  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Laziness!

Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. Found a recep in the master bedroom, right next to
the access panel for the bathroom plumbing. Ground was bootlegged to
neutral. There's a cold water pipe NINE INCHES away, and I didn't even
have to break any plaster to get to it! Sheesh.

Also went to replace the toggle switch in the bathroom. It seemed sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. Nope! Apparently someone had skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.

This would be one of those days where I'm really cussing the last
"contractor" to work in here... Only two trips to the store so far today.

Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. Picked up a 10-pack of "spec grade"
receps for $15. That's about what the Orange-Colored Store charges for
a "contractor pack" of the ****ty ones. This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Laziness!

On Nov 21, 3:43�pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. �Found a recep in the master bedroom, right next to
the access panel for the bathroom plumbing. �Ground was bootlegged to
neutral. �There's a cold water pipe NINE INCHES away, and I didn't even
have to break any plaster to get to it! �Sheesh.

Also went to replace the toggle switch in the bathroom. �It seemed sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. �Nope! �Apparently someone had skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.

This would be one of those days where I'm really cussing the last
"contractor" to work in here... �Only two trips to the store so far today.

Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. �Picked up a 10-pack of "spec grade"
receps for $15. �That's about what the Orange-Colored Store charges for
a "contractor pack" of the ****ty ones. �This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.

nate

--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....

you should run a proper ground wire
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Laziness!

On Nov 21, 3:43*pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. *Found a recep in the master bedroom, right next to
the access panel for the bathroom plumbing. *Ground was bootlegged to
neutral. *There's a cold water pipe NINE INCHES away, and I didn't even
have to break any plaster to get to it! *Sheesh.

Also went to replace the toggle switch in the bathroom. *It seemed sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. *Nope! *Apparently someone had skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.

This would be one of those days where I'm really cussing the last
"contractor" to work in here... *Only two trips to the store so far today.

Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. *Picked up a 10-pack of "spec grade"
receps for $15. *That's about what the Orange-Colored Store charges for
a "contractor pack" of the ****ty ones. *This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.

nate

--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


"There's a cold water pipe NINE INCHES away...Sheesh."

I'm ASSuming you made the sure the cold water pipe is actually copper
all the way to "ground" - and that it will remain that way forever,
right?

I'm ASSuming that one of the reasons code prohibits using a water line
as ground is because someone could come along at any time and
transition to PVC or PEX thus opening the ground.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,149
Default Laziness!

wrote:
On Nov 21, 3:43�pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. �Found a recep in the master bedroom, right next to
the access panel for the bathroom plumbing. �Ground was bootlegged to
neutral. �There's a cold water pipe NINE INCHES away, and I didn't even
have to break any plaster to get to it! �Sheesh.

Also went to replace the toggle switch in the bathroom. �It seemed sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. �Nope! �Apparently someone had skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.

This would be one of those days where I'm really cussing the last
"contractor" to work in here... �Only two trips to the store so far today.

Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. �Picked up a 10-pack of "spec grade"
receps for $15. �That's about what the Orange-Colored Store charges for
a "contractor pack" of the ****ty ones. �This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel

code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....

you should run a proper ground wire

Understood about code. But OP should also make sure that pipe is
actually grounded, at least. Even if it doesn't go through the water
heater fitting that typically breaks ground path, some previous owner
may have replaced part of that pipe run with plastic or something, or an
iron/copper junction may cause problems.

--
aem sends...
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Laziness!

wrote:
On Nov 21, 3:43�pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. �Found a recep in the master bedroom, right next to
the access panel for the bathroom plumbing. �Ground was bootlegged to
neutral. �There's a cold water pipe NINE INCHES away, and I didn't even
have to break any plaster to get to it! �Sheesh.

Also went to replace the toggle switch in the bathroom. �It seemed sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. �Nope! �Apparently someone had skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.

This would be one of those days where I'm really cussing the last
"contractor" to work in here... �Only two trips to the store so far today.

Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. �Picked up a 10-pack of "spec grade"
receps for $15. �That's about what the Orange-Colored Store charges for
a "contractor pack" of the ****ty ones. �This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel

code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....

you should run a proper ground wire


Is that a new revision? Last time I checked (which was admittedly a
while ago) when replacing a 2-hole recep with a grounding type with no
available ground (which is essentially what I am doing,) you were
allowed to run a separate conductor to the "nearest point in the
grounding system" or such like.

I agree that in new construction it would be complete BS, but I do have
faith that all the pipe is copper all the way to the point that it
leaves the building, and it is also bonded to ground/neutral at the
panel. Eventually I would like to ground everything properly, and
there's a run of receps in new romex that contains a ground conductor,
so at least those by code HAVE to be grounded (because I connected them
"properly," so technically it doesn't meet code at the moment)

I went ahead and threw a GFI recep in the first box anyway, seeing as
I'm using metal wall plates, but like having grounds where I can to
allow surge protectors to work better. Still breathing a sigh of relief
that I only lost a couple hundred bucks worth of stuff the last time we
got a BIG surge.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Laziness!

aemeijers wrote:
wrote:
On Nov 21, 3:43�pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. �Found a recep in the master bedroom, right
next to
the access panel for the bathroom plumbing. �Ground was bootlegged to
neutral. �There's a cold water pipe NINE INCHES away, and I didn't
even
have to break any plaster to get to it! �Sheesh.

Also went to replace the toggle switch in the bathroom. �It seemed
sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. �Nope! �Apparently someone had
skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.

This would be one of those days where I'm really cussing the last
"contractor" to work in here... �Only two trips to the store so far
today.

Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. �Picked up a 10-pack of "spec grade"
receps for $15. �That's about what the Orange-Colored Store charges
for
a "contractor pack" of the ****ty ones. �This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel

code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....

you should run a proper ground wire

Understood about code. But OP should also make sure that pipe is
actually grounded, at least. Even if it doesn't go through the water
heater fitting that typically breaks ground path, some previous owner
may have replaced part of that pipe run with plastic or something, or an
iron/copper junction may cause problems.

--
aem sends...


I can physically see (and have seen) all of the pipe between the shower
and the foundation, save for the vertical run up the chase through the
kitchen. I have no reason to believe that that is not copper as it
ought to be original to the house.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Laziness!

On Nov 21, 10:40*pm, Nate Nagel wrote:
aemeijers wrote:
wrote:
On Nov 21, 3:43 pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. Found a recep in the master bedroom, right
next to
the access panel for the bathroom plumbing. Ground was bootlegged to
neutral. There's a cold water pipe NINE INCHES away, and I didn't
even
have to break any plaster to get to it! Sheesh.


Also went to replace the toggle switch in the bathroom. It seemed
sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. Nope! Apparently someone had
skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.


This would be one of those days where I'm really cussing the last
"contractor" to work in here... Only two trips to the store so far
today.


Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. Picked up a 10-pack of "spec grade"
receps for $15. That's about what the Orange-Colored Store charges
for
a "contractor pack" of the ****ty ones. This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.


nate


--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....


you should run a proper ground wire

Understood about code. But OP should also make sure that pipe is
actually grounded, at least. Even if it doesn't go through the water
heater fitting that typically breaks ground path, some previous owner
may have replaced part of that pipe run with plastic or something, or an
iron/copper junction may cause problems.


--
aem sends...


I can physically see (and have seen) all of the pipe between the shower
and the foundation, save for the vertical run up the chase through the
kitchen. *I have no reason to believe that that is not copper as it
ought to be original to the house.

nate

--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


I have no reason to believe that that is not copper as it *ought
to be* original to the house.

"Ought to be"...isn't that the same as ASSuming?

You really don't know for sure, do you?

Have you tested the outlets there is a ground?

OK, so ASSuming you have, and it passes, then it's grounded *for
now*.

I guess you can ASSume that you will remember to run a new ground if
you ever break that copper run and transition to PVC or PEX, but I
doubt the next homeowner will. I ASSume that's one of the reasons why
code no longer allows the use of the plumbing system as a ground.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Laziness!

