for the bathroom. And when I installed in the panel, to be safe I wanted to de-energize the entire panel, but the only way to do that was to turn off the entire building.

I managed to install it anyway while the panel was live.



*With six circuits or less in each panel, no main breaker is required. You could have requested the mains to be installed at the time, but that would have added to the cost of the job.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default Question on 6 family apt building electric panels

I've heard of this "six breaker" rule, but was not sure what it meant.



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Question on 6 family apt building electric panels

On Sunday, December 14, 2014 1:47:26 PM UTC-5, wrote:
On Sun, 14 Dec 2014 05:34:18 -0800 (PST), Mikepier
wrote:

I own a 6 family apartment building in Brooklyn, and the electric was upgraded back in 2000.
I noticed on these panels in the basement, the feed coming straight from the meter to the panel, there is no main disconnect. Only way to disconnect the electric to the apt is to shut off the individual breakers ( see pic), or in the more recent renovations, shut off the main breaker in the basement panel feeding the sub-panel in the apartment.

https://plus.google.com/118428219834...ts/F9zvftJ7EvL

(Only the 2 apartments on the first floor do not have a sub-panel within the apartment).
All of the panels in the basement are main lug.
There is a main 200A disconnect for the entire building.

Is this correct? Isn't it necessary to protect the wiring or provide a means of disconnect from the meter to the panel?

I'm asking because we are doing a bathroom reno on the first floor, and I ran a new 12/2 BX just for the bathroom. And when I installed in the panel, to be safe I wanted to de-energize the entire panel, but the only way to do that was to turn off the entire building.

I managed to install it anyway while the panel was live.

+

There are 2 issues here. The first is the service disconnecting means.
The NEC requires
"The service disconnecting means shall be installed at a readily
accessible location either outside of a building or structure or
inside nearest the point of entrance of the service conductors."

... but they do not specify a distance.

The second issue is the disconnect itself.
It can be up to 6 breakers. There used to be an additional requirement
that this could only be 2 in a "lighting and appliance panelboard" but
that went away a couple cycles ago.

I need to also mention the NEC did not actually apply to NYC until
fairly recently but I understand the NYC code closely followed the NEC
with a few differences, mostly in wiring methods. (like no Romex)


If there is no main breaker that is sized to the service, what
prevents one from creating an overload in the panel with the sum
of the 6 breakers exceeding the capacity? If I have a 100 amp panel
with various breakers, all the breakers collectively could exceed the
100 amps, but the main breaker would trip. If I put six 30A breakers
in a panel, I could pull 180 amps, overload the service conductors,
but nothing would trip. Am I missing something?
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default Question on 6 family apt building electric panels

If there is no main breaker that is sized to the service, what
prevents one from creating an overload in the panel with the sum
of the 6 breakers exceeding the capacity? If I have a 100 amp panel
with various breakers, all the breakers collectively could exceed the
100 amps, but the main breaker would trip. If I put six 30A breakers
in a panel, I could pull 180 amps, overload the service conductors,
but nothing would trip. Am I missing something?


Exactly my point, what is protecting overcurrent from the meter to the panel?

I did notice when I took one of the panel covers off, the main feeding each panel looked pretty thick. I did not see what guage it is but perhaps it is rated for 200A? If that's the case, then maybe that's why there's no reason to put a separate main for each apt since the 200A main would protect everything.

Next time I'll take a closer look at what guage it is.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Question on 6 family apt building electric panels

On Monday, December 15, 2014 7:24:00 PM UTC-5, wrote:
On Mon, 15 Dec 2014 15:28:55 -0800 (PST), trader_4
wrote:

On Sunday, December 14, 2014 1:47:26 PM UTC-5, wrote:
On Sun, 14 Dec 2014 05:34:18 -0800 (PST), Mikepier
wrote:

I own a 6 family apartment building in Brooklyn, and the electric was upgraded back in 2000.
I noticed on these panels in the basement, the feed coming straight from the meter to the panel, there is no main disconnect. Only way to disconnect the electric to the apt is to shut off the individual breakers ( see pic), or in the more recent renovations, shut off the main breaker in the basement panel feeding the sub-panel in the apartment.

https://plus.google.com/118428219834...ts/F9zvftJ7EvL

(Only the 2 apartments on the first floor do not have a sub-panel within the apartment).
All of the panels in the basement are main lug.
There is a main 200A disconnect for the entire building.

