still over at my friend's house... cut on heat last night for the first time this year. He turned the heat on and went to bed; I realized after a while that the inducer blower was running but the air handler was not. Investigated; found that the flame was not lit, inducer was sitting there grinding away. Popped cover, found a cracked hose between the inducer fan housing and a pressure transducer. Cut it shorter, reconnected, OK furnace works. But I did notice that it seems to only run for about 5 minutes at a time, then will kill the flame, AH fan will run for a while then shut down. Almost immediately the inducer fan will start again, flame will relight, lather rinse repeat. My immediate thought was that it was restricted airflow due to a gunked up A-coil for the AC. This evening I got over there and ripped it apart, sure enough the A-coil looks gunky, however I could not clean it properly because I am still fighting one rusted screw for access to it. The access panel to the underside of the A-coil is in two parts; I removed one and replaced the access panel on the evaporator so that some air could bypass it if that were the problem. Unfortunately, it seems to be exhibiting the same behavior. I didn't time how long it took it to cycle last night (actually, early this AM - I got the thing working in the first place about 1 AM) so I can't say if the time between cycles is longer now with better airflow. Now here's the weird thing. There is absolutely no nameplate, data plate, whatever with any kind of part number that I can find on this furnace to give me any sort of clue as to where to find a manual online for it so I can delve deeper. Can anyone give me any hints as to where to look? So, I guess the question is, without knowing exactly what model furnace this is, can anyone tell me if this is this normal behavior for this type furnace, e.g. am I worried over nothing? I just don't want him to have to pop for a new heat exchanger due to constant overheating. I sadly do not have an IR thermometer - I own one, but I'll be damned if I can tell you where it is right now. Finally, do any of those A-coil cleaner sprays actually work well? The A-coil is quite filthy, probably due to some ductwork pulling loose and allowing air to bypass the filter. I'm a little concerned as this A-coil is well past its "best before" date and when looking on the Big Box's web site to see if my local store carried anything for this purpose, the reviews seemed to indicate that a few people had problems with their fins disintegrating after application of said cleaning spray. Is this a real concern? (when I said it was past its "best before" date, I meant it.) thanks much, nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#2
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
On Oct 4, 6:59*pm, Nate Nagel wrote:
Hi all, still over at my friend's house... *cut on heat last night for the first time this year. *He turned the heat on and went to bed; I realized after a while that the inducer blower was running but the air handler was not. * Investigated; found that the flame was not lit, inducer was sitting there grinding away. *Popped cover, found a cracked hose between the inducer fan housing and a pressure transducer. *Cut it shorter, reconnected, OK furnace works. *But I did notice that it seems to only run for about 5 minutes at a time, then will kill the flame, AH fan will run for a while then shut down. *Almost immediately the inducer fan will start again, flame will relight, lather rinse repeat. *My immediate thought was that it was restricted airflow due to a gunked up A-coil for the AC. This evening I got over there and ripped it apart, sure enough the A-coil looks gunky, however I could not clean it properly because I am still fighting one rusted screw for access to it. *The access panel to the underside of the A-coil is in two parts; I removed one and replaced the access panel on the evaporator so that some air could bypass it if that were the problem. *Unfortunately, it seems to be exhibiting the same behavior. *I didn't time how long it took it to cycle last night (actually, early this AM - I got the thing working in the first place about 1 AM) so I can't say if the time between cycles is longer now with better airflow. Now here's the weird thing. *There is absolutely no nameplate, data plate, whatever with any kind of part number that I can find on this furnace to give me any sort of clue as to where to find a manual online for it so I can delve deeper. *Can anyone give me any hints as to where to look? So, I guess the question is, without knowing exactly what model furnace this is, can anyone tell me if this is this normal behavior for this type furnace, e.g. am I worried over nothing? *I just don't want him to have to pop for a new heat exchanger due to constant overheating. I sadly do not have an IR thermometer - I own one, but I'll be damned if I can tell you where it is right now. Finally, do any of those A-coil cleaner sprays actually work well? *The A-coil is quite filthy, probably due to some ductwork pulling loose and allowing air to bypass the filter. *I'm a little concerned as this A-coil is well past its "best before" date and when looking on the Big Box's web site to see if my local store carried anything for this purpose, the reviews seemed to indicate that a few people had problems with their fins disintegrating after application of said cleaning spray. * Is this a real concern? *(when I said it was past its "best before" date, I meant it.) thanks much, nate -- replace "roosters" with "cox" to reply.http://members.cox.net/njnagel How is the internal air handler thermostat set, maybe the high limit switch is set toward the low side. What the unit is doing is actually the most efficient way to run the furnace. |
#3
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
