I've got an existing 10'x12' shed sitting on a 4" thick slab of slightly larger
dimensions. I'd like to anchor the shed to the slab without moving or raising
the shed.

The shed sits on several columns of pressure-treated 4x4's that are in mostly
good shape. These 4x4's only lie beneath the shed floor and do not extend beyond
the exterior wall.

See the drawing at the link below:
http://bit.ly/rf7o83

I've been looking for a bracket (e.g. Simpson) that looks like the one I've drawn
in the link above that can be used to anchor the ends of the 4x4's to the slab.
I cannot find one of these in the Simpson catalog. Does anyone know where I can
find something like this or similar?

Thanks.

--
Bill Bushnell
http://mrbill.homeip.net/
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,227
Default Anchoring an existing shed to a concrete slab

On Sep 2, 8:58*pm, Bill Bushnell wrote:
I've got an existing 10'x12' shed sitting on a 4" thick slab of slightly larger
dimensions. *I'd like to anchor the shed to the slab without moving or raising
the shed.

The shed sits on several columns of pressure-treated 4x4's that are in mostly
good shape. *These 4x4's only lie beneath the shed floor and do not extend beyond
the exterior wall.

See the drawing at the link below:http://bit.ly/rf7o83

I've been looking for a bracket (e.g. Simpson) that looks like the one I've drawn
in the link above that can be used to anchor the ends of the 4x4's to the slab. *
I cannot find one of these in the Simpson catalog. *Does anyone know where I can
find something like this or similar?

Thanks.

--
Bill Bushnellhttp://mrbill.homeip.net/


Bill-

I took a look in the SST catalog but didn't find any connectors that
would slip onto a 4x4...... too small.

How about lagging a 4x4 "rim joist" to the ends of the existing 4x's
(both ends of them)
and then anchor these added "rim joists" to the slab with a simple
angle bracket.

Use 1/2 lags x 8" long (6" seemed a bit short)
Check out the Simpson HL Heavy Angles

I think this will be the easiest way to anchor your shed.

cheers
Bob

cheers
Bob
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,106
Default Anchoring an existing shed to a concrete slab

On Sep 2, 11:58*pm, Bill Bushnell wrote:
I've got an existing 10'x12' shed sitting on a 4" thick slab of slightly larger
dimensions. *I'd like to anchor the shed to the slab without moving or raising
the shed.

The shed sits on several columns of pressure-treated 4x4's that are in mostly
good shape. *These 4x4's only lie beneath the shed floor and do not extend beyond
the exterior wall.

See the drawing at the link below:http://bit.ly/rf7o83

I've been looking for a bracket (e.g. Simpson) that looks like the one I've drawn
in the link above that can be used to anchor the ends of the 4x4's to the slab. *
I cannot find one of these in the Simpson catalog. *Does anyone know where I can
find something like this or similar?

Thanks.

--
Bill Bushnellhttp://mrbill.homeip.net/


It's called "angle iron" and you buy it in 10 or 20 foot lengths...

You cut it to size and drill it for anchors into the concrete and lag
screws
into the 4x4 beams under the shed...

~~ Evan
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 203
Default Anchoring an existing shed to a concrete slab

On 9/2/2011 11:58 PM, Bill Bushnell wrote:
I've got an existing 10'x12' shed sitting on a 4" thick slab of slightly larger
dimensions. I'd like to anchor the shed to the slab without moving or raising
the shed.

The shed sits on several columns of pressure-treated 4x4's that are in mostly
good shape. These 4x4's only lie beneath the shed floor and do not extend beyond
the exterior wall.

See the drawing at the link below:
http://bit.ly/rf7o83

I've been looking for a bracket (e.g. Simpson) that looks like the one I've drawn
in the link above that can be used to anchor the ends of the 4x4's to the slab.
I cannot find one of these in the Simpson catalog. Does anyone know where I can
find something like this or similar?

Thanks.



Why the 4x4's? I would think the concrete slab would make a much better
and longer lasting floor than whatever junk flooring came with the shed?

Anchor the shed walls directly to the pad. If its made of wood it should
have a 2x4 sill plate and if metal the sides should be bent inward with
punched holes just for that purpose.

Drill holes, insert short sections of all thread into a mortar mix made
for the purpose and bolt the sucker down to the pad.

John
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,353
Default Anchoring an existing shed to a concrete slab


"Bill Bushnell" wrote in message
...
I've got an existing 10'x12' shed sitting on a 4" thick slab of slightly
larger
dimensions. I'd like to anchor the shed to the slab without moving or
raising
the shed.

