Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 130
Default interior SER cable usage in 2008 NEC

My contractor's electrician mentioned that he thinks SER cable is no
longer allowed (or possibly no longer allowed to be run exposed) in
interior residential applications under the 2008 NEC for, e.g., feeding
sub-panels. Anybody know about this? If it is true there is going to
be a lot of painful conduit work to get to the planned sub-panel locations
in my new (very old) house...

Dan Lanciani
ddl@danlan.*com
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default interior SER cable usage in 2008 NEC


"Dan Lanciani" ddl@danlan.*com wrote in message
...
My contractor's electrician mentioned that he thinks SER cable is no
longer allowed (or possibly no longer allowed to be run exposed) in
interior residential applications under the 2008 NEC for, e.g., feeding
sub-panels. Anybody know about this? If it is true there is going to
be a lot of painful conduit work to get to the planned sub-panel locations
in my new (very old) house...

Dan Lanciani
ddl@danlan.*com


Apparently there is or was an older type of service entrance cable that had
a rubber covering which is no longer allowed. Plastic or thermoset covered
conductors are fine. Neutral has to be insulated, ground does not. Follow
the installation rules for Romex


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default interior SER cable usage in 2008 NEC

My contractor's electrician mentioned that he thinks SER cable is no
longer allowed (or possibly no longer allowed to be run exposed) in
interior residential applications under the 2008 NEC for, e.g., feeding
sub-panels. Anybody know about this? If it is true there is going to
be a lot of painful conduit work to get to the planned sub-panel locations
in my new (very old) house...




*As far as I know it is still permitted. However the ampacity rating is not
the same for interior circuits as it is for an electrical service. He would
have to size the cable according to table 310.15(B)(16) in the 2011 code
book and not by table 310.15(B)(7).

A call to your local electrical inspector should clarify things.

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 130
Default interior SER cable usage in 2008 NEC

In article , writes:
| On 6 Dec 2010 22:12:35 GMT, ddl@danlan.*com (Dan Lanciani) wrote:
|
| My contractor's electrician mentioned that he thinks SER cable is no
| longer allowed (or possibly no longer allowed to be run exposed) in
| interior residential applications under the 2008 NEC for, e.g., feeding
| sub-panels. Anybody know about this? If it is true there is going to
| be a lot of painful conduit work to get to the planned sub-panel locations
| in my new (very old) house...
|
| Dan Lanciani
| ddl@danlan.*com
|
| The only thing that happened was the plugged the loophole that let you
| use SE cable at the 75c ampacity indoors. I think that actually
| happened in 2002 or 2005 tho.
| In 2011 they massaged the language but it really did not change.
| SE/SER can be used inside but at the 60c ampacity.

So #2 SER aluminum is down to 75A? I think this is a fairly big change
because not long ago there were debates about whether the "service and
feeders" exception let you go to 100A as opposed to being limited to the
75c ampacity of 90A. Looks like now you would need 1/0 for 100A @ 60c and
(wow) 350kcmil for 200A. I don't think the catalog I was looking at even
has SER that big. With 75c rated conductors in conduit and 75c rated
breaker terminals/enclosure can you still use the 75c ampacity indoors?
If so, maybe conduit doesn't look so bad after all.

Dan Lanciani
ddl@danlan.*com
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 130
Default interior SER cable usage in 2008 NEC

In article , writes:
| On 7 Dec 2010 06:45:24 GMT, ddl@danlan.*com (Dan Lanciani) wrote:
|
| | The only thing that happened was the plugged the loophole that let you
| | use SE cable at the 75c ampacity indoors. I think that actually
| | happened in 2002 or 2005 tho.
| | In 2011 they massaged the language but it really did not change.
| | SE/SER can be used inside but at the 60c ampacity.
|
| So #2 SER aluminum is down to 75A? I think this is a fairly big change
| because not long ago there were debates about whether the "service and
| feeders" exception let you go to 100A as opposed to being limited to the
| 75c ampacity of 90A. Looks like now you would need 1/0 for 100A @ 60c and
| (wow) 350kcmil for 200A. I don't think the catalog I was looking at even
| has SER that big. With 75c rated conductors in conduit and 75c rated
| breaker terminals/enclosure can you still use the 75c ampacity indoors?
| If so, maybe conduit doesn't look so bad after all.
|
| Dan Lanciani
| ddl@danlan.*com
|
|
| You are confusing 310.15(B)(6) with 310.16.

No, I was just commenting that the clarification that you cannot use
310.15(B)(6) for sub-panel feeds (something that was done a lot and often
debated here) combined with the newer 60c limitation makes for a rather
substantial practical change. For example, my house (not the new old one)
has a 400A panel feeding a 200A sub and 2 100A subs with 4/0 and 2 AL SER
respectively. All installed by a licensed electrician, inspected and
approved. By the new rules those cables look terribly undersized and
should be 350kcmil and 1/0.

| The original question implied you were using SE for branch circuit or
| regular feeder wiring.

