Hello,

I have a Crown oil boiler and Crown megastor 40 gallon indirect water
heater. The system has 3 zone valves but a single circulator (water
heater is on zone 2).

Today we had only lukewarm water coming from the faucets. The zone
valve for this zone is open, the boiler is working and there is pipe
from the boiler to the water heater is hot. But the pipe coming from
the water heater returning to the boiler does not get hot.

The other two zones are getting heat so the circulator seems to be
working properly.

This problem has happened several times in the past few weeks and it
seems to start working again for a while.

Has anyone had this type of problem? I appreciate any advice that you
can offer to me.

Thank you in advance,

Scott



  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Indirect water heater question


wrote in message
...
Hello,

I have a Crown oil boiler and Crown megastor 40 gallon indirect water
heater. The system has 3 zone valves but a single circulator (water
heater is on zone 2).

Today we had only lukewarm water coming from the faucets. The zone
valve for this zone is open, the boiler is working and there is pipe
from the boiler to the water heater is hot. But the pipe coming from
the water heater returning to the boiler does not get hot.

The other two zones are getting heat so the circulator seems to be
working properly.

This problem has happened several times in the past few weeks and it
seems to start working again for a while.

Has anyone had this type of problem? I appreciate any advice that you
can offer to me.

Thank you in advance,

Scott

Most modern zone valves have a motor circuit, and an end switch. When
power is applied to the valve's motor, it cranks open and as it reaches
it's fully opened position, a cam closes the circuit on the end switch.
The end switch circuit typically turns on the circulator, and depending
upon the type of boiler controls, it may turn on the boiler as well. Most
zone valves have a lever to open them manually, however doing this doesn't
open the valve far enough to close the end switch. In some cases, a
damaged or worn zone valve will electrically open, but not close the end
switch and turn on the circulator. If you can identify the valve, I can
tell you how to prove the end switch circuit



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Indirect water heater question

On Sat, 22 Nov 2008 07:43:12 -0500, "RBM" wrote:


wrote in message
.. .
Hello,

I have a Crown oil boiler and Crown megastor 40 gallon indirect water
heater. The system has 3 zone valves but a single circulator (water
heater is on zone 2).

Today we had only lukewarm water coming from the faucets. The zone
valve for this zone is open, the boiler is working and there is pipe
from the boiler to the water heater is hot. But the pipe coming from
the water heater returning to the boiler does not get hot.

The other two zones are getting heat so the circulator seems to be
working properly.

This problem has happened several times in the past few weeks and it
seems to start working again for a while.

Has anyone had this type of problem? I appreciate any advice that you
can offer to me.

Thank you in advance,

Scott

Most modern zone valves have a motor circuit, and an end switch. When
power is applied to the valve's motor, it cranks open and as it reaches
it's fully opened position, a cam closes the circuit on the end switch.
The end switch circuit typically turns on the circulator, and depending
upon the type of boiler controls, it may turn on the boiler as well. Most
zone valves have a lever to open them manually, however doing this doesn't
open the valve far enough to close the end switch. In some cases, a
damaged or worn zone valve will electrically open, but not close the end
switch and turn on the circulator. If you can identify the valve, I can
tell you how to prove the end switch circuit




The zone valves are Honeywell model YHV8043E1012. Thank you for your
reply and advice.

Scott

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Indirect water heater question


wrote in message
...
On Sat, 22 Nov 2008 07:43:12 -0500, "RBM" wrote:


wrote in message
. ..
Hello,

I have a Crown oil boiler and Crown megastor 40 gallon indirect water
heater. The system has 3 zone valves but a single circulator (water
heater is on zone 2).

Today we had only lukewarm water coming from the faucets. The zone
valve for this zone is open, the boiler is working and there is pipe
from the boiler to the water heater is hot. But the pipe coming from
the water heater returning to the boiler does not get hot.

The other two zones are getting heat so the circulator seems to be
working properly.

This problem has happened several times in the past few weeks and it
seems to start working again for a while.

Has anyone had this type of problem? I appreciate any advice that you
can offer to me.

Thank you in advance,

Scott

Most modern zone valves have a motor circuit, and an end switch. When
power is applied to the valve's motor, it cranks open and as it reaches
it's fully opened position, a cam closes the circuit on the end switch.
The end switch circuit typically turns on the circulator, and depending
upon the type of boiler controls, it may turn on the boiler as well.
Most
zone valves have a lever to open them manually, however doing this
doesn't
open the valve far enough to close the end switch. In some cases, a
damaged or worn zone valve will electrically open, but not close the end
switch and turn on the circulator. If you can identify the valve, I can
tell you how to prove the end switch circuit




The zone valves are Honeywell model YHV8043E1012. Thank you for your
reply and advice.

