Default For the Electrical Wizards....

Awl --

So I finally unloaded those 20 old #14 bx cables off the ancient upstairs
fuse panel, onto a breaker panel downstairs, 7 (mis-wired) Edison circuits
and all....

It went pretty well, with about half the bx cables able to reach the new
panel, and half being spliced upstairs, via #14 wire in 3/4" Greenfield.

The advice here prior to the job proved invaluable, and **many thanks to all
who offered their thoughts and hard-earned knowledge and experiences**. ahr
is really a web-treasure.

But.... Holy ****, What a job!!!!. You might wonder, Well, what's so
tough about DAT?
I don't really know, as much of it is a bad fog now.

But, I can say that including the demolition (about 70 sq ft of heavy
plaster/lathe wall, about 30 feet of 10" duct in about a 1.5' x 1.5' wood
encasement), this was a 3-week job, many days 10 and 12 hours days.
Admittedly some head-scratching time, but mostly back-breaking and
finger-wearing labor. Including some moved appliances, gas plumbing.

What a I thought would be an afternoon's work would turn into days.... Good
thing I'm not in the contracting/estimating business, dats f'sure.... And
the cosmetic finishing still awaits, an even longer job. But everything is
at least functional now.

But here's some weird/funny stuff I encountered.

1. During the demo, I inadvertently cut a bx cable, an edison circuit.
Would normally not be a problem, except the "red" had so faded that it is
sort of indistinguishable from the white, ie, both appear tan/beige.
Worse, I don't really know what these wires control, as the house was wired
in a helter-skelter fashion, where one fuse would control a hodge-podge of
outlets/lites.

How do I sleuth this out? It seems to me, for the time being, it would be
best to keep both presumed hots on the same leg for now. Nothing is
blowing so far.


2. While unloading the fuse panel of its neutrals (first I'd remove the hot
from the fuse, then the corresponding neutral), my main temporary neutral
connection to one fuse panel became undone, unbeknownst to me.

As I unloaded the circuit neutral (hot already removed), there was still
arcing. I'm assuming that with the main neutral removed, this neutral was
carrying return current from *other* hots, with the current eventually
making its way to ground (btw, these bx cables don't have a ground wire).
Ergo, arcing from other hots?

Is this to be expected, with a main neutral removed?


3. With a non-edison circuit (one hot/neutral) controlling a few
lites/outlets in the kitchen, and all wires separated in a junction box from
a demo'd wall, I noticed on separating out the old mess that I could get an
outlet and lite to go in series, ie, both would dim.

I can readily see how this would happen in an edison circuit with a lifted
neutral (in which both lites etc would be normal OR one dim and the other
too brite), but I haven't been able to sketch out how, with just one hot,
parts of the circuit would wind up being in series.

Is this normal with a lifted local neutral? Or does this indicate a
fundamental wiring problem? How to sleuth?

tia.
--
EA


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default For the Electrical Wizards....

On Nov 23, 9:13*am, "Existential Angst"
wrote:
Awl --

So I finally unloaded those 20 old #14 bx cables off the ancient upstairs
fuse panel, onto a breaker panel downstairs, 7 (mis-wired) Edison circuits
and all....

It went pretty well, with about half the bx cables able to reach the new
panel, and half being spliced upstairs, via #14 wire in 3/4" Greenfield.

The advice here prior to the job proved invaluable, and **many thanks to all
who offered their thoughts and hard-earned knowledge and experiences**. *ahr
is really a web-treasure.

But.... *Holy ****, *What a job!!!!. *You might wonder, Well, what's so
tough about DAT?
I don't really know, as much of it is a bad fog now.

But, I can say that including the demolition (about 70 sq ft of heavy
plaster/lathe wall, about 30 feet of 10" duct in about a 1.5' x 1.5' wood
encasement), this was a 3-week job, many days 10 and 12 hours days.
Admittedly some head-scratching time, but mostly back-breaking and
finger-wearing labor. *Including some moved appliances, gas plumbing.

What a I thought would be an afternoon's work would turn into days.... *Good
thing I'm not in the contracting/estimating business, dats f'sure.... *And
the cosmetic finishing still awaits, an even longer job. *But everything is
at least functional now.

But here's some weird/funny stuff I encountered.

1. *During the demo, I inadvertently cut a bx cable, an edison circuit.
Would normally not be a problem, except the "red" had so faded that it is
sort of indistinguishable from the white, ie, both appear tan/beige.
Worse, I don't really know what these wires control, as the house was wired
in a helter-skelter fashion, where one fuse would control a hodge-podge of
outlets/lites.

How do I sleuth this out? *It seems to me, for the time being, it would be
best to keep both presumed hots on the same leg for now. *Nothing is
blowing so far.


You say you have an edison circuit, ie shared neutral and cut the
cable running from the panel. Now you propose to put both hots on the
same leg, exactly why, I'm not sure.