DerbyDad03 wrote:
On Nov 21, 10:40 pm, Nate Nagel wrote:
aemeijers wrote:
wrote:
On Nov 21, 3:43 pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. Found a recep in the master bedroom, right
next to
the access panel for the bathroom plumbing. Ground was bootlegged to
neutral. There's a cold water pipe NINE INCHES away, and I didn't
even
have to break any plaster to get to it! Sheesh.
Also went to replace the toggle switch in the bathroom. It seemed
sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. Nope! Apparently someone had
skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.
This would be one of those days where I'm really cussing the last
"contractor" to work in here... Only two trips to the store so far
today.
Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. Picked up a 10-pack of "spec grade"
receps for $15. That's about what the Orange-Colored Store charges
for
a "contractor pack" of the ****ty ones. This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.
nate
--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel
code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....
you should run a proper ground wire
Understood about code. But OP should also make sure that pipe is
actually grounded, at least. Even if it doesn't go through the water
heater fitting that typically breaks ground path, some previous owner
may have replaced part of that pipe run with plastic or something, or an
iron/copper junction may cause problems.
--
aem sends...

I can physically see (and have seen) all of the pipe between the shower
and the foundation, save for the vertical run up the chase through the
kitchen. I have no reason to believe that that is not copper as it
ought to be original to the house.

nate

--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


I have no reason to believe that that is not copper as it *ought
to be* original to the house.

"Ought to be"...isn't that the same as ASSuming?

You really don't know for sure, do you?


Strictly, no, but I'm 99% certain.


Have you tested the outlets there is a ground?


Yes.

OK, so ASSuming you have, and it passes, then it's grounded *for
now*.

I guess you can ASSume that you will remember to run a new ground if
you ever break that copper run and transition to PVC or PEX, but I
doubt the next homeowner will.


Well, I plan to do it anyway, just not now. I figure a good ground
through copper (and yes, it is bonded to the panel before it leaves the
house) is better than a bootleg. (of course, the only way I could be
*100%* certain is to drain the water to the bathroom, as the water
itself is conductive...)

I ASSume that's one of the reasons why
code no longer allows the use of the plumbing system as a ground.


I've seen this asserted several times in this thread, but that's the
first I've heard of it. Besides, *before* the introduction of grounding
receptacles, if one had a table radio, say, it was common for the
instructions to explicitly state that you should ground the chassis to a
water pipe - and this was back in the day where it was 50/50 whether it
would be copper or iron.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default Laziness!

On 2009-11-22, Nate Nagel wrote:

Is that a new revision? Last time I checked (which was admittedly a
while ago) when replacing a 2-hole recep with a grounding type with no
available ground (which is essentially what I am doing,) you were
allowed to run a separate conductor to the "nearest point in the
grounding system" or such like.


2008 NEC 250.130(C):

(C) Nongrounding Receptacle Replacement or Branch Circuit
Extensions. The equipment grounding conductor of a grounding-type
receptacle or a branch-circuit extension shall be permitted to be
connected to any of the following:

(1) Any accessible point on the grounding electrode system as
described in 250.50

However:

2008 NEC 250.52(A)(1) in part:

Interior metal water piping located more than 1.52 m (5 ft) from the
point of entrance to the building shall not be used as a part of the
grounding electrode system or as a conductor to interconnect
electrodes that are part of the grounding electrode system.

The upshot is that the "neareast point in the grounding system" can be
a water pipe, but only within 5' of the building entrance. Presumably
this is because of the likelihood of future downstream changes in the
piping to a non-conductive material.

Cheers, Wayne


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Laziness!