I'm talking about feeds to sub-panels. Are they regular feeders?

| Then you use the 60c column of 310.16.
| In past years you could use it at 75c. That changed a couple cycles
| ago. It was just reworded in the 2011 and 310.16 changed article
| number.

As far as I can tell from Googling it changed in 2008 and there was a
proposal (accepted in principle?) to change it back in 2011 unless the
cable was in thermal insulation in which case it would still be 60c.
I suppose this issue might be what made the contractor think you can't
use SER anymore; it isn't practical for the higher ampacities. Since
the new old house is in 2008 NEC territory I'll have to look at copper
SER (I'm guessing very expensive) or more likely go with conduit.

Dan Lanciani
ddl@danlan.*com


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default interior SER cable usage in 2008 NEC

Dan Lanciani wrote:
In article , writes:
| On 7 Dec 2010 06:45:24 GMT, ddl@danlan.*com (Dan Lanciani) wrote:
|
| | The only thing that happened was the plugged the loophole that let you
| | use SE cable at the 75c ampacity indoors. I think that actually
| | happened in 2002 or 2005 tho.
| | In 2011 they massaged the language but it really did not change.
| | SE/SER can be used inside but at the 60c ampacity.
|
| So #2 SER aluminum is down to 75A? I think this is a fairly big change
| because not long ago there were debates about whether the "service and
| feeders" exception let you go to 100A as opposed to being limited to the
| 75c ampacity of 90A. Looks like now you would need 1/0 for 100A @ 60c and
| (wow) 350kcmil for 200A. I don't think the catalog I was looking at even
| has SER that big. With 75c rated conductors in conduit and 75c rated
| breaker terminals/enclosure can you still use the 75c ampacity indoors?
| If so, maybe conduit doesn't look so bad after all.
|
| Dan Lanciani
| ddl@danlan.*com
|
|
| You are confusing 310.15(B)(6) with 310.16.

No, I was just commenting that the clarification that you cannot use
310.15(B)(6) for sub-panel feeds (something that was done a lot and often
debated here) combined with the newer 60c limitation makes for a rather
substantial practical change. For example, my house (not the new old one)
has a 400A panel feeding a 200A sub and 2 100A subs with 4/0 and 2 AL SER
respectively. All installed by a licensed electrician, inspected and
approved. By the new rules those cables look terribly undersized and
should be 350kcmil and 1/0.

..
Far as I know you could *never* use 310.15-B-6 for feeders unless, as
gfretwell wrote, they "have the entire load of a residential service".
That would be, for instance, a feeder from a single residential service
disconnect to a panel. There can be no other connections to the service.

Originally 310.15-B-6 was only for residential service conductors.
Feeders were added *if* they carry the same load as the service
conductors (which is reasonable).

The feeders to your subpanels could not use 310.15-B-6.

"Diversity" allows the smaller service wire in 310.15-B-6. You don't
necessarily have diversity on a feeder.
..

| The original question implied you were using SE for branch circuit or
| regular feeder wiring.

I'm talking about feeds to sub-panels. Are they regular feeders?


yes


| Then you use the 60c column of 310.16.
| In past years you could use it at 75c. That changed a couple cycles
| ago. It was just reworded in the 2011 and 310.16 changed article
| number.

As far as I can tell from Googling it changed in 2008 and there was a
proposal (accepted in principle?) to change it back in 2011 unless the
cable was in thermal insulation in which case it would still be 60c.
I suppose this issue might be what made the contractor think you can't
use SER anymore; it isn't practical for the higher ampacities. Since
the new old house is in 2008 NEC territory I'll have to look at copper
SER (I'm guessing very expensive) or more likely go with conduit.

Dan Lanciani
ddl@danlan.*com


I'm not following what the change was.

I don't see a code specified temp rating for SE. I would think it then
can be used at the rating marked on the cable. It must be derated if
ambient will be higher (including thermal insulation).

There are further limits in 110.14-C-1 (does not apply service and
related feeder wires rated under 310.15-B-6 above).
For circuits rated 100A and less, generally the wire can only be used at
its 60C rating.
For circuits rated over 100A generally the wire can only be used at its
75C rating (if rated 75C or higher).

--
bud--
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default interior SER cable usage in 2008 NEC

On 2010-12-07, bud-- wrote:

I'm not following what the change was.

I don't see a code specified temp rating for SE. I would think it then
can be used at the rating marked on the cable. It must be derated if
ambient will be higher (including thermal insulation).


2008 NEC 338.10(B)(4)(a) says:

Interior Installations. In addition to the provisions of this
article, Type SE service-entrance cable used for interior wiring
shall comply with the installation requirements of Part II of
Article 334.

