I'm installing a 35'x5" round aluminum chimney liner because my exterior chimney (terracotta inside block) is showing wet spots in the mortar joints. I have a 36,000 btu gas fired hot water heater that has a 3" gravity flue piped to my chimney and also a 100,000 btu input 80% power vented heater with a 3" flue that bumps up to 5" before it enters my chimney. I'm a pipe fitter by trade so I deal with installing these all the time but never deal with the flue side. My question is when I bring the 5" through my chimney and tie in a 5" wye, which appliance should go on the bull of the T? I've been told both ways, just curious what some thoughts are. Thanks.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default Chimney liner

I'm pulling the liner through an existing 5" hole in my basement and the wye will not be in the chimney
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 296
Default Chimney liner

On Thursday, February 6, 2014 6:04:08 PM UTC-5, wrote:
I'm installing a 35'x5" round aluminum chimney liner because my exterior chimney (terracotta inside block) is showing wet spots in the mortar joints.. I have a 36,000 btu gas fired hot water heater that has a 3" gravity flue piped to my chimney and also a 100,000 btu input 80% power vented heater with a 3" flue that bumps up to 5" before it enters my chimney. I'm a pipe fitter by trade so I deal with installing these all the time but never deal with the flue side. My question is when I bring the 5" through my chimney and tie in a 5" wye, which appliance should go on the bull of the T? I've been told both ways, just curious what some thoughts are. Thanks.



I'm not an expert but I've owned homes with the gas hw heater and gas T'd together before myself. I've always wondered how the waste heat from the hw was enough to get out the vent without condensing when the furnace was not on.

One consideration is that your next gas furnace will probably be a condensing one. How old is your furnace and hw heater now?
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,377
Default Chimney liner

On 02/08/2014 08:19 AM, jamesgang wrote:
On Thursday, February 6, 2014 6:04:08 PM UTC-5, wrote:
I'm installing a 35'x5" round aluminum chimney liner because my exterior chimney (terracotta inside block) is showing wet spots in the mortar joints. I have a 36,000 btu gas fired hot water heater that has a 3" gravity flue piped to my chimney and also a 100,000 btu input 80% power vented heater with a 3" flue that bumps up to 5" before it enters my chimney. I'm a pipe fitter by trade so I deal with installing these all the time but never deal with the flue side. My question is when I bring the 5" through my chimney and tie in a 5" wye, which appliance should go on the bull of the T? I've been told both ways, just curious what some thoughts are. Thanks.



I'm not an expert but I've owned homes with the gas hw heater and gas T'd together before myself. I've always wondered how the waste heat from the hw was enough to get out the vent without condensing when the furnace was not on.

One consideration is that your next gas furnace will probably be a condensing one. How old is your furnace and hw heater now?




It's interesting that you mentioned that...because that was the very
thing I did not bring up before. The building inspector I talked to told
me that the water heater alone is /not/ sufficient without the furnace
also running.


The reason I did not mention that was because it did not seem right...
but then realized that in the summer, when the furnace is not
running...since it's warmer, there of course would not be a condensation
problem. In my situation it needs to get to -10F before there's a problem.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Chimney liner

On Saturday, February 8, 2014 9:44:11 AM UTC-5, philo* wrote:
On 02/08/2014 08:19 AM, jamesgang wrote:

On Thursday, February 6, 2014 6:04:08 PM UTC-5, wrote:


I'm installing a 35'x5" round aluminum chimney liner because my exterior chimney (terracotta inside block) is showing wet spots in the mortar joints. I have a 36,000 btu gas fired hot water heater that has a 3" gravity flue piped to my chimney and also a 100,000 btu input 80% power vented heater with a 3" flue that bumps up to 5" before it enters my chimney. I'm a pipe fitter by trade so I deal with installing these all the time but never deal with the flue side. My question is when I bring the 5" through my chimney and tie in a 5" wye, which appliance should go on the bull of the T? I've been told both ways, just curious what some thoughts are. Thanks.






I'm not an expert but I've owned homes with the gas hw heater and gas T'd together before myself. I've always wondered how the waste heat from the hw was enough to get out the vent without condensing when the furnace was not on.




One consideration is that your next gas furnace will probably be a condensing one. How old is your furnace and hw heater now?










