Putty used to seal electrical service meter boxes, etc.
 
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?

jamesgangnc[_3_] October 13th 11 02:12 PM

Putty used to seal electrical service meter boxes, etc.
 
On Oct 13, 8:08*am, wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


I've not seen putty used in that situation.

Bill[_9_] October 13th 11 02:28 PM

Putty used to seal electrical service meter boxes, etc.
 
wrote in message
What is the technical term for the putty that electricians use to
seal
around service cables where they enter meter boxes, or pass through
walls?


For service cables, I use a weather head, bend the wires down prior to
entering the weather head (drip line), and don't use anything to seal
the holes.

For wires entering through the wall of a building, I route the wire
down, then back up (drip line), then use regular caulk.


Mr.E October 13th 11 02:35 PM

Putty used to seal electrical service meter boxes, etc.
 
On Thu, 13 Oct 2011 06:12:26 -0700 (PDT), jamesgangnc
wrote:

On Oct 13, 8:08*am, wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


I've not seen putty used in that situation.


Dust Seal or Duct Seal Compound is the trade designation of the
material.
--
Mr.E

Stormin Mormon October 13th 11 02:40 PM

Putty used to seal electrical service meter boxes, etc.
 
I've seen "Diversigum" used. At least, when I did HVAC
installs, that's what we used. The boss used to call it
"thumb gum".

--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


wrote in message
...
What is the technical term for the putty that electricians
use to seal
around service cables where they enter meter boxes, or pass
through
walls?



HeyBub[_3_] October 13th 11 03:20 PM

Putty used to seal electrical service meter boxes, etc.
 
wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


Great Stuff seems to work.



Stormin Mormon October 13th 11 03:27 PM

Putty used to seal electrical service meter boxes, etc.
 
Sunlight UV makes it brittle after a few years. But, it does
provide some sealing.

Now, for the OP question. What is that putty?

--
Christopher A. Young
Learn more about Jesus
www.lds.org
..


"HeyBub" wrote in message
m...
wrote:
What is the technical term for the putty that electricians
use to seal
around service cables where they enter meter boxes, or
pass through
walls?


Great Stuff seems to work.




John Grabowski October 13th 11 05:16 PM

Putty used to seal electrical service meter boxes, etc.
 

What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?



*Duct Seal

TimR[_2_] October 13th 11 05:27 PM

Putty used to seal electrical service meter boxes, etc.
 
On Oct 13, 12:16*pm, "John Grabowski" wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


*Duct Seal


It's Duct Seal, or as manufacturers call it, thumbgrade.

We use it only to seal conduits going into hazardous areas. It will
prevent a dust explosion from propagating through conduit, at least in
theory.

They sell it in all the big box home improvement stores, BUT the
actual purchasers are a very specialized group.

The only people who buy much duct seal are airgun shooters. Duct Seal
makes an ideal pellet trap, just fill a flat box with it. It absorbs
a pellet silently and traps all lead dust. Every once in a while (few
thousand rounds) you dig out the pellets and smooth out the duct seal
again.

Long ago I talked with an old timer at Johns-Mansville or whatever
they were at the time who used to make the stuff. It's basically
calcium oxide and grease, made in a big pug mixer in batches of about
1000 pounds at a time. Of course he wouldn't tell me the real
recipe.

George October 13th 11 05:45 PM

Putty used to seal electrical service meter boxes, etc.
 
On 10/13/2011 10:20 AM, HeyBub wrote:
wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


Great Stuff seems to work.



And who said you never give helpful answers?

Likely you have never even tried it because great stuff isn't UV
resistant so it quickly turns yellow and gets brittle. Other than that
it looks great on those infomercials.

On the other hand the stuff (duct seal) electricians use is easily
applied with your fingers without any mess and stays pliable for a long
time.

EXT October 13th 11 09:19 PM

Putty used to seal electrical service meter boxes, etc.
 