Scott



OK, sounds like typical Honeywell valve with two yellow wires and two red
wires. The red wires are the ones for the end switch. Typical zone valve
wiring is a birds nest mess, so be careful not to pull apart any splices
while you examine it. What you will find is that the red wires from all the
zone valves go together and are spliced to one pair of wires that go to a
relay box, probably on the face of the boiler, above the burner, and are
attached to the "T T " terminals in the upper left hand corner of the box.
Trace out the two red wires from the offending zone valve, and be sure they
are securely spliced to the others. Turn up the aquastat on the indirect,
it's zone valve should open, then the circulator should kick on. If the zone
valve opens, but the circulator doesn't kick on, strip back a little
insulation on that valves two red wires and touch the two wires together.
This is 24 volts , so no need to worry about getting fried. If, when you
touch the two reds together, the circulator comes on, you have a problem in
the valve, with it's end switch. The entire head of the valve is
replaceable, or you can possibly just get a new switch. Personally, I'd get
the entire head.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Indirect water heater question

On Sat, 22 Nov 2008 12:48:10 -0500, "RBM" wrote:


wrote in message
.. .
On Sat, 22 Nov 2008 07:43:12 -0500, "RBM" wrote:


wrote in message
...
Hello,

I have a Crown oil boiler and Crown megastor 40 gallon indirect water
heater. The system has 3 zone valves but a single circulator (water
heater is on zone 2).

Today we had only lukewarm water coming from the faucets. The zone
valve for this zone is open, the boiler is working and there is pipe
from the boiler to the water heater is hot. But the pipe coming from
the water heater returning to the boiler does not get hot.

The other two zones are getting heat so the circulator seems to be
working properly.

This problem has happened several times in the past few weeks and it
seems to start working again for a while.

Has anyone had this type of problem? I appreciate any advice that you
can offer to me.

Thank you in advance,

Scott

Most modern zone valves have a motor circuit, and an end switch. When
power is applied to the valve's motor, it cranks open and as it reaches
it's fully opened position, a cam closes the circuit on the end switch.
The end switch circuit typically turns on the circulator, and depending
upon the type of boiler controls, it may turn on the boiler as well.
Most
zone valves have a lever to open them manually, however doing this
doesn't
open the valve far enough to close the end switch. In some cases, a
damaged or worn zone valve will electrically open, but not close the end
switch and turn on the circulator. If you can identify the valve, I can
tell you how to prove the end switch circuit



The zone valves are Honeywell model YHV8043E1012. Thank you for your
reply and advice.

Scott



OK, sounds like typical Honeywell valve with two yellow wires and two red
wires. The red wires are the ones for the end switch. Typical zone valve
wiring is a birds nest mess, so be careful not to pull apart any splices
while you examine it. What you will find is that the red wires from all the
zone valves go together and are spliced to one pair of wires that go to a
relay box, probably on the face of the boiler, above the burner, and are
attached to the "T T " terminals in the upper left hand corner of the box.
Trace out the two red wires from the offending zone valve, and be sure they
are securely spliced to the others. Turn up the aquastat on the indirect,
it's zone valve should open, then the circulator should kick on. If the zone
valve opens, but the circulator doesn't kick on, strip back a little
insulation on that valves two red wires and touch the two wires together.
This is 24 volts , so no need to worry about getting fried. If, when you
touch the two reds together, the circulator comes on, you have a problem in
the valve, with it's end switch. The entire head of the valve is
replaceable, or you can possibly just get a new switch. Personally, I'd get
the entire head.



I checked the red wires and they were pretty secure with wirenuts.
I turned up the temperature on the front of the aquastat on the water
heater. The boiler kicked on and the zone valve opened for this zone.
Once the boiler turned off, I could hear water moving through the
circulator. The pipe below the zone valve was hot, above the zone
valve was also hot. A the water heater the pipe in from the boiler
was hot, but the pipe coming out of the water heater does not get hot.
None of the pipes on the return side get hot.

I also turned up the thermostat in one of the heat zones upstairs and
its zone valve opened too. So both its zone valve and the water
heater zone valve were now open. The circulator was still going and
within a minute or two, the pipes on the return side of the heat zone
was hot, but the return pipes for the water heater were still cool.

Do you think it could be air in the pipes inside the water heater? Or
is there someting else that could be wrong with the water heater or
another part of the system?

Thanks again for your advice.