The shed sits on several columns of pressure-treated 4x4's that are in
mostly
good shape. These 4x4's only lie beneath the shed floor and do not extend
beyond
the exterior wall.

See the drawing at the link below:
http://bit.ly/rf7o83

I've been looking for a bracket (e.g. Simpson) that looks like the one
I've drawn
in the link above that can be used to anchor the ends of the 4x4's to the
slab.
I cannot find one of these in the Simpson catalog. Does anyone know where
I can
find something like this or similar?

Thanks.

--
Bill Bushnell
http://mrbill.homeip.net/



Not aware of anything that looks like that.

As an alternate choice I would just buy heavy gauge wall angles and use
three along each side.

If you are in a windy area use the perforated metal like garage door openers
are installed with and run an strip along each wall as far as your budget
allows. The same could be done along each end but you would not have a many
place to attach it to the runners.


--
Colbyt
Please come visit http://www.househomerepair.com




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,946
Default Anchoring an existing shed to a concrete slab

"Colbyt" wrote in
m:


"Bill Bushnell" wrote in message
...
I've got an existing 10'x12' shed sitting on a 4" thick slab of
slightly larger
dimensions. I'd like to anchor the shed to the slab without moving
or raising
the shed.

The shed sits on several columns of pressure-treated 4x4's that are
in mostly
good shape. These 4x4's only lie beneath the shed floor and do not
extend beyond
the exterior wall.

See the drawing at the link below:
http://bit.ly/rf7o83

I've been looking for a bracket (e.g. Simpson) that looks like the
one I've drawn
in the link above that can be used to anchor the ends of the 4x4's to
the slab.
I cannot find one of these in the Simpson catalog. Does anyone know
where I can
find something like this or similar?

Thanks.

--
Bill Bushnell
http://mrbill.homeip.net/



Not aware of anything that looks like that.


Just needs to be bent 90°.

http://www.mcfeelys.com/product/SDB-0244?ICID=FP1M1H1

Hopefully could find a galvanized version much less expensive.


As an alternate choice I would just buy heavy gauge wall angles and
use three along each side.


Which would seem a lot stronger.


If you are in a windy area use the perforated metal like garage door
openers are installed with and run an strip along each wall as far as
your budget allows. The same could be done along each end but you
would not have a many place to attach it to the runners.



  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default Anchoring an existing shed to a concrete slab

DD_BobK wrote:
On Sep 2, 8:58?pm, Bill Bushnell wrote:
I've got an existing 10'x12' shed sitting on a 4" thick slab of slightly larger
dimensions. ?I'd like to anchor the shed to the slab without moving or raising
the shed.

The shed sits on several columns of pressure-treated 4x4's that are in mostly
good shape. ?These 4x4's only lie beneath the shed floor and do not extend beyond
the exterior wall.

See the drawing at the link below:http://bit.ly/rf7o83

I've been looking for a bracket (e.g. Simpson) that looks like the one I've drawn
in the link above that can be used to anchor the ends of the 4x4's to the slab. ?
I cannot find one of these in the Simpson catalog. ?Does anyone know where I can
find something like this or similar?

Thanks.

--
Bill Bushnellhttp://mrbill.homeip.net/


Bill-


I took a look in the SST catalog but didn't find any connectors that
would slip onto a 4x4...... too small.


How about lagging a 4x4 "rim joist" to the ends of the existing 4x's
(both ends of them)
and then anchor these added "rim joists" to the slab with a simple
angle bracket.


Use 1/2 lags x 8" long (6" seemed a bit short)
Check out the Simpson HL Heavy Angles


I think this will be the easiest way to anchor your shed.


Bob and others,

Thanks for your advice.

Looks like the SST HL37 angle bracket may work. I drew a new sketch of the
design he

http://bit.ly/qTB0IF

Questions I still have:

1) Should I use two HL37's per 4x4 end as shown in the sketch, or is one per 4x4
end sufficient?

2) If I use two anchors per 4x4 end, one on each side, should I connect them
using a 1/2" bolt through the 4x4, instead of using lag screws?

3) Should I use concrete anchors in the concrete, or would a two 4" lag screws
per angle bracket be adequate? In either case I'd use concrete anchoring epoxy.

4) I was planning to anchor at each corner of the shed. Is that adequate?

Other information:

The shed is a pre-fab shed with finished interior and electrical service. The
flooring is 5/8" or 3/4" plywood over 4x4 pretreated "joists" that are visible
underneath that lie directly upon the concrete slab, and to which I plan to
attach the anchors. The 4x4s are nailed from the inside to the plywood subfloor.

