Default Please explain "Parallel pressure reducing valves"

I found this at http://www.plumbinghelp.ca/pressure_reducing_valve.php

There's an image showing parallel pressure reducing valves along with
this text:

"Installing pressure reducing valves in parallel offers the ability to
service a valve while continuing to provide water to the occupants.
Parallel PRV's are also recommended for buildings with a wide variance
of water demand as each PRV can operate at a different pressure
setting to provide better performance at peak flow."


OK, how would that work in the case of "a wide variance of water
demand"? With 2 different settings, what would be the final output
pressure and how would that compensate for "peak flow"?

I don't think they expect manual switching of PRV's/
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,453
Default Please explain "Parallel pressure reducing valves"

DerbyDad03 wrote:

I found this at http://www.plumbinghelp.ca/pressure_reducing_valve.php

There's an image showing parallel pressure reducing valves along with
this text:

"Installing pressure reducing valves in parallel offers the ability to
service a valve while continuing to provide water to the occupants.
Parallel PRV's are also recommended for buildings with a wide variance
of water demand as each PRV can operate at a different pressure
setting to provide better performance at peak flow."


OK, how would that work in the case of "a wide variance of water
demand"? With 2 different settings, what would be the final output
pressure and how would that compensate for "peak flow"?

I don't think they expect manual switching of PRV's/


I suspect the 2nd PRV is set at a lower pressure - if demand is so high that
the pressure in the final pipework (after the PRVs) drops below the setting
of the 2nd PRV - then the 2nd PRV will also pass water in addition to the
1st PRV.

When I fitted a 22mm PRV to drop my supply (7.5 bar) to a more reasonable 4
bar, I did some measurements with a short stub of 22mm copper pipe directly
on the PRV output.

The PRV is fed by 2m of 22mm (ish) bore MDPE joined to 1/2" alkathene which
is about 11m length back to the main pipe in the road.

No matter where I set the PRV pressure from about 2 bar to 6 bar, the max
flow remained at about 55 litres/minute (which is considered good in
England[1])

[1] compared to an 80 year old scaled up bit of squashed lead pipe.

Obviously, the pressure setting will affect the flow through subsequant
restricted pipework - but the PRV itself did not seem to impede flow
significantly.


--
Tim Watts Personal Blog: http://www.dionic.net/tim/

"History will be kind to me for I intend to write it."

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Please explain "Parallel pressure reducing valves"

On Nov 28, 3:04*pm, Tim Watts wrote:
DerbyDad03 wrote:
I found this athttp://www.plumbinghelp.ca/pressure_reducing_valve.php


There's an image showing parallel pressure reducing valves along with
this text:


"Installing pressure reducing valves in parallel offers the ability to
service a valve while continuing to provide water to the occupants.
Parallel PRV's are also recommended for buildings with a wide variance
of water demand as each PRV can operate at a different pressure
setting to provide better performance at peak flow."


OK, how would that work in the case of "a wide variance of water
demand"? *With 2 different settings, what would be the final output
pressure and how would that compensate for "peak flow"?


I don't think they expect manual switching of PRV's/


I suspect the 2nd PRV is set at a lower pressure - if demand is so high that
the pressure in the final pipework (after the PRVs) drops below the setting
of the 2nd PRV - then the 2nd PRV will also pass water in addition to the
1st PRV.

When I fitted a 22mm PRV to drop my supply (7.5 bar) to a more reasonable 4
bar, I did some measurements with a short stub of 22mm copper pipe directly
on the PRV output.

The PRV is fed by 2m of 22mm (ish) bore MDPE joined to 1/2" alkathene which
is about 11m length back to the main pipe in the road.

No matter where I set the PRV pressure from about 2 bar to 6 bar, the max
flow remained at about 55 litres/minute (which is considered good in
England[1])

[1] compared to an 80 year old scaled up bit of squashed lead pipe.

Obviously, the pressure setting will affect the flow through subsequant
restricted pipework - but the PRV itself did not seem to impede flow
significantly.

--
Tim Watts * * * * * * * * Personal Blog:http://www.dionic..net/tim/

"History will be kind to me for I intend to write it."- Hide quoted text -

- Show quoted text -


But it still leaves the question as to why you'd want
the valves to operate at different pressures? If all
they are doing is providing more capacity, then why
not set them both to the same pressure? And why
not just install the right single valve that can handle
the flow?

I buy the maintenance issue, but don't see what
they are talking about here. Also note that citation
is not from a manufacturer of valves, it's from some
internet plumbing website.
  #4   Report Post  
Senior Member
 
Posts: 2,498
Default

Derby Dad:

PRV's are often a major bottle neck because not only does the water have to travel a tortuous path through the PRV, and the PRV will typically have a brass or stainless filtration screen (that can gradually clog), but the water has to lift a spring loaded diaphragm in order to get through the PRV, and that's the key here. So, there's a lot of flow resistance through a PRV.