Is this correct? Isn't it necessary to protect the wiring or provide a means of disconnect from the meter to the panel?

I'm asking because we are doing a bathroom reno on the first floor, and I ran a new 12/2 BX just for the bathroom. And when I installed in the panel, to be safe I wanted to de-energize the entire panel, but the only way to do that was to turn off the entire building.

I managed to install it anyway while the panel was live.
+

There are 2 issues here. The first is the service disconnecting means.
The NEC requires
"The service disconnecting means shall be installed at a readily
accessible location either outside of a building or structure or
inside nearest the point of entrance of the service conductors."

... but they do not specify a distance.

The second issue is the disconnect itself.
It can be up to 6 breakers. There used to be an additional requirement
that this could only be 2 in a "lighting and appliance panelboard" but
that went away a couple cycles ago.

I need to also mention the NEC did not actually apply to NYC until
fairly recently but I understand the NYC code closely followed the NEC
with a few differences, mostly in wiring methods. (like no Romex)


If there is no main breaker that is sized to the service, what
prevents one from creating an overload in the panel with the sum
of the 6 breakers exceeding the capacity? If I have a 100 amp panel
with various breakers, all the breakers collectively could exceed the
100 amps, but the main breaker would trip. If I put six 30A breakers
in a panel, I could pull 180 amps, overload the service conductors,
but nothing would trip. Am I missing something?


You would need to size the SE to the sum of the disconnecting
breakers. The reason why you can pack your panel, far beyond the
rating is your service disconnect is sized to the service entrance
conductors. If this is the main feeder to a dwelling, serving all the
loads you still get a break tho. You can use 310.15(B)(6)


K, that covers it and it makes sense.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default Question on 6 family apt building electric panels

If there is no main breaker that is sized to the service, what
prevents one from creating an overload in the panel with the sum
of the 6 breakers exceeding the capacity? If I have a 100 amp panel
with various breakers, all the breakers collectively could exceed the
100 amps, but the main breaker would trip. If I put six 30A breakers
in a panel, I could pull 180 amps, overload the service conductors,
but nothing would trip. Am I missing something?


Is this where the 6 breaker rule comes into play?

Anotherwords, if you have 6- 20A breakers, then you can only pull 120A max.

So as long as the feed from the meter to the panel can handle 120A, your good?

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Question on 6 family apt building electric panels

On Tuesday, December 16, 2014 5:16:20 AM UTC-5, Mikepier wrote:
If there is no main breaker that is sized to the service, what
prevents one from creating an overload in the panel with the sum
of the 6 breakers exceeding the capacity? If I have a 100 amp panel
with various breakers, all the breakers collectively could exceed the
100 amps, but the main breaker would trip. If I put six 30A breakers
in a panel, I could pull 180 amps, overload the service conductors,
but nothing would trip. Am I missing something?


Is this where the 6 breaker rule comes into play?

Anotherwords, if you have 6- 20A breakers, then you can only pull 120A max.

So as long as the feed from the meter to the panel can handle 120A, your good?


Yes, that's what Gfre said. The disconnect(s) have to be sized to the
sevice capacity. With a main breaker, the main breaker serves that purpose,
so then the individual breakers can add up to more than that main breaker.
With no main breaker and 6 separate breakers serving as the disconnect,
then the 6 have to sum up to equal to or less than the service capacity.

To be technical, it would not only be the feed from the meter to the panel,
it would also be the feed, service to the meter as well.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What's up with Canada and horizontal electric panels? [email protected][_2_] Home Repair 63 February 20th 18 02:48 AM
Building interior windows insulation panels MM UK diy 104 November 17th 13 04:47 PM
electric shock from solar panels Bill Wright[_2_] UK diy 83 July 12th 13 07:20 AM
Electric/Water Solar panels ? www.GymRatZ.co.uk[_2_] UK diy 167 June 1st 12 07:47 PM
Building and installing passive solar heating panels Morris Dovey Woodworking 14 April 2nd 07 03:08 AM


All times are GMT +1. The time now is 07:21 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"