"Stormin Mormon" wrote in message
...
I've seen "Diversigum" used. At least, when I did HVAC
installs, that's what we used. The boss used to call it
"thumb gum".


When I used to work in my fathers auto-body repair shop in the 1950s, a
lifetime ago, we used a similar sealant to plug holes where wires and pipes
went through the body. In those days it was called "dum-dum", it sounds
similar.


HeyBub[_3_] October 13th 11 09:42 PM

Putty used to seal electrical service meter boxes, etc.
 
George wrote:
On 10/13/2011 10:20 AM, HeyBub wrote:
wrote:
What is the technical term for the putty that electricians use to
seal around service cables where they enter meter boxes, or pass
through walls?


Great Stuff seems to work.



And who said you never give helpful answers?

Likely you have never even tried it because great stuff isn't UV
resistant so it quickly turns yellow and gets brittle. Other than that
it looks great on those infomercials.


I have tried it. Six years ago to fill the voids around a new circuit
breaker box. It's still there.

In the event it does turn brittle decades from now, who cares? Bricks are
brittle. As long as bricks, or Great Stuff, are not under shear stress,
brittleness is irrelevant.



aemeijers October 13th 11 10:40 PM

Putty used to seal electrical service meter boxes, etc.
 
On 10/13/2011 10:27 AM, Stormin Mormon wrote:
Sunlight UV makes it brittle after a few years. But, it does
provide some sealing.

Now, for the OP question. What is that putty?


At work, the red stuff they use going through walls is described as fire
stop. Never stuck my fingers in it, since it is up so high, but I always
assumed it dried hard, like drywall mud.

Or am I talking about something different?

--
aem sends...

[email protected] October 14th 11 03:11 AM

Putty used to seal electrical service meter boxes, etc.
 
On Thu, 13 Oct 2011 05:08:36 -0700 (PDT),
wrote:

What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?

Ducseal is one brand - often called DUMDUM. It if fireproof. I think
the original stuff had asbestos in it - not sur what is in it now.

Red October 14th 11 03:32 AM

Putty used to seal electrical service meter boxes, etc.
 
On Oct 13, 9:11*pm, wrote:
On Thu, 13 Oct 2011 05:08:36 -0700 (PDT),
wrote:

What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


* Ducseal is one brand - often called DUMDUM. It if fireproof. I think
the original stuff had asbestos in it - not sur what is in it now.


Very fireproof. We used it around cadweld mold holes to contain the
liquid copper when connecting copper cables to ground rods.

George October 14th 11 01:38 PM

Putty used to seal electrical service meter boxes, etc.
 
On 10/13/2011 4:42 PM, HeyBub wrote:
George wrote:
On 10/13/2011 10:20 AM, HeyBub wrote:
wrote:
What is the technical term for the putty that electricians use to
seal around service cables where they enter meter boxes, or pass
through walls?

Great Stuff seems to work.



And who said you never give helpful answers?

Likely you have never even tried it because great stuff isn't UV
resistant so it quickly turns yellow and gets brittle. Other than that
it looks great on those infomercials.


I have tried it. Six years ago to fill the voids around a new circuit
breaker box. It's still there.

In the event it does turn brittle decades from now, who cares? Bricks are
brittle. As long as bricks, or Great Stuff, are not under shear stress,
brittleness is irrelevant.


Absolutely relevant for the application. There is a really valid reason
why certain methods become standard methods.



HeyBub[_3_] October 14th 11 02:17 PM

Putty used to seal electrical service meter boxes, etc.
 
George wrote:
On 10/13/2011 4:42 PM, HeyBub wrote:
George wrote:
On 10/13/2011 10:20 AM, HeyBub wrote:
wrote:
What is the technical term for the putty that electricians use to
seal around service cables where they enter meter boxes, or pass
through walls?

Great Stuff seems to work.



And who said you never give helpful answers?

Likely you have never even tried it because great stuff isn't UV
resistant so it quickly turns yellow and gets brittle. Other than
that it looks great on those infomercials.