Now, imagine you own a hotel where between 7:30 and 8:30 in the morning, all of the conventioneers staying in the 400 rooms of your hotel are all wanting to take showers and baths and flush toilets at much the same time before they head downstairs for breakfast. In that case, for 23 hours out of a 24 hour day, a single PRV is sufficient to supply the demand. But, it's during that one stinking hour every morning that you need more flow, and a single PRV won't do. So, one way to solve that problem would be to install a second PRV which would allow more flow because of the extra path. Same would apply to a car wash where you can have anywhere from 0 to 50 people (say) that are each gonna want full water pressure in their wand all at the same time. 25 days out of the month a single PRV is sufficient. But, the day after a rain, then everyone and their dog wants to wash their car.

That statement in the web site you linked to saying:

"Parallel PRV's are also recommended for buildings with a wide variance of water demand as each PRV can operate at a different pressure setting to provide better performance at peak flow."

doesn't make any sense to me.

A PRV works by allowing water pressure and the force of a spring to act on a diaphragm. For the PRV to close, the water pressure acting on the upstream side of the diaphragm has to equal the combined water pressure plus the force of the spring acting on the other side of the diaphragm. You adjust the downstream pressure at which the PRV closes by changing the spring pressure being applied. The lower the applied spring pressure, the higher the downstream pressure at which the PRV closes, or, the lower the applied spring pressure, the higher the downstream pressure being maintained will be.

To get greater flow through the PRV, you need the diaphragm to open widest, and that means having the least spring pressure being applied, which means that the PRV will be maintaining the highest downstream pressure.

But, that also means that the pressure in your building's water supply piping is going to be maintained at that higher pressure by the second PRV, and the pressure setting of the first PRV is irrelevant.

I can't help but suspect that whomever wrote that explanation was groping for an explanation himself and really didn't expect that anyone out there would bother to think through the one he came up with. But, I have to admit that I don't know enough about PRV's to argue with him or prove him wrong. It just don't make no sense to my way of thinking.

If it wuz me, I would assume both PRV's would be set to the same pressure, and that the second PRV simply provides additional flow capacity by providing an additional path through which water can flow, and leave it at that.

Last edited by nestork : November 28th 12 at 10:08 PM
  #5   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Please explain "Parallel pressure reducing valves"

On 11/28/2012 1:39 PM, DerbyDad03 wrote:
I found this at http://www.plumbinghelp.ca/pressure_reducing_valve.php

There's an image showing parallel pressure reducing valves along with
this text:

"Installing pressure reducing valves in parallel offers the ability to
service a valve while continuing to provide water to the occupants.
Parallel PRV's are also recommended for buildings with a wide variance
of water demand as each PRV can operate at a different pressure
setting to provide better performance at peak flow."


OK, how would that work in the case of "a wide variance of water
demand"? With 2 different settings, what would be the final output
pressure and how would that compensate for "peak flow"?

I don't think they expect manual switching of PRV's/



As shown, it wouldn't do a thing useful...there's the same flow
restriction at downstream anyway.

--


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,405
Default Please explain "Parallel pressure reducing valves"

On Wed, 28 Nov 2012 11:39:45 -0800 (PST), DerbyDad03
wrote:

I found this at http://www.plumbinghelp.ca/pressure_reducing_valve.php

There's an image showing parallel pressure reducing valves along with
this text:

"Installing pressure reducing valves in parallel offers the ability to
service a valve while continuing to provide water to the occupants.
Parallel PRV's are also recommended for buildings with a wide variance
of water demand as each PRV can operate at a different pressure
setting to provide better performance at peak flow."


OK, how would that work in the case of "a wide variance of water
demand"? With 2 different settings, what would be the final output
pressure and how would that compensate for "peak flow"?


These valves have design limits on pressure depending on flow rates.
Under "normal" (design limit) conditions the "controlling" valve
provides its set pressure. If flow is too high for the controlling
valve, pressure drops. The second valve is set al at a lower
pressure. It then opens to provide addition flow/pressure.
So the final pressure will be lower.
But let's say both valves can handle 50 gpm at 40 psi output
pressure..
Demand goes to 75 gpm occasionally.
With one valve pressure drops to 20 psi.
With a second valve set to open at 38 psi, 38 psi is maintained.
All numbers pulled out of the air, but that's the concept.