On Nov 22, 9:32*am, Nate Nagel wrote:
DerbyDad03 wrote:
On Nov 21, 10:40 pm, Nate Nagel wrote:
aemeijers wrote:
wrote:
On Nov 21, 3:43 pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. Found a recep in the master bedroom, right
next to
the access panel for the bathroom plumbing. Ground was bootlegged to
neutral. There's a cold water pipe NINE INCHES away, and I didn't
even
have to break any plaster to get to it! Sheesh.
Also went to replace the toggle switch in the bathroom. It seemed
sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. Nope! Apparently someone had
skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.
This would be one of those days where I'm really cussing the last
"contractor" to work in here... Only two trips to the store so far
today.
Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. Picked up a 10-pack of "spec grade"
receps for $15. That's about what the Orange-Colored Store charges
for
a "contractor pack" of the ****ty ones. This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.
nate
--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel
code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....
you should run a proper ground wire
Understood about code. But OP should also make sure that pipe is
actually grounded, at least. Even if it doesn't go through the water
heater fitting that typically breaks ground path, some previous owner
may have replaced part of that pipe run with plastic or something, or an
iron/copper junction may cause problems.
--
aem sends...
I can physically see (and have seen) all of the pipe between the shower
and the foundation, save for the vertical run up the chase through the
kitchen. *I have no reason to believe that that is not copper as it
ought to be original to the house.


nate


--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


I have no reason to believe that that is not copper as it *ought
to be* original to the house.


"Ought to be"...isn't that the same as ASSuming?


You really don't know for sure, do you?


Strictly, no, but I'm 99% certain.



Have you tested the outlets there is a ground?


Yes.

OK, so ASSuming you have, and it passes, then it's grounded *for
now*.


I guess you can ASSume that you will remember to run a new ground if
you ever break that copper run and transition to PVC or PEX, but I
doubt the next homeowner will.


Well, I plan to do it anyway, just not now. *I figure a good ground
through copper (and yes, it is bonded to the panel before it leaves the
house) is better than a bootleg. *(of course, the only way I could be
*100%* certain is to drain the water to the bathroom, as the water
itself is conductive...)

I ASSume that's one of the reasons why
code no longer allows the use of the plumbing system as a ground.


I've seen this asserted several times in this thread, but that's the
first I've heard of it. *Besides, *before* the introduction of grounding
receptacles, if one had a table radio, say, it was common for the
instructions to explicitly state that you should ground the chassis to a
water pipe - and this was back in the day where it was 50/50 whether it
would be copper or iron.

nate

--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


"it was common for the instructions to explicitly state that you
should ground the chassis to a water pipe"

Are you really trying to use wording from the obsolete instructions
for an old radio to make a modern day point?

Did you ever consider that the reason it's no longer in the
instructions is because the manufacturers have figured out that's it's
dangerous?

They used to have lead in paint. They used have cars without seat
belts. They used to let drunk drivers *drive* home to sleep it off.

I believe that they have since determined that all of those were bad
ideas.

"...code no longer allows the use of the plumbing system as a
ground: I've seen this asserted several times in this thread, but
that's the first I've heard of it."

I'll never claim to be a NEC expert, but some light reading led me to
the following. I stand ready to be corrected if the section of code
I've quoted is not relevant to this discussion.

The second sentence is key.

--- Begin Included Text ---

*250.52 Grounding Electrodes

(A) Electrodes Permitted For Grounding

(1) Metal Underground Water Pipe. A metal underground water pipe in
direct contact with the earth for 3.0 M (10 ft) or more (including any
metal well casing effectively bonded to the pipe) and electrically
continuous (or made electrically continuous by bonding around
insulating joints or insulating pipe) to the points of connection of
the grounding electrode and the bonding conductors.

Interior metal water piping located more than 1.52 m (5 ft) from the
point of entrance to the building shall not be used as a part of the
grounding electrode system or as a conductor to interconnect
electrodes that are part of the grounding electrode system.

--- End Included Text ---

* Stolen without permission from page 104 of the online version of the
2005 NEC.


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2,679
Default Laziness!