I have tried it. Six years ago to fill the voids around a new circuit
breaker box. It's still there.

In the event it does turn brittle decades from now, who cares?
Bricks are brittle. As long as bricks, or Great Stuff, are not under
shear stress, brittleness is irrelevant.


Absolutely relevant for the application. There is a really valid
reason why certain methods become standard methods.


Oh, I mostly agree with conventional wisdom. So what is the "standard"
method in the instant case?



deadgoose[_2_] October 14th 11 02:48 PM

Putty used to seal electrical service meter boxes, etc.
 
There is also some stuff called "Coax Seal," available as strips in
small quantities used by ham radio operators to seal coaxial fittings
out-of-doors. It is really sticky and never seems to harden. You need
something like lacquer thinner to get it off! Any good ham radio
supply house, or by mail order. Good for small jobs.

/paul W3FIS

George October 14th 11 05:27 PM

Putty used to seal electrical service meter boxes, etc.
 
On 10/14/2011 9:17 AM, HeyBub wrote:
George wrote:
On 10/13/2011 4:42 PM, HeyBub wrote:
George wrote:
On 10/13/2011 10:20 AM, HeyBub wrote:
wrote:
What is the technical term for the putty that electricians use to
seal around service cables where they enter meter boxes, or pass
through walls?

Great Stuff seems to work.



And who said you never give helpful answers?

Likely you have never even tried it because great stuff isn't UV
resistant so it quickly turns yellow and gets brittle. Other than
that it looks great on those infomercials.


I have tried it. Six years ago to fill the voids around a new circuit
breaker box. It's still there.

In the event it does turn brittle decades from now, who cares?
Bricks are brittle. As long as bricks, or Great Stuff, are not under
shear stress, brittleness is irrelevant.


Absolutely relevant for the application. There is a really valid
reason why certain methods become standard methods.


Oh, I mostly agree with conventional wisdom. So what is the "standard"
method in the instant case?


You mean you don't bother reading replies to questions that have useful
answers? I believe there are at least three posts in this thread that
list the time tested and proven product that is ubiquitously used by
electricians.

Just wanted to follow up on one of your other great suggestions. We are
having a blast using that idea of yours to build shelf hangers out of
light gauge wire. Unsuspecting people set a heavy object on the shelf
and next thing they are on the floor under a pile of stuff. It is
hilarious...

Bud-- October 14th 11 06:04 PM

Putty used to seal electrical service meter boxes, etc.
 
On 10/13/2011 11:27 AM, TimR wrote:
On Oct 13, 12:16 pm, "John wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


*Duct Seal


It's Duct Seal, or as manufacturers call it, thumbgrade.


I have never heard it called anything but "duct seal", but lots of
products have different names in different areas. The last box I bought
was labeled "Duct Seal" (Panduit).

Where a conduit or sleeve goes between areas of different temperature
where "condensation is known to be a problem" an _"approved material"_
is required to seal around the wires or cables (300.7-A). The seal
prevents warm moist air from circulating to the cold area. Around here,
inside the service conduit into a building is always sealed. There are
other places where it is appropriate.

"Fire stop" is to maintain the fire rating of a wall or floor, but
should work.


We use it only to seal conduits going into hazardous areas. It will
prevent a dust explosion from propagating through conduit, at least in
theory.


Can't imagine protection to a hazardous area wouldn't require a seal-off
fitting with appropriate seal material. Can't imagine duct seal being
used as a hazardous seal.

--
bud--

HeyBub[_3_] October 14th 11 08:04 PM

Putty used to seal electrical service meter boxes, etc.
 
George wrote:
On 10/14/2011 9:17 AM, HeyBub wrote:
George wrote:
On 10/13/2011 4:42 PM, HeyBub wrote:
George wrote:
On 10/13/2011 10:20 AM, HeyBub wrote:
wrote:
What is the technical term for the putty that electricians use
to seal around service cables where they enter meter boxes, or
pass through walls?