It's interesting that you mentioned that...because that was the very

thing I did not bring up before. The building inspector I talked to told

me that the water heater alone is /not/ sufficient without the furnace

also running.





The reason I did not mention that was because it did not seem right...

but then realized that in the summer, when the furnace is not

running...since it's warmer, there of course would not be a condensation

problem. In my situation it needs to get to -10F before there's a problem..


That's the essence of the condensation issue. Condensation becomes
a problem when a chimney is sized for a furnace plus WH and then the
furnace is converted to direct vent. You then have a chimney that is
too large for just the water heater, making it very easy for condensation
to occur. With the large chimney and the furnace, when the weather was
cold enough for condensation to occur, the furnace was running enough
of the time to keep the chimney free of condensation. Also, with a
chimney that is too large, you won't get proper drafting. So, if you
go with a direct vent furnace and keep an existing WH,
you probably need a flue liner to reduce the
size. I guess at some point, if the run is long enough and the climate
cold enough, you're going to get condensation anyway, because the WH
doesn't generate enough heat. But with a liner, any condensation is
going to stay in the liner, not screw up the flue.


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,415
Default Chimney liner

" wrote:
On Saturday, February 8, 2014 9:44:11 AM UTC-5, philo wrote:
On 02/08/2014 08:19 AM, jamesgang wrote:

On Thursday, February 6, 2014 6:04:08 PM UTC-5, wrote:


I'm installing a 35'x5" round aluminum chimney liner because my
exterior chimney (terracotta inside block) is showing wet spots in the
mortar joints. I have a 36,000 btu gas fired hot water heater that has
a 3" gravity flue piped to my chimney and also a 100,000 btu input 80%
power vented heater with a 3" flue that bumps up to 5" before it
enters my chimney. I'm a pipe fitter by trade so I deal with
installing these all the time but never deal with the flue side. My
question is when I bring the 5" through my chimney and tie in a 5"
wye, which appliance should go on the bull of the T? I've been told
both ways, just curious what some thoughts are. Thanks.






I'm not an expert but I've owned homes with the gas hw heater and gas
T'd together before myself. I've always wondered how the waste heat
from the hw was enough to get out the vent without condensing when the
furnace was not on.




One consideration is that your next gas furnace will probably be a
condensing one. How old is your furnace and hw heater now?










It's interesting that you mentioned that...because that was the very

thing I did not bring up before. The building inspector I talked to told

me that the water heater alone is /not/ sufficient without the furnace

also running.





The reason I did not mention that was because it did not seem right...

but then realized that in the summer, when the furnace is not

running...since it's warmer, there of course would not be a condensation

problem. In my situation it needs to get to -10F before there's a problem.


That's the essence of the condensation issue. Condensation becomes
a problem when a chimney is sized for a furnace plus WH and then the
furnace is converted to direct vent. You then have a chimney that is
too large for just the water heater, making it very easy for condensation
to occur. With the large chimney and the furnace, when the weather was
cold enough for condensation to occur, the furnace was running enough
of the time to keep the chimney free of condensation. Also, with a
chimney that is too large, you won't get proper drafting. So, if you
go with a direct vent furnace and keep an existing WH,
you probably need a flue liner to reduce the
size. I guess at some point, if the run is long enough and the climate
cold enough, you're going to get condensation anyway, because the WH
doesn't generate enough heat. But with a liner, any condensation is
going to stay in the liner, not screw up the flue.


I don't think a normal furnace has enough exhaust heat to evaporate
condensation. I noticed a lo of water inside top of mine earlier in the
year. Even some moss. That's without liner.

On my living house, I got water heater up old chimney which is external.
HVAC installed it. It's probably ok except during a heavy storm, my
uncovered chimney leaked some water of of bottom clean out from old oil
burner furnace, which originally was coal.

Greg
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 178
Default Chimney liner

On 02/08/2014 10:34 PM, gregz wrote:


snip
I don't think a normal furnace has enough exhaust heat to evaporate
condensation. I noticed a lo of water inside top of mine earlier in the
year. Even some moss. That's without liner.

On my living house, I got water heater up old chimney which is external.
HVAC installed it. It's probably ok except during a heavy storm, my
uncovered chimney leaked some water of of bottom clean out from old oil
burner furnace, which originally was coal.

