I got home around 6 last night and around 7 noticed that it was pretty
cold. 63F to be exact, not really cold, but not the 68 that it should
have been. The thermostat was blinking, indicating that heat was on
the way, but the boiler was off. I panicked for a second since it was
going down to 10F that night, but I took off the front cover and tried
to remember what was supposed to be happening.

The last time this occurred was a few years back and the culprit was
the thermocouple, a fairly clever device looking like a 36" piece of
thick copper wire. After the service guy replaced it, I bought another
and had it sitting on top of the boiler all this time. I figured that
I'd replace it and see what that did.

One end screws into a slot that holds the end of the thermocouple in
the pilot flame, which was off. The other end screws into an
electrical box that I assume is the brains of the thing. The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

I turned off the power to the boiler but not the gas. I replaced the
thermocouple, turned on the power, pressed down the red switch that
controls the pilot gas and lit the pilot light. I know from the gas
water heater that you need to hold that switch down for 10 seconds or
so while it burns.

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default The Thermocouple and the Boiler - success

dgk wrote:

I got home around 6 last night and around 7 noticed that it was pretty
cold. 63F to be exact, not really cold, but not the 68 that it should
have been. The thermostat was blinking, indicating that heat was on
the way, but the boiler was off. I panicked for a second since it was
going down to 10F that night, but I took off the front cover and tried
to remember what was supposed to be happening.

The last time this occurred was a few years back and the culprit was
the thermocouple, a fairly clever device looking like a 36" piece of
thick copper wire. After the service guy replaced it, I bought another
and had it sitting on top of the boiler all this time. I figured that
I'd replace it and see what that did.

One end screws into a slot that holds the end of the thermocouple in
the pilot flame, which was off. The other end screws into an
electrical box that I assume is the brains of the thing. The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

I turned off the power to the boiler but not the gas. I replaced the
thermocouple, turned on the power, pressed down the red switch that
controls the pilot gas and lit the pilot light. I know from the gas
water heater that you need to hold that switch down for 10 seconds or
so while it burns.

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.


Hi,
You wanna one Atta boy for that?
  #3   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default The Thermocouple and the Boiler - success

On 3/4/2014 2:24 PM, dgk wrote:
....

The last time this occurred was a few years back and the culprit was
the thermocouple, ...


... The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

....

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.


That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

And, yes, the TC generates a thermoelectric voltage that is what's
needed for the gas safety valve to open. Before that, there were "wild
pilots" that didn't cut off. I have an old small stove in the pump
house that dates back to WW II era that was before in the bathroom of
the old house before central heat. It worked that way for 70 years w/o
it ever causing an issue even when the KS wind occasionally would blow
out the pilot light. The pilot assembly itself corroded so much that I
had to replace it a couple of years ago so when I did I put in a new
safety valve at the time as well...

--
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default The Thermocouple and the Boiler - success

dpb wrote:
On 3/4/2014 2:24 PM, dgk wrote:
...

The last time this occurred was a few years back and the culprit was
the thermocouple, ...


... The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

...

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.


That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

And, yes, the TC generates a thermoelectric voltage that is what's
needed for the gas safety valve to open. Before that, there were "wild
pilots" that didn't cut off. I have an old small stove in the pump
house that dates back to WW II era that was before in the bathroom of
the old house before central heat. It worked that way for 70 years w/o
it ever causing an issue even when the KS wind occasionally would blow
out the pilot light. The pilot assembly itself corroded so much that I
had to replace it a couple of years ago so when I did I put in a new
safety valve at the time as well...

--

Hi,
Only thermocouples in my house/cabin are in the NG fire places, almost
20 years old. So far they did not fail. Maybe OP is adjusting the pilot
flame size too big?
  #5   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default The Thermocouple and the Boiler - success

On 3/4/2014 5:27 PM, Tony Hwang wrote:
dpb wrote:
On 3/4/2014 2:24 PM, dgk wrote:
...

The last time this occurred was a few years back and the culprit was
the thermocouple, ...

....

That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

....

Only thermocouples in my house/cabin are in the NG fire places, almost
20 years old. So far they did not fail. Maybe OP is adjusting the pilot
flame size too big?


Indeed, I've never heard of one failing at all (altho I'm sure they do
on occasion) but twice within just a few years implies to me something's
just not right.

--


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default The Thermocouple and the Boiler - success

On Tue, 04 Mar 2014 15:12:16 -0600, dpb wrote:

On 3/4/2014 2:24 PM, dgk wrote:
...