The shed cannot be moved or raised! And, I cannot drill concrete anchor holes
directly under the shed--not enough clearance to get a drill and bit underneath,
hence the need to offset the anchor holes from their attachment to the 4x4s. I
can drill horizontal holes into the 4x4s if the holes are at or near the center
of the 4x4s (which means I may not be able to drill straight through holes to
attach the HL37 anchors to both sides of a 4x4 and may have to use lag screws
into the wood, even if I anchor both sides).

The shed is located in the San Francisco Bay Area, so my primary concern is the
shed sliding or being thrown off the slab due to earthquake.

Thanks for any additional advice.

--
Bill Bushnell
http://mrbill.homeip.net/
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,149
Default Anchoring an existing shed to a concrete slab

On 9/4/2011 1:53 PM, Bill Bushnell wrote:
wrote:
On Sep 2, 8:58?pm, Bill wrote:
I've got an existing 10'x12' shed sitting on a 4" thick slab of slightly larger
dimensions. ?I'd like to anchor the shed to the slab without moving or raising
the shed.

The shed sits on several columns of pressure-treated 4x4's that are in mostly
good shape. ?These 4x4's only lie beneath the shed floor and do not extend beyond
the exterior wall.

See the drawing at the link below:http://bit.ly/rf7o83

I've been looking for a bracket (e.g. Simpson) that looks like the one I've drawn
in the link above that can be used to anchor the ends of the 4x4's to the slab. ?
I cannot find one of these in the Simpson catalog. ?Does anyone know where I can
find something like this or similar?

Thanks.

--
Bill Bushnellhttp://mrbill.homeip.net/


Bill-


I took a look in the SST catalog but didn't find any connectors that
would slip onto a 4x4...... too small.


How about lagging a 4x4 "rim joist" to the ends of the existing 4x's
(both ends of them)
and then anchor these added "rim joists" to the slab with a simple
angle bracket.


Use 1/2 lags x 8" long (6" seemed a bit short)
Check out the Simpson HL Heavy Angles


I think this will be the easiest way to anchor your shed.


Bob and others,

Thanks for your advice.

Looks like the SST HL37 angle bracket may work. I drew a new sketch of the
design he

http://bit.ly/qTB0IF

Questions I still have:

1) Should I use two HL37's per 4x4 end as shown in the sketch, or is one per 4x4
end sufficient?

2) If I use two anchors per 4x4 end, one on each side, should I connect them
using a 1/2" bolt through the 4x4, instead of using lag screws?

3) Should I use concrete anchors in the concrete, or would a two 4" lag screws
per angle bracket be adequate? In either case I'd use concrete anchoring epoxy.

4) I was planning to anchor at each corner of the shed. Is that adequate?

Other information:

The shed is a pre-fab shed with finished interior and electrical service. The
flooring is 5/8" or 3/4" plywood over 4x4 pretreated "joists" that are visible
underneath that lie directly upon the concrete slab, and to which I plan to
attach the anchors. The 4x4s are nailed from the inside to the plywood subfloor.

The shed cannot be moved or raised! And, I cannot drill concrete anchor holes
directly under the shed--not enough clearance to get a drill and bit underneath,
hence the need to offset the anchor holes from their attachment to the 4x4s. I
can drill horizontal holes into the 4x4s if the holes are at or near the center
of the 4x4s (which means I may not be able to drill straight through holes to
attach the HL37 anchors to both sides of a 4x4 and may have to use lag screws
into the wood, even if I anchor both sides).

The shed is located in the San Francisco Bay Area, so my primary concern is the
shed sliding or being thrown off the slab due to earthquake.

Thanks for any additional advice.


It's a shed. Drill straight down through interior floor and 4x4, squirt
some of the fancy epoxy down there, and screw in big lag bolts, with a
big washer or spreader plate on top so the bolt doesn't go through
floor. Threaded rod pounded in with a mallet, and big nuts on top, would
make it removable. Won't look any worse than toe-stubbers out in the
weather. And if you pick you spots carefully, it won't interfere with
the usability of the shed. One in each corner, tucked right against the
walls, should be plenty.

As to earthquake protection- unless you are near the edge of a cliff
where the shed could slide over, tying it down hard to the slab will
likely INCREASE the damage in a quake. Instead of just bouncing around
as a unit, any ground flex will be transmitted to the structure of the shed.
--
aem sends...
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,227
Default Anchoring an existing shed to a concrete slab

On Sep 4, 11:42*am, aemeijers wrote:
On 9/4/2011 1:53 PM, Bill Bushnell wrote:









*wrote:
On Sep 2, 8:58?pm, Bill *wrote:
I've got an existing 10'x12' shed sitting on a 4" thick slab of slightly larger
dimensions. ?I'd like to anchor the shed to the slab without moving or raising
the shed.