Great Stuff seems to work.



And who said you never give helpful answers?

Likely you have never even tried it because great stuff isn't UV
resistant so it quickly turns yellow and gets brittle. Other than
that it looks great on those infomercials.


I have tried it. Six years ago to fill the voids around a new
circuit breaker box. It's still there.

In the event it does turn brittle decades from now, who cares?
Bricks are brittle. As long as bricks, or Great Stuff, are not
under shear stress, brittleness is irrelevant.


Absolutely relevant for the application. There is a really valid
reason why certain methods become standard methods.


Oh, I mostly agree with conventional wisdom. So what is the
"standard" method in the instant case?


You mean you don't bother reading replies to questions that have
useful answers? I believe there are at least three posts in this
thread that list the time tested and proven product that is
ubiquitously used by electricians.


Oh I read the replies. It's just that I figured they were, to you, as
cockamamie as mine. That's why I asked for your recommendation. I take it
from your lack of reply that you don't actually have an idea other than
disparaging those of others.


Just wanted to follow up on one of your other great suggestions. We
are having a blast using that idea of yours to build shelf hangers
out of light gauge wire. Unsuspecting people set a heavy object on
the shelf and next thing they are on the floor under a pile of stuff.
It is hilarious...


Only if you take pleasure in the misfortunes of others, which, when I think
on it...



George October 15th 11 01:45 PM

Putty used to seal electrical service meter boxes, etc.
 
On 10/14/2011 3:04 PM, HeyBub wrote:
George wrote:
On 10/14/2011 9:17 AM, HeyBub wrote:
George wrote:
On 10/13/2011 4:42 PM, HeyBub wrote:
George wrote:
On 10/13/2011 10:20 AM, HeyBub wrote:
wrote:
What is the technical term for the putty that electricians use
to seal around service cables where they enter meter boxes, or
pass through walls?

Great Stuff seems to work.



And who said you never give helpful answers?

Likely you have never even tried it because great stuff isn't UV
resistant so it quickly turns yellow and gets brittle. Other than
that it looks great on those infomercials.


I have tried it. Six years ago to fill the voids around a new
circuit breaker box. It's still there.

In the event it does turn brittle decades from now, who cares?
Bricks are brittle. As long as bricks, or Great Stuff, are not
under shear stress, brittleness is irrelevant.


Absolutely relevant for the application. There is a really valid
reason why certain methods become standard methods.

Oh, I mostly agree with conventional wisdom. So what is the
"standard" method in the instant case?


You mean you don't bother reading replies to questions that have
useful answers? I believe there are at least three posts in this
thread that list the time tested and proven product that is
ubiquitously used by electricians.


Oh I read the replies. It's just that I figured they were, to you, as
cockamamie as mine. That's why I asked for your recommendation.
I take it
from your lack of reply that you don't actually have an idea other than
disparaging those of others.



You mean this reply I made in this thread:

"On the other hand the stuff (duct seal) electricians use is easily
applied with your fingers without any mess and stays pliable for a long
time."

Or where I noted in my reply to you that at least 3 others noted the
same product:

"I believe there are at least three posts in this
thread that list the time tested and proven product that is
ubiquitously used by electricians."






Just wanted to follow up on one of your other great suggestions. We
are having a blast using that idea of yours to build shelf hangers
out of light gauge wire. Unsuspecting people set a heavy object on
the shelf and next thing they are on the floor under a pile of stuff.
It is hilarious...


Only if you take pleasure in the misfortunes of others, which, when I think
on it...




[email protected] April 6th 16 10:50 PM

Putty used to seal electrical service meter boxes, etc.
 
Whatever happened to the old term "monkey s__t" ?

Stormin Mormon[_10_] April 6th 16 11:16 PM

Putty used to seal electrical service meter boxes, etc.
 
On 4/6/2016 5:50 PM, wrote:
Whatever happened to the old term "monkey s__t" ?


Got replaced by thumb gum?