The last time this occurred was a few years back and the culprit was
the thermocouple, ...


... The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

...

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.


That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

And, yes, the TC generates a thermoelectric voltage that is what's
needed for the gas safety valve to open. Before that, there were "wild
pilots" that didn't cut off. I have an old small stove in the pump
house that dates back to WW II era that was before in the bathroom of
the old house before central heat. It worked that way for 70 years w/o
it ever causing an issue even when the KS wind occasionally would blow
out the pilot light. The pilot assembly itself corroded so much that I
had to replace it a couple of years ago so when I did I put in a new
safety valve at the time as well...

I've seen a lot of thermocouples fail. 2 on each of my old water
heaters, 2 on the old furnace, 1 on my old friend's water heater, and
2 on his boiler. That's in 32 years in this house, and just over 15 in
my old friend's.

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default The Thermocouple and the Boiler - success

On Tue, 04 Mar 2014 16:27:10 -0700, Tony Hwang
wrote:

dpb wrote:
On 3/4/2014 2:24 PM, dgk wrote:
...

The last time this occurred was a few years back and the culprit was
the thermocouple, ...


... The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

...

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.


That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

And, yes, the TC generates a thermoelectric voltage that is what's
needed for the gas safety valve to open. Before that, there were "wild
pilots" that didn't cut off. I have an old small stove in the pump
house that dates back to WW II era that was before in the bathroom of
the old house before central heat. It worked that way for 70 years w/o
it ever causing an issue even when the KS wind occasionally would blow
out the pilot light. The pilot assembly itself corroded so much that I
had to replace it a couple of years ago so when I did I put in a new
safety valve at the time as well...

--

Hi,
Only thermocouples in my house/cabin are in the NG fire places, almost
20 years old. So far they did not fail. Maybe OP is adjusting the pilot
flame size too big?

Thermocouple or thermopile??? Many fireplaces use milivolt systems
with thermopiles.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default The Thermocouple and the Boiler - success

On Tue, 04 Mar 2014 17:47:31 -0600, dpb wrote:

On 3/4/2014 5:27 PM, Tony Hwang wrote:
dpb wrote:
On 3/4/2014 2:24 PM, dgk wrote:
...

The last time this occurred was a few years back and the culprit was
the thermocouple, ...

...

That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

...

Only thermocouples in my house/cabin are in the NG fire places, almost
20 years old. So far they did not fail. Maybe OP is adjusting the pilot
flame size too big?


Indeed, I've never heard of one failing at all (altho I'm sure they do
on occasion) but twice within just a few years implies to me something's
just not right.

How about Chinese thermocouples?
  #9   Report Post  
Posted to alt.home.repair
dgk dgk is offline
external usenet poster
 
Posts: 521
Default The Thermocouple and the Boiler - success

On Tue, 04 Mar 2014 16:27:10 -0700, Tony Hwang
wrote:

dpb wrote:
On 3/4/2014 2:24 PM, dgk wrote:
...

The last time this occurred was a few years back and the culprit was
the thermocouple, ...


... The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

...

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.


That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

And, yes, the TC generates a thermoelectric voltage that is what's
needed for the gas safety valve to open. Before that, there were "wild
pilots" that didn't cut off. I have an old small stove in the pump
house that dates back to WW II era that was before in the bathroom of
the old house before central heat. It worked that way for 70 years w/o
it ever causing an issue even when the KS wind occasionally would blow
out the pilot light. The pilot assembly itself corroded so much that I
had to replace it a couple of years ago so when I did I put in a new
safety valve at the time as well...

--

Hi,
Only thermocouples in my house/cabin are in the NG fire places, almost
20 years old. So far they did not fail. Maybe OP is adjusting the pilot
flame size too big?


How often do you use the fireplace? This winter the boiler has been on
an awful lot. I will take a look at how high the pilot light is, and
whether the thermocouple is too close to the main burner.

Since it's the only house I own, I have nothing to compare it to.
That's sort of the problem for many of us who try to do some home
repairs. It's usually the first time on lots of things, and we learn a
lot and get better for the second time, if there is a second time.


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default The Thermocouple and the Boiler - success

dgk wrote:
On Tue, 04 Mar 2014 16:27:10 -0700, Tony Hwang
wrote:

dpb wrote:
On 3/4/2014 2:24 PM, dgk wrote:
...