This is an example of why I'm not a big fan of shared neutrals. It's
very easy for someone doing repair work who isn't familiar with these
to create a dangerous situation. If you do put both hots on the same
leg, you will now have a maximum current on the neutral that is twice
what it was previously, ie it will be equal to the sum of the two
breaker currents. I doubt the conductors are rated for that.

The rest of the stuff below is too confusing to even attempt to
comment on, except that if you are working on circuits that are de-
energized correctly PRIOR to beginning work, there shouldn't be arcing
going on while you are working on them

Given the above, I'd be concerned about safety of not only doing the
work, but also the finished product.




2. *While unloading the fuse panel of its neutrals (first I'd remove the hot
from the fuse, then the corresponding neutral), my main temporary neutral
connection to one fuse panel became undone, unbeknownst to me.

As I unloaded the circuit neutral (hot already removed), there was still
arcing. *I'm assuming that with the main neutral removed, this neutral was
carrying return current from *other* hots, with the current eventually
making its way to ground (btw, these bx cables don't have a ground wire).
Ergo, arcing from other hots?

Is this to be expected, with a main neutral removed?

3. *With a non-edison circuit (one hot/neutral) controlling a few
lites/outlets in the kitchen, and all wires separated in a junction box from
a demo'd wall, I noticed on separating out the old mess that I could get an
outlet and lite to go in series, ie, both would dim.

I can readily see how this would happen in an edison circuit with a lifted
neutral (in which both lites etc would be normal OR one dim and the other
too brite), but I haven't been able to sketch out how, with just one hot,
parts of the circuit would wind up being in series.

Is this normal with a lifted local neutral? *Or does this indicate a
fundamental wiring problem? *How to sleuth?

tia.
--
EA


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default For the Electrical Wizards....

Existential Angst wrote:

But here's some weird/funny stuff I encountered.

1. During the demo, I inadvertently cut a bx cable, an edison circuit.
Would normally not be a problem, except the "red" had so faded that it is
sort of indistinguishable from the white, ie, both appear tan/beige.
Worse, I don't really know what these wires control, as the house was wired
in a helter-skelter fashion, where one fuse would control a hodge-podge of
outlets/lites.

How do I sleuth this out? It seems to me, for the time being, it would be
best to keep both presumed hots on the same leg for now. Nothing is
blowing so far.


When all the other electric is reconnected find what is not powered. If
everything is powered I would probably leave the circuits disconnected.

If you find a receptacle, for example, is not powered plug-in a lamp
that is turned on. Connect the known hot to power. One of the other
wires may light the bulb if connected to the neutral bar. If not the
receptacle is probably is on the 2nd hot wire. In that case I might pull
the receptacle and if one wire is clearly a neutral check continuity to
the wires in the panel.

If you connect wires to power connect them to the same fuse/breaker.
(That may be what you did.) That covers trader's concern.


2. While unloading the fuse panel of its neutrals (first I'd remove the hot
from the fuse, then the corresponding neutral), my main temporary neutral
connection to one fuse panel became undone, unbeknownst to me.

As I unloaded the circuit neutral (hot already removed), there was still
arcing. I'm assuming that with the main neutral removed, this neutral was
carrying return current from *other* hots, with the current eventually
making its way to ground (btw, these bx cables don't have a ground wire).
Ergo, arcing from other hots?

Is this to be expected, with a main neutral removed?


If the hot is disconnected (or both hots for an Edison ckt) there
shouldn't be a significant spark when you disconnect the neutral. (There
could be a tiny spark from capacitive currents.)


3. With a non-edison circuit (one hot/neutral) controlling a few
lites/outlets in the kitchen, and all wires separated in a junction box from
a demo'd wall, I noticed on separating out the old mess that I could get an
outlet and lite to go in series, ie, both would dim.

I can readily see how this would happen in an edison circuit with a lifted
neutral (in which both lites etc would be normal OR one dim and the other
too brite), but I haven't been able to sketch out how, with just one hot,
parts of the circuit would wind up being in series.

Is this normal with a lifted local neutral? Or does this indicate a
fundamental wiring problem? How to sleuth?


I don't know how you get that with just one hot and the corresponding
neutral connected. For an Edison ckt with a lifted neutral, the light
and outlet could be on the same hot wire and something else could be
getting bright. I assume you fixed the floating neutral bar in #2 before
this occurred.

--
bud--
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage door wizards Douglas[_2_] UK diy 0 July 27th 09 10:35 PM
Any Taig Wizards Bob La Londe Metalworking 3 April 18th 09 02:15 AM
Any alarm wizards ? Colin Wilson UK diy 10 March 3rd 09 02:39 PM
ATTN: electrical wizards, ceiling fan and 3 ways...... Steve Barker[_3_] Home Repair 12 November 13th 07 10:28 PM
Calling all math wizards Keith Young Woodturning 7 October 31st 04 12:20 AM


All times are GMT +1. The time now is 07:35 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"