DerbyDad03 wrote:
On Nov 22, 9:32 am, Nate Nagel wrote:
DerbyDad03 wrote:
On Nov 21, 10:40 pm, Nate Nagel wrote:
aemeijers wrote:
wrote:
On Nov 21, 3:43 pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. Found a recep in the master bedroom, right
next to
the access panel for the bathroom plumbing. Ground was bootlegged to
neutral. There's a cold water pipe NINE INCHES away, and I didn't
even
have to break any plaster to get to it! Sheesh.
Also went to replace the toggle switch in the bathroom. It seemed
sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. Nope! Apparently someone had
skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.
This would be one of those days where I'm really cussing the last
"contractor" to work in here... Only two trips to the store so far
today.
Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. Picked up a 10-pack of "spec grade"
receps for $15. That's about what the Orange-Colored Store charges
for
a "contractor pack" of the ****ty ones. This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.
nate
--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel
code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....
you should run a proper ground wire
Understood about code. But OP should also make sure that pipe is
actually grounded, at least. Even if it doesn't go through the water
heater fitting that typically breaks ground path, some previous owner
may have replaced part of that pipe run with plastic or something, or an
iron/copper junction may cause problems.
--
aem sends...
I can physically see (and have seen) all of the pipe between the shower
and the foundation, save for the vertical run up the chase through the
kitchen. I have no reason to believe that that is not copper as it
ought to be original to the house.
nate
--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel
I have no reason to believe that that is not copper as it *ought
to be* original to the house.
"Ought to be"...isn't that the same as ASSuming?
You really don't know for sure, do you?

Strictly, no, but I'm 99% certain.



Have you tested the outlets there is a ground?

Yes.

OK, so ASSuming you have, and it passes, then it's grounded *for
now*.
I guess you can ASSume that you will remember to run a new ground if
you ever break that copper run and transition to PVC or PEX, but I
doubt the next homeowner will.

Well, I plan to do it anyway, just not now. I figure a good ground
through copper (and yes, it is bonded to the panel before it leaves the
house) is better than a bootleg. (of course, the only way I could be
*100%* certain is to drain the water to the bathroom, as the water
itself is conductive...)

I ASSume that's one of the reasons why
code no longer allows the use of the plumbing system as a ground.

I've seen this asserted several times in this thread, but that's the
first I've heard of it. Besides, *before* the introduction of grounding
receptacles, if one had a table radio, say, it was common for the
instructions to explicitly state that you should ground the chassis to a
water pipe - and this was back in the day where it was 50/50 whether it
would be copper or iron.

nate

--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


"it was common for the instructions to explicitly state that you
should ground the chassis to a water pipe"

Are you really trying to use wording from the obsolete instructions
for an old radio to make a modern day point?

Did you ever consider that the reason it's no longer in the
instructions is because the manufacturers have figured out that's it's
dangerous?

They used to have lead in paint. They used have cars without seat
belts. They used to let drunk drivers *drive* home to sleep it off.

I believe that they have since determined that all of those were bad
ideas.

"...code no longer allows the use of the plumbing system as a
ground: I've seen this asserted several times in this thread, but
that's the first I've heard of it."

I'll never claim to be a NEC expert, but some light reading led me to
the following. I stand ready to be corrected if the section of code
I've quoted is not relevant to this discussion.

The second sentence is key.

--- Begin Included Text ---

*250.52 Grounding Electrodes

(A) Electrodes Permitted For Grounding

(1) Metal Underground Water Pipe. A metal underground water pipe in
direct contact with the earth for 3.0 M (10 ft) or more (including any
metal well casing effectively bonded to the pipe) and electrically
continuous (or made electrically continuous by bonding around
insulating joints or insulating pipe) to the points of connection of
the grounding electrode and the bonding conductors.

Interior metal water piping located more than 1.52 m (5 ft) from the
point of entrance to the building shall not be used as a part of the
grounding electrode system or as a conductor to interconnect
electrodes that are part of the grounding electrode system.

--- End Included Text ---

* Stolen without permission from page 104 of the online version of the
2005 NEC.


Somehow I missed the 5 feet thing. Oh well. I still feel comfortable
with it as a temporary measure; I'll be doing everything properly soon
enough (there are still four or five receps with no ground at all, plus
several more that are wired with grounded romex and interconnected but
don't have an actual ground anywhere.

In any case my point that whoever did this before was lazy still stands;
I'm guessing it must have been done circa 1980 or earlier. The romex
has a 16AWG ground connection with green insulation rather than bare
14AWG, not sure when that was in common use.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default Laziness!