Scott



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Indirect water heater question


wrote in message
...
On Sat, 22 Nov 2008 12:48:10 -0500, "RBM" wrote:


wrote in message
. ..
On Sat, 22 Nov 2008 07:43:12 -0500, "RBM" wrote:


wrote in message
m...
Hello,

I have a Crown oil boiler and Crown megastor 40 gallon indirect water
heater. The system has 3 zone valves but a single circulator (water
heater is on zone 2).

Today we had only lukewarm water coming from the faucets. The zone
valve for this zone is open, the boiler is working and there is pipe
from the boiler to the water heater is hot. But the pipe coming from
the water heater returning to the boiler does not get hot.

The other two zones are getting heat so the circulator seems to be
working properly.

This problem has happened several times in the past few weeks and it
seems to start working again for a while.

Has anyone had this type of problem? I appreciate any advice that you
can offer to me.

Thank you in advance,

Scott

Most modern zone valves have a motor circuit, and an end switch. When
power is applied to the valve's motor, it cranks open and as it
reaches
it's fully opened position, a cam closes the circuit on the end
switch.
The end switch circuit typically turns on the circulator, and
depending
upon the type of boiler controls, it may turn on the boiler as well.
Most
zone valves have a lever to open them manually, however doing this
doesn't
open the valve far enough to close the end switch. In some cases, a
damaged or worn zone valve will electrically open, but not close the
end
switch and turn on the circulator. If you can identify the valve, I
can
tell you how to prove the end switch circuit



The zone valves are Honeywell model YHV8043E1012. Thank you for your
reply and advice.

Scott



OK, sounds like typical Honeywell valve with two yellow wires and two red
wires. The red wires are the ones for the end switch. Typical zone valve
wiring is a birds nest mess, so be careful not to pull apart any splices
while you examine it. What you will find is that the red wires from all
the
zone valves go together and are spliced to one pair of wires that go to a
relay box, probably on the face of the boiler, above the burner, and are
attached to the "T T " terminals in the upper left hand corner of the box.
Trace out the two red wires from the offending zone valve, and be sure
they
are securely spliced to the others. Turn up the aquastat on the indirect,
it's zone valve should open, then the circulator should kick on. If the
zone
valve opens, but the circulator doesn't kick on, strip back a little
insulation on that valves two red wires and touch the two wires together.
This is 24 volts , so no need to worry about getting fried. If, when you
touch the two reds together, the circulator comes on, you have a problem
in
the valve, with it's end switch. The entire head of the valve is
replaceable, or you can possibly just get a new switch. Personally, I'd
get
the entire head.



I checked the red wires and they were pretty secure with wirenuts.
I turned up the temperature on the front of the aquastat on the water
heater. The boiler kicked on and the zone valve opened for this zone.
Once the boiler turned off, I could hear water moving through the
circulator. The pipe below the zone valve was hot, above the zone
valve was also hot. A the water heater the pipe in from the boiler
was hot, but the pipe coming out of the water heater does not get hot.
None of the pipes on the return side get hot.

I also turned up the thermostat in one of the heat zones upstairs and
its zone valve opened too. So both its zone valve and the water
heater zone valve were now open. The circulator was still going and
within a minute or two, the pipes on the return side of the heat zone
was hot, but the return pipes for the water heater were still cool.

Do you think it could be air in the pipes inside the water heater? Or
is there someting else that could be wrong with the water heater or
another part of the system?

Thanks again for your advice.

Scott


With the heating zone turning on and confirming that the circulator is
functioning, it narrows it down to two possibilities, an obstruction in the
indirect's hot water loop, or air. I would have the system purged, which
will either eliminate the air or show up the obstruction, which can be
solder logged in the zone valve or a broken valve



  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4
Default Indirect water heater question

On Sun, 23 Nov 2008 07:14:05 -0500, "RBM" wrote:


wrote in message
.. .
On Sat, 22 Nov 2008 12:48:10 -0500, "RBM" wrote:


wrote in message
...
On Sat, 22 Nov 2008 07:43:12 -0500, "RBM" wrote:


wrote in message
om...
Hello,

I have a Crown oil boiler and Crown megastor 40 gallon indirect water
heater. The system has 3 zone valves but a single circulator (water
heater is on zone 2).

Today we had only lukewarm water coming from the faucets. The zone
valve for this zone is open, the boiler is working and there is pipe
from the boiler to the water heater is hot. But the pipe coming from
the water heater returning to the boiler does not get hot.

The other two zones are getting heat so the circulator seems to be
working properly.

This problem has happened several times in the past few weeks and it
seems to start working again for a while.

Has anyone had this type of problem? I appreciate any advice that you
can offer to me.