Greg




My house originally was coal. When I bought it, it used an oil burner
which I replaced and went to gas. I installed it myself.

Eventually as I finally managed to start saving up some money I had
professionals put in a new one.

They made one small error. The exhaust pipe going into the chimney was
not cut and the lower portion jutted out and collected a small amount of
moisture when it rained. That was just enough to clog the air flow
sensor. Once I cut the pipe flush, I have had no more problems.
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Chimney liner

On Saturday, February 8, 2014 11:34:46 PM UTC-5, Gz wrote:
" wrote:

On Saturday, February 8, 2014 9:44:11 AM UTC-5, philo wrote:


On 02/08/2014 08:19 AM, jamesgang wrote:




On Thursday, February 6, 2014 6:04:08 PM UTC-5, wrote:




I'm installing a 35'x5" round aluminum chimney liner because my


exterior chimney (terracotta inside block) is showing wet spots in the


mortar joints. I have a 36,000 btu gas fired hot water heater that has


a 3" gravity flue piped to my chimney and also a 100,000 btu input 80%


power vented heater with a 3" flue that bumps up to 5" before it


enters my chimney. I'm a pipe fitter by trade so I deal with


installing these all the time but never deal with the flue side. My


question is when I bring the 5" through my chimney and tie in a 5"


wye, which appliance should go on the bull of the T? I've been told


both ways, just curious what some thoughts are. Thanks.












I'm not an expert but I've owned homes with the gas hw heater and gas


T'd together before myself. I've always wondered how the waste heat


from the hw was enough to get out the vent without condensing when the


furnace was not on.








One consideration is that your next gas furnace will probably be a


condensing one. How old is your furnace and hw heater now?




















It's interesting that you mentioned that...because that was the very




thing I did not bring up before. The building inspector I talked to told




me that the water heater alone is /not/ sufficient without the furnace




also running.












The reason I did not mention that was because it did not seem right...




but then realized that in the summer, when the furnace is not




running...since it's warmer, there of course would not be a condensation




problem. In my situation it needs to get to -10F before there's a problem.




That's the essence of the condensation issue. Condensation becomes


a problem when a chimney is sized for a furnace plus WH and then the


furnace is converted to direct vent. You then have a chimney that is


too large for just the water heater, making it very easy for condensation


to occur. With the large chimney and the furnace, when the weather was


cold enough for condensation to occur, the furnace was running enough


of the time to keep the chimney free of condensation. Also, with a


chimney that is too large, you won't get proper drafting. So, if you


go with a direct vent furnace and keep an existing WH,


you probably need a flue liner to reduce the


size. I guess at some point, if the run is long enough and the climate


cold enough, you're going to get condensation anyway, because the WH


doesn't generate enough heat. But with a liner, any condensation is


going to stay in the liner, not screw up the flue.




I don't think a normal furnace has enough exhaust heat to evaporate

condensation.


For the most part the furnace doesn't have to evaporate the
condensation, the exhaust gases just never condense to begin with.
A conventional furnace is only 80% efficient. If you have a 100K BTU
furnace, you're putting 20K BTU up the chimney. If the chimney is
properly sized, it will keep it hot enough when it's cold out so that condensation is minimal.

If you take the chimney that was sized for a 100K BTU furnace and a
35K BTU water heater, ie 135K total and remove the furnace, then you
have a problem. The chimney is now oversized and the WH is typically
going to run a lot less
and for shorter periods than the furnace did. When it's 20F outside,
with the chimney not in a heated space, then you will get condensation.
And over time, with a gas furnace, it will deteriorate the mortar in
the flue joints because of the acidity. You might not see any evidence
of problems for a long time, but when you do, it will be too late.



I noticed a lo of water inside top of mine earlier in the

year. Even some moss. That's without liner.



Is the chimney properly sized?




On my living house, I got water heater up old chimney which is external.

HVAC installed it. It's probably ok except during a heavy storm, my

uncovered chimney leaked some water of of bottom clean out from old oil

burner furnace, which originally was coal.