Nate Nagel wrote:

DerbyDad03 wrote:
On Nov 22, 9:32 am, Nate Nagel wrote:
DerbyDad03 wrote:
On Nov 21, 10:40 pm, Nate Nagel wrote:
aemeijers wrote:
wrote:
On Nov 21, 3:43 pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. Found a recep in the master bedroom, right
next to
the access panel for the bathroom plumbing. Ground was bootlegged to
neutral. There's a cold water pipe NINE INCHES away, and I didn't
even
have to break any plaster to get to it! Sheesh.
Also went to replace the toggle switch in the bathroom. It seemed
sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. Nope! Apparently someone had
skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.
This would be one of those days where I'm really cussing the last
"contractor" to work in here... Only two trips to the store so far
today.
Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. Picked up a 10-pack of "spec grade"
receps for $15. That's about what the Orange-Colored Store charges
for
a "contractor pack" of the ****ty ones. This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.
nate
--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel
code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....
you should run a proper ground wire
Understood about code. But OP should also make sure that pipe is
actually grounded, at least. Even if it doesn't go through the water
heater fitting that typically breaks ground path, some previous owner
may have replaced part of that pipe run with plastic or something, or an
iron/copper junction may cause problems.
--
aem sends...
I can physically see (and have seen) all of the pipe between the shower
and the foundation, save for the vertical run up the chase through the
kitchen. I have no reason to believe that that is not copper as it
ought to be original to the house.
nate
--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel
I have no reason to believe that that is not copper as it *ought
to be* original to the house.
"Ought to be"...isn't that the same as ASSuming?
You really don't know for sure, do you?
Strictly, no, but I'm 99% certain.



Have you tested the outlets there is a ground?
Yes.

OK, so ASSuming you have, and it passes, then it's grounded *for
now*.
I guess you can ASSume that you will remember to run a new ground if
you ever break that copper run and transition to PVC or PEX, but I
doubt the next homeowner will.
Well, I plan to do it anyway, just not now. I figure a good ground
through copper (and yes, it is bonded to the panel before it leaves the
house) is better than a bootleg. (of course, the only way I could be
*100%* certain is to drain the water to the bathroom, as the water
itself is conductive...)

I ASSume that's one of the reasons why
code no longer allows the use of the plumbing system as a ground.
I've seen this asserted several times in this thread, but that's the
first I've heard of it. Besides, *before* the introduction of grounding
receptacles, if one had a table radio, say, it was common for the
instructions to explicitly state that you should ground the chassis to a
water pipe - and this was back in the day where it was 50/50 whether it
would be copper or iron.

nate

--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


"it was common for the instructions to explicitly state that you
should ground the chassis to a water pipe"

Are you really trying to use wording from the obsolete instructions
for an old radio to make a modern day point?

Did you ever consider that the reason it's no longer in the
instructions is because the manufacturers have figured out that's it's
dangerous?

They used to have lead in paint. They used have cars without seat
belts. They used to let drunk drivers *drive* home to sleep it off.

I believe that they have since determined that all of those were bad
ideas.

"...code no longer allows the use of the plumbing system as a
ground: I've seen this asserted several times in this thread, but
that's the first I've heard of it."

I'll never claim to be a NEC expert, but some light reading led me to
the following. I stand ready to be corrected if the section of code
I've quoted is not relevant to this discussion.

The second sentence is key.

--- Begin Included Text ---

*250.52 Grounding Electrodes

(A) Electrodes Permitted For Grounding

(1) Metal Underground Water Pipe. A metal underground water pipe in
direct contact with the earth for 3.0 M (10 ft) or more (including any
metal well casing effectively bonded to the pipe) and electrically
continuous (or made electrically continuous by bonding around
insulating joints or insulating pipe) to the points of connection of
the grounding electrode and the bonding conductors.

Interior metal water piping located more than 1.52 m (5 ft) from the
point of entrance to the building shall not be used as a part of the
grounding electrode system or as a conductor to interconnect
electrodes that are part of the grounding electrode system.

--- End Included Text ---

* Stolen without permission from page 104 of the online version of the
2005 NEC.