Nate Nagel wrote: Hi all, still over at my friend's house... cut on heat last night for the first time this year. He turned the heat on and went to bed; I realized after a while that the inducer blower was running but the air handler was not. Investigated; found that the flame was not lit, inducer was sitting there grinding away. Popped cover, found a cracked hose between the inducer fan housing and a pressure transducer. Cut it shorter, reconnected, OK furnace works. But I did notice that it seems to only run for about 5 minutes at a time, then will kill the flame, AH fan will run for a while then shut down. Almost immediately the inducer fan will start again, flame will relight, lather rinse repeat. My immediate thought was that it was restricted airflow due to a gunked up A-coil for the AC. This evening I got over there and ripped it apart, sure enough the A-coil looks gunky, however I could not clean it properly because I am still fighting one rusted screw for access to it. The access panel to the underside of the A-coil is in two parts; I removed one and replaced the access panel on the evaporator so that some air could bypass it if that were the problem. Unfortunately, it seems to be exhibiting the same behavior. I didn't time how long it took it to cycle last night (actually, early this AM - I got the thing working in the first place about 1 AM) so I can't say if the time between cycles is longer now with better airflow. Now here's the weird thing. There is absolutely no nameplate, data plate, whatever with any kind of part number that I can find on this furnace to give me any sort of clue as to where to find a manual online for it so I can delve deeper. Can anyone give me any hints as to where to look? So, I guess the question is, without knowing exactly what model furnace this is, can anyone tell me if this is this normal behavior for this type furnace, e.g. am I worried over nothing? I just don't want him to have to pop for a new heat exchanger due to constant overheating. I sadly do not have an IR thermometer - I own one, but I'll be damned if I can tell you where it is right now. Finally, do any of those A-coil cleaner sprays actually work well? The A-coil is quite filthy, probably due to some ductwork pulling loose and allowing air to bypass the filter. I'm a little concerned as this A-coil is well past its "best before" date and when looking on the Big Box's web site to see if my local store carried anything for this purpose, the reviews seemed to indicate that a few people had problems with their fins disintegrating after application of said cleaning spray. Is this a real concern? (when I said it was past its "best before" date, I meant it.) thanks much, nate Hi, No trouble code? |
#4
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
On 10/04/2011 08:16 PM, Malcom "Mal" Reynolds wrote:
In , Nate wrote: I can't answer your question, but is it possible that it is somehow being starved for combustion air? Recent weatherization? Don't think so; air intake appears to actually be inside house and only exhaust goes outside (I can only find one pipe anywhere,) I have not however checked exhaust for airflow as it has been raining for what feels like about a year straight now... nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#5
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
On 10/04/2011 10:35 PM, Tony Hwang wrote:
Nate Nagel wrote: Hi all, still over at my friend's house... cut on heat last night for the first time this year. He turned the heat on and went to bed; I realized after a while that the inducer blower was running but the air handler was not. Investigated; found that the flame was not lit, inducer was sitting there grinding away. Popped cover, found a cracked hose between the inducer fan housing and a pressure transducer. Cut it shorter, reconnected, OK furnace works. But I did notice that it seems to only run for about 5 minutes at a time, then will kill the flame, AH fan will run for a while then shut down. Almost immediately the inducer fan will start again, flame will relight, lather rinse repeat. My immediate thought was that it was restricted airflow due to a gunked up A-coil for the AC. This evening I got over there and ripped it apart, sure enough the A-coil looks gunky, however I could not clean it properly because I am still fighting one rusted screw for access to it. The access panel to the underside of the A-coil is in two parts; I removed one and replaced the access panel on the evaporator so that some air could bypass it if that were the problem. Unfortunately, it seems to be exhibiting the same behavior. I didn't time how long it took it to cycle last night (actually, early this AM - I got the thing working in the first place about 1 AM) so I can't say if the time between cycles is longer now with better airflow. Now here's the weird thing. There is absolutely no nameplate, data plate, whatever with any kind of part number that I can find on this furnace to give me any sort of clue as to where to find a manual online for it so I can delve deeper. Can anyone give me any hints as to where to look? So, I guess the question is, without knowing exactly what model furnace this is, can anyone tell me if this is this normal behavior for this type furnace, e.g. am I worried over nothing? I just don't want him to have to pop for a new heat exchanger due to constant overheating. I sadly do not have an IR thermometer - I own one, but I'll be damned if I can tell you where it is right now. Finally, do any of those A-coil cleaner sprays actually work well? The A-coil is quite filthy, probably due to some ductwork pulling loose and allowing air to bypass the filter. I'm a little concerned as this A-coil is well past its "best before" date and when looking on the Big Box's web site to see if my local store carried anything for this purpose, the reviews seemed to indicate that a few people had problems with their fins disintegrating after application of said cleaning spray. Is this a real concern? (when I said it was past its "best before" date, I meant it.) thanks much, nate Hi, No trouble code? This thing isn't that new... Just on appearance this looks older than the one that was in my last house which was installed in the late 80's. nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#6
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
And if he had a blinking trouble code, he can't look it up.
