I'm redoing the utility room in our 40 year old house, and I stupidly
removed the socket from the box to put in a GFCI without marking the
original wires. Stupidly because there has been some previous "work"
done by
possibly-incompetent folks, so I'm not sure what to make of this.
I've got
a blue wire and two white wires coming into the box, and the voltage
between
the two whites is 120, the voltage between one of the whites and the
blue is
120, and the voltage between the other of the whites and the blue is
240.
How is this possible? Or is there something obvious I'm missing? The
wires
themselves seem to be original wiring for the house, but I'm not sure
what
they might be connected to at the other end.

Any ideas what the blue wire was supposed to be originally for?

TIA!
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 680
Default white-white 240 volts?????

On Aug 9, 4:18*am, gmark wrote:
I'm redoing the utility room in our 40 year old house, and I stupidly
removed the socket from the box to put in a GFCI without marking the
original wires. Stupidly because there has been some previous "work"
done by
possibly-incompetent folks, so I'm not sure what to make of this.
I've got
a blue wire and two white wires coming into the box, and the voltage
between
the two whites is 120, the voltage between one of the whites and the
blue is
120, and the voltage between the other of the whites and the blue is
240.
How is this possible? *Or is there something obvious I'm missing? *The
wires
themselves seem to be original wiring for the house, but I'm not sure
what
they might be connected to at the other end.

Any ideas what the blue wire was supposed to be originally for?

TIA!


Measure each using electrical ground ( hoping you have one!) wire to
ground reading zero is neutral and wire to ground reading 120 is the
hot.
It would be difficult without tracing wires to tell the difference if
they used a white wire for ground though.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default white-white 240 volts?????


"gmark" wrote in message
...
I'm redoing the utility room in our 40 year old house, and I stupidly
removed the socket from the box to put in a GFCI without marking the
original wires. Stupidly because there has been some previous "work"
done by
possibly-incompetent folks, so I'm not sure what to make of this.
I've got
a blue wire and two white wires coming into the box, and the voltage
between
the two whites is 120, the voltage between one of the whites and the
blue is
120, and the voltage between the other of the whites and the blue is
240.
How is this possible? Or is there something obvious I'm missing? The
wires
themselves seem to be original wiring for the house, but I'm not sure
what
they might be connected to at the other end.

Any ideas what the blue wire was supposed to be originally for?

TIA!




It sounds like a multi-wire branch circuit, or Edison circuit. Two hot legs
of different potential sharing a common neutral. I'm assuming that if your
outlet was 120 volts, one of the wires was not connected. If all three wires
were connected, the brass tab was removed on the hot side of the receptacle,
separating the upper from the lower receptacle. Each receptacle would then
be on separate circuits. You should remark the white wire, which is hot,
with black tape of marking pen.


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default white-white 240 volts?????

On Aug 9, 7:00*am, "RBM" wrote:
"gmark" wrote in message

...





I'm redoing the utility room in our 40 year old house, and I stupidly
removed the socket from the box to put in a GFCI without marking the
original wires. Stupidly because there has been some previous "work"
done by
possibly-incompetent folks, so I'm not sure what to make of this.
I've got
a blue wire and two white wires coming into the box, and the voltage
between
the two whites is 120, the voltage between one of the whites and the
blue is
120, and the voltage between the other of the whites and the blue is
240.
How is this possible? *Or is there something obvious I'm missing? *The
wires
themselves seem to be original wiring for the house, but I'm not sure
what
they might be connected to at the other end.


Any ideas what the blue wire was supposed to be originally for?


TIA!


It sounds like a multi-wire branch circuit, or Edison circuit. Two hot legs
of different potential sharing a common neutral. I'm assuming that if your
outlet was 120 volts, one of the wires was not connected. If all three wires
were connected, the brass tab was removed on the hot side of the receptacle,
separating the upper from the lower receptacle. Each receptacle would then
be on separate circuits. You should remark the white wire, which is hot,
with black tape of marking pen.- Hide quoted text -

- Show quoted text -


Curiosity question:

If this is an Edison circuit which had each receptacle on a separate
circuit, how would the OP install the GFCI?

You can't split the circuits on a GFCI can you?

Would you just wire nut (and mark) one of the hot wires and push it
back into the box?

P.S. This leads to another issue:

Would an Edison circuit mean that either the breakers for these 2
circuits were ganged together (which should have been a clue) or the
OP was playing in a box with a live circuit, assuming he only shut off
one breaker?

I only mention that because I have an Edison circuit in my house and
the breakers were not ganged when I moved in. The receptacle I was
working on was not split, so when it went dead I though I was OK. As I
was working on the circuit and removing wires, I noticed a stair
landing light begin to glow dimly. That was my first clue that
something was amiss - and my first introuduction to Edison circuits.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default white-white 240 volts?????

DerbyDad03 wrote:
On Aug 9, 7:00 am, "RBM" wrote:
"gmark" wrote in message

...





I'm redoing the utility room in our 40 year old house, and I stupidly
removed the socket from the box to put in a GFCI without marking the
original wires. Stupidly because there has been some previous "work"
done by
possibly-incompetent folks, so I'm not sure what to make of this.
I've got
a blue wire and two white wires coming into the box, and the voltage
between
the two whites is 120, the voltage between one of the whites and the
blue is
120, and the voltage between the other of the whites and the blue is
240.
How is this possible? Or is there something obvious I'm missing? The
wires
themselves seem to be original wiring for the house, but I'm not sure
what
they might be connected to at the other end.
Any ideas what the blue wire was supposed to be originally for?
TIA!