Greg


  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,415
Default Chimney liner

" wrote:
On Saturday, February 8, 2014 11:34:46 PM UTC-5, Gz wrote:
" wrote:

On Saturday, February 8, 2014 9:44:11 AM UTC-5, philo wrote:


On 02/08/2014 08:19 AM, jamesgang wrote:




On Thursday, February 6, 2014 6:04:08 PM UTC-5, wrote:




I'm installing a 35'x5" round aluminum chimney liner because my


exterior chimney (terracotta inside block) is showing wet spots in the


mortar joints. I have a 36,000 btu gas fired hot water heater that has


a 3" gravity flue piped to my chimney and also a 100,000 btu input 80%


power vented heater with a 3" flue that bumps up to 5" before it


enters my chimney. I'm a pipe fitter by trade so I deal with


installing these all the time but never deal with the flue side. My


question is when I bring the 5" through my chimney and tie in a 5"


wye, which appliance should go on the bull of the T? I've been told


both ways, just curious what some thoughts are. Thanks.












I'm not an expert but I've owned homes with the gas hw heater and gas


T'd together before myself. I've always wondered how the waste heat


from the hw was enough to get out the vent without condensing when the


furnace was not on.








One consideration is that your next gas furnace will probably be a


condensing one. How old is your furnace and hw heater now?




















It's interesting that you mentioned that...because that was the very




thing I did not bring up before. The building inspector I talked to told




me that the water heater alone is /not/ sufficient without the furnace




also running.












The reason I did not mention that was because it did not seem right...




but then realized that in the summer, when the furnace is not




running...since it's warmer, there of course would not be a condensation




problem. In my situation it needs to get to -10F before there's a problem.




That's the essence of the condensation issue. Condensation becomes


a problem when a chimney is sized for a furnace plus WH and then the


furnace is converted to direct vent. You then have a chimney that is


too large for just the water heater, making it very easy for condensation


to occur. With the large chimney and the furnace, when the weather was


cold enough for condensation to occur, the furnace was running enough


of the time to keep the chimney free of condensation. Also, with a


chimney that is too large, you won't get proper drafting. So, if you


go with a direct vent furnace and keep an existing WH,


you probably need a flue liner to reduce the


size. I guess at some point, if the run is long enough and the climate


cold enough, you're going to get condensation anyway, because the WH


doesn't generate enough heat. But with a liner, any condensation is


going to stay in the liner, not screw up the flue.




I don't think a normal furnace has enough exhaust heat to evaporate

condensation.


For the most part the furnace doesn't have to evaporate the
condensation, the exhaust gases just never condense to begin with.
A conventional furnace is only 80% efficient. If you have a 100K BTU
furnace, you're putting 20K BTU up the chimney. If the chimney is
properly sized, it will keep it hot enough when it's cold out so that
condensation is minimal.

If you take the chimney that was sized for a 100K BTU furnace and a
35K BTU water heater, ie 135K total and remove the furnace, then you
have a problem. The chimney is now oversized and the WH is typically
going to run a lot less
and for shorter periods than the furnace did. When it's 20F outside,
with the chimney not in a heated space, then you will get condensation.
And over time, with a gas furnace, it will deteriorate the mortar in
the flue joints because of the acidity. You might not see any evidence
of problems for a long time, but when you do, it will be too late.



I noticed a lo of water inside top of mine earlier in the

year. Even some moss. That's without liner.



Is the chimney properly sized?



I think not. Like 10x10 at least. I noticed the moisture when outside temps
were 40-50 degrees. This is one shaft. Might have been 4 shaft with two
chimneys. 1900 house. I have not run the water heater yet. Its been off for
going on 3 years. There is also a trail of minerals on the bottom of the
flew to the furnace. I even think the minerals got on the exhaust fan
blades. Fun times.

The two chimney bottoms are also part of the support structure. All other
shafts are top sealed off.

Greg





On my living house, I got water heater up old chimney which is external.

HVAC installed it. It's probably ok except during a heavy storm, my

uncovered chimney leaked some water of of bottom clean out from old oil

burner furnace, which originally was coal.



Greg

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chimney liner Tim Lamb[_2_] UK diy 0 January 22nd 09 11:11 PM
Chimney Liner DSegal1027 Home Repair 0 January 21st 05 02:39 AM
Chimney Liner DSegal1027 Home Repair 1 January 19th 05 03:26 AM
New chimney liner nex barry martin Home Repair 1 October 19th 04 05:27 PM