I started a new thread on this because the old one was getting too
long. You can get the background he

http://groups.google.com/group/alt.h...9 bad0ef69ac0

http://groups.google.com/group/alt.h...ef f338195ed1

Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.

BUT...

The furnace it still losing pressure. Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.
Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?

Thanks for all the help so far.

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 746
Default Furnace saga continues

coustanis wrote:

I started a new thread on this because the old one was getting too
long. You can get the background he

http://groups.google.com/group/alt.h...9 bad0ef69ac0

http://groups.google.com/group/alt.h...ef f338195ed1

Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.

BUT...

The furnace it still losing pressure. Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.
Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?

Thanks for all the help so far.



This may verge on the drastic level, but consider
draining the system until just the boiler is full
(all piping empty).

Then pressurize the piping (and the boiler) with air.
Run it up to 30 psi. Over a couple of days you should
be able to get a feel for how much air is lost (or not).
Even a chance you could hear the air whistling out.

If it does lose pressure but you can't find where,
consider adding mercaptan to the compressed air so you
can smell the leak.

Jim
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default Furnace saga continues


"coustanis" wrote in message

Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.



Your connectors or your valve may have a leak also. Check them with a
bubble solution to be sure they are not part of the problem.


BUT...

The furnace it still losing pressure.


You don't have a furnace, you have a boiler. Furnaces heat air, boilers
heat water.


Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.


You are probably correct.


Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?


At least twice I've suggested you leave the valve open to be sure all the
air is purged. Have you tried that? Seems as though no. Another poster,
hvacmedic, also stated the valve should be open and gave a detailed
reasoning behind it all. Listen to the pro.


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Furnace saga continues

On Jun 18, 11:58 am, "Edwin Pawlowski" wrote:
"coustanis" wrote in message

Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.


Your connectors or your valve may have a leak also. Check them with a
bubble solution to be sure they are not part of the problem.



BUT...


The furnace it still losing pressure.


You don't have a furnace, you have a boiler. Furnaces heat air, boilers
heat water.

Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.


You are probably correct.

Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?


At least twice I've suggested you leave the valve open to be sure all the
air is purged. Have you tried that? Seems as though no. Another poster,
hvacmedic, also stated the valve should be open and gave a detailed
reasoning behind it all. Listen to the pro.


I believe it will overpressure if I do that but I will do it tonight.
If it over pressures I'll replace the auto fill valve and let you know
what happens.
I'll also get some detergent / water mix and check the connectors.
Thank you for the suggestions. I do appreciate it.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,300
Default Furnace saga continues

coustanis wrote:
I started a new thread on this because the old one was getting too
long. You can get the background he

http://groups.google.com/group/alt.h...9 bad0ef69ac0

http://groups.google.com/group/alt.h...ef f338195ed1

Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.

BUT...

The furnace it still losing pressure. Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.
Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?

Thanks for all the help so far.



Just out of curiosity, did you blow (or suck with a shopvac) the water
out of that loop before you pressurized it?

If not try doing so and see if your leakdown rate increases because air
can escape through a leak faster than water can be pushed out by air,
and you might, just might, be able to hear it hissing out.

It does sound like your worst fears will be realized and the leak is
buried under the concrete floor, so you'll have to replace the piping
with some above slab stuff.

Jeff

--
Jeffry Wisnia
(W1BSV + Brass Rat '57 EE)
The speed of light is 1.8*10^12 furlongs per fortnight.



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Furnace saga continues

On Jun 18, 11:58 am, "Edwin Pawlowski" wrote:
"coustanis" wrote in message

Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.


Your connectors or your valve may have a leak also. Check them with a
bubble solution to be sure they are not part of the problem.



BUT...


The furnace it still losing pressure.


You don't have a furnace, you have a boiler. Furnaces heat air, boilers
heat water.

Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.


You are probably correct.

Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?


At least twice I've suggested you leave the valve open to be sure all the
air is purged. Have you tried that? Seems as though no. Another poster,
hvacmedic, also stated the valve should be open and gave a detailed
reasoning behind it all. Listen to the pro.


A couple of weeks ago, either you or hvacmedic suggested a web site.
I looked for the thread but I guess it expired.
Would you mind listing it again? I could google but I want the one
you mentioned. It's probably a good site.
I want to read up on proper setup of the auto fill valve and air purge
valve.
For example, should the red cap on the air purge valve be open or
closed. I've kept it open so air can escape.

I know I'm probably getting teadious for you by now. Thanks for your
patience.

