Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
We had a leak in the master bath (upstairs) and so now in the midst of
a complete bathroom remodel. Electrical question.... The old bathroom had two circuits flowing into it - the first (15A, 14/2 wire) connected to one outlet (not GFI) and then hopped to another bathroom where it connected to an outlet there. The other circuit was sort of normal lighting/fixtures/15A/14-2 wiring, etc. My question is with the outlets. I want to A) make sure they're GFI, B) safe as they need to be, and C) add another. With the remodel & current code do I have to change the whole circuit to 20A? Which means I'd have to pull all the existing 14/2 cabling and replace with 12/2? If I do this, then what is the likelihood of me being able to disconnect the cable at the breaker box, and then pulling the cable up two floors to the attic through the wall? Is it likely stapled inside the wall? I don't want to damage the 4 or 5 other cables running down the same hole through top/bottom plates. Is a better bet for me to just disconnect the 15A circuit breaker & tie off that cable so it's dead. Then add a fresh 20A circuit breaker, and go in the crawl space (very accessible), run the cable down, then up the HVAC chase to the attic? I think the run length would actually be about the same. |
#2
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
On May 29, 2:41*pm, CB wrote:
We had a leak in the master bath (upstairs) and so now in the midst of a complete bathroom remodel. *Electrical question.... The old bathroom had two circuits flowing into it - the first (15A, 14/2 wire) connected to one outlet (not GFI) and then hopped to another bathroom where it connected to an outlet there. *The other circuit was sort of normal lighting/fixtures/15A/14-2 wiring, etc. My question is with the outlets. *I want to A) make sure they're GFI, B) safe as they need to be, and C) add another. *With the remodel & current code do I have to change the whole circuit to 20A? *Which means I'd have to pull all the existing 14/2 cabling and replace with 12/2? If I do this, then what is the likelihood of me being able to disconnect the cable at the breaker box, and then pulling the cable up two floors to the attic through the wall? *Is it likely stapled inside the wall? *I don't want to damage the 4 or 5 other cables running down the same hole through top/bottom plates. Is a better bet for me to just disconnect the 15A circuit breaker & tie off that cable so it's dead. *Then add a fresh 20A circuit breaker, and go in the crawl space (very accessible), run the cable down, then up the HVAC chase to the attic? *I think the run length would actually be about the same. If this is a new remodel, and walls are going to be open, you might as well run new 20A. Don't bother trying to use the old 15A wire as a drag line, just cap it off in the panel. I believe code now calls for 20A in a bathroom. If you are going to have a fan/light/heat combo unit, that alone needs its own circuit It would be different if you had to tear walls open if you have to run a new line, but since you have access to run cables, might as well do it. I would also like to add if you are putting a fan/light combo inside the shower/tub area, it must be GFI protected. You can just get the feed off of the GFI outlet to accomplish this. |
#3
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
If this is a new remodel, and walls are going to be open, you might as well run new 20A. Don't bother trying to use the old 15A wire as a drag line, just cap it off in the panel. I believe code now calls for 20A in a bathroom. If you are going to have a fan/light/heat combo unit, that alone needs its own circuit It would be different if you had to tear walls open if you have to run a new line, but since you have access to run cables, might as well do it. I would also like to add if you are putting a fan/light combo inside the shower/tub area, it must be GFI protected. You can just get the feed off of the GFI outlet to accomplish this. The bathroom walls are definitely out - I stare at insulation and studs every night when I get home - ugh. I may be missing something - if I am please forgive me. You said the fan/light combo must be on a dedicated circuit, but then you said that I could catch the GFI for the fan/light off the outlet run, implying that now it's on the same circuit as the outlets. And just wanted to confirm - I shouldn't mess with trying to fish the 15A cable out and then fish a 20A wire down via the attic? Did you think that I should run across the crawl space and then up the HVAC chase two floors? |
#4
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
"CB" wrote in message ... If this is a new remodel, and walls are going to be open, you might as well run new 20A. Don't bother trying to use the old 15A wire as a drag line, just cap it off in the panel. I believe code now calls for 20A in a bathroom. If you are going to have a fan/light/heat combo unit, that alone needs its own circuit It would be different if you had to tear walls open if you have to run a new line, but since you have access to run cables, might as well do it. I would also like to add if you are putting a fan/light combo inside the shower/tub area, it must be GFI protected. You can just get the feed off of the GFI outlet to accomplish this. The bathroom walls are definitely out - I stare at insulation and studs every night when I get home - ugh. I may be missing something - if I am please forgive me. You said the fan/light combo must be on a dedicated circuit, but then you said that I could catch the GFI for the fan/light off the outlet run, implying that now it's on the same circuit as the outlets. And just wanted to confirm - I shouldn't mess with trying to fish the 15A cable out and then fish a 20A wire down via the attic? Did you think that I should run across the crawl space and then up the HVAC chase two floors? First of all, it would make little sense to have the existing outlet circuit daisy chained from one bathroom to another unless it was in fact protected by a GFCI device upstream of these outlets. This was done commonly in the 80's. If you want to run new circuits to upgrade the bathroom, the easiest thing to do would be to run one 20 amp circuit and just use it for the outlets in the renovated bath. You can use the existing lighting circuit for any new lights and fans, etc. provided you're not adding any electric heat or Jacuzzi, and things of that nature. You cannot disconnect either of the existing circuits at the panel, as they are feeding things other that the renovated bathroom, so you have to locate junction boxes in some accessible place to splice those circuits through, to wherever they're going. |