Somehow I missed the 5 feet thing. Oh well. I still feel comfortable
with it as a temporary measure; I'll be doing everything properly soon
enough (there are still four or five receps with no ground at all, plus
several more that are wired with grounded romex and interconnected but
don't have an actual ground anywhere.

In any case my point that whoever did this before was lazy still stands;
I'm guessing it must have been done circa 1980 or earlier. The romex
has a 16AWG ground connection with green insulation rather than bare
14AWG, not sure when that was in common use.

nate

--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel


"Grounding electrode" = the ground rods and connection from them to the
service panel. For the purposes of using metal water supply pipe as a
"grounding electrode" this limits the connection to that pipe from the
service panel to within 5' of where the pipe enters the house. This
section does not relate to using the metal water pipe within the house
as a "grounding conductor".
  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,143
Default Laziness!

Pete C. wrote:

"Grounding electrode" = the ground rods and connection from them to the
service panel. For the purposes of using metal water supply pipe as a
"grounding electrode" this limits the connection to that pipe from the
service panel to within 5' of where the pipe enters the house. This
section does not relate to using the metal water pipe within the house
as a "grounding conductor".


And even then, you have to *know* that the pipe that goes out through
the wall is metal. I did not know that ours was polyethylene until it
sprang a leak. It was only then that a section was replaced by a few (4
or 5) feet of copper, which then tied in to the polyethylene again.

Perce
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Laziness!

On Nov 23, 5:11*pm, "Pete C." wrote:
Nate Nagel wrote:

DerbyDad03 wrote:
On Nov 22, 9:32 am, Nate Nagel wrote:
DerbyDad03 wrote:
On Nov 21, 10:40 pm, Nate Nagel wrote:
aemeijers wrote:
wrote:
On Nov 21, 3:43 pm, Nate Nagel wrote:
Replaced the last couple receptacles upstairs before starting to clean
up for the holidays. Found a recep in the master bedroom, right
next to
the access panel for the bathroom plumbing. Ground was bootlegged to
neutral. There's a cold water pipe NINE INCHES away, and I didn't
even
have to break any plaster to get to it! Sheesh.
Also went to replace the toggle switch in the bathroom. It seemed
sunk
a little too far into the wall; I ASSumed it was because the plaster had
broken around the ears - I have a stack of those little metal plates for
rectifying just that problem. Nope! Apparently someone had
skinned the
wall with drywall in the past, and instead of finding a box extender and
some longer screws, they busted the plaster ears off the toggle switch
and let the wall plate hold it in place.
This would be one of those days where I'm really cussing the last
"contractor" to work in here... Only two trips to the store so far
today.
Silver lining: the real electrical supply house's parts counter is
apparently now open on Saturday. Picked up a 10-pack of "spec grade"
receps for $15. That's about what the Orange-Colored Store charges
for
a "contractor pack" of the ****ty ones. This would be about where I
thank the Orange-Colored Store for not having the receps I wanted so I
had to drive past the supply house to get to the real hardware store.
nate
--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel
code prohibits using water line as ground, although no doubt its
better than a bootleg neutral.....
you should run a proper ground wire
Understood about code. But OP should also make sure that pipe is
actually grounded, at least. Even if it doesn't go through the water
heater fitting that typically breaks ground path, some previous owner
may have replaced part of that pipe run with plastic or something, or an
iron/copper junction may cause problems.
--
aem sends...
I can physically see (and have seen) all of the pipe between the shower
and the foundation, save for the vertical run up the chase through the
kitchen. *I have no reason to believe that that is not copper as it
ought to be original to the house.
nate
--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel
I have no reason to believe that that is not copper as it *ought
to be* original to the house.
"Ought to be"...isn't that the same as ASSuming?
You really don't know for sure, do you?
Strictly, no, but I'm 99% certain.


Have you tested the outlets there is a ground?
Yes.