Article 334 is for NM cable, so this basically says that if you are
using SER for interior branch circuits or feeders, you have to treat
it like NM. In particular 334.80 limits the ampacity of NM to the 60
degree column.

Earlier versions of 338.10(B)(4)(a) included a specific exemption from
334.80, but that got deleted in 2005 or 2008.

Cheers, Wayne
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default interior SER cable usage in 2008 NEC

Wayne Whitney wrote:
On 2010-12-07, bud-- wrote:

I'm not following what the change was.

I don't see a code specified temp rating for SE. I would think it then
can be used at the rating marked on the cable. It must be derated if
ambient will be higher (including thermal insulation).


2008 NEC 338.10(B)(4)(a) says:

Interior Installations. In addition to the provisions of this
article, Type SE service-entrance cable used for interior wiring
shall comply with the installation requirements of Part II of
Article 334.

Article 334 is for NM cable, so this basically says that if you are
using SER for interior branch circuits or feeders, you have to treat
it like NM. In particular 334.80 limits the ampacity of NM to the 60
degree column.


I read that. Most of Part 2 is mechanical installation requirements. I
would not call a 60C limit an installation requirement.


Earlier versions of 338.10(B)(4)(a) included a specific exemption from
334.80, but that got deleted in 2005 or 2008.


That certainly agrees with what you wrote above.

--
bud--

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default interior SER cable usage in 2008 NEC

Wayne Whitney wrote:

Earlier versions of 338.10(B)(4)(a) included a specific exemption from
334.80, but that got deleted in 2005 or 2008.

Cheers, Wayne


I was curious why the change, so I looked it up. You are right - it was
2008.

The argument was (interior use) "the ampacity of the conductors should
be the same as permitted for NM cable since the insulations used are the
same both NM and SE conductors."

I guess the question then is why is SE allowed at a higher temperature
rating outside. Looks like it has a 75 or 90C rating, depending on
conductor insulation. Or 75C if not otherwise marked.

--
bud--

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 130
Default interior SER cable usage in 2008 NEC

In article , (bud--) writes:
| Dan Lanciani wrote:
| In article ,
writes:
| | On 7 Dec 2010 06:45:24 GMT, ddl@danlan.*com (Dan Lanciani) wrote:
| |
| | | The only thing that happened was the plugged the loophole that let you
| | | use SE cable at the 75c ampacity indoors. I think that actually
| | | happened in 2002 or 2005 tho.
| | | In 2011 they massaged the language but it really did not change.
| | | SE/SER can be used inside but at the 60c ampacity.
| |
| | So #2 SER aluminum is down to 75A? I think this is a fairly big change
| | because not long ago there were debates about whether the "service and
| | feeders" exception let you go to 100A as opposed to being limited to the
| | 75c ampacity of 90A. Looks like now you would need 1/0 for 100A @ 60c and
| | (wow) 350kcmil for 200A. I don't think the catalog I was looking at even
| | has SER that big. With 75c rated conductors in conduit and 75c rated
| | breaker terminals/enclosure can you still use the 75c ampacity indoors?
| | If so, maybe conduit doesn't look so bad after all.
| |
| | Dan Lanciani
| | ddl@danlan.*com
| |
| |
| | You are confusing 310.15(B)(6) with 310.16.
|
| No, I was just commenting that the clarification that you cannot use
| 310.15(B)(6) for sub-panel feeds (something that was done a lot and often
| debated here) combined with the newer 60c limitation makes for a rather
| substantial practical change. For example, my house (not the new old one)
| has a 400A panel feeding a 200A sub and 2 100A subs with 4/0 and 2 AL SER
| respectively. All installed by a licensed electrician, inspected and
| approved. By the new rules those cables look terribly undersized and
| should be 350kcmil and 1/0.
| .
| Far as I know you could *never* use 310.15-B-6 for feeders

Honestly I don't want to start a long debate (especially because this
has been covered here extensively in the past) but for whatever reasons
(call it widespread misinterpretation of the code) it was used and
approved frequently. If you Google some of the discussions on the
latest change you will see some people are still using it. In many
(but not all) cases the 310.15-B-6 numbers weren't all that much
bigger than the 75c ratings, e.g., IIRC, 125A vs. 120A for AL 1/0
which in conjunction with the next-standard-sized breaker might have
contributed to the confusion. But I'm just speculating wildly.

| I'm not following what the change was.

As the 2008 NEC you have to use the 60c ampacity for indoor SE applications.
This can make for some pretty big conductors. The change was made by analogy
to NM cable, but I'm not sure that makes a lot of sense. Historically NM
cable had 60c conductors and I thought limiting it to 60c even after NM-B
went to higher-temperature conductors was in the nature of reverse
grandfathering. I really don't understand if the feeling is that you simply
cannot have a plastic cable usable at 75c or if different materials would
allow for it. Regardless, I think this is a significant change and makes
conduit atractive in cases where SER would have been the obvious choice
before.

Dan Lanciani