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Furnace saga continues

On Jun 18, 11:58 am, "Edwin Pawlowski" wrote:
"coustanis" wrote in message

Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.


Your connectors or your valve may have a leak also. Check them with a
bubble solution to be sure they are not part of the problem.



BUT...


The furnace it still losing pressure.


You don't have a furnace, you have a boiler. Furnaces heat air, boilers
heat water.

Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.


You are probably correct.

Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?


At least twice I've suggested you leave the valve open to be sure all the
air is purged. Have you tried that? Seems as though no. Another poster,
hvacmedic, also stated the valve should be open and gave a detailed
reasoning behind it all. Listen to the pro.


My plan for today is to set up the system properly.
To me that means:

Open the auto fill valve and check that it adds and closes at proper
pressure. Replace if necessary. It has a slide handle on
the side and a locking screw adjustment on the top. I have no idea
how to balance these out. I'll google but it's hasn't been much
help. My assumption is that the slider handle stays all the way open
and I adjust the open / close point with the screw on top. I'm sure
it's
out of adjustment because the screw turns somewhat freely. It wasn't
locked.

Pressurize the expansion tank to equal boiler pressure. I'll have to
go get another pressure gauge. My tire gauge doesn't read low
enough.

Set up the auto air purge valve. Is the red knob (escape vent) left
open or closed. If open, I can hear air hissing either in or out
depending on if
I am adding or removing water from the boiler. If closed, will it
purge?

I will continue to google this stuff but so far all I get is people
trying to sell me things.

Again, I appreciate your patience. If you ever get to Maryland, I'll
buy you a beer or 6.

  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Furnace saga continues

On Jun 18, 11:58 am, "Edwin Pawlowski" wrote:
"coustanis" wrote in message

Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.


Your connectors or your valve may have a leak also. Check them with a
bubble solution to be sure they are not part of the problem.



BUT...


The furnace it still losing pressure.


You don't have a furnace, you have a boiler. Furnaces heat air, boilers
heat water.

Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.


You are probably correct.

Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?


At least twice I've suggested you leave the valve open to be sure all the
air is purged. Have you tried that? Seems as though no. Another poster,
hvacmedic, also stated the valve should be open and gave a detailed
reasoning behind it all. Listen to the pro.


I took off work today to mess with this.

I replaced the boiler feed valve. The old one had the adjustment
screw loose and it was easier to spend 40 bucks on a new one that
was factory set. When I took the old one off I saw that it was heavily
damaged by electrolysis. Some of it's internal parts fell out through
the fitting
holes.
After install I left the new one in the auto position with the
isolation valve open as was suggested.

I verified that the expansion tank was good by checking that air, not
water came out of the snifter valve and that it's pressure equaled the
boiler pressure.

I isolated the entire second floor of the house by cutting and
capping. I know this sounds extreme but it only required two cuts and
two caps.
Total time for that was 10 minutes and 3 bucks. This allows me to
have no pipe connected to the boiler except what I can directly see.

Closed the air purge valve at the top of the system.

I filled he system to 20 psi. The feed valve kicks in at 12 psi.
If it maintains 20 then I fixed it. If it drops to and holds 12 then
I assume I still have a leak somewhere
although I can't imaging I have a leak that I can't see, at this
point.

Nothing to do now but wait a week and see what happens.

Look folks, I know I've been a pain in the ass with this. I get that
way when confronted with expensive things I don't understand.
I learned a lot and saved a pile of money. I needed to learn this
system. I couldn't go and spend a hundred bucks an hour every time
the system burped
or did some weird thing.

I do appreciate the patience and the advice.
The offer for beer still stands.



  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Furnace saga continues

On Jun 19, 11:17 am, coustanis wrote:
On Jun 18, 11:58 am, "Edwin Pawlowski" wrote:



"coustanis" wrote in message


Ok, the room that has the radiator pipes in the concrete slab has been
isolated and I put about 22 pounds of compressed air into it. After 4
or 5 days it had lost most of the pressure. In a day or so it will
probably be empty.
I assume then that there is a leak in that room unless there is some
other furnace phenomenon that would cause a system to not hold
compressed air. Since I don't see any water I assume it's in the
concrete pad.


Your connectors or your valve may have a leak also. Check them with a
bubble solution to be sure they are not part of the problem.


BUT...


The furnace it still losing pressure.


You don't have a furnace, you have a boiler. Furnaces heat air, boilers
heat water.


