DerbyDad03 wrote:
On Aug 9, 7:00 am, "RBM" wrote:
"gmark" wrote in message

...





I'm redoing the utility room in our 40 year old house, and I stupidly
removed the socket from the box to put in a GFCI without marking the
original wires. Stupidly because there has been some previous "work"
done by
possibly-incompetent folks, so I'm not sure what to make of this.
I've got
a blue wire and two white wires coming into the box, and the voltage
between
the two whites is 120, the voltage between one of the whites and the
blue is
120, and the voltage between the other of the whites and the blue is
240.
How is this possible? Or is there something obvious I'm missing? The
wires
themselves seem to be original wiring for the house, but I'm not sure
what
they might be connected to at the other end.
Any ideas what the blue wire was supposed to be originally for?
TIA!

It sounds like a multi-wire branch circuit, or Edison circuit. Two hot legs
of different potential sharing a common neutral. I'm assuming that if your
outlet was 120 volts, one of the wires was not connected. If all three wires
were connected, the brass tab was removed on the hot side of the receptacle,
separating the upper from the lower receptacle. Each receptacle would then
be on separate circuits. You should remark the white wire, which is hot,
with black tape of marking pen.


Curiosity question:

If this is an Edison circuit which had each receptacle on a separate
circuit, how would the OP install the GFCI?

You can't split the circuits on a GFCI can you?

Would you just wire nut (and mark) one of the hot wires and push it
back into the box?


That sounds good to me. You could use the other circuit on a different
receptacle or extend either or both circuits to elsewhere.

I would want to find out where the circuits landed in the panel before I
went further. And whether there is a ground at the box.


P.S. This leads to another issue:

Would an Edison circuit mean that either the breakers for these 2
circuits were ganged together (which should have been a clue) or the
OP was playing in a box with a live circuit, assuming he only shut off
one breaker?

I only mention that because I have an Edison circuit in my house and
the breakers were not ganged when I moved in. The receptacle I was
working on was not split, so when it went dead I though I was OK. As I
was working on the circuit and removing wires, I noticed a stair
landing light begin to glow dimly. That was my first clue that
something was amiss - and my first introuduction to Edison circuits.


The NEC has required breakers for a multiwire circuit where both
circuits connect to the same device ("yoke") to have a common disconnect
for, I think, at least 10 years. Could be a 2 pole breaker or listed
handle tie.

The 2008 NEC requires all [new] multiwire branch circuits to have a
common disconnect.

--
bud--