The shed sits on several columns of pressure-treated 4x4's that are in mostly
good shape. ?These 4x4's only lie beneath the shed floor and do not extend beyond
the exterior wall.


See the drawing at the link below:http://bit.ly/rf7o83


I've been looking for a bracket (e.g. Simpson) that looks like the one I've drawn
in the link above that can be used to anchor the ends of the 4x4's to the slab. ?
I cannot find one of these in the Simpson catalog. ?Does anyone know where I can
find something like this or similar?


Thanks.


--
Bill Bushnellhttp://mrbill.homeip.net/


Bill-


I took a look in the SST catalog but didn't find any connectors that
would slip onto a 4x4...... too small. *


How about lagging a 4x4 "rim joist" *to the ends of the existing 4x's
(both ends of them)
and then anchor these added "rim joists" to the slab with a simple
angle bracket.


Use 1/2 lags x 8" long (6" seemed a bit short)
Check out the Simpson HL Heavy Angles


I think this will be the easiest way to anchor your shed.


Bob and others,


Thanks for your advice.


Looks like the SST HL37 angle bracket may work. *I drew a new sketch of the
design he


http://bit.ly/qTB0IF


Questions I still have:


1) Should I use two HL37's per 4x4 end as shown in the sketch, or is one per 4x4
end sufficient?


2) If I use two anchors per 4x4 end, one on each side, should I connect them
using a 1/2" bolt through the 4x4, instead of using lag screws?


3) Should I use concrete anchors in the concrete, or would a two 4" lag screws
per angle bracket be adequate? *In either case I'd use concrete anchoring epoxy.


4) I was planning to anchor at each corner of the shed. *Is that adequate?


Other information:


The shed is a pre-fab shed with finished interior and electrical service. *The
flooring is 5/8" or 3/4" plywood over 4x4 pretreated "joists" that are visible
underneath that lie directly upon the concrete slab, and to which I plan to
attach the anchors. *The 4x4s are nailed from the inside to the plywood subfloor.


The shed cannot be moved or raised! *And, I cannot drill concrete anchor holes
directly under the shed--not enough clearance to get a drill and bit underneath,
hence the need to offset the anchor holes from their attachment to the 4x4s. *I
can drill horizontal holes into the 4x4s if the holes are at or near the center
of the 4x4s (which means I may not be able to drill straight through holes to
attach the HL37 anchors to both sides of a 4x4 and may have to use lag screws
into the wood, even if I anchor both sides).


The shed is located in the San Francisco Bay Area, so my primary concern is the
shed sliding or being thrown off the slab due to earthquake.


Thanks for any additional advice.


It's a shed. Drill straight down through interior floor and 4x4, squirt
some of the fancy epoxy down there, *and screw in big lag bolts, with a
big washer or spreader plate on top so the bolt doesn't go through
floor. Threaded rod pounded in with a mallet, and big nuts on top, would
make it removable. Won't look any worse than toe-stubbers out in the
weather. And if you pick you spots carefully, it won't interfere with
the usability of the shed. One in each corner, tucked right against the
walls, should be plenty.

As to earthquake protection- unless you are near the edge of a cliff
where the shed could slide over, tying it down hard to the slab will
likely INCREASE the damage in a quake. Instead of just bouncing around
as a unit, any ground flex will be transmitted to the structure of the shed.
--
aem sends...


Bill-

Upon reading aemeijers' suggestion, I'm inclined to agree with his
suggestion.

I think my original suggestion is a superior design but as aemeijers
says "it's just a shed".
And how much capacity do you really need?

Are we talking wind or earthquake restraint?

As aemeijers says....tying the shed down will transfer more load to
it.
Yeah, after you're done.....the 4x4 are tied down.
What's the rest of the load path like?

Connection from the 4x4's to the shed sill & walls?
Shear capacity of the walls? Plywood?
Wood sheathing? MDF crap siding?

The whole shed doesn't weigh much (less than 2000lbs) so you don't
need much anchorage.

Simply your life....either use aemeijers' suggestion or
my 4x4 (or 2x4) "rim joist" lagged to the exsiting 4x4's and anchored
with heavy angles and an epoxied anchor.

Or forget the rim joist & just put a single angle on the end.

Your concept with multiple HL37's is way too complicated & too much
work.

I'd install about 8 angles....two on each shed face
and that's probably 2x as many as you actually need.

cheers
Bob
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 679
Default Anchoring an existing shed to a concrete slab

In ,
DD_BobK typed:
On Sep 4, 11:42 am, aemeijers wrote:
On 9/4/2011 1:53 PM, Bill Bushnell wrote:


....