Thank you in advance,

Scott

Most modern zone valves have a motor circuit, and an end switch. When
power is applied to the valve's motor, it cranks open and as it
reaches
it's fully opened position, a cam closes the circuit on the end
switch.
The end switch circuit typically turns on the circulator, and
depending
upon the type of boiler controls, it may turn on the boiler as well.
Most
zone valves have a lever to open them manually, however doing this
doesn't
open the valve far enough to close the end switch. In some cases, a
damaged or worn zone valve will electrically open, but not close the
end
switch and turn on the circulator. If you can identify the valve, I
can
tell you how to prove the end switch circuit



The zone valves are Honeywell model YHV8043E1012. Thank you for your
reply and advice.

Scott


OK, sounds like typical Honeywell valve with two yellow wires and two red
wires. The red wires are the ones for the end switch. Typical zone valve
wiring is a birds nest mess, so be careful not to pull apart any splices
while you examine it. What you will find is that the red wires from all
the
zone valves go together and are spliced to one pair of wires that go to a
relay box, probably on the face of the boiler, above the burner, and are
attached to the "T T " terminals in the upper left hand corner of the box.
Trace out the two red wires from the offending zone valve, and be sure
they
are securely spliced to the others. Turn up the aquastat on the indirect,
it's zone valve should open, then the circulator should kick on. If the
zone
valve opens, but the circulator doesn't kick on, strip back a little
insulation on that valves two red wires and touch the two wires together.
This is 24 volts , so no need to worry about getting fried. If, when you
touch the two reds together, the circulator comes on, you have a problem
in
the valve, with it's end switch. The entire head of the valve is
replaceable, or you can possibly just get a new switch. Personally, I'd
get
the entire head.



I checked the red wires and they were pretty secure with wirenuts.
I turned up the temperature on the front of the aquastat on the water
heater. The boiler kicked on and the zone valve opened for this zone.
Once the boiler turned off, I could hear water moving through the
circulator. The pipe below the zone valve was hot, above the zone
valve was also hot. A the water heater the pipe in from the boiler
was hot, but the pipe coming out of the water heater does not get hot.
None of the pipes on the return side get hot.

I also turned up the thermostat in one of the heat zones upstairs and
its zone valve opened too. So both its zone valve and the water
heater zone valve were now open. The circulator was still going and
within a minute or two, the pipes on the return side of the heat zone
was hot, but the return pipes for the water heater were still cool.

Do you think it could be air in the pipes inside the water heater? Or
is there someting else that could be wrong with the water heater or
another part of the system?

Thanks again for your advice.

Scott


With the heating zone turning on and confirming that the circulator is
functioning, it narrows it down to two possibilities, an obstruction in the
indirect's hot water loop, or air. I would have the system purged, which
will either eliminate the air or show up the obstruction, which can be
solder logged in the zone valve or a broken valve




Hi,

I wanted to close the loop on this post. I tried to purge the system
and checked for physical obstructions in the water heater coil, but
still had the problem. I was stumped so I had a plumber over and the
problem turned out to be the aquastat on the boiler.

The aquastat was firing the boiler but wasn't turning on the
circulator pump.

I had ruled out the circulator pump because it's shared between 3
zones and the other 2 zones were working.

The plumber told me that those zones could have been getting heat by
gravity because those zones are on the ground floor, one floor above
the boiler. The water heater is in the basement with the boiler so
the water heated by the boiler was getting to the water heater inlet,
but didn't have enough momentum to circulate through again.

I had no idea that this was even possible, but after the aquastat was
changed, the water started to circulate normally and both the inlet
and outlet pipes on the water heater got hot immediately and we had
hot water in a half hour.

Gravity feed to the 2 heating zones upstairs isn't something I would
have ever considered as a possiblity. It's been so cold here the last
few weeks -- in the teens at night and 20s during the day -- and heat
upstairs has been working fine. All while the circulator pump was
off!

So I'm writing back to give a resolution for this post so others will
benefit from my experience as I have from so many posts in this group.
And thank you RBM for your advice. I'm sure that had you been here or
I'd given you more detail during our thread, you'd have come to this
conclusion. I certainly learned a lot more about the whole heating
system.

Thank you!

Scott



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Indirect Water Heater Question? Bob M Home Repair 1 September 29th 08 05:21 AM
Indirect Fired Hot Water Heater Malfunction [email protected] Home Repair 3 February 21st 07 06:37 AM
Smelly water from indirect-fired water heater Johnny Thunders Jr. Home Repair 2 June 6th 06 02:11 AM
Indirect water heater questions Steve Home Repair 5 March 13th 06 11:25 PM
Indirect water heater questions Steve Home Ownership 4 March 13th 06 11:25 PM


All times are GMT +1. The time now is 04:36 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"