The last time this occurred was a few years back and the culprit was
the thermocouple, ...

... The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

...

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.

That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

And, yes, the TC generates a thermoelectric voltage that is what's
needed for the gas safety valve to open. Before that, there were "wild
pilots" that didn't cut off. I have an old small stove in the pump
house that dates back to WW II era that was before in the bathroom of
the old house before central heat. It worked that way for 70 years w/o
it ever causing an issue even when the KS wind occasionally would blow
out the pilot light. The pilot assembly itself corroded so much that I
had to replace it a couple of years ago so when I did I put in a new
safety valve at the time as well...

--

Hi,
Only thermocouples in my house/cabin are in the NG fire places, almost
20 years old. So far they did not fail. Maybe OP is adjusting the pilot
flame size too big?


How often do you use the fireplace? This winter the boiler has been on
an awful lot. I will take a look at how high the pilot light is, and
whether the thermocouple is too close to the main burner.

Since it's the only house I own, I have nothing to compare it to.
That's sort of the problem for many of us who try to do some home
repairs. It's usually the first time on lots of things, and we learn a
lot and get better for the second time, if there is a second time.


Hi,
The position of it and flame size is adjustable. Even thermocouple in my
camping trailers for many years never failed during my ownership.



  #11   Report Post  
Posted to alt.home.repair
dgk dgk is offline
external usenet poster
 
Posts: 521
Default The Thermocouple and the Boiler - success

On Wed, 05 Mar 2014 18:51:28 -0700, Tony Hwang
wrote:

dgk wrote:
On Tue, 04 Mar 2014 16:27:10 -0700, Tony Hwang
wrote:

dpb wrote:
On 3/4/2014 2:24 PM, dgk wrote:
...

The last time this occurred was a few years back and the culprit was
the thermocouple, ...

... The job of
the thermocouple appears to be telling the brain that the pilot light
is indeed lit, so that the gas doesn't just fill up the house.

...

The pilot stayed lit, and as I stood there for a few seconds trying to
figure out what to do next, there's a click that was apparently the
brain getting the news from the thermocouple that all was well, and
the thing fires up. Catastrophe averted.

I'll pick up another thermocouple and leave it on top of the boiler.
I'll likely sell the house in a year or two and move to Florida, but
I'm sure the next folks will need it one day.

That's most unusual to fail a TC so rapidly -- I've never had the TC
itself fail in 40+ yr from the time the previous furnace was installed
until upgraded it a couple of years ago. I'd wonder why -- is it routed
too close to the main burner, perhaps?

And, yes, the TC generates a thermoelectric voltage that is what's
needed for the gas safety valve to open. Before that, there were "wild
pilots" that didn't cut off. I have an old small stove in the pump
house that dates back to WW II era that was before in the bathroom of
the old house before central heat. It worked that way for 70 years w/o
it ever causing an issue even when the KS wind occasionally would blow
out the pilot light. The pilot assembly itself corroded so much that I
had to replace it a couple of years ago so when I did I put in a new
safety valve at the time as well...

--
Hi,
Only thermocouples in my house/cabin are in the NG fire places, almost
20 years old. So far they did not fail. Maybe OP is adjusting the pilot
flame size too big?


How often do you use the fireplace? This winter the boiler has been on
an awful lot. I will take a look at how high the pilot light is, and
whether the thermocouple is too close to the main burner.

Since it's the only house I own, I have nothing to compare it to.
That's sort of the problem for many of us who try to do some home
repairs. It's usually the first time on lots of things, and we learn a
lot and get better for the second time, if there is a second time.


Hi,
The position of it and flame size is adjustable. Even thermocouple in my
camping trailers for many years never failed during my ownership.


I'm going to take another look. I guess if the thermocouple fails the
electronics also turn off the pilot light, which would be why it was
off.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
thermocouple [email protected] Home Repair 4 December 26th 08 07:02 PM
boiler pilot-or-thermocouple craps-out on COLDEST day; WHY? David Combs Home Repair 5 December 15th 05 12:46 PM
Apollo Boiler Thermocouple/Spark problem JohnGorrod UK diy 1 March 8th 05 06:53 AM
Thermocouple Christian Electronics Repair 2 August 31st 04 03:18 AM
gas boiler thermocouple Stoney UK diy 56 October 20th 03 09:02 PM


All times are GMT +1. The time now is 06:33 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"