Not knowing the brand and model of the furnace. With the reduced air flow, sounds like it repeatedly over heats. I havn't used any of the evaporator cleaners in a spray can, but "rinse well" is the key. Rinse the dirt and chemicals out. -- Christopher A. Young Learn more about Jesus www.lds.org .. "Tony Hwang" wrote in message news Nate Nagel wrote: Hi all, Now here's the weird thing. There is absolutely no nameplate, data plate, whatever with any kind of part number that I can find on this furnace to give me any sort of clue as to where to find a manual online for it so I can delve deeper. Can anyone give me any hints as to where to look? thanks much, nate Hi, No trouble code? |
#7
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
"Nate Nagel" wrote in message ... Hi all, CY: Hi, Nate! still over at my friend's house... cut on heat last night for the first time this year. He turned the heat on and went to bed; I realized after a while that the inducer blower was running but the air handler was not. CY: Sounds odd. Investigated; found that the flame was not lit, inducer was sitting there grinding away. Popped cover, found a cracked hose between the inducer fan housing and a pressure transducer. Cut it shorter, reconnected, OK furnace works. CY: Good diagnostic skill. But I did notice that it seems to only run for about 5 minutes at a time, then will kill the flame, AH fan will run for a while then shut down. Almost immediately the inducer fan will start again, flame will relight, lather rinse repeat. My immediate thought was that it was restricted airflow due to a gunked up A-coil for the AC. CY: I'd want to touch the supply air duct, see if it's super hot. Quick check, to see if it's cycling on thermal over heat. I worked on one furnace, the fan limit switch had gone bad, and wasn't letting the furnace properly heat up. Might be fan limit switch problem. This evening I got over there and ripped it apart, sure enough the A-coil looks gunky, however I could not clean it properly because I am still fighting one rusted screw for access to it. The access panel to the underside of the A-coil is in two parts; I removed one and replaced the access panel on the evaporator so that some air could bypass it if that were the problem. Unfortunately, it seems to be exhibiting the same behavior. I didn't time how long it took it to cycle last night (actually, early this AM - I got the thing working in the first place about 1 AM) so I can't say if the time between cycles is longer now with better airflow. CY: Would be nice to know if that helped. But, like you say, you were working on it a long time. Now here's the weird thing. There is absolutely no nameplate, data plate, whatever with any kind of part number that I can find on this furnace to give me any sort of clue as to where to find a manual online for it so I can delve deeper. Can anyone give me any hints as to where to look? CY: Typically, one of the narrow sides of the furnace lifts up and out. The name plate is often near the gas valve. So, I guess the question is, without knowing exactly what model furnace this is, can anyone tell me if this is this normal behavior for this type furnace, e.g. am I worried over nothing? I just don't want him to have to pop for a new heat exchanger due to constant overheating. CY: Not normal. The furnace should run constantly until the house is at temp (first run of the season) and then as needed to keep the temp. I sadly do not have an IR thermometer - I own one, but I'll be damned if I can tell you where it is right now. CY: I know that kind of trouble. Really irritating. Finally, do any of those A-coil cleaner sprays actually work well? The A-coil is quite filthy, probably due to some ductwork pulling loose and allowing air to bypass the filter. I'm a little concerned as this A-coil is well past its "best before" date and when looking on the Big Box's web site to see if my local store carried anything for this purpose, the reviews seemed to indicate that a few people had problems with their fins disintegrating after application of said cleaning spray. Is this a real concern? (when I said it was past its "best before" date, I meant it.) CY: Never used the cleaner sprays. I'd use a garden sprayer and hot water to rinse, until the rinse water came clean. thanks much, CY: You're welcome. Hope that helps. Sounds like you're a good friend. Ideally, to pull the A coil out totally, and clean it with refrigeration coil cleaner. However, that need a HVAC tech to pump it down, cut the lines, and rebraze, evacuate, and check the freon level after it's reconnected. nate -- replace "roosters" with "cox" to reply. http://members.cox.net/njnagel |
#8
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
On Oct 5, 7:45*am, "Stormin Mormon"