Bill-

Upon reading aemeijers' suggestion, I'm inclined to agree
with his
suggestion.

I think my original suggestion is a superior design but
as aemeijers
says "it's just a shed".
And how much capacity do you really need?

Are we talking wind or earthquake restraint?

As aemeijers says....tying the shed down will transfer
more load to
it.
Yeah, after you're done.....the 4x4 are tied down.
What's the rest of the load path like?

Connection from the 4x4's to the shed sill & walls?
Shear capacity of the walls? Plywood?
Wood sheathing? MDF crap siding?

The whole shed doesn't weigh much (less than 2000lbs) so
you don't
need much anchorage.

Simply your life....either use aemeijers' suggestion or
my 4x4 (or 2x4) "rim joist" lagged to the exsiting 4x4's
and anchored
with heavy angles and an epoxied anchor.

Or forget the rim joist & just put a single angle on the
end.

Your concept with multiple HL37's is way too complicated
& too much
work.

I'd install about 8 angles....two on each shed face
and that's probably 2x as many as you actually need.

cheers
Bob


When I anchored the walls of our shed to the slab I used a .22 calibre
gun-nailer. Then used it to toenail anything larger than a 2x4. Took about 2
hours, not counting moving all the crap out to make room to work and then
putting it back in. Use the rght size nails and locatoins and it's a breeze.
TEST beforehand in case the cement was a brittle mix done by some
neophyte. And be accurate; it's really tough to pull a cement-nail out of
cement once it's driven in. Wear ear protection; those 22 shells get really
loud inside a small building!




  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default Anchoring an existing shed to a concrete slab

DD_BobK wrote:
Upon reading aemeijers' suggestion, I'm inclined to agree with his
suggestion.


I think my original suggestion is a superior design but as aemeijers
says "it's just a shed".
And how much capacity do you really need?


Are we talking wind or earthquake restraint?


As aemeijers says....tying the shed down will transfer more load to
it.
Yeah, after you're done.....the 4x4 are tied down.
What's the rest of the load path like?


Connection from the 4x4's to the shed sill & walls?
Shear capacity of the walls? Plywood?
Wood sheathing? MDF crap siding?


The whole shed doesn't weigh much (less than 2000lbs) so you don't
need much anchorage.


Simply your life....either use aemeijers' suggestion or
my 4x4 (or 2x4) "rim joist" lagged to the exsiting 4x4's and anchored
with heavy angles and an epoxied anchor.


Or forget the rim joist & just put a single angle on the end.


Your concept with multiple HL37's is way too complicated & too much
work.


I'd install about 8 angles....two on each shed face
and that's probably 2x as many as you actually need.


The 4x4's are nailed to the 5/8" subfloor that itself is connected to the walls.
The shearwall looks like 3/8" (or maybe 1/4") plywood with a decorative
exterior. It bears a slight resemblance to the base Tuff-Shed with the addition
of a side window, attic turbine vent, and drywall finished interior with
electrical outlets and lights, but I have no way to confirm that. (The shed was
installed by the house's prior owner.) I have boxes of stuff stored in the shed's
attic, so the shearwall would be tested under lateral motion.

Anchoring the shed, even if only one anchor at each of the four corners, entails
some expense and labor. IF/WHEN we get a strong enough earthquake to move the
shed, the most likely damage is to shear off the electrical service that comes
from underground at one of the outside walls and to move the shed such that I'd
nead to empty it, and then move it back onto it's pad and re-attach electrical
service.

If I anchor the shed the floor may survive, but the building might collapse or
get tweaked so that it needs to be rebuilt or replaced. I assume that would be
far more expensive than moving the shed a foot or two and re-attaching electrical
service.

There is no nearby cliff. The pad extends at least a foot on each side, and the
side and rear property lines are about 4 feet from the shed walls.

I'll consider your suggestions. But, in the end doing nothing may be the most
economical.

Thank you, everyone, for your help.

--
Bill Bushnell
http://mrbill.homeip.net/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New concrete slab different shade to existing slab Dundonald UK diy 5 September 14th 10 11:24 AM
Anchoring new shed to existing pad? Kiwanda Home Repair 10 June 1st 07 04:34 PM
concrete over existing slab MC Home Repair 1 March 16th 05 01:19 AM
pouring concrete over existing slab MC Home Repair 1 October 30th 04 05:57 PM
Anchoring concrete block row and base plate to existing porch slab? Stellijer Home Repair 5 March 31st 04 04:51 AM


All times are GMT +1. The time now is 04:38 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"