OK, so ASSuming you have, and it passes, then it's grounded *for
now*.
I guess you can ASSume that you will remember to run a new ground if
you ever break that copper run and transition to PVC or PEX, but I
doubt the next homeowner will.
Well, I plan to do it anyway, just not now. *I figure a good ground
through copper (and yes, it is bonded to the panel before it leaves the
house) is better than a bootleg. *(of course, the only way I could be
*100%* certain is to drain the water to the bathroom, as the water
itself is conductive...)


I ASSume that's one of the reasons why
code no longer allows the use of the plumbing system as a ground.
I've seen this asserted several times in this thread, but that's the
first I've heard of it. *Besides, *before* the introduction of grounding
receptacles, if one had a table radio, say, it was common for the
instructions to explicitly state that you should ground the chassis to a
water pipe - and this was back in the day where it was 50/50 whether it
would be copper or iron.


nate


--
replace "roosters" with "cox" to reply.http://members.cox.net/njnagel


"it was common for the instructions to explicitly state that you
should ground the chassis to a water pipe"


Are you really trying to use wording from the obsolete instructions
for an old radio to make a modern day point?


Did you ever consider that the reason it's no longer in the
instructions is because the manufacturers have figured out that's it's
dangerous?


They used to have lead in paint. They used have cars without seat
belts. They used to let drunk drivers *drive* home to sleep it off.


I believe that they have since determined that all of those were bad
ideas.


"...code no longer allows the use of the plumbing system as a
ground: *I've seen this asserted several times in this thread, but
that's the first I've heard of it."


I'll never claim to be a NEC expert, but some light reading led me to
the following. I stand ready to be corrected if the section of code
I've quoted is not relevant to this discussion.


The second sentence is key.


--- Begin Included Text ---


*250.52 Grounding Electrodes


(A) Electrodes Permitted For Grounding


(1) Metal Underground Water Pipe. A metal underground water pipe in
direct contact with the earth for 3.0 M (10 ft) or more (including any
metal well casing effectively bonded to the pipe) and electrically
continuous (or made electrically continuous by bonding around
insulating joints or insulating pipe) to the points of connection of
the grounding electrode and the bonding conductors.


Interior metal water piping located more than 1.52 m (5 ft) from the
point of entrance to the building shall not be used as a part of the
grounding electrode system or as a conductor to interconnect
electrodes that are part of the grounding electrode system.


--- End Included Text ---


* Stolen without permission from page 104 of the online version of the
2005 NEC.


Somehow I missed the 5 feet thing. *Oh well. *I still feel comfortable
with it as a temporary measure; I'll be doing everything properly soon
enough (there are still four or five receps with no ground at all, plus
several more that are wired with grounded romex and interconnected but
don't have an actual ground anywhere.


In any case my point that whoever did this before was lazy still stands;
I'm guessing it must have been done circa 1980 or earlier. *The romex
has a 16AWG ground connection with green insulation rather than bare
14AWG, not sure when that was in common use.


nate


--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel


"Grounding electrode" = the ground rods and connection from them to the
service panel. For the purposes of using metal water supply pipe as a
"grounding electrode" this limits the connection to that pipe from the
service panel to within 5' of where the pipe enters the house. This
section does not relate to using the metal water pipe within the house
as a "grounding conductor".- Hide quoted text -

- Show quoted text -


So is there a section that relates to using the metal water pipe
within the house as a "grounding conductor"?

  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 634
Default Laziness!

On 2009-11-23, Pete C. wrote:

"Grounding electrode" = the ground rods and connection from them to
the service panel. For the purposes of using metal water supply pipe
as a "grounding electrode" this limits the connection to that pipe
from the service panel to within 5' of where the pipe enters the
house. This section does not relate to using the metal water pipe
within the house as a "grounding conductor".


Correct. You may not use the metal water pipe as a grounding
conductor, since it is not listed as an acceptable grounding conductor
in 2008 NEC 250.118 "Types of Equipment Grounding Conductors".
However, you may terminate your retrofitted grounding conductor at a
grounding electrode, e.g. the metal water service within 5' of the
building entrance.

Cheers, Wayne
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
London Underground shoes. Laziness on my part Stuart Noble UK diy 6 January 13th 09 06:01 PM


All times are GMT +1. The time now is 07:14 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"