wrote: "Nate Nagel" wrote in message ... Hi all, CY: Hi, Nate! still over at my friend's house... *cut on heat last night for the first time this year. *He turned the heat on and went to bed; I realized after a while that the inducer blower was running but the air handler was not. CY: Sounds odd. * Investigated; found that the flame was not lit, inducer was sitting there grinding away. *Popped cover, found a cracked hose between the inducer fan housing and a pressure transducer. *Cut it shorter, reconnected, OK furnace works. CY: Good diagnostic skill. *But I did notice that it seems to only run for about 5 minutes at a time, then will kill the flame, AH fan will run for a while then shut down. *Almost immediately the inducer fan will start again, flame will relight, lather rinse repeat. *My immediate thought was that it was restricted airflow due to a gunked up A-coil for the AC. CY: I'd want to touch the supply air duct, see if it's super hot. Quick check, to see if it's cycling on thermal over heat. I worked on one furnace, the fan limit switch had gone bad, and wasn't letting the furnace properly heat up. Might be fan limit switch problem. This evening I got over there and ripped it apart, sure enough the A-coil looks gunky, however I could not clean it properly because I am still fighting one rusted screw for access to it. *The access panel to the underside of the A-coil is in two parts; I removed one and replaced the access panel on the evaporator so that some air could bypass it if that were the problem. *Unfortunately, it seems to be exhibiting the same behavior. *I didn't time how long it took it to cycle last night (actually, early this AM - I got the thing working in the first place about 1 AM) so I can't say if the time between cycles is longer now with better airflow. CY: Would be nice to know if that helped. But, like you say, you were working on it a long time. Now here's the weird thing. *There is absolutely no nameplate, data plate, whatever with any kind of part number that I can find on this furnace to give me any sort of clue as to where to find a manual online for it so I can delve deeper. *Can anyone give me any hints as to where to look? CY: Typically, one of the narrow sides of the furnace lifts up and out. The name plate is often near the gas valve. So, I guess the question is, without knowing exactly what model furnace this is, can anyone tell me if this is this normal behavior for this type furnace, e.g. am I worried over nothing? *I just don't want him to have to pop for a new heat exchanger due to constant overheating. CY: Not normal. The furnace should run constantly until the house is at temp (first run of the season) and then as needed to keep the temp. I sadly do not have an IR thermometer - I own one, but I'll be damned if I can tell you where it is right now. CY: I know that kind of trouble. Really irritating. Finally, do any of those A-coil cleaner sprays actually work well? *The A-coil is quite filthy, probably due to some ductwork pulling loose and allowing air to bypass the filter. *I'm a little concerned as this A-coil is well past its "best before" date and when looking on the Big Box's web site to see if my local store carried anything for this purpose, the reviews seemed to indicate that a few people had problems with their fins disintegrating after application of said cleaning spray. * Is this a real concern? *(when I said it was past its "best before" date, I meant it.) CY: Never used the cleaner sprays. I'd use a garden sprayer and hot water to rinse, until the rinse water came clean. thanks much, CY: You're welcome. Hope that helps. Sounds like you're a good friend. Ideally, to pull the A coil out totally, and clean it with refrigeration coil cleaner. However, that need a HVAC tech to pump it down, cut the lines, and rebraze, evacuate, and check the freon level after it's reconnected. nate -- replace "roosters" with "cox" to reply.http://members.cox.net/njnagel First thing I would do is make sure the thermostat is constantly calling for heat. Could do that by temporarily bypassing the thermostat and connecting the wires directly. As Stormin said, I've found on the furnaces I've dealt with the tag with the model and other data has been located inside where the gas valve is, on the upper inside surface of the right side of the unit. |
#9
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
On Oct 5, 9:24*am, "
wrote: On Oct 5, 7:45*am, "Stormin Mormon" wrote: "Nate Nagel" wrote in message ... Hi all, CY: Hi, Nate! still over at my friend's house... *cut on heat last night for the first time this year. *He turned the heat on and went to bed; I realized after a while that the inducer blower was running but the air handler was not. CY: Sounds odd. * Investigated; found that the flame was not lit, inducer was sitting there grinding away. *Popped cover, found a cracked hose between the inducer fan housing and a pressure transducer. *Cut it shorter, reconnected, OK furnace works. CY: Good diagnostic skill. *But I did notice that it seems to only run for about 5 minutes at a time, then will kill the flame, AH fan will run for a while then shut down. *Almost immediately the inducer fan will start again, flame will relight, lather rinse repeat. *My immediate thought was that it was restricted airflow due to a gunked up A-coil for the AC. CY: I'd want to touch the supply air duct, see if it's super hot. Quick