Since all the pipes are either
visible or within the walls if this wood and sheetrock
house, I would assume that if there were an additional leak that I
would see a wet wall, a puddle or water dripping from a ceiling. I
see no water.


You are probably correct.


Someone in a previous thread said it could be a bad expansion tank.
The expansion tank is brand new and was installed after this pressure
problem started. The auto feed valve is closed and has always been
so, even when the system was not losing pressure. I'm not sure what
to do next or what to check. I can isolate another loop but I'm
wondering if it's a leak at all in this part.
Does anyone have any ideas?


At least twice I've suggested you leave the valve open to be sure all the
air is purged. Have you tried that? Seems as though no. Another poster,
hvacmedic, also stated the valve should be open and gave a detailed
reasoning behind it all. Listen to the pro.


I took off work today to mess with this.

I replaced the boiler feed valve. The old one had the adjustment
screw loose and it was easier to spend 40 bucks on a new one that
was factory set. When I took the old one off I saw that it was heavily
damaged by electrolysis. Some of it's internal parts fell out through
the fitting
holes.
After install I left the new one in the auto position with the
isolation valve open as was suggested.

I verified that the expansion tank was good by checking that air, not
water came out of the snifter valve and that it's pressure equaled the
boiler pressure.

I isolated the entire second floor of the house by cutting and
capping. I know this sounds extreme but it only required two cuts and
two caps.
Total time for that was 10 minutes and 3 bucks. This allows me to
have no pipe connected to the boiler except what I can directly see.

Closed the air purge valve at the top of the system.

I filled he system to 20 psi. The feed valve kicks in at 12 psi.
If it maintains 20 then I fixed it. If it drops to and holds 12 then
I assume I still have a leak somewhere
although I can't imaging I have a leak that I can't see, at this
point.

Nothing to do now but wait a week and see what happens.

Look folks, I know I've been a pain in the ass with this. I get that
way when confronted with expensive things I don't understand.
I learned a lot and saved a pile of money. I needed to learn this
system. I couldn't go and spend a hundred bucks an hour every time
the system burped
or did some weird thing.

I do appreciate the patience and the advice.
The offer for beer still stands.


Which doesn't change the fact that I have a leak in the pipe under the
concrete slab but, that's a separate issue I'll deal with that later,
after I get the main system set up properly.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,823
Default Furnace saga continues


"coustanis" wrote in message
I took off work today to mess with this.

I replaced the boiler feed valve. The old one had the adjustment
screw loose and it was easier to spend 40 bucks on a new one that
was factory set. When I took the old one off I saw that it was heavily
damaged by electrolysis. Some of it's internal parts fell out through
the fitting
holes.
After install I left the new one in the auto position with the
isolation valve open as was suggested.


If the valve was not part of hte problem, it certainly was ready to fail.
Smart move to replace it now.



Closed the air purge valve at the top of the system.


Is al lthe air purged?



I do appreciate the patience and the advice.
The offer for beer still stands.



Real beer, none of that "lite" crap. We don't drink cheap beer either.




  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 35
Default Furnace saga continues

On Jun 19, 11:42 am, "Edwin Pawlowski" wrote:
"coustanis" wrote in message
I took off work today to mess with this.


I replaced the boiler feed valve. The old one had the adjustment
screw loose and it was easier to spend 40 bucks on a new one that
was factory set. When I took the old one off I saw that it was heavily
damaged by electrolysis. Some of it's internal parts fell out through
the fitting
holes.
After install I left the new one in the auto position with the
isolation valve open as was suggested.


If the valve was not part of hte problem, it certainly was ready to fail.
Smart move to replace it now.



Closed the air purge valve at the top of the system.


Is al lthe air purged?

Probably not. I'll purge it manually every day or or so until no more
air escapes.

I do appreciate the patience and the advice.
The offer for beer still stands.


Real beer, none of that "lite" crap. We don't drink cheap beer either.


Not a problem. I'll go as heavy as you like.
And as much as you like.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
THANK YOU! (Apollo saga continues) Renata Woodworking 1 November 16th 06 11:22 PM
Door 'saga' continues..... Chas12 Woodworking 4 April 7th 06 01:07 AM
Encoder saga continues Eric R Snow Metalworking 0 September 28th 05 05:49 PM
Electrical Saga Continues Ryan Home Repair 17 July 21st 05 11:30 AM
ctc177 saga continues... :) Ken Weitzel Electronics Repair 3 March 20th 04 04:19 AM


All times are GMT +1. The time now is 03:05 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"