#5
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
First of all, it would make little sense to have the existing outlet circuit daisy chained from one bathroom to another unless it was in fact protected by a GFCI device upstream of these outlets. This was done commonly in the 80's. If you want to run new circuits to upgrade the bathroom, the easiest thing to do would be to run one 20 amp circuit and just use it for the outlets in the renovated bath. You can use the existing lighting circuit for any new lights and fans, etc. provided you're not adding any electric heat or Jacuzzi, and things of that nature. You cannot disconnect either of the existing circuits at the panel, as they are feeding things other that the renovated bathroom, so you have to locate junction boxes in some accessible place to splice those circuits through, to wherever they're going. I currently have one 15A circuit doing the bath outlets (for both baths) and another 15A circuit doing lights for that bathroom, a closet, and another bathroom. Tell me if this sounds reasonable: 1) leave the existing 15A circuit that currently powers the existing lights, etc. and remove bathroom B and closet from that circuit 2) leave the existing 15A circuit that currently powers the outlets, and in the attic, cut the line to remove the outlets from the circuit and splice/branch out to do the second bathroom's lights (and maybe a closet light?) 3) run new 20A circuit to 2 bathroom outlets in bath A, and then over to 1 bath outlet in bath B, with GFI on the 1st outlet in the run Does this sound logical? |
#6
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
"CB" wrote in message ... First of all, it would make little sense to have the existing outlet circuit daisy chained from one bathroom to another unless it was in fact protected by a GFCI device upstream of these outlets. This was done commonly in the 80's. If you want to run new circuits to upgrade the bathroom, the easiest thing to do would be to run one 20 amp circuit and just use it for the outlets in the renovated bath. You can use the existing lighting circuit for any new lights and fans, etc. provided you're not adding any electric heat or Jacuzzi, and things of that nature. You cannot disconnect either of the existing circuits at the panel, as they are feeding things other that the renovated bathroom, so you have to locate junction boxes in some accessible place to splice those circuits through, to wherever they're going. I currently have one 15A circuit doing the bath outlets (for both baths) and another 15A circuit doing lights for that bathroom, a closet, and another bathroom. Tell me if this sounds reasonable: 1) leave the existing 15A circuit that currently powers the existing lights, etc. and remove bathroom B and closet from that circuit 2) leave the existing 15A circuit that currently powers the outlets, and in the attic, cut the line to remove the outlets from the circuit and splice/branch out to do the second bathroom's lights (and maybe a closet light?) 3) run new 20A circuit to 2 bathroom outlets in bath A, and then over to 1 bath outlet in bath B, with GFI on the 1st outlet in the run Does this sound logical? Perfectly logical, and NEC legal |
#7
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
I may be missing something - if I am please forgive me. *You said the
fan/light combo must be on a dedicated circuit, but then you said that I could catch the GFI for the fan/light off the outlet run, implying that now it's on the same circuit as the outlets. If you have just a fan/light combo, it does not need its own circuit. If you have a fan/light/heat combo, then you do. Just the heat part of it will use at least 10-12 amps. Whatever you choose, if its going to be inside the shower area it needs to be GFI protected. If you have the fan/light just grab it off the GFI outlet. If it has heat also, run a dedicated line and put it on a GFI breaker. If its outside the shower, it does not need GFI protection. And just wanted to confirm - I shouldn't mess with trying to fish the 15A cable out and then fish a 20A wire down via the attic? *Did you think that I should run across the crawl space and then up the HVAC chase two floors? The 15A cable might be stapled, unless you know for sure you can pull it than go ahead. Otherwisw just run in the crawl space then up the chase. |
#8
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
"Mikepier" wrote in message ... I may be missing something - if I am please forgive me. You said the fan/light combo must be on a dedicated circuit, but then you said that I could catch the GFI for the fan/light off the outlet run, implying that now it's on the same circuit as the outlets. If you have just a fan/light combo, it does not need its own circuit. If you have a fan/light/heat combo, then you do. Just the heat part of it will use at least 10-12 amps. Whatever you choose, if its going to be inside the shower area it needs to be GFI protected. If you have the fan/light just grab it off the GFI outlet. If it has heat also, run a dedicated line and put it on a GFI breaker. If its outside the shower, it does not need GFI protection. And just wanted to confirm - I shouldn't mess with trying to fish the 15A cable out and then fish a 20A wire down via the attic? Did you think that I should run across the crawl space and then up the HVAC chase two floors? The 15A cable might be stapled, unless you know for sure you can pull it than go ahead. Otherwisw just run in the crawl space then up the chase. What you're suggesting regarding the GFCI protection for a fan over a tub or shower, is only acceptible if he's wiring one bathroom entirely on a 20 amp circuit. If, as he suggested,he feeds multiple bathroom receptacle outlets with one 20 amp circuit, no lighting, fans, or anything else, except other bathroom receptacle outlets can go on that circuit |
#9
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
Keep 'em coming - this good info.......glad to know the A/C chase is
legal.... |
#10
Posted to alt.home.repair
|
|||
|
|||
Bathroom remodel - keep 15A/14AWG or go to 20A/12AWG?
What you're suggesting regarding the GFCI protection for a fan over a tub or
shower, is only acceptible if he's wiring one bathroom entirely on a 20 amp circuit. If, as he suggested,he feeds *multiple bathroom receptacle outlets with one 20 amp circuit, no lighting, fans, or anything else, except other bathroom receptacle outlets can go on that circuit Correct. I was assuming he was running 2 seperate feeds for each bathroom. |