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Please explain "Parallel pressure reducing valves"

On Nov 28, 5:27*pm, Vic Smith wrote:
On Wed, 28 Nov 2012 11:39:45 -0800 (PST), DerbyDad03





wrote:
I found this athttp://www.plumbinghelp.ca/pressure_reducing_valve.php


There's an image showing parallel pressure reducing valves along with
this text:


"Installing pressure reducing valves in parallel offers the ability to
service a valve while continuing to provide water to the occupants.
Parallel PRV's are also recommended for buildings with a wide variance
of water demand as each PRV can operate at a different pressure
setting to provide better performance at peak flow."


OK, how would that work in the case of "a wide variance of water
demand"? *With 2 different settings, what would be the final output
pressure and how would that compensate for "peak flow"?


These valves have design limits on pressure depending on flow rates.
Under "normal" (design limit) conditions the "controlling" valve
provides its set pressure. *If flow is too high for the controlling
valve, pressure drops. *The second valve is set al at a lower
pressure. *It then opens to provide addition flow/pressure.
So the final pressure will be lower.
But let's say both valves can handle 50 gpm at 40 psi output
pressure..
Demand goes to 75 gpm occasionally.
With one valve pressure drops to 20 psi.
With a second valve set to open at 38 psi, *38 psi is maintained.
All numbers pulled out of the air, but that's the concept.- Hide quoted text -

- Show quoted text -


Why wouldn't you just set both valves to the same
pressure? That's the goal, isn't it? To maintain pressure
at say 40 psi. Then just set them both to 40.
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,405
Default Please explain "Parallel pressure reducing valves"

On Wed, 28 Nov 2012 15:31:56 -0800 (PST), "
wrote:



Why wouldn't you just set both valves to the same
pressure? That's the goal, isn't it? To maintain pressure
at say 40 psi. Then just set them both to 40.


Something about how they operate when too close in output setting -
maybe valve chatter. I forgot most of what I knew as a boilerman, and
never was a reducing valve expert anyway.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,415
Default Please explain "Parallel pressure reducing valves"

" wrote:
On Nov 28, 5:27 pm, Vic Smith wrote:
On Wed, 28 Nov 2012 11:39:45 -0800 (PST), DerbyDad03





wrote:
I found this athttp://www.plumbinghelp.ca/pressure_reducing_valve.php


There's an image showing parallel pressure reducing valves along with
this text:


"Installing pressure reducing valves in parallel offers the ability to
service a valve while continuing to provide water to the occupants.
Parallel PRV's are also recommended for buildings with a wide variance
of water demand as each PRV can operate at a different pressure
setting to provide better performance at peak flow."


OK, how would that work in the case of "a wide variance of water
demand"? With 2 different settings, what would be the final output
pressure and how would that compensate for "peak flow"?


These valves have design limits on pressure depending on flow rates.
Under "normal" (design limit) conditions the "controlling" valve
provides its set pressure. If flow is too high for the controlling
valve, pressure drops. The second valve is set al at a lower
pressure. It then opens to provide addition flow/pressure.
So the final pressure will be lower.
But let's say both valves can handle 50 gpm at 40 psi output
pressure..
Demand goes to 75 gpm occasionally.
With one valve pressure drops to 20 psi.
With a second valve set to open at 38 psi, 38 psi is maintained.
All numbers pulled out of the air, but that's the concept.- Hide quoted text -

- Show quoted text -


Why wouldn't you just set both valves to the same
pressure? That's the goal, isn't it? To maintain pressure
at say 40 psi. Then just set them both to 40.


That might work, or it might cause an oscillation between the units if they
can't decide who is the master? I thought about using two valves, two
lines, but I would need two hot water tanks.

Greg


  #11   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default Please explain "Parallel pressure reducing valves"

On 11/28/2012 1:39 PM, DerbyDad03 wrote:
....

OK, how would that work in the case of "a wide variance of water
demand"? With 2 different settings, what would be the final output
pressure and how would that compensate for "peak flow"?


OK, here's a link that actually does make some sense--NB that the
individual valves/lines are smaller capacity than the main line unlike
that shown in the previous. This _can_ make some difference and be of
use; imo the other has no useful purpose/can't work to any advantage
other than the redundancy.

http://www.watts.com/pages/learnabout/reducingvalves.asp#parallel

--

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"Reversible decking boards" Please explain! AL_z UK diy 23 February 25th 17 11:29 AM
LED curves (was "LEDs in parallel" on seb) - LEDEIR.pdf John Fields Electronic Schematics 5 January 31st 12 05:04 AM
I am looking for a local source for "Rockwool" / "Mineral Wool" /"Safe & Sound" / "AFB" jtpr Home Repair 3 June 10th 10 06:27 AM
water pressure reducing valves and a water leak Stephen[_6_] UK diy 7 April 20th 09 04:17 PM
Of pressure reducing valves, combis & showers... Scott M UK diy 4 January 28th 06 08:16 PM


All times are GMT +1. The time now is 03:51 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"