--
..
Christopher A. Young
learn more about Jesus
..
www.lds.org
..
..

Uncle Monster[_2_] April 7th 16 12:29 AM

Putty used to seal electrical service meter boxes, etc.
 
On Wednesday, April 6, 2016 at 4:50:48 PM UTC-5, wrote:
Whatever happened to the old term "monkey s__t" ?


Now it's "LGBT Poop" in order to include ALL the monkeys. I always called it by what was on the label,"Duct Seal". ^_^

[8~{} Uncle Seal Monster

[email protected] April 7th 16 12:49 AM

Putty used to seal electrical service meter boxes, etc.
 
On Wed, 6 Apr 2016 14:50:41 -0700 (PDT),
wrote:

Whatever happened to the old term "monkey s__t" ?


The same thing that happened to "ni**er rig" and "pollack threads", we
evolved.

Stormin Mormon[_10_] April 7th 16 01:53 AM

Putty used to seal electrical service meter boxes, etc.
 
On 4/6/2016 7:49 PM, wrote:
On Wed, 6 Apr 2016 14:50:41 -0700 (PDT),

wrote:

Whatever happened to the old term "monkey s__t" ?


The same thing that happened to "ni**er rig" and "pollack threads", we
evolved.


Anyone old enough to remember Jerry
built?

In any case, that's good enough for
government work.

--
..
Christopher A. Young
learn more about Jesus
..
www.lds.org
..
..

Uncle Monster[_2_] April 7th 16 02:01 AM

Putty used to seal electrical service meter boxes, etc.
 
On Wednesday, April 6, 2016 at 7:53:35 PM UTC-5, Stormin Mormon wrote:
On 4/6/2016 7:49 PM, wrote:
On Wed, 6 Apr 2016 14:50:41 -0700 (PDT),

wrote:

Whatever happened to the old term "monkey s__t" ?


The same thing that happened to "ni**er rig" and "pollack threads", we
evolved.

Anyone old enough to remember Jerry
built?

In any case, that's good enough for
government work.
--
.

I always called it,"Jerry Rigged". ^_^

[8~{} Uncle Rigged Monster

[email protected] April 7th 16 03:57 AM

Putty used to seal electrical service meter boxes, etc.
 
On Wed, 6 Apr 2016 18:01:16 -0700 (PDT), Uncle Monster
wrote:

On Wednesday, April 6, 2016 at 7:53:35 PM UTC-5, Stormin Mormon wrote:
On 4/6/2016 7:49 PM, wrote:
On Wed, 6 Apr 2016 14:50:41 -0700 (PDT),

wrote:

Whatever happened to the old term "monkey s__t" ?

The same thing that happened to "ni**er rig" and "pollack threads", we
evolved.

Anyone old enough to remember Jerry
built?

In any case, that's good enough for
government work.
--
.

I always called it,"Jerry Rigged". ^_^

[8~{} Uncle Rigged Monster

Around here there's a lot of "Jerry built" stuff - half the
population is German ancestry.

"Jerry rigged" is used for poorly done - also referred to, for some
reason, as "jury rigged"

rbowman April 7th 16 04:12 AM

Putty used to seal electrical service meter boxes, etc.
 
On 04/06/2016 07:01 PM, Uncle Monster wrote:
I always called it,"Jerry Rigged". ^_^


Jury rigged is more accurate.

EXT[_2_] April 9th 16 10:39 PM

Putty used to seal electrical service meter boxes, etc.
 


"Uncle Monster" wrote in message
...
On Wednesday, April 6, 2016 at 4:50:48 PM UTC-5,
wrote:
Whatever happened to the old term "monkey s__t" ?


Now it's "LGBT Poop" in order to include ALL the monkeys. I always called
it by what was on the label,"Duct Seal". ^_^

In the 1950s auto repair industry it was known as "dum-dum".


[email protected] April 10th 16 12:08 AM

Putty used to seal electrical service meter boxes, etc.
 