check, to see if it's cycling on thermal over heat. I worked on one furnace, the fan limit switch had gone bad, and wasn't letting the furnace properly heat up. Might be fan limit switch problem. This evening I got over there and ripped it apart, sure enough the A-coil looks gunky, however I could not clean it properly because I am still fighting one rusted screw for access to it. *The access panel to the underside of the A-coil is in two parts; I removed one and replaced the access panel on the evaporator so that some air could bypass it if that were the problem. *Unfortunately, it seems to be exhibiting the same behavior. *I didn't time how long it took it to cycle last night (actually, early this AM - I got the thing working in the first place about 1 AM) so I can't say if the time between cycles is longer now with better airflow. CY: Would be nice to know if that helped. But, like you say, you were working on it a long time. Now here's the weird thing. *There is absolutely no nameplate, data plate, whatever with any kind of part number that I can find on this furnace to give me any sort of clue as to where to find a manual online for it so I can delve deeper. *Can anyone give me any hints as to where to look? CY: Typically, one of the narrow sides of the furnace lifts up and out. The name plate is often near the gas valve. So, I guess the question is, without knowing exactly what model furnace this is, can anyone tell me if this is this normal behavior for this type furnace, e.g. am I worried over nothing? *I just don't want him to have to pop for a new heat exchanger due to constant overheating. CY: Not normal. The furnace should run constantly until the house is at temp (first run of the season) and then as needed to keep the temp. I sadly do not have an IR thermometer - I own one, but I'll be damned if I can tell you where it is right now. CY: I know that kind of trouble. Really irritating. Finally, do any of those A-coil cleaner sprays actually work well? *The A-coil is quite filthy, probably due to some ductwork pulling loose and allowing air to bypass the filter. *I'm a little concerned as this A-coil is well past its "best before" date and when looking on the Big Box's web site to see if my local store carried anything for this purpose, the reviews seemed to indicate that a few people had problems with their fins disintegrating after application of said cleaning spray. * Is this a real concern? *(when I said it was past its "best before" date, I meant it.) CY: Never used the cleaner sprays. I'd use a garden sprayer and hot water to rinse, until the rinse water came clean. thanks much, CY: You're welcome. Hope that helps. Sounds like you're a good friend. Ideally, to pull the A coil out totally, and clean it with refrigeration coil cleaner. However, that need a HVAC tech to pump it down, cut the lines, and rebraze, evacuate, and check the freon level after it's reconnected. nate -- replace "roosters" with "cox" to reply.http://members.cox.net/njnagel First thing I would do is make sure the thermostat is constantly calling for heat. *Could do that by temporarily bypassing the thermostat and connecting the wires directly. As Stormin said, I've found on the furnaces I've dealt with the tag with the model and other data has been located inside where the gas valve is, on the upper inside surface of the right side of the unit. good ideas, I will try both tonight. nate |
#10
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
Would be intersting if the furnace is behaving normally, but
the OP is over analyzing. Many times, it's easier for me to pop a digital pic of the serial number plate, and read it off my camera screen. Compared to trying to stick my head in. -- Christopher A. Young Learn more about Jesus www.lds.org .. wrote in message ... First thing I would do is make sure the thermostat is constantly calling for heat. Could do that by temporarily bypassing the thermostat and connecting the wires directly. As Stormin said, I've found on the furnaces I've dealt with the tag with the model and other data has been located inside where the gas valve is, on the upper inside surface of the right side of the unit. |
#11
Posted to alt.home.repair
|
|||
|
|||
Rheem "Imperial 90 Plus" forced air furnace - short cycling?
Be intersting to hear, when you find out what's the real
problem. And, if it's repaired. -- Christopher A. Young Learn more about Jesus www.lds.org .. "N8N" wrote in message ... First thing I would do is make sure the thermostat is constantly calling for heat. Could do that by temporarily bypassing the thermostat and connecting the wires directly. As Stormin said, I've found on the furnaces I've dealt with the tag with the model and other data has been located inside where the gas valve is, on the upper inside surface of the right side of the unit. good ideas, I will try both tonight. nate |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Hand tools: any reason to bother with imperial, and what brands are"quality"? | UK diy | |||
A/C goes into "run away mode" instead of cycling .. suggestions... | Home Repair |