It sounds like a multi-wire branch circuit, or Edison circuit. Two hot legs
of different potential sharing a common neutral. I'm assuming that if your
outlet was 120 volts, one of the wires was not connected. If all three wires
were connected, the brass tab was removed on the hot side of the receptacle,
separating the upper from the lower receptacle. Each receptacle would then
be on separate circuits. You should remark the white wire, which is hot,
with black tape of marking pen.


Curiosity question:

If this is an Edison circuit which had each receptacle on a separate
circuit, how would the OP install the GFCI?

You can't split the circuits on a GFCI can you?

Would you just wire nut (and mark) one of the hot wires and push it
back into the box?


That sounds good to me. You could use the other circuit on a different
receptacle or extend either or both circuits to elsewhere.

I would want to find out where the circuits landed in the panel before I
went further. And whether there is a ground at the box.


P.S. This leads to another issue:

Would an Edison circuit mean that either the breakers for these 2
circuits were ganged together (which should have been a clue) or the
OP was playing in a box with a live circuit, assuming he only shut off
one breaker?

I only mention that because I have an Edison circuit in my house and
the breakers were not ganged when I moved in. The receptacle I was
working on was not split, so when it went dead I though I was OK. As I
was working on the circuit and removing wires, I noticed a stair
landing light begin to glow dimly. That was my first clue that
something was amiss - and my first introuduction to Edison circuits.


The NEC has required breakers for a multiwire circuit where both
circuits connect to the same device ("yoke") to have a common disconnect
for, I think, at least 10 years. Could be a 2 pole breaker or listed
handle tie.

The 2008 NEC requires all [new] multiwire branch circuits to have a
common disconnect.

--
bud--


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,473
Default white-white 240 volts?????


"DerbyDad03" wrote in message
...
On Aug 9, 7:00 am, "RBM" wrote:
"gmark" wrote in message

...





I'm redoing the utility room in our 40 year old house, and I stupidly
removed the socket from the box to put in a GFCI without marking the
original wires. Stupidly because there has been some previous "work"
done by
possibly-incompetent folks, so I'm not sure what to make of this.
I've got
a blue wire and two white wires coming into the box, and the voltage
between
the two whites is 120, the voltage between one of the whites and the
blue is
120, and the voltage between the other of the whites and the blue is
240.
How is this possible? Or is there something obvious I'm missing? The
wires
themselves seem to be original wiring for the house, but I'm not sure
what
they might be connected to at the other end.


Any ideas what the blue wire was supposed to be originally for?


TIA!


It sounds like a multi-wire branch circuit, or Edison circuit. Two hot
legs
of different potential sharing a common neutral. I'm assuming that if your
outlet was 120 volts, one of the wires was not connected. If all three
wires
were connected, the brass tab was removed on the hot side of the
receptacle,
separating the upper from the lower receptacle. Each receptacle would then
be on separate circuits. You should remark the white wire, which is hot,
with black tape of marking pen.- Hide quoted text -

- Show quoted text -


Curiosity question:

If this is an Edison circuit which had each receptacle on a separate
circuit, how would the OP install the GFCI?

You can't split the circuits on a GFCI can you?

Would you just wire nut (and mark) one of the hot wires and push it
back into the box?

P.S. This leads to another issue:

Would an Edison circuit mean that either the breakers for these 2
circuits were ganged together (which should have been a clue) or the
OP was playing in a box with a live circuit, assuming he only shut off
one breaker?

I only mention that because I have an Edison circuit in my house and
the breakers were not ganged when I moved in. The receptacle I was
working on was not split, so when it went dead I though I was OK. As I
was working on the circuit and removing wires, I noticed a stair
landing light begin to glow dimly. That was my first clue that
something was amiss - and my first introuduction to Edison circuits.

See Bud's comments for the answers to your questions.

Regarding your first experience with an Edison circuit, often the three
wires were run to an outlet box, then two wires would split off from there
to another set of outlets. In the "main" junction box one of the hot legs
would go to that receptacle, the other hot leg would be spliced to the hot
leg going to the other circuit's outlets, but often the neutrals would be
connected to the receptacle. This is probably the situation that you
encountered. You killed the circuit to the outlet you were working on,
however the second circuit, which shares the neutral is still alive, and
when you lift the neutral from the receptacle, you lose you return path, and
create a dangerous situation. For this reason,and others, the code doesn't
allow the neutral of a multi wire branch circuit to be dependant upon a
device. Unfortunately, this situation is all to common.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
White induction hob on white marble/granite? Jason UK diy 10 January 14th 10 12:21 AM
Help needed with identifying cause for dirty white illumination in LCD monitors. Looks yellowish / off white! Chad Entringer Electronics Repair 6 July 22nd 07 02:05 PM
Nancy Loves George: The Elites-Driven 'White Trashing of America' to Degrade, Demoralize & Replace White America fred Home Repair 0 November 5th 06 01:54 PM
White is more purple than white on projection tv Raventy Electronics Repair 6 June 24th 05 07:37 AM


All times are GMT +1. The time now is 08:50 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"