On Sat, 9 Apr 2016 17:39:24 -0400, "EXT" wrote:



"Uncle Monster" wrote in message
...
On Wednesday, April 6, 2016 at 4:50:48 PM UTC-5,
wrote:
Whatever happened to the old term "monkey s__t" ?


Now it's "LGBT Poop" in order to include ALL the monkeys. I always called
it by what was on the label,"Duct Seal". ^_^

In the 1950s auto repair industry it was known as "dum-dum".

Still is.

John G[_8_] April 10th 16 01:00 PM

Putty used to seal electrical service meter boxes, etc.
 
On Thursday, October 13, 2011 at 8:08:36 AM UTC-4, wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


Duct seal


John Grabowski
www.MrElectrician.TV

[email protected] September 14th 16 09:19 PM

Putty used to seal electrical service meter boxes, etc.
 
On Thursday, October 13, 2011 at 8:08:36 AM UTC-4, wrote:
Helpful thread. Thanks all! Never knew the official name of this very useful stuff!

Taxed and Spent September 14th 16 09:29 PM

Putty used to seal electrical service meter boxes, etc.
 
On 9/14/2016 1:19 PM, wrote:
On Thursday, October 13, 2011 at 8:08:36 AM UTC-4, wrote:
Helpful thread. Thanks all! Never knew the official name of this very useful stuff!



hmm. I still don't.

[email protected] September 14th 16 10:55 PM

Putty used to seal electrical service meter boxes, etc.
 
On Wed, 14 Sep 2016 13:29:46 -0700, Taxed and Spent
wrote:

On 9/14/2016 1:19 PM, wrote:
On Thursday, October 13, 2011 at 8:08:36 AM UTC-4, wrote:
Helpful thread. Thanks all! Never knew the official name of this very useful stuff!



hmm. I still don't.

DuctSeal

rbowman September 15th 16 04:06 AM

Putty used to seal electrical service meter boxes, etc.
 
On 09/14/2016 02:29 PM, Taxed and Spent wrote:
On 9/14/2016 1:19 PM, wrote:
On Thursday, October 13, 2011 at 8:08:36 AM UTC-4,
wrote:
Helpful thread. Thanks all! Never knew the official name of this very
useful stuff!



hmm. I still don't.


Monkey ****.

Uncle Monster[_2_] September 15th 16 08:35 AM

Putty used to seal electrical service meter boxes, etc.
 
On Wednesday, September 14, 2016 at 10:06:58 PM UTC-5, rbowman wrote:
On 09/14/2016 02:29 PM, Taxed and Spent wrote:
On 9/14/2016 1:19 PM, wrote:
On Thursday, October 13, 2011 at 8:08:36 AM UTC-4,
wrote:
Helpful thread. Thanks all! Never knew the official name of this very
useful stuff!

hmm. I still don't.


Monkey ****.


A lot of people call it elephant dung. I just call it by the name on the wrapper,"Duct Seal". Wouldn't it be fun to buy a lot of it, put a new wrapper on it that actually read,"Monkey ****"? I could be a popular gag gift for contractors and mechanics. \(—¦'Œ£'—¦)/

[8~{} Uncle Monkey Monster

[email protected] October 25th 17 07:09 PM

Putty used to seal electrical service meter boxes, etc.
 
On Thursday, October 13, 2011 at 8:08:36 AM UTC-4, wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


I was always told 30 + years ago it was called Monkey ****.

[email protected] October 25th 17 08:27 PM

Putty used to seal electrical service meter boxes, etc.
 
On Wed, 25 Oct 2017 11:09:51 -0700 (PDT), wrote:

On Thursday, October 13, 2011 at 8:08:36 AM UTC-4, wrote:
What is the technical term for the putty that electricians use to seal
around service cables where they enter meter boxes, or pass through
walls?


I was always told 30 + years ago it was called Monkey ****.


The counter guy probably knows that term but the real name is duct
seal.