I have heard in the trade as a general rule if you are using #12 wire
for a 20A circuit you should go to #10 if the run is over 100 ft.

The fan #14 or #12 thread prompted me to just do a quick check at one
of the voltage drop web pages.

http://www.csgnetwork.com/voltagedropcalc.html

If you use this web page and try using 16A which would be the max on a
20A circuit you get 5% voltage drop in just the branch circuit.

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,375
Default Voltage drop

In article , Terry wrote:

If you use this web page and try using 16A which would be the max on a
20A circuit you get 5% voltage drop in just the branch circuit.


The maximum load on a 20A circuit is... any guesses? ...wait for it... 20A.

16A is the maximum *continuous* load on a 20A circuit.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.
  #3   Report Post  
Posted to alt.home.repair
M Q M Q is offline
external usenet poster
 
Posts: 257
Default Voltage drop



Terry wrote:

I have heard in the trade as a general rule if you are using #12 wire
for a 20A circuit you should go to #10 if the run is over 100 ft.

The fan #14 or #12 thread prompted me to just do a quick check at one
of the voltage drop web pages.

http://www.csgnetwork.com/voltagedropcalc.html

If you use this web page and try using 16A which would be the max on a
20A circuit you get 5% voltage drop in just the branch circuit.


My copy of NEC (1990 -- somewhat obsolete) only mentions voltage drop
in FPN's (non-manditory notes). It recomends a max of 3% on branch
circuits "at the farthest outlet of power, heating, or lighting loads",
and a max of 5% on both feeder and branch circuit.
10ga copper is about 1.25 ohms / 1000', and
12ga copper is about 2 ohms / 1000', and
14ga copper is about 3.1 ohms / 1000'

3% of 120v is 3.6v.
100' of 12ga is actually 200' (hot & neutral) is .4 ohms
so 3.6/.4 = 9 amps for 3% voltage drop at 100'.
10 ga. will give you 14.4 amps at 100' and
14 ga. will give you 5.8 amps at 100'.

Of course you may be willing to withstand greater voltage drops.

(and yes, you get 5.33% voltage drop at 16A on 100' of #12: .4*16/120)

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5
Default Voltage drop

On Jul 10, 8:25 pm, (Doug Miller) wrote:
The maximum load on a 20A circuit is... any guesses? ...wait for it... 20A.


Just to be anal, the maximum load on a 20A circuit can be far greater
than 20 amps, at least for a short period of time. According to the
Trip Curves on the Square D web site, their QO series of breakers can
handle a 2x load (or in this case, 40 amps) for just under 10 seconds
before tripping.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Will my voltage drop? RayV Home Repair 15 September 6th 06 03:04 PM
Low voltage lights - voltage drop/cable size [email protected] UK diy 2 October 31st 05 09:54 AM
I need a reminder, what causes voltage drop.. alitonto Electronics Repair 9 February 17th 05 01:06 AM
Voltage Drop Under Load [email protected] Home Repair 12 January 12th 05 10:08 PM
Voltage drop switching relays? Joe in Bendigo Electronics 10 June 13th 04 06:59 AM


All times are GMT +1. The time now is 06:00 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"